T.R | Title | User | Personal Name | Date | Lines |
---|
83.172 | Pilot keeps going out | ECAD::SCHIPANI | | Thu Nov 06 1986 12:39 | 17 |
| We have a furnace about 18 yrs old made by Johnson Controls.
It is gas with a blower motor. The problem I have is that with
the temperature set between 62-65 it will come on several times
in the middle of the night, and when the flame goes off, it will
sometimes suck the pilot flame out. The Gas co has beenout three
times, and cannot find what causes it. It has done it while they
watch. It doesn't do it at any other temperature setting.
They replaced the cupler, and the part where the gas comes out on
the pilot, and checked the thermostate. Nothing.
Anyone have this occur? Any ideas would be helpful.
Hope I've explained this clearly
thanks
Gary
|
83.173 | Draft Control Widget | POP::SUNG | Al Sung (Xway Development) | Thu Nov 06 1986 13:45 | 9 |
| Maybe you need one of those draft control devices that goes on the
flue (or maybe it just needs an adjustment).
Probably what is happening is that the remaining hot air in the
flue is causing a suction within the burner unit. What you want
to happen is have the suction open the draft control and suck
the air out of the basement.
-al
|
83.174 | ask them to look at the air valve | THEHUT::TAYLOR | | Thu Nov 06 1986 15:14 | 12 |
|
I had a similar problem last year. I have both a gas fired boiler
and gas water heater. Some times one went out and somtimes they
both would. There is a valve directly off of the meter which allows
some air to mix with the gas and on this valve there is an air inlet
pipe which extends out side through the wall. Our problem was that
the air inlet pipe, which is threaded, was pushed down allowing
water to enter the air valve. This water caused the valve to
malfunction.
wayne
|
83.175 | finally?? | ECAD::SCHIPANI | | Mon Nov 17 1986 15:52 | 12 |
| Well, the gas co. came out for the 4th time last week. This time
the supervisor came along. I think they finally have it.
The last guy opened the dampers too much, put in the wrong size
coupler, and had the pilot too low and the gas too high. Not bad
huh?
He actually made the problem worse. However, it's been fine for
a week, knock on wood.
Thanks for the advise.
Gary
|
83.176 | | ESTORE::GELLER | | Fri Dec 12 1986 16:30 | 6 |
| I've had problems with the pilot light going out in a gas furnace.
There were two reasons for this happening:
- The gas company made a fresh batch of "natural gas" and the
pressure surge caused the pilot to go out
- I had a defective thermocouple. When it was replaced the problem
went away.
|
83.177 | I wanna watch... | NEXUS::GORTMAKER | | Tue Dec 16 1986 00:16 | 7 |
| How does the gas company make a fresh batch of gas?
Natural gas is just that it is in a gasious state when produced
from the ground.
Also the pilot light should have an orfice to limit the flow
preventing a pressure surge for blowing it out.
-j
|
83.178 | | VINO::KILGORE | Wild Bill | Tue Dec 16 1986 09:16 | 15 |
|
re .5
Natural gas is shipped and stored in a liquid state. Before final
distrbution, it is allowed to expand to a gaseous state. Perhaps
.4 was referring to the utility's process of gasifying the gas
as 'mixing a new batch'. Also, being a product of nature, natural
gas can vary greatly in thermal energy content. The utility might
have been blending different batches to produce a mixture with some
standard therm value.
An orifice meters gas to a flame, assuming that there is constant
pressure on the supply side. A pressure surge would not be controlled
by the orifice, and could blow outh the flame. The pressure regulator
at the gas meter should take care of surges from the utility,
establishing a constant pressure within the house pipes.
|
83.179 | They DO MIX natural gas! | NETCOM::HARRIS | Mark Jay Harris, Term Srvr Mktg Mgr | Tue Dec 16 1986 09:24 | 6 |
| The utility also adds some type of ODOR to the natural gas as
it has little if any SMELL when it comes from the ground
as TRUE NATURAL GAS. The ODOR addition is a safety precaution.
Maybe this is the 'mixing' referred to.
M
|
83.180 | corrected facts. | NEXUS::GORTMAKER | | Wed Dec 24 1986 21:20 | 19 |
| I based my question on what i have learned from my father whom is
an eng. for the local gas company.
Natural gas is in liquid form only for overseas shipping and is
not kept in a liquid state by utility companies the cost of doing
so would be far too high. Instead the popular method for storage
is underground in rock and pumped out to meet demand.
The problem sounds like a regulator the pressure should be 3 1/2
inches of water.
BTW- the oderant is added constantly and is metered into the gas
in the distribution lines. It is very highly concentrated and
a half cup poured onto the ground is enough to produce a "gas smell"
covering about fifty square miles. Natural gas may/maynot have a
smell of its own before adding the oderant it all depends on such
thing as sulfur content,ect.
I stand corrected on the orfice it would do little to prevent pressure
surges from causing the flame to"pop out". Thats what i get for
twisting details in my mind.
-j
|
83.163 | Pilotless Retrofit Ignitions for Gas Appliances | USFHSL::SONNTAG | Steve Sonntag | Tue Jan 06 1987 15:30 | 24 |
| After having read all of the other topics concerning
furnace and water heater questions, a question that I
have is yet to be asked.
This may fall on a lot of deaf ears in New England (due
to the high percentage of oil users), but I have
confidence that a lot of you have gas, also. :^)
Here in Michigan, I have FHA by gas and a gas water
heater. Both of the burners have pilot lights. Now,
for the question: Have any of you ever heard of a
retrofit that can be installed to make them pilotless
ignition?
A recent state law mandates that all new gas burner
units must be pilotless, so I know that I could buy a
new furnace and WH. However, I think that this would
be an unneccessary expense, considering the reasonably
good condition of my current units. I just want to get
a little better efficiency by not burning gas during
the "off" times.
Thanks for your help,
SAS
|
83.164 | | BPOV09::SJOHNSON | Steve | Tue Jan 06 1987 15:43 | 17 |
|
Steve,
The Jan.'87 issue of Consumer Reports had a write-up on super efficient
heating and hot water heating systems, and I know they talked about
pilotless systems. I'll check the article, and reply again.
I do remember though, that you can purchase heating systems with
efficiency ratings in the 90's. But you have to PAY for efficiency,
unit costs are on the order of 3 times that of regular systems.
CU also gave a formula you could use to calculate if it would be
cost effective for someone to buy one of these, or how long it
would take to be cost effective.
Steve
|
83.165 | YES | DRUID::CHACE | | Tue Jan 06 1987 15:57 | 6 |
| I have seen kits to refit gas furnaces to pilotless ignition. i
can't tell you where to look since I'm from Mass. Also, the kits
may not be available for every brand of furnace. I believe that
it's not possible to refit a gas water heater. (can't imagine why)
Kenny
|
83.166 | the worry wart asks | REGENT::MERRILL | If you've got it, font it. | Wed Jan 07 1987 08:46 | 6 |
| How does "pilotless ignition" work? Does it require electricity?
What if the electricity/battery fails?!
Rick
Merrill
|
83.167 | Not to worry | CHAMP::KEVIN | Kevin O'Brien | Wed Jan 07 1987 12:43 | 5 |
| I have a pilotless gas furnace. The starter is electric. If the
power fails (or if it's shut off) there is no demand for heat so
the furnace doesn't try to start.
KO
|
83.168 | Some places, it's cheaper to keep the pilot | CLOSUS::HOE | | Mon Jan 12 1987 17:46 | 20 |
| Re: How it works.
Pilotless system is based on a pizeo-electric igniter. The system
is actuated with a solenoid, striking the pizeo element. In turn,
the pizeo crystal oscillates and generates a 2 to 5 kilovolt spark
that ignites the natural gas (much like the spark plug in your car).
I am not totally how the pizo-electric works. The pilotless gas
stove has a clicking sound when it starts to ignite the surface
element. I believe that the thermostat actuates a electric gas valve
that turns on the gas for the igniter to work.
In California, by turning off the pilot gas, we saved about $5.00
per gas appliance (water heater, stove, oven, and furnace). We usually
turned off the pilots to the stove and the furnace from April through
mid-October. Here in Colorado, we leave the pilot on the furnace
on. I'd like to install a pilotless system on the Lennox furnace
that we have, when I find one.
/cal hoe
|
83.169 | Glow coil units | MAY11::WARCHOL | | Tue Jan 13 1987 09:20 | 11 |
| Not all pilotless systems are pizeo-electric (sp?) based. The new
Amana high efficiency furnaces use a glow coil. The glow coil turns
bright orange while heating (actually lights up the basement a little)
and a circuit senses the temperature of the coil. When the coil
is hot enough the gas is turned on.
I just took out my old gas fired hot air furnace an put in one of
these Amana units. Very nicely made. My father, who installs furnaces
for a living, is even impressed with them.
Nick
|
83.170 | Retrofit IIDs & flue dampers | CAM2::BLESSLEY | Life's too short for boring food | Thu Jan 22 1987 17:07 | 9 |
| Retro-fit IID's (intermittent ignition devices) are not approved for use in
Massachusetts. I have FHA by gas too, and just went from a piloted furnace to a
pilotless one with flue damper. Payback is mighty long, but the old furnace was
noisy and too small to heat the whole house.
Flue dampers are only permitted on furnaces designed for them, that have a
double-interlock to ensure that no gas flows if the damper is closed.
-scott
|
83.171 | intermittent pilot systems | CLOVAX::MARES | | Tue Mar 10 1987 12:26 | 30 |
| W.W.Graingers, a national distributor, carries two types of gas-pilot
to electric-light conversion systems:
1. Dayton gas pilot ignition system (WWG stock # 2E563/2E564) for
price range of $182 to $234. They use 24V control with pilot
flame burning only during periods when heating system thermostat
calls for heat. A solid state igniter is used. Kit includes
pilot igniter, electrode assembly, ignition cable with connectors,
plug-in pilot switch and flame sensing element, 3/4" x 3/4"
335,000 BtuH dual gas valve gas control, 1/2" bushings, 3/8"
bushings and misc hardware.
2. Honeywell intermittent gas pilot system -- uses gas only when
system calls for heat; is lit by high voltage capactive discharge
spark, turns off automatically when demand for heat is satisfied.
Includes prewired intermittent pilot module; universal igniter-
sensor assembly, 1/2" x 3/4" high-capacity dual valve gas control
with reducer bushings, ignition cable and misc hardware. Prices
range from $220 to $284, depending on natural, LP, full off/on
models.
BTW, sounds like you folks in MA have a lot of strange laws to cope
with when DIYing. Guess I won't consider transferring there.
Happy in Cleveland with the Lake that is Erie
Randy
|
83.71 | Furnace Hookup to New Room | 3D::BOOTH | Stephen Booth | Mon Jul 13 1987 09:34 | 11 |
|
I have an oil forced hot air system that I want to hook up to
my new addition. I already have the ducts in the new room but I'm
unsure how to hook to my furnace. There is a heating pipe going
right past the new duct. Can I buy a Y pipe and connect to it or
should I go directly to the furnace housing. I have never seen a
Y connector so I'm assuming there not made or that is the incorrect
way.
-Steve-
|
83.72 | | MAY11::WARCHOL | | Mon Jul 13 1987 11:09 | 15 |
| Depending upon how the rest of the system is set up you might be
able to get away with cutting it into the side of the existing
supply duct. Chances are that you could unbalance the air distribution
to the other rooms. It is very hard to determine this without
seeing the whole system. I'd suggest running the new duct back to
the supply chamber on top of the furnace if you're not sure.
If you've never done this type of work before you probably won't
have the tools that you need to metal ductwork with. They are pretty
special purpose and not readily available. Why not have a sheet
metal shop come over and give you an estimate?
Nick
(ex-sheetmetal mechanic)
|
83.1 | Also need a new furnace | PATSPK::PAGLIARULO | | Mon Sep 14 1987 22:24 | 9 |
| I'd like to try reopening this note.
I had the gas company out today to check out my FHA furnace before
the heating season starts and found out that my heat exchanger is
cracked to the point that you can see the flame inside the tubes.
Since this can add nasty things like fumes like carbon monoxide
to the circulating air I'm also now in the market for a new furnace.
Anyone have any ideas on what things I should look for in a new
furnace? Is installation something for the DIY'er (it's natural gas)?
|
83.2 | Practical Homeowner | AKA::SUNG | In search of a personal name | Tue Sep 15 1987 14:34 | 4 |
| The latest issue of Practical Homeowner has a section on high
tech furnaces. They seem to like the Lennox Pulse.
-al
|
83.3 | Heil or Magic- Chef | NISYSG::PAGLIARULO | | Mon Sep 21 1987 09:07 | 10 |
| I went out and looked at furnaces this weekend. The two I'm
considering are a Heil and a Magic Chef. My current furnace is
a 100,000 BTU but since I'm going to add heat to the basement I'm
going to upgrade to a 125,000. After seeing the prices on them
I've decided to not go with the extra cost of the high-efficiency
units. For almost 1/2 the price I can get a unit with 78% efficiency
vs the 95% of the high efficiency unit. It would take a long time to
save enough for the unit to pay for the difference. The 2 furnaces
I'm considering are a Heil and a Magic Chef. Anyone have any
experience with either of these?
|
83.4 | | 3D::BOOTH | Stephen Booth | Tue Sep 22 1987 16:20 | 5 |
|
I have a Magic Chef 125,000 BTU that was installed about 1 year
ago. Works OK.
-Steve-
|
83.7 | Gas FHA Fan Limit Controls | LOONMT::PAGLIARULO | | Fri Oct 23 1987 13:39 | 25 |
| I have a question about adjustments on a FHA gas furnace.
I just finished installing a gas FHA furnace and everything is working
fine except that the air that reaches the living spaces doesn't
seem to be very warm. I slowed down the blower speed but that didn't
seem to help to much. I think the problem is that the fan is going
on too early and not allowing the heat exchangers to really heat
up. When I looked at the installation manual it said to adjust
the fan limit controls to a satisfactory comfort level. Just below
that in big highlighted letters it said "CAUTION, FAN LIMIT CONTROLS
ARE PRESET AT FACTORY - DO NOT ADJUST" Arrggghhhhh.....
These controls are the ones that set the temperatures that the fan
goes on and off at. The only danger I can see is that the "on" control
is set so high that the fan comes on only after the unit has gotten so
hot that it is a fire hazard. With this in mind I adjusted the
control so that the fan comes on at 130 degrees. That helped a
lot and the air coming up through the ducts is a lot better but
still could be a little warmer to my liking. How high can the "on"
temperature be set and still be safe? Is there something I'm missing
and should I just leave these controls alone?
Thanks,
George
|
83.8 | how it works (I think) | MORMPS::WINSTON | Jeff Winston (Hudson, MA) | Fri Oct 23 1987 15:45 | 33 |
| I just went through this on my system - there are really 4 settings to
play with:
3 On the furnace: (in increasing order)
fan-off temp
fan-on temp
furnace-off temp.
WHen the thermostat calls for heat, the furnace comes on, when it
reaches fan-on temp, the fan comes on, when it passes furnace-off
temp, the gas turns off untill the temp falls back below furnace-off
(I think). When the thermostat shuts off, the fan runs until fan-off
temp is reached before shutting off the fan.
My settings are
fan-off temp 100F
fan-on temp 150F
furnace-off temp. 250F <-cannot be increased - anyone know why?
This seems to work adaquately well.
4) On the thermostat is a hysteresis control - I had a problem in that
this was set too fine - so that by the time the fan came on, the
thermostat stopped calling and the burner shut off - thus cold air
thru the ducts. I've been told this has to be 'matched' to the
current rating (in amps) provided by furnace - but this usually gives
too tight a range for me - you might want to try increasing the
hysteresis until you feel its running comforably - that's what I had
to do.
Other comments? I'm still futzing with mine /j
|
83.9 | Ulitmate goal = Economy! | TUNER::DINATALE | | Fri Oct 23 1987 16:30 | 15 |
| Re .1
1> fan-off temp 100F
2> fan-on temp 150F
3> furnace-off temp. 250F <-cannot be increased - anyone know why?
1) 100F leaves a lot of heat still in the furnace/ducts. I adjusted
the fan-off switch at about 75F. Works fine, puts more usable heat
where we need it.
3) I don't know. Is this a trick question??
Richard
|
83.10 | keep the air moving | BSS::HOE | | Fri Oct 23 1987 18:50 | 18 |
| If your furnace is one of the high efficiency ones, the fan comes
on early to get air circulating through the air preheat (from the
exhaust heat recovery) before the air is passed through the heat
chamber.
Other problems are the length from the furnace to the air registers.
There is a volume of air that has to be moved out of the ducts before
the heat comes through. I have a fan control switch to keep my blower
on so that air is always moving through my furnace, hot or cold.
I have an electronic filter and a hudmidifier in the furnace and
the air movement keeps the amount of cold air in the duct at a minimum.
The fan speed control is one of the types used for the ceiling fans,
and I hooked it to the slowest speed of a four speed furnace blower
motor. You will find that filtering the air with air filters will
reduce the amount of dusting that you or your spouse have to clean.
/cal hoe
|
83.11 | want to make heat hotter | MORMPS::WINSTON | Jeff Winston (Hudson, MA) | Fri Oct 23 1987 22:11 | 20 |
| >Re .1
>
>1> fan-off temp 100F
>2> fan-on temp 150F
>3> furnace-off temp. 250F <-cannot be increased - anyone know why?
>
>
> 1) 100F leaves a lot of heat still in the furnace/ducts. I adjusted
> the fan-off switch at about 75F. Works fine, puts more usable heat
> where we need it.
>
> 3) I don't know. Is this a trick question??
These setting reflect the position of stops on a mechanical
thermostat. Accuracy of 25% not guaranteed. (The air is cool when
the fan shuts down).
Not a trick question - I'd like to defect the 'lock' and push it up
hotter - question is - what is my risk (house fire?)
|
83.5 | DIYer gas furnace installation | DECWET::FURBUSH | EF Hutton says: #@%$! | Sun Oct 25 1987 21:12 | 6 |
| I'm considering replacing my electric furnace with a gas one. The
gas company quoted a price of around 5K (installed). This is a
"little" too high for me.
Has anyone had any experience installing a gas furnace? What does
a typical high-efficiency gas furnace cost?
|
83.12 | | NISYSG::PAGLIARULO | | Mon Oct 26 1987 07:42 | 7 |
| I believe that one problem you would have is shortened life on the
heat exchangers by letting them get too hot. The metal gets pretty
brittle after a while. The return duct on my old furnace was about
1/3 of the size it should have been so I didn't get enough air
circulation. Differrent problem but same result - heat build-up.
The heating people I spoke to believe that this played a big part in
the exchagers cracking.
|
83.13 | DON'T TOUCH THAT SETTING! | XANADU::SCHNEIDER | Dennis Schneider | Mon Oct 26 1987 14:11 | 79 |
| I'd be wary of fiddling with the burner shutoff temperature. If you screw
up, you could get lucky and at MOST damage the furnace; if you DON'T get
lucky, you could cause a fire - and it'd be intriguing to see if your insurance
company will pay up given you have mucked with a control marked "DO NOT
MUCK WITH ME".
Does the air EVER get warm at the register you are referring to?
If NOT, you should consider insulating the ducts (as long as air coming
out SOMEWHERE gets hot).
If it eventually gets hot, then the issue isn't with the furnace fan, it's
the duct's contents of cool air you're feeling. Even the coolest fan-on
setting should ship air that feels "warm". Air that's just moving at ambient
temperature feels cool.
An earlier note mentioned keeping the fan on at all times as one way to
make things more comfortable. Some more experience:
I have a humidifier and an electronic air cleaner on my furnace. I recommend
both highly. The humidifier comes with a humidistat (humidity sensing switch)
that installs in the return air plenum, senses return air humidity, and
switches on the humidifier when humidity is needed. I added a pair of relays
to make the following change: Whenever the humidity sensed is too low, Turn
On the furnace blower at it's slowest setting UNLESS it's already running.
Note that most furnace fan motors have several "speeds" (windings) that
you can chose from, so you may not need to consider a speed control. the
wiring "looks" something like
*----------* *----* Humidifier ---*
|Humidity | | |
|Sensor |-----*----* Relay #1 Coil *------Neutral (WHITE)
|(Closes |
|if too dry|---------------------------------110V (BLACK)
*----------*
*----------*
|Blower |
|High Speed|---------* Relay #2 Normally OPEN contacts *------110V (BLACK)
|Winding |
*----------*
*----------*
|Blower |
|Low Speed |-* Relay #1 Normally OPEN contacts *
*----------* |
*Relay #2 Normally CLOSED*
Contacts |
|
110V
*----------*
|Present |
|Furnace |---------* Relay #2 Coil *------------------------Neutral (White)
|Connection|
|to Fan |
*----------*
I used two 110V-coil relays - #1 is Single Pole Single Throw (SPST); #2
is Double Pole Double Throw (DPDT) rated at 15A (more than enough for the
motor windings; same ratings as those in the furnace).
What all that does is lets the humidistat turn on the furnace fan at its
lowest fan setting whenever the house needs humidity, but allows the fan
to run at its high setting - the humidifier runs whenever it's needed at
either fan speed.
Relay #1's job in life is to "know" that humidity is called for; relay 2's
job in life is to decide whether the furnace fan should run at High Speed
(the furnace wants the fan on) or Low Speed (only the humifier wants the
fan on). Relay #2 also prevents both fan windings from being energized at
once.
I have tried keeping the blower on at slow speed at all times - costs mucho
bucks in KWH.
Dennis
|
83.14 | run humidifier when fan is off? | ZEN::WINSTON | Jeff Winston (Hudson, MA) | Mon Oct 26 1987 22:01 | 13 |
| Note - many of the multi-speed fans draw the same energy regardless of
speed. They just run less efficiently at the lower speeds. -
I was thinking of doing the reverse of what you mentioned - my
humidifier (on my central FHA system) runs continually, governed only
by the humidistat. My heat is OFF for several hours each day, and
turned down quite a bit at night. This suggests that the humidifier
will run for a great deal of time when the fan is off - does this do
me any good? any harm? Was thinking of wiring it so the humidifier
runs ONLY when the fan is on - ?????
/jeff (who has left the max temp of his
furnace at factory setting)
|
83.15 | RE:.-1 | XANADU::SCHNEIDER | Dennis Schneider | Tue Oct 27 1987 08:52 | 11 |
| I'd guess that running the humidifier with the furnace fan off would do
a heck of a job of getting the ducts wet - do you have a belt-type/evaporative
humidifer or is it a mist-type? If it's the mist type, you probably ought
to wire it in to the furnace fan circuit so it won't soak the ducts. If
it's evaporative, it's less of an issue - all it will do is raise the humidity
in the ductwork near the unit.
Either way, not much point in running it when the fan's off....
Dennis
|
83.16 | High Limit Shouldn't be Reached | AKOV11::COLES | | Wed Oct 28 1987 13:46 | 45 |
|
---> From .1 <---
> When the thermostat calls for heat, the furnace comes on, when
> reaches fan-on temp, the fan comes on, when it passes furnace-off
> temp, the gas turns off untill the temp falls back below furnace-off
> (I think). When the thermostat shuts off, the fan runs until fan-off
> temp is reached before shutting off the fan off.
If your FHA system is working properly, the burner should never
get turned off on account of the furnace-off temperature being reached.
(This may not be the case for the pulse-type systems, I don't know.)
The circulating air should keep the heat exchanger temperature below
the furnace-off temperature. The burner should only have to turn
off when the thermostat's demand is satisfied. The high-limit
(furnace-off) should only come into play if:
1) The fan never came on.
2) Insufficient return air is available.
3) The hot air has nowhere to go, registers shut.
4) For any reason the burner is generating more heat than
the fan and/or rest of the system can deal with.
The settings for my FHA system are:
Fan-on: 120 <--- Fixed, can't be adjusted. Also has
a timer that will turn the fan on in case
the temp. sensor in the switch fails.
Fan-off: 110 <--- Adjustable with a screwdriver at the fan-limit
(Low-Limit) switch.
Furnace-off: 220 <--- Fixed, can't be adjusted. The heat
(High-Limit) exchangers in home FHA systems frequently
have a maximum operating temp. of 200.
I recently had the fan-limiter (camstat) replaced on my FHA furnace.
Its problem was that the fan-off (low-limit) took forever to shut the fan
off; once it came on it would run for hours or until I killed
the power to the furnace. The Gas Company tried 4 new switchs with
adjustable high-limit off controls. None of them (same kind) worked.
In each case the furnace burner would cycle on for 1 min. then off for
1 min. then on for 1 min. etc... until the thermostat's demand for
heat was satisfied. What was happening was that the high-limit
circuit was getting energized even though the temperature was still
below the high-limit. The switch they tried last worked. It had a
fixed high-limit (like the one they were replacing except the new
switch's high-limit was 220 while the old switch's high-limit was 240).
|
83.17 | re -.1 | MORMPS::WINSTON | Jeff Winston (Hudson, MA) | Thu Oct 29 1987 12:30 | 6 |
| Well...this is the 3rd place I've lived with FHA heat, and on all of
them the burner would cycle (though with low frequency) when the fan
was on - but only if you were calling for heat for a while.
I think some systems may be designed this way (energy efficient?
faster heating?)
|
83.18 | I'll throw another two furnaces into that list | STAR::SWIST | Jim Swist ZKO1-1/D42 381-1264 | Thu Oct 29 1987 13:46 | 0 |
83.19 | six and counting | PLDVAX::TRANDOLPH | | Mon Nov 02 1987 12:35 | 4 |
| Make it six - the apartment on the first floor of the building I'm
in has gas FHA. Their furnace is in the basement, where I am, so
I can hear it - the burner cycles on and off while the blower runs.
-Tom R._who_will_have_wood_and/or_FHW_in_his_half_of_the_new_duplex
|
83.6 | Shouldn't be too difficult | TLE::WILD | Joe Wild: LSE Developer | Thu Nov 05 1987 14:21 | 28 |
|
5K seems pretty steep, especially if the ductwork is already in place. I
just replaced an old steam boiler (oil) with FHW (gas) and in the process
looked into gas furnaces. I think the higher efficiency models (100K BTU)
cost around $1000. You should probably get a few more estimates
before making any decisions. I was quoted a 6K figure by the Nashua, NH
gas company and that included replacing the entire boiler and all the
the pipes and radiators.
Anyway, I think it should be fairly easy to replace a furnace yourself. I
found a couple of places, Total Air Supply and Masi's, in Nashua that would
sell me a furnace and ductwork along with a plan of how it should be all
layed out. If you are inexperienced at this like I am, it is important to
purchase your furnace from some place that will be able to answer your
questions. It may be necessary to have some custom ductwork built to
connect the new furnace to the present ductwork.
A couple of other things to think about are wiring the furnace and running
the gas lines. I hired someone to do them for me due the fact that it was
getting cold and I was running out of time. Another problem for you may be
the chimney. If you don't have a chimney available, I suggest the very high
efficiency furnaces that can be vented through an outside wall with PVC
pipe.
Good luck,
Joe
|
83.159 | Electronic Ignition and Power Losses | SALEM::PAGLIARULO | | Tue Jan 05 1988 07:44 | 13 |
| Sunday the power in my section of Nashua went of twice. It
was only a couple of minutes each time but it was long enough for
me to realize that even though I have gas heat my nice new FHA
burner with the electronic start is useless with no power. Does
anyone know if it's possible to hook up some sort of external power
source like a battery to handle such emergencies? I realize a
generator would be a perfect answer but I don't want to spend that
much money and all I really want is enough power to keep the furnace
going.
Thanks,
George
|
83.160 | | 3D::BOOTH | Stephen Booth | Tue Jan 05 1988 08:27 | 12 |
|
It would cost more for the batteries and converter then it would
for a good Honda generator. The batteries you need are called Deep
Charge Marine batteries which cost about $100 a piece. I can just
imagine how many you would need. A furnace has a capacitor type
start system which requires a surge of electricity to get the burner
going. The converter would be very expensive also.
-Steve-
|
83.161 | Alternate heat | PSTJTT::TABER | Transfixed in Reality's headlights | Tue Jan 05 1988 08:46 | 5 |
| Besides, it probably wouldn't be useful (or maybe even safe) to have the
burner cut in on your FHA furnace when you have no power for the
blowers. You need a generator or a woodstove to see you through those
power hits.
>>>==>PStJTT
|
83.162 | generator a good idea | BINKLY::WINSTON | Jeff Winston (Hudson, MA) | Tue Jan 05 1988 22:42 | 8 |
| Just bought a Honda generator for exactly the same reason. One
problem with FHA is that the furnace fan STARTING current can be like
15A. Elsewhere in this file (check 1111.x under electrical) is a note
on generators, and a more detailed one in OVDVAX::ELECTRO_HOBBY.
In a word - you can get industrial (read noisy, need some expertise)
generators for as low as $400, or idiot-proof Honda generators for
about $800.
|
83.76 | Sealing gap next to furnace | LABC::FRIEDMAN | | Thu Feb 04 1988 14:31 | 18 |
|
I have a central-heating gas furnace. It is installed in a closet.
(I live in the Los Angeles area, so the furnace is small.)
The furnace is held off the floor by a plywood board. Part of the
furnace is below this platform and part of the furnace is above
this platform. Thus the furnace passes through the wood board.
However, the wood board does not fit snugly around the furnace.
There is gap in one area. The gap measures about 1" x 12". The gas
company says I must seal this gap, or carbon monoxide could get
into the house.
They say I need to cut a piece of wood the size of the gap and somehow
fill up the gap with it. Now, if the piece of wood is slightly
smaller than that size, the piece will just fall through to the
floor. On the other hand, if the piece of wood is slightly larger than
the gap, it won't fit in the gap. What is my best strategy for closing
the gap? Make the piece of wood slightly smaller than the gap and
smother the edges with glue?
|
83.77 | one way | BINKLY::WINSTON | Jeff Winston (Hudson, MA) | Thu Feb 04 1988 17:26 | 2 |
| make it slightly smaller, put a metal brace or 2 under it (or over it)
to hold it there, and fill the cracks with caulk or mortite
|
83.78 | Furnace filter clearance??? | 29105::HOE | from Colorado with love! | Fri Feb 05 1988 12:10 | 10 |
| Before you seal off the gap, check to see about access to your furnace
filter. My girl-friend's house in San Jose was built on a slab and
the furnace was mounted just as you described, with the cold air
return underneath. The burner area was seperated from the air return
area with the same gap so that we could get the filter out. I believed
that the furnace was modified by the contractor to fit the house.
If you close off the gap, make it removeable.
/cal
|
83.21 | old Gas FHA Furnace unsafe non-obviously? | BINKLY::WINSTON | Jeff Winston (Hudson, MA) | Thu Sep 22 1988 00:43 | 16 |
| "Mr. Moderator" (e.g., Paul, DCL) _ I checked 1111.35 and couldn't find a good
home for this. Please correct me if I'm wrong. If its a real concern, it
might be worth a new note anyway? Thanx /jeff
================================================================================
I <thought> my gas FHA furnace was in great shape, even though its 25 years
old. The outboard motor for the belt-drive squirrel cage fan has been
replaced recently, and the burner itself seems to heat up a storm...
Until someone recently mentioned that this could all be ok, but due to some
unseen crack or defect in the burner it could be emitting a hi-level of
noxious fumes (CO?)
anyone more expert on this than I???
thanx/j
|
83.22 | Its true | NEXUS::GORTMAKER | Whatsa Gort? | Thu Sep 22 1988 05:48 | 9 |
| A crack in the heat exchanger part of the system can allow CO to
enter the system as it is the only thing seperating the combustion
gasses from the air passing thru the heater. I have been told the
way to check is to darken the room and shine a flashlight on one
side of the exchanger while observing the other if you see light
then CO could be passing thru into the system.
-j
|
83.23 | | SALEM::PAGLIARULO_G | | Thu Sep 22 1988 08:40 | 4 |
| Or you might be able to find the problem like I did. Just go
downstairs when the furnace is on and look through the grill at
the heat exchanger. The flames coming out were quite easy to see
on mine.
|
83.24 | | SWSNOD::BARRETT | | Thu Sep 22 1988 09:45 | 6 |
| Hi,
I just purchased a house that had a problem with the gas furnance.
The inspection company put some burning substance(hemlock??) in
the furnance, when the smell was carried through out the house we
knew the the heat exchanger was bad.
|
83.25 | dumb question # 37J | BINKLY::WINSTON | Jeff Winston (Hudson, MA) | Thu Sep 22 1988 19:42 | 11 |
| > A crack in the heat exchanger part of the system can allow CO to
> enter the system as it is the only thing seperating the combustion
> gasses from the air passing thru the heater. I have been told the
> way to check is to darken the room and shine a flashlight on one
> side of the exchanger while observing the other if you see light
> then CO could be passing thru into the system.
what is the 'heat exchanger? My furnace merely blows air past a set
of lit gas jets (like the unit in a big gas oven) into the ductwork.
|
83.26 | The concern IS real | BSS::DAHLGREN | Ed Dahlgren | Fri Sep 23 1988 14:26 | 63 |
| Interesting I should find this conference on my first full day as a
homeowner, and this note was started on the day I noticed my furnace-
to-be had a problem! (Is it coincidence, or is it karma?)
Our final walk-through was this past Wednesday. All through the house-
hunting process my nit-picking had aggravated everyone involved. BUT
on this particular day I scrambled into the crawlspace and found what
the seller had "forgotten" to mention on the disclosure sheet, what
our "friend" who inspected the house missed, and what the appraiser
obviously didn't bother to find:
A note was stuck to the side of the forced-air gas furnace
with the name of a local heating company and the words,
"Caution, this furnace has a cracked heat exchanger."
Well the seller called in an inspector, and we called in an inspector
(about $30 each) and they both said, "Yup, there's a crack. Can't use
it, gotta buy a new one." One of the guys doesn't even sell furnaces,
so he wasn't there to do a sales job on us.
The heat exchanger is kinda like a radiator in reverse -- the flames
and associated gases are kept away from the house air by keeping each
to its chamber. If there's a leak, the combustion gases and unburned
gas (if that's what you're using) leaks into the house. Bad news.
Wanting to make an expensive job cheaper, we asked if just the
exchanger could be replaced. Nope. It's too difficult to warranty.
Or the labor's not worth it, especially in a crawl space. Or whatever.
To make a long and exciting (to me) story short, the sellers agreed
to replace the furnace. They had to; the sales contract said they would
convey certain items to us in good working order. (Oh yeah, the water
heater was leaking too. But that was a simple pressure release valve,
and it was handled quickly and cheaply.)
The guy who doesn't sell furnaces had some interesting recommendations.
He works for a non-profit outfit that services about 700 furnaces a
year for the city's low-income housing. He made a brand recommendation,
which is probably irrelevant. And he said NOT to buy one of those 90+%
effficiency jobs. Sure they convert more flame into useable heat, and
sure they save a few dollars a month by not having a pilot light, but
the payback just isn't there.
What happens is that the complicated electronics fail more frequently
than the old technology, and they're more expensive to repair. For
example (he said) the ignition system on a no-pilot unit can run $400.
So, he recommends to the city that they buy old-style, reliable stuff.
This cuts the cost down from $1800-2000 to $900-1200 for us. (And the
seller. They had to take some proceeds from the closing and put it
in escrow for us to buy a new furnace with.)
ON THE OTHER HAND -- just to be perfectly fair I'll tell you what the
seller said. The seller claims she was told by the guy who put the
sticker on the furnace that it was okay the way it was, that it didn't
have to be replaced. (Something doesn't ring true here -- why did he
put the sticker on it? Either to scare her into buying a new furnace,
or to cover himself because it really was dangerous. Hmmm....)
So Jeff -- I'd say have it checked by someone with experience who you
can trust. There's a lot at stake (health and pocketbook)!
-- Ed
|
83.27 | not a DIY??? | BINKLY::WINSTON | Jeff Winston (Hudson, MA) | Fri Sep 23 1988 20:26 | 4 |
| Gee, I was sort of hoping I could inspect it myself - anyone know if
this is a good idea, and what to look for (still don't know what a
'heat exchanger <looks like>, or do I need a pro (maybe they have
calibrated eyeballs? :-} )
|
83.28 | Easy to do yourself | SALEM::PAGLIARULO_G | | Mon Sep 26 1988 09:21 | 29 |
| It shouldn't be difficult to inspect this yourself. In the cabinet
above the burners is a series of large metal tubes. These tubes
enclose the burner flame. On my old burner I could look through
a grill at the exchanger and see the flames coming out through cracks
in the tubes. I was also able to remove a panel, one of the cabinet
sides really, that covered the heat exchanger and could inspect
it directly. When the burner is on look for flames coming out of
the heat exchanger or if you can get the exchanger itself look for
cracks or holes in the metal tubes. A REAL crude drawing of the
set up I had is below.
George
-------------------------
Cabinet ----> | ||====||====|| |
| || || || |
Heat Exchanger ---------|-> || || || |
| || || || |
| || || || |
| || || || |
| || || || |
| /\ /\ /\ |
Burners---------|-> /\ /\ /\ |
| ====================
|_______________________|
|
83.29 | Move fast | AMUSE::QUIMBY | | Tue Sep 27 1988 19:15 | 28 |
| 1. If the heat exchanger is cracked, you're getting CO in the
house. It's not economical to replace the exchanger, unless
it's still under warranty.
2. If you need to replace the furnace, MOVE FAST NOW because the
contractors will become harder and harder to reach as the
weather gets colder.
3. There are alternatives between the "old standard" and the
"super-efficient" -- Carrier (also carried by Bryant and
others) makes one that is very similar to a standard, except
for the heat exchanger design. Instead of the straight
vertical tubes running from the flame to the flue, they create
an "S"-shaped path with about four turns, and add a fan to
create draft through the higher resistance of the longer path,
(It's called "induced draft" design). Between this and the
pilotless ignition, you get close to 90% efficiency.
4. Find out who services furnaces in your neighborhood. In Boston
Gas areas (Winchester, anyway), Boston Gas does no inatallations,
but does all the service. This screwy arrangement can easily
leave you facing a service person who literally has no idea
how to deal with your furnace. Boston Gas even had some
difficulty figuring out the "modest-tech" design I described
in #3 above.
dq
|
83.34 | Gas FHA smells funny @ fall startup | SMAUG::WOODS | Jim | Wed Oct 12 1988 11:17 | 22 |
| [I've read 2646.* and this may belong there, so feel free to move it Mr. Mod]
Monday I started up Gas FHA system for the winter. In the spring I turned
it off completely. (ie. turn the elec. as well as all the gas valves off).
Since I started it up on Monday, I have smelled a "funny" smell. I'm not
sure if its gas or not, can't really distinguish what it is.
My questions are: Is it "abnormal" for a gas FHA to give off a funny odor for a
while once being turned on after being shut down all summer? It ran fine all
last winter, and I certainly don't remember this smell last winter. If
something is amiss, what could have happened this summer (while it was
shutdown) to cause the system to malfunction now? Could it be the heat
exchanger as mentioned in note #2646? Should I get my gas company out there
ASAP or someone else who specializes in FHA systems? Should I shutdown the
system until I can get someone out there to verify that all is okay? Enough
questions...hopefully someone will be able to answer some of them.
Thanks in advance
-Jim
PS: It's a Miller Gas FHA system, if anyone is familar with them.
|
83.35 | Maybe | HEYDEN::BBARRY | | Wed Oct 12 1988 11:42 | 14 |
| If the smell is musty, it is normal to get a musty smell for about
a day after firing up a FHA system, especially after a humid summer.
If the smell like rotten eggs, smoke or oil, then their is something
wrong with your furnace.
If it smells like something died, then probably some critter has gotten
stuck in you ducts. Finding it will be difficult plus you have to
find and plug the hole used to get in.
Other odd smells could be caused by recirculating odors from the
basement or utility rooms.
Brian
|
83.36 | | MTWAIN::WELLCOME | Steve Wellcome (Maynard) | Wed Oct 12 1988 12:24 | 4 |
| Probably just a summer's worth of accumulated dust in the ducts
getting heated up and blown around. It should go away in a couple
of days. If not, you may want to investigate further.
|
83.37 | | SALEM::PAGLIARULO_G | | Wed Oct 12 1988 12:50 | 1 |
| Have you cleaned the filter?
|
83.38 | yes, I think so | SMAUG::WOODS | Jim | Wed Oct 12 1988 15:01 | 12 |
| re: .3
I'm not very familiar with these heating systems, so please excuse my
ignorance, but by filter do you mean the "mesh" that is on the inside
of the cabinet door, covering the vents that draw air in from the room?
If so, I cleaned this in the spring.
Is there any regular (annual?) maintenance that needs to be done on these
systems? Anything that is not a DIY and needs a service person?
Thanks again,
-Jim
|
83.39 | please please check it | SPGOGO::YIFRU | | Wed Oct 12 1988 15:40 | 0 |
83.40 | | BINKLY::WINSTON | Jeff Winston (Hudson, MA) | Wed Oct 12 1988 22:20 | 8 |
| On the other hand, my system gives off a slight 'heat' smell often
when it turns on, just like the one did at my last place. I think
gas heat inherently can have a minor odor - or maybe it comes from
starting to blow air thru the ducts.....
(on the other hand, maybe both systems had badly cracked heat
exchangers, - except that the airflow would be FROM the air chambers
INTO the flue)
|
83.41 | Get it checked, it's fairly cheap... | WEFXEM::COTE | It was a dark and stormy night... | Fri Oct 14 1988 17:14 | 14 |
| You don't by any chance get headaches do you???
My 20 year old heat exchanger in my gas FHA rusted through
during the *summer* a couple years back, blowing exhaust
into the house. Though I never connected the 2 (headaches
and furnace) together, other phenomena (pilot wouldn't stay
lit) finally prompted me to have a repairman look at the
furnace. He pronounced it 'dead' and said summer was often when
a rust-through occurs as the furnace could stay damp for an
extended period of time...
The headaches stopped immediately upon replacement.
Edd
|
83.181 | Variation on the theme... | DPDMAI::AINSLEY | Less than 150 kts. is TOO slow! | Mon Oct 31 1988 10:43 | 12 |
| I've got a slight variation on the theme here...The pilot light
stays on until I turn the gas valve to 'on'. Then it slowly fades
out. Turning it back to 'pilot' brings it back. Thinking I may
have had 'on' and 'off' confused, I turned it to 'off' and the pilot
light immediately went off.
Is this something I should be messing with, or should I bite the
bullet and call a repairman?
Any ideas?
Bob
|
83.182 | | CALVA::WOLINSKI | uCoder sans Frontieres | Mon Oct 31 1988 11:21 | 14 |
|
rep .9
You have either a bad gas valve or thermocouple. My guess is the
thermocouple. I had the same problem as you described and the fix
was the thermocouple. If the gas valve is the problem you had better
get a licensed repairman to fix it. I'm thinking od insurance problems
if anything happens if you DIY.
-mike
|
83.183 | | NEXUS::GORTMAKER | Whatsa Gort? | Tue Nov 01 1988 04:10 | 4 |
| re.8 & .9
I second the thermocouple fixed mine too.
-j
|
83.184 | Now it's working... | DPDMAI::AINSLEY | Less than 150 kts. is TOO slow! | Tue Nov 01 1988 09:51 | 12 |
| Well, when I went home last night, I decided to give it one more
chance and turned the gas to 'on'. The pilot light stayed on.
Turned the thermostat to heat and got heat.
I wonder, was that an early warning of a dying thermocouple, or
just something strange? I don't want to pay to have the thermocouple
replaced if it isn't required. On the other hand, we all know how
much fun it is to track down intermittent problems :-{
Should I make the call.
Bob
|
83.79 | DYI Furnace replace | NRPUR::FORAN | | Tue Nov 01 1988 10:28 | 10 |
| Guy's and gals, what do you think about DYI, gas hot air furnace
replacement. My furnace is 28 yrs old and I have added on to the
house and I feel that its no longer adequate to do the job. I'm
told that there have been some significant advances in furnace design
w/ regards to efficiency. It almost seems like it shouldnt be
that bad of a job, so lets hear from some who may have done it or
are contemolating doing it!!
Jim
|
83.185 | replace it!!!! | CALVA::WOLINSKI | uCoder sans Frontieres | Tue Nov 01 1988 10:37 | 17 |
|
rep .12
A new thermocouple is about $5 and is a DIY item. Most hardware
stores carry them and they are for the most part universal. I
just replaced the one in my two week old hot water heater over
the past weekend. The thermocouple I bought at the local hardware
store had all the nuts and clips I needed. From the symptoms
you describe I would go ahead and change it. My hot water heater
died saturday morning, I relit it and then it died about four
hours later. Sunday morning it was dead and the mad rush to replace
it began not a great way to start a sunday morning.
-mike
|
83.88 | Furnace Automatic Vent Damper Problem | AKOV11::COLES | Richard Coles -- GIA Field Service | Tue Nov 01 1988 10:46 | 49 |
| I have a Bryant (BDP) GAS FHA furnace. I had been hearing chatter
(click, click, click...) when the burner ignited and then at sporadic
intervals during the heating cycle when the burner was lit. I had the Gas
Company (Colonial Gas of Lowell) come out and take a look at it. The first
set of technicians (two) that they sent cleaned the flame sensing probe.
This had no affect. The next technician that they sent out said the problem
was an end switch in the automatic-vent-damper unit (a Bryant manufactured
add on to the furnace -- not covered by my service agreement, which I
started last year after the fan/limiter switch failed). The chatter was the
gas valve solenoid repeatedly openning/shutting the gas valve because of a
flakey signal from the automatic-vent-damper. The technician said that the
part would have to be ordered and that it was expensive so why didn't I see
if I could live with it the way it was for a while. The next day, when I
turned the thermostat up from a lower/night-time setting, all I got was
chatter -- no ignition. So I de-installed the circuit for the
automatic-vent-damper, the result is the vent damper stays open (it is
powered shut) and the furnace burner ignites and stay lit with no chatter.
I intend on getting a quote from Colonial Gas on what the price of the
part is and what installation would run, but what I'd like to know first is:
- How much does an automatic-vent-damper contribute to fuel savings?
- How reliable are they? (I've had this house for about 4 years now
and the furnace is around ten years old, so my guess is that the
current automatic-vent-damper is also about ten years old.)
- What is the pay-back period or cost benefit to having an automatic-
vent-damper (cost vs. fuel savings)?
The last thing I wanted to mention is the fact that the furnace now
seems to be cycling more frequently, but for shorter periods of time. It
keeps the house quite close to the temperature that the thermostat is set
at; although, in the past, I thought there used to be more over-shoot of the
set temperature (about 3 or 4 degrees). I checked the heat-anticipator
setting on the Honeywell thermostat (it's the gold round type) and it is set
at 0.5 which is what the furnace documentation states is correct (this topic
is discussed in Note 15). Could it be that the automatic-vent-damper was
allowing the furnace to capture that much more heat from each cycle? At
this point I'm using the furnace's past performance as my reference point.
Is it that the furnace is functioning correctly now (more frequent shorter
cycles) and it was not in the past (less frequent longer cycles)?
Anyone's comments or comparisions against their own furnace observations/
experiences would be appreciated.
Thanks,
--- Richard ---
|
83.80 | Go for it! | DRUID::CHACE | | Tue Nov 01 1988 10:47 | 0 |
83.186 | Perhaps this will help... | WOODRO::DCOX | Try? Try not! Do, or do not. | Tue Nov 01 1988 15:46 | 42 |
| First, if you need to ask, you need the Gas company. Safety first, and all
that.
That said, I have always worked on my gas appliances. What follows is, for
simplicity's sake, a layman's, not_very_technical, description and will apply
generically to MOST gas appliances.
Most of the problems have been due to thermocouples. The thermocouple is,
essentially, a wire that generates an electric current when it gets hot. The
end that mounts into the gas valve is attached to the coil of an electromagnet.
The thermocouple gets hot, generates a current and operates the electromagnet
which, in turn, operates a switch/valve to permit gas to flow through the gas
valve. If the thermocouple cools off (very quickly), the switch "snaps" back
and shuts off the gas flow. When you light the pilot, you usually hold down a
button that operates the valve. That is, you bypass the thermocouple. If the
thermocouple does not get long enough as it heats up, the valve will not stay
open when you release the button.
Thermocouples are inexpensive and easy to replace. When I have a problem, I
replace it and hope it is fixed. Since they ALWAYS go bad on a cold, winter
Sunday am, I keep a couple around.
The next problem area is the previously mentioned electromagnet switch. The
real problem here is that they usually last years (or decades, even,) and you
cannot find a replacement when you finally need one. You wind up buying a new
gas valve ($100+++). Sigh...
Finally, the gas valve can go bad for numerous reasons and I never recommend
anyone try to fix one. For one thing, you seldom can find the necessary parts
for the same reason as above. Replacement is easy, but, again, if you have to
ask, pay the labor costs.
A common problem happens to those folks who turn off their pilots during the
summer. There is seldom a problem when you shut it off at the gas valve,
however if you shut it off further back down the line, you can have moisture
(condensation) get into the line. Then, when you fire it up, the moisture is
pulled through to the gas valve and causes strange symptoms like dying out and
coming back until the moisture is finally pulled out.
Hope this explanation was worth the time.
Dave
|
83.81 | No Problem | SALEM::PAGLIARULO_G | | Tue Nov 01 1988 16:27 | 8 |
| I replaced mine last year. I was surprised how easy it was. Be
sure to get your new furnace from a place that is willing to answer
any DIY questions you might have. I found the people where I bought
my furnace to be invaluable. Where you're not just replacing the
furnace but also increasing the heating capacity there may be some
issues around cfm etc. that I didn't have to deal with.
George
|
83.187 | When is 'on' not 'on'? | DPDMAI::AINSLEY | Less than 150 kts. is TOO slow! | Tue Nov 01 1988 17:51 | 13 |
| re: .13, .14
Thanks for the info. I am familiar with how a thermocouple works. That
is why I was confused when the pilot light would stay on, in the
'pilot' position, but not when the gas was turned to 'on'. I can't see
the connection between turning the gas on, and the thermocouple. The
thermocouple will always turn off the gas if it cools off and the gas
supply is not being held on by the spring-loaded bypass switch. As
long as the pilot light is on and heating the thermocouple, the gas
should continue to flow and hence the pilot light stay on, regardless
of the switch position. (Ignoring the 'off' position).
Bob
|
83.42 | More oil company propaganda | PALMER::PALMER | half a bubble off plumb | Wed Nov 02 1988 08:00 | 12 |
| Has anyone else seen the new round of ads sponsored by the New
England Oil Heat Council? It starts off with a simulated Gas company
commercial stating: If you smell gas call right away, but if you
are having trouble with you heating system we'll get back to you.
It then goes on to show what *wonderful* service you get with a
full service Oil Dealer.
I guess it's time for the Oil vs Gas heating fights. I don't
mind the ads, it the Oil company's assertion, Get Gas, go BOOM
that bothers me as misleading.
=Ralph=
(Oil heat, gas dryer, hot water and stove)
|
83.82 | worth the effort ! | AXIS::BERUBE | | Wed Nov 02 1988 08:58 | 21 |
|
I also replaced my hot air furnace, its not that difficult, any
sheet metal shop can make up the adapters for connection of the
new furnace plenums with the old ducting. Where I bought my furnace
they also did sheet metal work so it was easy. Dont forget to consider
offsets as well as the diameters and heights, most likely the openings
won't line up evenly due to the decreased size of the newer furnaces.
One more thing to note there is some set up and nozel selection
of the oilfired type furnaces for maximum efficientcy but if you using
gas then I don't believe theres any. The set up of the oil burner
is much what they would do in a professional cleaning, the selection of
nozel for the oil gun is something the sales place should be able
to tell you.
good luck,
Steve
believ
|
83.43 | They add the odor to the gas so you can smell it | CLOSET::T_PARMENTER | Tongue in cheek, fist in air! | Wed Nov 02 1988 09:21 | 5 |
| Just yesterday a house in Weston (owned by a lady who retired after
40 years with Boston Gas) disappeared in a gas explosion. A contractor
was digging in her yard and ruptured a pipe close to the house.
The basement filled with gas (the lady heard the sound and left
the house) and then after less than 2 minutes, (how you say?) BOOM!
|
83.83 | Better & Better | NRPUR::FORAN | | Wed Nov 02 1988 11:12 | 4 |
| Thanx, folks for the replies, the more I hear the better it
sounds. I'm going to sart to get some prices for furnaces.
|
83.84 | | MPGS::DEHAHN | | Wed Nov 02 1988 12:02 | 9 |
|
When I had my new burner put in, I was told that it must be installed
by a licensed burner technician. If the house burnt down because I
installed it myself, I wouldn't collect a dime. Better check your
insurance policy first.
CdH
|
83.89 | Some ideas to get started with. | SALEM::M_TAYLOR | Dial 1-900-490-FREAK | Wed Nov 02 1988 13:03 | 47 |
| Richard,
You are now allowing fresh air to flow through your furnace and
extract heat from your furnace, and shoot it right out of the chimney.
You will notice a big-time difference in your gas bill very shortly.
The reason you had over-shoot in your previous condition was that
the furnace was indeed holding onto your heat longer and therefore,
in a FHA system, the blower might always run until the heat exchanger
cooled sufficiently. Now, your burner shuts off, allowing a rapid
cooling effect by the hot chimney causing an up-draft through your
furnace. With the damper fixed, the recommended action would be
to lower the anticipator a notch and go further is that still causes
overshoot.
Fix your damper. If you are in field service, as a technical person,
you should have no problem. (You bypassed the circuit already,
correct?) The furnace burner control must see a "damper open" condition
in order to sustain ignition. Your damper is doing one of probably
only three things:
either the spring which opens this damper up has weakened, allowing
the damper to flutter off of the open mark;
or the micro-switch which detects wide open damper position is flakey
and is in need of replacement or adjustment;
or finally, the relay which switches the drive power to the damper
motor is noisy and causing the damper to be driven at the wrong
time.
You can find out for sure by ohming out the line that goes to the
switch and the common line to the motor/switch and wiggling the
damper while checking continuity there. If there's intermittance,
the switch or the spring may be at fault. if there's no intermittance,
then power on the furnace with all connections back to normal. Attempt
to start the burner, and check the VOLTAGE to the torqueing motor.
If there's any sign of 28 vac, then the relay or its decision logic
could be at fault. I vote for a cruddy set of relay contacts in
the control followed by a flakey switch in order of probablilty.
If you need anything else, please send me VAXmail, as I don't get
much opportunity to read this file (I'm a field service monkey,
too!)
Mike
|
83.90 | Gas furnace outside air intake | CRAIG::YANKES | | Mon Nov 14 1988 11:04 | 24 |
|
I would like to install an outdoor air intake for my gas furnace.
(This weekend, I realized just how much air I'm losing from the
upstairs to the basement due to the combustion exhaust. Wow!)
Two questions: (and Mr. Mod, I know the idea of an outside air intake
was recently discussed, but I don't think these particular questions
were discussed.)
1) How large of an intake should I put in? A 6 or 8 inch pipe
would be do-able, but would I need a larger one?
2) The inside part of the project looks real easy given where
my furnace is and its orientation. What do I put on the outside,
though? Do they make flapper valves (or whatever they are called)
for 8 inch pipe? And don't flapper valves require the pipe to be
horizontal? Wouldn't that let rain water in?
(Incidently, no, putting weatherstripping on the door at the
top of the stairs isn't a viable solution. I have my hobby room
in the basement, so sealing off the upstairs would force the furnace
to draw its air through the basement door and various airholes.
I'd end up with a basement that is too cold to work in comfortably.)
-c
|
83.91 | Good Idea! | LEDDEV::HASTINGS | | Mon Nov 14 1988 17:26 | 22 |
| My last house had an outside air intake. It appeared to have been
installed by the previous owner. It was 6 inch galvinized duct pipe.
The outside end was curved down and covered with window screen to
keep out critters.
I would recommend using a much larger diameter pipe. My furnace
was in a small utility room with an accordian door. This room was
entered through a larger room with an accordian door also. When
the furnace turned on these doors were sucked in noticably.
I had a wood stove in the basement near these rooms. It was
importand for me to open the door when lighting the stove, it was
*vital* if the furnace was firing! If not I couldn't get enough
updraft to prevent my house from filling with smoke! (Fortunately
the one or two times I made this mistake I was able to use the whole
house fan.
As a rule of thumb I would recommend an outdoor intake a bit
larger than the exhaust stack of the furnace. Making it larger will
compensate for the reduced airflow because of the screen you will
want to cover it with.
Good luck
Mark
|
83.92 | Update -- and questions... | CRAIG::YANKES | | Mon Nov 28 1988 14:56 | 24 |
|
An update on the project.
I've decided to modify the plans. Rather than put the pipe
through the siding of the house (messy if the overall project
fails...), I've decided to use a basement window as the air intake.
(It is one of those casement windows around 30 inches long and 8
inches high or so. For the winter, I tape a rigid foam "plug" into
the window to cut down on the heat loss -- so losing the window to the
winter air intake is no big deal at all.) The window, incidently,
is close enough to the furnace that only around four/five feet more of
ducting would be needed compared to poking the hole in the wall.
Before I begin the implementation of this, however, I'd like
to ask one more question: Are there any code requirements that
I should be aware of in doing this??? Even though it will be carrying
cold air, the entire assembly will be sheetmetal/ductwork just to
be sure. I'm planning on attaching it to the furnace via sheetmetal
screws. Is there anything else that I should be cautious/aware
of?
Thanks!
-c
|
83.93 | *** snow *** | LEDDEV::HASTINGS | | Tue Nov 29 1988 16:09 | 2 |
|
Make sure that you won't ever get a snow drift filling up the window!
|
83.94 | | CRAIG::YANKES | | Tue Nov 29 1988 16:59 | 16 |
|
Re: .3
Good point, and was another reason why I was hesitant to poke
the hole through the wall -- that would leave the intake only around
2-3 feet above the ground level. My window, on the other hand,
is above my patio, so a snowdrift of around 7 feet would be needed
to block it! And if that happens, the intake will probably be only
one of my many problems!
-c
p.s. Since the through-the-window option must be made so it can
be taken down in the summer, if we *did* get a snowdraft that high,
I could just "unplug" the intake from the window and I'm no worse
than what I have today with air loss.
|
83.95 | don't forget the screen | LEDDEV::HASTINGS | | Tue Nov 29 1988 17:25 | 10 |
| Sounds like you have it well figured out. Are you going to include
screening to keep out creepy-crawlies. They may not bother you much
but I bet they won't smell to good in your heating system.
Other than that I like your idea. Sounds like you will have
adequate draft...hmmm, could the draft become excessive? What are
the wind patterns like around your home in the winter? Will there
be any gusts blowing into you vent that could disrupt the burner?
Mark
|
83.96 | The window has a screen, but... | CRAIG::YANKES | | Tue Nov 29 1988 17:33 | 10 |
|
Gusts?
Gusts???
Oh oh. Frankly, I don't really know. How would I test this
short of building the whole contraption and seeing if it blows out
my pilot light??
-c
|
83.97 | checks for gusts | LEDDEV::HASTINGS | | Tue Nov 29 1988 17:48 | 21 |
| Well... I suppose you could rig up a damper of some kind if you
really needed to but first...
Try to recall how the snow settles on you patio (beneath where
your intake will be). Does your patio get swept clean during blizzards?
If so it indicates high winds and gusts there. Does the patio face
north, or north/east (I'm assuming you live in New England), if
so worry about gusts, thats where you will see the worst storms
coming from. When you open doors or windows on that side is ther
much wind blowing into the house during storms?
Of course these "tests" are not perfect as the wind can blow
in any direction, however I think you can rest easier if the answer
is generally "no" to the above questions. In addition you should
probably plan to extend you intake *through* the window so that
you can add a downward scoop to it. In addition to keeping out the
rain it should prevent an errant gust of wind from trying to turn
your furnace into a ram jet.
Mark
|
83.98 | | CRAIG::YANKES | | Tue Nov 29 1988 18:07 | 16 |
|
Thanks, Mark. The patio faces slightly north of north-west.
One good sign, though, last winter I had to shovel the patio and
there were no signs of significantly less snow than on the ground.
Of course, the surface of the patio is around 3.5-4 feet below
the ground level at the deepest point, so the snow can't easily
blow sideways "off" the patio. (Well, not until this winter now
that the "front" of the patio has been terraced out so you don't
feel like you're sitting in a hole. :-) The level of snow cover was
pretty consistant across the patio.
Good comment on the turned-down part of the pipe. I'll have
to remove the glass from the window or else make another box on
the outside. I'll take a look at it...
-c
|
83.99 | | CRAIG::YANKES | | Tue Nov 29 1988 18:09 | 2 |
|
P.S. Yes, I'm in New England -- northern end of Nashua.
|
83.100 | A few serious problems. | POOL::LANDMAN | VMS - Not just for minis anymore | Wed Nov 30 1988 13:15 | 16 |
| > ... the entire assembly will be sheetmetal/ductwork just to
> be sure. I'm planning on attaching it to the furnace via sheetmetal
> screws.
If your house is properly humidified (forced air heat with central
humidifier, or room humidifiers), you will get a lot of condensation
and dripping from the sheet metal ductwork. They make flexible,
insulated pipe for this purpose.
The code that I've seen for this (back in the cold midwest) stated that
you can NOT attach it to the furnace. You must run it to the vicinity
of the furnace's air intake.
Some special furnaces are make to accept direct connection, but they
are rare.
|
83.101 | | CRAIG::YANKES | | Wed Nov 30 1988 13:33 | 16 |
|
Re: .10
Thanks. I'm curious as to why the code would forbid attaching
the air intake to the front of the furnace? Making the outlet of
the ductwork only in the "area" of the front of the furnace won't
do me much good in cutting down the cold air coming into the house
-- and may make it worse, although it would at least be concentrated
in the basement.
Is the code problem with the "attachment" itself, i.e. an amateur
like myself drilling holes around what should be a sealed cavity,
or with the problem of potentially limiting the amount of air that
can come into the intake? Thanks for the code checkups!
-c
|
83.102 | What about anti-gusts? | RGB::SEILER | Larry Seiler | Fri Dec 02 1988 00:26 | 12 |
| Let's suppose the air intake is attached to the furnace.
Let's also suppose that, to avoid gusts, the other end
of the intake is on the side of the house away from the wind.
Now, when the windo blows, it creates higher air pressure
on the side it blows against, and creates a slight vacuum
on the opposite side. Does this mean that the air intake
could have air sucked out of it instead? Presumably that
would not be good for the furnace! Is this a problem?
Thanks,
Larry
|
83.103 | Another use for air shredders? | CRAIG::YANKES | | Fri Dec 02 1988 10:49 | 15 |
|
One more nail for the coffin...
I'm starting to think that this outside air-intake idea just
might not work -- safely, that is. One question, though -- what
keeps a blast of outside air from coming down my chimney and blowing
out my pilot light right now? I have a plastic sheet in front of
my fireplace and you should see it billow when the wind blows outside!
There might be a way around the anti-gust problem. Since that
scenario would involve air getting pushed down the chimney, wouldn't
my chimney air shredder keep the pressure from building up and blowing
out the pilot light?
-c
|
83.104 | | LEDDEV::HASTINGS | | Fri Dec 02 1988 16:42 | 1 |
| Oh no... I think we've lost another topic...
|
83.105 | It does work. | POOL::LANDMAN | VMS - Not just for minis anymore | Fri Dec 02 1988 18:49 | 20 |
|
> Thanks. I'm curious as to why the code would forbid attaching
> the air intake to the front of the furnace? Making the outlet of
> the ductwork only in the "area" of the front of the furnace won't
> do me much good in cutting down the cold air coming into the house
> -- and may make it worse, although it would at least be concentrated
> in the basement.
Put a 'plumber's trap' in the hose, so that the cold air at the bottom
of the loop serves as a plug. The air will then only flow when the
furnace starts up.
I had this in Minnesota, and even at 45 below zero, or in blizzards (wind
chill -80) the furnace room stayed warm.
The house stayed warmer, since it eliminated all of the drafts in the
house (the pressure differential was satisfied in the furnace room, not
by every little pinhole in the house). It also stops the garage fumes
from being drawn into the house when you open the connecting door.
|
83.106 | Interesting, but help me understand better. | CRAIG::YANKES | | Mon Dec 05 1988 10:18 | 10 |
|
Plumbers trap in the airhose? I thought a plumbers trap worked
by holding water in the bottom of the loop so there couldn't be
any air exchange (i.e. no sewer gas coming out of the sink). I
guess I don't understand why the cold air would form a sufficient
plug to keep the cold air from coming out. (I presume you're talking
about just having the opening of the vent near the furnace and not
coupled via an airtight box?)
-c
|
83.107 | | CRAIG::YANKES | | Mon Dec 05 1988 10:21 | 7 |
|
Just thought of something -- would a dryer vent covering the
inside opening work? It might be difficult to get it balanced "just
right" so that the pressure differential would be enough to open
it up, though.
-c
|
83.108 | More stuff | RETORT::GOODRICH | Taking a long vacation | Tue Dec 06 1988 08:27 | 15 |
| Much of this has been said...
Don't connect the vent to the furnace unless you know the
furnace is designed for it.
Do run the vent down so that it outlets just above the floor
- this reduces the chimney effect as does a "Trap".
4" pipe is usually large enough - cold air is much denser
than the hot flue gasses so the sizes can be very different.
4" meets the code requirements for most furnaces when they
are in a confined space such as a furnace room. Codes don't
require any vent in larger open areas such as basements.
- gerry
|
83.109 | Almost time to begin the project! | CRAIG::YANKES | | Tue Dec 06 1988 09:51 | 70 |
|
Re: .18 and various others back there...
>Do run the vent down so that it outlets just above the floor
>- this reduces the chimney effect as does a "Trap".
Please forgive me, but I'm still a bit confused as to what the
pros/cons are of the various venting options. Lets say I have the
following cross section in the basement:
----------------------------------------------------- ceiling
window
+
|
| +------+
| | |
| |air |furnace
| vents |
| | |
| | |
+------------------------------------------------- floor
Is this what is meant by a "trap?":
---------------------------------------------------- ceiling
window =
+ \Vent /-\
| \ / \
| \ Trap / \ +------+
| \ | / \ | |
| \ V / \ |air |furnace
| \ / \== vents |
| \ / | |
| \_/ | |
+------------------------------------------------- floor
I've probably exaggerated the scale of the trap, but do I have
the right idea? As I understand it, the purpose of this is to hold
a plug of cold air in the "valley" so that very little excess cold
air will come down the final slope towards the furnace. (The siphoning
would be trying to move denser air and so wouldn't work.) Right?
Is this what you were describing in .18?:
---------------------------------------------------- ceiling
window =
+ \Vent
| \
| \ +------+
| \ | |
| \ |air |furnace
| \ vents |
| \ | |
| \=================== | |
+------------------------------------------------- floor
As I figure it, once the 4 inches of air immediately above the
floor would get as cold as the outside air, there would be no more
excess air infiltration through the vent, right? As long as there
wouldn't be much activity in the room to stir up the air currents,
this probably would be as effective as the plug method.
If I have all this right, I'll have to go with the "plug" method
since I'm in that room enough to stir up the air currents. Thanks,
everyone, for all the wonderful comments! With my saved heating
money, I'll raise a toast to the homework notesfile coming through
again.
-c
|
83.110 | Silly me, I thought I had it all figured out... | CRAIG::YANKES | | Fri Dec 09 1988 15:46 | 28 |
|
...and then my thoughts were changed.
A couple of evenings ago, I happened to be going up the basement stairs
when I heard the furnace burners turn on. (I haven't added any air intakes
yet.) Just to confirm the "worst", I put my hand near the bottom of the first
floor door (where I first noticed the huge draft going downstairs) and...
...not much of a draft at all. ???
Then the blower kicked on and the huge draft started that initiated this
whole discussions two weeks ago.
Hmmm. The timing didn't look right at all. If the draft was caused
by the combustion air going up the chimney, it should have started as soon as
the burners turned on, not when the blowers turned on. I investigated further,
and it seems that when they installed the cold-air-return ductwork, the work
was a bit sloppy and there are some openings (one big one around 1 square inch)
sort of hidden. It seems to me now that the main reason for the draft under
the door leading to the basement is that a lot of the cold-air being returned
is coming through that hole instead of only through the cold air vents on the
first floor. That would force a lot of air under the door to make up for the
lowered pressure in the basement.
So, to get to my real question... Is it ok to close up this hole (and
the smaller gaps in the seams) with just duct-tape? Its only on the cold-air
side, so there shouldn't be any issue of heat-contact. Thanks!
-c
|
83.111 | Possible dangerous situation | POOL::LANDMAN | VMS - Not just for minis anymore | Fri Dec 09 1988 17:26 | 3 |
| If the hole in your cold air return is anywhere near the furnace
itself, close it off! The fan will draw air down your furnace flue,
putting poisonous products of combustion into your house.
|
83.112 | It may be a more general problem | MAY11::WARCHOL | | Mon Dec 12 1988 11:35 | 7 |
| If the cold air returns are formed by sheets of metal nailed across
two joists to form a duct then you will lots of places to try and
seal and you'll never get them all. I don't think that a single 1
square inch hole is causing your problem, it sounds like it is more
than one in order to get a draft that you can feel and the door.
Nick
|
83.113 | Air holes everywhere... Can I tape the hot air side also? | CRAIG::YANKES | | Mon Dec 12 1988 12:25 | 15 |
|
Yeah, I started sealing up the holes on Saturday and found lots of those
"ducts" created with the sheet metal spanning joists. What a way to build
ductwork. :-( There is enough air holes in both hot and cold air directions
that I'm suprised the upstairs gets any warm air at all! (Well, ok, its not
quite that bad...) Anyway, I've sealed like crazy on the cold air side (with
_much_ more to do!) and want to start tackling the hot air ducts. Is there
any problems with using duct-tape on the hot-air side? My concerns might be
totally unwarranted -- after all, it _is_ called duct-tape -- but I don't want
to accidentally tape too close to the furnace if there are any temperature
limits on the tape.
Thanks!
-c
|
83.114 | Duct tape is fine. | MAY11::WARCHOL | | Mon Dec 12 1988 14:02 | 31 |
| There is no problem using duct tape on the supply lines, that's
exactly what it is made for.
The reason for the sheeting of existing joists to form the return
ducts is generally to increase headroom in the basement. It's usually
difficult enough to find room for just the supply lines let alone
the returns also. A lot more leeway is taken with the cold air returns.
There is also a special duct caulking that comes in the standard
tubes that you can use. It is specifically designed to handle the
heat range. I doubt you can find it in any place but a heating/air
conditioning/sheetmetal supply house. It is a red colored caulk.
You can also use the gray rope caulk that is sold under the Mortite
brand name. This also holds up very well. I'd stay away from silicone
caulks unless you like distributing the odor that they emit while
curing.
I think what you have stumbled on is the difference between a quality
duct system and a low cost system. You usually can't tell the
difference unless you've worked on them for a while. But the quality
of the joints is a key feature. If the joints are done correctly
you shouldn't need any sealant.
I worked my way through college in my father's sheet metal business.
Thinking back the amount of ductwork I've fabricated and installed
can probably be measured in miles. A conservative 100 ft/week is
about a mile per year. I couldn't even guess how much
my father has done in his 40 years in this trade.
Nick
|
83.115 | | CRAIG::YANKES | | Mon Dec 12 1988 14:20 | 10 |
|
Thanks, Nick! Sounds like you sure have done a lot of ductwork and want
to do it right! Where were you when the previous owners built my house??!!? :-)
Duct-taping here I come...
-c
p.s. By the way, Nick, I even found a place where a 6-inch elbow attaches to
a straight section and they were misaligned by 3/4s of an inch! It took me
about 30 seconds to fix it...
|
83.116 | DUCT TAPE + HEAT has not worked for me! | DSTR08::SMICK | Van C. Smick | Wed Dec 14 1988 08:19 | 14 |
| re: .24
I can not compete with Nick's experience, but I have never had good luck
with duct tape on the hot air supply and I've bought "expensive" duct tape,
not the cheap stuff from Kmart. The stuff sticks fine for about two weeks
of heating, then it starts to curl. Maybe there is some sort of rating or
classification that Nick can share with us?
In a related question, the duct tape I have also does not stick worth a
darn to the duct insulation (vinyl coated fiberglass), even though that's
what was recommended. Any suggestions on what to use to tape/glue the seams
on duct insulation?
VCS
|
83.117 | | NEXUS::GORTMAKER | Whatsa Gort? | Wed Dec 14 1988 09:59 | 5 |
| I duct taped all my ducting 5 years ago and its still holding strong.
Did you clean away the dust first mine had quite alot built up.
-j
|
83.118 | Aluminum duct tape | WILKIE::BERKNER | Tom Berkner 264-7942 MK01 | Wed Dec 14 1988 12:18 | 8 |
| I have been using an aluminum tape that is designed for installing
fibreglass duct work (got it from MASI plumbing and heating in Milford
NH) and it works great. It's actually an adhesive coated aluminum
foil and comes with a paper covering the adhesive which you peel
off before use. Costs $10 a roll but well worth it.
Tom
|
83.119 | Interesting... | CRAIG::YANKES | | Wed Dec 14 1988 14:29 | 6 |
|
Thanks for the suggestion, Tom. I've put on some regular duct-tape
and it seems to get real soft and bubble up if the area gets too hot. Perhaps
that tape at MASI would be better. Where in Milford is this store?
-c
|
83.120 | Help... I need a bigger job jar! 8^) | MISFIT::DEEP | Sometimes squeaky wheels get replaced! | Wed Dec 14 1988 15:28 | 25 |
|
Why does this NOTES file always cause me extra work? 8^)
This discussion got me wondering about the vent for my fireplace insert.
I knew the vent was there... cover looks just like the ones for the
bathroom vents, and the dryer vent. But...I say to myself... knowing
the builder like I do, I wouldn't be at all surprised to find that
he used *EXACTLY* the same vents... meaning it has a flap that opens
when air is blown out.
Of course, on the firsplace, I want the air to suck in... not blow out...
thus the flap would never open, and the fireplace would suck my heat up
the chimney. Well, surprise of surprises! For once, the builder did
something right... the vent didn't have a flap, just a screen.
However... THE VENT DOESN'T HAVE A FLAP! (I know...I just said that...)
But that means the vent is always open...fire or not. Hence the cold draft
that I get when there is no fire.
So now, I'm trying to figure out a way to rig up a flap, or some other kind
of cover, that I can operate from inside the house.
Any ideas?
Bob
|
83.121 | too simple? | MYCRFT::PARODI | John H. Parodi | Wed Dec 14 1988 16:18 | 6 |
|
Re: .30
Why not put a plug or a flap on the fireplace end of the vent pipe?
JP
|
83.122 | Fancy Idea #12964 | MISFIT::DEEP | Sometimes squeaky wheels get replaced! | Thu Dec 15 1988 10:04 | 21 |
|
Not sure where that is? Its a fireplace insert, and I think the air for
combustion comes in from a gap all the way along the base... (3 sides).
I think the only real place to work a valve is on the vent. I can't get to the
tube that connects the vent to the firebix very easily. I was thinking about
a couple of round plates with holes that line up at a certain orientation,
and close tightly at another orientation...kind of like the top of a grated
cheese jar or something. I figure if I can get it to work smoothly enough,
I can put a little step motor on the assembly, and just push a button to
open, and push again to close. If the holes are set up right, and symmetric,
I should be able to just keep stepping the motor from open to closed...
Then if I want to get fancy, I can get an IR emitter/detector set from
Radio Shack, and set ot up to "look" through the holes, and provide a
signal to red and green LED's for some positive feedback regarding the
position of the plates... 8^)
Bob_who_needs_to_figure_out_how_to_keep_it_all_from_freezing_in_the_wrong
_position! 8-)
|
83.123 | duct tape | MAY11::WARCHOL | | Thu Dec 15 1988 10:43 | 33 |
| I was away from my terminal for a few days so this response is for
a couple of replies back.
Yes duct tape sometimes comes loose, especially if there is any
bit of dirt or oil on the metal. We never used just duct tape to
secure round pipe connections like you'll see in some installations.
The joints are first screwed together using self starting sheetmetal
screws (drillscrews) and a 1/4" magnetic chuck in a variable speed
drill or special screw gun. The duct tape is only used as a sealant.
One trick with duct tape is to leave about 2" of tape hanging free
when you start wrapping the connection and when you bring the tape
all the way around the joint have the two ends meet glue to glue.
Then continue with the tape a bit more to secure this tab down to
the duct. It's very difficult to separate the ends this way.
Duct tape does not work well in securing duct insulation. We used
1 1/2" insulation with a nylon thread reinforced foil backing. There
is a special nylon thread foil tape with peel off paper to expose
the adhesive. This is the only thing that we've found to work and
that is only on new, clean insulation. Once the insulation gets
dusty in an attic it is very difficult to get anything to stick
to it. We also used to use small thin metal disks about 1 1/2" in
diameter to secure the insulation. I believe that roofers use a
similiar disk to hold tar paper down. We'd punch holes through the
centers of the disks and use screws through the disk and insulation
into the metal duct to hold the insulation in place. Normally you
didn't need to do this, but it is a reasonable fix if you have
insulation falling off your ducts.
I still get itchy remembering all the insulation we wrapped around air
conditioning ducts in hot attics.
Nick
|
83.124 | About that foil tape... | SMURF::LESNIAK | | Thu Dec 15 1988 11:34 | 9 |
| Just what I've been looking for to seal the seams of some foil faced
rigid insulation.
How long are the rolls?
The only stuff I've been able to find is for sealing flue pipes and
would end up costing me as much as the insulation did!
Ken
|
83.125 | | MAY11::WARCHOL | | Thu Dec 15 1988 14:30 | 8 |
| The insulation seam tape comes in rolls that are probably about
100 ft in length. I've never really measured one and I didn't see
the invoices from the supply house to know what it costs. All I
remember is my father telling me to stop wasting it because it was
expensive. I'd try a heating/airconditioning supply house if you
were looking for some.
Nick
|
83.126 | | WHOZAT::BB | Bob (PICA::)Blanchette | Fri Dec 16 1988 00:43 | 9 |
| Re .29: Where is Masi Plumbing?
Clinton St. in Milford. (Near the oval... 1 way street running from
South St. to Amherst St. Enters Amherst St. near the Fish Market.)
Otterson St. in Nashua. (Same building as The Grainery restaurant.)
I suspect you could find the aluminum tape at most bulding supply
stores as well.
|
83.85 | where to run condensate line? | ERLANG::SOUZA | For Internal Use Only | Thu Dec 29 1988 12:45 | 11 |
|
I'm installing a condensate pump for my condensing propane fha furnace.
It currently drains through a hole in the slab.
Should the line run outside (where it might freeze?) or into an inside
drain (where the condensate might kill the happy microbes in my septic system?).
Thanks
bob
|
83.86 | Let Gravity Keep It Clear | CAMLOT::JANIAK | | Thu Dec 29 1988 16:44 | 14 |
| I recently installed a furnace with some guidance from the heating
contractor and his recommendation was to run it alongside the exhaust
PVC pipe and through the outside wall next to exhaust vent. The
trick is to make sure the last foot inside the house slope downward
to the outside such that no water (condensation) sits in a freezable
location. It's easily done by just taping the tube to the exhaust
pipe 18" from the end, bending the condensation tube towards the
ceiling, and then taping the tube just before in goes through the
wall to the outside. Works quite well. The other suggestion he
had was to soak the tube in warm water prior to taping it to the
exhaust pipe. It helped take the kinks out the tubing and allowed
it to run much straighter along the PVC.
-Stan
|
83.87 | Did it myself with a little guidance | CAMLOT::JANIAK | | Thu Dec 29 1988 16:59 | 16 |
| With regards to .3's comments on different nozzle sizes for oil
burners there is a similar situation on a gas fired burner. The
nozzles (orafices) are different depending on whether you are burning
street gas or propane. In my case the burner came set for street
gas but I had to modify it (replace nozzles) to handle propane.
Also - in reply to the base note - I've done the majority of the
installation myself, running all the ductwork, etc. I did contract
the heating contractor for about 6 hours one day to come and work
with me on setting the furnace up and running the gas line (black
iron pipe) from the furnace to the outside regulator. He was excellent
in guiding me in the furnace connections (electrical, exhaust, etc.)
and offered many subtle hints along the way.
-STan
|
83.44 | Uooo that smell... | OASS::B_RAMSEY | Bruce Ramsey | Wed Jan 11 1989 19:04 | 9 |
| FHA furnace collect dust in the summer. When you first start it
up for the heating system, it burns off the dust/dirt which smells.
This usually lasts for less than a week when all the dust/dirt is
burned off.
So common is FHA in the south that the radio annoucers make jokes about
the funny smell the first time it gets cold enough to start the heating
plant for the season.
|
83.20 | | INGOT::KILGORE | Wild Bill | Thu Apr 06 1989 08:33 | 3 |
| I seem to have a problem similar to .9. The fan won't shut off at
all. Is replacing the fan limit control a DIY job? Where do you
get parts?
|
83.30 | Pilots lights may not be a waste | YODA::MEIER | Steve Meier | Mon Nov 13 1989 14:28 | 11 |
| I too have an old gas-FHA furnace. Last year, I had the gas company guy out
to give it a checkup and he made a comment about pilotless ignitions that
is relevant to the discussion here. I commented on all the "waste" of running a
pilot light throughout the summer and he said that it is better for the furnace
to keep it going. He explained that the pilot light keeps the system warm
enough to keep it dry. He felt that occasional condensation was the cause
of much rust and premature failure. This makes sense to me. Perhaps someone
could verify his opinion.
-Steve Meier
|
83.31 | Last furnace lasted 20+ years.... | WEFXEM::COTE | OK, who wants a Tangwich??? | Mon Nov 13 1989 17:01 | 7 |
| I'd heard the same thing also, but considering the size of the pilot
flame, the size of the heat exchanger, and the distance between the
two, I tend to doubt it.
Maybe tho...
Edd (who shuts the pilot down for summer)
|
83.32 | something else to think of... | RAMBLR::MORONEY | How do you get this car out of second gear? | Mon Nov 13 1989 17:19 | 3 |
| Also, the pilot flame is a source of moisture...
-Mike
|
83.33 | Off it goes... | MED::D_SMITH | | Wed Nov 15 1989 10:26 | 5 |
| In my case, with central AC, I also shut of the pilot to elminate heating
any of the chamber containing cool air.
Dave
|
83.45 | Keeping a fha gas furnace quiet | KDCFS1::LANGE | | Wed Dec 12 1990 14:46 | 24 |
| I recently had a high eff. gas furnace installed in my
newly aquired home. The problem is that there seems to be more
furnace noise (ie: air noise) following the installation as
compared to that of the electric furnace that was in previously.
The fan speed is set to medium (can't go lower or will burn heat
exchangers). The plenums and duct work in the house are straight,
therefore less corners for noise. Because I work so closely with
systems all day (literally) I have grown to dispise this type of
noise, or to put it "IT DRIVES ME !@#$% GRAZY" ..oh... that's better.
Anyway, I would like to know if any of you readers out there
who enjoy this kind of noise as much as I do, have any suggestions
on curbing this noise. The installer (after I complained) mentioned
that for a mere $350 he would install insulated plenums. Previous
to the installation he guaranteed that it would be *very* quite.
Huh!~
So, whats the work around? and dosen't this insulated duct work
(pressed fiber brd or what ever) created more dust? (wifes got real
bad alergies).
THANX
gently going insane GGI
|
83.46 | check the grates | SALEM::PAGLIARULO_G | | Wed Dec 12 1990 16:24 | 18 |
| Where is the noise coming from? Do you hear it at the furnace or is it
an increased noise upstairs at the intakes/outputs. If it's upstairs
make sure all the grates are opened. I believe a FHA system is
balanced and if you close the dampers you can screw up the balance.
I have one intake in the kitchen that, when closed, noticeably
increases the noise.
This is really stupid but last year I put a humidifier on the
return plenum of my furnace. The upstairs air noise got noticeably louder
but I didn't question it - just chaulked it up to splitting the air
flow to the humidifier. This year I was getting the humidifier ready
for the heating season and noticed that I never cut a hole in the
return plenum for the humidifier. The furnace was losing about a third of
the return air and it was making up for it by drawing more from the rooms.
Once I cut the hole the furnace got real quiet! Now you can hardly
hear it upstairs.
George
|
83.47 | | CSS::DCOX | | Wed Dec 12 1990 17:45 | 6 |
| If the problem is the sound of rushing air as heard through the grates,
try "installing" fiberglas filters (make your own) behind the grates.
They will reduce the noise quite a bit without making much difference
in the air flow.
Dave
|
83.48 | | KDCFS1::LANGE | MADVAX - Beyond the thermal zone | Fri Dec 14 1990 09:36 | 15 |
| The noise seems to be mostly coming form he cold air returns.
Most notibly form the large grate in the living room.
What do you mean by "installing" fiberglas filters? Is this going
to restrick air flow. Could you further explain this please.
This sounds sorta like the insulated plenum/ductwork idea the
installer mentioned.
What I would like to know is, "is this really worth $350?"
Will I be a happy camper with a noticably quieter furnace or am
I throwing away $350?
confused...
GGI
|
83.49 | | CLOSUS::HOE | Daddy, what's transision? | Sun Dec 16 1990 22:17 | 16 |
| < Note 4056.3 by KDCFS1::LANGE "MADVAX - Beyond the thermal zone" >
You would probably loose. If the fan is running, there's bound to
be some noise from the blower, air moving through the filters and
the various other noise that the air ducts conduct and seeming
multiply; ie reverberation as the sound level bounces around
inside the duct.
A muffler system can be installed by looking at the frequencies
of the sound and setting tuned ports for the air system.
Insulating the air ducts does very little to reduce noise.
calvin hoe
BTW, I know what you mean; a hundred blower fans can be defening.
|
83.128 | Gas furnace in ATTIC? | GWRRA::BROWN | | Wed Jan 09 1991 08:39 | 16 |
| Greetings
Ok I've read all the other notes/conf on Gas/Oil/conversions from
electric heat...none referenced the following:
The local gas installers quoted me a price of $2800 for heat and $1800
for central air..problem/question I have is they stated they would
install the gas furnace in the ATTIC! (the AC goes outside). What
happens when it's time for repair/tune-up...??
Anybody out there have this kinda of setup? The unit is the super
duper efficiency cost you nothing to run cheaper than any type blah
blah...
Thanks folks
Canuck
|
83.129 | Have seen, but not lived with | EVETPU::IMPINK::mccarthy | Well Norm, lets go take a look. | Wed Jan 09 1991 11:19 | 8 |
| Back in my early days working with an electrian, such a setup was
done in renovated condo's near the Bunker Hill Monument. What ended up
happening for access was the entire ceiling in a square closet was
removeable to allow the unit to be installed, and removed if needed.
The furnace was for forced hot water, not hot air. The hot water tank,
20 gal's only, was also up there.
Brian
|
83.130 | I've seen it too | SSDEVO::JACKSON | James P. Jackson | Wed Jan 09 1991 11:37 | 6 |
| I've seen this in ranch houses in Austin. There's no basement due to the
limestone ("soil" is too kind a word). I observed horizontal FHA furnaces
in attic crawl spaces. I'm not sure that it would be any worse than the
horizontal FHA furnaces that I have in my under-floor crawl space in my
current house. As long as you can get to it to replace the filters, there
should be no problem.
|
83.131 | attic is just fine | PCOJCT::MILBERG | I was a DCC - 3 jobs ago! | Wed Jan 09 1991 12:32 | 25 |
| When I lived in Atlanta, I bought a brand-new, energy efficient, etc.
house in about 1982. It was a 2 story, colonial 'farm-house' (full
front porch) with
2 separate, gas FHA furnaces with air conditioning -
one in the basement for the first floor and one in the attic for the
second floor.
There was the normal, pull down stair to the attic and I had no problem
changing filters, normal maintenance, etc.
The setup was GREAT! Saved lots on both heating and air-conditioning
with the capability to regulate each floor - both daytime activities
and night-time sleeping.
When I can afford it, I will add a unit in the attic of my house in NJ
to take care of the second floor, not pump hot/cold air up from the
basement (thru the 1950's non-insulated ducts in the non-insulated
outside walls)!
I would definitely go with it!
-Barry-
|
83.132 | Y'all come see us, y'heah? | CIMNET::MOCCIA | | Wed Jan 09 1991 13:00 | 8 |
| Re .0
I have to guess from your signature that you're from the Great White
North. Actually, gas furnace/ac units on upper floors and in attics
are a very common practice in the southern and western U.S.
pbm
|
83.133 | ex | GWRRA::BROWN | | Wed Jan 09 1991 14:41 | 10 |
| Ok Thanks folks for your reply. I guess I'm having a problem with the
heat unit over my head rather than in the cellar.
Yup from the great white north...Went to the University of Ft. Bliss
Texas in El-Paso though and cant recall seeing "heat units" on the
ceiling (Air/water conditioners on the roof of most dwellings).
Thanks
Canuck
|
83.134 | Heated Attic? | EAGLE1::CAMILLI | | Wed Jan 09 1991 16:01 | 6 |
|
Could having a furnace in the attic in a cold/snowy climate
cause problems such as condensation (on the underside of the
roof) and ice dams on the eaves? Supposedly, almost all
attics have inadequate ventilation, but adding a furnace
might make some things worse.
|
83.135 | No heat left-over | BOSOX::GAGER | Swap read error-lost my mind | Fri Jan 11 1991 09:05 | 5 |
| RE: .6
New type furnaces don't have any "waste heat" that would accumulate
in the attic, due to thier high efficiencies.
|
83.136 | It doesn't matter... | LIEBE::PIZZELANTI | | Fri Jan 11 1991 14:36 | 9 |
| While the idea seems a good one, such as controling zones, making waste
space to good use etc., I would think a lower unit would be better
since the hot air doesn't have to be pumped downward since heat
naturally rises; by the same token an air conditioner in the attic
would be a good idea, although attics in the summer are terribly hot
so... The conventional set up I think is easier to service.
Personally, I m more interested in engineered solutions (ie. heat
pumps, etc)
Frank
|
83.137 | | SAHQ::DERR | Tom Derr @ALF | Fri Jan 11 1991 15:54 | 5 |
| re .8
Heated air will rise when surrounded by cooler air, thus in a vent it
wouldn't make any difference whether you were pumping the heated air up
or down.
|
83.138 | | RAMBLR::MORONEY | Shhh... Mad Scientist at work... | Fri Jan 11 1991 16:43 | 9 |
| re .9:
> Heated air will rise when surrounded by cooler air, thus in a vent it
> wouldn't make any difference whether you were pumping the heated air up
> or down.
Not correct. Otherwise chimneys wouldn't work.
-Mike
|
83.139 | rathole alert | SAHQ::DERR | Tom Derr @ALF | Mon Jan 14 1991 13:49 | 4 |
| re. 10:
Close the flue and see how fast the smoke left in the chimney escapes.
|
83.140 | | VMSDEV::HAMMOND | Charlie Hammond -- ZKO3-04/S23 -- dtn 381-2684 | Mon Jan 14 1991 15:01 | 6 |
| re: 11
...or close the vent and see how much good it does.
-- sorry, I couldn't resist. Please insert the smiley face of
you choice here:
|
83.73 | Where would you put FHA registers? | ESCROW::KILGORE | Wild Bill | Thu Feb 28 1991 15:16 | 34 |
|
Below is a rough idea of an addition I'm contemplating. It's a 20x16
family room with cathedral ceiling, connected to the existing house
by a 6' extension to the den. Rough guesses at windows, sky lights and
doors are shown by w's, s's and d's.
Heating is FHA, with existing registers in den shown by h(ot) and
r(eturn). Foundation is 4' frost walls.
I've talked to different contractors, and gotten different assessments
on the amount and placement of heating registers in the addition.
So if anyone out there has any ideas, or a similar project, I'd
appreciate your insight.
|
existing | new *-dddd-----------*
<== | ==> | |
| w
*- --------*------*-----------*------* w
| | | h | sss |
| | bath | w
| kitchen | | den w
| *- ---* |
| r | sss w
| * * *-----------*--ww--* w
| |-| | | |
| |-| | | |
| dining |-| living | *----wwwwwwww----*
| |-| |
| |
| |
*------------- ---------------*
|
83.74 | Under the windows | ODIXIE::RAMSEY | EMT's Save Lives | Thu Feb 28 1991 16:12 | 22 |
| Most common place for H(ot) registers to be placed is directly
underneath a window. I can only assume this is to help offset the cold
being added to the room by the window.
You have a lot of window space in the addition. I would look at the
direction of the prevailing cold winds. I would also look at what
would be the most typical furniture arragement patterns for this room.
I would put the register under the window that is most likely to get
the cold prevailing wind and least likely to be blocked by furniture.
These may be at odds with each other. I would fall back to heating the
window as priority one and furniture as priorty two.
You might put in two registars in places where you would normally only
put one. Like where you know a couch will most likely be. Put a
registar on either side of the designated couch area. The furniture
does not block the air flow but you still have heat on the wall with
lots of windows! You could run one duct to the middle of the addition
and them split it off into several smaller ducts.
Don't forget to put a ceiling fan in this addition to run backwards
during the winter to move the heat collected at the top of the vaulted
ceiling back down to people level.
|
83.75 | | STROKR::DEHAHN | No time for moderation | Fri Mar 01 1991 13:46 | 18 |
|
Another consideration is; where are the existing registers? It may make
your plumbing easier. How high is the ceiling?
Rooms with high ceilings can soak up a LOT of heat. It's not the square
foot area you're dealing with, it's the CUBIC feet of volume. Fans can
help but are not a panacea, they create their own problems. If this is
truly a cathedral ceiling, and fairly high, I wouldn't be surprised if
you would need registers on at least two of the three walls, if not
all.
Re:-1
A vaulted ceiling is one half of a cathedral ceiling, with a wall in
the middle.
CdH
|
83.50 | | CHIRPA::LEMIEUX | | Mon Sep 09 1991 14:39 | 14 |
| My furnace and ductwork are also not as quiet as I'd like. However, I'm
more interested in saving some oil (although I wouldn't mind killing two
birds). I'm entering this here because it's the only note I could find
that mentioned insulating plenums.
I am going to insulate my ductwork this Fall (strictly for energy
savings reasons) and it seemed to me that if you were going to insulate
the ductwork then you should insulate the plenum. Afterall, the plenum is
just the beginning of the ductwork. So, does this make sense; should the
plenum be insulated or are the possible savings relatively insignificant ?
Do they make an insulation to withstand the high temps or do you have to
buy an insulated plenum ?
thanks
|
83.53 | Microtemp device on FHA furnace - what function | AKOCOA::CWALTERS | | Mon Jan 13 1992 10:29 | 34 |
|
I have an intermittent problem on a Borg-Warner FHA gas system.
Checked out all the basics - pilot flame adjustment etc. Unfortunately
I didn't inherit the manual with the boiler.
Step by step:
Thermostat closes, relay triggers & gas main valve (apparently) opens.
I read the note regarding sticky valve pistons and I'm pretty certain
that is not the problem.
Boiler fires up, runs for a few seconds and then cuts out, never
getting hot enough to trip the fan limiter (so the fan never starts)
Setting the fan limiter all the way to the lowest temperature has
no effect, the boiler never gets hot enough before it cuts out.
When the valve cuts out, It *also* cuts off the pilot light and requires
a 5-min wait before I can relight the pilot. After a few cycles of
this, the thing works fine.
The pilot flame valve has a pair of wires going to a device mounted
in the upper refractory chamber. It's marked "Microtemp" & a model
number and looks like a thermocouple. I pulled this out, connected
it to a multitester and applied heat up to about 190deg. No effect.
Can anyone confirm what this device is, and what it is supposed to do?
Is it a one-shot or can it reset itself?
Regards,
Colin
|
83.54 | | KAOFS::S_BROOK | | Mon Jan 13 1992 10:54 | 12 |
| It sounds like a failsafe thermocouple to show that the burner has
actually lit. If it hasn't it is designed to turn off the entire
gas supply. (On the grounds that if the burner hasn't lit, there
must be something wrong with the pilot light and that the pilot
thermocouple may have failed too).
Sounds like time to get out the repairman --- when it comes to the
safety devices like this, even I, the inveterate I'll have a go at
repairing anything type, prefer to leave it to someone who knows the
device.
Stuart
|
83.55 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Mon Jan 13 1992 13:29 | 7 |
| I don't think there's much safety risk in replacing a thermocouple (if that's
what you're dealing with).
Once when I was visiting my parents, the gas-fired water heater died. They
called the gas company. The gas company guy said that it was the thermocouple,
he couldn't fix it, but that it was simple job that I could do. I picked up
a replacement at a hardware store, and installed it in about 10 minutes.
|
83.56 | it was the thermocouple after all | AKOCOA::CWALTERS | | Tue Jan 14 1992 09:22 | 9 |
|
.1 is right - I took no risk and called a repirman. However,
I was wrong about it being the source of the problem it was
the main pilot thermocouple that had burned out due to a bad pilot.
Thanks,
Colin
|
83.141 | Gas Heater shuts off pilot light | ANVIL::BUEHLER | Pro-choice. One choice. Life. | Mon Sep 28 1992 18:15 | 22 |
| I've got a finnicky gas heater. I can light the pilot light just fine, and
the burner will kick in and everything will work wonderfully. Until the thermo-
stat tells the heater to shut off. It shuts off both burner and pilot light.
I can then relight the pilot and start the whole thing all over again.
I had the gas company come around to fix it (took two tries - I was not pleased
with them at all). That fix lasted me the past heating season. Now that I've
turned it back on again (relit the pilot), I'm getting the above behavior again.
The thermocouple looks pretty beat up, but I have no idea what a good thermo-
couple looks like. That was one item replaced during the 'fix'.
1. Does this behavior ring any bells for anybody?
2. Does anybody know a good gas heater repair service in the Nashua area?
3. Does anybody have any comments on conversion of a heater from pilot light
to spark ignition?
For what it's worth, my water heater also runs from a pilot light and has had
no problems at all.
JB
|
83.142 | one recommendation | AKOCOA::CWALTERS | | Tue Sep 29 1992 09:40 | 13 |
|
Wells & Son, Crown St nashua fixed a similar problem on my furnace
for $50. Included a new thermocouple and an adjustment to the
pilot flame. It has worked fine since.
Only thing I know about conversions to spark ignition is that some
programmable thermostats will not work with spark iginition, so check
that when you convert.
Regards,
Colin
|
83.143 | Pros and cons of summer pilot off syndrome | RESYNC::D_SMITH | | Tue Sep 29 1992 14:37 | 7 |
| Back to the basenote...I always heard it was not a good idea to shut
the pilot down for the summer. Maybe it's do to the thermocoupler corrosion
factor?
I would do it myself if it wasn't for that rumor. Why pay the gas comp.
anymore than we do. With no competition, they charge enough as it is.
Dave'
|
83.144 | some gas companies have service contracts | DUSTER::MCDONOUGH | | Tue Sep 29 1992 14:39 | 13 |
| reply .0
Not sure in N.H., but Boston Gas has option where you can pay then $30
a year for a service contract. The $30 covers all service costs. Last
year we bought a new gas furnace. The electric pilot was not working
properly. The company we bought it from told us to have the gas
company come out and fix it and send them the bill. After three times,
the manufacturer finally figured out what they had done wrong and were
able to fix it. Each of the three times the gas company came out, it
was $25 as a base and more depending on how long they stayed. This
year we'll probably get the service contract.
Rhonda
|
83.145 | It looks corroded alright | ANVIL::BUEHLER | Pro-choice. One choice. Life. | Tue Sep 29 1992 19:02 | 9 |
| > Back to the basenote...I always heard it was not a good idea to shut
> the pilot down for the summer. Maybe it's do to the thermocoupler corrosion
> factor?
The thermocouple does look corroded and I did shut the pilot off for a couple
months this summer. It was also shut down prior to my purchasing the place,
where I had problems immediately afterwards. Perhaps that's the answer.
JB
|
83.146 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Wed Sep 30 1992 13:21 | 7 |
| re .7:
Slightly off the topic, but I've had a very bad experience with Boston Gas's
service people. We bought a service contract, and ended up paying $125 to
an electrician to fix what Boston Gas broke. They wouldn't admit that they
had been the ones who rewired our boiler controls incorrectly. We just got
the renewal notice for the service contract, and I immediately tossed it.
|
83.147 | | DUSTER::MCDONOUGH | | Wed Sep 30 1992 16:01 | 12 |
| re .9
I had execellent service from Boston Gas (once they finally arrived 23
and 1/2 hours after the call). They didnt touch the electrical part of
the system. My husband stayed with the service man while he was
servicing the system because we were afraid he would break something he
knew nothing about. I can understand why you wouldnt renew with them
and your misfortune will make us doublely careful if/when we have to
call them again. I think with Boston Gas, it's the luck of the draw as
to which service man you get. Some are excellent and others ....
Rhonda
|
83.148 | Public Service is Pot Luck | ANVIL::BUEHLER | Pro-choice. One choice. Life. | Thu Oct 01 1992 12:20 | 9 |
| >I think with Boston Gas, it's the luck of the draw as
>to which service man you get. Some are excellent and others ....
No question. I'd say that public service companies are like that. I had the
same kind of experience with Energy North up here in Nashua. As diagnosticians
these guys rated pretty low on the scale. But one workman was well ahead of the
other in skill.
JB
|
83.51 | | TNPUBS::MACKONIS | We are a compromise of nature! | Tue Nov 17 1992 12:43 | 9 |
| Can you tell me where I can get insulating jackets for the ductwork? I would
rather do this myself than pay a heating contractor. I really would rather
not pay any more $ to they guys who did the shabby job on my house.
It looks simple enough. Half my pipes are wrapped now -- don't ask why the
other half isn't.
dana
|
83.52 | I'd like some of this too. | HDLITE::NEWMAN | Chuck Newman, 297-5499, MRO4-1/H16, Pole J13 | Tue Nov 17 1992 21:21 | 4 |
| I would also be interested. I'm hooking up a wood furnace, and was thinking
about wrapping the sheet-metal shroud in this.
-- Chuck Newman
|
83.127 | Literature from my gas furnace's manufacturer | HDLITE::NEWMAN | Chuck Newman, 297-5499, MRO4-1/H16, Pole J13 | Thu Feb 17 1994 14:09 | 139 |
| I wrote to the manufacturer of my gas furnace (Heat Controller, Inc.) about
hooking up duct work to provide combustion air for my furnace, and got some
interesting information (this worked so well for my wood furnace, I figured I'd
do it for my gas furnace too).
From of the literature:
--------------------------------------------------------------------------------
WARNING: ALL FURNACE INSTALLATIONS MUST COMPLY WITH THE NATIONAL FUEL GAS CODE
AND LOCAL CODES TO PROVIDE ADEQUATE COMBUSTION AND VENTILATION AIR.
Combustion air requirements depend on whether the furnace is in an open,
unconfined location or in a confined space such as a closet or small room.
FURNACES LOCATED IN AN UNCONFINED SPACE AND USING INDOOR AIR FOR COMBUSTION
An unconfined space must have at least 50 CUBIC FEET volume for each 1000 BTUH
of the TOTAL INPUT FOR ALL COMBUSTION APPLIANCES in the space. The following
table gives examples of the room sizes required for different inputs. The room
dimensions are based on an eight foot ceiling height
Example table for rooms with an 8' ceiling:
BTUH Min. sq. feet with typical room size
input an 8' ceiling with 8' ceiling
50,000 336 14'x24 or 18'x18'
75,000 469 15'x31 or 20'x24'
100,000 625 20'x31 or 26'x30'
125,000 833 23'x34 or 26'x30'
150,000 938 25'x38 or 30'x31'
A confined space is any space housing a combustion appliance with dimensions
smaller than those shown in the above table. A confined space must have TWO
OPENINGS INTO THE SPACE. ONE MUST BE WITHIN 12" OF THE CEILING AND THE OTHER
MUST BE WITHIN 12" OF THE FLOOR. Size the openings based on how they connect to
the heated area or to the outside, and by the input of all combustion appliances
in the space.
If the confined space is within a tightly constructed building, combustion air
must be drawn from outdoors or from an area freely communicating with the
outdoors.
USING INDOOR AIR FOR COMBUSTION
If combustion air comes from a heated area, EACH opening must have at least one
square inch of free area for each 1,000 BTUH of total input in the space. In no
case should each opening have less than 100 square inches of free area. Here
are examples of typical openings required.
BTUH Free Area
input Each Opening
50,000 100 sq. inches
100,000 100 sq. inches
150,000 150 sq. inches
Caution: Never take combustion air from a heated space containing a fireplace,
exhaust fan, or other device that can cause a negative pressure.
USING OUTDOOR AIR FOR COMBUSTION
If combustion air comes from outdoors through VERTICAL DUCTS the opening and
ducts must have at least one square inch of free area for each 4,000 BTUH of
total appliance input. Here are some typical sizes.
BTUH Free Area Round
input Each Opening Pipe Size
50,000 12.50 sq. inches 4"
75,000 18.75 sq. inches 5"
100,000 25.00 sq. inches 6"
125,000 31.25 sq. inches 7"
150,000 37.50 sq. inches 7"
Caution: Never take combustion air from an attic space equipped with power
ventilation if the ventilation system can be powered in the heating season.
If combustion air comes from outdoors through HORIZONTAL DUCTS, the opening and
ducts must have at least one square inch of free area for each 2,000 BTUH of
total appliance input. Here are some typical sizes.
BTUH Free Area Round
input Each Opening Pipe Size
50,000 25.00 sq. inches 6"
75,000 37.50 sq. inches 7"
100,000 50.00 sq. inches 8"
125,000 62.50 sq. inches 9"
150,000 75.00 sq. inches 10"
If the furnace is in a location with an exhaust fan, there must be sufficient
ventilation to prevent the exhaust fan from creating a negative pressure in the
room.
Combustion air openings must NOT BE RESTRICTED in any manner.
CONSULT LOCAL CODES FOR SPECIAL REQUIREMENTS.
Air opening in the furnace casing front, return air grilles, and warm air
registers must not be obstructed.
----------------------------------------
The literature shows illustrations for outdoor air using vertical and horizontal
ducts. The building is a single room with a water heater and a furnace, and an
attic (with gable or soffit vents).
VERTICAL DUCTS:
This drawing shows a vertical duct (labeled inlet air) starting in the attic and
ending just above the floor next to the furnace, and a grate in the ceiling
(with a note: outlet air in attic must be above insulation).
HORIZONTAL DUCTS:
This drawing shows a horizontal duct (labeled inlet air) going out the side of
the house just above the floor, and another (labeled outlet air) just below the
ceiling.
--------------------------------------------------------------------------------
This all left me with a couple of questions:
1) Why two openings? The only think I could think of would be for pressure
differentials, but especially in the case where both ducts end in the attic I
don't see how this would help.
2) If a plenum was attached to the furnace covering all openings (except the
exhaust, of course) to which both of these were attached, I would think that
should accommodate these conditions. Any comments? Probably want to insulate
the ductwork and the plenum.
3) If the ductwork contained both vertical and horizontal sections, (e.g.,
down from the attic then over to the furnace), I would think that their sizes
could be treated separately (e.g., 6" duct coming down from the attic, then 8"
duct going over to the furnace).
B.T.W., for the wood furnace I have a single 4" duct hooked up to the draft
blower, and I usually have that throttled way down.
-- Chuck Newman
|
83.57 | First Floor Only FHA GAS heat | KISMIF::STUKALIN | | Tue May 24 1994 13:25 | 25 |
|
I am thinking about converting house heating system from electric to
gas. The house is colonial with electric radiators in each room. I have
no problem with existing system, exept cost.
One of the possible options is to convert 1st floor only to gas FHA. The
thought is that it will cost less, gives most bang for the buck, and
retaines some of the flexibility of electric on the second floor.
The house 2nd floor is well insulated. The first floor has all the
doors, vents ( range top, and dryer ), and half the basement is under
the house garage. All of these add up to drafts and heat loses on
the 1st floor. The second floor gets the radiant sun heat, and
convectieve heating from first floor ( heat rises ).
All seems great in theory. Has anybody seen something like that done.
Could yo see any problems I am overlooking.
Thanks in advance for any advice,
Felix
|
83.58 | | TLE::FELDMAN | Software Engineering Process Group | Tue May 24 1994 13:40 | 4 |
| This has been asked and answered numerous times. Please
see note 1111.47 for a directory of relevant notes.
Gary
|
83.59 | Reply to .1 | KISMIF::STUKALIN | | Tue May 24 1994 16:25 | 10 |
|
to .1
I checked 1111.47 and 1111.51 before posting this note. I read thru
notes and replies for 19, 802, 2466, and 1909. There is no postings
I can find that has ONLY first floor converted to gas. If you aware
of such a note, please post a pointer.
|
83.60 | partial answer | TPSYS::WEST | | Tue May 24 1994 17:34 | 61 |
|
I have a situation which parallels yours:
I have a small cape (28 x 32) which has oil FHA for the first floor.
It has old windows and is not insulated (75 yrs old)
The full upstairs was insulated and then finished but the owners put in
electric baseboard heat (about 30 L.F. of it), and a separate thermostat
on the 2nd floor for it.
Basically we then have two zoned heat.
1. We would keep the upstairs cool (55) most of the day and night, and
just turn it up when needed in the evening. It was (and IS)
expensive and that would limit our use.
Downstairs the oil heat would be kept about 65 or so.
About $1000/winter oil cost, plus electric bills in the cold months
that could get to 80-90 bucks (normlly about 40-50)
2. Then we got a large wood stove for the basement (old Jotul 118 that
takes 26" logs and used 4-6 cords of wood per season).
We used it to heat the basement (previously unheated and down
to 45 or so in winter) and the whole first floor, using oil
only at the end of the night or in extreme cold or wind to help
the wood stove).
Total winter cost about $1000/winter for both oil and wood.
PLUS: hardly ever ever ever turned on the electric heat
upstairs. Wood heat would permeate up from basement steps
and whole first floor and got up into second floor - very
noticeable difference.
Final Plus: Your choice of heat source should the power go
out or something happen to one unit or the other (like when
oilfurnace started making noise Christmas Eve when it was 10
degrees) -- just turn on the electric and wood.
SO:
depending on how open your stairs are and circulation, you may
get some additional 2nd floor benefit from your first floor
oil heat.
you get some flexibility in heat control of floors
you get backup in case of failure (one way -- cant run a
FHA fan with no juice).
Bob
|
83.61 | First floor is plenty | BOBSBX::CHIQUOINE | Who audits the IRS? | Wed May 25 1994 08:51 | 19 |
| Our house has oil FHW with two zones. One for the basement, (which is
never turned on) and one for the first floor. There is no heat at all
in the second floor. The house is a high post cape with cathedral
ceilings, so there's a lot of air space upstairs. In the winter the
second floor is always at least 5 degrees cooler than the first floor,
but I kind of like it that way (though my wife would like heat in the
bathroom).
Our last house had electric heat and wood stoves in the basement and
living room. We never turned on the electric heat except when we left
for extended periods or had guests in the coolest upstairs room. I
second the experience of .-1 who found that running the woodstove in
the basement help everywhere.
Kind of like the apartment I lived in in college. The crew above us
paid about 1/3 of what we did for heat and kept the thermostat set
higher!
Ken
|
83.62 | my house has 5 rooms, his only has 4 1/2 | CSLALL::NASEAM::READIO | A Smith & Wesson beats four aces, Tow trucks beat Chapman Locks | Wed May 25 1994 11:38 | 6 |
|
So, what's wrong w/ note 907? ....Jeezis
|
83.63 | | TLE::FELDMAN | Software Engineering Process Group | Wed May 25 1994 13:57 | 17 |
| re: .2
Note 722 is relevant, though it may not be obvious that
it is. There are many others that are relevant one way
or another, and that are appropriate to continue.
In any event, please don't start new topics when existing
topics would suffice. Alternatively, if you feel a need
to start a new topic, please try to use a title that
emphasizes the distinction you're trying to make. That
will always help the next person down the line. (Consider
that you researched four topic lines; the next person
now has at least five to look at. We all need to help
keep things organized, or it will become totally impossible
to find things.)
Gary
|
83.64 | Thanks for replies. | KISMIF::STUKALIN | | Wed May 25 1994 14:33 | 20 |
|
reply .5
I do not see why 907 is relevent. Did you read the note or just first
line.
re .6
Thanks for pointer to note 722. It is not relevent to the question I
asked, but informatieve anyway. Your point about " Emphasizing
distinction in the title " is well taken. Moderator please feel free
to change title to more apropriate. ( I would try myself, if I can
figure out how )
I would like to thank everybody else who replied and send mail.
Felix
|
83.65 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Wed May 25 1994 14:46 | 5 |
| > Moderator please feel free
> to change title to more apropriate. ( I would try myself, if I can
> figure out how )
Go to the base note and do SET NOTE/TITLE="new title"
|
83.66 | HELP! what a great title wording | CSLALL::NASEAM::READIO | A Smith & Wesson beats four aces, Tow trucks beat Chapman Locks | Wed May 25 1994 18:04 | 20 |
|
> I do not see why 907 is relevent. Did you read the note or just first
> line.
If I were a curious person, I'd read the note title and say to myself "now,
there's a subject I should read if I'm interested in converting to one form
of home heating vs. another"
Even if the discussion rambled within the base note, it's still easier to
find the info than the current state of affairs where everyone feels their
situation is unique.
Changing heating systems is changing heating systems PERIOD. It doesn't
matter whether you have a 3 1/2 bath house and two dogs or a 2 1/2 bath
house and a parakeet.
The title of 907 fits your problem
|
83.149 | Maintenance on a forced hot air gas burner | SMURF::CMEYER | Mainstream Bohemian | Mon Sep 26 1994 13:03 | 16 |
|
Is any sort of maintenance recommended for a gas-fired, forced hot air
burner? The Bryant unit I have is about 20 years old and I don't
know if it's ever been serviced. Except for changing the air-intake
filter each year, I haven't done anything to it in the six years
I've owned it.
Also, if I should have someone come in to service it, does anyone
have a recommendation for a company in the Lowell, Mass. area?
(I looked for an appropriate topic in the index, but found none
that seemed to fit. If there is one, I'd appreciate a pointer.)
Thanks,
Craig
|
83.150 | | QUARK::LIONEL | Free advice is worth every cent | Mon Sep 26 1994 15:48 | 7 |
| Do you have the manual for it?
Usually the only service needed for a gas-fired burner is to add oil to the
blower motor (there's usually a small tube you drop a few drops in) - use
motor oil.
Steve
|
83.151 | oil | JOKUR::FALKOF | | Mon Sep 26 1994 17:04 | 2 |
| re -.1, use motor oil for small electrical motors, not 10W-30
automotive motor oil.
|
83.152 | | QUARK::LIONEL | Free advice is worth every cent | Mon Sep 26 1994 19:22 | 4 |
| 10W30 automotive oil is what I meant. It's what my Weil-McLain
manual recommends as well as the company which installed it.
Steve
|
83.153 | engine oil .ne. bearing oil | LEZAH::WELLCOME | Steve Wellcome MRO1-1/KL31 Pole HJ33 | Tue Sep 27 1994 09:26 | 17 |
| re: .3
They may recommend it, and it probably works, but it's NOT what
should be used for bearings. Engine oil is designed to emulsify
water and hold it in suspension. Oil for motor bearings should
precipitate water, so it drops out of suspension and doesn't
corrode the bearing. There are a bunch of other differences
between engine oil and bearing oil too, but that's the major one.
Now, in the bearings on your oil burner, it's probably only of
theoretical interest because it's unlikely you'll get significant
water in the oil, and the bearings aren't all that high-precision
anyway. But ideally, you should probably use something like a
#20 non-detergent oil specifically formulated for electric motor
bearings. I suppose most people would never take the trouble to
find it though, so Weil-McLain recommends something that will work
and people will be likely to find.
|
83.154 | also interested | CSC32::KING | | Tue Sep 27 1994 20:09 | 14 |
|
I was also wondering what maintenance was needed. It seems most
heating companies have some annual checkup package available,
and was wondering if it was really necessary. I guess a check
of belts, if any, would be part of that. Isn't there also some
check of the flame color to see how efficient the flame is
burning? Related, but maybe a different topic, aren't there
some thermostat checks/adjustments that can be made? My 1914
house has a BIG old gas/FHA furnace, that works great. I just
want to keep it that way. Probably any company would want to
sell me a newer model if they see it. Thanks.
Peter
|
83.155 | | QUARK::LIONEL | Free advice is worth every cent | Tue Sep 27 1994 22:11 | 6 |
| The company which installed my system said no maintenance other than
the oiling of the bearings was required. I'm sure you could find
someone willing to take your money. Unlike an oil burner, a gas
burner doesn't go out of adjustment.
Steve
|
83.156 | No maintenance blower | SMURF::CMEYER | Mainstream Bohemian | Wed Sep 28 1994 01:02 | 8 |
| No owner's manual, Steve. Also, there doesn't seem to be any way
to oil the blower without removing it. There's a tag on it that
says "pre-lubricated," which I assume means it requires none.
I can't believe there's something in this house that I don't
have to spend money on. (I suspect I'm the main reason for
Home Depot's rapid expansion.)
|
83.157 | | QUARK::LIONEL | Free advice is worth every cent | Wed Sep 28 1994 10:57 | 4 |
| Well, it won't cost more than $50 or so to have someone out to look
at it and advise you. If it makes you feel better, do it.
Steve
|
83.158 | | KAOFS::B_VANVALKENB | | Tue Oct 04 1994 12:05 | 11 |
| Try vacuuming (sp?) the burner area and the blower area.
Oil the motor if required (I use light wieght machine oil)
Check belt for tension and wear.
Clean out bottom of chimney...black soot and dead birds...YUK !
About every 3 years I take my blower right out and try to give it
a real good cleaning. These squirrel cage blowers can trap a lot of
dirt.
Brian V
|
83.67 | Gas furnace bangs after blower goes off | VAXUUM::FARINA | | Mon Dec 18 1995 19:23 | 21 |
| There are several notes on gas furnaces, but since this one mentioned
noise, I thought I'd ask here.
When I bought my house almost two years ago, I was very pleased that it
has a gas furnace. When the building inspector checked out the house,
he said that it was relatively new.
I had always heard that gas heat is extremely quiet, but mine is not.
Not only is it loud as the heat is on (I haven't paid close attention
to whether it's the cold air returns or the actual heat registers, but
will tonight), once the heat goes off, there is a loud bang! The
blower stops, there is a pause, then a bang. I am totally clueless
about this stuff, so would appreciate help on what to look for. Has
anyone encountered this before?
I can certainly call Energy North and have them come to service it, if
necessary, but if there is something simple I can look for myself, I'd
rather do that first!
Susan
|
83.68 | Expansion/contraction. | REFINE::MCDONALD | shh! | Tue Dec 19 1995 08:24 | 21 |
|
My guess is that the BANG being heard is the a stretch of ductwork
(probably the main trunk line) that is expanding and contracting.
There are a number of things that can cause this such as:
- It can be caused by a system that is too pressurized (the
blower is set too high, or there aren't enough registers to effectively
distribute the outgoing air.
- I've also seen one case where the cold air return was undersized and
the duct actually collapsed a bit whenever the furnace kicked in,
causing a bang.
- Most common though, is due to simple contraction and expansion due
to the heat. Most trunk lines have an "X" pressed into the sheet
metal to prevent noise due to expansion... but not always.
Start by tracking down the location where the bang is actally coming
from.
- Mac
|
83.69 | set screw | JOKUR::FALKOF | | Tue Dec 19 1995 08:46 | 5 |
| I once had a bang after the unit turned off. Seems the squirrel cage
fan blower was loose on its shaft. So, when the motor stopped, the cage
kept turning a fraction of a turn until the set screw found a stopping
point on the shaft. A quick turn of a screwdriver secured the set screw
and the bang went away.
|
83.70 | Thanks for the suggestions! | VAXUUM::FARINA | | Tue Dec 19 1995 11:46 | 6 |
| The bang does sound like it's in the ductwork under my bedroom. I'll
try to be in the basement when it goes off. Thanks for the
suggestions. I think I know what the problem may be, since you said
that "not enough registers" could cause the problem. The ducts to the
bedrooms are pretty much closed off. I'll try opening them to see if
it alleviates the problem. --S
|
83.162 | | CSLALL::NASEAM::READIO | A Smith & Wesson beats four aces, Tow trucks beat Chapman Locks | Thu Jan 11 1996 13:34 | 9 |
83.188 | Sequence of events for gas hookup in Nashua | SKYLAB::FISHER | Gravity: Not just a good idea. It's the law! | Thu Oct 10 1996 16:24 | 102 |
83.189 | never easy | HNDYMN::MCCARTHY | A Quinn Martin Production | Fri Oct 11 1996 06:58 | 9 |
83.190 | Another installation story, Do-It-Yourself version | VAXCPU::michaud | Jeff Michaud - ObjectBroker | Fri Oct 11 1996 12:31 | 74 |
83.191 | | SKYLAB::FISHER | Gravity: Not just a good idea. It's the law! | Fri Oct 11 1996 14:52 | 12 |
83.192 | Need advice on furnace work | DECWET::FARLEE | Insufficient Virtual um...er.... | Mon Jan 27 1997 00:28 | 33 |
| Well, I'm typing this in the cold...
Early this morning, the entire house smelled "hot". Not
electric-wiring-hot, but hot-iron-on-clothes hot.
Well, we crawled through the entire house and couldn't find the
problem, although it did seem stronger near the heat registers!
As the morning wore on, the house cooled down, and we noticed that the
furnace wasn't kicking on... Bad sign!
This is in Seattle, so it could be worse, still, the lows are around 20
right now, so it could be better.
We finally got someone out this afternoon, who said that our 8-year-old
Carrier unit had a "pretty much dead" blower motor (I can sometimes
coerce it into running, I suspect sticky bearings.) and the "control
circuit board" in the furnace is completely dead.
Now, the estimate for repairs is $500 plus tax, but they immediately
started pitching the idea of replacing it to the tune of $1300. They
said that there's lots more that could start going wrong, and that
"they just don't last much over 10-15 years anymore".
So, my questions: (finally!)
1) Do these estimates seem at all reasonable? In the ballpark?
2) The statement that furnaces aren't expected to last much over 10
years really surprised me. What is your experience with recent
FHA furnaces?
Thanks,
Kevin
|
83.193 | If $500 is good - then I'd go for the whole thing | ZEKE::ASCHNEIDER | Andy Schneider - DTN 381-1696 | Mon Jan 27 1997 09:48 | 29 |
| re: duration of FHA furnaces
We have a Bryant unit that's 16 years old and it's still working
fine. There aren't many things that can go wrong with a FHA
furnace - blower, burners, and heat exchanger. The blower going
bad is obvious, like you've experienced. The burners don't
really go bad - they can burn out or have the gas regulators
go bad -b ut you usually start seeing problems visually before
that goes. The only real "invisible" problem that can occur
is with the heat exchanger. If one of these starts to burn
out (get a hole in it), it can leak CO into the house, which
can be dangerous. We have a digital-readout CO detector in the
house, and as of now it still reads 0 most all of the time.
When we had our furnace serviced this past fall, they cleaned
it all up and said that the only thing they couldn't verify was
the solidness of the exchanger - and to keep an eye on the CO
level as it was one of the early-warning-signs that the exchanger
might be going south.
I can't answer you as to whether $500 is valid for a blower
replacement - but if it's $500 vs $1300, I'd be tempted to go
for the whole new unit so you start from ground zero on the
whole unit - plus you'll probably get a more efficient unit in
the deal as well. Up here in NH you can't mess around with
nickel and diming a furnace - losing heat when it's -10 with
a -40 wind chill factor ain't fun!
andy
|
83.194 | | STAR::DZIEDZIC | Tony Dziedzic - DTN 381-2438 | Mon Jan 27 1997 10:03 | 10 |
| One of the "improvements" which have been made to forced hot air
furnaces over the past decade or so is to reduce the thickness
of the heat exchanger to speed up initial heat transfer. This
has the side effect of reducing the useful life of the exchanger;
the thinner metal is more susceptible to stress cracking. I've
heard numbers in the 15-year range for furnaces of recent vintage.
If you're switching from a 80% efficiency unit to a 95%+ unit you
might be able to justify the difference between a $500 repair and
a $1300 replacement in reduced energy costs.
|
83.195 | Expected furnace life only ten years??!! | WRKSYS::RICHARDSON | | Mon Jan 27 1997 10:07 | 10 |
| I'd be *mad* if my furnace only lasted ten years! My FHA gas unit is 25
years old, and it's fine. Well, it's burned out a few thermocouples in
its time, but not recently. (I suppose a newer one would be marginally
more efficient, but since we only heat three rooms of the house in the
winter, the heating bill is real small anyways, so the payback period
would be longer than my lifetime.) Bad enough that water heater tanks
don't last - I've replaced two of those in fifteen years (the gas-fired
one once and the solar preheat tank once).
/Charlotte
|
83.196 | Not much help, but... | FOUNDR::DODIER | Double Income, Clan'o Kids | Mon Jan 27 1997 10:48 | 24 |
| re:192
Sounds like it's time to start reading up on your furnace. You
don't need to be an expert, but there are certain things that you
probably should know.
In my case, I have forced hot water oil, but it also has a control
module. The control module has a couple of leads labled B1 and B2. They
are the neutral and hot wire feed to the ignition module, which starts
the blower and lights the furnace when the boiler temperature goes below
a certain point. Your system should be even simpler.
The point being that I can take a meter to B1 and B2 myself and
help isolate down the possible cause of the problem, where you're at
the mercy of the repair person. If they say something's bad, you have
to take their word for it, and if they're guessing and wrong, then they've
already set you up by telling you to expect "other things" to go bad.
Without knowing your system, I can't say whether replacement is
worth while or not. Your best bet at the moment would be to spend time
with the repair person asking questions and learning as much as possible
about your system.
Ray
|
83.197 | My story | 25421::FALKOF | | Mon Jan 27 1997 12:45 | 11 |
| Several years ago, I replaced a FHA furnace. The generic, contractor's
unit that was installed was mfd by Magic Chef (the stove/oven people).
The old heat exchanger went bad because the humidifier had been
installed above the exch and condensation over the years corroded the
metal until a hole started to grow.
Lesson: the humidifier should be in the return side, not the feed side
of the warm air.
Several years later, we moved, so I don't know if that furnace is still
there. Good luck.
|
83.198 | replace if builder special | CPEEDY::BRADLEY | Chuck Bradley | Mon Jan 27 1997 13:21 | 26 |
|
most manufacturers of things that are sold as part of a house have
several lines of different quality. most include a line of builder's
specials. for an oil fired, hot water system, there are lots that
are over 50 years old. in a new house, many fail in five to ten years.
a agree that more knowledge will be a big help. get the model number
and find out where it sits on the quality scale. the lower it is,
the more likely you should replace it. ask a dealer.
if you can not find out, use the rest of the house and possibly the
neighborhood as a guide. if the dishwasher or stove has already
failed, or the plating has worn off the doorknobs, you should suspect
the furnace is also probably a builder special. if you are in
a development, see what has failed for the neighbors.
there is lots of valuable info in this conference even if you are
not going to DIY.
get several estimates, and check references. don't be surprised to
get one estimate that is double another. check carefully what is
included. one might propose using your old blower (that
is going bad). another might not remove the old unit,
or might add the charge to dispose of it at the local dump.
good luck.
|
83.199 | ... And Now , the Rest of the Story... | DECWET::FARLEE | Insufficient Virtual um...er.... | Wed Jan 29 1997 12:17 | 38 |
| Follow-up to .192:
Well, the more I got to thinking about the less it was adding up.
Furnaces have hi-temp cutoffs that are supposed to keep it from getting
hot enough to damage itself (or torch your house!). Why should the control
board go out at the same time as the blower? And, if I could get the
blower to run, why was it called "dead"?
I went through the meager docs that I had for the furnace, looking for the
location of the "fusable links" that are supposed to be the primary failsafe
in the furnace. I saw references to "manual-reset hi-temp cutoff switches"
that are only in some models (mine). Sure enough, I went spelunking in the
guts of my furnace and found such a switch on the top of the blower unit
which had never been reset. I pushed it, and closed up the furnace and
it immediately started up!
Scratch one "dead control circuit board"
Now, the blower motor was definately struggling to spin up, and not always
making it. Nonetheless, I cancelled my order for a new furnace, and warmed
the house up for the night.
In the morning a furnace technician (from a DIFFERENT place!!) came out
prepared to install a new blower motor, tore it down and informed me that,
"There's nothing wrong with this blower that a good cleaning and some oil
won't fix!".
Scratch one "dead main blower motor".
Morals of the Story:
*Maintain your equipment better than I did.
*Get a second opinion when somebody tells you that you need expensive work done.
*Get to know your own equipment so that incompetent/dishonest techs can't
take advantage of you.
|
83.200 | Knowledge = $$$ (saved in this case) | FOUNDR::DODIER | Double Income, Clan'o Kids | Wed Jan 29 1997 12:39 | 13 |
| re:199
Congrat's on your success. If the blower motor has brushes, the brushes
can wear or you could get dust, or possibly oil in there that would cause
a poor contact with the commutator. I think this is what they look for
when they look for "dead spots" on a motor. As with any motor with
brushes, cleaning the commutator can sometimes be all that's needed.
As you found, there are good techs and bad, and having a little
knowledge can mean the difference between getting taken or not. It's
always nice to hear a success story.
Ray
|
83.201 | Help for musty odor? | 11666::GERACE | Cindy Gerace @297-3884 | Wed Apr 09 1997 13:34 | 23 |
|
I think I wrote about this problem a couple of years ago, but I thought
I'd try again since I haven't solved it. 4 years ago I had a new
2-stage gas heater installed. After it was installed, I noticed a
musty odor in the house whenever the heat ran. Knowing that the
previous owners never had the ducts cleaned, I figured after 30 years,
they could use it, so I had them cleaned. The cleaning helped reduce
the dust, but the house still has that musty/stuffy smell. I change
the filter regularly. I've asked the gas company about it and they
weren't any help. My basement is dry - the dehumidifier doesn't run
much at all until summer.
So, I was wondering - is there a way to pull fresh air from outside and
have it go through the heater? I'm thinking that since I live alone,
the house is closed up tight most of the time, so maybe it's just the
recirculated air that gives off the musty smell?
Does anyone know if there is someone I can call who specializes in
problems like this?
Thanks,
- Cindy
|
83.202 | | skylab.zko.dec.com::FISHER | Gravity: Not just a good idea. It's the law! | Thu Apr 10 1997 13:21 | 12 |
| If you have a forced hot air system, I should think it would be pretty easy to
make a small connection between your return air duct and the outside, if it is
not done already. My system has one although it is not obvious. The return air
ducts in the basement are really just the space between the floor joists, with
some sheet metal covering the bottoms of the joists. In any case, this just
goes along up to an outside wall, and outside, you can see a little vent hole.
I wonder...you might check to see if you already have such a thing and look what
is around outside where the vent is. Perhaps there is something musty/smelly
there.
Burns
|
83.203 | Check your cold air returns.... | FOUNDR::SKABO | Expect Nothing U never disappointed | Thu Apr 10 1997 13:25 | 24 |
| re -.1
Hello Cindy...
There was a story last night on one of the news shows (20/20 or
something like that) about a series of children becoming very sick (not
to scare you...) in the Cleveland, Ohio area - turned out that most of
these homes had forced hot air systems, and the furnace was taking the
basement air only, as they had no cold air returns from the upstairs living
area. This was causing mold spores being sent through out the house.
So you may want to check to see where your cold air is coming from
to your furnace.
As for pulling air from the outside, it could work, but to heat the
outside air from -0 to 70, you will use a lot of gas... First check
your cold air returns.
Also, if you have a humidifier connected you may want to have that
checked out.
Good Luck,
Tom
|
83.204 | | USDEV1::GERACE | Cindy Gerace @297-3884 | Thu Apr 10 1997 14:25 | 20 |
|
Hi Tom,
Thanks for the info and the e-mail. I will have the cold air returns
checked out - that sounds like a definite possibility. There was a
humidifier on the old furnace, but it had been disconnected and it was
removed when I had the new one installed. I had hoped cleaning out the
ducts would get rid of any moldy dust that was leftover from the
humidifier.
How much of a vacuum does as cold air return create? I was wondering
if I a piece of paper would stick to the return to show that it was
working.
Does it make more sense to call the gas company since they installed
the furnace or an independent heating company?
Thanks again,
- Cindy
|
83.205 | | REGENT::POWERS | | Mon Apr 14 1997 10:00 | 9 |
| Yes, job #1 is to check the return path for your "used air."
Pulling air in from outside won't solve the problem, because you still need
to get the used air out of the rooms to make way for new air.
High-tech tight-house systems use a heat exchanger to bring is fresh
outside air and exhaust used air to outside, but use the exhaust air
to pre-heat the incoming air, saving the heating that you've already paid for.
- tom] (the other one)
|
83.206 | | HYLNDR::BROWN | | Mon Apr 14 1997 12:51 | 7 |
|
...plus FHA units can only impart a delta temperature to
the return air. If you start pulling a lot of outside
air, the return (inlet) temp. into the furnace drops and
you'll get a similar drop at the output. I'd venture a
guess that a typical delta rise for an FHA unit to be
30 degrees or so.
|
83.207 | | USDEV1::GERACE | Cindy Gerace @297-3884 | Mon Apr 14 1997 21:09 | 8 |
| The cold air returns are working in all the rooms. When the furnace
was running, I went to each return with a piece of paper and it stuck.
I put a strong air freshener in the basement and after a day, the smell
is now throughout the house. Not sure if it came up through the
furnace or just through the door and floors. I'll get a professional
in soon to check it all out - thanks for the advice!
- Cindy
|
83.208 | Static relief damper in return? | HYLNDR::BROWN | | Tue Apr 15 1997 11:16 | 31 |
|
Ok, look for what is called a static relief damper in the return in the
basement. When a furnace is sucking air from the return sometimes it
can't pull as much air as it needs thru the return and a static relief
damper is inserted. This is usually nothing more than a weighted
damper leaf in a round duct that is open to the basement. It will
appear closed or almost closed much of the time. It is more often
present in multi-zone air based systems because its nearly impossible
to balance air flow when only one zone is calling for heat.
When the furnace is running and attempting to pull air from the return
across the heat exchanger if it can't pull enough air a negative
pressure is created in the return. The static relief damper opens
in response to this negative pressure and air from the basement
is sucked into the return to reduce the negative return pressure.
Such a complicated explanation for such a simple mechanical device.
Anyway, the damper can be adjusted with a small weight on the damper
usually. But the real question then becomes why isn't the return
drawing enough air. It might be a partially clogged return, a return
may have been removed or reduced in size. If you need the static
relief damper, typically the only way of eliminating it is to add
more return volume from the living space. Also, in some systems
this is a design feature in that the input thru the static releif
damper permits the slow/eventual replacement of cold basement air
so that the air down there doesn't completely stagnate.
Just my opinions from what little experience I have with them in
my parents house.
Bud
|