85.1 | | GALLO::PALMIERI | | Wed Jan 22 1986 10:34 | 11 |
| You didn't say whether the oil is ignited during the rumbling so I don't
know if what I am going to say applies. I observed the same rumbling with
my FHA furnace. The rumbling ocurred at startup before the oil ignited.
The problem was a faulty high voltage transformer whose output is used
to create a spark to light the oil. The rumbling I had lasted several
seconds until the transformer could get its act together and create a
spark. I never did determine why that scenario actually makes the furnace
rumble. If you examine the transformer in the dark when the furnace is
running you may see some arcing outside the combustion chamber. I
think that this indicates a faulty transformer.
|
85.2 | | VENNEX::ARNOLD | | Thu Jan 23 1986 11:48 | 1 |
| Thanks for the response.I will try what you suggested.
|
85.3 | | ISHTAR::MBOX | | Mon Jan 27 1986 14:10 | 3 |
| Last night I got the rumbling again.It happened after the oil is lit.
I think maybe the oil feed needs adjusting.It probably is feeding too
much.
|
85.4 | | GALLO::PALMIERI | | Mon Jan 27 1986 17:23 | 15 |
| Do you know when the nozzle was last replaced? I have a service contract
and they come once a year to clean/service the furnace. I know that nozzle
has been replaced several times over the last eleven years. I don't know
why it is replaced periodically; possibly the oil is somewhat abrasive
and wears the nozzle. There is a rating plate on the furnace that states
the maximum nozzle size to use and I think it would be bad if it wore to
too large a size. The only other thought I have relates to my delayed
ignition. Possibly the igniting of some oil the fell to the bottom of the
combustion chamber before ignition causes the rumbling until it is burnt.
Does your furnace ignite within a 1/2 second or so of the pump starting?
Of course, if the rumbling is intermittent, you may not be at the furnace
when the delayed ignition happens.
Marty
|
85.5 | | SNICKR::ARDINI | | Tue Jan 28 1986 09:02 | 8 |
| I had a delayed ignition problem where the chamber was saturated
with oil before it ignited. This happened at 3 am and the house filled with
thick oil smoke. We woke, got everyone up and out of the house. The fire
department came down. It ended up that we got enough insurance money to
clean all our oil soaked walls (we cleaned it up ourselves)that we bought
a new burner. A blessing in disguise. Delayed ignition is usually caused
by the igniting unit.
Jorge'
|
85.6 | | SNICKR::ARDINI | | Tue Jan 28 1986 09:14 | 13 |
| I have a different concern with my FHA system, humidity. My house
is super dry because of the FHA system. I have a humidifier buildt into
the system but it rusted out. It is a long tub with absorbing fins in it
that remain wet as the hot air flows by and thus humidifies the air. It
is maintained thru a float valve that keeps the water level constant. The
problem is the tub and float chamber rusted out and leaks. I tried fiberglass
and bonding but it never lasted. I would like some info from anyone about
the availability of these units, price, and possible repair (lasting repair).
In the meantime I got a console humidifier that takes care of the kids while
sleeping. One night my 2 yr old woke up with a bloody nose it was so dry.
Dry Martini's Only Please
Jorge'
|
85.7 | | ISHTAR::MBOX | | Tue Jan 28 1986 17:46 | 8 |
| I dont know when parts(as nozzle) were last changed on my furnace,
but I am about due for my yearly checkup.I'm thinking of going
to a different oil company because they some times give you intro-
ductory rates which may include free cleaning.Also my current oil
company wants $95 just for a basic check-up.That seems pretty high.
BTW,I am the same person who originated this note-I am under a
different username right now,
Scott
|
85.52 | FHA ducting and basement ceiling insuation | THORBY::MARRA | This space intentionally left blank ... | Mon Mar 10 1986 09:53 | 27 |
| This summer I plan on finishing off the downstairs on my split. I plan
on having a coal/wood stove, and no door going upstairs, but rather,
have the stairs open so that the heat can rise. In addition I'm
thinking of putting a cealing fan in the entrance, above the stairs.
Also, for 'air conditioning', I was thinking of a "whole house" attic
fan in the hall cealing to suck the air out of the house (mainly thru
basement).
My questions are these:
Since the ductwork for the FHA heat is not installed for downstairs
(which is made up of the foil wrapped fibre board stuff), what
type of ducting / vents / fans / recirculation thingys should I
look into. What is available?
Can fans be installed that can be turned on anytime to circulate
air around the house?
Should I take the insulation out of the cealing downstairs so that the
heat will rise thru the floors?
.dave.
(The house is 2x6 plywood construction)
|
85.53 | moving the main gas line? | THORBY::MARRA | This space intentionally left blank ... | Tue Mar 11 1986 14:35 | 14 |
|
In addition to all this, I would like to move the gas pipe that
the builders installed. The pipe is 2" and runs across the cealing
of half of the room. It hangs about 3" below the 2x8's, and would
be a pain to have to lower the cealing on that side (of the main
beam). I'd like to move it next to the main beam in the center
of the house. Who would I have to contact to have this done, or
can I do it myself and save the money. (is that legal?) - I could
say that the house came that way!
If I can do it, how? - turn off the gas and move it? - any special
sealers required???
.dave.
|
85.54 | | PEANO::WHALEN | TPU hacks while you wait | Tue Mar 11 1986 16:40 | 14 |
| One of this year's episodes of "This Old House" covered installation
of some new gas pipes as part of the renovation. The impression
that I got from it was that even if it was legal for you to do it
yourself, you would probably still want to have someone experienced
do it because of the dangers involved if it isn't done correctly.
Also, the cutting and threading of that steel pipe is best done
with some expensive tools that experts tend to have ready access
to.
Probably the place to start with talking to people about having
it moved is with your gas company. If they don't do it they might
be able to suggest plumbing/heating contractors that do.
Rich
|
85.55 | Stove in a split? Lots of luck!!! | MRMFG1::D_BROUILLET | Don Brouillet MRO1-3/B41 297-5280 | Wed Mar 12 1986 08:30 | 19 |
| Warning - It is very, very difficult to heat a split with a stove
in the basement (make that 'lower level'). I tried it, and had
to run the stove so hot that it was 90 degrees down there in order
to keep it close to 70 upstairs. I know other people with splits
who have had the same problem. The design of the house just doesn't
allow efficient heat transfer. You can probably alleviate this
somewhat by cutting holes in walls and putting fans in all over
the place, but I didn't want to do that. I tied my wood stove into
my main heating system (oil-fired FHW) through a device called a
"Fireplate", and that works great! It's comfortable all through
the house, and the stove helps heat domestic hot water, too.
This may not apply to your case (I think you said you had a FHA
system), but you still might want to consider putting a hood over
the stove and tying it into your ductwork, rather than relying on
convection.
-db
|
85.56 | Wood Stove? | KATIE::CHAI | | Wed Mar 12 1986 12:25 | 6 |
|
I have a wood stove sitting in my besement which I have no intention
to use. it's about 6 years old, and was not used at least for the
past 3 years. and it has its own flue/chimney. Please send me a message
on KATIE::CHAI if any one is interested.
|
85.57 | accessories for FHA duct work??? | THORBY::MARRA | This space intentionally left blank ... | Thu Mar 13 1986 08:00 | 17 |
|
re .3 (or .4)
That is why I want to find out about auxiliary fans for the FHA
system. I plan on re-working the return ducts so that I can select
where the return air can be sourced from. When the stove is in
use, I will source the return from the cealing of the downstairs
and just turn the fan on (by a timed switch) to circulate the air.
During the summer (when it's cool down there), I will source the
air from the floor of the downstairs, etc. The return source upstairs
will only be used occaisionally.
So... What kind of accessories are made for FHA duct systems?
ie valves, electrostatic cleaners, fans, etc.. How do these things
work (not how, but how well)....
.dave.
|
85.58 | Use existing funace blower... | COBRA::DUTHIE | | Thu Mar 13 1986 10:11 | 20 |
| What I have planned for the multi-level house that I am building
sounds like it would fit your situation. I am putting a hood over
the wood stove in the "lower level" and ducting this to the furnace
as the cold air return. In the hood will be a thermostatic switch,
the same as the one in the hot air plenum of the furnace, which
will be wired in parallel with the existing one in the furnace.
This way, when either the furnace plenum is hot, or the air over
the wood stove is hot, the furnace blower will come on automatically
and heat the whole house. By setting the house thermostat a bit
low, the furnace will only come on and burn oil when the house drops
to the lower temperature. As long as the wood stove is going, only
the furnace blower will run. So, if I burn wood, the heat gets
blown through the house by the furnace blower, and if I don't burn
wood, the furnace starts burning oil to heat the house, all
automatically.
The cost for the second plenum thermostat is $10.00 to $15.00.
jim d.
|
85.59 | Stove in a split? Terrific! | OZ::DAHLSTROM | | Thu Mar 13 1986 16:49 | 19 |
| I have a small split (44 ft.) with a small woodstove (Vermont Castings
Resolute) in the downstairs family room and I think it does a very
good job of heating the whole house. The bedrooms are above the
family room and vents are cut in the floor of one bedroom, at the
end of the hall between the other two bedrooms, and also in the
bathroom. Two of the vent cutouts have fans but I rarely turn
them on. The entrance to the family room has been enlarged to
about 4 1/2 ft. and the heat from the woodstove rises up the
stairwell and heats the living room, kitchen and dining room
quite well. The kitchen and dining room are the coolest parts
of the house come morning--they are the farthest away from
the woodstove and, they sit over the unheated garage.
I removed the insultation from the ceiling downstairs too.
Can't help with info on ductwork for FHA heat. I'm stuck with
an all-electric house!
Carole
|
85.60 | Wait with the modifications | 11740::KENT | Peter | Thu Mar 13 1986 20:18 | 26 |
| We have a split entry with a family room downstairs and a living
room, dining room, and kitchen above it. The bedrooms are off to
one side of the house. I first put in a whole house fan that cools
the whole house. It works very well. The neighbor (with a similar
house) across the street has installed air conditioning only in the
upstairs. In the summer, the downstairs stay cool because the heat
rises.
I've installed a coal/wood stove in the family room. I don't have
a door on the stairway, so the heat flows up the stairs. It is
comfortable in the family room (except at the ceiling) and the heat
flows upstairs to the kitchen, LR, and DR. At about 20 deg. F outside
without too much wind, the temp in the living room without additional
oil heat is about 68 deg. The bedrooms don't benefit from the heat,
so the oil heat is used there (there are 3 zones of FHW heat).
I did not put any holes in the floor, ducts, or any fans to move
the heat.
My suggestion is twofold: (1)If you are going to buy at stove anyway,
try the stove without putting in holes or ductwork. (2)Rent a kerosene
heater of equivalent BTU output to see how a stove might work.
The kerosene heater is for test purposes only, so I don't think
there would be any great danger involved (if it is kept burning
in a safe manner).
Good luck!
|
85.61 | Tying woodstove into FHA system | FRSBEE::PAGLIARULO | | Sat Nov 22 1986 18:27 | 8 |
| I have a forced hot air heating system. I also have a wood stove in
the cellar. When I have the stove going the cellar gets pretty warm.
Rather than put grates in the floor to get the heat upstairs I'd like to get
the heating system blower to trip on without turning on the heat. I'm hoping
that this will help circulate the warm air upstairs. Anyone know how this can
be done? If it's any help it's a Rheem system and the thermostatic components
are Honeywell.
|
85.62 | Information on furnace wiring | MAY11::WARCHOL | | Mon Nov 24 1986 09:47 | 36 |
| You have a couple of choices. If you don't mind a manual system
it is very easy to wire a switch in parallel with the fan limit
switch in the furnace to apply power to the blower motor whenever
the switch is on.
On furnaces equiped for airconditioning there is a relay setup that
will select a cooling blower speed and a heating blower speed. The
thermostat is mounted on a subbase that has the switches to select
heating/cooling and auto/manual for the fan. Your furnace could
be setup for cooling and you may not know it. If it is you should
be able to locate the connecting screws inside the furnace for the
thermostat wires. A heating only setup just uses two wires (white
and red) while a heating cooling setup has four wires (white, red,
green, and blue).
The wires have following functions:
White - 24V common
Red - heat
green - fan
Blue - cooling
Connecting any of the red, green or blue wires to the white will
select the appropriate function. It would therefore be very easy
to connect a switch (or even a switch that would close when the
air around the woodstove was hot) between the white and green wires
to turn on the blower.
If you have a heating only system than a manual switch to apply
power to the blower would be the easiest to install. But it would
be possible to mount a relay and use 24V to control it.
Nick
|
85.63 | It's all automatic... | COBRA::DUTHIE | | Mon Nov 24 1986 11:35 | 10 |
| There should be a small thermostatic sensor on the hot air plenum
that controls when the fan turns on/off. Buy a replacement sensor the
same as the origional, place it somewhere above the wood stove,
and wire it in parallel with the existing one. Now, when either
one senses a high enough temperature it will start the blower.
Now, if you can put a sheetmetal hood over the wood stove and duct
it into the cold air return.....
Jim D.
|
85.64 | Here's how I have done it. | SAVAGE::SLIZ | | Tue Nov 25 1986 11:18 | 12 |
|
I have a typical hot air system an a Nashua wood stove with a built
in blower system. I heat the whole house (split level) with the
wood stove. I have ducted the output of the stove into the hot air
duct of the furnace, and use that duct to move hot air from the
stove through the whole house. I have been doing his for 4 years
and it works great. Both systems are independent and therefor manual.
It may not be as efficient as it could be, but it was simple to
do, and the cost was minimal. Even when the stove goes out in the
middle of the night when it's real cold, the furnace comes on and
there is no problem with both systems using the same duct.
|
85.298 | Four warm ducts and one hot one | QUOKKA::SNYDER | Wherever you go, there you are | Tue Nov 25 1986 15:31 | 39 |
|
Having read a ton of notes on furnaces without finding the answer
to my question, I thought I'd give the sundry furnace gurus
another chance to show their stuff. And I humbly preface this
with the admission that what I know about furnaces is essentially
doodly-squat, so don't be surprised if my terminology is a bit
off.
Here is my (perceived) problem:
My gas FHA furnace seems to come on regularly as it should
according to the thermostat setting (though it's hard to really
tell, since we keep the thermostat at 50�).
However, the air coming out the floor registers doesn't feel hot.
It is generally slightly warm, and sometimes not even that. Never
cold, though. In previous residences, the air was always much
hotter.
So, I went down the basement to see what I could figure out. There
are five ducts (not counting cold air return). With the furnace
blazing away, four of them were just warm to the touch and the
fifth was hot. The four so-so ones lead to registers. The one
hot one is about six feet long and goes into what used to be the
chimney (now blocked off and not used for anything that I can
see).
What should I be looking for? Are there adjustments that can be
made? Does this sound like the beginning of end? If so, I don't
want to know.
If it makes any difference, the furnace is a Carrier, about 15
years old according to the guy who inspected the house before we
bought it. No air conditioning, no humidifier.
Thanks in advance.
Sid
|
85.299 | Fan control switch | MAY11::WARCHOL | | Tue Nov 25 1986 15:56 | 18 |
| The duct that you say is hot sounds like it is the smoke pipe, it
is supposed to be that way. The rest of the supply ducts may be
hot directly over the furnace but are are usually only warm further
away from the furnace.
The furnace blower is normally set to come on when the air inside
reaches around 120 and will turn off when the temperature drops
to about 80. These values vary since the fan control switches
are usually adjustable. You could have a poorly adjusted or
defective fan switch.
The adjustment is relatively simple but if you really don't know your
way around inside I'd suggest having a service company come it to look
it over. The replacement cost for the switches is under $20 and armed
with the little bit of information that I've given you, you can protect
yourself from being taken.
Nick
|
85.300 | check air filter first | HARPO::B_HENRY | Bill Henry | Tue Nov 25 1986 16:21 | 11 |
| Something simple to check first. Has the air filter been changed recently?
The reply about the upper and lower limits is good, I moved into an
apartment once that the upper limit was set so low that the burner
kept coming on for short periods and the fan never seemed to shut off.
The symptoms sound the same. I don't remember what I finnaly set the
limits at. This sounds like a good time to have a burner man come in
and do a cleaning and adjustment. For what that costs, it is usually a
good investment.
bill
|
85.301 | Get it 'tuned up' first... | BEING::PETROVIC | If you don't do it, no one will | Wed Nov 26 1986 10:10 | 12 |
| I assume that this is a 'new' house and you don't know what PM was done
on the furnace. I had a similar situation with an oil-fired system that
was fixed by replacing the filter and having the oil company I deal with
tune it up. The firebox has a system of passages that had gotten clogged
and once they were vacuumed out, the furnace started acting the way I
remembered it should...HOT air emanating from all the registers.
So, I suggest that you get a tune-up before doing anything else...it may
be that simple...
Hope this helps...
Chris
|
85.302 | Adjusting the blower control switch | VINO::TREMBLAY | | Mon Dec 01 1986 11:51 | 35 |
| RE: .1
If it is your blower control switch it can be easily adjusted,
which it sounds like it is to me too.
Locate the control switch inside your furnace. It's the control
with the calibrated temperature dial. There are 3 tab setting for OFF,
ON and LIMIT (or OVERTEMP). [Some only have two: OFF/ON and LIMIT]
OFF and ON control the temperature that the blower cycles at, while the
LIMIT switch shuts down the furnace incase it overheats because of a blower
failure (you should not have to adjust this switch which is usually set
around 200 degrees). What you what to do is adjust the ON tab (setting)
20-40 degrees higher than it is. Now turn on the furnace via your thermostat
and observe the temperature dial. You will see it turn as the heat exchanger
heats up. When it reaches the ON setting, the blower will come on and the
dial will go back down (usually about 10-30 degrees) and remain at a certain
temperature. This is your "steady state" temperature for your furnace
(with current atmospheric conditions). Steady state temperature is a function
of several things; thermostat setting, blower speed, temp of air in cold air
return, air resistance in ducts, etc.) Basically what you what to do is
adjust the ON setting so its 10-40 degrees higher than the steady state
temperature you observed. This allows the heat exchanger to have enough
residual heat so it can handle the "recovery period" after the blower turns
on. Conversely, the OFF setting should be 10-40 degrees lower than the steady
state temperature. Adjust this by feeling the temperature coming from your
heating registers in your living area after the burner has shut down and
the blower is still going. You what to remove as much heat from the heat
exchanger as you can but still have warm air coming from the ducts. So if
the air is too cool just before the blower shuts off, raise the OFF setting.
If its still warm enough lower the OFF setting. With a little trail and error
you'll find the settings you like for your system.
NOTE!!! ALWAYS hold the temperature dial when changing the settings
(tabs) on it. It can "freewheel" and if it moves you'll
lose the calibration.
/Glenn
|
85.65 | but be careful to get it right | BEING::MCCULLEY | RSX Pro | Mon Dec 01 1986 20:14 | 22 |
| .2 suggests buying a thermostatic sensor like the one already on
the hot air plenum - but that might not be the optimal temperture
to distribute heat from the woodstove, you might want to investigate
other thermostats, those for starting central air conditioning will
turn on when temperture exceeds the setpoint (inverse of the thermostat
for controlling your furnace).
Our new house has the cold air intake for the gas-fired hot air furnace
located in the highest part of the second-floor cathedral ceiling with
a fairly long duct run to the furnace. My plan (after consultation
with the electrician) is to wire a line voltage thermostat in the grill
of the duct intake, turning on the blower if the temperture at the
intake exceeds a threshold value. I may also add a manual "blower on"
switch, and a manual override of the automatic blower control for those
times when the woodstove threatens to cook us all out of the house. The
electrician did warn that caution is necessary, the blower must operate
correctly if the furnace burner is on, *AND* the furnace cutoff switch
must still cut all power to the furnace including the blower. So you do
need to be careful to get the wiring right for that to function
correctly - it might be important the first time somebody thinks
the furnace kill switch cut all the power and goes poking around
in there....
|
85.303 | no, I haven't frozen to death (yet) | QUOKKA::SNYDER | Wherever you go, there you are | Wed Dec 10 1986 22:47 | 72 |
| From the author of .0, thanks for the info thus far. However,
having been thwarted in my attempts to implement the suggestion in
.4 by a shoulder separation and then a vasectomy that took more
than two weeks to heal, I finally made my way into the basement
this evening. Actually, access to my basement deserves an entry
in the "Why did they ever do that?" note. Maybe later.
Anyway, when I got down there, this is what I found (within the
limits of keyboard sketching):
__________________________________________
/ \
| CAM-STAT INC. |
| _ |
__________| / \ |
/ | \_/ |
| | _____ |
| | /###/#\ |
| | |###/###| |
| | |##/####| |
| | \#/#####/ |
| | ------- | \
| \__________________________________________/ |
| / / / | \ ##### \ LIMIT |
| / / / | \ #### \ |
| / / / | \ ### \ |
| |
| 90 95 100 105 110 115 120 |
\___ ___|
| |
| |
\________________________________________________/
The "circle" with the line through it is where you stick a
screwdriver to turn the white plastic cam to make it point at the
setting you want. Currently, it is set at 115�, as indicated in
the diagram. Beneath this gizmo is a sticker with the words:
IMPORTANT
---------
The numbered graduations on the fan switch are
the "OFF" setting. The fan will turn "ON" at
about 25� above this temperature. Factory setting
will meet average installation conditions, but
for best results, adjust when balancing system.
"LIMIT CONTROL SETTING" prevents discharge air
temperature from exceeding 200� F.
A-75575-A
I saw no other places to make adjustments than the one cam. I
assume that the LIMIT setting is out of my control. Is there
anything tricky about making adjustments with this gizmo (excuse
my highly technical language)?
Mind you, I may still call someone to come give the furnace a good
once over. Having always been a renter before this winter, I
never paid much attention to furnaces; they were in the slumlord's
domain. I don't like having lots of things in my house that I
don't at least nominally understand, however, so I thought I'd try
to glean a little more from you furnace wizards.
Now that I'm feeling better, I'd like to feel warmer, too.
Sid
|
85.304 | Still worth a try | VINO::TREMBLAY | | Thu Dec 11 1986 11:58 | 10 |
| RE: .5
As you noticed, I avoided talking about the fan controls
that only have one OFF/ON setting. These don't provide the resolution
of the previously mentioned units. I would suggest you just turn
up the OFF/ON setting several degrees (5-20) to force the ON temp higher.
That way you'll have more latent heat built up before the blower
turns on. You have nothing to lose trying this. Just remember where
the fan control was set originally so you can always set it back.
/Glenn
|
85.305 | ON, OFF, ON again | GENRAL::HUNTER | from SUNNY Colorado, Wayne | Thu Dec 18 1986 17:56 | 14 |
| I know very little about furnaces since our furnace when I grew
up was: go down to basement, make sure coals and fire are still
going, shovel small coal in first, shovel in at least 4 pieces of
approx. 1 foot diameter coal (up to 8 if it was going to be a cold
night), close door, pile lots of covers on the bed.
So, given the above, my question is this. I have a FHA furnace
(lennox). I found the control for shut-off temp as stated in a
previos reply. The furnace kicks on OK and blows plenty of hot
air. What I wonder about is when the furnace fan is shutting off.
The fan will kick off, wait anywhere from 30 seconds to 2 minutes,
then kick back on for a short period of time. Is this normal?
It has done this every since I bought the house. This action is
hard on the fan relay. I have had to eplace it twice in 5 years.
If the above is NOT normal, what are some of the possible fixes???
|
85.306 | | VINO::KILGORE | Wild Bill | Fri Dec 19 1986 09:48 | 7 |
|
I believe that's a 'feature' built into some furnaces. After the
burner shuts down, the blower stays on until the heat exchanger
cools to a certain point. After the blower turns off, the heat
exchanger is probably still warm enough to heat the now-still air
around it. After a short time, the blower turns back momentarily
to scavenge this heat.
|
85.307 | Adjust the blower control switch | VINO::TREMBLAY | | Mon Dec 22 1986 11:19 | 21 |
| RE:. .7,.8
That's not a feature, but a blower control switch once again
in need of adjustment. Lower the blower "OFF" setting a few degrees
lower. That way you'll pull off that residual heat your not getting
while the blower was on the first time (and sparing the blower/relay
all that additional cycling for nothing).
The idea is to get all the heat you can from the heat exchanger
(remember the burner has shut off a long time ago now and only the
blower is on) without blowing cold uncomfortable air into your living
space. Therefore, you can turn your "OFF" setting down to the point
where the air coming from your heating registers is comfortably
warm just before the blower shuts off.
[Note: As mentioned before, the blower controls with the "OFF" and
"ON" temperature settings "tied" together (i.e. Raising the ON temp
raises the OFF temp and visa versa) involve more of a trade off to
adjust and take alittle more tweaking to find the right setting.]
/Glenn
|
85.308 | Check the schematic | VINO::KILGORE | Wild Bill | Mon Dec 22 1986 11:41 | 5 |
| re .7, .8, .9
Just make sure you're not battling the furnace design. I know of
a 14-year-old oil FHA system on which the second fan cycle really is a
scavenging feature built into the fan circuit.
|
85.309 | FHA ceiling vents? | YODA::BARANSKI | Laugh when you feel like Crying! | Mon Dec 22 1986 12:06 | 8 |
| Question:
Recently I've seen some apartments where the FHA vents were in the ceiling.
Now I imagine that that would be great, cause you can put your furniture
where ever you want without worrying about the vents, but is there some drawback
to havinbg the vents in the ceiling? Any personal experience?
Jim.
|
85.310 | remember, hot air rises | BEING::MCCULLEY | RSX Pro | Mon Dec 29 1986 13:37 | 10 |
| re .11 - off the top of my head it seems that ceiling vents might have
a drawback because hot air is less dense and thus tends to rise while
cold air sinks to the floor. Delivering the warm air to the top of the
room would thus seem likely to contribute to stratification and
uneven heating. Since my personal perception of FHA is that it
is not a particularly even heat, in designing our system I tried
to place vents so that they would contribute to mixing the air to
even out the heat delivery. (Now that the woodstove is our major
heat source, this is a moot point until I add the secondary blower
to distribute the stove heat through the same FHA system.)
|
85.66 | FHA air filter | MORMPS::WINSTON | Jeff Winston (Hudson, MA) | Thu Apr 23 1987 19:18 | 8 |
| anyone else out there have allergies?
I do, and am thinking of adding an air cleaner to my FHA heat/AC
system. I was planning on a standard electrostatic air cleaner, but
the contractor is pushing a 'passive' "SPACE-GARD" filter that is
supposed to be better, and filters out particles down to 1 micron.
anyone have any experience with these?
|
85.67 | | NEXUS::GORTMAKER | | Thu Apr 23 1987 20:56 | 9 |
| Yes, It is close to impossible to get rid of everything but the
electro-static filters do a good job. The price was very high
when I got mine I belive $200~ was the price I paid.
Have they come down at all?
This is the type that replaces the regular furnace filter right?
-j
|
85.68 | | MAY11::WARCHOL | | Fri Apr 24 1987 15:29 | 10 |
| The Space Guard 'passive' filters are cheaper at first, but will
cost you about $25 a year to replace the element. With the
electrostatic units the initial cost is higher but you can then
wash the cells as often as you like.
If you have very bad allergies you might want to use an electrostatic
unit and follow a more frequent cell washing schedule. Replacing
the Space Guard elements frequently could be expensive.
Nick
|
85.73 | FHA Humidifier Needed | GNERIC::FARRELL | Thirty Six Bit Paleontologist.. | Mon Apr 27 1987 16:08 | 7 |
|
I'm looking for a store in the Worcester area that sells humidifiers for
FHA heating systems. Tried Sommerville Lumber with it's "5 employee to
1 customer" showroom ratio and was told "We don't sell 'em".
|
85.74 | | VIA::ASCHNEIDER | Andy Schneider - DTN 381-2475 | Mon Apr 27 1987 16:11 | 2 |
| Try Sears. They've got 'em.
|
85.69 | info on purifiers? | ERLANG::SUDAMA | make my day | Thu May 07 1987 21:43 | 9 |
| Can anyone give a little more info on air filtration/purification?
For example, what are the trade-offs between free standing units
and things that are built into the heating system? How effective
are these units, and what kind of things do they help with? My wife
has sinus problems (not necessarily allergy related), and we find
it helps to use a warm air vaporizer in the bedroom at night. Would
air purifiers of any sort help with this sort of thing?
- Ram
|
85.70 | FHA filters | ZEN::WINSTON | Jeff Winston (Hudson, MA) | Fri May 08 1987 00:19 | 18 |
| A sinus problem per-se is usually humidity sensitive - but NOT
ncessarily sensitive to pollen levels. An ultrasonic humidifier is
quite useful to keep humidity in the mid-range in the winter, as a
de-humidifier or air-conditioner in the summer. She may also want to
carry a bottle of "ayr" or "ocean" (salt-water solution for applying
humidity directly to the affected area).
I, unfortunately, have some allergies. I did a teo-month trial with a
'room-size' electrostatic air cleaner once in a 2-room apartment
(recommended by my Dr.) and found it quite useless. However, the
in-central-system unit in my folks' house worked wonders - for
ALLERGIES.
Apparently the fad now is a 'passive' air filter called "space-guard".
Supposedly catches particles in the single-micron range. Advantage:
No moving or electrival parts => nothing to break. Disadvantage:
$15-$25 for a new filter once a year.
|
85.71 | Check for "ozone-free" specification | ALEX::CONN | Alex Conn, ZKO | Tue May 12 1987 18:05 | 21 |
| My wife and I both suffer from allergies. In Maryland, the problem is
particularly bad due to the humidity during the summer. We installed
an electronic air cleaner on our FHA system and found--a couple of
hundred dollars later--that she was *worse* off with the thing on than
when it was switched off.
The dealer had heard of similar problems but only rarely. One guess
was that the thing produced small amounts of ozone which could be
irritating to some people. I noticed on a recent brochure for a
similar unit a statement in bold letters that it was "ozone free," so
the problem was apparently not that rare, and might well have been her
problem.
Allergies and sinus problems are frequently related.
The Bionaire thing we use here at work is fairly effective against
cigarette smoke and probably would do some good if pollen is the
problem. But I agree that the whole-house unit is appealing--
especially if they have licked the problem we encountered.
Alex
|
85.94 | Oil FHA furnace Replacement | WELFAR::PGRANSEWICZ | | Thu May 14 1987 13:29 | 44 |
|
Boy have I got problems!
My oil-fired FHA system heats my house but at the same time fills
it with exhaust fumes. No smoke, just fumes. The independent
oil-burner guy said my heat exchanger was cracked and thus the
exhaust was being circulated with the warm air.
The furnace is only 7 years old and is/was made by Blueray Systems
Inc., which went out of business. Thank God they warrenteed it for
10 years though ;-). I think I'm up the proverbial creek.
My oil-burner guy said he can install a new system, complete for
$1700. Names he suggested were Ford/Carlin (not the car) and
Duomatic/Olson. They come with a 1 yr warrenty and he adds 1 year
himself. You can get 10 or 20 year warrenties on the exchanger (and
we know how handy it is to have warrenty). The current system is
85,000 BTU. The Duomatic/Olson gives you the flexibility of
increasing the nozzle size to increase the BTU's to ~120,000.
My questions are many:
1. Has the ever happened to anybody else? Is this furnace really
dead after 7 years!!!
2. Who built YOUR FHA furnace? Anybody have Ford/Carlin or
Duomatic/Olson? How has your furnace performed? I don't want
another worthless lemon.
3. Is $1700 a good deal?
4. Do I have recourse against the company that installed the lemon?
They are still in business and not returning my calls.
5. Should I get a second opinion from another company?
My suggestions are few:
1. If you have a Blueray system, run for your life (or by spare
parts from me :-))
Thanks for any help,
Phil
|
85.95 | | HAZEL::THOMAS | No <ESC> from reality | Thu May 14 1987 13:48 | 7 |
| Do you have a humidifier on the system? They are frequently responsible
for premature failure of the heat exchanger. The water drips down
inside and it rusts through.
Rich
|
85.75 | Try your oil dealer | GENIE::LUSTMAN | | Thu May 14 1987 13:49 | 5 |
| I bought one from my oil dealer. They will clean the unit out
for me each year when they do burner maintenance.
Ira
|
85.96 | | WELFAR::PGRANSEWICZ | | Thu May 14 1987 14:16 | 7 |
| re: .1
Nope, no humidifier on it now. I don't know if the previous owners
had one on and then removed it. I noticed some rust on one section
of the duct work and one of those screw in taps in the cold water
line near the furnace.
|
85.97 | | HPSMEG::LUKOWSKI | I need an 'AUX' for my stereo | Thu May 14 1987 14:54 | 8 |
| Did the oil-burner guy open up the system to see what the problem
was or did he assume this from what you told him? If the heat
exchanger is in fact cracked, I wonder if it can be welded. I really
don't know anything about the internals of the system but it's a
thought.
-Jim
|
85.98 | Saw it with my own 2 eyes, I think. | WELFAR::PGRANSEWICZ | | Thu May 14 1987 17:23 | 6 |
| RE: .3
Yes, he did open the plenum and point out the crack on the front
of the exchanger. I did ask him if it could be repaired but he
said he didn't think any type of fix would hold because of the heat
swings of the exchanger. Anybody know if this is B.S.?
|
85.99 | Having it welded... | BARNUM::DVORAK | | Thu May 14 1987 20:41 | 14 |
| Two Items
1) If you are thinking of having it welded, I suggest you call
Mark Brown at Precision Weldments in Chelmsford MA. (617) 458 4890
I have had Mark do a lot of welding for me, and I am very pleased
with the quality of his work. No, I do not get money for saying
this. If Mark does not think a weld will hold, he will tell you.
Mark is a one-man buisness. He has done an aluminium bicycle frame
for me, A stainless steel pressure vessle, seats in my car...etc..
2) I renember *hearing* somewhere that welding a heat exchanger
is illegal. I have no idea if this is true or not.
George Dvorak BARNUM::DVORAK 297-5386
|
85.100 | weldable | MAY11::WARCHOL | | Fri May 15 1987 12:02 | 11 |
| If it really is a crack and not a rust-through condition then you
shouldn't have any problems with welding it, aside from having to
remove the heat exchanger from furnace (not an easy job). The heat
exchangers are "soft" steal as apposed to cast iron and will weld
very nicely, in fact that is how they are made.
If the burner unit is good see if you can get a new furnace and
have the installer use your current burner. This may save you a
few bucks.
Nick
|
85.76 | BUT | MAY11::WARCHOL | | Fri May 15 1987 12:03 | 5 |
| Humidifiers should be drained and flushed monthly during the heating
season.
Nick
|
85.101 | | WELFAR::PGRANSEWICZ | | Fri May 15 1987 12:41 | 20 |
| RE: .6
The spot that he pointed out to me did look "bubbly" like rust was
undermining the steel. I did ask him if any of the other parts
had any value (circular, burner) and he said no, he would just haul
the whole furnace out and trash it. This I thought sounded shady.
He said the burner for this particular brand of furnace was custom.
This burner is made by a different company whose name escapes me
at the moment. But it is a well-known name.
If there is rust on the exchanger, is there any way of removing it
before welding? I don't know why it would be illegal to weld an
exchanger. Of course, after it was removed from the furnace! It's
sounding more and more like I need a second opinion from another
oil company and possibly a welding outfit also.
Keep the input coming! I'm beginning to feel a litte more hopeful.
Phil
|
85.77 | A word of caution | WELFAR::PGRANSEWICZ | | Fri May 15 1987 12:45 | 6 |
| Beware. Humidifiers may cause rusting of heating ducts and furnace.
My FHA just bite the big one and it MAY have been caused by a
humidifier. You might want to ask people who install them about
this aspect and see if their answers sound reasonable.
Phil
|
85.102 | | AUTHOR::WELLCOME | Steve | Fri May 15 1987 14:20 | 3 |
| Another opinion might be a good idea. Are you anywhere within range
of Boylston, Ma.? I've had good luck with Carlisle Fuel Co. Phil
Carlisle is very straighforward and honest, from all I've seen.
|
85.103 | | WELFAR::PGRANSEWICZ | | Fri May 15 1987 14:42 | 16 |
| RE: .8
I've talked to the company that originally installed the system.
I'm having them come out and render their opinion of the situation
and give me estimates for replacements if it is dead. He's charging
$28 for the service call.
He has been very helpful. He gave me the address and telephone
number for a "field service rep". The line was busy when I called.
Probably another satisfied customer ;-). I'll see what I can get
from them. He did say that welding, if it did take, would only
be a temporary fix. If the metal is fatigued, he said the weld
may hold for a year or a day. I wouldn't sleep well knowing this.
I think welding is out.
By the way, I live right next door in Holden.
|
85.104 | Rules sometimes = Safety | USMRM2::CBUSKY | | Fri May 15 1987 15:29 | 12 |
| I don't know if its illegal or not to weld a heat exchanger but it
won't suprise me. When you consider what's happening, spewing exhaust
gases into the air ducts for the house, your lucky you discovered the
problem and not the ParaMedic's! If it needs welding then chances are
there other weak spots as well. Better and safer to just replace the
whole unit.
Can't you replace just the heat exchanger? If not, I would stay
away from that brand of furnace. It's like buying a new car because
the exhaust system is shot.
Charly
|
85.105 | YAAyes, a MIRACLE HAass Occurred... | WELFAR::PGRANSEWICZ | | Fri May 15 1987 15:36 | 15 |
|
EUREKA!!! PAY DIRT!!! DRINKS FOR THE HOUSE!!!
I called the number that the installing dealer gave me and found
out I can get a replacement heat exchanger for $148 plus freight
COD! The 10 year warranty is full for the first 5 years and prorated
for the next five years. These damn warranties always seem to screw
you out of full replacement but it's a hell of a lot better than
$1700. Now to find out how much to get a new exchanger t installed.
Probably $1552!
Moral of the story: Don't believe everything you're told.
Now I'm suspicious of my oil-burner service
guy...
|
85.106 | | CRETE::FLANNERY | | Fri May 15 1987 15:57 | 4 |
| If you decide to switch burner companies, Sterling Plumbing
and Heating are fantastic but impossible to get hold of.
Ouellette and Wheeler from Fitchburg also seem good and have
done lots of work for us.
|
85.107 | *avoid* the servicemen | BARNUM::DVORAK | | Sat May 16 1987 22:10 | 4 |
| Have a go at putting in the new heat exchanger yourself. FHA is
just a pile of sheet metal, and you have all summer to finish
the job. Even if you have to buy tin snips and an electric drill
you will be far better off financiall
|
85.108 | Quit while I'm not too far behind? | WELFAR::PGRANSEWICZ | | Mon May 18 1987 15:27 | 17 |
| The original installer of the furnace said the job is an all day
affair for two people. The furnace basically has to taken down
to scratch to get to the heat exchanger. Cost is $350. So I've
gotten the initial cost of $1700 for a new installation down to
$500 to install a new heat exchanger and provide any misc.
parts/gaskets that are needed. He's coming out tomorrow morning to
confirm that is indeed the heat exchanger. $28 for the call.
RE: .13
I've never done anything with a furnace except turn the thermostat
up or down. I don't think starting by tearing the entire thing
apart is a valid option at this time. I enjoy trying to do things
myself, but I think I'm a bit out of my league with this one.
Has anybody out there ever replaced a heat exchanger? Any special
tools or materials needed? Or is my gut feel correct?
|
85.109 | have them do it. | MAY11::WARCHOL | | Mon May 18 1987 17:34 | 13 |
| Go with your gut feel and have them do it. It sounds like you don't
have the confidence yet to tackle something like this. There are
no special tools required (there are some that can save time).
Basically you have to take the entire furnace apart since the part
you want to replace is the only thing left after you remove everything
else.
I've been on a few furnace replacement jobs where the unit had
to be dismantled to fit into the house. I was not a fun job and
did take some experienced people the better part of a day to do,
so their estimate doesn't seem out of line.
Nick
|
85.110 | I plan on doing mine this year! | MILT::JACKSON | The last of the red-hot sportscars! | Wed May 20 1987 10:02 | 28 |
| We have a 'dry base' boiler that got a little plugged up last year
(the guy who used to own the house never cleaned it) which caused
the base to melt (Dry base boilers have the burner in the lower
part which is not surrounded by water, and thus lots of heat causes
them to melt a little)
Anyway, I called the manufacturer and he told me that the base is
replacable, but I have to tear the whole furnace apart. I plan
on doing it this summer some time by myself. When I'm finished,
I'll call the local rep for the manufacturer (HydroTherm) and have
him come over and inspect it. (I asked, they'll do this for a small
fee)
I couldn't get anyone to come out and repair the furnace, they all
wanted to replace it for a cost of about $1800 or so. the new base
is $267 and gaskets, and other stuff should cost me another $100
at most.
It doesn't look like that big of a job. If I totally screw it up,
it won't cost me any more than $300 or so, so I think it's worth
the gamble.
-bill
|
85.111 | DIY, not DYI | WELFAR::PGRANSEWICZ | | Wed May 20 1987 12:21 | 16 |
| RE: .16
To me, the INCREMENTAL cost of having someone replace the heat
exchanger is not worth the potential problems and worries. I don't
want to have to worry about the oil line and exhaust connections.
Did I do them right? Will they leak? Should I have replaced that
gizmo?
I made an agreement with the oil-burner serviceman. He won't get
into the computer game and I won't get into furnace replacement.
I don't mind paying for his 20-30 years of expertise.
With all of the independent servicemen around, I can't understand
why you can't find anyone to do the job? In the summer, many of
them are DYING to get more business.
|
85.313 | Forced-hot-air registers | BAEDEV::RECKARD | | Mon Jul 13 1987 13:00 | 8 |
| Where should we put the forced-hot-air registers in the house-we're-
going-to-build-someday - the floor or the wall? What are the arguments
(if any) pro and con, including cost and/or effort of installation,
furniture location, etc?
One I know of would be that in-the-floor registers would make the
flooring more difficult to install - hardwood or wall-to-wall carpet or
whatever.
Also, is there a brand or style that someone could recommend?
|
85.314 | | JOET::JOET | Deatht�ngue lives! | Mon Jul 13 1987 14:19 | 6 |
| I don't like the floor jobbies. They always fill up with furballs and
old lollipops and it makes furniture placement that much harder.
They MUST be cheaper to install, but the wall-mounted ones are almost
totally unobtrusive.
-joet
|
85.315 | Floor vents vs wall vents | SEESAW::PILANT | L. Mark Pilant | Mon Jul 13 1987 14:54 | 9 |
| Another problem with the floor mounted vents is that unless they
are in the center of the room, the head always seems to just follow
the wall up, and keep the cieling nice and warm.
With the wall mounted units, the air is forced out horizontally
before it is allowed to rise. I would think that this would give
you a better utilization of the heated air.
- Mark
|
85.316 | registers take up more then physical space | YODA::BARANSKI | What, I owe you money?!? | Mon Jul 13 1987 15:20 | 9 |
| The biggest problem with *any* registers is where to place them in relation to
any furniture: bookcases, desks, couches, so that the furniture, whatever they
maybe in the future, will not block the ducts.
The only solution I can think of is to have built in furniture sharing the
space where the register is, such as a builtin bench seat in front of a window,
or a bookcase with the register built into the base...
Jim.
|
85.317 | Vents.. | GNERIC::FARRELL | Thirty Six Bit Paleontologist.. | Mon Jul 13 1987 15:35 | 8 |
| RE: .1
I put a section of screen in each of the vents in the house, and
that seems to prevent anything from falling into the vents. Also, most
stores sell plastic deflectors to prevent the hot air from going straight
up, and force the air to go out along the floor....
|
85.318 | Where do you get the stuff? | AKOV04::KALINOWSKI | | Mon Jul 13 1987 19:02 | 9 |
| Can anyone recommend anyplace to get registars and ducts for
forced hot air. I am finally at the point of bolting up some
heat registars for my new room addition to my old system.
The system was rated the extra capacity, but I am unsure who
to contact in getting the materials.
thanks
john
|
85.319 | non metal Hot Air Ducts? | YODA::BARANSKI | What, I owe you money?!? | Tue Jul 14 1987 09:06 | 7 |
| I've heard that new construction is now using nonmetal Forced Hot Air heating
ducts: Plastic, or sealed Cardboard. It's supposedly cheaper, and more
efficient; less heat conducted out through the walls of the ducts.
Anybody know anything about this?
Jim.
|
85.320 | Forced hot air fitting suppliers | SEESAW::PILANT | L. Mark Pilant | Tue Jul 14 1987 10:13 | 11 |
| I'd check in the yellow pages; try under heating or some variant.
I would imagine that you should be able to get the standard stuff
at any heating distributor. If all else fails, you could have the
pieces made up at a sheet metal shop.
One thing that is being used in some (a lot?) of new construction
is a flexible, insulated, plastic pipe. Sort of a rather large
insulated dryer vent hose. This is supposed to be really great;
but I haven't seen anything about it other than the installed system.
- Mark
|
85.321 | Fiberglass Duct | LDP::BURKHART | | Tue Jul 14 1987 10:26 | 9 |
| I saw some on TV (This Old House, I think) a fiber glass insulation
material with silver paper fron and back. It comes in sheets about 1/2 in
thick that you cut and build into box sections and seal with duct
tape. They were useing a special knife which cut a notch into fiber
glass which allowed the sheet to be folded into a box.
As always check with local building codes as to the use of this
stuff. Where it can be purchased? Your guess is as good as mine.
...Dave
|
85.322 | Try Summerville Lumber | DRUID::CHACE | | Tue Jul 14 1987 11:28 | 4 |
| Summerville Lumber has a pretty good supply of ducting and registers
off different sizes and configurations.
Kenny
|
85.323 | Supposed to be good | POP::SUNG | Dept. of Redundancy Dept. | Tue Jul 14 1987 12:24 | 7 |
| I saw the fiberglass ducting used on This Old House. I've seen
it used in conjunction with metal and flexible tubing. The flexible
stuff seems to be used when it's laid on top of the ceiling rafters.
The fiberglass ducting when it's under the joists (basement) and
then metal where all else fails (weird bends).
-al
|
85.324 | | MAY11::WARCHOL | | Tue Jul 14 1987 13:17 | 30 |
| The fiberglas duct board tends to come apart after a few years,
that tape won't hold forever. It also tends to get damaged very
easily if it is in a vulnerable location.
If you want to add a new outlet or two the round duct is probably
the easiest for the typical do-it-yourselfer. The elbows can be
adjusted to strange angles, and through the use of sheet-metal
screws, duct tape to seal the joints and metal hanging straps you
can come up with a solution that should be fairly solid.
When you start to get into rectangular duct things begin to get
a bit harder. Experience in fabricating and installing metal ducts
is helpful, especially when you get into some tough spots. Knowing
how to make a special offset or transition fitting from flat sheets
of metal is sometimes required to end up with a job that fits into
an existing structure. Take a look in a sheet metal shop sometime
to get a feeling for the quantity of special metal working tools
required.
If you know what you want you can have someone fabricate what you
need. If your not sure how to specify the ducts or assemble them
later then you are probably better off having them install it also,
compared to the cost of the fittings their installation time may
not be that much more.
I wish I could show you all the tricks through this notesfile, but
it is too difficult to do. Once you've watched someone put this
stuff in you could probably do most of it yourself.
Nick
|
85.325 | Lets heat up, keeps marbles out ! | DRUID::MEANEY | JIM | Thu Jul 16 1987 14:52 | 17 |
| >> I don't like the floor jobbies. They always fill up with furballs and
>> old lollipops.
Most of the registers in my 102-year old house are in the floor,
and most of them have a piece of heavy hardware cloth (3/8" squares)
cut to size and set into them to stop most of what's dropped thru
the louvered registers from rolling down the duct.
The large register in the dining room had no screening in it and
recently, while vacuuming it out, I wondered what has been accumulating
in there over the years. I took a small mirror and flashlight and,
like an upside-down periscope looked down the duct. In one cranny,
there were 7-8 glass marbles (some cat's-eyes) and one plastic soldier.
Ah, the joys of owning an old house...
JPM
|
85.326 | Dining room = Par 3 | CYGNUS::VHAMBURGER | Vic Hamburger IND-2/B4 262-8261 | Fri Jul 17 1987 16:09 | 13 |
| < Note 1319.12 by DRUID::MEANEY "JIM" >
-< Lets heat up, keeps marbles out ! >-
The large register in the dining room had no screening in it and
recently, while vacuuming it out, I wondered what has been accumulating
in there over the years. I took a small mirror and flashlight and,
like an upside-down periscope looked down the duct. In one cranny,
there were 7-8 glass marbles (some cat's-eyes) and one plastic soldier.
AHA.....sorta like the 18th hole at the miniature golf course......I always
wondered where those little colored golf balls went to!
8^)
|
85.327 | | WELFAR::PGRANSEWICZ | | Fri Jul 17 1987 17:42 | 3 |
| I have enough trouble walking without tripping over floor vents!
I've got wall vents and they seem to have been placed so that they
rarely interfere with furniture placement.
|
85.112 | Final Chapter, I hope | WELFAR::PGRANSEWICZ | | Mon Aug 03 1987 13:28 | 36 |
|
Well, time to put in the final chapter.
I had the replacement heat exchanger put in last week. The final
dollar totals were:
$132.00 Heat exchanger (prorated cost)
28.00 Diagnostic visit
57.62 Shipping
350.00 Installation + misc. parts
-------
$567.62 Total
- 30.00 Cleaning (that would have had to be
done to the old one anyway)
-------
$537.62
K. W. Stidsen of Worcester installed the heat exchanger. He was the
one who originally installed the furnace and tipped me off to the
replacement option. He told me I basically have a new furnace now.
They went through the whole system. Cleaned and tuned it. I would
recommend them. It's a father/son team. The father seemed very
thorough and meticulous.
Savings:
$1700.00 Suggestion of "old" service co.
- 537.62
--------
$1162.38
Lesson learned:
Make sure the person who works on your furnace receives technical
updates from the manufacturer. And by all means, check around
for alternatives and estimates. For $1162 it was certainly worth
the time and aggravation.
|
85.8 | My FHW furnace rumbled also | RICKS::STLAURENT | | Fri Sep 25 1987 09:09 | 14 |
| I know this is very late, but I thought I'd leave my experiences
here incase anyone uses this for reference.
I have an oil fire FHW system and had trouble with the furnace
rumbling when it started. The service man found that the ignition
unit was faulty. It produces a high voltage (roughly 11kv I believe)
and my was putting out about 8kv. He used and instrument very similiar
the the type used to measure the high voltage on TVs.
I pay $25 per year for a basic cleaning. The company I have also
offers a service contract (about $60), but I've elected not to get
it (and haven't needed it yet - knock knock).
John
|
85.113 | FHA duct work?? | MKFSA::STEVENS | | Sat Sep 26 1987 22:11 | 13 |
| I have an oil/wood forced hot air heating system that only has ducts
going to the first floor of my house. I'd like to extend the duct
work to the upstairs but I only have one place I can do it, in the
hallway closet. That could let me put direct heat to the bathroom
and one bedroom. I don't have a way to get direct heat to the
other two bedrooms without remodeling the whole first floor to make
a shaft. My question is this, can I run the duct work up into
my attic space and branch off from there? Could I insulate the
duct work in the attic? If anyone can offer me some suggestions
or alternatives I would appreciate it very much.
Thanks,
Dave
|
85.114 | | ZEN::WINSTON | Jeff Winston (Hudson, MA) | Mon Sep 28 1987 00:37 | 12 |
| depends on how long an attic run it is, and how powerful your existing
system is - if it was sized for only the existing ducts - a long run
through the attic may not be feasible. Anyway, its not that effective
to feed hot air from the top of a room (it rises, natch?)
Are you sure there is no way to get it up to the 2nd floor near the
other bathrooms? You can move a fair amount of heat with only 4" or
5" ducts, or ducts 3" x 9" or some such - take a creative 2nd look.
Maybe you can run it on a wall in a wide hallway and box around the
duct or some such...
|
85.115 | One observation, and noise! | ASD::DIGRAZIA | | Mon Sep 28 1987 23:41 | 17 |
|
I once rented a room in a house with attic ducts. There
didn't seem to be much air flow from the ceiling outlets.
Maybe the return inlet wasn't placed right.
Boxing a duct seems a good idea. Can you make the box
big enough to accommodate wiring or plumbing? Might be
handy. (Can you put electric wire in with a hot-air duct?)
Also, would the noise of expanding and contracting sheetmetal
matter if it's overhead? I have rectangular ducts running
about 50' along the length of the house, and they make a
racket when they change temperature.
Does anyone know how to make quiet hot-air ducts? Do they
have to be mounted in some kind of slip-hanger? Does anyone
else have noisy ductwork?
|
85.116 | Ductwork 101 | XANADU::SCHNEIDER | Dennis Schneider | Tue Sep 29 1987 12:38 | 29 |
| First, as recommended before, check out the blower capacity of what you
have now - a good heating supplier ought to be able to help.
Second, DON'T use sheet metal ducts if you're going into the attic. There
are two types on non-metal insulated ducts: Square foil faced/fiberglass
insulated rigid ducts and round flexible plastic and fiberglass.
The general practice would be to run a large square duct across the attic,
feed by a good sized duct up from the furnace, and branch off that duct
with the round stuff going into ceiling registers. You could install a booster
fan in the duct going up into the attic IF you have enough BTUs in the furnace
but not enough CFM in your blower.
Spend the time to learn EXACTLY how all the parts mate - this stuff is
REMARKABLY easy to do if you use it as intended, but a real bear if you
don't.
Also, DO NOT FORGET a cold air return - preferably in each room.
Technically, the "right" place to provide heat is to place the source of
hot air near the floor of the outside wall in a room, and have the return
on the opposite wall waist high. Most folks opt for two low wall positions.
The sheet metal ducting is fine for short runs (I did a finished basment
with three 5' 3x9 sheet metal ducts). Long runs of metal ducts DO make
expansion/contraction noises that can be really annoying.
Dennis
|
85.117 | | ZEN::WINSTON | Jeff Winston (Hudson, MA) | Tue Sep 29 1987 23:53 | 13 |
| My understandng is that you should stay away from fiberglass duct
board, as it is an inferior material for duct work (see note elsewhere
in this file entitled 'upgrading an FHA system for A/C" or some such).
6" fiberglass flexible ducting is the way to go.
We have an A/C system in our attic - recently (and well) installed,
and fan noise was a problem - easily solved by partially closing the
dampers to the ducts to the bedroom (the dampers were thoughtfully
located back where the individual run meets the main).
so - as you put this in - don't forget to put a few dampers along the
way. (you may also want one at the bottom, to balance the air flow
between the new and old sections)
|
85.118 | Thanks | MKFSA::STEVENS | | Wed Sep 30 1987 00:35 | 9 |
| Thanks for all the input so far. I think at this point I'll probably
run one branch of duct work up through the hallway closet and see
how that does. If that's not enough then I'll probably go with
the boxing in a shaft in the corner of the bathroom as suggested.
The attic option seems like something I should avoid if I can. I
don't want to make my heating systems less efficient, but I do want
the upstairs to be comfortably heated. Thanks again,
Dave
|
85.119 | | ZEN::WINSTON | Jeff Winston (Hudson, MA) | Wed Sep 30 1987 14:19 | 3 |
| well- your heat should have no problem making it into the attic - you
might want to leave hooks for a fan, either in the main attic duct, or
in the ceiling vents - to get it where it finally has to go
|
85.120 | does heat stilll rise?? | VICKI::ESONIS | What now? | Mon Oct 05 1987 08:13 | 6 |
| STOP!!!
heat rises, if i remember correctly.... wouldn't a floor vent
in the floor of each room which you wish to have heated serve the
purpose?
|
85.121 | RE:.-1/It do rise, but.... | XANADU::SCHNEIDER | Dennis Schneider | Mon Oct 05 1987 14:10 | 14 |
| Yes, heat does rise - but the issue you need to provide air circulation.
If all you do is cut holes in floors, and do not provide a means for returning
air from the highest heated spaces, you end up with a rather warm (a great
deal of the heat will rise) and stuffy (the air will become stagnant) room
at the top of the house.
It will also be nearly impossible to maintain the temperature of the rooms
at the top - the amount of heat you'd need is enough to maintain whatever
temperature you like. The amount of heat you'll GET is whatever rises.
Dennis
|
85.122 | Heat Does Rise, or Does Cold Sink? | MKFSA::STEVENS | | Mon Oct 05 1987 20:27 | 13 |
| As a matter of fact I do have one large vent which the previous
owner had put in to allow the heat to rise. I'm not sure how
much it really helps because I've never blocked it off to see
if the room gets colder. During the early and latter part of
the winter I would say that the heating upstairs is adequate.
But in dead of winter, Jan. & feb., I really need the heat
forced into each room upstairs. It's a 36 year old house and
they didn't insulate as well as they do nowadays. I'm definately
going to put one duct up through the closet, that's no big deal.
If I find that isn't enough, I'm sure Jan. & Feb. will motivate
me to continue branching out. Thanks for all the suggestions,
Dave
|
85.153 | FHA Efficiency Check | BARNUM::JORGENSEN | | Tue Oct 20 1987 09:53 | 14 |
|
I have been trying to optimize the operation of my FHA oil
fired heating system before winter rolls around. As I look at
the various parts of the system I have a good understanding
how most will affect the efficiency... accept the differential
setting on the thermostat. Currently if I set my thermostat
at 62 degrees, it comes on at 62 and lets the furnace run until
the house heats up to 70. The large fluctuation is not a real
problem, although it does take a bit of getting used to. Is
there any way of determining whether or not a smaller differential
would improve the systems efficiency? Any experience would be
a great help.
/Kevin
|
85.154 | Long Cycles | AKA::SUNG | In search of a personal name | Tue Oct 20 1987 12:16 | 11 |
| I have a FHW oil system, but from what I've seen, frequent cycling
is less efficient than long cycles. That is why a lot of thermostats
have a control for cycling. So it's actually better for the
burner to come on for 10-15 minutes and overshoot the thermostat
setting by a few degrees, than for it to go on and off every 2-5
minutes to maintain the exact temperature.
Supposedly it is very difficult for the human body to distinguish
a 2-3 degree temperature differential.
-al
|
85.155 | y | WORDS::DUKE | | Wed Oct 21 1987 13:01 | 8 |
| It could be the heat anticipator in the thermostat. This is a very
small heater in the stat which warms the stat in anticipation of
the room warming. It helps prevent the overshoot problem you are
having. The anticipator must be 'calibrated' to match the fan control
current.
Peter Duke
|
85.156 | another though or two | WORDS::DUKE | | Thu Oct 22 1987 12:49 | 17 |
| ref .2
Since this is hot air my last sentence is in error. The stat controls
the burner. The fan is controlled by the temp. of the plenum hence
the importance of the anticipator working properly. The stat shuts
down the burner but the fan keeps running to cool the plenum, hence
oevershoot.
.1 is true also that short cycles are ineffecient. The cycles could
be stretched out some by cutting the firing rate (gal/hr) of the
burner, but you could end up short of capacity on a real cold day.
Somewhere there is a happy medium. There may even be burners and
controls these days that monitor outside temp. and adjust firing
rates, etc. accordingly.
Pete Duke
|
85.157 | Actually two ways to adjust. | ALEX::CONN | Alex Conn, ZKO | Thu Oct 22 1987 18:18 | 30 |
| Re: .1
There are really two approaches to FHW: (1) to cause the thermostats to
call for heat less often (greater overshoot), and (2) to cause the
burner to stay on longer and come on less frequently (by adjusting the
max boiler temperature and the delta (range) on that honeywell device.
Thermostats usually have directions for affecting the degree of
overshoot--the digital Robertshaw has a number you can code in. The
Honeywell boiler temperature control has an outside control for the
upper temperature range, but you must take the cover off to adjust the
size of the range (which determines the minimum temperature).
Actually, in FHW, the boiler temperature control is the key to
determining how long the burner is on. The thermostats really only
control how often the circulators go on and off (which only indirectly
affects how often the burner goes on).
RE: .*
For FHA units, as stated above, the thermostat can be adjusted to
determine how often heat is called for.
In a manner akin to the above Honeywell boiler temperature control,
you can adjust the max and min temperatures for when the fan comes on.
The most efficient is having the min temperature very low (you get as
much heat out of the furnace as possible), but at some point it is not
very comfortable to have relatively cold air blowing out of the vents.
Alex
|
85.163 | FHA furnace blower motor source | STAR::SWIST | Jim Swist ZKO1-1/D42 381-1264 | Fri Oct 23 1987 11:59 | 21 |
| The blower motor in my FHA furnace crapped out last week. Disassembled
and found a corroded/burnt out connection among other signs of general
wear. Kludged it back together but will probably need to replace
it soon. It's a 1/2 hp westinghouse induction motor mounted via
rubber gaskets/clamps around the bearing sleeves.
Someone told me these things are standard and that any old 1/2 HP
motor will do. Don't quite believe that - the mounting would have
to be exactly the same as what I have and I don't notice that 1/2
hp ac induction motors are all the same.
At any rate, where do you go for something like this. An appliance
parts place? Is a furnace an appliance? The bulk of the yellow
page ads on furnance/appliances are people who expect to do the
repairs and pull the parts out of their truck or wherever they get
them. I can DIY this in 15 mins given the right motor.
Jim
(Keyword HEATING_FHW added, didn't match existing topics in 1111
so new note)
|
85.164 | Replacement heater motor | SEESAW::PILANT | L. Mark Pilant | Fri Oct 23 1987 16:39 | 11 |
| As far as I know, there are standards for motor mountings. For
most motors, ther are a half dozen or so.
One place to check is the Sears tool catalog (them again, it may
be in the big book; it has been a while since I did this). There
is a table, along with the rest of the motor specifications, that
list the mounting plate/hole specifications. That should get you
started.
- Mark
|
85.165 | a *great* line seen on an cubicle wall... | TOOK::CAHILL | Jim Cahill | Fri Oct 23 1987 18:35 | 4 |
| ��� As far as I know, there are standards for motor mountings. For
��� most motors, ther are a half dozen or so.
"The nice thing about standards is there's so many to choose from!"
|
85.166 | | BARNUM::DVORAK | | Fri Oct 23 1987 18:42 | 12 |
| On the old motor, find the frame number. Use this, as well as any
part number you find, when you call the places listed under electric
motors in the yellow pages. And when you call, talk like you know
what you are looking for, that may get you a lower price. And if
they ask who is calling, say "(your name here) Job Shop, and I
will send someone over today to pay cash".
Good luck
George Dvorak
Barnum::
297-5386
|
85.167 | Standard, I think | SETH::IVANY | | Mon Oct 26 1987 06:06 | 8 |
| I just had the blower motor replaced on my 37 year old hot air furnace
last week(under service contract, no charge) and he had the motor
in stock on board the truck. This would lead me to believe that
there must be some sort of standardization involved here. I would
think that you could get the correct one by taking all the numbers
off the motor tag and calling around to some heating supply places,
or electric motor supplies as mentioned in an earlier note.
|
85.168 | Re-build? | 39507::PGRANSEWICZ | Auhhhhh, I've been slimed! | Mon Oct 26 1987 12:25 | 4 |
| These motors can be repaired too. Probably cheaper than a new one.
Anybody ever have a motor rebuilt? .0, where are you located?
I know of a couple places in central Mass that rebuild motors.
|
85.169 | Heating supply wholesalers/retailers. | GLIVET::BROOKS | I'll see you one day in Fiddlers Green | Wed Oct 28 1987 12:27 | 7 |
| I've used a place called Total Air supply in Nashua for some
heating supplies. You may want to give them a call (889-0100). As
I recall they have some induction blower motors. If they don't have
what your looking for give Heating Specialties a call (882-2726)
also in Nashua.
Dick
|
85.123 | Putin return ducts first. | CURIE::BBARRY | | Tue Nov 03 1987 12:42 | 7 |
| Before you go to the trouble of putting heat ducts in the attic, install just
the return duct to the upstairs. Leave enough room for the heat duct in the
closet incase you do need to add heat ducts to the upstairs. The return duct
may improve air circulation enough to give the upstairs adequate heating. If
not the return ducts will still be needed if you put in heat ducts.
Brian
|
85.158 | more efficiency ideas | BINKLY::WINSTON | Jeff Winston (Hudson, MA) | Thu Dec 03 1987 10:08 | 31 |
| For those of us who have Forced Hot Air Heat (gas in my case)...
You may raise the question: "what can I do to make my system more
efficient (same heat for less $)".
0) One thing you can do is to make sure the thermostat on your fan and
burner is set properly (see note 1637). I spoke to a FHA furnace
repair person today, who also recommended:
1) If your basement gets hot from the furnace -cut a hole in the
air return in the warmest spot and put a vent in. This will improve
the heat efficiency. [this is a new one on me, anyone heard of this?]
2) make sure the 'heat anticipator' setting on your home thermostat
(the thing that slides inside the unit, with numbers like .25-.9
marked on it) matches the current in the thermostat wire (while I was
measuring the current with my Fluke multitester to be .43A, i noticed
the number .45A printed on the furnace control block - so to do this,
all you may need to be able to do is read). [does anyone know what
this is supposed to match?)
3) Make sure the heat coming out of the ducts closest to the furnace
is at least 120degF. (this is true for me, unfortunately, at the
ducts farthest away, its only 100degF)
4) If its accessible, insulate the main heating outgo duct (usually
theres a single large long duct with several small branches off it -
if all the branches are at the far end of the duct, the insulation
will help..)
other ideas????
|
85.159 | Cheap, quick, effective | 15934::PALMER | half a bubble off plumb | Fri Dec 04 1987 08:12 | 8 |
| The biggest single thing I did to improve the overall efficiency
of my FHA system was to caulk and tape up all the duct joints.
You would be amazed how much hot air leaks out. I spent
two hours and $10 on materials on the job and now my cellar is 10�
colder. This year I wrapped insulation around the main portion
of the air to air heat exchanger to help eliminate more heat loss.
=Ralph=
|
85.160 | | VINO::KILGORE | Wild Bill | Fri Dec 04 1987 11:52 | 7 |
| re .5, 1)
Is this something I dreamed, or is there some kind of rule about
not having an air return register in close proximity to the furnace
(something about possible creating a negative pressure gradient
that could suck exhaust gases back down the flue)? Anybody ever
hear anything like this?
|
85.161 | | BINKLY::WINSTON | Jeff Winston (Hudson, MA) | Fri Dec 04 1987 17:07 | 4 |
| can anyone suggest some inexpensive by-the-roll material to insulate
my main heating duct? Seems like everything I can find is $.50/sq.ft.
- hadn't planned to spend $80 - $100 just to cut down the heat loss
INTO the basement /j (p.s., it also has to be less than 2" thick)
|
85.162 | I used standard stuff | PALMER::PALMER | half a bubble off plumb | Mon Dec 07 1987 07:48 | 11 |
| RE .8
I too had trouble finding FHA duct insulation. The only stuff
I could find was �" thick and had an R value of 3, not worth the
effort. I wrapped 4" unfaced insulation around the ducts, then
covered the insulation with 6 mil thick black plastic. It wasn't
hard to do and looks ok.
Remember not to cover the thermal shut off wiring box located
next to, or on the ductwork. It looks like a standard electrical
box but has a round 'valve' type fitting on top.
=Ralph=
|
85.311 | Airflow Question for FHA experts... | BINKLY::WINSTON | Jeff Winston (Hudson, MA) | Thu Jan 07 1988 22:58 | 18 |
| I'm not sure anyone can help me on this one, but, im hopeful....
The problem: The air temp at a duct near my furnace is close to 180degF.
However, by the time it gets 1/2 way across the house, it has dropped to 120,
and is as low as 110-115 at the far end.
It is an old Coleman "high velocity" furnace. The hot air leaves the furnace,
goes through a large (28"x6") main for about 24', and then splits into about
16 4" ducts, one for each vent in the house. The ducts are not abnormally
cooled elsewhere, and are well insulated where they run over the garage. The
area around the furnace is VERY WARM, and the 24' main duct seems to shed a
lot of heat. It almost seems as if the blower (about 900RPM) is inadaquate to
force the air through the vents, though you can feel the airflow at the far
end. (the fact that the motor appears to have been recently replaced lends
credence to this). Does anyone know how to get more HEAT through the ducts?
would it help to insulate the main? to increate the blower speed?
thanx /j
|
85.312 | | VINO::KILGORE | Wild Bill | Fri Jan 08 1988 08:57 | 4 |
| I would tape and insulate as much ducting as possible. (Assuming
that "high velocity" means higher airflow speed, which probably
means slightly higher air pressure in the ducts and resultant higher
exfltration through duct seams.)
|
85.72 | space-gard works | BINKLY::WINSTON | Jeff Winston (Hudson, MA) | Fri Jan 22 1988 22:18 | 19 |
| Just want to put in a recommendation for the "Space-Gard" passive air
filter - (I make $0 from this) - have had it for the last 6 months now
(in my central ventilation system) and in addition have done a number
of comparisions (spending a night with the fan off and with the fan
on). It works, it seems to make the house significantly more
comfortable to someone with Mold, ragweed, pollen and dust allergies
(lucky me!). Its passive - nothing to break (electrostatic air
cleaners aren't so simple) and draws no electricity. The filter unit
itself costs only $140. Installation depends on how long it takes -
any duct work company can do it. roughly $150.
Disadvantage: Need to replace the filter every year or so, depending
on use - they're $15 from the distributor.
PS: I used Jay Moody & Co in Leominister (534-9483) a duct work
company. I recommend them VERY highly (they have done a number of
jobs in my house - #1 quality work)
|
85.9 | FHW rumbles also | DANUBE::C_JALBERT | | Sat Jul 23 1988 16:33 | 26 |
| Me too! My furnace has been rumbling... followed by a puff of
black smoke and the smell of "oily kerosene type smell".
Now, here is more information. It is a fairly new furnace, 6 years
old... Burnham, Beckett and HOneywell parts. Just before winter,
I was upstairs, when the house shook and there was a loud
explosion from the cellar... after I got my courage up, I went
downstairs, which had smoke and smell... I called our furnace
man, who came up and said it was a problem with the nozzle, which
he replaced... It was fine for awhile, then it started again,
not as bad, but at least several times a week, it will rumble
followed by a puff of black smoke and the oil smell. A friend
of my husband's came to take a look ( he's in the oil business)
said it needed a new "transformer"? and replaced it for him, plus
cleaned it... Again, fine for a few weeks... but now it has started
again. My husband moved my dryer, thinking that could be "clogging"
something up, that didn't work
He also adjusted the "air" flow ( I think that's what it was)..
That worked for a bit, but now it's doing it again. NOt all the
time, but avery few days.
Any other suggestions!!
Carla
|
85.10 | | PRAVDA::JACKSON | All I want is the key to your Ferarri | Mon Jul 25 1988 13:00 | 42 |
| I went through these problems for a whole winter last year, and
ended up with a new burner.
Things to check:
Take the flue pipe out and see if it's plugged, also look in
the chimney for obstructions. If you don't have enough draft, the
fumes will back up in the chimney and eventually you'll have a problem.
If the boiler is relatively new, the passages through the boiler
will be small, this increases the efficiency of the boiler by making
a larger heating area in the same number of cubic feet of boiler
space. Make sure that these passages are absolutely clean. A burner
that is mis-adjusted will plug up a boiler in less than 10 minutes,
so make sure that it's clean.
Check the nozzel and flame retention tip of the burner, if these
are bad, they can cause fuel to burn in the wrong `pattern' where
more oil goes to one spot than another. If this happens, you end
up with residue on the end of the retention tip, or in the fire
chamber. If this is happening, I'd say that a burner replacement
is in order.
With our furnace, we had all kinds of trouble, and could adjust
the air, replace the nozzle and get things running for a couple
of days, then the furnace would start smoking again. We tried several
things before having the burner replaced. Since then, we've had
absolutely no problems and the furnace hasn't even THOUGH about
getting dirty inside. The burner people never could figure out
what was wrong with the old one, but there was SOMETHING wrong with
it cause as soon as it was gone, the problems disappeared.
-bill
By the way, you CAN adjust the air/fire on your burner by yourself,
but you've got to know what you're doing. I'd suggest that you
have someone that knows what they're doing do the adjustments, as
you can cause some real problems if you don't do it right.
|
85.209 | Holes in furnace air exchanger? | SWSNOD::BARRETT | | Tue Aug 09 1988 09:35 | 19 |
| -< gas furnance question >-
Hello,
The house I am in the process of buying has a gas furnance that
is between 10 and 20 years old. During a house inspection the
inspector said that the air exchanger in the furnance could have
holes leading to the possibilty of gas exhausts getting circulated
through out the house.
Does anyone have experience with this problem? Would it be possible
to get a best guess cost estimate? Should the furnance be replaced?
Any information or pointers to other notes would be greatly
appreciated.
Thanks in advance!
-Tim
|
85.210 | Replace | MAY11::WARCHOL | | Tue Aug 09 1988 10:46 | 15 |
| The inspection said "could have holes" do you have any reason to
believe that there really are any? Is there rust and corrosion that
leads you to believe this? If there really is a reason to believe
that the furnace is at the end of its useful life get an estimate
on a furnace replacement and work this into the negotiations for
the house.
Replacing a heat exchanger is a very labor intensive operation.
Replacing the furnace would be a better alternative, there are
more efficient gas furnaces available today and in the long run
it will save you money in gas bills and repair costs.
Nick
|
85.211 | Consider replacement | SALEM::PAGLIARULO | | Tue Aug 09 1988 10:46 | 15 |
| I had the same problem when I had my furnace inspected last year.
The gas company technician said that the exchanger couldn't be replaced
and the furnace would have to be replaced. Actually he said that
it would cost just about as much to replace the exchanger as the
furnace if we could even find one. This was confirmed by several
heating contractors that I called at the time so we replaced the
furnace.
Are you sure there are holes in the heat exchanger? You can
tell for sure very easily by unscrewing the access panel. If there
are holes then maybe you can make a deal on the cost of the house
since it needs a new furnace. If there aren't holes yet, with a
furnace that old I wouldn't expect to get much more use out of it.
George
|
85.212 | Don't live with it! | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Tue Aug 09 1988 11:50 | 8 |
| If you confirm that this is a problem, don't live with it. Exaust
gas in the house means carbon monoxied -- read "poison in the
air".
It sounds like the exchanger is at the point where it is in danger
of going bad at any time. It would seem to make sense to replace
it now, on your schedule, rather than having it go bad in
mid-winter.
|
85.213 | Gas Co. Shut Mine Off! | CASV01::FALKOF | | Tue Aug 09 1988 13:47 | 18 |
| I had a house with FWA and when the gas company person came in to
do a routine cleaning, he found a small hole. In Mass., the gas
company has the power of law to shut down the heating plant until
it is fixed because of the danger of carbon monoxide poisoning.
Our Armstrong heat exchange, although only in year 12 of a 20 year
warrantee needed to be replaced but the model was out of manufacture,
therefore a new one was needed.
The cause of the hole was an improperly located humidifier which
condensed and dripped on to the exchange and over time corroded
a hole.
When you get a new furnace and if you plan a humidifier at the same
time, place the humidifier in the return line, not the feed (where
it can drip).
Negotiate about $2K off the house price; you'll need it all.
|
85.214 | Thanks...one last question | SWSNOD::BARRETT | | Tue Aug 09 1988 22:44 | 11 |
| Thanks for all the input, its a big help!
We do have a signed P&S and we did stipulate that the house must
pass a heating plant inspection as a condition of the p&s. The
realtor (who up until now has been honest) spoke of getting the
local gas service to inspect the furnance. Should I ask for a
written copy of there report if they do?
Thanks again.
|
85.215 | Danger... | JAWS::COTE | Are you with me, Dr. Wu? | Fri Sep 02 1988 11:59 | 17 |
| Aside from the afore mentioned carbon monoxide problem, there is
at least another issue... fire.
My heat exchanger rusted out after ~20 years, without me realizing
it. As a result, when the thermostat ignited the furnace all would
go well until the blower started. Then the blower would cause
turbulance in the fire box often blowing flames OUT THE SIDE!!
Luckily (?) this action would often cause the pilot to go out
and the furnace would shut down completely leading me to realize
I had a problem.
Cost $1300 to replace the whole she-bang. FHA, gas. 1985.
Edd
|
85.11 | Check those insulators!!!!!!! | HYDRA::LEMKE | Just another colorful metaphor | Wed Sep 21 1988 17:21 | 23 |
|
I had the same problem last year where the system came on but within
5 or 10 seconds there was a rumbling from down in the basement.
My oil company came out and tested my furance and replaced the
transformer. The problem went away for about 2 days, then was back.
After a second call to the oil company the serviceman discovered
that the insulators that hold the electrodes going fom the transformer
to the area of the nozzle had hair-line cracks in them which had
filled with soot and carbon.
These cracks acted like a short circuit, same as a crack in the
distributor cap for your car, and reduced the efficiency of the
transformer enough not to be able to provide adequate voltage to
ignite the oil when the system first came on, thus the chamber filled
with oil for a short period of time and was then ignited when the
transformer could supply the required voltage causing the rumbling.
Don't just think of the transformer being bad, look at all the parts
that make up the ignition system..
|
85.174 | DIY FHA Ductwork???? | WMOIS::JORGENSEN | | Thu Nov 03 1988 13:31 | 25 |
| Although I'm not installing a furnace yet,(but intend to in the future)
I am considering installing the ductwork for a forced hot air system in my
electrically heated house: a) for better heat circulation of my heat that is
currently generated by my wood stove in the basement, and b) because I
am eventually intending to install(have installed) a FHA furnace. I thought
I could install the duct work and use is now, though. I have several
questions(I haven't contacted any professionals, "yet")
o Is this an easy installation(my house is a small ranch)?
o How much $$ is ductwork per foot/yard/whatever?
o how many returns/ducts should I use in each room? Is there
a formula for room size to # of ducts?
o What size ductwork should be used?
o What kind of ductwork is best? Metal, plastic, etc
o Are there any good publications regarding FHA installation?
I currently have electric heat, and the Realtors that I have talked to
seem to think that converting to oil/gas is a reasonable "investment"
considering I'll be in the house for a while and can enjoy the comfort.
Thanks for any help!
Brian Jorgensen
|
85.175 | You to can do tin knocking | BAGELS::RIOPELLE | | Thu Nov 03 1988 14:40 | 55 |
|
o How much $$ is ductwork per foot/yard/whatever?
> if you have a basement under you both the returns and
the supplys can be on the floor. It is better to have
the return in the ceiling or near the top of the wall, but
you can get away with putting both on the floor. In the new
houses in my area they are putting in on the floor. Its more
work to run it up the walls. 10" x 8" x 10' snap lock from
supply house was $13.00 a section, round pipe is cheaper.
o how many returns/ducts should I use in each room? Is there
a formula for room size to # of ducts?
> Yep there's a formula for it. I haven't done FHA ductwork
but I have done Air Conditioning Duct work in my house, and
there is a formula for that. The A/C duct work is sized larger
to carry the cooler heavier air where the opposite is true for
FHA. I sized my own duct work then took it to a duct supply
house and had them check it. But they will also help you
do it.
o What size ductwork should be used?
> this isn't an easy question to answer, you have to get all the
dimensions in your house, draw them on some paper, runs a few
copies on the copier and then figure out where you would like
the return and supplys to be. Then calculate the returns and supplys.
Also figure out where the Air Handler will be placed, and also
calculate how big it should be.
o What kind of ductwork is best? Metal, plastic, etc
> All the FHA duct work I have seen in my area is all metal.
o Are there any good publications regarding FHA installation?
> if you want to get into the basic as well as technical aspects
of heating or cooling :
The Audel Library ,by Macmillian Publishing Co
Heating, Ventilating and Air Conditioning Library
( I have only vols 2 & 3 )
You can call toll free and ask for a list of books
1-800-257-5755 or order any of the books too.
I currently have electric heat, and the Realtors that I have talked to
seem to think that converting to oil/gas is a reasonable "investment"
considering I'll be in the house for a while and can enjoy the comfort.
> Smart broker electric houses always sell cheaper, my last house
was electric and I converted it to FHW baseboard.
A few other hints:
Call a few people for estimates they may or may not supply
a diagram of all the duct work in their estimate. When I did this
for my A/C none of them would supply it the estimate always
says all duct work is covered regardless. I found that a lot of
the A/C, FHA guys take the house dimensions to the supply house
who does the calculations for them.
Do you think you might put in A/C someday,
include that as a selling point "Ready for A/C", and size the duct work
to hold both. It won't cost much more.
|
85.176 | Thanks! Keep the experience coming! | WMOIS::JORGENSEN | | Thu Nov 03 1988 15:58 | 13 |
| Thanks for your reply... very informative! It sounds like you did the
duct work yourself. Is that correct?? How difficult was it?
Any special tools?
I plane to draw a diagram of my house before the weekend and take it to a
supply house. Did you shop around at all for your materials? Can
you suggest a good supply house in the greater Worcester/495 area?
(I live in Bolton).
Yes, I would very like to make the provisions for central air. Thanks
for the tip!
/Brian
|
85.177 | What tools you need and where are the supply houses | BAGELS::RIOPELLE | | Fri Nov 04 1988 13:31 | 52 |
|
It isn't very difficult to do ! The returns and the supplys are
the easy part. Cutting holes to put in the registers is what will
take the most of your time, and then putting them in. I did all
that while the house was being built so I didn't have to deal with
the furniture, or carpets etc.
Tools I used to put in my duct work:
- A sabre-saw with a sheet metal blade for cutting holes
or sections to length.
- A hex screw driver for driving sheet metal screws with my
drill.
- A pair of sheet metal snips
- For insulation in A/C work a heavy duty stapler made by
ARROW for use with 1/4" heavy duty staples P-19 I think.
- a level
Where are the supply houses ?
_ there are three that I delt with I don't have telephone
numbers handy.
The first I dealt with was :
M.A. Peacard in Boston, they supply the downtown boston
area and the people in the office were very helpful, but
I didn't buy any materials here because If I needed more
supplys I wasn't to keen on going into Boston all the
time to get them (long drive, too much traffic)
The second is S.G. Torrice in Woburn near the Woburn Mall,
I believe Everberg St. I ordered mostly all my materials
there and any custom work such as Plenums. Their service
is great but they don't always have the stock.
The third place that I did business at was great for supplies
but lacked in service (you really had to know what you wanted
because if you weren't in the trades they had to be pushed
to get an answer) This place is called Air Supply in Burlington
Take a left or right at Frud Rukers of rte 3A its up on
the left.
Prices between all places were with a few cents, I saw trucks
from all over MA at Air Supply. Bring your check book or
cash , they don't take American Express or anything else,
and use your last name as the contracting outfit.
Go For It !!
|
85.216 | CAST IRON HEAT REGISTER | ESPN::SIMMONS | | Thu Feb 09 1989 13:25 | 19 |
| I recently put new ceramic tile in my bathroom. One thing I have
left to do to finish the room is to replace the heat register/diffuser.
My problem is that I would like to replace it with a cast/wrought
iron one. I have seen them advertised in magazines as well as in
a local hardware store in the past. Of course, now that I want
one I can't even find the ad anymore. The opening is 2" by 12"
and is right up against the wall. So ... I am looking for one that
would attach to the wall and not set into the floor. It can be
little larger than the opening. Does anyone know where I can find
one of these?
Joyce
Oh yeah ... I live in Townsend and work in Chelmsford (MA) So anything
within commuting distance of those areas would be great. Or, mail
order would be just fine.
In advance ... Thanks!
|
85.217 | I got one | HJUXB::LEGA | Bug Busters Incorporated | Thu Feb 09 1989 13:58 | 22 |
| I recently installed an inwall steam radiator, its designed to fit
between studs... (18H*4Deep*12W).. its cast iron, grey color, and
throws good heat. Although it sounds like you have an indent, not
a full hole in your wall, this unit looks fine from all angles
so it could poke out a bit from inside the wall.
I picked mine up at the local plumbing supply house (the kind plumbers
go to) and it cost $70 new. any such store should be able to point
you in the right direction.. I looked in the hardware stores,
but they don't have any steam stuff.
Also, Check where your steam input is for the existing radiator
you have.. My unit was fed from the center bottom, not the side
like most old radiators ie:
-------
| |
| |
| |
|--|--|-<not here
|
^here
so make sure you can plumb it before you buy it.
|
85.218 | Forced Hot Air ? | NEBVAX::FRAZER | | Thu Feb 09 1989 15:42 | 6 |
| If you are looking for a register for a Forced Hot Air system, then
I suggest Reggio Registers in Ayer, Mass. I'm sure they're in the
book. BTW, I went to school with the Reggio family but haven't visited
their store in Ayer.
Regards, Jim Frazer.
|
85.219 | Braun's Fireside Emporium | IAMOK::SDANCAUSE | | Fri Feb 10 1989 14:51 | 8 |
| Another place you can call is Braun's Fireside Emporium in
Leominster. Last time I was there he had cast iron and brass
registers.
The size may be a problem, but he's been pretty good about special
orders and helping to locate things for me.
Steve
|
85.220 | Reggio's Registers! | ESPN::SIMMONS | | Tue Feb 14 1989 09:58 | 16 |
| Thanks for your replies. My heating system is a FHA Gas system.
The opening is in the floor, not in the wall. But, the register
needs to attach to the wall. The register does not need to produce
heat, just cover the opening.
As for the two places mentioned, I will check with Reggio Registers
first. This is the place I saw advertised in a magazine several
years ago but couldn't remember the name of it. Do you know where
they are located in Ayer? I have also heard a lot of good things
about Braun's Fireside Emporium Steve ... When we start on our family
room, I will definitely check them out for Woodstoves!
Thank you everyone for your quick response!
Joyce
|
85.12 | "funny" smell | DASXPS::LEVESQUE | The hardest thing to give is in. | Wed Mar 08 1989 13:42 | 18 |
| Our new FHA system creates an "oily" kind of smell from the ductwork
just after the furnace starts and before the blower fan comes on.
We had the heating contractor come out and make some adjustments,
but the smell persists.
He said the furnace wasn't running efficiently. Initially it was
installed and tested out during the real hot spell last August.
We really didn't have much cause to run it much prior to Nov/Dec.
Once the furnace/blower has been running a while, the smell goes
away.
Anyone have similar problems? Any suggestions on fixes or is this
normal?
Thanx for any/all replies.
Ted
|
85.13 | | TRITON::CONNELL | Down on Toidy-toid 'n Toid Avenue | Wed Mar 08 1989 14:26 | 14 |
| >< Note 47.12 by DASXPS::LEVESQUE "The hardest thing to give is in." >
> -< "funny" smell >-
What you're experiencing is pretty common with FHA. I believe what
is happening is when the furnace initially ignites, and the chimney is COLD,
the exhaust gases will "kick-back" into the chamber and drift into the duct
system. This only happens until the chimney warms and a draft is established.
The same thing occurs with any system (FHW, Steam) but it's more noticable
with FHA because the fumes have a more direct access to the living space via
the ducts. The colder the weather, the worse it is because it takes more
time and "effort" for the exhaust to move that big column of cold air out
of the chimney.
--Mike
|
85.14 | Please respond! | LIONEL::SAISI | | Wed Jul 19 1989 11:33 | 13 |
| I just had a new FHA furnace installed and when it comes on smoke
comes out of it. The guy who installed it said that this is because
the furnace is new and after it runs a couple of times this won't
happen anymore. Is this guy lying or what? The smoke doesn't smell
like gas or anything, it is more like a wood burning smell, although
there isn't any wood in there. I am a little concerned after reading
a few replies back, in that this is a Burnham furnace, and it is
vented out of a chimney running through the center of the house.
The previous furnace was one of those old cast iron jobs. Is this
a sign that the ventilation is inadequate or that the furnace was
improperly installed or is there any truth to what the guy told
me?
Linda
|
85.15 | Me too.... | GIAMEM::LAMPROS | Bill Lampros | Wed Jul 19 1989 11:56 | 8 |
|
Linda,
When I installed my new furnace I had the same problem. After
a few uses it disappeared. I also experienced this ( real bad )
on a heater/furnace on my Camper trailer when it was new. Same thing,
It disappeared after a few uses. I don't think you have a problem
but keep an eye on it...
Bill
|
85.16 | | LIONEL::SAISI | | Wed Jul 19 1989 12:14 | 4 |
| Thanks Bill for your quick response. I will let it run some this
weekend while I am around to monitor it. (and before the furnace
guy has a chance to leave the country!)
Linda
|
85.17 | Break In Period | OASS::B_RAMSEY | only in a Jeep... | Wed Jul 19 1989 15:21 | 3 |
| This is all the paint and "stuff" applied to the furnance during
making of the furnance. It will take a while for this stuff to
burn off.
|
85.18 | | BOSTON::SWIST | Jim Swist BXO 224-1699 | Thu Jul 20 1989 12:12 | 4 |
| Also note that FHA furnaces that have not been run for a while (like
all Summer) will give off a slight burning smell for a bit. Don't
know the exact cause but it's probably dust and other accumulated
crud burning away.
|
85.178 | supplier for hard-to-find shapes/sizes? | RAB::GLANTZ | Mike, DTN 381-1253 | Mon Jul 24 1989 17:39 | 6 |
| Can anyone recommend a supplier of ductwork of unusual shapes and
sizes? I need some 90-degree bends for 8x6.5" duct for a range hood
(both kinds of bend), and I'm hoping to avoid custom fabrication if
possible. Most of the home-improvement centers don't carry much in
this size. I also called the people listed in the Yellow Pages in my
area, and didn't get much help. Thanks very much for any info.
|
85.179 | | STROKR::DEHAHN | | Tue Jul 25 1989 09:26 | 8 |
|
I know it's a long drive from Nashua but Air Conditioning Supply on
Piedmont St. in Worcester should have everything you need. They are
very helpful and have no problem dealing with homeowners. There must
be someplace closer to you, though.
CdH
|
85.180 | thanks | VIA::GLANTZ | Mike, DTN 381-1253 | Tue Jul 25 1989 11:55 | 6 |
| Thanks for the recommendation. I don't mind going to Worcester too
much, since it's convenient on a Spag's run. However I just called
them and they don't carry 8x6.5 and said I'd probably have to get it
custom-made. I'll report back here if I locate anyone who stocks this
size. It's for a range hood, believe it or not -- should this
discussion be moved to that topic?
|
85.181 | More ductwork supply houses boston area | BAGELS::RIOPELLE | | Wed Jul 26 1989 17:46 | 17 |
|
Try Air Purchases in Burlington MA., or S.G. Torrice in Woburn
Ma.
If neither one of thes guys have that size you probably find it
anywhere else either.
Most of these places should have standard ducting for range hoods.
Is your range hood non standard or very old ?
Can you maybe use standard sizes that they offer ?
Or maybe are you extending or moving a duct that you need to match
?
|
85.182 | thanks again. no luck -- custom fab required | VIA::GLANTZ | Mike, DTN 381-1253 | Thu Jul 27 1989 10:42 | 15 |
| Thanks. I tried both places -- no luck. It will have to be custom
fabricated. I got one estimate of $50 per elbow so far, in case
anyone's interested. This is for 24 gauge galvanized steel (standard
for residential use -- 16 ga is required for commercial, according to
several of the shops I talked to). The hood is apparently non-standard
(it's brand new). The installation instructions which came with it
showed pictures of "typical ductwork available at any supplier of
sheet metal products". Ha. Maybe they're typical in Mississippi where
the hood is manufactured, but not in Mass. I have one last option:
call the manufacturer and ask for the name of a supplier. But I need
it in a week or two, so I think I'll just get it made locally.
Thanks to all those who answered. Just from the telephone
conversations I had with these people, they seem like folks you'd want
to do business with.
|
85.183 | | CHART::CBUSKY | | Thu Jul 27 1989 11:22 | 9 |
| > Thanks. I tried both places -- no luck. It will have to be custom
> fabricated. I got one estimate of $50 per elbow so far, in case
Why not have just ONE custom transition fitting made that will convert
your non-standard duct to a more readily available standard pieces.
Sommerville lumber has a decent selection of FHA ducts, elbows, and
transition fittings.
Charly
|
85.184 | exactly | VIA::GLANTZ | Mike, DTN 381-1253 | Thu Jul 27 1989 12:20 | 1 |
| In fact, that's just what I'm having done.
|
85.185 | Call the MFG for recomendations before custom work | BAGELS::RIOPELLE | | Fri Jul 28 1989 10:31 | 11 |
|
BE sure you call that range hood supplier and put them on the spot
let them know what you went through looking for duct work. And then
ask them where they would recommend the would get it. It might be
possible that they can direct you to a supply house that will for
a charge ship you what you need at a cost lower than being
customized. In any event don't let the manufacturer off th hook.
|
85.124 | how important is the cold air return? | TOOK::HUGHES | | Tue Aug 29 1989 17:50 | 12 |
| I have forced hot air fired by oil in my house. Part of the cellar
is finished, heat included. We had to take down the sheetrock because
the previous owners let it get all moldy. The walls are now sheetrocked
again. I just noticed that the sheetrocker covered up the cold air
return with sheetrock. How important is that return? The room is
fairly large, it has two grates in the ceiling where I assume the hot
air comes from (we haven't tested the heat in that room), and one
larger grate close to the floor (that I assume is the cold air return)
that is now covered up.
Linda
|
85.125 | Find and reopen the return duct | TRITON::FERREIRA | | Wed Aug 30 1989 08:12 | 9 |
| Let's assume the the original installer did his homework and a good job.
The system needs to be in balance, volume of air out = volume of air in....
that should have idealy been the case to begin with. This is a real
world and we don't always meet ideal goals. Secondly, having a return
in the same air helps circulate the warm air to give you a more unified
overall room temperature, fewer if any cold/hot spots, thereby fewer
apparent drafts. IMHO go for it. It's relatively easy to cut sheet rock
with a keyhole saw, and it doesn't have to be a saw specifically made for
sheet rock.
|
85.126 | Could it be your heat duct? | AKOV13::FULTZ | ED FULTZ | Wed Aug 30 1989 09:47 | 8 |
| One other thing to consider. Hot air rises and cold air falls. Would
this mean that the heating ducts would be on the floor level so that
the heat would filter up to the ceiling? If so, then it would seem
that your heat duct is covered, not your cold air return duct. I could
be wrong, but this is how I would think it would be set up.
Ed..
|
85.221 | Help, Can't paint sheet metal heat vent... | XCUSME::SUKIEL | | Wed Sep 27 1989 14:24 | 15 |
| I'm finishing my basement and have a problem!!! I have a heating
vent that runs horizontally across the ceiling. I've decide to
hang my suspended ceiling about half way down the vent leaving the
bottom portion exposed bu no matter what I do to paint it it keeps
bubbling up!! I've sanded the areas, wire brushed them, steel wooled
them and cleaned the area with TLP a heaving duty cleaner I got
from grossmans... my last attempt to patch up the areas that are
taking to Rustoleum White was to paint the areas with STAIN KILL.
This seemed to work a little but didn't do the job. Most of the
duct came out great with just two coats od spray rustoleum but a
few areas are really messing up the appearance of the rest... Can
anyone help me out??? I've also primed the areas with metal primer...
still bubbles up in some sections.... If nothing works, can I put
contact paper or something on it??? will the warmth of the vent
bother anything???? thanks for any help!!!!
|
85.222 | holes in the metal | MADMXX::GROVER | | Wed Sep 27 1989 17:04 | 13 |
| One question, might there be VERY small pin sized holes (pits) in
the sheet metal which would allow air to get under paint before
fully dry.
I had a similar problem when I did my basement. It turned out that
in the problem area, there were in fact two small pin sized holes
caused from oxidation(sp?).
I found it purely by accident, when I attempted to clean the metal
with full strength pine sole. The soap bubbled (when the heat came
on) around that area.
Get the magnifying glass out, you'll need it for this.!
|
85.223 | Primer? | MAMIE::COBB | | Wed Sep 27 1989 17:43 | 5 |
|
Have you tried using a metal primer on it before you paint it?
Chuck
|
85.224 | acid treat the metal | CSCMA::LEMIEUX | | Thu Sep 28 1989 10:02 | 9 |
| Hi,
If the sheet-metal duct is the galvanized type, you will have
to treat it with something before you paint it, some type of acid
if I remember right, maybe vinegar will do it. Try asking a commercial
paint distributor, such as a autobody supply store. I know that
some of the mid 70's Ford products had galvanized outer body parts.
Good luck!
|
85.225 | Try cleaning with turpentine (sp?) | EXPRES::CASEY | | Thu Sep 28 1989 13:12 | 6 |
|
Turpentine works. I know, when I was a grunt for a construction co.,
I wiped down hundreds of feet of the stuff before painting.
Be sure to wear rubber gloves, and just wipe it with a rag as if you
were cleaning it.
|
85.226 | painted ductwork | WFOV12::KULIG | | Fri Sep 29 1989 11:24 | 6 |
| Several years ago, they painted all of the galvanized ductwork
here in Westfield. It is now all peeling and falling off in
big chunks.
mike
|
85.227 | Thurmalox Stove Paint | BAGELS::RIOPELLE | | Fri Sep 29 1989 11:47 | 33 |
|
I had great experience with a product called THURMALOX STOVE PAINT
I've used it on an old cast iron stove that I acquired which made
it look new. I also used it on the the stove pipe that was attached
to the stove, lighlty sanded and cleaned. I've also used it on a
new woodstove that I bought that was stove black, with the paint
we changed it to warm brown to match our decor. It comes in many
colors, and in the case of a wood stove it hardens with the next
fire in the box. In any event I check the product label last night
and here's what is covers :
" for painting touching up woodstoves, stovepipes, fireplace hoods,
screens, and accessories, grates, barbeque qrills, heaters, furnaces,
engines, manifolds, mufflers "
" Won't blister, peel, or dicolor, with cherry red heat to 1200f"
The product is made by :
The Dampney Co.
85 Paris Street
Everett, Mass. 02149
They mail out, they also will mail out a color chart
As it says above it also works great on gas Grills, make them
look new, just clean all the grease off first and paint.
Hopes this helps some.
|
85.228 | High Heat paint | GIAMEM::RIDGE | | Mon Oct 02 1989 14:29 | 4 |
| They also sell engine paint in automotive stores. I used it on
motorcycle engines. Looks good and never peeled.
Steve
|
85.229 | thanks for all the thoughts!!!! | XCUSME::SUKIEL | | Tue Oct 03 1989 09:29 | 2 |
| thank you very much!!!! I'll check into it.....
|
85.230 | Oops! | WECARE::BAILEY | Corporate Sleuth | Thu Oct 05 1989 17:31 | 22 |
| Galvanized duct work isn't MEANT to be painted -- my Dad was in
the biz. Although you can treat the metal, I don't think you'll
ever be happy with it.
The only solution that suits me, aesthetically, is a lot more work
but looks the best. Build a cover. Since you have suspended ceilings,
you could build the cover of light plywood or something and paint
it with laytex to match your ceiling tiles. Contact paper might
stick, but it can bubble too and looks REALLY tacky when it does.
Also, if the heat is sufficient it scorches.
In those places (like the basement) where hiding the ducts was
impossible, we just lived with the raw metal. I sort of like the
appearance, myself!
Good luck!
(Oh, do check with paint dealers and/or sheet metal contractors
-- my perception of the situation is relatively dated, and they
might have new products now.)
Sherry
|
85.231 | Vinegar | GIAMEM::LAMPROS | Bill Lampros | Fri Oct 06 1989 13:11 | 6 |
|
Rub the sheet metal down with vinegar. wait 24 hours and paint
away. It works great with oil based or latex paint. The paint will
not peel or bubble. I've done it on many galvanized air ducts and
cabinets over the past 20 years.
Bill
|
85.331 | Wall creaking due to hot air | LANDO::RAYMOND | | Fri Dec 08 1989 11:06 | 15 |
| Please, I have read through all the notes on walls and all the notes on
hot water heating systems and couldn't find anything about my problem.
I am aware that I might have overlooked something but I don't believe
so.
Situation: We just converted our heating system from electric to FHW.
The problem is that where the pipe goes through one of the interior
walls I am getting a "clicking" sound. Sounds like dripping water but
it isn't. It is caused by the air inside the wall expanding and
pushing on the sheetrock causing it to slowly vibrate. I can repeat
the sound if I push on the sheetrock just above where the pipe goes
through the wall. What's the best way to fix this??? More sheetrock
screws??? Insulation??? What??
Thanks for your help.
Ric
|
85.332 | | VAXUUM::PELTZ | Perhaps if we build a giant badger... | Fri Dec 08 1989 14:53 | 21 |
| Ric
I have lived in many places with FHW heat and now own a house with FHW
heat. There is clicking every now and then when the metal pipes expand and
contract in every place I lived.
Perhaps the hot water pipe which is going through your wall may be rubbing? or
whatever agains the sheetrock or stud when the hot water expands the copper
pipe as opposed to the air in the wall getting hot.
If its just the pipes expanding this is probably normal. I personally do not
know of a way to stop the clicking if its just the pipes I would guess that
there is no way to do it. If its real loud and irritating then perhaps you
should inform the installers.
If it is rubbing or pushing on the sheet rock, perhaps you can carefully file a
slightly bigger opening in the sheetrock where the pipes enter the the wall.
Good luck in fixing your problem,
Chris
|
85.333 | Block the heat or vent it. | POLAR::MACDONALD | | Sat Dec 09 1989 11:44 | 16 |
| Assuming the piping is going through the wall from on room to the other
I would concur with .1, make the holes just slightly larger to allow
some breathing and prevent heat buildup. If that does not solve the
problem, try putting a larger sleeve over the FHW pipe that goes
through the wall and snug the sleeve to the edges of the hole to block
any heat from getting in between the walls. You can check this out by
using the cardboard core from a roll of paper towels, or toilet paper,
and put it in place for a few weeks. If it works, make a more perman-
ent fix by using a metal sleeve.
If the plumber has run the FHW pipe along, and inside, the length of
the wall, call him back and beat him about the head, or otherwise
vent the wall above the FHW pipe. In most homes less than say 20 years
old there will be firestops between the wall studs and venting cannot
be done from the top of the wall; you will have to find these firestops
(2x4 cross-pieces) and vent just below them.
|
85.334 | Pipes Need Clearance | WFOV11::TRUSTY | | Tue Dec 12 1989 19:21 | 6 |
| Have recently completed a kitchen renovation, and had the VERY
same problem, (clicking / dripping, etc).
The sub-flooring I put down was drilled too small for the sink
drain, and caused the same "noise". Removed the pipe, enlarged
the hole a bit, and no more noise.
Jim
|
85.335 | Ah, well, back to work | LANDO::RAYMOND | | Wed Dec 13 1989 11:28 | 3 |
| Thanks for the ideas. Now, where did I put that saw....time for a
little "wall surgery"!!!! Will let you know how it works.
Ric
|
85.187 | FHA system leaks water | CALCCO::CONDO | | Fri Jan 05 1990 12:26 | 13 |
| I have a Gas FHA high-efficiency model( Duomatic - Olson brand)
heating system in my home.
The problem I'm having is that the water collection system seems
to be backing up somewhere and overflowing inside the funace,
eventually getting to the floor. Has anyone had this problem with
water condensing heating systems? Any help would be appreciated.
I've checked the 1111 listing and did not find any reference to
this kind of problem.
Chris
|
85.188 | Check documentation, if it's still available | LYCEUM::CURTIS | Dick "Aristotle" Curtis | Sat Jan 06 1990 01:10 | 16 |
| This may be your problem, or be totally irrelevant; you should check
the documentation on your system.
I was perusing some literature on *humidifiers*, that indicated that
(for this manufacturer's kind, at least) they have an outlet that lets
water out of the system. One of the reasons why the more expensive
varieties were more expensive is that they have outlets which can be
plumbed into the drain used by central air conditioning apparatus;
the cheaper model, if I remember correctly, had a drip pan or some such
thing that required periodic monitoring.
At this time of year, you probably aren't running a *dehumidifier* (not
if you live in New England, anyway); one of those doing the entire
house would have a serious need for a plumbed drain, I would think.
Dick
|
85.189 | system is plumbed, and plugged I suspect | CALCCO::CONDO | | Mon Jan 08 1990 10:18 | 9 |
| This type of heater which I have, has various pipes running from
the heat transfer box down to other various pipes and then is pumped
out of my basement by a pump. It is in effect a dehumidifier.
I suspect not many people have such systems. I will probably try
tinkering with it myself this weekend, and then end up calling the
plumbing guy who installed it.
Chris
|
85.190 | | EUCLID::PETERSON | Panama has no Second Amendment | Mon Jan 08 1990 13:54 | 14 |
|
It de-humidifies the flue gasses. It sounds like one of the more
efficient models being offered. They glean so much heat from the
furnace, that the water vapor(that is a by product of combustion)
which in less efficient models goes up the flue, is condenced.
This "water" is VERY acidic, and will cause harm to any
(non-stainless) steel surfaces that it contacts. Call the furnace
guy to have it checked out. You could try checking the overflow
line to be sure that it's not kinked/clogged. In any rate, you should
get it checked a.s.a.p
CP
|
85.191 | similar problem | NSSG::ROSENBAUM | Rich Rosenbaum � � � � � � WA2AOI | Mon Jan 08 1990 14:14 | 6 |
| My Duomatic Olsen FHA (Oil) furnace sometimes overflows condensate during
the air conditioning season. The pipe to the condensate pump gets clogged.
Annoying.
__Rich
|
85.192 | Thanks for the warning | CALCCO::CONDO | | Wed Jan 10 1990 11:54 | 11 |
| I didn't realize that it was that acidic, I've called the guy, but
thanks for the warning.
BTW. The furnace has rating of about 97%. I have the same gas
bill for my 3 bed room garrison, as I did for my 2 bed room, interior
townhouse. The flue gasses are cool enough that they are pumped
out of the system via a PVC pipe. My house has no chiminey or roof
vent.
Chris, I'll report back on the needed repairs and cost when they
happen.
|
85.361 | Duct Sizing | MAMTS5::GHALSTEAD | | Fri Mar 09 1990 17:38 | 8 |
| To heat and cool a large one room addition on my house I plan
to exit off of existing main heat/AC trunk with another
trunk line to addition and then run my ducts off of that
to various locations around the room.
I know my system has extra capacity to handle this but
how do you determine size of trunk line, size of duct lines
and how many for the room.
|
85.362 | 1578, 2423, 2782 | BEING::WEISS | Trade freedom for security-lose both | Mon Mar 12 1990 08:36 | 18 |
| This note has been temporarily write-locked pending approval of the author.
To the author: This subject is already under discussion in this file, under the
topics listed in the title. Please look at these notes; you may find that your
question is already answered, or you may find a note where your question would
be an appropriate continuation of the discussion. Note that since nearly
everyone uses NEXT UNSEEN to read notes, your question will get the same
exposure whether it is a response to a two-year-old note or it is its own new
note. These topics were found using the keyword directory (note 1111), and you
may find other notes relating to this subject by examining the directory
yourself.
We do, however, welcome new notes if they explore a specific aspect of a
problem that may be under general discussion. And this moderator has been
known to make mistakes. :^) So if after examining these notes, you wish to
continue the discussion here, send me mail.
Paul [Moderator]
|
85.19 | What's that smell? | DCSVAX::COTE | Bain Dramaged | Mon Mar 19 1990 19:29 | 32 |
| Seems like a reasonable note...
My heat is FHA by propane. For years, when I first fire the furnace up
in the fall, the first blast of air out the registers was musty
smelling. Seemed reasonable....
I notice that if my furnace sits idle for even a day, the first
blast of air is musty smelling. Subsequent cycles smell OK. The odor
drifts out of the registers before the blower kicks in, and is gone
within seconds of the blower starting...
The furnace is fairly new, about 6 years old. The filter is changed
regularly.
I should add that this isn't something that started recently. It's done
this for a couple years, which tends to elliminate exhaust being vented
into the house. (Chances are I wouldn't be typing this if that was the
case!)
My father, whom I bought the house (with a different furnace) from,
knew exactly what smell I was talking about, as the old furnace would
do the same thing at the beginning of the season...
It smells 'musty' or even 'dusty' or stale. The cellar does tend to be
a bit damp, but nothing all that far out of the ordinary.
Would cleaning the duct work out possibly be of any value? I've never
done that. Any other suggestions?
Thanks,
Edd
|
85.127 | Heating the 2nd floor addition | ISLNDS::JULIEN | DTN 226-2736 | Fri Jul 06 1990 11:52 | 46 |
| Here is my problem: We are adding a second story to our tiny (28x32)
house. The house currently has FHA that has been very comfortable,
though I believe it is small (85000 BTUs? I am not sure). Because
of the difficult with heating the upstairs, we put in extra insulation
(6" in walls; 8" in ceilings). There are also four big windows
on the south-south-east side, and a central and open stairway to
allow heat to rise. But we think we should also extend the
ducting to the second floor. And here are the constraints;
THe furnace has a small box from which the heat ducks come. The
heat ducts are generally the small ones (4"?). Can we make a bigger
box? (It cannot be higher - goes to the ceiling already)
I think we can tuck ducts into closets, cupboards, etc, through
the first floor but they will not be placed right on the second
floor - which is a garison. Can you run the ducks horizontally
for a few feet? Where we need to cross joists, can we do that by
notching the joists?
If we can't duct horizontally or notch any joists, what about floor
vents? Are these flush with the floor or do they pose a tripping
hazard?
How important is the air return? what is the appropriate ratio
of number and size of return ducts to supply ducts? On the exitsing
house there are fewer returns than supplies, but they are bigger.
Would the first floor return ducks suffice for the whole house?
What about a discreetly placed floor vent to allow heat to rise into
the bathroom? Would this create problems with steam venting downstairs
from showers etc?
We have a big wood stove in the breezeway, that brings the breezeway
up to tropical temperatures but does little for the rest of the
house. Is it possible to shuttle the heat from that stove down
about 6 feet and across about 8 feet to furnace to link into the
furnace duct system? If so, are there battery/gas powered fans
to help heat when our power goes out?
Any ideas?
Thanks,
Sheila
|
85.128 | Yes, Yes, No, Yes | OASS::RAMSEY_B | Put the wet stuff on the red stuff | Fri Jul 06 1990 13:10 | 18 |
| So many questions! ;^)
Yes duct work can be run horizonitally. We live in a ranch and ALL
ducts are horizontal, almost no vertical.
Yes, you can change the box at the end of the furnance to allow you
addtional runs.
No, you should not notch the joists if possible. Maybe small notches,
not to exceed 2 inches deep. The joists hold up important things like
ceilings and floors and if you cut them, these things may collapse on
you.
Yes, you need returns if you can on the second floor. These take away
the cool air and help to recirculate that air in to the furnace.
Otherwise you keep "stuffing" more hot air in the rooms and don't give
the existing air anyplace to go.
|
85.129 | | COOKIE::HOE | Hi hoe, hi hoe, it's Sammy Hoe's we go! | Fri Jul 06 1990 13:59 | 17 |
| Perhaps it might be more economical to add a second furnace and
associated duct work so that you have a second heated zone so
that your upstairs rooms are not overheated. I noticed that
you're adding extra windows to help capture the sun's energy in
heat.
The alternative is to upgrade the exsisting furnace, then add the
ductwork to the second story. I also recommend that in the second
story, two return air ducts be used, a high, ceiling return duct
for summer air return and a low one for winter air return. In the
summer, the hot air rises to the ceiling so if you add A/C or
just turn on the fan to circulate the air, the hot air is drawn
into the furnace and added to the cooler air from the basement or
lower level. The lower air return is for winter so that you can
pull the cold air down to the furnace to heat.
cal
|
85.130 | second floor FHA
| AKOV13::LIBBY | | Fri Jul 06 1990 16:47 | 24 |
| Haveing added a second floor, I tend to disagree with some of the others.
You do not need return ducts on the second floor since cool air falls, but for
the system to be most efficient, the return duct on the first floor should be
at the foot of the stairs, and the doors in the upstairs rooms should be left
open.
What I have is 150K BTU FHA Propane gas heating the first floor, two big returns
(the returns = the size of the plentum opening is sq inches) and 4 hot air
registers. The first floor is over 1k sq ft of heated area.
On the second floor approx 800 sq ft, is two bedrooms and a bath, the bath has
back up elec heat (used about 4 times a winter, but quite often in the spring
and fall to kill the chill) and the door is left open, there are two bed rooms,
which I leave the doors closed, one room is 14 x 16, and takes about 2-3 hrs to
warm up, and the other is the master 16 x 26 with 20ft ceiling, this room takes
5-6 hrs to warm up, which is just right, go to bed cool, wake up warm.
Since heat rises, it's going to go up to the second floor, it is just a matter
of how fast, and how warm do you want it, if in doubt, add elec heat for back up,
but I think you will find that you won't use it.
Good luck
Les
|
85.232 | any mad scientists out there? | LEZAH::QUIRIY | Christine | Tue Aug 14 1990 17:37 | 11 |
|
Well this is sort of related! I want to make something out of ducting.
Someone at work told me to use vinegar first, if I want to paint the
duct-work, but what I was really wondering is, is there some (noxious)
chemical out there that will produce a really neat-looking effect when
applied to the galvanized steel?
If so, what is it and what is the effect? (How dangerous is it, what
precautions should I take, etc.)
CQ
|
85.233 | acids are great for etching metal | KAYAK::GROSSO | | Wed Aug 15 1990 17:06 | 16 |
|
Oh yes, get some muriatic acid from your local hardware store and pour
some of that on the metal. It will foam and give off noxious fumes and
take the finish right off the metal, leaving it a different color. Is
muriatic acid, a dilute hydrocloric acid? If it isn't I'm sure somebody
will jump all over this note to correct me. Let me save at least four
other replies by stating you should wear rubber gloves, protective or
at least dispensible clothing and work in a well ventilated area,
preferably outside. The other standards precautions of using acid also
apply, don't drink it, pour water into it, pour it in your nose, or
work with it around small children, or any desirable mammals for that
matter. By the way, its also great stuff for removing cement from
anything. It foams greens and dissolves it.
-Bob
|
85.234 | thanks | LYRIC::QUIRIY | Christine | Wed Aug 15 1990 22:19 | 10 |
|
Wow, I think I'll stick with the vinegar and the paint. I was hoping
for something a little less messy. (I really used noxious half-jokingly,
hoping against hope that something not-noxious would do the trick,
even though I figured that wouldn't be the case.)
However, I won't start my projecttill the weekend, so until then, I'm
still open to suggestions!
CQ
|
85.235 | | CLOSET::DUM::T_PARMENTER | Joe Dodo and the Groovers | Thu Aug 16 1990 10:29 | 1 |
| Webster's Ninth New Collegiate says muriatic acid is hydrochloric acid.
|
85.236 | | 25520::WELLCOME | Steve Wellcome (Maynard) | Mon Aug 20 1990 14:42 | 9 |
| "Muriatic acid" is just another name for hydrochloric acid. It is
usually low-purity grade, not laboratory-grade.
I don't know of any clever ways to treat galvanized metal to get
interesting effects. Zinc (what the galvanizing is) just looks
like zinc.
Best bet is probably to paint it; vinegar will etch the surface
enough so the paint will stick well.
|
85.237 | I used "stove paint" | CADSYS::HECTOR::RICHARDSON | | Mon Aug 20 1990 15:13 | 23 |
| High-temperature black "stove paint" sticks to galvanized metal ducts
OK - I decided several years ago to paint the woodstove's pipe to the
same color as the stove, and it sticks fine (we don't actually USE the
woodstove because Paul is so allergic to smoke: if we do use it, he
gets too much smoke if he goes out the door nearest the chimney,
depending on the wind direction. I just wanted the pipe to look better;
I didn't like the zinc color). My neighbor painted his woodstove's
outside "chimney" (galvanized metal; mine has a brick and stone
chimney) with normal house paint to match his house, and that did not
stick at all and is currently pretty messy-looking (I don't think the
current renters of that house use the woodstove, either) -- that was
latex exterior house paint (I helped him do the house), so don't try
that!
The previous owner covered since of the ceiling duct work in our house
with some kind of contact-paper stuff that matches the wall paneling to
make the ducts less obvious - this stuff sticks just fine also. Of
course, the ducts do not get very hot (especially compared to the
woodstove's pipe into the chimney) in the basement, since we normally
have the heat shut off down there.
/Charlotte
|
85.20 | Furnace proble, | TLE::ZANZERKIA | | Wed Nov 14 1990 10:00 | 33 |
| Hi,
I have a problem with the GAS-FHA system (Rheem brand).
Problem 1: Blower motor is very noisy.
Yesterday I took apart the blower and motor. It is a Westinghouse
1/4 HP directdrive(fan is mounted on the motor shaft) motor. After
taking apart the motor I saw cracked bushings ??(It's a plastic round
piece inside bearings.) One is good so I assembeled it back without one
plastic piece. There are two pieces on on each bearing.
This reduced the noise some what however I can see that I really
want to replace that other plastic piece.
Question: Where can I get this piece or do I have to get the whole new
motor ??
BIGGER PROBLEM:
I did the above work yesterday and today I have NO HEAT. Blower
does run though burners are creating problems. Few months ago I added
the digital thermostate(four stage setback) so I don't think the
thermostat is a problem. The thermostate does show ON and the temp.
reads 62. This turns on the blower motor and I can see the flames
coming on in the burner however after a short while flames go off and
blower continues.
I guess there is an internal thermostate that turns off the gas
valve..
Any ideas ?? Anything I can check or adjust ??
thank you in advance
Robert
|
85.21 | | FSDB46::FEINSMITH | | Wed Nov 14 1990 10:12 | 14 |
| I'd assume (usually a mistake), that the furnace has some way of
detecting that once the gas valve has opened, the gas has ignited. When
the heat exchanger gets hot enough, a sensor in the furnace then
turns on the fan. When the wall thermostat says "enough" the gas shuts
off, but the fan may run and use residual heat in the exchanger till it
cools off enough to shut the sensor off. How long does the gas stay on
when it lights? If it runs for a while (my FHA system in Texas often
has a comparitively short cycle), then perhaps the thermostat is
telling it to shut off too early. As a test, you could put the heat way
up ( say 80) to see if the gas stays on or its being shut off by some
internal problem at the furnace.
Eric
|
85.22 | found the problem | TLE::ZANZERKIA | | Wed Nov 14 1990 13:07 | 20 |
| .21
Thanks for the suggession. After I entered the note I read the
notes 605 & 1637 which explains the blower motor control and burner
control switch.
THis was an error on my part. Yesterday when I re-assembled the
blower I put it backwards, thus no air in the furnace which caused
the burner control switch to shut-off promptly. I was able to detect
this after observing the switch in action as explained in 605. What was
happening that wall thermostate was asking for more heat though
internal thermostate was stopping the burner, except it kept the blower
going as heat was very high in the furnace.
I re-did the blower and everything is fine now..
However I still have question is there an easy way to get the plastic
bushing in the bearing ?? If so where, I am in Nashua NH.
thanks
Robert
|
85.193 | Rewire FHA Blower for 3-speed | WYNTON::BMCWILLIAMS | Improvise if you have to ... | Tue Dec 11 1990 23:04 | 15 |
| How hard is it to rewire a FHA blower so that you can use all three speeds?
According to the wiring diagram, my Trane FHA electric furnace (w/ heat pump)
blower motor has three speeds (lo, med, high). As far as I can tell, it only
uses one of those speeds (high) when the furnace is running or if you manually
turn on the fan using the fan switch on the thermostat upstairs.
I'd like to be able to run the fan (alone) on low speed to pull heat out of the
basement that I'm generating via woodstove.
Can someone help me, an electrical motor novice, figure out how to DYI this
re-wiring project? The heating contractor I called said it would be $100 labor,
plus parts ...
Brian
|
85.194 | Need basement vents | SALEM::PAGLIARULO_G | | Wed Dec 12 1990 11:20 | 6 |
| Don't know how to rewire the motor but if you want to pull heat out of
the basement you will need to add, if not already present, intake vents in
the basement. Otherwise the fan will just circulate the ait from the
upstairs.
George
|
85.195 | It can be done quite easily | CSCMA::LEMIEUX | | Wed Dec 12 1990 11:50 | 27 |
|
Did you say it was a heat pump? If it is it probably runs on
the lowest or med low during the heating cycle and on high for the
cooling cycle. Just turning the fan switch to on, the one that is
on the thermostat may do it, it may already be wired for the same
speed that is used for the heating cycle which may not be low enough
for what you want to do.
If the above does not apply, you will need to add a relay with
a 24volt coil and contacts rated for at least 10 amps 120volts,
that has enough poles to break the other speeds and make the lowest
speed on the fan motor. Then you wire a "manual overide" switch
to the outside of burner that uses the control voltage available
in the furnace (24volts) to pull in the relay and turn on the lowest
fan speed. Keep in mind that this cuts out the highest fan speed
and could cause the exchanging coil in the plenum to frost up
during the cooling cycle if you forgot to turn the "manual" switch
back to the normal position.
The method I just described is the simplest one. I am sure there
are other more complicated means of doing this but without having
seen the wiring diagram for that particular unit I would only be
guessing on the method. If you need more details contact me off
line.
Paul
|
85.196 | | CLOSUS::HOE | Daddy, what's transision? | Wed Dec 19 1990 15:38 | 8 |
| < Note 4054.0 by WYNTON::BMCWILLIAMS "Improvise if you have to ..." >
Brian,
You can rewire the blower to run on high by running a wire from
the high-speed tap to the relay that turns on the fan (manually).
Be sure to put a wire nut on the wire that is the slow speed tap.
calvin
|
85.131 | HELP!! Registers on Ceiling?? | MR4DEC::DABELOW | David Abelow | Tue Feb 12 1991 08:21 | 18 |
| HELP!!! I need some input REALLY FAST!!!
The FHW radiant heat needs to be replaced in my slab ranch. The
decision to replace has been made. It will be done within the next 60
days.
I prefer to go with FHA (for many of the reasons listed in 49.*), but
I need to feel comfortable with the answer to one simple question:
Since it's a slab, the duct work must be run through the attic (...no
basement). This means that the registers will all be in the ceiling.
The contractor will have one large return register low in one wall near
the center of the house. Will the house be warm enough with the
registers up high?
Thanks
David
|
85.132 | | NOVA::ASCHNEIDER | Andy Schneider - DTN 264-5515 | Tue Feb 12 1991 09:54 | 22 |
| RE: FHA registers in ceiling
Our split entry has FHA, and the finished basement (1/2 cement wall)
has heat only in the ceiling and a cold air return in the middle
of the room. To put it bluntly - the room ain't anywhere near as
warm as the rest of the house. Now, it could be the fact that
it's a basement - but it's fully insulated, etc. The fact that
you're putting it on a slab may show some similarities. The problem
with our setup is that the warm air really never makes it down to
the ground except near the middle of the room (near the cold return).
In the corners of the room, it's fairly chilly.
If you really want FHA, I'd investigate the ability to drop perhaps
some surface-run ducts down some walls and have the air exit
near the bottom of the room. Perhaps even removing some sheetrock
between 2 studs to run ductwork down may be an option. But if you're
in the northeast, I'd try to find a way to get heat near the bottom of
the room.
good luck,
andy
|
85.133 | Wouldn't catch me doing that. | HYEND::C_DENOPOULOS | Men Are Pigs, And Proud Of It! | Tue Feb 12 1991 12:42 | 7 |
| My inlaws HAD ducts in the ceiling of their slab house. They ended up
going to electric baseboard. I guess from the warm ducts and the cold
attic, condensation would build up on the outside of the ducts and
completely soaked/ruined the ceiling sheetrock. After seeing their
problems, I would never do it.
Chris D.
|
85.134 | We've got FHA ducts in out second story, and it works great. | HDLITE::NEWMAN | Chuck Newman, 297-5499, MRO4-1/H16, Pole J13 | Tue Feb 12 1991 13:28 | 22 |
| When we moved into our house, only one upstairs room had heat. After our house
fire, we added a dormer upstairs and put in real heat. Our furnace is in the
basement and a big duct runs up to the attic where the hot air is distributed
to each of the three bedrooms and the bathroom from the ceiling. There are no
cold air returns upstairs.
I have to partially shut all the registers upstairs or it gets too warm up
there. I've not walked around with a thermometer, but the upstairs is
noticeably warmer than the downstairs (where the registers are in the floor,
and where the cold air returns are.
Of course, the ducting in the attic is insulated, but it lies on top of the
attic insulation.
re: .20 -- I don't understand where the condensation would come from. The only
thing that should be cooling down (and therefore subject to condensation) would
be the air in the ducts. But that air was originally room air, sucked up by the
cold air returns, heated, and sent out the hot air ducts. If it didn't
condense at room temp. and didn't have water added to it (e.g., by a furnace
humidifier), why would it condense in the hot air duct?
-- Chuck Newman
|
85.135 | | MOOV01::S_JOHNSON | D.B.Cooper's ground accomplice | Tue Feb 12 1991 14:07 | 11 |
| re <<< Note 1578.20 by HYEND::C_DENOPOULOS "Men Are Pigs, And Proud Of It!" >>>
> I guess from the warm ducts and the cold
> attic, condensation would build up on the outside of the ducts and
> completely soaked/ruined the ceiling sheetrock. After seeing their
> problems, I would never do it.
Don't tell me-----there was no insulation covering the ductwork, and the
attic was not vented----right?
Steve
|
85.136 | Ceiling fans will help, but... | SSDEVO::JACKSON | James P. Jackson | Tue Feb 12 1991 14:07 | 15 |
| My parent's house in Tucson is a ranch on a slab with combined
heating/cooling ducts. The source ducts are high on the wall over the door
(the ducts were routed through the hallway; the rooms had cathedral
ceilings). Each room had a cold air return that went through the slab.
Tucson is not known for its chilly winters, but I still found it too cold
at floor level. My bedroom was an add-on that didn't have a cold air
return, and I had to supplement with an electric heater.
I guess I would say "it depends": If any family members have arthritis or
other cold-sensitive conditions, the floor will seem extremely cold,
especially compared to slab radiant heat. On the other hand, you may find
that ceiling fans will distribute the warm air adequately (and you can use
the fans on those muggy summer days). Run the fans in reverse (blowing
"up") on low speed.
|
85.137 | Then I'll go with FHW!! | 21752::DABELOW | David Abelow | Wed Feb 13 1991 10:06 | 15 |
| Thanks for all the QUICK responses! You have all helped me make up my
mind NOT to proceed with the FHA with the ductwork in the attic and
registers in the ceiling. The main reason for changing the heating
system out is to get warmth back in the house !! :)
Although the FHW presents the problem of baseboard running around the
entire house, I like the idea of having three zones (as opposed to the
one zone that FHA would allow), of getting uniform heat (which the
prior replied indicated I might not get with FHA from the ceiling), and
the fact that with FHW I will not need a separate hot water heater (at
least not yet, anyway).
Thanks again!
David
|
85.138 | FHA CAN have multiple zones | STAR::DZIEDZIC | | Wed Feb 13 1991 14:17 | 12 |
| Re "one zone that FHA would allow":
You CAN get multiple zones with FHA. This is done via electro-
mechanical dampers in the ductwork. When a "zone" "calls for heat"
the furnace starts, the appropriate damper is opened, and heat
is sent only to the requesting zone.
There was a short article about this in one of the Globe's handyman's
columns this past weekend; you could send away for information on
zone control systems for FHA.
Just FYI.
|
85.139 | | HDLITE::NEWMAN | Chuck Newman, 297-5499, MRO4-1/H16, Pole J13 | Wed Feb 13 1991 16:17 | 13 |
| re: .25 -- Must have been the same article that was in the Worcester Telegram &
Gazette.
Also, note that Jim Jackson's Tuscon home (.23) was on a slab (read: cold floor)
with cathedral ceilings. That's very different from a second floor (read: warm
floor) with regular height ceilings -- what I have in my house and what I
suspect you have in yours.
Not trying to set your mind one way or another. I personally *love* hanging out
over the FHA ducts in our first floor, but do what you feel best with. I'm sure
either FHA or FHW would work fine.
-- Chuck Newman
|
85.140 | | HYEND::C_DENOPOULOS | Men Are Pigs, And Proud Of It! | Thu Feb 14 1991 12:32 | 8 |
| My father in law has a ridgevent on his roof. I tend to think now that
maybe the condensation happens because instead of a normal furnace, he
has a heat exchanger outside. Maybe that has something to do with it.
As far as the ductwork being insulated, I don't know, but knowing my
F-i-l and his brother that did most of the work, I wouldn't be
surprised if it wasn't insulated.
Chris D.
|
85.141 | He *is* on a slab | SSDEVO::JACKSON | James P. Jackson | Thu Feb 14 1991 13:35 | 9 |
| Re: .26
In .18, David Abelow stated that he had a "slab ranch", i.e. cold floors.
Also, "cathedral ceilings" on my parents' house is perhaps misleading: roofs
in Tucson are about 6 - 10% pitch (no snow load), so a cathedral ceiling is
8 feet at the outer wall, and 10 feet at the inner wall. This is
essentially the same as a flat ceiling with a ceiling duct.
I think he's made the right decision to go with FHW.
|
85.142 | Oops -- I was looking at .0, not .18 | HDLITE::NEWMAN | Chuck Newman, 297-5499, MRO4-1/H16, Pole J13 | Fri Feb 15 1991 10:25 | 4 |
| It's great having related conversations all together in one place. I forgot
that this conversation started with not .18, not .0 -- two different houses.
-- Chuck Newman
|
85.186 | "Measure twice, cut once" and all that... | LYCEUM::CURTIS | Christos voskrese iz mertvych! | Tue Apr 16 1991 11:49 | 8 |
| Getting back to a facet of the base note:
How do you determine what effect one or more new ducts will have on the
balancing of the system? I'm looking at adding some ducts to heat
portions of the cellar, and want to have some idea of what I'm doing
before I start hacking things.
Dick
|
85.336 | Fiberglass ductwork | SUBWAY::PIZZELANTI | | Fri May 10 1991 17:23 | 17 |
| Has anyone used the new Fiberglass venting/ductwork in their homes? I ve heard lots
about it, but no real practical experiences. Some concerns I have about it are would the
ducts release shards of fiberglass over time? Considering high temps from an errant furnace
could the ducts burn? dust buildup? and so on...
Some practical applications for this would be: over range hood ( restaurant style with high
CFM change_); bath vents and finally regular ductwork. I would like to consider this as it
is supposedly cheaper without any loss of heat , no drawbacks etc. Another consideration that
some people may have experienced ( especially those with newer, tighter houses) is the
way heat/cold tends to coagulate in high/low areas in winter/summer. The optimum design
calls for delivery of a/c through high vents and delivery of heat through floor or low
registers. Is there a way to do this while minimizing duct-runs? ( automatic ) what about
return vents in such a system. Looking for a design/system that provides an optimum return.
( in various ways...;)
I d like some practical experiences - I ve spoken with several contractors, and of course all
you get is the general "Yeah I can do that - no problem" as long as they get the business.
thanks for all replies.
Frank
|
85.337 | | QUARK::LIONEL | Free advice is worth every cent | Fri May 10 1991 18:11 | 5 |
| My previous home had fiberglas ducts. I never noticed any problem with
them, other than a tendency for the joints to come apart if not secured
tightly.
Steve
|
85.338 | DUCTS AND MORE DUCTS | SUBWAY::PIZZELANTI | | Fri May 10 1991 18:36 | 11 |
| >...tendency for the joints to come apart if not secured
>tightly.
Ok. I'll bite. how do you keep them secure? brackets?
I would guess that would rip the stuff; Crazy glue duct tape?
It would be too bad if you were putting up pictures and a
nail( or pix hanger ) ripped the duct...;-)
Steve, if you did this yourself, what was the cost?
regards,
frank
|
85.339 | Same question... | TLE::G::MORRIS | Greg Morris | Fri May 10 1991 20:16 | 53 |
| Hi!
re .0:
I've been trying (and failing) to build a house for some time now, and the
choice between fiberglass or metal ductwork has been one of the issue I've
found hard to decide. I did not get the "I'll do anything you want" from
the contractors I've talked to, some favor it, and others hate it.
Quickly, this is what I've heard:
Advantages:
Much quieter.
Less expensive.
Self insulating.
Disadvantages:
Fiberglass emitted into home air?
One GC told me he had to replace all the ductwork in a home
because the owner became allergic to the fiberglass.
A heating contractor told me if fibers are emitted it is due
to poor design and installation of the particular heating system.
He said that the fiberglass ducts are fine when properly installed.
He did confirm if the ducts are over pressured, the fiberglass will
erode. He told me he saw one system where only the outer foil
was left.
Ducts are fragile.
I heard about attic ducts having to be replaced after being sat
on and stepped on.
Mold growth?
I asked a heating contractor that proposed metal ducts about
fiberglass ducts and he mumbled about there would be changes to
them soon due to problems with mold growth.
Cleaning?
Some other notes in this conference talk about having your ducts
cleaned after a zillion years of dust have built up in them.
Seemed to me like it would be hard to drag any sort of brush
through these ducts to extract the dust without taking a chance
on ripping them up. I asked a heating contractor about this and
he said they just spray disinfectant in the ducts when they get
dirty.
At this point I'd probably go with metal ducts. What have other people
heard/experienced?
Greg
|
85.340 | No complaints | STAR::DZIEDZIC | | Mon May 13 1991 08:53 | 25 |
| Re .0:
Fiberglass is considered non-flammable so I wouldn't worry about
the ducts burning up unless the furnace got so hot it started the
rest of the house on fire.
I wouldn't use the fiberglass ductwork for venting grease or moisture
(in both cases the exhaust products would build up on the interior of
the fiberglass ductwork; in the former case you'd have a ready recipe
for a nasty fire - the grease could eventually catch fire).
The fiberglass ductwork is rated at R4.3. It is somewhat sturdy but
will of course crush if you run into it or step on it.
As for fibers being dislodged, that's interesting. Our ductwork has
what appears to be a "binder" mixed in with the fibers so it would
seem not to be a problem. (I had to cut into the ductwork to add a
few tap-offs; the stuff was pretty stiff.) Perhaps during the first
few months any left-overs from manufacturing and installation would
be dislodged.
It is definitely quieter than metal ductwork.
We have no complaints after a year's use.
|
85.341 | Ducts, and system design | SUBWAY::PIZZELANTI | | Mon May 13 1991 11:20 | 10 |
| Thanks for the replies... Has anyone done anything with HVAC design -
ie. high/low registers, etc., as mentioned in the base note? One comment
that I ve read over the weekend - the ridges in ducts impede airflow. So do
elbows and turns. At the risk of this becoming a rathole note, Elbows for range
ventilation( including downdrafts ) slow the effective airflow by 7CFM. every
20' is another 6CFM "wasted". I m certain the same principles would hold for
FHA; decreased temps would result at the register. Taking this into account
a central location for the furnace would be ideal. Barring this ( long stacks )
if its in the middle but towards the center there might be a noticable
improvement in system performance.
|
85.342 | | QUARK::LIONEL | Free advice is worth every cent | Mon May 13 1991 12:47 | 13 |
| Re: .2
I didn't install the ducts - they were put in when the house was built in
1985. The problem I had was where the duct had an elbow to go up to
a vent, and wasn't properly supported. The connection between the two
pieces came apart and started leaking air into the basement. The joints
appeared to be sealed with something like duct tape, and that should work
quite well. As long as the ducts are properly supported, and there isn't
any twisting pressure on joints, they should work fine. They will lose
less energy than metal ducts and will be quieter. They can also withstand
a small bit of crushing to fit in tight spaces.
Steve
|
85.343 | no conplaints | 37339::GHALSTEAD | | Mon May 13 1991 16:14 | 12 |
| Don't forget most air handler fans have at least 3 blowing speeds. I assume
this is to help fit in different configurations, ie. size of duct,
length of run etc., position of air handler within the duct
configuration.
I like my fiberglass ducts, because I hooked up a woodburning furnace
into the system and it was easy to "cut and splice" it into the
existing system. I also did an addition and again adding a main trunk
line addition was easy, oh yeah, I also installed a humidifier, cutting
the duct was easy. When I cut into 5 year old fiber duct there was
no trace of any mold, it was a little dusty.
|
85.344 | | KAHALA::FULTZ | ED FULTZ | Tue May 14 1991 13:10 | 6 |
| How about a semi-compromise? Use the metal ducts for their advantages, and
wrap the ducts with fiberglass insulation. I realize this would be more
expensive, but it seems you would get the best of both worlds. How much more
expensive would it be? I couldn't tell you.
Ed..
|
85.345 | | CIMNET::LUNGER | H 2... ��WHOA!! | Tue May 14 1991 15:22 | 13 |
| We did a DIY home heating system with this stuff. Worked out real well.
I still have the special tools required to form the ducts out of the
sheet ductboard which I might be able to part with...
We used an aluminum plenum chamber to start things off (too big to deal
with ductboard... just gave the dimensions and had someone else in a shop
do it), and aluminum for one large return duct. Everything else was
the fiberglass insulated ductboard. Joints were sealed with this iron-on
tape with blue dots. When enough heat was applied, the dots turned black.
Its been about 5 years now... no major problems with molds, dust or
fiberglass. Its basically a very responsive, silent heating system.
|
85.346 | Good stuff | SSDEVO::JACKSON | James P. Jackson | Tue May 14 1991 17:41 | 8 |
| I helped my dad put in some fiberglass ductwork in his house about 20 years
ago. I lived in one of the bedrooms served by the new duct for about 6
years, and never noticed any fiberglass or any other problems. No problems
after 20 years.
It was a piece of cake to put in - a magic tool that cut a groove that you
folded into a corner, and some metallic duct tape to hold it all together.
Just make sure that you support it adequately.
|
85.363 | Foam/washable filters vs conventional/throw-away filters | TLE::REAGAN | Sharp tools for sharp programmers | Fri Sep 27 1991 15:47 | 7 |
| I currently have a washable foam filter on my FHA furnace/AC.
I'd like to switch to a normal throw-away filter type. However,
on the edge of the foam filter is a warning about high-volume
air flow and it warns not to use conventional filters. Should
I listen to this warning or is it just a lot of hot air :-)
-John
|
85.364 | 2c worth.. | ELWOOD::DYMON | | Tue Oct 01 1991 07:32 | 10 |
|
.....It must be there for a reason........
There might be a "throw-away" filter you can use but it may
not be the one you buy in the HW store. I would call someone
who does this for a living......
JD
|
85.78 | current recommendations? | TNPUBS::STEINHART | | Mon Dec 02 1991 10:33 | 11 |
| Because technology changes, and I am in the market for a unit:
Can anyone recommend a brand, model, dealer?
We had a drum type unit that died an early death.
Located in southern New Hampshire. We have an oil burner and forced
hot air with insulated metal ducts.
Thanks,
Laura
|
85.79 | | QUARK::LIONEL | Free advice is worth every cent | Mon Dec 02 1991 12:11 | 6 |
| I liked the Sears model I installed in my last house. It has a drum but
does not place any parts inside the furnace duct, relying on a fan to draw
air into the unit and back into the duct. It was inexpensive (I paid about
$130 on sale) and I could install it myself.
Steve
|
85.328 | which way to aim them? | OASS::BURDEN_D | He's no fun, he fell right over | Fri Jan 03 1992 20:34 | 15 |
| All the ceiling registers in our house (and all the other houses in our
subdivision) have the air aimed at the outside walls. The registers are
between 1' and 2' from the outside walls and some are right in front of
windows. Because of this, some of them ended up blowing all the hot air
(or cold air, depending on the season) on top of a wall unit or the kitchen
cabinets.
I went around and rotated them all 180 degrees so they aim in towards the
middle of the rooms. It seems to circulate the heat better and we certainly
feel the heat more when it comes on.
Why would the builder aim them all at the wall? Did I do something wrong
or doesn't it really matter?
Dave
|
85.329 | | RAMBLR::MORONEY | Is the electric chair UL approved? | Fri Jan 03 1992 22:24 | 12 |
| The major area of heat loss (other than the roof) is the walls, especially
the windows. There is no heat loss at the center of a room or interior
walls. If the heat is applied to the interior of the house, you'll get
hot spots and cool spots, and it will tend to be drafty. If the heat
is applied along the outside walls the whole house will tend to be evenly
heated throughout.
I know from experience, my house had its air vents along interior walls
and it was drafty. It now has FHW along outside walls and is much better
in this regard.
-Mike
|
85.330 | So long as you don't freeze the plumbing, do whatever you like | KAYAK::GROSSO | Prevent & Prepare or Repent & Repair | Wed Jan 08 1992 12:21 | 17 |
| You balance cost and comfort. You didn't do anything "wrong" per se. Beyond
comfort, I believe the only real concern is to keep plumbing from freezing.
Just check that you didn't create a cold wall that might have plumbing in it
running up to a bathroom upstairs. (Not likely but in an old house, anything
is possible)
One winter we elected to keep the house at 52 and saved a lot of money, and no
we weren't comfortable unless we were heavily dressed or under quilts. If you
can afford to keep the house heated to the level where you are most
comfortable, then you decide what comfortable is and aim the registers anywhere
you want. I agree with -.1 that you'll get more even heat by heating the
external portions of the room, but in theory, that should also cost more money
as heat loss is proportional to the differential temperature. If you sit in
the middle of the room, heat the middle and you'll lose less heat than you would
if the walls were warmer.
-Bob
|
85.143 | How to run FHA duct under porch? | KRULES::FORSBERG | LENaC Product Development | Fri Sep 25 1992 13:56 | 44 |
| I have just added a three-season sunporch to my house and would now like to
add heat to it. The house has forced hot air (FHA) heat. Fortuitously,
there is an FHA duct currently _exactly_ where I'd like it to be. It ends
under the sliding door (to the new porch) and is currently capped.
I would like to extend this duct and run it out to the far edge of the
porch (15 feet) and bring it up to a floor register. My question is: how
best to go from under the house to under the porch?
As seen below in the ASCII diagram, the joists kind of line up. As viewed
from above, there is distance of about 10" common to the box that the duct
is now in and the box in which I'd like to continue it. The present duct
is 7" dia. round so from a top view there should be no problem.
But my band joist is a 2x8, I think. If I cut a 7"+ diameter hole in it,
there won't be much wood left over. Maybe the answer is to go to a
rectangular duct at the band joist and continue it rectangularly for the
15' under the porch.
Suggestions? Do the adapters which I'm considering exist off-the-shelf? or
will I need custom ductwork to do this?
Thanks for any advice.
Erik
[ TOP VIEW ]
|<------------ 16" ------------>|
|<------ 10" ------>|
| | | |
| | want to continue | |
| | duct out here | | (porch joists)
| | | |
--------------+--+----------------------------+--+-----
B A N D J O I S T
-----+--+----------------------------+--+--------------
| | | |
| | existing 7" duct | | (house joists)
| | between these joists | |
| | | |
|<------------ 16" ------------>|
|
85.144 | some suggestions | AKOCOA::CWALTERS | | Mon Sep 28 1992 10:54 | 37 |
|
There shouldn't be a problem with connecting the ducts - you can get
angles or flexible ducts to negotiate any direction changes. Even with
a rectangular box, you would have to cut away a lot of the band joist
to get through. I'm not sure, but that may cause more problems and
could be against code.
Is there any way you can go across a few feet, up the main house wall
and across the porch ceiling to a central down vent? The other
things you have to consider are; insulating the duct - what's under the
porch? and how the air flows back to the return registers to the
furnace. If you close the porch door, the air cannot recirculate
so you will have a problem balancing the temperature
How about something like this:
to ceiling down vent
^ +--+
" | door to porch
" | |
" | | [] <-return vent from porch
" ---+--+------
"=====[] <-existing duct
This would also give you an opportunity to install a vent baffle,
so you can close off the duct to the porch or balance the airflow.
An alternative could be just to take a short route, across, up a few
inches and put a register straight through the wall. Then install
a circulating fan to distribute the warm air. This may even be
more energy efficient if the porch has a high ceiling.
Regards,
Colin
|
85.200 | FHA furnace size ? | MAST::HILL | | Mon Oct 26 1992 18:41 | 10 |
| I have converted a screen porch into a sun room and want to add heat from
the existing house furnace. Also I have a bedroom that is not currently
heated that I would like to hook up too.
The system is gas heated FHA.
My question is, how do I calculate what size of furnace is required (ie is
my current furnace big enough)??
Paul
|
85.201 | on the spec sheet | DUSTER::MCDONOUGH | | Tue Oct 27 1992 09:22 | 7 |
| When we bought our new FHA furnace last Dec, we just told the salesman
the number of rooms we needed to heat and the total square footage.
One of the spec on the furnace spec sheet is the square footage it can
heat. If you dont have the spec sheet for your current furnace, the
manufacturer can give you this information.
Rhonda
|
85.202 | 22% more heating space to handle @9' | SENIOR::HAMBURGER | Life is a Do_It_Yourself project! | Wed Oct 28 1992 15:34 | 14 |
|
> When we bought our new FHA furnace last Dec, we just told the salesman
> the number of rooms we needed to heat and the total square footage.
> One of the spec on the furnace spec sheet is the square footage it can
> heat. If you dont have the spec sheet for your current furnace, the
> manufacturer can give you this information.
Um....not having FHA, but doesn't the ceiling height have something to
do with the capacity as well. 9' ceilings will take longer than 7' ceiling
rooms I would guess.....Maybe cubic feet is what you need to figure?
Vic
PS: This note is no longer write-locked at request of the author.
|
85.203 | | VMSDEV::HAMMOND | Charlie Hammond -- ZKO3-04/S23 -- dtn 381-2684 | Wed Oct 28 1992 16:02 | 7 |
| It also makes a difference whether the house is well inulated and
has good, tight windows and doors.
If you compare a house with wall insullation the R30s and triple
pain, draft free windows to one with R13 and drafty, single pain
windows you'll find that the second house requirs a furnace with
literally 2 to 3 times more capacity.
|
85.23 | FHA furnace not working | MIASYS::CURRIER | Matt DTN 285-3820 | Wed Nov 04 1992 09:13 | 28 |
|
Hi,
My FHA furnace is not working. The brand name of the furnace is HEIL
and it is 3 yrs old.
The problem is that when it is turned on, it just makes a humming noise,
as if something is stuck. After awhile, it shuts off. Pressing the
primary reset button on the motor does not help. It only brings it
back to the humming condition.
Background:
About a month ago, the furnace stopped working. I pressed the reset button
and it started working again (until 2 nights ago!). Also, don't know if
this is related but lately I have noticed a delay of a few seconds
between when the furnace turns on and when the oil ignites.
I've tried:
- changed oil and air filters
- took out the firing head and cleaned
- checked electrical wiring to the furnace
Anyone have any ideas? This unit is only 3 years old!
Thanks,
Matt
|
85.24 | | VERGA::WELLCOME | Steve Wellcome PKO3-1/D30 | Wed Nov 04 1992 10:36 | 7 |
| May be a weak transformer so you're not getting enough spark.
May be a clogged nozzle; is there oil in the bottom of the
combustion chamber? If not, after pushing the reset with no
ignition, you're probably not getting oil through.
Can you tell if the motor that drives the oil pump is working?
|
85.25 | | RAMBLR::MORONEY | Is the electric chair UL approved? | Wed Nov 04 1992 12:34 | 14 |
| re .23:
Where is this button you are pushing? On the burner motor or on a control
box? If the motor, it's likely a thermal circuit breaker and it sounds
like the motor is jammed somehow or something. This would give a humming
sound like you describe.
There is also a safety cutout. A sensor detects if there is a flame in
the burner within a certain time, if not it will cut it off.
Reasons for no flame? Bad ignition transformer, oil pump lost its prime
(did you run out of oil?) for some.
-Mike
|
85.26 | ex | VICKI::CURRIER | Matt DTN 285-3820 | Wed Nov 04 1992 13:24 | 28 |
|
Hi
Thanks for the quick responses!!
re: .24:
When I had the firing head out, I verified that the nozzle is not
clogged. I put pressure on the input end and saw oil come out...
How do I check if there is oil in the combustion chamber?
It doesn't seem that the motor is working at all. Is there only one
motor? While I had the firing head out (under the transformer), I made
sure that the air fan was able to freely spin. I thought the motor was
jammed. I assume this fan is driven by the motor...
re: 25:
I tried both reset buttons. If it is the safety cutout you mention,
is there a special way to reset this. I also made sure I have oil in
the tank. This furnace is a 2-way system. Excess oil is pumped back
to the tank. My manual says a 2-way system doesn't need to be primed.
Is there a simple way to test for a bad transformer? (btw, I have a
multimeter) Also, is there a way to verify the motor is shot.
Thanks
Matt
|
85.27 | | RAMBLR::MORONEY | Is the electric chair UL approved? | Wed Nov 04 1992 14:41 | 20 |
| The safety cutout is reset by waiting a couple minutes from the time it
trips and pressing the button. Don't do this more than a couple times
without waiting an extended period, as oil fumes in the combustion chamber
can build up and go boom. The safety cutout exists to prevent this from
happening.
I'd reset both switches, try running the furnace and see which one trips.
Does the furnace blower spray oil? If not, 1) the motor is seized, 2)
Nozzle is plugged or 3) blower is not getting oil (out of oil, plugged line/
filter, no prime (I'm not familiar with the 2 line system, can't verify if
it needs prime or not)) Does it blow air? Does it sound "normal" except
for the sound of burning oil?
The transformer should draw a definite arc across the ignition electrodes.
Thes electrodes sometimes burn back or get rounded off, they can be adjusted
or replaced. Don't try to test it with a voltmeter not designed to test
thousands of volts, you'll damage it and likely seriously shock yourself.
-Mike
|
85.28 | simple tests... | BUSY::CLEMENT | Smells like Nirvana | Wed Nov 04 1992 15:01 | 37 |
| I'm no expert...
I'm also not familiar with a 2 line system. But you could do a couple
of easy things to make sure it is primed and the pump is working.
Shut off the electrical switch to the heating system.
Place a bucket under the oil filter (next to the tank), there should
be a bleed screw on top of the filter (screw is in the bolt that
tightens the filter housing). Loosen the screw. If air is coming out
of this screw, you have air in the line. Leave the screw loose until
oil starts coming out, let the oil come out until all the little air
bubbles go away. Then tighten down the screw.
If you had air in the line. Turn switch back on and try the system
again.
If it still does not work. Prime the line by the pump motor. There
should be a nozzle on the motor that you can attach a hose to. Place
other end of hose in a jar. Turn on heating system, back off on the
nozzle nut (just slightly). You should see or hear air or oil coming
out of the hose. IF there is air (you have air in the line), if there
is foam (you have air in the line). Let the pump work all the air out.
When there is only oil coming thru the hose (no air or foam) tighten
the nut. Oil will now go to the nozzle and should startup the furnace.
This entire process (depending on how much air is in the line) should
take under 30 seconds.
If there is anything coming out of the hose (including air) I would
think that the burner motor (the pump) is working. (Fellow DIY's
correct me if I am wrong). If nothing is coming out of there then
there is a problem with the pump.
If the line is primed, and the pump is working. I would check out the
transformer... An area I have yet to get familiar with...
Good luck, Mark
|
85.29 | like bleeding brakes | KOLFAX::WHITMAN | Acid Rain Burns my Bass | Thu Nov 05 1992 10:26 | 15 |
| < Place a bucket under the oil filter (next to the tank), there should
< be a bleed screw on top of the filter (screw is in the bolt that
< tightens the filter housing). Loosen the screw. If air is coming out
< of this screw, you have air in the line. Leave the screw loose until
< oil starts coming out, let the oil come out until all the little air
< bubbles go away. Then tighten down the screw.
When I had a oil fired FHW system, my "bleed screw" was on the pump, at the
burner end of the line, not on the filter at the tank (supply) end of the line.
The process was just like bleeding brakes on a car.
Considering we are literally playing with fire here, I am not about to
suggest anyone DIY... if you don't know what you're doing, get a pro.
Al
|
85.30 | How about the blower motor? | RESYNC::D_SMITH | | Thu Nov 05 1992 13:21 | 15 |
| Are you sure at least the blower motor is working? Usually there is an
internal themostat that checks chamber temp. in gas heating system. May
also be true for a oil fired FHA.
When the chamber hits the 135 degree mark or so, then the blower kicks in.
to exhaust the heat in the chamber.
If the chamber is already at that temp, when you turn the heat on,
the blower will attempt to kick in, and if the motor is bad, the
breaker will trip.
Check the blower in addition to the other checks mentioned. You should
be able to at least eliminate possibilities and help a certified
tech. quickly isolate the problem and save some $$$.
Dave'
|
85.238 | NOISY forced hot air heat. Help! | GEMVAX::ROSS | | Tue Nov 10 1992 13:30 | 20 |
| Our house has oil heat, with forced-hot air. What an
experience!
It's so NOISY that we can hear the noise on the second floor of
the house.
Part of the living room floor actually VIBRATES when the furnace
comes on (the living room has a hardwood floor).
Is this common? It's really awful to live with. The house is 38
years old, and the furnace is new. There's no insulation in the
basement. (It's debatable how much insulation is in the rest of
the house too.)
Any solutions???
Thanks.
Gale
|
85.262 | DIRTY forced hot air heat | GEMVAX::ROSS | | Tue Nov 10 1992 13:40 | 17 |
| I discovered that when people say forced-hot air heat with oil is
DIRTY, they're right!
We change the filter on the furnace each month. This week-end
we removed the heating grates from each room and vacuumed the areas.
Are there any other kinds of filters (or something else) you can use
to prevent dirt from entering the rooms. For example, can you put
a filter behind each grate?
Any other dirt-eliminating suggestion? (I'm really not obsessed
with cleanliness, but our house gets filthy.)
Thanks.
Gale
|
85.31 | Just like a car, check the spark gap! | SMURF::DIBBLE | RECYCLE - do it now, or pay later! | Tue Nov 10 1992 15:04 | 13 |
| I've had this same problem.
Check the gap of the electrodes. If you have the paperwork for the
furnace gun, then look up the proper specs for the location and
gap of the electrodes. This may fix the problem.
BTW - be careful when you finally relight the furnace. Everytime you
tried to start it you put oil into it. Now there is a lot of oil
around and it make surprise you with the, um, exuberance of it's
starting.
BLD
|
85.239 | | SENIOR::HAMBURGER | Life is a Do_It_Yourself project! | Mon Nov 16 1992 21:29 | 8 |
|
I have set this note to write mode again. Note 4056 addresses noise
in FHA systems as well but have at it...
Vic
|
85.263 | | SENIOR::HAMBURGER | Life is a Do_It_Yourself project! | Mon Nov 16 1992 21:32 | 6 |
|
Note 4056 discusses filters at the grates.
I have set this note to write again to continue the discussion.
Vic
|
85.240 | ducts vibrating against the floor? | SMURF::WALTERS | | Tue Nov 17 1992 09:15 | 12 |
|
As it's a recent installation, perhaps you should get the installer to
check that the fan is OK first. If that checks out, try finding where
it is vibrating by pressing on the ductwork above and around the
furnace (may be hot!) to see if that reduces the vibration. If you can
find a bad spot, it may be possible to adjust the duct brackets or
wedge a bit of non-combustible material (scrap of sheetrock ect.)
between the duct and the floor. Getting the ducts insulated might help
too.
Colin
|
85.241 | | TNPUBS::MACKONIS | We are a compromise of nature! | Tue Nov 17 1992 12:38 | 23 |
| I am having the same problems with noise and also with air being returned from
the furnace. The heating contractors -- who I have littel faith in, are coming
over tomorrow morning after the 5th phone call to "review" the problem.
The noise that comes out of the ducting is phenomenal. The worst part is that
the return starts at the same time the blower is going, and this is all in the
;living room -- you can not watch TV. When the noise starts it is as if the
TV is on mute, if you turn up the volume when the blowers go off you are
blasted out of the room. I HATE it!!!!!!
The heating contractors told me to cover up the air return to see if that would
stop the frequent cycling and perhaps ;cut down the noise. Well, I covered up
most of it but now when the air return shuts down the sheet metal clanks so
loud it starts the dogs barking. I don't know what is worse.
This is a new furnace installed into a very old home. My biggest problem is
that they reused the ductwork from the old furnace and the I think they are too
big. Also part of the pipes are uninsulated and the air that goes into the
kitchen -- the very next room is 15 degrees colder than the living room.
I will let you know what they say about my noise problem....
dana
|
85.242 | try slowing down the blower | PACKED::USAGE::ALLEN | Christopher Allen, DEC COBOL, ZKO 381-0864 | Tue Nov 17 1992 15:55 | 16 |
| We lived in a house once which had FHA with an oil burner. This was a big old
green thing; the house was built in the 1960s. It was loud too, we had banging
too when the thing started up. There was lots of air being pushed through the
ducts.
We were fortunate to have an intelligent guy come out to look at the problem
(this was COAN oil service out of Natick, MA). What he did was to slow the blower
down. He may have put a speed-reduction pulley thingie on the blower shaft, but
at any rate, the effect was to "gear down" the RPMs from the motor to the blower.
The change was amazing! It was much much quieter and there was no more banging
(this was likely from the initial blast of air through the ducts). Lastly, the heat
in the house was much more constant: because the blower was running slower (and
longer), it was also cycling much less frequently.
-Chris
|
85.243 | | JUPITR::HILDEBRANT | I'm the NRA | Wed Nov 18 1992 08:22 | 7 |
| RE: Last Two
The blower speed on most furnaces is adjustable. Typically, you can
select low, medium, and high. Find out what speed the blower is set
to, and try a lower speed.
Marc H.
|
85.244 | how long do your furnaces run? | APLVEW::DEBRIAE | It's apple picking season! | Wed Nov 18 1992 08:52 | 10 |
|
How do you adjust the speed? Is there a switch on the blower motor
I didn't see right away?
I'm the reverse, I want to boost mine. It took the furnace being
on (non-stop) for over an hour and a half just to bring the house
(a smallish 7 room colonial) up to 60 degrees last night. That doesn't
seem right to me... (the wood stove in the other room helped too)
-Erik
|
85.245 | | MANTHN::EDD | $49,000, I think it'll work out... | Wed Nov 18 1992 09:01 | 20 |
| > how long do your furnaces run?
7 room ranch, with two bedrooms closed. Takes about 50 minutes to bring
temp from 54 to 64.
Which brings me to the next question... Is there anyway (charts,
programs, etc.) other than T&E to determine if it's more efficient to
(a) maintain a particular temp by keeping the heat up and using the
furniture, walls, etc as thermal mass to maintain the temp, thereby
resulting in shorter run cycles, or (b) let the temp drop and then have
to overcome the thermal inertia of the same furniture, etc.
When my house is warmed up, the run rates go about 9 minutes every 70
or so, at an outside temp in the 20-30 degree range. What I don't know
is how long it takes the house to cool down to the 54 degrees I set the
temp at during non-occupied periods or at night...
I wish I had a meter that would track run rates and outside temp...
Edd
|
85.246 | smart 'stat | SMURF::WALTERS | | Wed Nov 18 1992 12:16 | 9 |
|
According to the guy that fixed my furnace last year, Honeywell
does a "smart" thermostat for about $70 that will help you work
out the most efficient burn cycle.
Regards,
Colin
|
85.247 | Move the air.. and a lot of it! | INDEV1::GSMITH | I need two of everything | Wed Nov 18 1992 13:34 | 20 |
|
I just added an addition to my house (26x28), garage under, rooms
above. The heating guys suggested not to add another zone, (which
was my intent), but he would add a switch that will run the blower
ONLY. What this will do (I hope), is to circulate the air
throughout the house. If one part of your house is warmer than
te rest, the heat will be more even throughout. In my case I have
skylights in on large room, with ceiling fans. During the day, this
room should actually generate heat and be moved through the house.
It has yet to get very cold (In Mass).. so it really hasn't ben
tested out, but the heating guy said he had experience. I also
wired it, so that I can put in another zone if not satisfied. He
also INCREASED the size of the RETURN duct. This (if your system
has the capability), will increase the amount of air that is being
moved. I wasn't aware that the RETURN was very important until
educated!
Smitty
|
85.248 | multi-speed pulley changes the speed | PACKED::USAGE::ALLEN | Christopher Allen, DEC COBOL, ZKO 381-0864 | Thu Nov 19 1992 10:08 | 8 |
| re: the question on how to change the blower speed ...
Our blower had the "speed reduction pulley thingie" I referred to in
4790.4 ... This technical term was supposed to describe a belt pulley which
actually had 3 or so different diameter "notches" in it. Moving the belt
from one to another would change the blower's speed.
-Chris
|
85.249 | | TNPUBS::MACKONIS | We are a compromise of nature! | Thu Nov 19 1992 14:39 | 22 |
| Well, the furnace man came out. There might be some fixes that will help for
the time being. When I bought the house, a new furnace was part of the deal --
and that is exactly what was put into the house. The sellers didn't want to
spend more than they had to and I was too naive to put anything else in
writing. Silly me.
A new furnace, old ducts, old everything else. The duct pipe varies in size
from 12", 10" and 8". The air intake is about 3x the size it needs to be
and this where the majority of the noise is coming from.
We are going to install a damper in the main pipe so that the living room is
not the only room to heat up. Temporarily, we closed the vent in the LR and
now the other rooms have a chance at being luke warm. He is also going to
install some flex pipe which he feels will cut down the noise.
There will also be some insulation put onto the pipes that go under the house
thru the crawl space -- they were told any new pipes were to be just that --
pipes with no insulation. I love it!
At least I don't see my breathe in the kitchen and sweat in the LR!
dana
|
85.250 | | DAVE::MITTON | Token rings happen | Thu Nov 19 1992 17:17 | 8 |
| - blower speed: examining the labels inside my Lenox Gas FHA furnace
there are several different colored wires coming off the motor.
You wire it up according to the speed desired.
- FYI: Home Depot has quite a selection of smart thermostats (including
Honeywell) Buying one is on my list for RealSoonNow.
Dave.
|
85.251 | A different type of noise | SUBWAY::GREENSTEIN | | Fri Dec 25 1992 13:20 | 14 |
| I have an American Standard Gas hot air furnace that I guess is as old
as my house. (about 35 yrs) My noise problem is different: When the
blower turns on, the sheet metal on the sides of the furnace bows out
kind of like an oil can effect. This causes a real loud banging sound
that can be heard throughout the house. When the fan turns off and the
unit cools, the sheet metal sucks in causing the same noise again. The
movement of the sheet metal I guess is caused by both the expansion
from the heat and the pressure caused by the blower. Any ideas
regarding this annoying problem?
By the way I recently installed a humidifyer in the system. Not the
plate type but the type that sprays water in like a fuel injector. It
cost $99 at Home Depot. It works great!
|
85.252 | humidifiers tend to cause rust | PACKED::USAGE::ALLEN | Christopher Allen, DEC COBOL, ZKO 381-0864 | Tue Dec 29 1992 10:07 | 2 |
| Beware of your humidifier, that the water it sprays doesn't rust out
your plenum. Those are *expensive* to replace!
|
85.253 | Good advice, I'm aware, | SUBWAY::GREENSTEIN | | Tue Dec 29 1992 10:14 | 15 |
| re: Rust problem
Good point. The ducts themselves are galvanized. I already had to
reduce the humidity level, the unit has a humidistat. If the humidity
level is too high some of the water will not be absorbed into the air.
As a result, the water collects on an inside waal of the furnace and
runs down. This can sure cause rust. Another sign of the humidity
level being too high is condensation on the insides of the windows in
the house.
I have to tell you thoug that a feel so much better physically not
having to breathe that terrible dry air. The humidifier also saves
heating costs because higher humidity levels cause you too feel warmer
at lower temperatures. I can keep the thermostat at 64-66 and still
feel comfortable.
|
85.254 | The saga continues . . . | SUBWAY::GREENSTEIN | | Wed Dec 30 1992 13:59 | 5 |
| Re: banging furnace.
I had LILCO look at it this morning and they told me that it's a common
problem but there is nothing that they can do.
|
85.255 | easy fix | ISLNDS::LAMPROS | | Wed Dec 30 1992 14:29 | 6 |
|
Re: banging furnace...
The plunim chamber (sheet metal) should be ribbed to avoid the noise.
Buy some cheap angle iron and screw horizontally across chamber on the
outside of the sides that expand. The noise will go away.
|
85.256 | That's an idea. | SUBWAY::GREENSTEIN | | Wed Dec 30 1992 22:16 | 5 |
| I think I'll try that. I was thinking of a heavier guage sheet metal
to screw or rivet to the outside of the furnace to add rigidity. But
your idea is probabally easier. How certain are you that the noise
will go away?
|
85.257 | Silicone helps keep the noise quiet... | WFOV11::KOEHLER | Personal_Name | Thu Dec 31 1992 07:49 | 5 |
| When you attach the angle iron to the chamber you can add a line of
silicone to sort of glue the two together along with rivits or screws.
I did this on my rental unit and it been quiet for four years now.
TMW
|
85.258 | How about band iron? | SUBWAY::GREENSTEIN | | Thu Dec 31 1992 10:41 | 4 |
| Thanks I'll try the silicone too. Do you think I could use band iron
instead of angle iron? I think it would be easier and look a little
better.
|
85.259 | You Need More Than A Flat Reinforcement | MSBCS::LIU | Jazz Fish Zen Mambo | Thu Dec 31 1992 11:20 | 6 |
| You want something to stiffen or dampen the panel. Anything that is
flat will not really do that. But before you drill holes, try just
sticking a stiffener on with silicone. Lay a nice straight bead
down the width of the panel and stick down the stiffener of your
choice. No holes may be needed at all. Good luck.
|
85.260 | Hardware stores have galv. angleiron | WFOV11::KOEHLER | Personal_Name | Thu Dec 31 1992 13:05 | 5 |
| I'm not sure if the silicone will hold a stiffener in place without
screws or rivits. The champer does get warm so that might be a
negative factor.
TMW
|
85.261 | Works For Me | MSBCS::LIU | Jazz Fish Zen Mambo | Thu Dec 31 1992 14:13 | 8 |
| The heat won't bother the silicone. I use silicone sealer around engines
with no problems.
Its quick and inexpensive to try. And its easier to scrape off silicone
if you change your mind about placement than it is to fill in holes.....
Once you are satisfied that you have siliconed the stiffener in the
right place, THEN you drill a hole or three.
|
85.170 | Sanity check a repair to FHA gas blower | BOWLES::BOWLES | Bob Bowles - T&N EIC/Engineering | Tue Mar 16 1993 10:21 | 50 |
|
Fair and reasonable sanity check please:
I diagnosed a failing blower motor on a friend's FHA Gas furnace
(Bryant, installed 1968). The motor seized, heated and wouldn't turn.
In addition to the motor feeling a bit tight when turning the blower, I
noticed one of the mounting bracket bolts was loose. Tightened the
bolt, and spun the blower a bit by hand. I allowed to motor to cool
overnight (in addition to the occupants) and it started just fine the
next morning.
A local heating contractor was called, informed of the specific
problem, model and type of furnace. Over the phone, the estimate was
$130-$160 for the blower motor and 1 - 1.5 hours labor.
The real bill was:
Motor $139.50
Motor bracket $ 15.00
Capacitor $ 12.50
3 hours labor $114.00
The motor is no problem, but 3 hours labor? The service person didn't
have the proper parts, had to make a retrun trip with the bracket and
motor, wired the motor to the medium speed (the original was wired for
the low speed). Service person returned a 3rd time with CO detection
stickers and a statement claiming that (although no formal inspection
was performed) the heating system may be unsafe. The service person
said there was rust in the heat exchanger, but as far as I know he did
not find (or look for) any cracks.
Is the bracket a resonable additional expense? And why is the
capacitor necessary for the replacement motor? And if the original
motor was wired for low-speed, shouldn't the new motor also be wired to
a similar speed? My friend claims that the air flow is greater than
it ever was by a significant amount.
I realize that concerns about CO leaks in the heat exchanger are
serious, but it is just too easy to scare people into buying new
furnaces.
I just don't get the feeling that the repairs were done with true
knowledge of the specific system involved. The repairman didn't bother
looking at the Bryant specs that were given to him for the system. I'm
concerned about the correctness of the repair.
Any advice welcome,
bob
|
85.171 | | SOLVIT::REDZIN::DCOX | | Tue Mar 16 1993 11:57 | 30 |
| re <<< Note 1634.7 by BOWLES::BOWLES "Bob Bowles - T&N EIC/Engineering" >>>
-< Sanity check a repair to FHA gas blower >-
lots of issues....
re overcharges...I had a similar situation where a plumber installing
gas lines had to drive back to the shop to get something. Since the
contractor knew what had to be done before sending the plumber out, I
balked at paying for his labor while he drove around getting pipe he
should already have with him; I refused to pay for that time. In this
case, 1-1.5 hrs would have been reasonable.
re bad motor. It is possible that the motor had come loose in the
bracket and jammed against something, therefore stopping. It would not
have been the first motor that ran forever after it had been freed up.
Might not have needed replacing, however that would have been the
owner's call, not the tech.
re speed. Most likely, the low speed hookup was designed for central
air. Some thermostats can automatically select low speed for air
conditioning, medium for heating and some have a manual switch for high
speed if you just want to circulate air.
re exchanger. They do rust out. It is a problem if they become
perforated. I had mine checked by the local Gas Co. At the same time,
they did a safety check of all gas appliances. The charge was minimal.
They seem to care little if you buy a new furnace. When you do, they
just steer you to a local contractor.
Dave
|
85.172 | liability is the reason for the warning | SPEZKO::LEMIEUX | | Tue Mar 16 1993 15:36 | 14 |
|
The reason for the statement concerning safety is probably to Cover his
Butt. The furnace is old, FHA furnaces tend to rust out, he was the
last to work on it. If your friend has a CO problem tomorrow and someone
gets sick or dies....guess who gets blamed for not inspecting or at least
warning him that the furnace could be a problem. The Service company.
Fan speed: Low or medium for heat, high speed for cooling is
usually the way they are setup from the factory.
|
85.173 | Any recommendations for motor rebuilders? | HDLITE::NEWMAN | Chuck Newman, 297-5499, MRO4-1/H16, Pole J13 | Thu Jun 17 1993 12:56 | 14 |
| Re: .5
� These motors can be repaired too. Probably cheaper than a new one.
� Anybody ever have a motor rebuilt? .0, where are you located?
� I know of a couple places in central Mass that rebuild motors.
The motor on the distribution blower on my wood furnace needs at least a good
cleaning. There were a couple of times this past winter when it slowed down a
*lot*. I ended up oiling it several times.
Can anyone recommend anyone to clean/rebuild motors in the Worcester MA area? I
live in Grafton, and Phil Gransewicz's recommendation was in Gardner MA.
-- Chuck Newman
|
85.264 | "Supplier for brass type heating vents" | SVCRUS::BOURQUE | | Mon Aug 02 1993 12:24 | 5 |
|
anyone know where I can find Brass type heating vents I have looked
around and the ones I nee to replace are an odd size I haven't found in
any of the Do-It-Yourself-Stores that I have looked in.
Thanks,Ron
|
85.265 | | PATE::MACNEAL | ruck `n' roll | Mon Aug 02 1993 12:58 | 2 |
| Renovators Supply in Sturbridge, MA may have them. They seem to have
brass everything. They do mail order too, if you aren't in the area.
|
85.266 | Ayer, MA | PINION::MCCONNELL | | Mon Aug 02 1993 13:50 | 3 |
| Don't know where you are located, but I have heard of a place in Ayer,
MA that has them. Have been meaning to get over there myself. I think
I have the address at home. If so, I will post it.
|
85.267 | Reggio Register | CADSYS::FLEECE::RITCHIE | Elaine Kokernak Ritchie | Mon Aug 02 1993 13:59 | 5 |
| Reggio Register
20 Central Ave
Ayer, MA
(508)772-3493
|
85.32 | FHA system cycles on and off too much. | KALI::FORSBERG | LENaC Product Development | Fri Aug 20 1993 12:23 | 46 |
| I have an oil-fired forced-hot-air heating system. My question concerns
the way that it cycles on and off to maintain temperature.
The way it used to work is that the air circulation blower would start
about twenty seconds after the burner had started. It would
correspondingly stop about twenty seconds after the burner had stopped.
See timing diagram below:
on +-------+ +-------+ +-------+
Burner: | | | | | |
off +-------+ +-------+ +-------+
on: +-------+ +-------+ +-------+
FHA blower: | | | | | |
off: +-------+ +-------+ +-------+
First question: what controls this timing? Is there a timer or is the
circulation blower controlled thermostatically?
a few years ago, I let the filter go too long between changes. The first
symptom I noticed from the heating system was that the circulation blower
would stay on for a long time during which the burner would cycle on and
off repeatedly:
on +-------+ +-------+ +-------+
Burner: | | | | | |
off ------+ +-------+ +-------+
on: +--------------------------------------+
FHA blower: | |
off: -------+
I tried the obvious thing first (changing the filter) and this behavior
stopped.
It's doing it again now even with a clean filter. What should I check?
Another air blockage somewhere?
Thanks for any help.
Erik J. Forsberg
|
85.33 | Check these points | MPGS::MASSICOTTE | | Sat Aug 21 1993 23:20 | 54 |
|
When the thermostat call for heat, it energizes the burner
only.
Once the heat exchanger is up in temp., approx 120 degrees, the
fan limit switch starts the fan. Should the fan not be delivering
the CFMs the unit was designed for, the heatx high temp limit will
shut the burner off and the fan will continue to run.
Reasons for insufficient air flow are; Dirty filter. Loose belt.
Buckets in the fan full of dirt. Something restricting the return
air grille(s). Outlet diffusers closed down too much.
KILL THE POWER TO THE FURNACE !!!!! Then:
If you have a blower with the motor on the inside of the squirrel
cage, remove the whole assy. Usually there are just a few screws
on the top of the fan volute and the bottom slips into a slot.
On the opposite side of the fan you'll find (usually 2) set screws
holding the fan on the shaft. Loosen them. Then remove the three
bolts holding the motor brackets onto the fan housing. Set the
housing on a couple pieces of 4 X 4 or larger with the shaft side
up. Find something made of brass, copper or aluminum which you
can put on the end of the shaft. A long brass rod 1/2" dia. is best.
If the motor shaft has one flat side, where the set screw on the round
part is, there is a little hump which is going to make life a little
miserable now. Never, ever, beat on the end of a shaft with a steel
object. Once you've pushed the little hump mentioned, you'll have a
mushroomed shaft end to contend with next. Takes a little patience
also self control to keep from really BELTING IT, but it'll go.
Remove the motor. Look in the air outlet. Should be a piece of
sheetmetal which prevents the fan from comming out. Remove it.
Remove the fan and scrub the buckets good'n clean. Got an air
compressor? If not, use your vac and blow out the motor.
Look around the perimeter of the silver end bells. Any holes
with plastic plugs for oil? If not, place it shaft up and put
about 6 drops of SAE 30 oil on the outer edge of the bearing.
wait a few minutes, turn it over and do the same. Don't over
oil a motor. 6 drops is plenty.
RE-assemble and try it! You should have a burner serviceman
do his thing once a year. If it's not set right, you'll pay
more than his bill would've been, for fuel. If you have the
factory start up paperwork, give it to him. Makes it a bit
easier.
If your fan has an external motor and belt, Your part of the bargain
has been made easier. :^) Always keep a spare belt hanging
around. They never break until it 10 degrees at 2 AM.
Have fun. :^)
Fred
|
85.34 | Could need a tune up... | STRATA::CASSIDY | | Mon Aug 23 1993 00:36 | 11 |
|
It sounds as though the air from the blower is not cooling
the plenum (hot box) as quickly as it should/used to. I would
guess that there is an ostruction to air flow. Does the air
from the registers feel as though it's blowing strong enough?
You may need to vacuum out the plenum. There's a cover you
remove to do this. This is a normal procedure during a tune up.
If the furnace hasn't been tuned for a couple of years, it will
be worth the cost to have it done.
Tim
|
85.35 | windedge.... | ELWOOD::DYMON | | Mon Aug 23 1993 07:51 | 4 |
|
...I'd bet on loose or worn belt.....
|
85.36 | | SOLVIT::CHACE | My favorite season is getting nearer! | Mon Aug 23 1993 10:30 | 5 |
|
It could also be that one of the temperature senors is failing and
getting way out of adjustment.
Kenny
|
85.80 | | 12GAGE::DERIE | Quis custodes ipsos custodiet? | Sat Sep 04 1993 11:41 | 26 |
|
I'm in the process of looking for a FHA humidifier and was wondering if
any of you folks have anything new to add since this was last discussed
here.
I went to Sears and was told that they don't carry them anymore and
that they can set me up with an outfit that would install one for me. I
don't like paying for things I can do myself.
I checked out some Hamiltom units at Home Depot. They had a few different
models to pick from, the typical drum/wick type that attach to the warm
air ducts.
They had another model that consisted of a little box with a spray
nozzle that sprays a fine mist into the warm air duct. In theory I like
the idea, but I'm not sure how well this particular model would work.
Would something like this produce the white powder usually given off
by the ultrasonic humidifers? I didn't like the fact that it doesn't
have a humidistat that connected to the cold air return. The
three units they had on the shelf were all re-packaged so I opened one
up to find it was used/missing parts and instructions. Obviously, folks
have had problems with these ($108).
Anyone have any recent experience they can share with FHA humidifiers?
Steve
|
85.81 | | STAR::ALLISON | | Tue Sep 14 1993 15:13 | 5 |
| > I went to Sears and was told that they don't carry them anymore...
I don't know which Sears you went to, but the one at PLM carries two
models, the Kenmore 2500 and 3000. Looks like I"ll be installing the
3000. The type that draws air into the unit..
|
85.82 | Atomizing Humdifiers | DELNI::HOO | | Tue Nov 02 1993 12:45 | 26 |
| Re:.7
Last weekend I went to Sears and Home Depot in search of a
whole-house humidifier on an FHA system. Sears had the Kenmore ones
on sale ($119 and 139). Home Depot had 3: 2 were from HHP (Hamilton
Home products) and 1 was the atomizing unit (don't remember the name
offhand but I have it written down at home). The HHP's were under
$100.
I asked to speak to someone knowledgeable in that area, I got Andre
the plumbing expert. He said the best one was the atomizing unit for
these reasons:
1- Adjustable humidity switch (5 settings from hi to lo) which the
other types don't have.
2- No black filters to change as there is none.
3- Don't have to treat sitting water with the bacterio-something
solutions as you do with regular humidifiers that work on the
sitting water concept.
4- Ease of installation as the unit is only 3x5 on the surface you
screw into the duct. The atomizer has a sprayer nozzle that
is centered in the middle of supply duct.
I plan on contacting the manufacturer and getting more literature and
information. I ended up not buying anything that day. Andre put some
more on order that day and they'll have some new, unopened packages in
3 wks. By the way, I did not read this notes file before I went and am
now looking through to see if anyone else has any opinions. As for the
opened packages, I found 2 of them and I think it's not so much that they
are returns but from curious shoppers.
|
85.83 | Liked it... | STAR::ALLISON | | Wed Nov 03 1993 09:52 | 14 |
| I recently installed an atomizing humidifiers and am pleased with the
results.. It is a very easy installation (as long as there is an outlet
nearby -- I had to wire one..)
It's hard to tell whether I notice a difference. I have it turned all
the way up and it's always on. I haven't really noticed more
condensation on the windows yet. But I'll bet I'll notice a difference
with a humidistat (compared to our neighbor's house, for example).
One recommendation.. Replace the cheap plastic compression fitting with
a brass one.. I feel a lot better knowing that the brass fitting is
going to hold the connection to the water better..
-Gary
|
85.84 | On indoor humidity | CADSYS::FLEECE::RITCHIE | Elaine Kokernak Ritchie | Wed Nov 03 1993 10:22 | 12 |
| Re: .10
You won't see condensation on the windows until the weather gets consistently
very cold and try outside. I have experience with humidifiers in one house
without adequate ventilation, and in another with too much ventilation. I have
mold and dust allergies which are controlled by careful maintenance of relative
humidity in the home. My suggestion is to get an independent humidity gauge.
For many homes, the humidifier does not need to be on all the time. Your ideal
target RH in a home in the winter is 40-50%. More than that is a waste of time,
and you just may find yourself with dust and mold allergies, too!
Elaine
|
85.347 | Floor grates? | VMSMKT::COLEMAN | | Wed Nov 03 1993 12:53 | 11 |
| We are building a home and want to install "floor grates" at the front
and side doors. We have seen these in commercial buildings or in homes
(non-U.S.) but can't locate them at your typical hardware store.
They are grates built into the floor which catch sand, etc. upon
entering and they have a trap underneath to clean it out.
Any suggestions where we could find these to order/purchase?
Thanks,
Betty
|
85.85 | Humidistat call furnace fan too? | MIYATA::LEMIEUX | | Wed Nov 03 1993 18:27 | 6 |
| re .10:
Does the humidistat also turn the furnace fan on when it calls
the humidifier?
|
85.348 | Never seen one. How 'bout some more hints? | TOOK::DELBALSO | I (spade) my (dog face) | Wed Nov 03 1993 19:01 | 4 |
| Can you describe the nature of the grate a little more fully? Decorative or
non-? Type of metal? Weight? Finish?
-Jack
|
85.86 | No, not normally. | MPGS::MASSICOTTE | | Wed Nov 03 1993 19:47 | 40 |
|
Not normally. However it can be wired to do so.
If you have a regular round Honneywell T87 Tstat which is
the most common, and don't have air conditioning, you'll
have to have a relay installed in the furnace to parallel
the 115 volts from the fan limit control to the motor.
If you elect to do this, I suggest the installation of a
high limit humidistat in the duct, about 1/2 way down
the main branch. Set it about 80% and this will keep
you from getting the air too saturated and having the
moisture condense out when the fan shuts down and the
duct work is cool. Wire it in series with the space
humidistat.
But, unless you have a rather "loose" house, the running
time of your system should be able to keep the RH +- 3%
from setpoint. If you have a tight house and the humidity
will not rise, you could have the fan limit "OFF" point
set too high. This will shorten the run time of the fan.
You could lower the cut in temp also which wouold bring
fan on sooner. Don't lower it more than 10 degrees without
your serviceman there, unless you are familiar with it's
operation. This will have a slight effect on the efficiency
in the first minute or two of operation but the heat-x will
catch up. If your Tstat is too close to a diffuser that too
will cause a short cycle of your system. If you have the
blueprints of the home, check for the CFMs that should be
comming out of each diffuser/register. If the house is not
properly balanced out, you'll notice some areas cold and clammy
while others could be too warm and dry. If you have these
figures available, check with the HVAC man at your plant. They
should have a simple device you could borrow and should be able
to instruct you on how to go about balancing things. It's a little
time consuming, but it's well worth it in the long run.
Fred
|
85.87 | Bad luck | USCTR1::BJORGENSEN | | Wed Nov 03 1993 23:51 | 20 |
| I bought a Atomizing Humdifier from home depot a few years ago - just
like the one that *I* saw there on Saturday! I had TERRIBLE luck with it.
I have a humidstat that called the Atomizing Humdifier and turned it
on. I mounted it per the instructions over my furnace. The problem
was that it dripped for a period of time after the furnace shut off, even
though power was shut off. This often resulted in a puddle on the floor.
I called and worked with the co rep for months. They did send me some more
parts that didn't seem to help. Finally I demanded my money back and the
company was NOT cooperative. I finally dropped it. I would have given
you the unit - but I took it to the dump a few weeks ago. I went with a
sears unit - clean it once a year, and it works fine.
I think the concept of the Atomizing Humdifier is better - no reservoir
and threat of bacteria, I just had terrible luck with the product and
the company.
FWIW,
Brian
|
85.88 | | STAR::ALLISON | | Thu Nov 04 1993 07:50 | 12 |
| RE: .11 No, I don't have it wired to turn on the furnace.. Not sure I
would want it to in case the humidity level never got high enough to
turn the furnace back off...
RE: .14 I too have noticed that the unit turns off a few seconds *after*
the blower has stopped. The manual noted this saying it shouldn't be a
problem since it'll be spraying into the sides.. I positioned my unit
directly above the furnace, I certainly hope that any extra water is
not dripping down into the furnace. I've got the insulation-type duct
work (as compared to metal). I'll definitely be watching this..
_Gary
|
85.349 | | SMURF::WALTERS | | Thu Nov 04 1993 08:23 | 23 |
|
They're usually 1x.125 flat metal bars, something that won't corrode
drilled every 6" or so. The edges are milled as an anti-slip.
There's a spacer between the bars and they are stacked together on rods
or long bolts. Like the big subway vent grilles in NY City.
The grate is inset in concrete in front of the door over a low pit so
that dirt & sand falls in. (Imagine the grille over a barbecue). An
alternative is the heavy-duty "articulated" rubber flooring.
You'd probably be able to assemble one from flat stock and long
threaded bars. It's probably something any wrought-iron foundry would
be able to fabricate.
I'm not sure this would be a good idea in NE, unless it was in a
covered porch. You'd have problems with it filling with snowmelt
and freezing. There's a lot more salt to corrode it, and it's
a also killer for high heels.
regards,
Colin
|
85.350 | Inside... | REFINE::MCDONALD | shh! | Thu Nov 04 1993 09:07 | 21 |
| > The grate is inset in concrete in front of the door...
> I'm not sure this would be a good idea in NE, unless it was in a
> covered porch. You'd have problems with it filling with snowmelt
> and freezing. There's a lot more salt to corrode it, and it's
> a also killer for high heels.
Actually I think the originator is talking about the type
that is seen in some European homes (saw it on T.O.H once).
They are actually installed INSIDE the house. Some are metal
grates... some are wooden grates... both are placed over a
shallow "well" with a tray that catches the drippings off of
your shoes.
Curiously, when I first saw one I had the same thought "What
does a woman in heels do? Jump over this thing?"
- Mac
|
85.351 | | IMTDEV::BRUNO | Father Gregory | Thu Nov 04 1993 09:15 | 9 |
|
I've seen these in some older houses I've visited. There's a company
that puts out a catalog with lots of antique-style fixtures and probably has
this kind of thing. It's called something like Renovator's Supply or something.
The catalog has been mentioned in this conference (somewhere).
Buy the grate from them, and construct the crud-bin yourself.
Greg
|
85.89 | Water in and around the furnace | USCTR1::BJORGENSEN | | Thu Nov 04 1993 09:22 | 7 |
| RE: -1 I too installed mine directly over the furnace and my duct
work is insulated. I was very concerned about having the water
drip down into my furnace - as I said earlier, I even had a puddle on
the floor. My application/installation/experience may be the
exception and not the rule. But, the company was not very cooperative.
I was very concerned about having water down in and around the firebox
in my furnace.
|
85.352 | FHA return grate..... | BUSY::JWHITTEMORE | Carp Perdiem | Thu Nov 04 1993 11:24 | 4 |
|
You could probably get by quite nicely using the grate from the cold-air
return on a FHA heating system. The one from my old house was approx.
2' by 4' and would fit quite nicely at a threshold..........
|
85.353 | how about a floor register? | TFH::DONNELLY | Take my advice- Don't listen to me | Thu Nov 04 1993 11:35 | 6 |
| call for a 'reggio registers' catalog. they make very nice cast iron floor
registers in various sizes. they are a little costly but probably worth it
if you're considering only one or two. -craig
p.s. i think the catalog notesfile contains their number, they are in north
central ma somewhere.
|
85.90 | | MIYATA::LEMIEUX | | Thu Nov 04 1993 18:49 | 11 |
|
I asked the question .11 because I have worked on many FHA furnaces
that were in pretty sad shape rust wise. They all had humidifiers in
them that were controlled by a humidistat that called the humidifier
which in turn was simply dumping water into the ductwork and it was
running back into the plenum. A few others I've seen had the humidifier
on the return air side. The furnace pulled the water through the heat
exchanger....yikes! Lots of rust on those also.
i]
|
85.91 | | MIYATA::LEMIEUX | | Thu Nov 04 1993 19:00 | 12 |
|
I just re-read the note a few replies back by Fred Massicotte. What he
says makes sense the humidifier only comes on when the furnace runs. Not
when the fan isn't running.
Thanks for clarifying that Fred. As an electrician I get to wire
these from time to time and I've used a sail switch or a
pressure switch in line with the humidifier contol circuit to make
sure the humidifier wouldn't run unless the fan was running also.
|
85.92 | Rusty return? | MPGS::MASSICOTTE | | Fri Nov 05 1993 09:11 | 12 |
|
RE: -.2
If there's rust in the return plenum from the humidifier, an
excess amount of water is, more than likely, being "blown"
off the wheel. Warm air from the heat-x discharge should
"evaporate" the water from the wheel, not force it off in
droplets. Suggest 25% of warm air to the inlet of the
humidifier be blocked off, to begin with.
Fred
|
85.354 | Thanks for the info | VMSMKT::COLEMAN | | Fri Nov 05 1993 13:31 | 13 |
| Good ideas -- and the noter is correct that stated this particular
grill goes on the INSIDE of the house, just inside the door, and
exactly as stated (a trap underneath that catches the dirt, etc.)
I guess I don't wear high shoes much as that never crossed my mind, but
it's definately something to think about.
Renovator's Supply doesn't carry it, I have their catalog. I'll check
the heat register and consider that, or the wrought-iron approach, both
of which are good ideas for making it ourselves.
Thanks,
Betty
|
85.355 | where does the hole go? | SMURF::WALTERS | | Fri Nov 05 1993 14:59 | 5 |
| Interesting. I don't recall seeing one inside a house - at least in
the UK. Most houses are mostly built on a slab, so the well would have
to be formed during the cement pour. How do you plan to install it?
C
|
85.37 | After a tune-up, it's still cycling... | KALVIN::FORSBERG | NIPG, Hub Products Group | Mon Nov 08 1993 08:51 | 10 |
| Two more questions:
> Remove the fan and scrub the buckets good'n clean.
Does "buckets" mean the vanes of the fan?
Also, with an external-motor fan, how does one lubricate the
fan bearings?
Thanks again.
|
85.356 | y | VMSMKT::COLEMAN | | Mon Nov 08 1993 10:50 | 8 |
| We saw them in Japan...
Ours will not be built into concrete as it's on the 1st floor and we
have a full basement. We plan to create a wooden box as part of the
sub-floor, dropped down to create a catch-bin and the grate would go
over it flush with the first floor. We would, of course, have to
reinforce the wooden box to hold weight appropriately.
|
85.357 | | CADSYS::FLEECE::RITCHIE | Elaine Kokernak Ritchie | Mon Nov 08 1993 11:13 | 4 |
| I'm not sure what you are planning to do, but you may want to make the wooden
box out of pressure treated lumber. Consider that wet or snow covered shoes
make it inside the house no matter what you do. At inside temperatures, that
moisture will soak into the wood before it evaporates.
|
85.38 | That's them! | MPGS::MASSICOTTE | | Mon Nov 08 1993 11:58 | 18 |
|
The "buckets" are the scoop shaped pieces. If they have dirt
collecting in them it reduces the amount of air the fan moves.
If you have sleeve bearings, there's two ways to lube them.
One, you can remove the bearing from it's resilient mount and
soak it in SAE-10 non det oil for a little while.
Two, in the metal ring that the bearing sits in you'll see a
hole on top about 5/16" in dia. Cut the rubber out below this
mount and drill a 1/8" hole thru the first layer of metal.
Probably a 1/16" thick - if that. Do not drill any further.
This will allow you to wet the wicking with SAE-10 oil. 8 or
or 10 drops added slowly will take you to next year.
Find something to plug the little holes.
Fred
|
85.358 | I wouldn't leave it as bare wood | TOOK::DELBALSO | I (spade) my (dog face) | Mon Nov 08 1993 17:01 | 6 |
| I'd go a step further than the PT lumber and line the box with a galvanized
sheet metal coated with something (plastic/polymer/sealer) to prevent corrosion
from any salt, etc. Easy to clean up, as well. I'd think an FHA installer
that makes ductwork could fabricate a box liner for you for little money.
-Jack
|
85.359 | | REFINE::MCDONALD | shh! | Tue Nov 09 1993 08:24 | 6 |
|
Or less elaborately:
Line the box with a removable plastic tray for easy cleaning.
- Mac
|
85.360 | Cat litter box | VICKI::DODIER | Cars suck, then they die | Tue Nov 09 1993 10:31 | 3 |
| A cat litter box would probably work.
Ray
|
85.268 | UNEVEN HEATING | ANGLIN::SVOSS | | Thu Nov 11 1993 12:40 | 16 |
| I COULDN'T FIND A NOTE PERTAINING TO THIS PROBLEM SO HERE GOES...
I HAVE 2 ROOMS IN MY HOME THAT GET VERY LITTLE HEAT FROM THE FURNACE.
ONE IS MY 3 YEAR OLD'S ROOM. IT IS THE FURTHEST FROM THE FURNACE AND
IS ALLWAYS THE COLDEST. THE OTHER IS THE BASEMENT. THERE ARE 3 VENTS
IN THE BASEMENT. ONE OF THEM BLOWS QUITE WELL, THE OTHER 2 BLOW VERY
LITTLE SO ITS AT LEAST 10-15 DEGREES COLDER IN THE BASEMENT WHICH IS
WHERE MOST OF OUR TIME AT HOME IS SPENT.
I HAVE TRIED CLOSING OTHER VENTS TO FORCE MORE AIR TO THE STARVED VENTS
BUT THAT DIDN'T HELP AT ALL. I HAVE CHECKED AS MUCH OF THE VENTING AS
I CAN SEE TO SEE IF SOME JOINTS WERE LEAKING BUT DIDN'T FIND MUCH.
ANY IDEAS. ALL HELP WILL BE APPRECIATED.
SV
|
85.269 | | POWDML::MACINTYRE | | Thu Nov 11 1993 13:00 | 22 |
| A couple of things:
You might place insulation around the ductwork to prevent heat loss as
the air travels to your son's room.
You could check the windows for drafts and install some of that shrink
wrap type window covering.
The vent that blows well might be the one leading to your son's room.
If so, it might be diverting too much hot air into the basement before
it can reach your son's room.
Your basement will almost always be cooler than the rest of the house.
You could check the foundation sill for leaks and caulk them. You
could stuff insulation around that area also.
Your basement could be too humid. Consider a dehumidifier.
I'm sure there are lots of other things to do.
Marv
|
85.270 | Check insulation above and below the room | CADSYS::FLEECE::RITCHIE | Elaine Kokernak Ritchie | Thu Nov 11 1993 13:10 | 9 |
| I had the bedroom you describe when I was growing up, the end room, furthest
from the furnace. I was always cold. In the 70's when fuel got really
expensive, my mother has the attic insulation increased. That helped quite a
bit, but it was still a cool room. Then one day, for reasons I don't remember,
we were in the basement looking at the sill. There was a 1/4 to 3/8" gap in the
sill, and it was under my old room! We couldn't believe it! Plugged that up
right away, and now that room is just as comfortable as all the others.
Elaine
|
85.271 | | CSC32::S_BROOK | There and back to see how far it is | Thu Nov 11 1993 14:05 | 7 |
| Remember too that most ducts have baffles in them, apart from the grille
controls. They look like handles on the side of the pipe. Make sure
that those for rooms furthest away are wide open. If they are closed
or nearly closed, you will definitely see the problem where closing
near to the furnace ducts have little impact on those far away.
stuart
|
85.272 | I covered this elsewhere, but anyway... | MPGS::MASSICOTTE | | Thu Nov 11 1993 14:31 | 42 |
|
IF - you can find some prints on the house, they should give you
the amount of air that should be comming from each diffuser/floor
grille. Also what should be comming out of those in the cellar.
Total them up. If you are unfamiliar with taking CFM measurements,
talk to one of the HVAC techs at your site.
Have you checked the blower belt? How about the filter? Are the
buckets in the fan clean? Is there an item blocking the return
air grille such as a bureau? Do you have the specs for the
furnace? They should tell you how much air the unit is designed
to move with a certain temperature rise across the heat exchanger
and the duct static pressure the fan was designed to operate at.
This may sound rather "deep" to someone who don't normally tinker
with this stuff so to put it into perspective simply, how far can
you go on a tire without pressure? Same thing in duct work.
The process is as follows. You have to know the total CFMs the house
requires. Open all registers/grilles/diffusers. Once the fan is
operating at designed speed and the motor is not overloaded by trying
to speed up the fan with the adjustable pulley, velocity readings
are taken in the duct after the furnace and before the first room
takeoff and not near an elbow. If the house calls for 1200 CFMS
and that is the amount going down the ductwork ( a bit more is fine )
then you start with the closest outlet and set it per spec. Then each
in turn and the last one gets what's left which should be exactly
on the money. If not, check for leaking connections. Actually,
if you had a reputable service tech come in that could assure you
he has the tools to do this, has done it before, and guarantees his
work, you'll be bucks ahead of the game by next march. But, you
need to have "DESIGN DATA" for him. He should also be able to
clean and adjust your burner for maximum efficiency.
Suggest you do the simple things first as I mentioned. The belt(s),
filters, restrictions and leaks at connections.
Elaine had an excellent point to check into also. But you mentioned
air flow. Not every room gets the same amount of the same temperature
air. You could cook one room with 100 CFMs of 130 degree air while
you'd freeze in another larger room on the north side with the same.
Fred
|
85.273 | inline booster | SMURF::WALTERS | | Fri Nov 12 1993 08:53 | 8 |
|
You cvould just install a booster fan for that one room. It costs $30
and takes an hour or so to install.
Colin
|
85.204 | makeshift filtering for FHA system ? | RDVAX::SRCHER::BREEDING | | Tue Dec 07 1993 17:17 | 7 |
| I'm currently renting a house w/ an ancient oil powered forced hot
air furnace. So far as I can tell there is no air filtration
used in the system. Is it possible to buy a filter or some filter
element and place it in the air intake duct? Or is this not
a good idea? Any suggestions are appreciated.
-Andy Breeding
|
85.205 | filter it out... | ELWOOD::DYMON | | Wed Dec 08 1993 06:59 | 18 |
|
You might want to hunt around a little more for a filter
slot. It might not be located in a well to do stop or
there is an access cover over it. If all else fails,
find an easy to get at spot in the intake. Measure and
see if you can find a filter to fit. Get the jigsaw out and
cut a slot in one side and something in the other to prevent
the filter from getting sucked in. Then cover the hole with
duct tape....
Then again you can aways place the filter behind the intake grate
on the wall......
Depending on the condition. You might want to have the system
cleaned.....
JD
|
85.206 | | MROA::MACKEY | | Wed Dec 08 1993 14:44 | 5 |
| Mine used to be in the bottom door (lift off) of the furnace
were the air came in just before the blower motor. You just slid it
into the grooves and pushed it onto some pins. The filter I
used came from somerville lumber at apx $1.00
|
85.207 | Another spot | MPGS::MASSICOTTE | | Thu Dec 09 1993 09:58 | 6 |
|
Look behind the return air grille(s) in the living quarters.
Many are placed there to catch airborne particles before they
enter the ductwork.
Fred
|
85.208 | I'll look some more and then go filter hunting | RDVAX::SRCHER::BREEDING | | Thu Dec 09 1993 12:22 | 4 |
| Thanks for the suggestions. I'll look harder and if I don't
find a filter slot I will try the suggestion in .1.
Andy Breeding
|
85.39 | shuddering, smoky start-ups | LGP30::FLEISCHER | without vision the people perish (DTN 223-8576, MSO2-2/A2, IM&T) | Wed Jan 12 1994 07:09 | 41 |
| re Note 47.0 by VENNEX::ARNOLD:
> My oil fired furnace has a problem.Every once in a while,usually at night,
> when it first turns on and starts firing oil,it rumbles like crazy and
> shakes the whole furnace.
My oil-fired boiler has developed a similar problem. An
additional symptom is a large cloud of black smoke in the
basement which appears from the flue weighted venty thing
(what is the technical term?) when this happens.
I would suspect delayed ignition.
My heating contractor has checked the transformer and
electrodes, and replaced the nozzle. He thinks the next
thing to replace is the pump. (Although he tested the
transformer, he said that he would still suspect it after
that.)
An additional complication in this all is that the boiler is
a 6 year old Weil-McLain into which a 15 year old Carlin
burner has been installed (from the previous boiler that
failed). My present contractor, and the one I had before
him, seems to blame a lot of my problems (and I've had a lot
of firing problems over the years) on the Carlin burner.
They both said that a Carlin is the wrong burner for a
Weil-McLain and that a Becket is the right one. The
implication is that I really can't expect it to work really
well unless I replace the burner -- at $500 (is that the
right price?).
I need advice. Should I replace the pump (at about $100, I
would guess) first, and then possibly the transformer, or
should I go right to a new burner?
Is there anything else that could cause this symptom, either
in the burner (what else is there besides the fan) or the
boiler (e.g., the boiler controls)?
Thanks,
Bob
|
85.40 | Pop goes the furnace... | ELWOOD::DYMON | | Wed Jan 12 1994 11:41 | 11 |
|
Hummmmmm...... sounds like a late fireup. What happens is in
most cases, the spark isnt good enought and there is a delay
in igniton. This gives raw oil fumes to fill the chambor and
when it fires.....boom! Black smoke out the seams of the pipe...
Granger in Worc. might have what you need for about $40 if your
local supplier dosnt.
JD
|
85.41 | what does the $40 get? | LGP30::FLEISCHER | without vision the people perish (DTN 223-8576, MSO2-2/A2, IM&T) | Wed Jan 12 1994 12:02 | 8 |
| re Note 47.40 by ELWOOD::DYMON:
> Granger in Worc. might have what you need for about $40 if your
> local supplier dosnt.
But what is it that I need!
Bob
|
85.42 | Carlins are tough to get right | SOLVIT::CHACE | My favorite season is getting nearer! | Wed Jan 12 1994 13:31 | 8 |
|
Regardless of what may or may not be wrong with your Carlin, I know
that Carlins are more difficult than Beckets to get adjusted right.
They seem to be more sensitive to everything. My Carlin was doing what
yours is and I tried several things until I saw somebody selling a 1
year old Becket for $90. I bout it, problems solved for good.
Kenny
|
85.43 | New nozzle & electrode adjustment | SALEM::JGREEN | Living beyond my emotional means | Wed Jan 12 1994 16:50 | 5 |
| My oil fired FHA had the same problem. A service call fixed it by
replacing the nozzle & resetting the electrodes to the 'proper' spacing
and alignment relative to the nozzle. Been fine for over a year now.
~jeff
|
85.44 | beware the connections you can't see | LGP30::FLEISCHER | without vision the people perish (DTN 223-8576, MSO2-2/A2, IM&T) | Thu Jan 13 1994 11:25 | 22 |
| re Note 47.43 by SALEM::JGREEN:
> My oil fired FHA had the same problem. A service call fixed it by
> replacing the nozzle & resetting the electrodes to the 'proper' spacing
> and alignment relative to the nozzle. Been fine for over a year now.
A close neighbor and good friend of mine (Joe Hamlin,
co-owner of TES electrical contractors) had serviced heating
equipment earlier in his career and he came over to look at
the burner.
An interesting thing he noticed was that the coil-spring
high-voltage contacts on the ignition transformer weren't in
line with the back end of the electrodes. One of them would
have been barely touching (although it is really hard to see
this "in place" when the unit is closed up -- he measured
offsets).
He bent the contacts and/or the electrodes into alignment, put
it back together, and all is working fine now.
Bob
|
85.45 | Either way, he makes money... | STRATA::CASSIDY | | Fri Jan 14 1994 00:10 | 13 |
| > My heating contractor has checked the transformer and
> electrodes, and replaced the nozzle. He thinks the next
> thing to replace is the pump. (Although he tested the
> transformer, he said that he would still suspect it after
> that.)
One thing I suggest you get is a new repairman. This person is
not troubleshooting, he is shotgunning! He obviously doesn't mind
replacing parts, at YOUR expense, until (hopefully) the problem goes
away.
Tim
|
85.296 | question on our heating system | STRATA::RDOZOIS | justice will prevail... | Tue Jan 18 1994 23:29 | 17 |
| Hi,
I have a couple of questions regarding our heating system.
We live in a ranch on a slab with forced hot air. The first
question I have is, is there a way to add a humidifier either
to our furnace or in the air-ducts?? My second question is,
our oil tank is in the ground and this spring we are planning
to have it removed. Instead of investing the money for a
new tank, would another form of heating be better?? I'd
really like to take out the furnace which sits in the middle of
my house taking up a ton of room. I'm just not sure what
we'd have to do and how much it would cost us for either options??!!
Suggestions and advice would be welcome.....
thanks,
renee
|
85.297 | Need more info on your requirments | ELWOOD::DYMON | | Wed Jan 19 1994 07:19 | 15 |
|
1. Humidifier....they sell one that is a stand a lone and that
plugs into the furnace.
2. FHA is cheep. It would have been nice if the slab had radient
heat. Wood stove? Solar. FHW. But they would require
some type of space similar to your furnace area now.
Maybe a Gas wall unit. Do you have city gas. If not, a tank
would go out side...
Do you have any room for an addition outside the house such
as a "furnace room"?
Well, there is always electric baseboards.......
Just a few quick ideas.....
JD
|
85.46 | follow-up on late, smoky starts | LGP30::FLEISCHER | without vision the people perish (DTN 223-8576, MSO2-2/A2, IM&T) | Sat Feb 19 1994 10:07 | 37 |
| re Note 47.40 by ELWOOD::DYMON:
> Hummmmmm...... sounds like a late fireup. What happens is in
> most cases, the spark isnt good enought and there is a delay
> in igniton. This gives raw oil fumes to fill the chambor and
> when it fires.....boom! Black smoke out the seams of the pipe...
>
> Granger in Worc. might have what you need for about $40 if your
> local supplier dosnt.
Well, the transformer was changed for a "new" one (obviously
not new, but new to me :-{) and the problem still persists
the same as before.
As I mentioned above, I have a friend who used to be in the
business who is helping me since I'm reluctant to call back
the burner man I was using (who charged $100 for parts and
labor for that "new" part -- and it failed to fire at all
within 24 hours)!
My friend typically examines the nozzle/electrode assembly,
puts it back together, and it runs for about a week. At
first it runs just fine and towards the end of that time I
have occasional smoky, pulsing starts before it quits
entirely. This scenario has repeated about four times now.
Even after the burner has stopped firing there is no evidence
that there is anything wrong with the electrode assembly. We
have connected the electrodes to the transformer outside of
the burner and it sparks normally -- although occasionally
with a second or two delay.
Should we just replace the electrodes and insulators? What
else could possibly deteriorate in about a week's time with
no visible failure?
Bob
|
85.47 | why? (why ask why?) | LGP30::FLEISCHER | without vision the people perish (DTN 223-8576, MSO2-2/A2, IM&T) | Sat Feb 19 1994 10:10 | 13 |
| re Note 47.42 by SOLVIT::CHACE:
> Regardless of what may or may not be wrong with your Carlin, I know
> that Carlins are more difficult than Beckets to get adjusted right.
> They seem to be more sensitive to everything. My Carlin was doing what
> yours is and I tried several things until I saw somebody selling a 1
> year old Becket for $90. I bout it, problems solved for good.
But what is there to adjust? There is the fuel/air mix, the
electrodes, and what? And the Carlin visually looks like the
same design as the Becket I saw.
Bob
|
85.48 | A few suggestions. | HDLITE::FLEURY | | Mon Feb 21 1994 07:15 | 10 |
| RE: .- a few
Sounds to me like there is a problem with the nozzle. Have you changed
it? Or perhaps the filter within the pump is clogged a bit. If the
electrical portion of the system checks out OK, start looking at the
oil supply lines. I would check all of the filters and the pump
itself. It is possible that the pump is not strong enough to atomize
the oil all of the time.
Dan
|
85.49 | fuel ok?? | ELWOOD::DYMON | | Mon Feb 21 1994 07:41 | 6 |
|
you dont have any water in your tank or a fuel jelling problem????
$100!!!! I hope he sent you a post card on his next vacation!..:)
JD
|
85.50 | clean and maintain | BUSY::CLEMENT | Smells like Nirvana | Mon Feb 21 1994 08:48 | 12 |
| I second what Dan said.
Replace the nozzle. Check the specs on the position of the electrodes
and make sure they are seated where they are suppose to be seated.
This should be in the burners owners manual.
You should replace filters and nozzle once a year. They are cheap
enough. Also make sure the electrodes are clean and not built up
with carbon. My unit was failing and I corrected it by removing all
the carbon with carb cleaner and a rag.
Mark
|
85.51 | Transformer | AWECIM::ERICKSON | | Tue Feb 22 1994 09:36 | 11 |
| The transformer may be the culprit. After 6 years, I replaced mine form $56.00
myself. The symptoms were smokey fumes, delayed start, and ... explosions.
Good luck,
The transformer is the black square box on top of the burner.
Another unrelated problem I encountered was an oily smell and no heat. I could
also hear a whizzing noise when I manually restarted the burner. The problem
turned out to be a worn plastic connection tube between the fan/motor and oil
pump. 25 cent piece.
|
85.145 | Ran duct to porch but airflow is weak. | 56821::FORSBERG | NIPG, Hub Products Group | Mon Oct 17 1994 11:00 | 13 |
| Well, it took over two years, but I finally ran the ductwork as I
asked about in .30. It was actually pretty easy and I did the job
only with 7" round ductwork. I didn't need to go to rectangular
ductwork to exit the basement or anything. It's all in and
insulated but...
The airflow is quite weak. Given that I took a 12' length of 7"
duct and added another 15' onto that, I guess I shouldn't be
surprised. The question now is: what is the simplest way to
overcome this? I've heard about in-line fans that can boost
airflow .. any recommendations or prices?
Thanks \ Erik
|
85.146 | | REFINE::MCDONALD | shh! | Mon Oct 17 1994 13:44 | 17 |
|
A few thoughts:
Is this a straight duct... or are there bends (e.g. if there is
a 90� bend it counts as [something like] another 25 feet of
straight run).
Regarding duct boosters, there are inline duct boosters for both
round and square ducts. They're often wired into the blower circuits
so they kick in when the furnace blowers kick-in. Northern
Hydraulics catalogues have them... might even be at Home Depot.
Also, if you don't have any kind of return in the room and you keep
the doors into the main house closed, you can severely limit the
flow of air into the room.
- Mac
|
85.147 | No bends except at the register. | 56821::FORSBERG | NIPG, Hub Products Group | Mon Oct 17 1994 13:53 | 6 |
| It's virtually straight (except for the end where it makes the turn
to the floor register).
There is no return except the sliding door that leads to the porch.
This is open now and will normally be so.
|
85.148 | | REFINE::MCDONALD | shh! | Mon Oct 17 1994 17:39 | 16 |
|
...then it sounds like you have two options:
1. Now that the air distribution has changed (due to the change
in length of that run) adjust all the other dampers in the
house to see if the air distribution just needs balancing.
or
2. Install a booster fan.
Regardless of which works, when the sliding door is closed the
room will pressurize and reduce the airflow significantly... but
things should flow fine with the door open.
- Mac
|
85.149 | advantages of register-mounted booster | SMURF::WALTERS | | Tue Oct 18 1994 09:38 | 8 |
|
The register-mounted booster fans don't require installation and no
additional wiring. They have an advantage that you can easily switch
them to other locations. HD sells one for $34 which has a built-in
thermostat for heating or cooling.
Colin
|
85.150 | Where to buy 7" inline booster fan? | 56821::FORSBERG | NIPG, Hub Products Group | Fri Oct 21 1994 09:41 | 6 |
| A friend looked in his Northern Hydraulics catalog and did not see
any fans of the type we've been discussing. I called Home Depot in
Nashua, NH and they sell ones for 6" diameter duct but not for 7".
So I'm still looking for a supplier of an inline booster fan for a
7" round duct. Thanks again...
|
85.151 | | SHRMSG::BUSKY | | Fri Oct 21 1994 10:01 | 13 |
| > any fans of the type we've been discussing. I called Home Depot in
> Nashua, NH and they sell ones for 6" diameter duct but not for 7".
The 6" ones would probably work. I have one that is simply a fan
mount on a curved piece of sheet metal. You cut a square opening
in the duct and then cover this opening with the fan assembly. It
wouldn't be much trouble to bend the fan mounting plate slightly
to conform to a 7" or even an 8" diameter duct.
The one I noticed about the inline booster fans, is that they are
somewhat noisy.
Charly
|
85.197 | Want to upgrade my furnace blower... | STRATA::CASSIDY | | Fri Dec 09 1994 04:21 | 20 |
| This topic is close enough. I read an article about variable
speed blowers for FHA systems. The idea is to run the blower at a
higher speed when trying to heat up a zone and then run at a lower
speed for maintaining temperature. When running at the lower flow,
the plenum will cool off slower so you'll be pumping heat longer.
This is supposed be more efficient and room temperatures should be
more stable.
What I'd like to do is install an after factory `automatic'
blower speed control to my 5 year old Becket furnace. My plan is
to switch the blower speed between medium and slow with a relay
tied into the thermostat. When the thermostat calls for heat, the
relay will be energized and toggle to the medium position. When
the thermostat stops calling for heat, the relay will default to
the slow speed position.
Sounds pretty easy, but I'm not sure about the wiring in the
furnace. I measured 28 VAC to the thermostat wires. Can I wire
the relay between the return and ground? Does anyone have sche-
matics?
Tim
|
85.198 | inside the door? | SMURF::WALTERS | | Fri Dec 09 1994 08:54 | 7 |
|
The wiring diagram should be pasted on the inside of one of the
doors - probably the fan box. Has been on most FHA furnaces that
I've seen.
C
|
85.199 | Might have overlooked it... | STRATA::CASSIDY | | Fri Dec 09 1994 23:57 | 7 |
| The diagram for the blower motor is mounted on the casing.
The panel on the fan side is insulated; I'm pretty sure there
is no shematic there. But it makes sense that there should be
one somewhere. I'll have to look around.
Tim
|
85.152 | A question of balance? | VMSSPT::LYCEUM::CURTIS | Dick "Aristotle" Curtis | Tue Jan 03 1995 00:29 | 31 |
| This looks to be about as close to my problem as I'm likely to get.
I just moved an existing duct to a new tap (on top of the plenum), and
added two more (one to the old tap on the back, one to a new tap on
the top). After getting the sheet metal work done, I realized that I
was lacking two dampers; I forged ahead anyway, expecting to fiddle
with the controls on the grillework at the ends of the ducts. They
are set to be "mostly closed" (20% of full volume, perhaps).
Turned on the furnace, and noted that the blower seemed to "pulse":
the noise it makes seems to periodically decrease, as if it's catching
its breath, and then return to what seems to be the normal level.
I tried running it for a short period without the panel over the
blower, and during the test this pulsing was absent (and the blower
pulled a fair bit of air in through the panel aperture).
Would this indicate that I've badly screwed up the balance between
ducts, or that the return (description below) is too small for the
ductwork, or some other problem?
How many minutes of run time does the system have left before the
blower blows (up), or something else goes permanently OTL?
RETURN -- it's 3�" x 12" �, with two 6"x10" grilles facing each other.
It has one 90� bend before entering the bottom of the return
plenum (tell me there's nothing wrong with that, please!)
DUCTS -- 6" round insulated flexible ductwork to the wall, feeding
3�" x 10", terminating in a 6" x 10" boot & grille (same
size as the return grilles)
|
85.274 | Two zone Force Hot Air heating systems? | LJSRV1::CAMPBELL | | Thu May 11 1995 14:41 | 15 |
| I'm in the process of having a two story house built. I like force hot air
heat, but I'd also like to have two zones - one upstairs and one down.
I talked to a heating contractor, and he tells me two zone FHA systems
are not uncommon and work fine. This these systems, there is one burner
(oil in my case) and two sets of ducks. Two baffle doors are used
to allow heat into one set of ducks (down stairs), or other set
(up stairs), or both.
I haven't been able to find anyone that has such a system.
Does anyone have a system like this?
Has anyone heard of systems like this?
Thanks for the input. Jim...
|
85.275 | | WLDBIL::KILGORE | Missed Woodstock -- *twice*! | Thu May 11 1995 15:09 | 4 |
|
I'd go for the plan that has the fewest ducks. They don't eat much, but
they sure can poop up a storm.
|
85.276 | | VMSSPT::PAGLIARULO | | Thu May 11 1995 15:24 | 9 |
| Precisely why I don't like FHA. There's nothing worse than a couple of
ducks passing air.
Just so you know why you're about to get a bunch of smart-a**ed replies,
the word is ducts. :-)
George
|
85.277 | A duct by any other name... | LJSRV1::CAMPBELL | | Thu May 11 1995 21:03 | 8 |
| Hmmm. Wise-quacks huh? &^}
So I blue it. It happens. 8^]
Come now, enough of this hot air - does anyone have experience with
these systems?
Jim...
|
85.278 | I've seen them in action - nice | STAR::DZIEDZIC | Tony Dziedzic - DTN 381-2438 | Fri May 12 1995 08:36 | 14 |
| I don't HAVE one of these systems, but have seen several; a house
I was trying to purchase (before the builder went bankrupt!) had
a two-zone forced hot air system. The plenum off the furnace was
split into two "feeds"; each feed had a motorized damper which
was controlled by the furnace electronics (which in turn used the
appropriate zone thermostat to decide when to actuate the furnace
and open the damper). The only downside (other than the additional
equipment) was that the "parallel" supply ductwork took up somewhat
more width than a single supply duct.
I would have preferred such a system, but my builder wanted an
exhorbitant amount of money to install one. Having come from
a house with (zoned) FHW, I liked the control multiple zones
gave.
|
85.279 | | BIGQ::GARDNER | justme....jacqui | Fri May 12 1995 10:31 | 7 |
|
I guess you guys don't have to do the dusting or put up
with allergies. The worst kind of heating system to put
into a home is FHA.
|
85.280 | FHA is the best | STRATA::CASSIDY | Tim Cassidy, #365 | Fri May 12 1995 21:55 | 9 |
| > I guess you guys don't have to do the dusting or put up
> with allergies. The worst kind of heating system to put
> into a home is FHA.
I use my FHA system to create a reduced pollen zone inside my
house. A good filter and a little Endust goes a long way. I like
FHA and how quickly I can heat my house.
Tim
|
85.281 | See topic 49 for sub-discussion of pros/cons of FHW vs. FHA | NETRIX::michaud | Jeff Michaud, That Group | Sat May 13 1995 22:43 | 20 |
| >> I guess you guys don't have to do the dusting or put up
>> with allergies. The worst kind of heating system to put
>> into a home is FHA.
> I use my FHA system to create a reduced pollen zone inside my
> house. A good filter and a little Endust goes a long way. I like
> FHA and how quickly I can heat my house.
I've lived in both houses heated by FHW and houses heated by FHA.
I personally prefer FHW. I find FHA drafty (wind-chill caused
by the air being moved), and find it noisier than FHW. I
also find FHW also quickly heats the living area (if anyone
finds otherwise they either don't have enough baseboard, or
undersized boiler).
The major disadvantage of FHW (IMHO) is that traditional FHW
systems need hog all that wall space with baseboard.
BTW, this sub-discussion already has a topic of it's own ....
49 TRACTR::DOWNS 22-JAN-1986 22 WHAT KIND? FHW vs FHA
|
85.282 | | SEND::KILGORE | Missed Woodstock -- *twice*! | Mon May 15 1995 12:55 | 6 |
|
.6> I use my FHA system to create a reduced pollen zone inside my
.6> house. A good filter and a little Endust goes a long way.
What do you consider a good filter? And what do you do with the Endust?
|
85.283 | So what of multiple zone FHA systems? | LJSRV1::CAMPBELL | | Mon May 15 1995 14:36 | 12 |
| The controversy of FHA verse FHW is a long one - and is covered in
other notes.
However, the question of multiple FHA zones is the subject of this
note.
I take it from the lack of response, that this is an uncommon
configuration (although someone did email me a note that explained
his *5* zone system!)?
Jim...
|
85.284 | 2 zone FHA is very common | RECV::REALMUTO | | Mon May 15 1995 14:58 | 11 |
| > I take it from the lack of response, that this is an uncommon
> configuration (although someone did email me a note that explained
I think that would be an erroneous conclusion, based more on the
way you phrased the question than the facts.
I've never seen a multi-story FHA heated home with WITHOUT multiple
zones. A split level home we owned had a 2 zone FHA system as did all the
other homes in the development.
--Steve
|
85.285 | probably depends on the local contractors | TEKVAX::KOPEC | we're gonna need another Timmy! | Mon May 15 1995 14:59 | 4 |
| Every FHA house in my neighborhood that I've been in has multi-zone
(typically 2 or 3) forced-air systems.
...tom
|
85.286 | True enough - this contractor doesn't like 'em! | LJSRV1::CAMPBELL | | Mon May 15 1995 17:40 | 21 |
| Interesting, thanks for the input. If I could ask .11, do these
homes have a single burner with two sets of ducts or two separate
burners? Where abouts is your neighborhood - Boston area? Other?
The builder I am working with is small - he builds 1 to 3 houses
at a time. He says he hasn't used single burner, two zoned FHA systems
'...in decades. They don't work'. He most often uses FHA, and
in the couple of houses he most recently built (that I went to see)
they were two story (colonial), ~2400 sq foot structures that had single
zoned FHA heat. The owners did not complain about this...
I prefer FHA, but am concerned about difficult to manage heat
distribution in a two story house with one zone. However I don't want
to go to the expense of putting a second oil burner in the basement.
A single oil burner, with two sets of ducts appropriately controlled
seems to be a reasonable solution to me, but not to my
builder. That is why I am seeking input from folks that have such a system.
Thanks, jim...
|
85.287 | | TEKVAX::KOPEC | we're gonna need another Timmy! | Mon May 15 1995 18:29 | 9 |
| This is the Amherst, MA area ("Amherst Woods"); they are all
single-burner, multi-zone; typically with A/C as well. Mostly
oil-fired, some gas-fired condensing furnaces.
They have a moderately complex controller (more than just the typical
box of relays); it might be that the reason "they don't work" is that
the controls are wrong.
...tom
|
85.288 | | NOVA::FISHER | now |a|n|a|l|o|g| | Tue May 16 1995 08:39 | 4 |
| I have a two story colonial, LP FHA, one zone. Brookline, NH.
Built in 1995.
ed
|
85.289 | | LEFTY::CWILLIAMS | CD or not CD, that's the question | Tue May 16 1995 11:16 | 7 |
| A more common system in bigger houses uses a furnace for each zone -
one in the basement, one in the attic. It cuts the ducting way down,
gives some redundancy in case one fails, but costs a bit more to put
in due to the dual furnace.
Chris
|
85.290 | Single zone can be quite comfy | SSDEVO::JACKSON | Jim Jackson | Tue May 16 1995 13:02 | 21 |
| I used to have a 2400 ft� single-level ranch house (that's right - no
basement, no upstairs). It had two 100K BTU gas FHA furnaces in the crawl
space, two independent sets of ductwork, and two thermostats. The house
was moderately uncomfortable, due to drafts, poor installation, and poor
ducts.
I'm currently in a 3800 ft� ranch with a fully finished basement. The main
part of the house, 3400 ft� (1/2 basement) is heated by a single 137K BTU
gas FHA furnace. I spent some time adjusting the air registers to get the
desired heat balance, but now in the winter it is the most comfortable house
I have ever lived in. The summer is a different issue - thanks to lots of
glass and a cathederal ceiling, the summer heat build up can be quite
intense. I've had several contractors out to quote an A/C system, and all
are quoting single-zone systems. When I asked about multi-zone, they
mentioned the problems with sizing a furnace and A/C that can work well with
a 2-to-1 ratio of ductwork and registers (when both zones are on, you're
trying to push air to the whole house, and need a certain blower size/BTU
rating. When one zone turns off, you are suddenly trying to push that same
amount of air through only half as many registers).
This is in Colorado Springs, BTW.
|
85.291 | 5 zone fha system | HELIX::LUNGER | | Tue May 16 1995 17:13 | 28 |
| I'm the one referred to earlier with a 5 zone FHA system...
Its one burner, one furnace. Two of the zones are by dampers
that are in the furnace room itself. The other three zones
are via remote dampers: the wires controlling the dampers are
routed next to the ductwork. The electronics are a bit more
complex, but once setup and working, have had no problems.
Setup was a bit tricky though, and took a bit more than
usual to debug it.
Someone mentioned the noise of FHA vs FHW.... this depends
on the ductwork used. I have metal plenums in the basement;
but the ductwork thru walls and up to rooms are fibreboard,
and thus the system is extremely quiet. The only noisy part
is the airflow at my single grate return duct.
There is an electrostatic filter that is great during the
pollen seasons. Never have to buy/replace the filter... just
slide out the electrostatic filter and spray with the
garden hose. Only additional step is to hook up a wire from
the filter to a control box (it has some air flow sensor poking
into the return duct to sense when to turn on/off the
filter).
An air-to-air heat exchanger is the last element of the system...
|
85.292 | | NOVA::FISHER | now |a|n|a|l|o|g| | Wed May 17 1995 07:52 | 3 |
| 5 zones to heat but only one return?
ed
|
85.293 | | HELIX::LUNGER | | Thu May 18 1995 13:40 | 23 |
| re: 5 zones to heat, one return
Prior to the addition, the house was a superinsulated
1-zone system. All interior doors had an extra 3/4" or so
gap between the door bottom and the floor to help air
circulation. There are 2 1-st to 2nd floor stairways
that also helps. The return duct is centralized; actually
it opens up on two sides of a wall between kitchen and dining
room. System seemed to work just fine, thank you... house
heated with 600 gallons per year, including hot water.
The addition posed new heating concerns, so the existing
system was broken into zones with dampers, and new ducts
added for the new zones. It was deemed unnessary to add
ductwork for the return. Again, system seems to work
just fine as is. Not sure yet what my yearly tally's will
be for oil... but I think its jumped to in the 800 gal range.
The main problem with the addition was the adding of
all the additional duct outlets... the fan would not be
able to supply them; thus dividing it into zones made
it more likely the fan would be supplying only a subset
of the system at any one time.
|
85.294 | dual zone heating system | CSLALL::RIZZO | | Thu May 25 1995 13:28 | 16 |
| Jim,
I just finished building a two story 36x28 colonial and utilized a
newer type of heating system called "Hydro Air" . Basically, the
system is a combination of a hot water and forced hot air system.
The boiler feeds hot water to an air handler/blower which contains a
fan and a series of coils/fins. The air handler/blower sends air across
the coils/fins and out through the duct work in the house. The system is
two zones, requiring an additional air handler/blower in the attic.
The heat from the system is not as dry as a regular FHA system, and
coupled with a good electrostatic filter is not very dusty at all. I
put the system in after recommendations from friends that had utilized
this system and have had good success with it and have been very
pleased with its performance.
Charlie R
|
85.295 | Good idea... | LJSRV1::CAMPBELL | | Fri May 26 1995 14:26 | 9 |
| Very interesting. This would seem to make multiple zone forced
hot air very easy. Although, if someone latter wanted to put in
AC, it might be a bit difficult...
What part of the world are you in? If you don't mind me asking,
do you know how much more expensive this type of system was
then a conventional, one zone system?
THanks for your input. Cheers, Jim...
|
85.93 | Atomizing Humidifier | DUNKLE::MCDERMOTT | Chris McDermott | Tue Oct 31 1995 14:16 | 13 |
| Does anyone have any recent experience with the atomizing humidifier that Home
Depot currently sells? I have a gas fired FHA system to which I need to add a
humidifier, but I am agognizing over which type to use.
I like the idea of the atomizing unit because off all the advantages mentioned
in previous relpies. However, I certainly do not want water dripping back into
the furnance.
The particular model that I saw does not use a humidistat to call atomizer,
rather the atomizer detects that the furnace/fan is on by the tempature change
in the duct.
Chris
|
85.365 | Musty smell through air ducts? | 11666::GERACE | Cindy Gerace @297-3884 | Wed Jul 10 1996 22:55 | 13 |
| I didn't see a "duct" note, so I thought I'd try here. While I have a
dehumidifier in my basement, sometimes there is still a slight musty
smell down there and it seems like the smell is coming up through the
heating vents into the rest of house. Last fall I had the ducts
cleaned, so I can't believe there's anything in them that could be
causing the smell. A friend of mine has a really musty smell in his
basement, but I've never noticed it in the rest of his house. Is
something messed up with my ducts? I only notice it in some rooms
(3-bedroom ranch), so I can't figure it out.
Any suggestions greatly appreciated!
- Cindy
|
85.366 | Sounds like a job for... | FOUNDR::DODIER | Double Income, Clan'o Kids | Thu Jul 11 1996 11:13 | 17 |
| DUCT TAPE !!!
If you have any leaks in the duct work, it could be drawing the
musty smell in through the ducts. The best way to eliminate this is to
isolate and eliminate the source of the musty smell in the basement,
if possible.
You can also check for leaks and apply duct tape to any seams that
might be leaking. Oh my god, someone may actually wind up using duct
tape for its intended purpose ;-)
Ray
Duct tape is like the force. It has a dark side, a light side, and it
binds the universe together.
By unknown author
|
85.367 | Who cleans them? | WMOIS::FLECK_S | Love me, Love my dogs, cats, etc. | Thu Jul 11 1996 12:58 | 6 |
|
Cindy,
You mention that you had your air ducts cleaned. I really need
to have mine done but don't know who to call or how much I should pay.
Can you write to me (e-mail) and let me know some more info?
Thanks Sue
|
85.368 | | 11666::GERACE | Cindy Gerace @297-3884 | Thu Jul 11 1996 13:30 | 16 |
| re: -2, thanks for the duct tape suggestion, I'll look at them tonight.
The finished part of the basement smells okay, it's the unfinished side
that smells kind of musty - like many basements! One thing that I
noticed is the filter for the furnace just slides in, so it seems like
it's possible for the basement air to get pulled through the furnace.
Is this normal? The furnace is just a few years old - the old one had
the filter in drawer that had to be opened.
re: -1
I had a company in Marlboro clean the ducts - I think the name was
Airtek or Cleantek, but I'm not positive. I can look for the receipt when
I get home. The cost was $300 for a 3-bedroom ranch w/finished basement.
It was amazing how much dust and other things (toys, nails, wood pieces)
were in the ducts.
|
85.369 | Electronic ignition test? | SMURF::HURST | | Fri Feb 07 1997 10:01 | 11 |
| Anyone know how to test the igniter output on a FHA furnace. My
electronic ignition bit the dust last night. I checked the electrode
and there doesn't appear to be a visible problem there. Cleaned up the
surfaces but still no spark. The only other possible problem there that
I can think of is a crack in the ceramic holder for the electrode. I
didn't notice any visible cracks though. Before I replace the igniter
module itself I'd like to verify that it is in fact dead. The igniter
module also controls the gas valve, heat senser, etc. That all works as
I can light the thing with a match and it works like a champ!
Steve.
|
85.370 | Xformer ? | NETCAD::MCGRATH | | Fri Feb 07 1997 10:25 | 9 |
| RE: -.1
Check the xformer input/output if you can. To create the spark across
the electrode gap the transformer must deliver several (5-10) thousand
volts.
Roger
|
85.371 | ignition control module | SMURF::HURST | | Mon Feb 10 1997 08:46 | 4 |
| I took a chance and dropped $80 on a new ignition control module. 5
minutes to install... click click click poof, we're back in business.
|