T.R | Title | User | Personal Name | Date | Lines |
---|
630.89 | Wiring a Shop | FRSBEE::PAGLIARULO | | Thu Feb 19 1987 15:38 | 14 |
| I'm wiring my basement for a workshop. I want to put alternate outlets
on different circuits so that if I can run several tools at once without having
to worry about the load, i.e a shop vac with the disk sander.
Someone told me the simplest way to do this was to run 1 three conductor romex
cable. Use the black and red as hot connnected to two separate breakers. Use
the white as a common ground for both circuits. Since I'm using EMT to run
the cable over the cement basement walls I agree that this would simplify the
wiring but it doesn't sound too legal. Anyone know if this would conform to
N.H. code? What would the dangers be?
Thanks,
George
|
630.90 | | AUTHOR::WELLCOME | Steve | Thu Feb 19 1987 15:49 | 4 |
| Sounds fine to me. Take the black and red off the two different
input lines from the street and have 240 if you want it too. I
can't see why it wouldn't be legal...but I'm not all that up on
current code.
|
630.91 | | VIDEO::DCL | David Larrick | Thu Feb 19 1987 16:13 | 48 |
| This technique is perfectly legal. It's even specifically mentioned in the
NEC, as a "3-wire circuit" or some similar term. (Disclaimer: I don't
know about any NH amendments to the NEC).
It's important that the two circuits be opposite in phase, so the return
current in the single white wire tends to cancel, rather than double.
Furthermore, the two circuit breakers must have a common shutoff lever,
under some circumstances. Read about it in the NEC.
I used this technique in two different ways:
1. In the kitchen, I ran two different circuits to each duplex outlet. The
top hole in each outlet is one circuit, the bottom is the other. So I
can run two high-powered devices off the same duplex outlet, or from any
pair of outlets in the room, and be sure I'm using different circuits.
I would recommend this technique for your shop - it seems easier to use
than alternating outlets would be.
2. In the bedroom, the red and black wire are from the same circuit, but
the red wire is switched. Each duplex outlet is, again, wired
red-and-white on top and black-and-white below. Thus every outlet has
one switched hole and one unswitched hole.
To use this technique, be sure to get outlets that have removable metal
strips joining the top and bottom screws. Most modern ones have them.
You ask "what would the dangers be?":
1. As mentioned above, the two hot wires must be opposite in phase.
Otherwise, the white neutral wire would have to carry twice its rated
current, causing it to melt and burn.
2. As also mentioned above, you may need a two-pole breaker. Otherwise,
when working on the outlet later, someone could shut off a breaker, test
the outlet and determine that it's off, and start work, while the other
half of the same outlet is still hot.
3. Being opposite in phase, the two hot wires together constitute a 240V
circuit. Nothing magical or terrifying about this, it just means
there's a little more at stake in using safe practices and good
workmanship.
4. The white neutral wire must be installed in such a way that it can be
disconnected from an outlet without breaking its path to other outlets
further down the circuit (i.e. use a jumper wire rather than jumpering
through the outlet). Otherwise, the downstream outlets could have a
floating neutral during service, which is dangerous given that the other
wires in those outlets are 240V apart.
|
630.92 | | ULTRA::PRIBORSKY | Tony Priborsky | Thu Feb 19 1987 17:00 | 9 |
| Re: .2: Opposite phase is essential, and the way to get it is
to put the breakers in adjacent slots. Or, get one of the 240V
breakers that looks like two 120V breakers joined together. I'm
curious: What does the code say about the tripping of the breakers
in such an arrangement? Must they trip together? If so, then
you MUST get one of the double breakers, or otherwise join them
so that they trip together. (I put in one of these in my house,
I just used two breakers, but the lack of common trip has bothered
me.)
|
630.93 | Oops, no breakers - yet | FRSBEE::PAGLIARULO | | Fri Feb 20 1987 07:48 | 28 |
| >> Furthermore, the two circuit breakers must have a common shutoff lever
Thanks for the quick answers. I re-read my base note and saw that I was a
little misleading. I do not have circuit breakers, I have fuses. I will
convert to a breaker panel but that probably won't be til next winter. My
primary need right now is for the shop. How does this affect what I would
do? I don't see how you could connect 2 fuses together so should I stay with
the alternating outlet plan?
>> As mentioned above, the two hot wires must be opposite in phase.
Otherwise, the white neutral wire would have to carry twice its rated
current, causing it to melt and burn.
Reply .3 outlines how to make sure the wires are opposite in phase for breakers.
Would it be the same for fuses (seems like it should be)?
I plan on using 12 gage wire for all circuits in the shop. Both circuits will
have 3 duplex outlets plus an outside GFCI plug. There will be 4 florescent
lights in the shop. I'd like to put 2 on each circuit. Is this a good idea or
should I run a third lighting circuit. I'm thinking that the lights would be
allright on the outlet circuits because this is a shop and I can only use one
tool at a time. At most I would use a shop vac while using a tool that
created a lot of dust so I'm not really worried about load. Should I be?
Thanks again for the help
George
|
630.94 | Keep 'em off the shop circuit | BEING::WEISS | Trade freedom for security-lose both | Fri Feb 20 1987 08:01 | 19 |
| re:flourescents on the wiring circuit
If I were wiring my shop again, I'd keep all the lights on a separate circuit.
I have 3 flourescents, and two of them are tied into the basement lighting
circuit. The third was easier to wire connected to one of the shop circuits.
Whenever I turn a tool on, particularly the table saw, that light dims and
flickers for the duration of the time the tool is on. Luckily the tablesaw is
lit by the other two lights.
Flourescents are very sensitive to slight voltage fluctuations. Go with the
extra circuit, or tie them in to an existing one, but seperate from the shop
circuit. If you put in a new circuit, you can save some money by making it 15
amp instead of 20, and using 14 gauge wire instead of 12.
And BTW, 12/3 wire is going to be expensive. Not as expensive as two runs of
12/2, but a heck of a lot more than 14/3. It's the old demand problem - not
many people use much 12/3 wire.
Paul
|
630.95 | just a bit more | WORDS::MCLAUGHLI | | Fri Feb 20 1987 08:25 | 6 |
| Just to add a little bit more. Put your lights on a different circuit
for safty reasons. If you should trip the breaker and are working
at night, your lights will remain on. Very important to see a high
speed piece of equipment thats still spining down.
|
630.96 | 2 lights/circuit | FRSBEE::PAGLIARULO | | Fri Feb 20 1987 09:48 | 9 |
| Re: .6 >>Put your lights on a different circuit for safety reasons. If
you should trip the breaker and are working at night, your
lights will remain on. Very important to see a high speed piece
of equipment thats still spining down.
I agree totally. That's why I want to put only 2 lights on each circuit. If I
blow one circuit then the shop is still lit by the lights on the other.
|
630.97 | | ULTRA::PRIBORSKY | Tony Priborsky | Fri Feb 20 1987 10:24 | 3 |
| I'm almost certain that a three-wire circuit with fuses would violate
the code. Be safe - use two two-wire circuits or wait until you
change your service over to breakers.
|
630.98 | Ground Fault Interupt | AMULET::YELINEK | | Mon Feb 23 1987 09:33 | 9 |
| Is a GFI required because you're wiring below grade....?
I'm in the process (for 'bout 2 months now) of planning where my
power tools and benchs will be prior to wiring and that is one question
I haven't answered as yet.
Mark
|
630.99 | GFI's are outside | FRSBEE::PAGLIARULO | | Mon Feb 23 1987 11:02 | 12 |
| Re.: 816.9
>> Is a GFI required because you're wiring below grade....?
The 2 GFI's that I'm putting in are outside outlets that will be on the shop
circuits. I have heard that it is a good idea to put GFI's in a shop because
of all the hand tools that are used. Seems like it would be awfully expensive
though.
George
|
630.100 | one per | Q::ROSENBAUM | Rich Rosenbaum;mail->Boehm::Rosenbaum | Mon Feb 23 1987 11:40 | 8 |
| � I have heard that it is a good idea to put GFI's in a shop because
� of all the hand tools that are used. Seems like it would be awfully expensive
� though.
Keep in mind that you only need one GFCI (breaker or outlet) per
circuit.
__Rich
|
630.101 | | VINO::KILGORE | Wild Bill | Mon Feb 23 1987 11:49 | 7 |
| re last few:
Doesn't the latest code require GFCI-protected circuits in basements?
re .10:
~$15 per circuit if you use the outlet models.
|
630.102 | | FRSBEE::PAGLIARULO | | Mon Feb 23 1987 12:30 | 6 |
| Re:.11 & .12
Thanks for the information. I thought every outlet had to be a GFCI not
one/circuit. That's why the cost seemed high.
George
|
630.103 | more on installing GFCI's | Q::ROSENBAUM | Rich Rosenbaum;mail->Boehm::Rosenbaum | Tue Feb 24 1987 14:42 | 5 |
| More on saving money and GFCI's
If using a GFCI outlet (rather than a circuit breaker), the GFCI
must be installed first in the line, that is, closest to the service
panel.
|
630.104 | Buy the right GFCI for your application | AMULET::YELINEK | | Mon Mar 02 1987 13:16 | 28 |
| Happened to pull my elec. book out this past weekend as I to am
about to wire my basement for my workshop. I found that there are
actual circuit breakers (placed within service panel) that also
have inherent within them..the GFCI capability. That is (I forgot
if this was already explained earlier..) the ability to sense the
load current in the hot wire (black) and compare it to the current
in the neutral wire (white) and if the currents differ by ~5-6 mA...
then the GFCI interrupts and the circuit becomes open rendering
it unable to fry you should you be a path to ground somehow.
These combination 'circuit breaker' / 'GFCI' breakers are expensive
however and it would be cheapest to 'insert' the GFCI somewhere
just beyond the service (as previously mentioned) so that all outlets
feed from that circuit are protected.
More info: The GFCI must be rated the same as the breaker/fuse
in your main service i.e. 115V > 15A or 20A
There are also GFCI for 2 and 3 wire circuits handling
240V up to 30A so...........buy the right one for
your application.
****** till Weds. March 4th...these GFCI's are on sale at ann&hope
stores for $10.00 and Sommerville Lumber has them on sale
now for how long ?? for $9.00? or $10.00. I've never seen
them cheaper.
MArk
|
630.105 | Stay away from Breaker/GFIs | USMRM2::CBUSKY | | Mon Mar 02 1987 14:40 | 16 |
| Stay away from the combination circuit breakers/GFI. I have one
in my house and it is a constant problem, they trip in the middle
of the night or when ever for no reason what so-ever. I get up in
the moring, get ready to shave, switch on the razor, HONEY.... THE
*&+$ %^&# BREAKER TRIPPED AGAIN.... WOULD YOU PLEASE FIX IT.
I trouble shooted the whole GFI circuit looking for loose connections
or whatever and found nothing. It still would trip whenever it felt
like it. Later when talking to an electrician, I asked him about
it and he said he wasn't suprised, he's replaced many in his days
and converted back to a conventional breaker and replaced the outlet
with a GFI outlet.
I did this to mine this weekend.
Charly
|
630.106 | | FRSBEE::PAGLIARULO | | Mon Mar 02 1987 14:49 | 12 |
| Re: .14
>> If using a GFCI outlet (rather than a circuit breaker), the GFCI
>> must be installed first in the line, that is, closest to the service
>> panel.
If I understand you correctly, as long as the GFCI is the first outlet
in the circuit, than the subsequent outlet on the exterior of the house can be
a normal outlet - properly weather protected of course.
I want to make sure because I thought that outside outlets had to be
GFCI.
|
630.107 | | POWPAC::CONNELL | Bust a deal....face the wheel | Mon Mar 02 1987 15:30 | 22 |
| Re: .14
>> If using a GFCI outlet (rather than a circuit breaker), the GFCI
>> must be installed first in the line, that is, closest to the service
>> panel.
I think that the GFCI can be placed anywhere in the ciruit, but only those
outlets placed after it will be protected.
> If I understand you correctly, as long as the GFCI is the first outlet
>in the circuit, than the subsequent outlet on the exterior of the house can be
>a normal outlet - properly weather protected of course.
> I want to make sure because I thought that outside outlets had to be
>GFCI...
(PROTECTED)
^
|
They do, but all the "weather-tight" outlet enclosures I've seen commonly used
will only fit a standard duplex outlet, not the square shape of a GFCI.
--Mike
|
630.108 | Where else?? | BEING::WEISS | Trade freedom for security-lose both | Tue Mar 03 1987 08:18 | 8 |
| >They do, but all the "weather-tight" outlet enclosures I've seen commonly used
>will only fit a standard duplex outlet, not the square shape of a GFCI.
You can get weather tight outlet boxes that will fit a GFCI at (of course)
Spags.
Paul
|
630.109 | | VINO::KILGORE | Wild Bill | Tue Mar 03 1987 08:24 | 4 |
| The outlets on the GFCI unit, and all outlets or fixtures wired to
the LOAD side of that unit, are protected. Any outlets or fixtures
between the panel and the SUPPLY side of the GFCI unit are not
protected.
|
630.110 | The Human Engineering Aspects | AMULET::YELINEK | | Wed Mar 04 1987 16:16 | 56 |
| Well, we've spoke of * wiring techniques
* outlets separated from lighting circuits
* and the GFCI...
Hows about hearing from you guys that have your workshop already
wired and functional but have had some thoughts about things you would
have done differently if you could do it all over again. This info
will certainly fill out the heading of this note: "Wiring A Shop"
I'm in the process of planning where my stationary power tools will sit
along with locations of my benches etc. I'm figuring on placing
both 120V/20A and 210V/20A outlets around the perimeter of the shop
a hammers height above the floor (roughly code height) for my
stationary power tools and whatever. I also plan to place outlets
located just above bench height where my benches are. I recently
looked into 'strip' wiring whose cost was prohibited for use as
a continous strip all the way around the shop.
Anyway, you guys with the established workshops....any hindsight
advice you could lend us before we embark on this project..?
* Did you give yourselves enough outlets
* Did you(or would you consider) mounting the outlets over the bench
sideways vs. up and down..?
-------- -----
| * * | vs. | * | as strip wiring would have dictaded
-------- | * |
-----
* Did you install Any special MAIN shut-off device (for all the
stationary power tools) that would be located either up high or
behind a hidden panel? This is something I'm considering so my
kids could never start anything up. Its somewhat impractical to
go around unplugging everything after you're done working all
the time as I'm forced to do at the present time. Think Safety.
* A central vacuum system is a little elaborate for me...I'll just
wheel around the shop-vac for sawdust clean-up...BUT a ventilating
fan is something I've planned, so you'd need to wire for this.
During my planning I also came across a few books on the topic
of woodworking and workshops. Included within these are illustrations
of various stationary power tools along with the clearances required
for the tools' operation. Also the pictures indicate where (ideally)
the light source for each tool should be directed from. To consider
all these aspects would certainly make for a well engineered shop.
Hows about it...What else is there to consider in Wiring A Shop
MArk
|
630.111 | More is better | REGENT::GETTYS | Bob Gettys N1BRM | Wed Mar 04 1987 19:58 | 9 |
| Just some general advice for wiring any hobby area. (It
would also apply somewhat for any area!)
Put in more outlets and circuits than you think you
need. Someday you will be glad you did! I think one of Murphy's
corallaries is that "All available outlets will be in use when
you want to plug something in!"
/s/ Bob
|
630.112 | Instal flexibility | NEXUS::GORTMAKER | | Wed Mar 04 1987 22:46 | 9 |
| If your shop is going to have an open ceiling (may apply to finished
too) leave extra wire going to the fixtures. I wish i had done
this in mine. After a few months of working in my shop I had decided
i dident like the lighting the way it was and had to almost start
from scrach just to move the light 2 1/2 feet.
Ok so i dident plan well......
-j
|
630.113 | | BEING::WEISS | Trade freedom for security-lose both | Thu Mar 05 1987 08:54 | 6 |
| I don't remember whether you're already doing this, but be sure to put in a
220V circuit also, with outlets spaced around the room. Many of the larger
woodworking tools come 220V only, and you never know where you'll want to put
one.
Paul
|
630.114 | | VINO::KILGORE | Wild Bill | Thu Mar 05 1987 10:03 | 5 |
|
I have a free-standing work bench. Some day, I'm going to wire an
outlet box onto a joist over the bench, into which I can plug a
cord wired to a strip of outlets under the bench, so tha I'm not
always tripping over the cords currently hidden in the sawdust.
|
630.115 | Strip outlets are OK, but NOT on top | DRUID::CHACE | | Thu Mar 05 1987 10:56 | 44 |
| Having built an extensive shop in two houses (I moved) I am willing
to give some advice (though I do not portend to know everything).
DO NOT put the bench outlets at the back of the bench top. This
is a logical place and I did this in my first shop. BUT every time
you work on something on top of the bench, the thing you're working
on gets in front of the outlets. Also, if you want to lay something
flat on the bench you have to slide it under the wires. Then when
you want to pick it up you have to move the wires again. If you're
doing some work on the floor, even something as simple as drilling
a few holes, the cords might not reach because they have to go all
the way across the bench first.
The best place to put the outlets is under the front edge of your
workbench. They're easy to get at but not in the way.
Right now my main bench is 12' long, and I have a double
outlet 2' from each end and one in the middle. I have found that
this is a reasonable amount of outlets for JUST the workbench.
If you have an unfinished ceiling, there's no need to install
anything you aren't going to need (why install 220v if you have
no 220v tools). Figure where you want your tools, (actually put
them in place if possible to get the best idea of how it will be)
and put outlets on the joists above them.(actually just behind)
Since it's extremely unusual to have 2 major tools running at
the same time, I wired 1 20A circuit to all of the stationary tools,
and 1 20A circuit to the workbench outlets. This has been plenty
of power for my 120V needs. Any 220V tools get another
circuit, with one 20A circuit being sufficient for all of my 220V
tools. (the only exception would be a tool that has an unusual current
requirment, you don't want a tool that can fry at 10 amps on a 40
Amp line. At least I don't)
Do yourself a favor a wire the overhead lights to anything except
any power tool circuit. Even tapping off another basement light is
usually ok. If you can, put a switch for the overhead lights near
the entrance to your work area. Also, don't put any basement outlets
low like you would in a living area. They're not really accessable,
and I think code says they have to be high up. (keeps them away
from water ect.)
I hope this helps, I've made my share of bad decisions when it
comes to setting up a shop, maybe this can keep you from making
some of mine. (I'm currently moving my big woodworking vise because
it's right in my way.)
Kenny
|
630.116 | Outlet Placement | FRSBEE::PAGLIARULO | | Thu Mar 05 1987 11:50 | 16 |
| >> Figure where you want your tools, (actually put them in place if
possible to get the best idea of how it will be) and put outlets
on the joists above them.(actually just behind)
My original plan was to put all outlets on the wall. This involves
running conduit down the cement walls with all the associated connectors and
bending (I know I can run the wire down a board but I just don't like that
idea esthetically). Aside from the added cost of the EMT the outlets would
also take up wall space that can be used for shelving, stacking wood etc.
Is there any disadvantage to putting all outlets on the joists? When using
hand tools would the cords get in the way? There will still be outlets
on/under the bench to take care of the tools I might use there. Has anyone
wired their shop this way and would you do it again?
George
|
630.117 | Just below joists. Outside, etc. | NACHO::DIGRAZIA | | Thu Mar 05 1987 15:15 | 28 |
|
I attach a 10" X 18" 3/4" plywood board to the ceiling joists,
extending down about 10". I attach a quad surface-mount
box to the plywood, below the joists. This gets the outlets
overhead, but not up in the joists. They are high enough to
prevent bonking the noggin, but not too high to reach for most
people. I haven't tried the alternative of spanning a couple of
joists, and mounting the box with the outlets pointing down.
By the way, any comments on adding a couple of outside outlets
to a 20A basement circuit now supplying only outlets (no lights)?
It would be easier for me to extend some wiring to outsiders than
to start at the box. Would the NEC people laugh me off the planet?
More by the way: the quantity-one price for a circuit-breaker
GFCI is about $41 (Ralph Pill, Nashua, NH). The q-6 price is $34.
Anyone wish to pool a purchase? I'm planning to buy 2 or 3.
(For that price, they better be stable, no false trips, etc.
All right, you parsimonious pinch-pennies, don't tell me to buy
$10 receptacle GFCIs. I don't like gadgets that don't work unless
they're in the right place.)
That reminds me, contrary to a couple of reports elsewhere herein,
the GFCI circuit breaker in my service box hasn't tripped falsely
yet. Then again, I haven't tested it for tripping truely. Time to
plug something into the ground!
Regards, Robert.
|
630.118 | table saw wiring | MAY11::WARCHOL | | Thu Mar 05 1987 17:28 | 9 |
| Wiring a table saw has always been a problem. In order to be useful
the saw should have space all around it which makes wall mounted
or ceiling outlets awkward. There's always an extension cord from the saw to
some wall outlet that is just waiting to trip me.
If I ever had the space to make sure my saw didn't have to move
I'd run the wire under the floor and up the saw leg.
Nick
|
630.119 | I just tape the wire to the floor with duct tape | BEING::WEISS | Trade freedom for security-lose both | Fri Mar 06 1987 08:22 | 0 |
630.120 | | MAY11::WARCHOL | | Fri Mar 06 1987 13:01 | 5 |
| For the short term taping the wire to the floor is a good solution.
I'm just afraid it would get too much abuse after awhile. Murphy's
Law tells me exactly where that awl I drop will fall.
Nick
|
630.121 | | AMULET::YELINEK | | Fri Mar 06 1987 13:12 | 12 |
| RE: .28
> By the way, any comments on adding a couple of outside outlets
> to a 20A basement circuit now supplying only outlets (no lights)?
> It would be easier for me to extend some wiring to outsiders than
> to start at the box.
OK, but don't forget any outside outlets require the whether proof
cover and must be wired through a GFCI....or is this existing circuit
the one having the combination breaker/GFCI. ? in which case
no additional GFCI is required.
MArk
|
630.122 | keep the shop idiosyncrasies coming | AMULET::YELINEK | | Fri Mar 06 1987 13:20 | 8 |
| You're right about the table saw....this machine gets its electricity
at the most convenient outlet in sight depending where the saw is
set up.
I have a lolly column where I don't want it but I was thinking of
boxing it in with outlets enclosed on a couple sides.
MArk
|
630.123 | Wiring channels? | ULTRA::BUTCHART | | Mon Mar 09 1987 08:04 | 9 |
| re .31:
Anybody know where to get that aluminum ramp/channel stuff that
you can run a wire through? I've seen it used in the ZK labs to
protect floor wiring from abuse and people from tripping on the
cords. That might be a good solution to the problem of dropping
tools, boards, and other stuff on the wires.
/Dave (four thumbs, but dedicated)
|
630.124 | Wiremold | Q::ROSENBAUM | Rich Rosenbaum;mail->Boehm::Rosenbaum | Tue Mar 10 1987 12:35 | 9 |
| You can get the Wiremold brand of pseudo-conduit at Aubuchon hardware
stores, as well as Mass Hardware in Acton (it's cheaper at Aubuchon).
I've used it to add an outlet on my garage ceiling (to plug a shoplite
into). It's a little expensive, but looks decent and is fairly easy
to use.
However, I don't think it's sturdy enough to be stepped on.
__Rich
|
630.125 | | NEXUS::GORTMAKER | | Tue Apr 07 1987 22:05 | 9 |
| I belive wire mold does make (a hard plastic designed to be walked
on type of) exactly what you're looking for. At least they used to
special order in most cases. I just went down to the office supply
store and bought it last time. It is expensive though.....
-j
P.s. carol cable made them too.
|
630.144 | detached workshop needs power | ARCHER::BMDLIB | | Fri Apr 17 1987 17:16 | 17 |
| At some point in the future (namely, when we can afford it) I would like to
build a small detached workshop, complete with electricity and heat, the
later coming from a woodstove.
This idea started with a simple shed but after giving it some thought,
and looking at the basement after I finish with a "project", I figure
why not move the whole shebang outside.
What I want is about a 12 x 16 building with, say a window or 2, some
overhead storage, etc. Basically room for lawn and garden crap and some
room left over for a small workshop.
I'm sure there's plenty of plans available for the structure itself,
but what I'm concerned with is how to get the electicity to the workshop.
What's the best and/or cheapest way to do this?
BTW, the shed, er, I mean "workshop" will be about 30-35 feet from the
house.
John
|
630.145 | Go Underground | USMRM2::CBUSKY | | Fri Apr 17 1987 17:33 | 12 |
| The neatest way would be to burry the electrical cable. Two or three
lines should be enough for what your planning. Dig a trench a foot
or two in the ground, install 4" plactic drain pipe as a conduit
and then snake your wires through that. The conduit will, besides
offering protection, allow you to upgrade, replace, add phone lines
or what ever later on. Use undergroud electrical cable as well.
I would think hard about the size of your planned shop too. 12x16
is not really that big. My 12x12 garden shed (garden stuff only) is
filled, and I thought it would be more than enough when I built it!
Charly
|
630.146 | | WELFAR::PGRANSEWICZ | | Fri Apr 17 1987 17:41 | 8 |
| Re: .1
Thats assuming you CAN dig 2-3 ft. down! Watch out for rocks, ledge,
septic systems, gas lines, etc.
I agree. 12x16 (?) is small. Measure the size of your basement
thats too small.
|
630.1 | | VIDEO::DCL | David Larrick | Sat Apr 18 1987 12:57 | 10 |
| The National Electric Code is quite explicit on how this job is to be done.
Get yourself a copy (references elsewhere in this conference) and be sure
you understand it thoroughly before you start the job.
But yes, there's a special type of wire that you use, Type UF (for
"Underground Feeder"), not cheap but readily available at Spag's. (The
stuff is a bitch to strip, by the way - regular stripping tools don't work
- the best I could do was to use a sharp knife and hope for the best).
You'll need conduit to bring the wire out of the house and into the garage.
|
630.147 | 220 VAC + dual Telephone quad + coax for tv | ZENSNI::HOE | | Sun Apr 19 1987 15:43 | 11 |
| Re .1
Planning ahead is great but it's cheaper to bury at least two quad
wires, a 3 12AWG copper wire with breaker for 20amp, 220 volt so
that when the shop gets powered up for saws, compressor, etc, you
have the option for the 220 VAC for the compressor. The multiple
quad wire allows for a RS232 hookup if you want to do any computing
out there. May be, whole you're at it, try adding a coax for watching
the football game.
/cal
|
630.2 | see 1037 also | ZENSNI::HOE | | Sun Apr 19 1987 15:45 | 2 |
| Also see 1037...
cal
|
630.148 | Run TWO pipes if in MA | CADSE::MCCARTHY | Excellent, more than a match for poor Enterprise. | Mon Apr 20 1987 15:43 | 11 |
| It is against the MASS electrical code to run low voltage wiring
(phone/cable) in the same "gutter" (conduit,pipe...) as high voltage
(110V/220V) wiring except where the low voltage wiring is done with
a gauge wire equal to that of the high voltage wiring.
I don't have the code book in front of me but I know that you have
to run seperate pipes for low voltage and high voltage.
Think about 110V hitting a 22 guage phone line........!
Brian mac
|
630.3 | | NEXUS::GORTMAKER | | Tue Apr 21 1987 00:22 | 5 |
| re.1 You only need to have the conduit on the above ground portion
of the run. I.E. between house and ground and ground and garage.
The buried part dosent need to be run inside conduit.
-j
|
630.149 | | NEXUS::GORTMAKER | | Tue Apr 21 1987 00:30 | 15 |
| I belive it is against code everywhere to run low voltage and high
voltage in the same conduit. Unless it is as you said the same size
and I would add clearly marked as such.
I'd not bother putting the whole run inside conduit unless you
need/want the extra protection from digging. If you decide to not
run inside conduit you want to get the marker tape to bury with
the cable. I would use the tape anyway since it is cheap.
The tape is bright orange or red and white with high voltage written
on it. This tape saved my butt a few years ago when I nearly cut
into a 220v line buried in my backyard while laying sprinkler lines.
-j
|
630.150 | Maybe I'll buy a generator... | ARCHER::BMDLIB | | Tue Apr 21 1987 15:54 | 9 |
| Ok, it seems like going underground is the way to go on this.
What about getting it from the box to the ground?
At what point does the power exit the basement? Above ground or
at the level it will be travelling below ground?
My basement is dry, and I'd like to keep it that way. I'm a little
leary of cutting holes in it. Any experienced suggestions?
John
|
630.151 | Above ground if possible | NEXUS::GORTMAKER | | Wed Apr 22 1987 00:27 | 9 |
| I would try to go out above the concrete foundation and then down.
This way would avoid having to put a hole in the foundation(hard
work) and avoid the possibility of water problems from the hole
later when the rains come.
I wouldent think you would need conduit inside the house only outside
check the local code to be sure though.
-jerry
|
630.152 | | MKTGSG::PETITO | | Wed May 06 1987 16:07 | 19 |
| SINCE I WAS APPRENTICED AS AN ELECTRICIAN (LONG TIME AGO) I THOUGHT
I WOULD ADD MY 2 CENTS FOR WHAT IT'S WORTH.
I WOULD RUN A 220 FEED FROM THE MAIN HOUSE PANEL TO A SUB-PANEL
IN THE WORKSHOP. THE FEED BREAKER IN THE MAIN PANEL WOULD BE A TWO-POLE
60 AMP. I BELEIVE 6 GA. WIRE WOULD BE NEEDED FOR THE FEED LINE.
(THIS FROM MEMORY, CHECK CODEBOOK). THE FEED LINE SHOULD BE ROUTED
UNDERGROUND IN SCHEDULE 40 PVC UL-APPROVED CONDUIT. IT IS BASICALLY
THE SAME AS PLUMBING PIPE EXCEPT IT'S GRAY IN COLOR AND HAS BUILT
IN COUPLINGS. 1 INCH DIAMETER PIPE WOULD BE SUFFICIENT. ONCE INSIDE
THE WORKSHOP THE FEED CABLE RUNS TO THE BRANCH PANEL WHERE YOU CAN
NOW PLACE LOCAL BREAKERS (15 & 20AMP) FOR THE VARIOUS WORKSHOP CKTS.
THIS WAY YOU ALSO HAVE 220 CAPABILITY FOR WELDERS, LARGE AIR
COMPRESSORS, ETC. BE CERTAIN THAT YOU KEEP THE NEUTRAL (WHITE) AND
GROUND WIRES SEPARATE IN THE PANEL OR YOU WILL VIOLATE CODE. AS
A FURTHER SUGGESTION, I WOULD ALSO RUN A LOCAL COPPER GROUND ROD
WHICH WILL CONNECT TO THE GROUND BUSS AS A FURTHER SAFETY.
A PROJECT LIKE THIS WILL PROBABLY REQUIRE A BUILDING PERMIT,
SO MAKE SURE IT'S DONE RIGHT OR IT WILL FAIL INSPECTION.
|
630.153 | TWO grounds are TOO much | USMRM2::CBUSKY | | Wed May 06 1987 17:16 | 14 |
| Re. A local copper ground
I believe this would violate the code in that you would have TWO
places where you electrical system is grounded. It's my understanding
that you only ground the system ONCE.
You are correct in that the ground and ground and neutral should be
kept seperate and ONLY tied together at the main panel.
Charly
P.S. ALL CAPITAL LETTERS is considered SHOUTING according to noting
ediquette, unless of course you terminal won't do lower case letters.
Please don't shout. :-)
|
630.154 | RE .9 | MKTGSG::PETITO | | Thu May 07 1987 09:46 | 13 |
| ACTUALLY THE OPPOSITE IS TRUE. YOU CAN RUN LOCAL GROUNDS AS OFTEN
AS YOU LIKE, AS LONG AS THERE IS A CONTINUOUS GROUND BACK TO THE
MAIN ENTRANCE. I CHECKED THE CODEBOOK, ARTICLE 250 SECTION 24. THE
CODE ACTUALLY REQUIRES A SEPARATE GROUNDING ELECTRODE WHEN A SEPARATE
BUILDING IS SUPPLIED FROM A COMMON SERVICE. THERE ARE EXCEPTIONS,
THE TWO NOTABLE ONES BEING IF THERE IS ONLY ONE BRANCH IN THE BUILDING
OR IF THE BUILDING IS A METAL FRAME STRUCTURE BONDED TO THE EARTH.
THE NEC STANDARDS ARE MINIMAL AND MUST BE MET THROUGHOUT THE NATION,
THEY DO NOT SUPERCEDE LOCAL ORDINANCES WHICH MAY BE MORE STRINGENT.
I.E. IT MAY BE REQUIRED IN ANY INSTANCE BY LOCAL ORDINANCES. WHEN
IN DOUBT, GROUND IT.
I NEVER SHOUT.
|
630.155 | 1 or 2 or n? I give up! | USMRM2::CBUSKY | | Thu May 07 1987 10:45 | 17 |
| Re. .8, .9, .10
Sorry for the confusion, at this point I'm not sure what is correct.
On one hand we have a noter telling us that multiple grounds are OK.
On the other hand, I had work done this past January by a licensed
electrician who told me ONE ground only.
I previously was using and 8 foot ground rod buried in the cellar
floor. I wanted to start using a recently installed 65 foot copper
water main as the ground rod. My electrician said that we could use
one or the other, BUT not BOTH?
Since I'm the least qualified (lacking any formal training) of the
three, (1. MKTGSG::PETITO, 2. my licensed electrician, 3. myself),
I'll step out of the dicussion.
Charly
|
630.156 | | NEXUS::GORTMAKER | the Gort | Fri May 08 1987 21:09 | 12 |
| I have a seperate ground on my garage that was recently inspected
and passed if that helps.
I dont know if it is code but I do know I wasent called on it.
What would be the problem with two grounds? Ground is ground unless
it is logic ground but then we are talking about apples instead
of oranges. Are we confused yet?
-jerry
|
630.126 | Time delay fuses | WELFAR::PGRANSEWICZ | | Wed Jul 22 1987 13:13 | 14 |
| I don't remember seeing this mentioned anywhere in this notes files
(believe it or not).
For people out there with fuse boxes, you should use a time delay
fuse for a circuit running any large motors. Every time I turned
on my new table saw, POOF the 20 amp fuse blew. I put in a 30 amp
and it worked so I figured it wasn't the saw. Then I was enlightened
to the time delay fuses made for just these situations. Seems when
the saw first starts, it draws more current than it normally does.
Question: Do circuit breakers "delay" for these surges?
This remains the only problem I've been able to resolve cheaply in
this house!
|
630.127 | yup, breakers delay.. | REMEDY::KOPEC | How did I get myself into this?? | Wed Jul 22 1987 13:27 | 1 |
| Most breakers have a time delay.
|
630.128 | yup, motors draw.. | TOOK::CAHILL | Jim Cahill | Wed Jul 22 1987 13:44 | 3 |
| ... and most larger motors draw more current when starting, due
to their design. Once the motor is spinning, it requires a lot
less juice to keep it that way.
|
630.129 | Careful about changing breaker sizes | FURILO::KENT | Peter | Wed Jul 22 1987 14:53 | 16 |
| Re. .37
A breaker, like a fuse, is a device that works on heat and time.
The higher the current for the longer the time, the quicker the
fuse/breaker blows. AC motors, depending on type, typically need about
6 times as much current to start as they do to run under rated full load.
It does depend on the type, because there are all kinds of AC motors -
squirrel cage, synchronous, universal, etc. And within types there are
different ratings. Be careful about replacing with larger fuses/breakers
than were in the circuit originally. The fuse or breaker that was put
in by the electrician that first wired up the circuit had sized it
for the wiring going to the outlet. The fuse/breaker is there to
protect the wiring - not the device you plug into the outlet. You
may not get into trouble this time, but if you hang more devices
on the circuit and have a larger protective device in there than
originally planned, you risk a fire.
|
630.130 | Testing 1-2-3-4 | WELFAR::PGRANSEWICZ | | Wed Jul 22 1987 15:05 | 8 |
| RE: .40
I only put the 30 amp fuse in to test for approximately 30 seconds.
I now have a 20 amp time delay fuse for the line. Thanks to this
file, I already knew about wire size vs fuse/breaker capacity.
Hell, I even replaced the outlet with a 20 amp!!!
Phil
|
630.131 | | Q::ROSENBAUM | Rich Rosenbaum;mail->Boehm::Rosenbaum | Tue Jul 28 1987 16:57 | 3 |
| >>> Hell, I even replaced the outlet with a 20 amp!!!
Did you replace the wiring also?
|
630.132 | Using single breakers for 240V applications... | 3D::WHITE | Randy White, Doncha love old homes... | Wed Jul 29 1987 10:38 | 23 |
| RE: < Note 816.3 by ULTRA::PRIBORSKY "Tony Priborsky" >
>> Must they trip together? If so, then
>> you MUST get one of the double breakers, or otherwise join them
>> so that they trip together. (I put in one of these in my house,
>> I just used two breakers, but the lack of common trip has bothered
>> me.)
Being relatively new to notes and still trying to weed through
all the older stuff, lots of good info. I am also researching
a shop set up. I didn't see an answer to this question about
individual breakers. So to clarify, the code does allow using
individual breakers on opposite phases AS LONG AS THE TRIP
LEVERS ARE MECHANICALLY BONDED TOGETHER. This will depend on
what type of breaker you have but you should be able to get
either a clamp or a locking pin from an electrical supply
house to connect the trip levers together.
Good Luck Randy
P.S. You are right to feel bothered this is a potentially dangerous
situation not only for you but for the next owner who doesn't
know about it.
|
630.133 | | WELFAR::PGRANSEWICZ | | Wed Jul 29 1987 10:47 | 8 |
|
RE: .42
>>> Did you replace the wiring also?
The wire was already correct for the application, 12-2.
|
630.4 | another garage/electical question | FLIPIT::PHILPOTT | Rob Philpott, ZKO2-2/M37 | Wed Sep 23 1987 15:53 | 71 |
| I have a related question. My 2-car garage is under my family room
(the house is ~8 years old). Thus, due to safety codes, the garage
had to be "finished"; that is, all walls (except one, which is
concrete, floor to ceiling) and the ceiling have wallboard
and have been plastered.
Is it legit to run electrical wiring over the surface of the plastered
ceiling (held up with insulated U-shaped nails (staples?)? I haven't
checked local codes yet, but thought I'd ask you folks. Either
the builder (probably) or the previous owner (doubtful) did this
with a wire running from the basement, through the wall to the garage,
along the ceiling of the garage, and through a hole in the ceiling
where it then runs up though the family room wall to a light switch.
When the building inspector came through, he said nothing about
it, although he was pretty picky about most other things. My reason
for asking is as follows:
Just after we bought the house, we bought garage door openers.
The easiest way for me to get them connected was to do the same
sort of thing. I tapped into a lightly used circuit in the basement,
ran a wire through the wall, running along the ceiling and installed
an electrical outlet on the ceiling within reach of both door openers.
To run the wiring above the ceiling would be a real PITA becase
of the direction of the floor joists (see diagram). Since there
was already a precedent for running wiring this way, I figured it
wasn't a big deal. I figured I'd go back someday and do it "right".
That is, rather than plugging the openers into an outlet, I'd run
a circuit directly to them (behind the ceiling) and use permanent
wiring in place of the plugs.
Well, "someday" is getting close. I really have 2 questions:
1. can anyone suggest the easiest way to snake the wires above
the ceiling to the openers given the way the joists
run (from the basement)?
2. would it be legit to leave the outlet I installed in it's
present form (run along the surface of the ceiling)?
It is in a handy location.
| basement |
| | * = wire run over
| * * \ | ceiling surface
| * * \ |
+-----*--#----------*--------+ +-+ # = outlets (side
| * ||* | wall and ceiling)
| * ||* |
| * ||* |
| ||* | ++ = garage door
| O ||* O | ++ openers
wallboard/ | ||* |
plaster | ||* | O = overhead lights
wall ---> | ++ ||# ++ |
| ++ || ++ | Family room floor
| || | joists run perpendicular
| || | to center beam
| ceiling beam-->|| |
| || | <-- concrete wall
+--+=============+--+=============+--+ floor to ceiling
^ ^
| |
overhead doors-+---------------+
Note that exising wiring for the ceiling lights is above the ceiling
and several joists away from the door openers.
Does any of this make sense?
rob
|
630.5 | | NEXUS::GORTMAKER | the Gort | Wed Sep 23 1987 21:18 | 6 |
| If you run the wire in conduit you will be fine. I'm not sure about
just running the romex across the wallborad but here in colorado it
is not to code to do so.
-j
|
630.6 | | VIDEO::DCL | David Larrick | Thu Sep 24 1987 10:24 | 16 |
| Yeah, the code problems with finish-surface-mounted Romex may be:
- it's a finished room, so it isn't allowed.
- it's a garage, so you need special oil-resistant cable (even some
conduit installations don't satisfy this one).
Note that I said "may" above; it's also possible that it's legally
considered unfinished even if, legally, it has to be finished (got that?),
so certain types of wall- or ceiling-mount may be OK, as in a basement or
attic.
Since you're talking about an existing installation, the most important
considerations are safety and practicality: is the Romex reasonably safe
from physical damage? from moisture? from gasoline and oil spills and
concentrated fumes? Is it out of the reach of the people who normally use
the garage? If all "yes", you're probably OK.
|
630.7 | another idea | TOOK::CAHILL | Jim Cahill | Thu Sep 24 1987 11:03 | 8 |
| Hi, Rob!
I've also seen what's advertised as "surface-mount" wiring.... it
looks like it's just flat conduit; the system includes surface mount
outlets, switches, wiring runs, etc. You might want to look into
this type of wiring.
Jim
|
630.8 | | NEXUS::GORTMAKER | the Gort | Thu Sep 24 1987 21:58 | 4 |
| re.7 You refer to a product known as Wiremold (tm) great stuff but
expensive if its a big job.
-j
|
630.9 | Not big enough for me | VIDEO::DCL | David Larrick | Fri Sep 25 1987 10:03 | 9 |
| Wiremold has another drawback besides price: capacity.
I wanted to install two 3-way switches next to a door, and didn't want to
tear the wall apart to do it. But (details get hazy here) I couldn't find
2-gang or gangable Wiremold boxes, and I certainly couldn't find Wiremold
conduit that would handle the large number of wires involved.
As I considered the option of running multiple conduits to multiple,
discrete boxes, tearing that wall apart looked better and better.
|
630.10 | sizes available, but it still sucks | CADSE::MCCARTHY | CADSE software engineering | Fri Sep 25 1987 11:33 | 9 |
| RE: .9
They make the 2-gang wiremold but they are ugly because of the
depth. The wiremold track comes in several sizes, 200, 500 700
are they ones I know about. I don't know wire capacity per size.
As for working with the stuff, it sucks, like working with EMT
pipe only it has to look alot better when you are done.
mac
|
630.11 | yes, and yes | Q::ROSENBAUM | Rich Rosenbaum;mail->Boehm::Rosenbaum | Tue Sep 29 1987 22:39 | 9 |
| I have used the Wiremold conduit to add an outlet to the ceiling
of my finished garage (how's that for tying all these replies
together?) It looks good (not as good as hidden wiring, of course)
and I don't worry about it.
I have found Aubuchon to be the cheapest place that carries the
stuff.
Rich
|
630.12 | I'm an engineer,not a ditch digger | TOOK::ARN | | Fri Nov 20 1987 09:40 | 8 |
|
Has anyone ever heard of a place that will bury the electrical
cable with one of those machines that they use to run cable
underground? My garage is about 50' away from the house and
digging a trench that far doesn't sound appealing.
Tim
|
630.13 | almost makes the job fun | TOOK::CAHILL | Jim Cahill | Fri Nov 20 1987 09:57 | 8 |
| Hi, Tim!
Rent a trencher from Taylor Rental (Hudson, MA has one, probably
others do, too). The thing looks like a big snowblower, only instead
of a rotating blade up front, it has a large toothed circular blade
on one side for digging up roots and smashing into rocks.
Jim
|
630.14 | | NEXUS::GORTMAKER | the Gort | Fri Nov 20 1987 21:24 | 8 |
| I say the ditchwitch would work better the bucket type dig a 24"
wide ditch the ditchwitch is only 4-6" wide which is plenty for
cable. The type that have a knife that slices the ground and lays the
cable at the same time are not approved for electrical service cable
at least not here in colorado.
-j
|
630.15 | Help me out of the house ... | TOOK::ARN | | Wed Apr 06 1988 12:56 | 13 |
| I am about to run a line out to my garage and have a question on
how to get it out of the house. I would run the line from the basement
to the outside through the sill but there is a two foot wide concrete
drainage slab along the back of the house. So, if I came out through
the sill I would have too much conduit exposed to be a neat job.
Therefore I was thinking of making a hole in the cinder block at
the right depth using two weather tight boxes on either side with
a section of pipe inbetween. Does this sound OK? Anybody have any
tips on good methods of sealing this? I have no water problems
in the basement.
Thanks
Tim
|
630.34 | Overhead wiring to detached garage | REGENT::POWERS | | Thu Jul 28 1988 16:26 | 35 |
| I have offered to install a garage door opener in my inlaws' garage.
Of course, it's a detached, unpowered garage, so this topic revolves
around getting power to the garage. I have read entries on underground
power, but the combination of brick house, paved driveway, and brick
patio precludes running wires out through the walls and under the ground.
I have to go overhead, out of the eaves of the house and over to the garage.
The house and garage are about 25 feet apart at their closest corners.
Add to that about a ten foot rise from basement to eaves and another 25
feet through the basement to the breaker box/service entrance.
Then add the feeder into the garage, and we have about 70 feet of run.
Specific questions:
1) Is there special overhead outdoor cable as there is underground feeder?
2) What support is required for the cable over a mere 25 foot hang?
3) What minimum ground clearance must be maintained, and how much
droop is appropriate?
4) Does the circuit have to be GFCI'd?
(If so, at the source or in the garage?)
5) Must there be fuses or breakers in the garage, or can the circuit
be protected at just the source?
6) Do I have to splice the cable at the entrance/exit nipples,
or can I run a continuous feed from breaker box to the garage outlets?
(That's sort of assuming that the outdoor part of the cable is not
that much more expensive than normal NM.)
7) Presuming a pair of 15 amp legs (110/220), is #12 wire suitable
for a 70 foot run?
8) Is it hard to find multi-conductor combination cables, say 12/3
for power out combined with 14/2 or 14/3 to allow wiring a light
that be controlled from both the house and garage?
The $1.98 Basic Wiring books are pretty terse on outdoor overhead wiring.
Any pointers to better references will be apreciated.
- tom powers]
|
630.35 | Easy! | CLOSUS::HOE | Sammy's daddy | Fri Jul 29 1988 13:34 | 38 |
| Tom,
I suggest that you ask your city electrical inspection dept these
same questions. you don't have to tell them where you're doing
the work, just tell them you are planning this project.
I did this for both my parents and my inlaws, parents in
Vancouver, BC and in-laws in Manti, Utah (different electrical
codes but what I did was more than code requirements).
Aerial cables come with a steel cable as the weight bearing. You
will be assured of passing the code to get the wires as high as
possible. The wires are fed to the aerial wires through RIGID
conduit (like steel pipe with threaded fittings) if you plan to
guy the messenger (weight bearing) wire from the pipe. If you use
a seperate anchor, be sure that the anchor is insulated (ceramic
insulator). The wires should be fed from the circuit box through
a 20 amp breaker. The feed wires should be #10 wires, black,
white and ground. Connection to the aerial wires is through a
weather head.
At the garage, be sure that the first plug is a Ground Fault
Interruptable outlet. All other outlets and lights should be off
the load side of the GFI outlet (you can get GFI circuit breakers
but GFI outlets are cheaper to buy). You will need a fuse box or
breaker box as a service interruptable so that you can work on
the garage wiring without someone frying you. Oh yes, be sure
that the fuse box in the garage is tied to a ground rod.
If it was my garage, I would put 220V to the garage since you
might eventually want to use a compressor; if not, 110V is ok.
Other stuff that might be good to add to the garage is an outside
security or yard light on a photo cell to turn it on and off.
hope this helps
cal hoe
|
630.36 | | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Mon Aug 01 1988 11:28 | 10 |
| The details you ask are beyond my knowledge. I'm glad you
recognize the various problems/questions. Best advice is to find
an electrician who will advise and O.K. your work for a minimal
fee.
BTW where are you located? I understand that in MASS you _MUST_
have a licensed electrician do electrical work. In NH I was told
(~ 3 years ago) that state law permits a home owner to do wiring
in his own home. Some NH municipalities may (probably do) have
more restricting laws.
|
630.37 | | BINKLY::WINSTON | Jeff Winston (Hudson, MA) | Mon Aug 01 1988 13:07 | 5 |
| > BTW where are you located? I understand that in MASS you _MUST_
> have a licensed electrician do electrical work.
thought this only applied to plumbing...
|
630.38 | Keep asking questions | KATRA::RICE | | Tue Aug 02 1988 09:49 | 20 |
| You DO NOT need an electrician in MASS. As long as it is your own
home, ie. no apartments or such. You would be wise to get a permit
and inspection to CYA for insurance purposes.
There are many ways to do this job. The method described is one
of them. If you really want to do it yourself then do check local
codes and ask the local inspectors what they expect. Then go down
to your local electrical supply house and talk to them. Tell them
what you're going to do and ask them for what material they recommend.
Folks tend to think they're getting a special deal ($$$) if they
go straight in and ask for specific materials. Believe me, you're
providing them with entertainment and its costing you extra bucks.
From their side they know the local electrical folks and know you're
not one of them. If you were a new electrican in the area you'd
want to see what this place had to offer. Not all electrican material
is the same, there are a good number of manufacturers. Each house
will carry what they can deal with best. The combinations of materials
can add up differently (different $$$).
|
630.39 | other ways | RETORT::GOODRICH | Taking a long vacation | Fri Aug 05 1988 10:55 | 20 |
| Other ways of doing it...
The national electric code allows #10 wire to be used overhead
without a steel support wire.
Conduit only needs to be used where mechanical protection
is needed. Plastic conduit is a lot easier to work with.
#12 can be used for all but the overhead portion, if the
run isn't too long #14 is ok for 15 amps.
The code is a bit hard to read about this, but I believe
that overhead runs must be treated as a service - that is
a ground rod is required at the garage and it must be bonded
to the "white" conductor.
If you use AL wire wire overhead, be sure you know the correct
way to bond AL and CU wire.
- gerry
|
630.40 | | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Mon Aug 08 1988 17:05 | 41 |
| >< Note 2502.5 by RETORT::GOODRICH "Taking a long vacation" >
> -< other ways >-
> The national electric code allows #10 wire to be used overhead
> without a steel support wire.
Does this mean only #10? or #10 and larger? or #10 and smaller?
OR...
And do you mean individual wires or cables with this size
conductors?
And what kind of wire/cable? NMB? UF? SE? etc.?
And are there specific types of "strain relef" required where the
ends of the overhead run are attached to the house/garrage?
> Conduit only needs to be used where mechanical protection
> is needed. Plastic conduit is a lot easier to work with.
I think this is basically true, but the NEC is often rather
specific about where mechanical protection is required, and the
places/reasons are not always obvious.
> The code is a bit hard to read about this, but I believe
> that overhead runs must be treated as a service - that is
> a ground rod is required at the garage and it must be bonded
> to the "white" conductor.
I'm not completely sure about this, but I think that if you drive
a ground rod at the garage they you must _NOT_ run a ground wire
out from the house. You would attach the "white" (or neurtral)
conductor from the house and all neutrals for garrage circuites to
a bus which is grounded at the garrage. (And since neutral is
grounded you can use a common ground/neutral bus. (Ground wires
are bare or green.)
As you can see from all these questions, I don't know how to do
this safely. If I were doing it I'd talk to either a licensed
electrician and/or the local building inspector to be sure that
what I did met code and was safe.
|
630.41 | | CADSE::MCCARTHY | Fixed in previous release. | Tue Aug 09 1988 07:08 | 11 |
|
RE: -1
I thought the code read that there should only be one "common
ground". This means only one point where the neutral and ground
wires touch. This would be in the main panel. Driving another
ground outside would mean that you would need to provide a seperate
grounding bar from that of the neutral strip. This is the case
with sub panels located away from the main.
bjm
|
630.42 | | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Tue Aug 09 1988 11:34 | 45 |
| >< Note 2502.7 by CADSE::MCCARTHY "Fixed in previous release." >
>
> I thought the code read that there should only be one "common
> ground". ....
I'm not a licensed electrician nor an "expert" on the NEC. With
that ceavet here is my understanding.
You're right that in general there is only one common ground. But
there are exceptions. For example, you'll find that the neutral
and ground are tied together in both the meter box and your main
breaker box. (At least I know that mine are that way.) I think
that seperate grounds for seperate buildings is the rule for at
least some case of home/farm wiring. There are probably other
exceptions for commercial/industsrial wiring which I know NOTHING
about.
The reason for the "one common ground" is to ensure that a short
circuit will connect (via the neutral wire) back to the main
breaker box and trip the main breaker if necessary. If the neutral
were grounded elsewher it could possibly dump an overload to
ground without tripping the main breaker. That's why "sub-main"
distribution pannels have seperate neutral and ground buses with
the neutral electrically isolated from ground.
However, in a seperate building the theory I understand is that
the ground wire gets "too long" to work effectively. (No, I m not
sure what that means.) So you install a breaker pannel and ground
it just like your main pannel. i.e. you treat it essentially like
service entrence equipment. The problem with tying together the
grounds from seperate buildings is that you can get a significant
electrical potential between different grounds. (Oh, yes! I've
seen ICs literally exploded by this!) Now you're going to ask why
the neutral, tied to grounds in different buildings, doesn't cause
a problem. Frankly, I'm over my head at this point. I think it has
to do with the fact that the neutral is a current carrying
conductor while the ground is not, but I'm not sure just how/why
this makes a difference.
As I think about this I'm not sure but what the garrage in
question might be close enough to the main house so that it need
not be treated as a seperate building. Which leads back to the
suggestion that you should get advice from a building inspector or
licensed electrician who knows the applicable code and the local
interpretation of it.
|
630.43 | I recommend a good book.... | LITLTN::CAHILL | Jim Cahill | Tue Aug 09 1988 13:36 | 17 |
| re .8:
I'm fascinated by your attempts to explain several rules of electrical
wiring, in particular the following:
� The reason for the "one common ground" is to ensure that a short
� circuit will connect (via the neutral wire) back to the main
� breaker box and trip the main breaker if necessary. If the neutral
� were grounded elsewher it could possibly dump an overload to
� ground without tripping the main breaker.
How "it could possibly dump an overload to ground" without tripping
*any* breaker (let alone the main) is beyond my limited knowledge.
I thought it had something to do with what's been mentioned a number
of times in other HOME_WORK notes on wiring: ground loops.
Jim
|
630.44 | | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Thu Aug 11 1988 14:18 | 25 |
| >< Note 2502.9 by LITLTN::CAHILL "Jim Cahill" >
> -< I recommend a good book.... >-
>
> How "it could possibly dump an overload to ground" without tripping
> *any* breaker (let alone the main) is beyond my limited knowledge.
Normally a "short circuit" places an effectively infinite load on
the breaker (or fuse), exceeding the rated ampacity and triping
the breaker.
However, it is also possible for the current carrying path of a
"short circuit" to follow a very circuitious route (no pun
inteneded), sometimes including the ground wire and/or the ground
itself. In this case it is possible for a current flow to be
present which is dangerous/injurious to people and/or equipment
WITHOUT exceeding the ampacity of the breaker. This happens
because the "short circuit" has enough resistance to reduce the
current flow to the rated ampacity or less. Since the ground
itself can be part of such a circuit I called this dumping "an
overload to ground". I suspect that "overload" was a possibly poor
choice of words.
The NEC rules requiring, generally, a single common ground, and
bonding neutral to ground only at the service entrance are
intended to minimize this possiblity.
|
630.16 | PVC conduit to garage: Codes? | CIMAMT::KELLY | Feelin' a little edgy | Tue Oct 11 1988 17:50 | 44 |
| I'm also in the process of increasing the electrical capacity to
the garage located adjacent to my house. I plan to run a 30A, 220V
line to a breaker panel in the garage, and to tap some 110V off
that.
My questions center around the means of getting the juice to the
garage. My service entrance and breaker are located in the basement.
The electrical contractor I've engaged suggested running 2 inch ID
PVC from the house to the garage.
1. The contractor said the bends in the conduit cannot total more
than 360 degrees, without introducing an access point. True?
2. Assuming I go the PVC route, are there fittings available to
terminate the conduit? Someone (I believe in note 1037)
mentioned UL approved PVC; does anyone know where I can locate
this material.
I'm particularly interested in getting from the conduit into
the structures (garage and house):
|
What goes here?..........> *********** UF 12/3 ******
(to connect PVC to wall) * ||
* || garage
+-*-+ || <........garage wall
2in ID PVC -----> | * | ||
| * | ||
--------+-*-+------------- ground level
| * |
| * |
*
*******
3. Where can I get a copy of the National Electrical Code?
4. Is there a Massachusetts Electrical Code, or does each town
have it's own, or does each town have additions that tag along
with the national and state codes?
Thanks in advance for your help,
John Kelly
|
630.18 | | STROKR::DEHAHN | | Wed Oct 12 1988 11:40 | 17 |
|
You can get a copy of the Mass Code at Central Electric in Worcester.
It's $19.00. The Mass code is the NEC with Mass exeptions. In almost
every case, Mass disallows something that is allowed in the NEC.
So make sure you check the first few pages before you plan your
design.
I don't think 12/3 UF is what you want to use for a 220V 30A run
inside conduit. I have my code book at home, but my guess is that
10G THW is what you really want. Be careful about the length of
the run as well as the bends in it. You may have to either go up
in size on the wire to pull the long length or add a junction box.
The box must be sized according to the size of the conduit entering
and exiting, and whether it's a straight thru or angle bend.
CdH
|
630.19 | Thanks, and a few more questions | CIMAMT::KELLY | Feelin' a little edgy | Wed Oct 12 1988 15:05 | 30 |
| Re -.2: Thanks for the info. I've been looking at PVC in the plumbing
area of my favorite hardware stores, but didn't see any
(let alone any esoteric) fittings that were meant for
electrical work. The electrical departments of these stores
also had no PVC fittings.
Re -.1: (and also to -.2) Hi, there, Chris. You guys are probably
right about the actual choice of line to put in...see, that's
why I need the Code! I'm more intent right now in getting
the raceway with sufficient capacity dropped in before it
starts to snow.
I'll have a 100A breaker panel in the garage, with only
partial utilization at this point.
Inevitably, good answers like these lead to more questions:
1. Could either of you recommend a good source of electrical supplies
for this type of work? I work in SHR (Shrewsbury, Mass) and
live in Maynard, Mass.
2. I'm assuming that I would need to run a seperate conduit for
signal, as opposed to power, lines. For example, if I was to
run a terminal drop or a phone line to the garage, I can't put
that in the same raceway as the AC...correct?
Thanks for help,
John Kelly
|
630.20 | | HEYDEN::BBARRY | | Wed Oct 12 1988 15:14 | 7 |
| < I'll have a 100A breaker panel in the garage, with only
< partial utilization at this point.
This is a no-no. The potential capacity of the panel can not exceed
the line feeding it. In your previous note you said you were only
running a 220V 30Amp service.
|
630.22 | More wiring info | GWYNED::MCCABE | | Wed Oct 12 1988 15:22 | 29 |
| 2" conduit sounds like overkill, 1" would be fine. You definately
do not want to run 12/3 uf. If you are running the PVC all the way
from the house to the garage, pull in #6 THNN of THHN. You can put
in a 60A submain and run everything you want. If you only need a
couple of light duty outlets you could use #12 but keep in mind
the voltage drop. The formula is in the code. You take the type
of wire (copper or alum) a constant, times the area of the wire
in circular mills and the voltage and divide by the # of feet.
you will get your voltage drop. I haven't done this calculation
in a while so the formula probably is off, look it up.
All the info is in the code. The piece that joins the garage is
called an LB, L bend. "elbows" are called sweeps when you are
dealing with conduit, ie 90 degree sweep... Couplings join sections
and sweeps together and connectors teminate to a box. You want nuts
for the connectors and insulated bushings for the end of the connector.
Note: some inspectore require the bushings to prevent the insulation
from getting ripped when pulling. For an outside corner there is what
is called pull a through elbow, I doubt you will use one of these.
GE makes a nice all plastic 60A sub main great for possibly damp
garages. Run the pvc right to your main and put in a two pole breaker,
you will connect 4 wires, hot "red" leg, hot "blue"leg, neutral and
ground. At the sub main do not connect the ground to the neutral.
Keep in mind all outlets in a garage have to be GFI.
Oh yea, the pvc has to be burried at least 18" unless you pour a
concrete pad over it.
Hope this helps,
Chris
|
630.24 | | TYCOBB::POWELL | Reed Powell HPS Marketing | Wed Oct 12 1988 16:48 | 28 |
| on the no-no of the 100A breaker, and the subsequent comment in
.-1, I belive that it is a definite NON-NO to have multiple breakers
on the same circuit; but I cannot find the citation in the code
book that I'm pretty sure I saw once before.
If you are in SHR, I'll second the earlier comment on Central Electric
in Worcester (Main St to Chandler, turn right coming from SHR, then
a left at the Y, 1 1/2 blocks and it's on the left). Good selection,
and they are smart enough to second guess you if they think you
aren't asking for the right thing.
Be careful about using the narrow PVC and turning corners - pulling
UF through the 90 deg sweeps is a b**ch and a half. Question to
the audience: on internal wiring being put inside of conduit, you
do not need to run sheathed cable. UF is designed primarily to
be buried without the aid of conduit - it is legal to place it directly
in the ground, if you follow the associated caveats. So, is it
legal for external runs being put inside of PVC (or whatever) to
just be unsheathed lengths of appropriate guage wire? It is MUCH
easier to pull that through, sweeps and all, and the sheathed wire.
Anyone know?
Definitely try and get as much service as you can, plans always
change once you start using the structure for new things. Can you
rearrange things to just use 2" plumbing PVC and running 6-3 to
get 50A service, or maybe 000 aluminum to get 100A?
|
630.25 | Thanks...the beat goes on | CIMAMT::KELLY | Feelin' a little edgy | Thu Oct 13 1988 10:25 | 74 |
| Re .20:
I don't understand why one cannot install a breaker panel that has
blanking plugs for possible future expansion. If I follow your
logic correctly, that says that every sub-main has to be totally
designed and fixed in capacity, up front, with no upgrade potential.
Re .21 and .23:
Thanks for the pointers to Maynard Supply and the place in Marlboro.
Re .22:
Thanks for the tips and the 'buzzwords'; never again will I call
a sweep a bend! As soon as I locate the Code, I'll be able to more
fully understand the details of your reply. I do plan to make two
45 degree sweeps in place of 90 degree sweeps, where possible.
I do plan to install GFCI outlets. I think I will stick with the
2in. PVC, for potential expansion.
End-of-replies...thanks for your time. I really feel like this
is the only accurate source of unbiased information available to
me. Now, on to the update:
1. Here's a plan view of my house:
+------------+
| |
|-+ |
2in PVC ************* | GARAGE |
* |-+ |
* | New sub-main 100A
* +------------+
*
*
+-------------------------*--------+
| ******Feed to garage***** |
| * |
| * |
| * |
| * HOUSE |
| * |
| * New main |
| +----+ 200A |
->[| | | |
| +----------------------------------+
|
Service
entrance
I'm having contractors in to bid the following:
a. Remove old 60A fuse panel, plus some other minor electrical
additions and replace it with a 200A main.
b. Run the service to the garage, including digging the trench for
the PVC and installing it.
c. Install a 100A sub-main in the garage.
d. Provide two 220v branches in the garage, plus two 20A 110v branches.
e. Remove the existing wiring in the garage: 3 outlets, 3 fixtures.
GFCI outlets.
The first bid I got was $2000! Is this reasonable?
What about a requirement to run signal lines in a different conduit?
Regards,
John Kelly
|
630.26 | | STROKR::DEHAHN | | Thu Oct 13 1988 10:47 | 27 |
|
THW and THHW are unsheathed wires with insulation, which is what
I suggested a few notes ago. Again, I don't have the book in front
of me so I'd have o look it up in the tables for the exact wire
for your needs. Running UF or Romex in a conduit is overkill, just
use what you have to.
As far as I know, all the code requires is to have all openings
in the panel covered by an approved plug or panel. There is nothing
wrong with using a 100 amp feeder and using a 60 amp submain breaker.
You can't use a 60 amp feeder with a 100 amp submain breaker, that's
obvious.
As for the signal lines, you have to define what kind of signal
they're carrying, because various types of systems (audio, telephone,
etc) each have their own section in the code and have their own
special restrictions. Now, I know Mr. Kelly, so I'd guess he wants
to run telephone cable and maybe an audio line to the garage. The
telephone I'm not sure about, but you can run audio lines in the
same conduit as power cabling as long as the voltage on the audio
lines doen't exceed 70 volts (number sound familiar?). Also, in
most cases, you can only fill a conduit, raceway, or wireway to
40% of it's capacity with wires. There are exceptions, you have
to check the code to see how far you can go.
CdH
|
630.27 | 220v GFI? | MILVAX::HO | | Thu Oct 13 1988 10:57 | 4 |
| Re .25
Would the 220v circuits also require GFI protection? If so, how
would this done? I've never seen GFI 220v outlets.
|
630.28 | | STROKR::DEHAHN | | Thu Oct 13 1988 11:47 | 7 |
|
Use four pole GFCI breakers in the subpanel. They have to be ganged
for both sides of the 220V line, when one shuts off the other one
must too.
CdH
|
630.29 | clarrification of .20 | HEYDEN::BBARRY | | Thu Oct 13 1988 11:59 | 15 |
| < Note 1038.20 by HEYDEN::BBARRY >
To clarrify my previous note. The ampacity of the wire between the
main and the sub-panel must meet or exceed the breaker rating
(no problem). The ampacity of the wiring must meet or exceed the
capacity of the sub-panel(i.e. you can not have a panel rated for
100 Amps connected to 30 Amp wiring). The rating of panels already
takes into consideration the usage factors.
I haven't had a chance to look this up in the codes. I vaguely
remember this from the last time I wired up a sub-panel(1981,
100 Amp, commercial building, Phoenix, AZ). If this is wrong could
somebody explain why?
Brian
|
630.30 | | HPSMEG::LUKOWSKI | Nat'l apathy week & nobody cares! | Thu Oct 13 1988 12:23 | 6 |
| re: .25
If you go to Marlboro Electric (if that's the name), don't forget
to ask for the discount for DEC employees. It's either 30% or 40% off
list.
|
630.32 | Have NEC; will read | CIMAMT::KELLY | Feelin' a little edgy | Thu Oct 13 1988 14:55 | 9 |
| Thanks again...I went and got the NEC (they were out of the Mass
EC)at lunch. I'm going to do some digging (in the Code, that is!)
tonight.
I'll be back with more questions once I get a tiny bit more educated.
Regards,
John Kelly
|
630.33 | More sub-main info | GWYNED::MCCABE | | Thu Oct 13 1988 15:18 | 6 |
| ref .26, In general in a single family house, if you run a feeder from
the main through a seperate breaker, you would put in a sub-main without
a main disconnect. If you ran a sub-main for a two family house and
tied into the feed before the main you would install a main disconnect
in the sub-panel rated the same as the main panel.
Chris
|
630.157 | Don't you HAVE to have the conduit? | DEMING::HLQAR | | Fri Jan 13 1989 05:50 | 16 |
| re .5
It was my understanding that underground cable (in Mass (in Billerica))
HAD to be in some kind of conduit. A neighbor was installing a
pool and was running a line out to the pump box. He had to dig
a trench which was three feet deep, lay the line and conduit with
the fittings open, have THIS inspected, then close everything up,
have the guy look at it AGAIN, and then backfill with the marker
tape. The inspector was being a real hard-nose throughout the entire
operation; I think he was upset that we didn't tip him. I, personally,
was too busy trying to keep the red ants from crawling up my legs,
since we had hit a nest by digging so deep. This has been my only
brush with electrical inspectors, so if you've had better luck,
I'll keep hope ...
Frank
|
630.178 | Estimating wiring needs | TOKLAS::FELDMAN | PDS, our next success | Mon Jun 26 1989 20:37 | 31 |
| I'm doing the plans for wiring our garage addition, and it's time for a
sanity check. I haven't seen any notes on estimating wiring needs.
I figure on:
1 20 Amp GFCI circuit for 6 garage outlets, one exterior outlet,
one bathroom outlet.
1 20 Amp circuit for the two 1/2 hp garage door openers, two light
fixtures in the garage, one exterior fixture, and possibly the bathroom
light.
1 20 Amp circuit for the upstairs bedroom (9 or 10 outlets)
Optional luxury items:
1 dedicated 20 Amp circuit for an airconditioner for the upstairs
bedroom.
1 dedicated 20 Amp circuit for a whirlpool in the upstairs bath.
Is this reasonable, overkill, or am I missing anything? Are there
better layouts.
How do I estimate the amount of wire to buy? Do I have to map out
paths in advance? Or do I just buy a 250' roll of 12/2, and buy more
if/when I run out? Is it worth drilling holes through studs (since my
labor is free), or should I just run wire along the joists between the
first and second floors, and through the attic?
Gary
|
630.179 | one circuit in a room = dark | TFH::DONNELLY | Take my advice- Don't listen to me | Tue Jun 27 1989 00:29 | 4 |
| one idea i used when planning was to mix rooms and circuits. then, for
instance, if you pop a breaker in the bedroom you will only have 1/2 the
room out. or, you will always have one garage door working. you get the
idea. -craig
|
630.180 | | TOKLAS::FELDMAN | Day 1: A couple of footings, a couple of walls | Tue Jun 27 1989 11:21 | 12 |
| Good idea, but I already have one existing light in the garage on a
separate circuit. Since I don't want the openers to share anything
except light fixtures, and I only have five new light fixtures to add,
I think I'll keep the openers on the same circuit.
You have given me an idea for an improvement upstairs. Rather than
wiring just one outlet box for the air conditioner, one in the vicinity
of each window. That way the bedroom will have two outlets on one
circuit, with a choice of windows to use for the AC, and four or five
outlets on another circuit.
Gary
|
630.181 | RE .17 | WONDER::COYLE | Only 48.8% of my former self! | Tue Jun 27 1989 11:26 | 11 |
| RE .17
I would NOT drill holes in the studs to pass the wireing through.
The possibility of a nail in the stud accidently hitting a wire
would dicourage me from trying to save a few bucks that way.
This might not happen today when you are doing the work an know
how/where what is what. But, when you/next_owner, remodel it
would be a more likely possibility.
-Joe
|
630.182 | | BEING::WEISS | Trade freedom for security-lose both | Tue Jun 27 1989 14:24 | 15 |
| > I would NOT drill holes in the studs to pass the wireing through.
> The possibility of a nail in the stud accidently hitting a wire
> would dicourage me from trying to save a few bucks that way.
Wires are put through studs all the time. What is necessary is that you use a
drill bit no larger than 5/8", and that you center the hole on the stud. This
ensures that there will always be 1�" of stud on either side, 2" counting
sheetrock. Sheetrock is normally put up with 1 5/8" screws.
You can put the wire closer to the face of a stud, but you have to cover it
with a metal plate.
For the same reason, you should never drive a nail more than 2" into a stud.
Paul
|
630.183 | | HANNAH::DCL | David Larrick | Wed Jun 28 1989 13:24 | 48 |
| .17> 1 20 Amp GFCI circuit for 6 garage outlets, one exterior outlet,
.17> one bathroom outlet.
As mentioned in this conference in a few other places, you may be sorry if
you GFCI protect all of these outlets from a GFCI breaker or from one GFCI
outlet. When you trip the GFCI, you want to be able to reset it without
walking around too much in the dark. GFCI outlets are cheap enough that
you could put one in the bathroom, another protecting all the garage
outlets, and a third as the outdoor outlet. Then it's immaterial whether
all of these GFCI-protected outlets are on the same circuit or not.
One 20A circuit for garage and exterior outlets, shared with the bathroom,
is OK if your maximum load is a shop vac, hedge clippers, or a hair dryer
(not at the same time, though!). If there's much chance of using the
garage as a workshop with stationary power tools, and/or running an
electric garden shredder outside, consider more circuits, 30A, and/or 240V
now. It's a lot easier to run more wires before the walls are closed up.
On the same theory, run all the telephone cable, video cable, doorbell
wire, etc. that you could think of using in your wildest dreams. You don't
need to install any wall plates etc. for these now; just take copious
photographs just before you close up the walls so you can find the ends of
these wires when you need them.
.17> How do I estimate the amount of wire to buy? Do I have to map out
.17> paths in advance? Or do I just buy a 250' roll of 12/2, and buy more
.17> if/when I run out?
Since I'm lazy, and since I always seem to find more wiring projects to do,
I would buy a 250' roll. It's amazing what sorts of obstacles and changes
present themselves that invalidate your carefully planned cable-routing
schemes.
If you're using 3-way switches, you'll need some 12/3 also.
.17> Is it worth drilling holes through studs (since my
.17> labor is free), or should I just run wire along the joists between the
.17> first and second floors, and through the attic?
Only you can trade off your time/labor vs. wire cost. And you can use
different strategies in different situations: if two cables need to take
the same path, you can often run both of them through the same hole, so
drilling holes saves twice as much wire in this case.
If you're going to drill more than a half-dozen studs and/or joists,
though, you'll need a serious drill and an auger (self-feed) bit.
|
630.184 | | TOKLAS::FELDMAN | Day 3: Joyful joists in place | Thu Jun 29 1989 16:52 | 16 |
| Using two GFCI's is a great idea. Thanks.
The workshop, if any, will be in the basement, at a much later date.
The only heavy duty tool I might put into the garage would be a
compressor, for air tools for working on cars. How much does current
does a reasonable compressor draw? This won't be a serious hobby, so I
don't need the deluxe, heavy duty model.
We are planning on running phone, video, and audio, but we'd forgotten
about the door bell. Thanks.
Do I really need to get an industrial strength drill? I would have
thought my 3/8 hp mid-quality Black & Decker would be sufficient,
especially if I take my time?
Gary
|
630.185 | | HANNAH::DCL | David Larrick | Thu Jun 29 1989 17:58 | 12 |
| .23> Do I really need to get an industrial strength drill? I would have
.23> thought my 3/8 hp mid-quality Black & Decker would be sufficient,
.23> especially if I take my time?
I burned out two 3/8" "better-quality homeowner" drills - one B&D and
one Sears - drilling holes for wiring in studs and joists in our
addition. My new 1/2" Milwaukee doesn't even shrug at the same jobs -
and I no longer need to take a break after every couple of holes.
You may not be drilling through the same intricate window framing that
I was, nor through 80-year-old full-dimension joists. But if you need
an excuse to buy a great drill, here it is.
|
630.186 | plan ahead for 220 | PCOJCT::MILBERG | Barry Milberg | Thu Jun 29 1989 18:41 | 12 |
| re .23
Put in a 220 line for the compressor. The 220 ones usually have
more 'bang' for the buck and you can also pick up a used industrial
one cheap.
Since my 'new'_old house in NJ had central air put in and the 220
lines were no longer needed, I pulled one down from the living room
to the garage and use it for the compressor.
-Barry-
|
630.187 | | STROKR::DEHAHN | | Fri Jun 30 1989 09:51 | 11 |
|
A basic 1 horsepower 12 gallon 'homeowner' compressor will suck the
life out of a 15A 110V circuit. Even at 20A it's marginal. A lot of
these can be run on 220V with a simple wiring change in the motor.
20A at 220V should be plenty for that size compressor. I currently run
mine off the dryer outlet, using a 30A dryer cord, swapping it out
whenever I need to use the compressor. The lights don't even dim. In
the new house I'm going to run a 30A dedicated circuit for it.
CdH
|
630.134 | special code requirements for a shop? | RGB::SEILER | Larry Seiler | Tue May 01 1990 02:42 | 31 |
| I am now working on wiring up a shop, and I have some questions about
special code requirements for a shop -- and a garage, too. I've looked
through my old code book and a workshop doesn't not seem to fall into any
of the "hazardous location" categories. Even a home garage is exempt.
Anyway, here are some specific questions:
One of the replies to this note refers to placing outlets at "hammer height,
which is the code height". Just what is the code height for outlets in a
shop? My dad, who lives in CA, was required by his inspector to put all
workshop outlets 4' off the floor. Does anyone know if that is part of
the code or standard practice in Mass.? I want to avoid this if possible.
Another reply refers to putting multiple 20A 240V outlets on the same
circuit. I seem to recall a discussion elsewhere in which it was claimed
that 240V outlets must all be on separate circuits. Can anyone tell me
whether they can be on the same circult?
How about special rules for a garage? I plan to put all of my garage
outlets on the ceiling, but I'm thinking of eventually installing a
couple of electric baseboard heaters later -- it's a detached garage,
so it would be nice to be able to have heat if I have to work out there.
I'm planning to mount them up off the floor, but does anyone know of
any special restrictions that I may have to face?
Naturally, I'm going to ask my town electrical inspector these questions.
However, I like to go to inspectors with as good a general knowledge
as I can -- it helps me to understand what they are talking about.
Thanks,
Larry
|
630.135 | 30a vs 20a | WARLRD::BURDEN_D | No! Your *other* right! | Tue May 01 1990 15:23 | 5 |
| I have 2 30a 240v outlets in my garage and they were wired to seperate
circuits. I don't know if going with 20a lines will make any
difference or not.
Dave
|
630.45 | what size wire? | MCDONL::BARANSKI | Neomaniac on the loose! | Wed Sep 26 1990 15:03 | 10 |
| I want to run electricity out to my garage. It's about 50 ft away from the
fuse box. What size wire would be required for 20A? 30A?, 50A?
It's hard to say how much load this will have to bear, as it's big three car
two story gambrel garage. I do want to put a wood working shop out there,
so figure a couple of good sized motors: drill press, table saw, or lathe,
and a dozen lights. Who knows what I might put upstairs later, so I'd like
to put down the biggest I might need that won't cost me an arm and a leg.
Jim.
|
630.46 | | DICKNS::WELLCOME | Steve Wellcome (Maynard) | Wed Sep 26 1990 15:16 | 11 |
| I'd probably run a 240V line of 10-3 (good for 30 amps per side) to
a separate breaker box in the garage, where the 240 volts could
be broken down into separate 120V circuits and possibly a 240V
circuit.
You'd come off a double-pole 30A breaker in your main box to feed
the separate box. There are a few oddities in the electrical code
about installing a separate breaker box, the main one being that
the ground and neutral wires are *NOT* tied together; they have
to be kept strictly separate right back to the main breaker box.
|
630.47 | I would use a separate panel. | HDLITE::FLEURY | | Thu Sep 27 1990 09:13 | 13 |
| RE: .-2
My suggestion would be to add a sub-panel to the garage. Run a line of
2-O SER cable to the panel. This would allow you up to 100A of breaker
space. I am currently using this method in my workshop. I have the
main breaker set to 60A with the cable capable of handling 100A. This
gives me quite a bit of flexability in terms of breakers for various
equipment. I am running conduit from the ceiling down to the equipment
so I can place things where I want them without worrying about cables
on the floor.
Have fun,
Dan
|
630.158 | Feed my shed | ODIXIE::RAMSEY | Take this job and Love it! | Fri Oct 05 1990 12:30 | 46 |
| Well, now that my shed/workshop is complete except for some exterior
trim, it is time to start planning phase II, the Utilities Phase.
The shed is 100-110 ft from the house and the service pannel is an
additional 10-15 ft cable run from the exterior of the house. 150 ft
of wire should be adequate to allow me to have extra on both ends of
the run. I plan on putting a small subpanel in the shed.
Since the shed is only 12x12 and it will be partly storage and partly
workshop/hobby area, and I don't have any 220 tools or plan on getting
or using any within the foreseeable future, 110-120 circuits will fill
the bill. Discussion about extension cords has lead me to think about
running 10 guage to the shed and then using 12 guage for the outlets
and lighting circuits.
Home Depot has a 250 ft. box of 10-3 for $79. If I buy 150 ft., it
costs $.47 a ft. or $71. For the additional 8 bucks, I might as well
buy the entire box. The entire run if I am careful might be 125 ft.
So I might be able to run two 10 guages wires to the subpanel.
Finally the questions.
- What amp fuse should I put on a single 10 guage wire assuming it is
the only feed to the subpanel?
- Can I have two power feeds to a subpannel?
- With two feeds, I probably should use a single fuse for both in the
main panel. What should it be rated at?
- Would a single fuse allow four contacts or do I have to have a junction
box where I tie the 2 10# to one 8# guage?
- Do they make ground contact rated phone cable so that I can bury it
in the same ditch or must it be in a conduit?
- Since the wire is ground rated (UB?) and will not be in a conduit,
can I run a water supply line in the same ditch or must they be in
seperate ditches or the electrical placed in conduit?
(The frost line here is 12 inches and the ditch witch digs a 24 inch
ditch so water supply would be safe from freezing and frost heaves.)
The cost of 8 guage is significantly higher than 10 so it not a real
solution to double feed. I am just trying to take advantage of left
over wire. The double feed is not needed for capacity, just an idea I
am toying with.
|
630.159 | | DICKNS::WELLCOME | Steve Wellcome (Maynard) | Mon Oct 08 1990 14:20 | 4 |
| Run the 10-3 off a double 30A breaker in your main panel and
you'll get two 120V circuits of 30A each for your outbuilding,
which you'd want to split at the subpanel into multiple 15A
ands/or 20A circuits, plus you'll have 240V if you ever need it.
|
630.160 | | VMSDEV::HAMMOND | Charlie Hammond -- ZKO3-04/S23 -- dtn 381-2684 | Mon Oct 08 1990 15:34 | 21 |
| > Well, now that my shed/workshop is complete except for some exterior
> trim, it is time to start planning phase II, the Utilities Phase.
Wrong. The time to plan the Utilities was the same time that you
planed the rest of the construction. Seriously, you don't seem to
have made yourself any additional problems, but many people have
done so by not planning the entire project up front. And you're
not done yet...
O.K., having said that I'll put in my 2� worth. What do you want
to have in your workshop? If you someday find yourself trying to
run two machines plus some lights you may find that 30A is a bit
light. I'd opt for 50A, which calls (I think) for number 6 wire.
If you stay with 30A, I'd still recommend spending the bucks for
#8 wire, because your pushing 200' of wire and you'll be getting
significant voltage loss. Using #8 will reduce the loss.
Do you understand the need to have separate neutral and ground
busses in the sub-pannel you put in your shed/shop? If not, ask
before you proceed -- or find the discussion somewhere in this
file (I think).
|
630.188 | need box ? | SHALOT::GRACE | sailing is in my blood | Thu Oct 17 1991 16:42 | 24 |
|
I am installing a surface mount fluorescent light on the ceiling of
my garage. The attic of the garage is open and will never be
finished. Do I have to put a box in the ceiling or can I run the
wire through the sheetrock into the fixture. The lights will be screwed
into the ceiling and are considered permanent.
The light fixture only has 5/8 knockouts, not 2".
With small bolt on conduit Box installed in ceiling.
and cable clamp.
-
| |
--------------- -----------
| | \ ___ | __
- ||| | | |
----------------|||---------------------------- | | | ------------
----------------|||---------------------------- | | | ------------
------------|||------------- ------------- | --------
| | | | | |
| | | |
---------------------------- ------------------------
|
630.189 | light is a box | N1BRM::GETTYS | Bob Gettys N1BRM 235-8285 | Mon Oct 21 1991 13:34 | 7 |
| My understanding is that a flourescent fixture is considered to be a box
in and of itself. Thus there is no need for a separate box to feed it from. You
use the same cable clamp that you would put into a box that doesn't have a built
in one and install it into a knock out somewhere on the fixture. I have installed
fixtures in that manner and it works out just fine.
/s/ Bob
|
630.136 | general shop wiring questions | CSC32::S_MAUFE | gotta get a new personal name | Mon Oct 21 1991 16:37 | 21 |
|
guess what I'm doing this weekend, yup wiring the shop 8-) I've read
all the previous replies, and have a couple of questions.
Could I wire the sockets in a ring? ie, wire leaves breaker box, passes
through a bunch of outlets and returns to breaker box? Would this give
me anything, I'm thinking in terms of wiring capacity? In a couple of
months I'll have some stationary power tools, table saw, drill press
and jig-saw.
Anybody have prices/details of the central GFCI boxes? Can you get 30
AMP ones? I'm used to seeing the GFCI sockets, but am interested in
getting a GFCI box that protects the entire circuit.
The shop(ex-barn) is approx 100 yards from the house. Current a 12/2
wire runs from a breaker box in the house out to the barn(overhead).
I'm going to change this to 10/2 that taps off the electricity company
line, then goes into a new breaker box in the shop/barn. Is this
goodness?
thanx for all advice, Simon
|
630.137 | | TOKNOW::METCALFE | Eschew Obfuscatory Monikers | Mon Oct 21 1991 17:15 | 1 |
| Why would you want to go back to the breaker box?
|
630.138 | | CSC32::S_MAUFE | gotta get a new personal name | Mon Oct 21 1991 17:30 | 3 |
|
that was *MY* question. I wondered whether it would get me anything?
|
630.139 | GFI outlet cheaper than GFI breaker | POBOX::KAPLOW | Have package, will travel | Mon Oct 21 1991 22:15 | 20 |
| If you went back, what would you connect to?
Seriously, this is reasonable for low voltage lighting, where the
current loads are very high. It prevents the lights from getting
dim on long runs. For 120v in a shop I don't think it is
necessary, even if possible.
As to GFI outlets, forget the GFI breakers if possible. They cost
many times what a GFI outlet costs, about 5:1 for my Square-D box.
The GFI offers better protection the closer it is to the point of
use. A single GFI outlet will protect everything downstream, so
don't worry that you will need a handful of them on each circuit.
The only reason for using a GFI breaker is that there is no outlet
to put the GFI on. My whirlpool tub is protected by a GFI breaker
in the main box as it is direct wired and there is no plug. All
other GFIs in the house (3 bathrooms, kitchen, basement, garage,
and outside) are provided by GFI outlets. I'm still surprised that
the NEC didn't require GFI for the laundry, but I intend on
replacing that outlet with a GFI as well.
|
630.140 | Check list time | ELWOOD::DYMON | | Tue Oct 22 1991 07:58 | 9 |
|
Have you done any wiring before?????? The reason I ask is
if it dosnt get done to Codes, and something happens......well
your insurence may not cover you! 300' is long way to go if
you decide to run something that draws a fair amount of amps.
JD
|
630.141 | | STAR::DZIEDZIC | | Tue Oct 22 1991 08:52 | 41 |
| I think I'd ask the same question as .51 - do you have any idea
what you're doing? Please don't mis-interpret this as being a
poke at your abilities, but from the questions you've asked it
appears you're not real familiar with wiring methods.
That said, a few specifics:
1) The "circular connection" (radial) of outlets could be seen
as a way to reduce voltage drop, especially if the length of
cable from the breaker to the last outlet "in the ring" is
substantially greater than the DISTANCE from the breaker to
the last outlet "in the ring" (assume one is installing the
outlets around the perimeter of a room to visualize this).
I don't believe the NEC would like this scheme, though; the
multiple connections to a single breaker in the panel seems
to smelly fishy (sorry, can't quote chapter & verse). The
possible reduction in voltage drop is probably not going to
be that significant anyway.
A simpler solution is to "break" the run into two branches,
one for each "half" of the circle, each on a separate breaker.
Since this is a shop you want multiple branch circuits so you
don't have problems when running more than one power tool at
the same time.
2) As has already been mentioned, GFI outlets protect all outlets
downstream of them. They are quite a bit cheaper than the panel-
mounted GFI breakers (about $7 as compared to $30 or more). The
outlets aren't available (typically) above 15A (20A feedthrough),
so there ARE cases where you might need to use a GRI breaker, but
those are relatively infrequent.
3) How do you plan to "tap off the electricity company line"? You'd
be better advised to install a dual-pole breaker in your existing
service panel & use that to feed a subpanel in your shop. Note
that when you use a subpanel you'll need to isolate the neutral
busbar in the subpanel from the subpanel cabinet, so you'd need to
use 10-3 w/ground to meet NEC requirements.
Don't rush out to do this job. Buy a copy of H.P. Richter's book on
"Wiring Simplified", or something similar, and READ, READ, READ.
|
630.142 | | KAOFS::S_BROOK | | Tue Oct 22 1991 10:40 | 55 |
| OK Guys, in best tradition, lets shoot first and ask questions later.
In Simon's defence, he's not asking dumb questions really; he's
comparing wiring methods used in the UK and Europe with that used
here.
It is normal in the UK for example to use a "ring" circuit, where
both ends of the same wire enter the breaker / fuse. The purpose
of such an arrangement allows higher current loads on the circuit
than a single conductor would allow, thus permitting a smaller
conductor. Such an arrangement does not have to use significantly
more wire with a good arrangement of outlets. For example, the
English 30 Amp "ring main" is actually wired with cable with a
20 amp rating. Many outlets rated individually at 13Amps are allowed
on such a circuit, and each outlet is fused by a fuse in the plug,
thus protecting the higher current circuit from failures of the
applicances plugged in. The whole circuit is protected at 30 Amps
in the fuse / breaker box.
Also, it is normal in the UK to have a master GFCI for the entire
box ... consider it safety overkill. These GFCIs work in one of
two ways ... either by detecting current in the grounding conductor,
or by detecting current differential in the live and neutral (ground)
conductors.
The ring circuit is specifically prohibited by code (NEC in the USA
and it's extremely close equivalents here in Canada). This is because
of the limited current handling capabilities of connectors and loop-
throughs on things like outlets. All the connections and loop throughs
are rated for about 20 Amps, where the ring circuit would in theory
allow higher currents, making this a safety hazard.
The idea of the central GFI is just not popular here, although I expect
if you could find one it may not be prohibited. On the other hand,
the cost of such a GFI would be very expensive here, and must meet
UL standards. Remember too that you would have a double ganged one
to disconnect BOTH live conductors ... remember domestic power here
is distributed as 220 V centre tapped to ground ... i.e. 110-0-110
The GFI outlets are a good idea because they are cheaper. For some
circuits, I do prefer a GFI breaker on the circuit because I am far
happier to know that the entire circuit is dead in many circumstances.
It would be a good idea though, to have a look at some of the diy
electrical guides. Most of them do follow codes pretty closely.
If you should read a book of electrical codes, beware of the terms
ground conductor and *grounding* conductor. They are different.
The former is Neutral, the second is the bare wire ground! If you
ponder things not covered in the diy guides, like teh ring main,
they probably aren't code here and shouldn't be used.
Good luck!
Stuart
|
630.143 | I think ... | NOVA::FISHER | Rdb/VMS Dinosaur | Wed Oct 23 1991 10:30 | 4 |
| I think a 300' ft length of 14 guage wire will leak enough current to
trip a GFCI breaker.
ed
|
630.51 | Installing a 220v outlet in an attached garage. | TLE::LEGERLOTZ | Alan Legerlotz: Repository Engineering | Wed Dec 02 1992 16:39 | 39 |
| I just bought an Arc Welder, which I'll be using to restore an old MG.
The problem:
The welder is a 220v and I don't have a suitable outlet in the garage;
everything is standard 110v (and on one circuit; which is another problem 8^).
I need to put in a 220v outlet in. My box is down in the basement and the garage
is on what's considered the 1st floor. The both share a wall, however, so the
length of wire from the box to the outlet would be about 20 feet at maximum.
The box has a main switch which consists of 4 breakers tied together with a bar.
There are three 220v circuits coming out of the box already; all three of them
consist of two 50 amp breakers tied together with a bar.
I have a few questions...
1) Can I do this job myself, or must it be done by a licensed electrition?
2) If I can't do it myself, can I at least save some money by running the wire
myself?
3) If I do any part of the job myself, will that require me to have it
'inspected'?
4) I don't know what the house is feed into the house is. How much of a bearing
will this have on the amperage of the new outlet? The other 220v circuits
are 50 amps, and I'd like this one to be, too. The guy I bought the welder
from had it wired to a 30 amp circuit, but he only used the welder set on
75 amps of lower. I probably won't use it higher than that, but if I can
put in 50 amp circuit, I might as well do that...I'd rather have more than
I need.
5) How do you wire of of these?
I'm an engineer and understand basic electronics; I've never working in an
electrical box before, though.
-Al
|
630.52 | Sounds simple - a question and a suggestion | SEIC::DUKE | | Thu Dec 03 1992 12:39 | 24 |
| | must it be done by a licensed electrition?
In New Hampshire you can do it your own home. This is, I believe, true
statewide. In MA I get the impression you need a license to change a
light bulb. (-: Nit pick - I'd suggest an electrician. (-: [spelling]
Sorry, I couldn't resist.
You description of the main breaker is a bit odd. A four pole main?
Doesn't sound correct.
Where do the three 50 amp circuits mentioned go. If one of them is not
in use, how about moving it?
If you have spare positions in the panel it is pretty simple. A new
breaker, enough wire and a receptacle should be about it.
If you are going to be using the garage for a shop a regular basis, how
about a small subpanel for garage circuits including the welder? Not a
huge increase in cost and the breakers are handy. Also allows locking
to help prevent unauthorized use of welder and such.
Regards,
Peter Duke
|
630.53 | stuff. | TLE::LEGERLOTZ | Alan Legerlotz: Repository Engineering | Thu Dec 03 1992 13:02 | 58 |
| >> ... must it be done by a licensed electrition?
>>
>> In New Hampshire you can do it your own home. This is, I believe, true
>> statewide. In MA I get the impression you need a license to change a
>> light bulb. (-: Nit pick - I'd suggest an electrician. (-: [spelling]
>> Sorry, I couldn't resist.
I KNEW that the first response would be "Get a pro to do it" 8^). I'm an
engineer, so even if I end up paying to have it done, I have a *need* to know
what the person is going to do for my $xx an hour plus materials...
"electrition"...yeah, that the Olde English spelling...yeah, that's the ticket!
>> You description of the main breaker is a bit odd. A four pole main?
>> Doesn't sound correct.
Perhaps my terminology or something is funny. There are, however, 4 breakers
which are tied together with a bar. They don't have an amperage number written
on them (that I can see from the front of the pannel with the breakers in the
'on' position.
>> Where do the three 50 amp circuits mentioned go. If one of them is not
>> in use, how about moving it?
One goes to the central air conditioning (2 units), one goes to the kitchen (for
the stove top and oven), and I'm pretty sure that the other goes to electric
dryer. All three of the pairs of breakers (again, tied together with poles) have
50 Amps written on them.
>> If you have spare positions in the panel it is pretty simple. A new
>> breaker, enough wire and a receptacle should be about it.
There are several empty positions in the box.
>> If you are going to be using the garage for a shop a regular basis, how
>> about a small subpanel for garage circuits including the welder? Not a
>> huge increase in cost and the breakers are handy. Also allows locking
>> to help prevent unauthorized use of welder and such.
I won't be in this house much longer, but long enough that I want to be able to
use the welder there. If I were staying, I'd definitely put in a sub panel
(since all of the 110 outlets in the garage are on ONE breaker - which is stupid
for a 24 x 24 garage with lots of outlets); since I won't be staying, I'd like
to do this as cheaply as possible. As far as locking things up goes, its really
not an issue. If someone used it without my permission, they would have had to
break into the house, so they're probably just steal the whole welder (or fry
themselves 8^)
Can you offer more info about the gauge wire to purchase, and other things like
that?
Thanks,
-Al
|
630.54 | Didn't intend for you to hire an electrician | SEIC::DUKE | | Thu Dec 03 1992 15:24 | 16 |
| re: .2
Hiring an electrician was not my intent at all. I was trying to be
funny about the spelling. I do all my own work if at all possible.
A 50 amp welder circuit should be #6 copper if memory serves me. Home
Depot in Nashua has 6-3 w/ gnd romex for $1.21/ft as of a couple of
weeks ago. They very likely have the receptacle also. They carry Square
D breakers if that is the brand you need.
For the short time you are going to be there, how about boring one of
the A/C circuits? At least use the breaker and save probably $10.00?
Pete Duke
|
630.55 | Gotcha | TLE::LEGERLOTZ | Alan Legerlotz: Repository Engineering | Thu Dec 03 1992 15:59 | 22 |
| >> Hiring an electrician was not my intent at all. I was trying to be
>> funny about the spelling. I do all my own work if at all possible.
Oh. I got the spelling part 8^). People around here keep saying "Get someone
to do it", but that's what most of them do for any home job like this, anyway.
>> A 50 amp welder circuit should be #6 copper if memory serves me. Home
>> Depot in Nashua has 6-3 w/ gnd romex for $1.21/ft as of a couple of
>> weeks ago. They very likely have the receptacle also. They carry Square
>> D breakers if that is the brand you need.
I usually shop at Home Depot or Builder's Square, so I'll check there.
>> For the short time you are going to be there, how about boring one of
>> the A/C circuits? At least use the breaker and save probably $10.00?
I probably could, but I'd like to be in the box one time, and one time only. For
the $10 or whatever extra it'll cost me, I'll just do it once and for all.
Thanks for the info!!
-Al
|
630.56 | | QUARK::LIONEL | Free advice is worth every cent | Thu Dec 03 1992 19:50 | 5 |
| I strongly suggest pulling a permit for the work - it's technically
required and will keep you from getting burned (so to speak) if there's
any problem in the future.
Steve
|
630.57 | Works fine for me! | VSSTEG::TOWLE | Corky | Fri Dec 04 1992 07:42 | 26 |
| Having had to do this myself.
To provide poratbility for the welder I made an extention cord 50' long.
Can't offhand remember the gage of the wire in the extention cord but if you
go to an electrical supply house for the other stuff just tell them what
you're going to use it for and they'll provide the correct gage. Mine is heavy
gage 3 conductor stranded rubber covered and is very flexible. (Sort of like a
VAX system power cord)
Get a Female 3 prong 220 v receptacle as is used for an electric stove or
dryer that matches the male plug on the buzz box (welder). (There is usually
one provided with the welder). Put this on one end of the extention cord.
Get a male 3 prong and another female 3 prong.
Mount the second female 3 prong to the side of the breaker box and put the
male plug on the other end of the extention cord.
Install and wire up a common trip 2 pole 60 amp breaker, (or whatever your
welder calls for) to the breaker box mounted female receptacle. If you can't
find a common trip breaker get a regular 2 pole and put a hunk of 12 ga solid
wire through the breaker switch lever holes and bend each end over to hold it
in place and now you have a common trip breaker.
Plug everything in and enjoy!
|
630.58 | Dont over design it | EMDS::COHEN | | Fri Dec 04 1992 12:31 | 31 |
| Adding a 220v line to ones garage is not too difficult. I use mine
for heater (17,000 btu Dayton) and an air compressor.
The most critical issue facing you is space in the circuit/fuse panel
and what kind of breakers did the builder use. If you have space,
I suggest you buy a pair of 15 or 20 amp singles (gives you30 or 40 amps)
and mount them across each side of the box. If you check the price of
a 50 amp breaker you might get a "shock".
There are several types of breakers. If your box is a Federal-Pacific
you have my sympathy, and if you staying, recommend you replace it now
with a Square-D, or other brand.
As far as the wire is concerned, depending on where you live, you
might have to get something with four (4) conductors, even though
you only need three. Some counties and cities in Ma require seperate
grounds and neutrals. 10 Gauge is adequate for 30-amps, is easy to
work with, and is relatively inexpensive. Number #6 is fine if
your restoring Budliners, Peterbuilts or the hull of the QE-2.
If your in Ma. I recommend you use "Buchanan clips" for the grounds.
They look like little .22 shells with holes in both ends. You can
crimp them with pliers. The use of wire nuts on grounds is a no-no
in Plymouth County.
In closing, as far as taking out a permit, most towns and cities
require you to have a journeyman electricians license
hope this helps some....
Ron
|
630.170 | "they're spooky and they're creepy" | VAXWRK::OXENBERG | illigitimus non conderendum es | Tue Jul 13 1993 10:23 | 20 |
|
"A funny thing happened on my way" up the driveway! My garage
door automagically opened for me! My hands were nowhere near the
remote, noone was in the garage pressing the buttons, nor was
anyone using another remote!
The second thing I noticed once I eneterd the garage was that I
couldn't close the door with either the remote or the pushbutton on
the wall.
I finally pulled the power cord from the socket, re-inserted it
and tried the button again and this time it worked.
SO, what's wrong? Time to buy a new one?
Thanks
-Phil
|
630.171 | | STRAY::BUSKY | | Tue Jul 13 1993 11:52 | 17 |
| > "A funny thing happened on my way" up the driveway! My garage
> door automagically opened for me! My hands were nowhere near the
>
> The second thing I noticed once I eneterd the garage was that I
> couldn't close the door with either the remote or the pushbutton on
> the wall.
A guess... the button in your car was somehow closed (heat related -
hot car warped the remote's platic case?) and when you approached the
garage and got within range the door opened. Because the remote button
was still closed, the wall switch wouldn't work. Pulling the plug and/or
reapeated pushing of the remote button finally released it and cleared
the problem.
Either that or it's possesed!
Charly
|
630.172 | | VAXWRK::OXENBERG | illigitimus non conderendum es | Tue Jul 13 1993 12:57 | 12 |
|
>A guess... the button in your car was somehow closed (heat related -
>hot car warped the remote's platic case?) and when you approached the
>garage and got within range the door opened. Because the remote button
>was still closed, the wall switch wouldn't work. Pulling the plug and/or
>reapeated pushing of the remote button finally released it and cleared
>the problem.
The car was cooled by a/c, I'd been driving for about an hour.
Maybe it's time to replace the remote?
|
630.173 | | TROPPO::QUODLING | | Wed Jul 14 1993 06:43 | 5 |
| Someone in your neighbourhood, has the same brand of remote? recently
installed?
q
|
630.174 | | DTRACY::ANDERSON | There's no such place as far away | Wed Jul 14 1993 10:29 | 5 |
| did you replace the batteries in the remote recently? We had a problem
when we put the cover back on too tight - the connection was always
being made.
marianne
|
630.175 | | POCUS::CUFF | | Wed Jul 14 1993 12:21 | 18 |
| As suggested by a previous noter, perhaps a neighbor has the same
model whose remote activates your opener.
Some of these units have dip-switches to set "password" on opener and
remote, must match. You can reset them yourself (my Sears brand
had this). If by dumb luck, a neighbor happens to have the same
setting, this could happen. We know someone who had this sort of
thing happen to them, with remote-control ceiling fans. They installed
one upstairs, one down, by dumb luck the two fans were set to the
same code out of the box, although it took them quite some time to
figure it out. He was downstairs, turned the fan on; she was already
upstairs, saw that fan go on, turned it off, which also turned his fan
off, he turned his on, which also turned hers on, etc..........
brought fans back to the store, rep shows them how to reset dipswitch
they felt like complete jerks for complaining that the fans were
garbage.
|
630.176 | not a bug, a feature... | SALEM::LAYTON | | Wed Jul 14 1993 14:37 | 6 |
| I set the dip switches the same for my house and my mother in law's
house. Eliminates carrying extra keys.
If you saw the movie "Spaceballs" where the "secret" combination to
blow up the universe (or something) was "1-2-3-4" you could relate
to this...
|
630.177 | | VAXWRK::OXENBERG | illigitimus non conderendum es | Sat Jul 24 1993 12:18 | 17 |
|
Since it only happend two or three times within about a 2 day
period, perhaps it's just dirty contacts that were sticking.
I hadn't changed batteries or opened them up recently.
I have no idea what my neighbors have done or do. (It's possible
it's "their" fault.)
I think this is a single frequency model, I believe I checked when
we bought the house because I would've wanted to change the switch
settings.
Thanks for your suggestions. We haven't experienced any problems
lately (that we're aware of).
-Phil
|
630.59 | Electric Power to Shed | BUSY::CLEMENT | Smells like Nirvana | Thu May 12 1994 09:45 | 16 |
| I would like to bring electricity to my shed within the next
couple of weeks. I will be running a line underground from the
house to the shed. I will probably install 2 lights and 2 outlets
(one outlet inside and one outside). I will run tools and a battery
charger at this point.
I was wondering if I need to use a pvc conduit to contain the wire.
I will use 12 guage. I know that my pole light at the front of
the house is wired with just a wire in the ground with no conduit
to protect it. It has served without problem for 30 years.
I was also wondering what the general code requirements were.
I plan to hook into a GFCI (sp?) line. How deep it needs to
be buried and if it does need to be in a pvc type conduit?
Thanks, Mark
|
630.60 | some info | MIYATA::LEMIEUX | | Thu May 12 1994 10:07 | 22 |
| Mark,
Its OK to use cable but it must be rated for direct burial. I suggest
12-2 UF for your application. I would run a length of PVC conduit from the
bottom of the trench to where you go through the rim band of the house and the
wall of the shed. Use a fitting called and "LB" to make the turn from the
conduit into the house. I'd draw picture except that I'm pressed for time and
terrible at ASCII drawings :')
Use a 20 amp breaker in the panel and use a GFCI receptacle in the shed. This
isn't required but I would do it. The lights don't have to be gfci protected.
As for the trench depth...I'll look it up. It's been a while since I've run
UF in the gound. I want to say it needs to be 18 inches but it might be 14
inches. Any one have a 93 or 90 code book in the office? Anyway may sure the
trench is clean of rocks and backfill the trench with clean sand around the wire
if the soil is rocky. If it's all sand don't worry about it as long as there
aren't any rocks.
Later
Paul
|
630.61 | initial cost is more but may save in long run... | HNDYMN::MCCARTHY | Languages RTLs | Thu May 12 1994 11:00 | 8 |
| I would suggest running PVC conduit all the way. If something comes along and
rips it up, you can patch the problem and re-snake new 12G THHN wire. If you
run a single cable, and it gets damaged you have to re-dig the entire trench to
replace it.
I belive the depth is 18", but as Paul L. says "its been a while".
bjm
|
630.62 | | MIYATA::LEMIEUX | | Thu May 12 1994 11:29 | 7 |
| Brian,
They have a new product out (sort of new) for splicing UF cables.
Works really good and leaves you with a water tight splice. No longer
have to dig up the entire thing.
BTW, I second the motion for the conduit run if you can spend the extra bucks.
It's worth it if you ever add anything in the shed. PVC is cheap too.
|
630.63 | thanks! | BUSY::CLEMENT | Smells like Nirvana | Thu May 12 1994 17:29 | 18 |
| After discussions and reading everyones input I am considering this;
Run a pvc conduit the entire length from the house to the shed. Run a
12-2 guage standard house wire plus a phone wire to the shed. Use the
"LB"s for leaving and entering the shed.
Before leaving the house I will pass the line thru a GFCI outlet.
Paul, thanks for the nice drawing.
Is it correct practice to glue the ends of the pvc pipes or just
press them togther. I ask this in case I would need to dig up the
line someday for a possible repair or additional feed of some sort.
If glued they will not come undone. If not glued would they allows
moisture to enter?
Thanks, Mark
|
630.64 | can't run phone/AC in same pipe | HNDYMN::MCCARTHY | Languages RTLs | Thu May 12 1994 21:10 | 30 |
| >> Run a pvc conduit the entire length from the house to the shed. Run a
>> 12-2 guage standard house wire plus a phone wire to the shed. Use the
>> "LB"s for leaving and entering the shed.
Well it sounds nice except its against code to run low-voltage (phone) and high
voltage in the same "chase" (I think that's the correct term). Anyway, along
with being against code you will pick up a really nice hum on the phone because
of it being so close to the 120V. The rule may actually read something about
every wire in the same chase must be able to handle the max voltage present in
the chase (ie 24G wire won't handle 120V)
Either run two PVC lines (which may still cause you to pick up the hum) or do
what I did, get a portable phone :-)
>> Is it correct practice to glue the ends of the pvc pipes or just
>> press them togther. I ask this in case I would need to dig up the
>> line someday for a possible repair or additional feed of some sort.
>> If glued they will not come undone. If not glued would they allows
>> moisture to enter?
Yes - always glue.
1) Clean both ends
2) Apply glue to both ends
3) Put ends together and TWIST
Worry about fixing problems later !
Brian J.
|
630.65 | | MIYATA::LEMIEUX | | Fri May 13 1994 08:45 | 7 |
| re .4
The picture: Your welcome!
Telephone cable....see if you can find some direct burial phone
cable...do you know anybody that works for Ma bell? Or put it in its
own conduit. Brian is right on, you shouldn't put it the same conduit.
|
630.66 | NEC says 12" is enough | BOBSBX::CHIQUOINE | Who audits the IRS? | Fri May 13 1994 08:47 | 11 |
| Table 300-5 of the 1990 NEC indicates that you only need to bury
to 12" for "residential branch circuits rated 120 volts or less with
GFCI protection and maximum overcurrent protection of 20 amperes."
Sounds to me like it's an easy job for a single circuit. I'm not
clear, though on what GFCI protected means -- should it be on the
house side or in the shed? Wouldn't you want it in the house,
in case you hit the buried cable with a shovel, or something?
Ken
|
630.67 | | MIYATA::LEMIEUX | | Mon May 16 1994 08:42 | 7 |
|
GFCI protection: On the house side. IE the wire in the ground needs to be
protected.
Thanks for looking that that up! Forgot all about it.
Paul
|
630.68 | Taxes. | MPGS::RUSSO | | Tue May 17 1994 08:23 | 5 |
| In some towns if you run electricity to a shed they consider it
to be living space. Taxes increase at a different rate than just
shed. Check it out.
Joe
|
630.69 | USE PVC & GLUE | ISLNDS::CARLBERG | | Thu May 19 1994 13:53 | 6 |
| I ran power and phone line to my shed. I would definetly use pvc pipe
and definetly glue it. I ran the direct burial phone wire right along
the pipe and have no problems with humming. You might consider running
an extra set of wires while your doing it in case you need to add
another cicuit in the future. It's a lot easier to snake the wire all
at the same time.
|
630.48 | How to ground an outbuilding? | UNXA::LEGA | System V Environment,462-6025 | Wed Jul 06 1994 14:02 | 31 |
|
I've got a wiring problem. I have a barn powered by
some overhead triplex wire. (steel neutral wrapped by
2 hots (110 each side). In the barn, theres a 2x20 amp
subpanel. Inside the panel, the bare copper ground and
the white neutrals are tied together with the triplex
neutral on a buss bar, the hots are on each breaker.
The box is not grounded to anything at the barn.
I was getting a mild buzz/shock when touching a grounded
box at the barn. I checked how another barn was wired,
and they had a ground stake attached to the neutral
buss. I mimicked this at the ungrounded barn, and the
ground stake was now providing a slight shock.
Whats strange is that an LED outlet tester indicates
everthing is correct, and the GFI at the barn hasn't
tripped, and the panel has 110VAC. My meter shows
110VAC between the shocking box case and hot, and
0VAC from neutral to the box.
Any suggestions on how to proceed? I was going to
somehow check the neutral connections leading back
to the house, since the wire was replaced and reconnected
within the last year. But Im baffled on the shock situation.
What is the common method for wiring the barn within
the box? Are the grounds and neutrals supposed to be
tied on the same bus along with the ground stake?
|
630.49 | 110/220 subpanels need 4 wires.. | TEKVAX::KOPEC | I know what happens; I read the book. | Wed Jul 13 1994 09:17 | 14 |
| That doesn't sound legal. Two possible cases:
1.) the box in the barn is a "service entrance". This means that
neutral and ground are connected together at that point, and the groupn
rod is also connected at that point. I doubt this is the case, unless
the barn is separately metered.
2.) the box in the barn is a "subpanel". In this case, you need to run
a separate ground and neutral from the main panel. If you don't, any
voltage drop on the neutral shows up on ground, and that's *not good*.
I think in this case, you have two "ground bars" in the subpanel, one
for ground (bonded to the panel) and one for neutral.
...tom
|
630.50 | time to check the code book.... | HNDYMN::MCCARTHY | Languages RTLs | Wed Jul 13 1994 10:09 | 13 |
| I'll second what .15 says. does not sound legal except if it is a seperately
metered feed. The way the code reads is something about per service feed,
having only one common point between neutral and ground, and there is also a
rule about having only one point of grounding (either a ground stake or to
public water supply). Note that you always need to ground the internal water
supply of a house but in some cases this man not be the ground point for the
meter.
If it is a subpanel, you need to seperate the neutral and ground (neutral
should never touch the box) - and you should not have a grounding rod
out there.
bjm
|
630.70 | lighting for shed behind house | MICROW::SEVIGNY | I know what I'm doing... in theory. | Fri Jul 15 1994 18:00 | 14 |
|
Is there some practical maximum distance for running electrical power
to a shed? I was planning on extending an existing circuit in my
basement underground to a shed which is about 150' behind the house.
Is this too far?
Also, I was planning on having power only for lighting (not for power
equipment) and would like to use 14-2 UF for cost considerations.
Sound practical?
Thanks,
Marc
|
630.71 | | MAY30::CULLISON | | Fri Jul 15 1994 18:23 | 12 |
| The further you go you will lose a little in wiring due to losses, the
wiring does have resistance. Our old house had a shed that was about
200' from corner of house. I would think that it should be a
seperate circuit for shed. If i was going to the trouble to run
it then i would use heavier wire, and add another wire so you
could have two circuits in future. Anytime you have a shed, sooner
or later you will want more than just lights.
There is should be a wiring table that specifies when 14-2
should be bumped up to 12-2 at a certain distance.
|
630.72 | go heavy.. | HNDYMN::MCCARTHY | Languages RTLs | Sun Jul 17 1994 10:14 | 10 |
| 150' - run at least 12g wire (IMO).
As I mentioned in another topic somewhere in here, I'd think about runing PVC
(1') out there. This way, if you need to snake more lines, or replace that
line, it is much easier than re-digging the hole.
When you end up digging the trench remember that there are different depth
requirements for GFI protected and non-GFI protected lines.
bjm
|
630.73 | Run 12 gauge... | STRATA::CASSIDY | | Mon Jul 18 1994 01:22 | 4 |
| I believe 12 gauge is required for runs over 100'.
Tim
|
630.74 | Might as well use an extension cord | CSLALL::NASEAM::READIO | A Smith & Wesson beats four aces, Tow trucks beat Chapman Locks | Mon Jul 18 1994 17:49 | 5 |
| Twelve ga????????? What're you running, a 40 watt light bulb?
I have 3-3 or 4-3 (Don't recall as it's been in there 10+ years now)
running 165 feet to the garage.
|
630.75 | It's for a shed, not a garage... | STRATA::CASSIDY | | Tue Jul 19 1994 01:16 | 10 |
| >Twelve ga????????? What're you running, a 40 watt light bulb?
>I have 3-3 or 4-3 (Don't recall as it's been in there 10+ years now)
>running 165 feet to the garage.
What are you running, dueling arc welders? With 12 gauge, you
could run a 1500 watt heater AND a 40 watt light bulb! (with a few
amps to spare)
Tim
|
630.76 | like watering your lawn through a straw.. | TEKVAX::KOPEC | I know what happens; I read the book. | Tue Jul 19 1994 08:33 | 6 |
| Skip's point is not current-carrying capacity, but rather voltage
drop. I'd bet for that run you'll need to go at least to 10-gauge.
I think the NEC has charts for this in it..
...tom
|
630.77 | | WRKSYS::MORONEY | rearranger of rotating rust | Tue Jul 19 1994 17:05 | 12 |
| With a 150' run, definitely go at least one gauge better than the current
rating of the circuit. With 150' 12 gauge and the 1500 watt heater your 40
watt bulb will be a little dim.
Also, some day you'll probably want to run power tools, and you may curse
yourself for 150' feet of 14 gauge which won't be good for much beyond a few
40 watt bulbs.
If nothing else a high current 240V subcircuit to a subpanel will increase the
value of the property to potential future buyers.
-Mike
|
630.161 | 100-amp service to a garage | NETCAD::GAUDET | | Wed Feb 22 1995 08:50 | 45 |
| The story:
My brother-in-law built a detached garage/workshop in his backyard.
Now he wants to run power out there. Yes I know, he should have
thought of it sooner. I told him that when he was building it, and he
did build in a section of 1-1/4" conduit into the foundation that
sticks out both inside the building and outside under the ground.
There is sufficient conduit sticking out to attach extensions to bring
the wire to the house via underground conduit.
The details:
The garage is about 75' from the house, and by my estimates about 145'
of wire is needed to get from the house service panel to the garage
service panel that will be installed. The large amount of wire is
needed because the main panel in the house is literally in the opposite
corner from where the wire will enter the house from the garage
(believe me, the landscape does not allow an entry point closer to the
panel).
The questions:
He wants 240V/100-amp service out there to operate a compressor,
welder, power tools and of course lights. My question is how to hook
into the main panel to do this. Should a separate breaker box with a
100-amp breaker be installed in the house off the main panel, then run
the service to the garage from that? Or can this be directly run off
the main panel into a service panel in the garage? Is this something I
can do myself without a) becoming a Roman candle and b) taking out the
rest of the street? Or is this a good candidate for calling in a
licensed electrician to play with the main panel connection. I'm
leaning toward the latter (hey, it's not *MY* money :-)) since I've
never connected such a large service from a main panel. I have,
however, done my share of electrical work including normal in-home
wiring and installing/connecting main panel circuit breakers for
outlets, appliances, etc. including 240V and 120V long-distance runs
to an outdoor pump.
FYI, I have already been to Home Depot, etc. to get prices on wire.
The code book says I need #2 wire for this, and have seen 2-2-2-4 wire
that looks like it will do the trick.
Thanks in advance for your guidance.
...Roger...
|
630.162 | | MOLAR::DELBALSO | I (spade) my (dogface) | Thu Feb 23 1995 11:23 | 4 |
| I'd be curious as to whether or not you might be able to get the power
company to simply install another meter on this building. It could save
a whole lot of money and trouble if they'd be willing.
|
630.163 | | EVMS::MORONEY | Verbing weirds languages | Thu Feb 23 1995 11:59 | 24 |
| Hey Roger,
There really isn't much different between this and putting in a 15A light
circuit. You should probably put in a 100A breaker in the main panel and
a subpanel in the garage, as long as the main panel has the capacity and
the physical room for the cable. With the main breaker off the only thing
you have to worry about touching is where the main feed attaches.
Things to look out for:
1) Wrestling with such heavy cable.
2) Such cable is likely to be aluminum, use the antioxidant designed for
AL wiring on all connections and be sure the breaker can be used with AL
wiring (almost certain it can)
3) You need 4 wires for such a feed, 2 hot, neutral ground as the N and G
must be separated in the subpanel.
4) Is the conduit large enough for the wiring?
5) Use the correct cable rated for underground use in a conduit.
6) Does the existing main panel have any limitation to the max. size of a
circuit or physical room in the box. Is the main breaker big enough for
the added load?
7) Is #2 large enough considering both the current and length of run?
-Mike
|
630.164 | I'll have more details after this weekend | NETCAD::GAUDET | | Thu Feb 23 1995 12:27 | 25 |
| Hey Mike,
According to the book, #2 cable is big enough to run something like 143
feet and carry 95A. The book says these numbers take into account a 2%
loss over the given distance from the main panel. Now that I think
about it, they might have been talking about copper and not AL. I'll
definitely check the book again tonight.
As for the main panel, it's got 200A coming from the street. The issue
may be whether or not there's room for a 100A breaker. I looked at
this setup about 3 months ago and frankly just don't remember how much
space is left in the main panel. I'll be at my brother-in-law's this
weekend so I'll make a more detailed survey of the situation.
And no, I don't relish the thought of playing around with cable of that
size (or bigger). I hate screwing around with #12, never mind #2!
Maybe I'll get my brother-in-law to do all the stripping and snaking of
the cable. I'll just direct traffic! :-)
BTW, I initially posed the idea of having the power company run a
separate feed & meter to the garage, but my b-in-law balked at it.
Thanks for the responses so far.
...Roger...
|
630.165 | always uses CA as base | HNDYMN::MCCARTHY | Disabled Service Button | Thu Feb 23 1995 12:54 | 10 |
| The #2 the book specifies is for CA, increase the size if you are dealing with
AL. Personally I'd stick with the CA. They guy I used to work for never used
AL for anything except once in a while he'd use the SE AL cable. He said he
had fixed too many problems relating to AL connections.
I don't think you want to sleve the #2 RX into any pipe, I would suggest using
4 #2 THHN lines inside of the pipe and switching to the #2 RX cable inside for
the run from the entrance into the house to the panel.
bjm
|
630.166 | mondo wire.. | TEKVAX::KOPEC | we're gonna need another Timmy! | Mon Feb 27 1995 12:28 | 20 |
| Geez, Rog.. I leave ya alone for a few days and..
Anyway, my code mini-book says #2 Cu is OK drop-wise for 145 feet at
100A/240V, but that Type TW wire doesn't have enough ampacity in a
conduit. RH, RHW, and THW are OK. My copy of the actual NEC is in a box
somewhere, so I can't say whether you even have a prayer of getting
those wires into the conduit.. I think for Al conductors you'll have to
go to 2/0, but again I don't have my NEC handy. Other than the size, I
wouldn't expect any problems with Al wire of that size IF installed
properly (ox-gard, etc..); I suspect it will be a LOT cheaper than
copper.
Don't forget that you'll need two "ground" busbars in the subpanel; one
isolated from the panel for the white wires (neutrals), and one bonded
to the panel for the bare wire (grounds).
No, I'm not planning any trips to Rhode Island in the near future, so
don't get your hopes up 8-)
...tom
|
630.167 | Progress so far ... | NETCAD::GAUDET | | Tue Feb 28 1995 13:25 | 42 |
| Well Tom, you know the story: Hey, Roger is a electrical engineer, so
he *must* know how to install electricity! :-) But anyway, running
small circuits is one thing, installing a sub-panel with 100A service
is another (though similar).
At any rate, we did a semi-intelligent thing this weekend and invited
an real live electrician to give us his "opinion" on how to do the job.
He recommended that we install a 100A breaker in the main panel (yes,
there's room) and run #2 SER from there to the point where the cable
will exit the house. Inside a junction box, connect up individual
strands of #2 CU THHN and #4 CU THHN to be run in the conduit to the
garage panel. And yes, he mentioned having separate neutral and ground
bars in the garage panel. He said that for residential applications he
prefers running the ground from the main panel all the way to the
remote building's panel instead of driving a ground rod and connecting
the grounds locally. One man's opinion.
OK, materials. Here's what I found: Home Depot carries #2 SER cable
(2-2-2-4 aluminum) for $1.40/ft. They also have #2 CU THHN for
$0.56/ft and #4 CU THHN for $0.35/ft.
It looks like I have several alternatives:
1) Run #2 SER the whole way (in the house and through the conduit).
That's $210 for 150' of wire. No ground rod.
2) Run #2 SER in the house, splice individual #2 & #4 at the exit of
the house, then run #2/#4 CU in the conduit (as recommended by the
electrician). No ground rod. Splitting the distance in half (that's
pretty accurate in this case), it looks like about $260 for the wire.
Pulling three strands of #2 CU and one strand of #4 CU through a 1-1/4"
pipe is not something I'm looking forward to, but if we decide to go
this route will see how it goes (may have to jump up to 2" pipe).
3) Don't run the ground from the main panel. Drive an 8' ground rod
near the garage and connect up all the grounds locally. Run three #2
conductors from the house panel to the garage panel using some
as-yet-undetermined combination of cable types.
I'm leaning toward the option #2.
...Roger...
|
630.168 | same thing, just bigger.. 8-) | TEKVAX::KOPEC | we're gonna need another Timmy! | Wed Mar 01 1995 08:40 | 13 |
| Hm. Might want to find another electircian.
First off, whether you have a ground rod at the sub-panel or not, all
the "grouding electrodes" have to be connected together. So, whether
you have one there or not, you still need to run the wire between them.
(this could be buried bare copper wire, however..)
Next, I don't think #2 SER is big enough for 100A; again, I haven't
been able to find my NEC, but I think #2 Cu is just big enough for 100A
ampacity-wise.. (but I don't recall the ratings that are specifically
for se/ser cables..)
...tom
|
630.169 | just confirming the grounding issue | HNDYMN::MCCARTHY | Disabled Service Button | Wed Mar 01 1995 09:32 | 14 |
| >> Hm. Might want to find another electircian.
>>
>> First off, whether you have a ground rod at the sub-panel or not, all
>> the "grouding electrodes" have to be connected together. So, whether
I thought this was the case also. I don't think it matters if the sub-panel is
1 foot away or 200 feet away in a seperate building, there should only be ONE
grounding point per service entrance.
The size of the ground wire does not need to be equal to the wires needed for
the sub-panel. I think for a 100A "main panel" the ground wire needs to be #4
CU.
bjm
|
630.78 | Lots of Power needed | BIRDIE::ORLOWSKI | | Tue Aug 15 1995 09:20 | 23 |
|
I would like to have enough power for the following items:
(2) Spot Lights on a 3 way switch (switch between house and shed)
(1) interior light on a 3 way switch (switch between house and shed)
(1) additional interior light on single switch
(3) Recepticles capable of handling bench grinder
I also would like to have running water (Cold only). This would have to
be blown out before winter sets in. Is copper ok for this application?
Phone line is optional.
I prefer to use PVC all the way because of all the rocks and frost
heaves.
I have about 100 foot run between the cellar and the shed.
How many wires and what size and type wire would you use??
~Steve
|
630.79 | | DSSDEV::RICE | | Tue Aug 15 1995 15:05 | 38 |
| Electrical:
The simple way.
- 20A GFI circuit with GFI located in electrical panel.
- run three 12-2 UF cables between shed and house. (switch box to switch box)
- feed power from panel to switch box in house.
- Hot (black) goes to each of the 3-way switches common lug in house.
- Neutral (white) and hot (black) go out to shed via one of the three UF cables.
- The other two UF cables are the switch legs for each 3-way.
- Hot (black) of shed 3-way commons go to lights, neutral (white) from the power
feed cable.
- Feed outlets in shed off power cable. (Shed switch box to outlets)
- Feed the other switch and light.
There are a number of variations you could make.
- You really want the 20A circuit for power out in the shed. You need the GFI
somewhere before it leaves the house. A panel GFI breaker is usually twice
the receptacle sort. You might be able to save some money there and get
another outlet someplace you'd like by using the receptacle GFI.
- Using the UF romex cable is more than enough. You don't need to run any pipe.
If it is exposed as it comes out of the ground and you think it needs
protection you could slip a section of pipe over it there. Also, this is
supposed to be buried below the frost line.
- If you're really concerned about power out there then you can do a balancing
act. Use a 12-3 UF cable and 2-pole 20A GFI in place of the 12-2 UF power
feed to the shed. This will put 240V out there but you're just going to have
120V outlets. You split the load, say 2 outlet on each pole for 4 total.
You'll be able to use up to 40A @120V this way.
Plumbing:
I'd use the flexible PVC piping they use for in-ground sprinklers. Its pretty
inexpensive and easy to use.
-Tim
|
630.80 | 3-way switch | BIRDIE::ORLOWSKI | | Thu Sep 07 1995 15:03 | 14 |
|
I was thinking of running a 10-3 as a feed from a Single Pole, DOuble
Throw GFI (that gives me 2 110v legs) to a panel in the shed,,,,and for
the 3-way switch,,a 12-3 for the spot lights. I decided to scrap the
interior 3-way from the house to the shed.
The 3-way goes black from switch 1,,black from switch 2,,black feed
tied together. White from switch 1,,white from switch 2 white from feed
all tied to spotlight. Now the red has me confused. Does it go red from
switch 1,,red from switch 2 tied to the black on the light?? I've done
several of these before but on paper it doesn't look right and I want
to be sure before I bury the wire.
-Steve
|
630.81 | my lesson | HNDYMN::MCCARTHY | A Quinn Martin Production | Thu Sep 07 1995 19:16 | 52 |
| 12-3 for spot lights? Is this a long run?
Your description of the 3-way is confusing - esp when you have white wires
connecting to it. The standard method I was taught was:
First, each 3-way switch has two same-color terminals (ie the travelers) and
one (usually black) colored terminal called the point.
Assuming there is a three conductor wire between the two switches:
red/black conductors in a 14/3 setup go to the traveler poles of the switch
Now, depending on where the feed and swtich leg is coming in:
Feed at S1 - Switch leg at S2 (or reverse that!)
At S1:
Black of feed on point of s1, white of feed to white 14/3
At S2:
white of 14/3 to white of switch leg, black of switch leg to
point of s2.
Feed at S1, Switch leg at S1, 14/3 between s1/s2:
At s1:
red/black of 14/3 on traveler terminals
Black of feed to WHITE of 14/3 - by code - the only time you can
have a white wire be a feed is when it is used in a switched
configuration)
Black of switch leg to point of s1
White of feed to white of switch leg
At s2:
red/black of 14/3 on traveler terminals
white of 14/3 on point
Feed at light with switch leg coming into s1, 14/3 between s1/s2
Assume the WHITE of the switch leg is wired to the HOT and the
BLACK of the switch leg is wired to the light
At s1:
red/black of 14/3 on traveler terminals
white of switch leg to white of 14/3
black of switch leg to point
At s2:
red/black of 14/3 on traveler terminals
white of 14/3 to point.
>> to be sure before I bury the wire.
Bury the wire? Hmm - I end to use PVC for all underground work now. I like
the idea of being able to replace the wires by pulling a new set - not that
I've ever had to :-)
Brian J.
|
630.82 | Another version (took me long time to remember this) | NETRIX::michaud | Jeff Michaud, That Group | Thu Sep 07 1995 19:29 | 14 |
| > First, each 3-way switch has two same-color terminals (ie the travelers) and
> one (usually black) colored terminal called the point.
What you call the point I believe I usually see labeled "common".
Way I usually remember it is the "common" goes to either the black
power source or to the black lead of the applicance. And as Brian
said, the red & black of the 3 conductor wire goes to the other
two terminals on the switches. The white and ground wires simply
feed through (ie. on one end the 3 conductor white wire connects to
the power source's white wire, and on the other end the 3 conductor
white wire connects to the applicances white wire [or in other words
all white wires on both sides should be connected, as should the grounds
with maybe a pig-tail to the ground terminal on grounded switches).
|
630.83 | Memories... | BIRDIE::ORLOWSKI | | Fri Sep 08 1995 08:46 | 12 |
| Thank you! I was getting ready to pull a few covers off in my house to
see how I did them way back when. It makes sense now.
Refer to my original note .19
I would think 12-3 should be able to carry enough line voltage to power
3 spot lights 120 feet (from house to shed)?
Now to rent the Kabota and have some digging fun...
-Thanks again
-Steve
|
630.84 | I think its overkill | HNDYMN::MCCARTHY | A Quinn Martin Production | Fri Sep 08 1995 10:46 | 8 |
| I ran 3 14g THHN wires out. Distance is about 75'. If you have 150w bulbs
each one draws about 1A - so 3+A on a 14g wire is fine. 12g is almost always
overkill when it comes to lighting.
See note 1694.18 for my very old line-drawing of how a 3-way works. It runs
way too fast - maybe I'll enter a new version with more time delays...
Brian
|
630.85 | | NETRIX::michaud | Jeff Michaud, That Group | Fri Sep 08 1995 11:22 | 4 |
| > See note 1694.18 for my very old line-drawing of how a 3-way works. It runs
> way too fast - maybe I'll enter a new version with more time delays...
You need to update it for present times, ie. convert it to HTML! :-)
|
630.86 | maybe some day = BUT I WON'T USE TABLES ! | HNDYMN::MCCARTHY | A Quinn Martin Production | Fri Sep 08 1995 13:26 | 8 |
| >> You need to update it for present times, ie. convert it to HTML! :-)
I was thinking the same thing :-) - actually just a few gif files would do the
trick. It was 1987 - and "2 minutes at 1200 baud" - I tried to get to slow
down between the drawings - the file ended up being over 1000 lines long - and
it was still too quick.
bjm
|
630.87 | | DSSDEV::RICE | | Sun Sep 10 1995 14:58 | 25 |
| RE: .21
You sure you want to do this yourself? Just from gathering impressions as I've
read these notes I'd say you're a ways off from knowing what you want to do, not
to mention how you're going to do it.
Digging the trench is a good start and probably the most work (sweat) intensive
part of the job. After that, noone would ever do it the way you've described.
Here are some points.
1. The lighting and receptacles, same circuit or not?
2. Use the appropriate wire and guage.
3. There is no need for a subpanel in the shed.
4. You only want to do this once.
5. Get an electrical permit and use the inspector to your advantage. He/She can
be very helpful if you just ask/show them ahead of time what you'd like to
do. Don't be afraid of the inspector. When its done you'll have done the
job correctly.
Most of what you've described is just a big waste of money.
Really, I'm just trying to help.
Tim - started life as an electrian 20 years ago...
|
630.88 | The ground work is complete | BIRDIE::ORLOWSKI | | Tue Sep 19 1995 11:17 | 18 |
| re.28
The outside part of the job is complete..I trenched the hole with the
Kabota,,,layed the conduit with 10-3 and 12-3,,,,layed the water pipe,,
and covered the hole,,all in 1 day. I have the service panel up in the
shed,,,,,,life is good.
Oh and BTW,,,,,my father is a liscensed electrician (retired and not
well) and I have worked for him for many years. The purpose of this
notes conference is to discuss projects and get other views and
opinions which may or may not help.
I already had my idea what I wanted to do but running it through here
should bring up anything overlooked,,,,,,,,,,,,and it did and I thank
all for their ideas and advice.
-Thank you
-Steve
|