T.R | Title | User | Personal Name | Date | Lines |
---|
1013.24 | Popcorn popper's cord is hot | MRFLEX::RECKARD | Jon Reckard, 381-0878, ZKO3-2/T63 | Mon Aug 21 1989 14:10 | 8 |
| Our popcorn popper's plug got real hot last time we used it - the end that
plugs into the popper, not the wall - the rest of the cord felt ok.
I'm pretty sure I can get a replacement power cord, but I'm concerned that the
problem is in the popper, not the cord.
What should I look for that is fixable - wires with no insulation, bare wires
touching each other, etc?
|
1013.25 | Try this....... | MAMIE::DCOX | | Mon Aug 21 1989 16:46 | 15 |
| Not an uc-common problem in counter appliances and electric shavers.
If the appliance was running without this symptom for a while, then...
The cord gets flexed quite a bit during use and the flex point is often where
the wires enter the hard, molded end. Enough flexing, and some of the wires
inside each or both sides of the cord break. This causes the same amount of
current to flow through an effectively smaller wire causing heat.
It could also be that the base of the popper is getting too hot and the heat is
transferring to the cord. However, I usually fix the problem by replacing the
cord.
Luck,
Dave
|
1013.26 | | REGENT::POWERS | | Tue Aug 22 1989 10:42 | 9 |
| Another likely problem is minor crud on the plug and socket at the appliance.
This crud (oil from the popcorn popper is a good candidate) causes
a slightly higher resistance path at the plug, generating the heat.
The effect is the same as the broken wires. Slide the plug into and out of
the socket briskly a few times, then wipe off the contacts, maybe with
a Q-tip or a tissue. Note that if you replace the cord, the socket
at the appliance will remain dirty, so a new cord is only half the fix.
- tom]
|
1013.1 | | VMSDEV::PAULKM::WEISS | Trade freedom for security-lose both | Thu Sep 27 1990 12:07 | 8 |
| One other thing - DO NOT - REPEAT - DO NOT - go out and buy one of those 100 ft
16 gauge extension cords and then do a bunch of cutting with the saw on that
cord. Given the amperage a saw draws, there is just too much voltage drop,
and you'll burn out even a good motor. I have a 100 ft 10 gauge cord that I
use for the saw. It was $60, but it has saved me more than that in tools that
weren't destroyed.
Paul
|
1013.2 | | STROKR::DEHAHN | Sept 18 '90 - Hack Holocaust | Thu Sep 27 1990 12:16 | 12 |
|
That's a very good point. BTW, I was using a 50 foot 12G cord when the
B&D went south.
For the given power the saw is drawing to get through the piece of
wood; when the voltage drops, the current increases, until you either
a) trip the breaker or b) burn up the motor. Long, undersized cords
cause voltage drops.
CdH
|
1013.4 | Saws and Amps and Power Cord question | RVAX::HURWITZ | | Sat Sep 29 1990 01:22 | 20 |
| I plan on building a workbench in my basement and I originally thought
that one of those 6-outlet power strips (the kind with its own circuit
breaker built in/ available everywhere) would be good enough to
handle a circular saw as well as all my other tools. It seems sturdy
enough, but the cord from the power strip it self doesn't seem _that_
thick. I'll have to check its size. The convienience of 6 outlets
would be nice.
Would this power strip hurt the brand new but chances-are-only-10amp
saw I'm planning to buy this weekend? Coincidently the house came
with an extension cord that I found in the basement that is at _least_
1/2 inch thick with a 4 outlet square box in the end. I would just assume
use this for the bench but I'd rather use it for outside and change
the 4 outlet box to just a heavy duty single weather resistant socket.
With out having the thick cord dedicated permanently to the bench.
Will the built in breaker in the power strip save the new saw some life?
I think the breaker is a 15 amp.
Steve...........................
|
1013.5 | | QUARK::LIONEL | Free advice is worth every cent | Mon Oct 01 1990 12:05 | 8 |
| Re: .17
Those outlet strips typically have 14-gauge wire, but over a 6-foot
length, it's not something to worry about.
The breaker in the strip won't do anything for the saw one way or another.
Steve
|
1013.3 | Moved by moderator | ODIXIE::RAMSEY | Take this job and Love it! | Mon Oct 01 1990 12:21 | 22 |
| <<< SERENA::SERENA$DUA2:[000000.NOTES$LIBRARY]HOME_WORK.NOTE;1 >>>
-< Better living through DIY >-
================================================================================
Note 3985.14 Circular saws 14 of 19
VMSDEV::PAULKM::WEISS "Trade freedom for security-l" 16 lines 27-SEP-1990 13:38
--------------------------------------------------------------------------------
You can use the smaller blades no problem, they all have a 5/8" arbor. You'll
just get a little shallower depth of cut. But why are you constantly buying
blades anyway? I bought a good Oldham carbide blade when I got the saw, and
I've had it sharpened a couple of times since then. I expect the blade to last
nearly my lifetime, unless I build a couple more houses.
The cord probably has the gauge stamped on it somewhere. But if you didn't
specifically look for a heavy gauge cord, then you don't have one. My 10 gauge
cord is about 1/2" in diameter.
The standard orange cords that most places sell - the one where the cord is a
little more than 1/4" in diameter - is usually 16 gauge. This is fine for a
short cord - like 15 feet or so. The 100 foot cord is also fine for low-draw
tools like a string trimmer.
Paul
|
1013.6 | Ideas to Check OUt | ODIXIE::RAMSEY | Take this job and Love it! | Mon Oct 01 1990 12:37 | 6 |
| .re .5
You might want to review some additional notes for your side topics.
Bench Plans/ideas 179, 846, 1730, 2438
Power for Shop 816, 1037, 2987
|
1013.7 | | RAMBLR::MORONEY | Shhh... Mad Scientist at work... | Tue Oct 02 1990 21:51 | 22 |
| I looked up the resistance of (copper) wire, to see how much better the
large gauge cords were, and listed it below. I also computed the length of
cord that has the same resistance as Paul's 100' of #10 cord.
The resistance doesn't count whatever the plug/socket contributes. I don't
know how much that is except it's better to use 1 100' cord instead of 2
50' cords of the same gauge.
re .2: Is that cord homemade? I've never seen larger than #12 for sale as
premade cord.
Wire | Ohms per | Length of cord with same
Gauge | 1000 feet | resistance as 100' of #10 cord
--------+----------------+----------------------------------
8 | 0.6405 | 158.9 ft. (!)
10 | 1.018 | 100 ft.
12 | 1.619 | 61.7 ft.
14 | 2.575 | 38.8 ft.
16 | 4.094 | 24.4 ft.
18 | 6.510 | 15.6 ft. (normal 'lamp cord' extension cord)
-Mike
|
1013.8 | | VMSDEV::PAULKM::WEISS | Trade freedom for security-lose both | Wed Oct 03 1990 09:32 | 13 |
| > re .2: Is that cord homemade? I've never seen larger than #12 for sale as
> premade cord.
Nope. Bought it at my local building supply (East Coast Lumber) about 7 years
ago. Although I agree that I have seldom seen 10 guage cords elsewhere, and I
have no idea whether East Coast still has them.
I believe that the resistance of the wires is slightly higher than that listed,
because they are stranded wire. That does increase the resistance, no? The
table you have is probably for solid wire, and extension cords need to be
stranded for flexibility.
Paul
|
1013.9 | 12-3 available | ODIXIE::RAMSEY | Take this job and Love it! | Wed Oct 03 1990 12:58 | 11 |
| I was in Home Depot this week and since I have been using an 100' and a
50' 16-3 extension cords for the past 8 weeks while building my shed, I
checked to see if they carried anything other than 16-3.
Home Depot has 12-3 in both 50' and 100' lengths. The pricing seems a
bit strange. The 100' is $35 and the 50' is $38. I guess they sell
more 100' so can offer a price break. They also were pushing 16-3 and
reels for long cords. The largest I saw in stock was 12-3 but they had
relatively few in comparsion to the number of 16-3 and smaller guage
cords.
|
1013.10 | | RAMBLR::MORONEY | Shhh... Mad Scientist at work... | Wed Oct 03 1990 13:11 | 16 |
| re .9:
>I believe that the resistance of the wires is slightly higher than that listed,
>because they are stranded wire. That does increase the resistance, no?
The resistance depends on the material and the total cross-section of the wire.
As long as the total cross-section of all the strands in a "#12" cord add up
to the same as #12 solid, the resistance should be the same. However, the
copper used may be an alloy with higher flexibility than straight copper, and
if this has a higher resistivity than straight copper THAT will increase the
cord's resistance.
I got 100' of 12-3 from Spags a few months ago for $26.50. I think they want
a little more for them now.
-Mike
|
1013.11 | additional considerations | PCOJCT::MILBERG | I was a DCC - 3 jobs ago! | Thu Oct 04 1990 14:00 | 8 |
| re: .10
Bruce- the difference may be in the receptacles. The price of a good,
short extension with a triple outlet is MUCH higher than the single
outlet, longer cord.
-Barry-
|
1013.12 | Pointer to digression | ODIXIE::RAMSEY | EMT's Save Lives | Tue Feb 19 1991 09:44 | 1 |
| Also see note 4116 for some specific examples of this idea.
|
1013.27 | Bad extension cord? | ASDG::SBILL | | Mon Apr 06 1992 13:21 | 12 |
|
I looked through the electrical directories and couldn't find a note about
this subject so here goes. Yesterday when I plugged in my electric
hedge trimmer it blew a fuse. The trimmer wasn't on when I plugged it
in so I don't think the problem is there. There were two extension
cords plugged into each other, when I removed the longest one, it
worked fine (but it won't reach the hedges that I need to trim :-[).
Could it be a bad extension cord? I don't think it's very old, maybe a
couple of years and hasn't been used a whole lot. Or could it be that
I'm trying to use too long an extension cord for the circuit?
Steve B.
|
1013.28 | | FORTY2::PALKA | | Mon Apr 06 1992 13:39 | 12 |
| An extension cord which is too long wont blow fuses. It will cause a
larger voltage drop than desirable, so whatever you connect to the end
may not work too well.
If it blows a fuse it is bad. It could well be the connector at one end
or then other, so you could try replacing that. Otherwise look for
signs of physical damage. If you can find the bad section then you can
cut it out and join the cable with a plug and socket or a one piece
connector. (If you intend to use it outdoors then make sure your
connectors are suitable). It may be cheaper just to replace it.
Andrew
|
1013.29 | | VMSDEV::HAMMOND | Charlie Hammond -- ZKO3-04/S23 -- dtn 381-2684 | Mon Apr 06 1992 15:00 | 31 |
| I agree with .1 -- you have a bad extension cord.
At least one of three things is bad; maybe two or possibly all
three.
1) the plug on one end of the extension cord
2) the socket on the other end
3) the wire in between
WITH THE CORD UNPLUGGED, check for signs of physical damage. Does
the plug or socket appear to have been crushed? Is either on
cracked? Are the blades and grounding pin on the plug bent?
Loose? Are there cuts or tears in the insulation of the wire?
Does the cord cause the breaker to pop if you just plug in the
cord by itself? If so, it sounds like the socket might be bad --
causing a short when a plug is inserted.
If the plug and/or socket looks bad you can replace it/them. Cost
should be around $2-3 each. Check your friendly, neighborhood
hardware store. CAUTION: if the plug is grounded (three pins) or
polarized (one blade wider) you *MUST* connect the wires correctly
to preserve polarization. If you don't understand how to do this,
then don't undertake to replace the plug or socket yourself.
If the wire is bad consider cutting the bad piece off one end and
having a shorter cord. If its bad in the middle, considef cutting
it out and making two shorter cords.
And also consider that for safety and piece of mind it might be
better to just buy a new extension cord. Might even cost less.
|
1013.30 | My father the handyman...NOT! | ASDG::SBILL | | Wed Apr 15 1992 08:59 | 22 |
|
I took apart the socket and voila! Mystery solved! For some reason,
there weren't any wires connected to the terminals. I talked to my
father (he gave me the cord, among other things when he sold his house)
and he told me that he accidently cut the cord when he was trimming his
hedges. He thought he had either bought a replacement or repaired it.
I guess he just put the cut end back into the socket so he wouldn't
lose it and then totally forgot about it. Two of the exposed wires were
probably touching the same terminal in the socket causing the fuse to
blow.
Anyway, the repair looks straightforward enough. I just need to know
which wires to connect to which terminal. It's a polarized socket with
a ground. The cord has a green wire and a black wire and a wire wrapped
in a paper like material (I assume that's the ground). If I guess, I
know I have a fifty percent chance of getting this right ;-). If any of
you know which one is which (I'm sure a LOT of you do) I'd appreciate a
reply.
Thanks,
Steve B.
|
1013.31 | | SNAX::HURWITZ | T H I N K - B I G | Wed Apr 15 1992 17:29 | 9 |
| (someone else correct me if I'm wrong)
Green is usually ground.
Black is nuetral.
The one with paper around is probably white (?) and would be "hot".
(hows that sound?)
Steve
|
1013.32 | Almost but not quite! | VLNVAX::HEDERSTEDT | T.B.S. | Wed Apr 15 1992 17:42 | 9 |
|
Wrong....
Green is ground, White is neutral and black is hot. If this is a
110v the neutral is on the left as you face the socket. It is bigger
then the hot side. If it is 20amp outlet (110volt) the neutral looks
like a sidways t.
Wayne
|
1013.33 | | RAMBLR::MORONEY | Is the electric chair UL approved? | Wed Apr 15 1992 17:51 | 22 |
| re .4:
Black is hot and white is neutral in US electrical wiring. You have this
backwards.
re .3:
I don't like this cord! The ground is supposed to be green or bare, and
you have one of each! As described, the cord has one hot, no neutrals, and
2 grounds!
In reality, the electrons don't care about the color of the insulation.
But if anyone else opens up the cord to modify/repair it, a dangerous
situation could result.
The most important connection to get right is the ground. Determine with
an ohmmeter which wire is connected to the ground prong on the 'good' end.
That's the ground. While you're at it, determine which wire goes to the
neutral (larger prong) and hook that to the larger slot. You should have one
wire left, I think you can figure out where it goes.
-Mike
|
1013.34 | | SNAX::HURWITZ | T H I N K - B I G | Wed Apr 15 1992 21:16 | 7 |
| Sorry guys. (At least I had the green one right...)
(I just figured white = hot like "whitehot" and so far at the house
I've only added to existing wiring by adding white to white and black
to black... Time to get a good home-electricity book..)
Steve
|
1013.35 | ground UP | MEMORY::MYERS | Digital Services Engineering | Thu Apr 16 1992 09:33 | 14 |
| Re: 0.5
And just to confuse things a little more, the larger prong (nuetral)
is on the RIGHT-HAND side facing the outlet (new code) thus:
U
I
I I
I
As the ground lug is now installed UP.
Sorry for the crude drawing.
/Russ
|
1013.36 | | KEYBDS::HASTINGS | | Thu Apr 16 1992 10:33 | 4 |
| re: .7
Try thinking of BLACK = HOT as in the charred color you will be if
you make a mistake with the black wire.
|
1013.37 | | KAOFS::S_BROOK | | Mon Apr 20 1992 12:36 | 18 |
| In the PLUG, usually, the screws are coded to indicate which is
which.
The ground screw head attaching to the u shaped ground pin, is often
lacquered Green.
The neutral screw head is usually "silver" in colour, attaching to the
white or white paper wrapped wire.
The hot screw head is usually "brass" in colour, attaching to the
black (or VERY occasionally red).
(Re wire colours, be thankful you aren't in Europe where Brown is hot,
Blue is Neutral and Green or Gree/Yellow is ground!)
Stuart
|
1013.38 | | RAMBLR::MORONEY | Is the electric chair UL approved? | Tue Apr 21 1992 00:21 | 11 |
| re .10:
> (Re wire colours, be thankful you aren't in Europe where Brown is hot,
> Blue is Neutral and Green or Gree/Yellow is ground!)
...or Japan, where red is ground!
p.s. I have a US power cord color-coded with the above brown/blue/green color
code, not sure where it was made.
-Mike
|
1013.39 | White wire insulated like the other two... | ASDG::SBILL | | Tue Apr 21 1992 09:06 | 11 |
|
I made a bit of a mistake when I wrote the base note. I said that the
white wire was wrapped in paper. When I stripped back some of the
orange sheathing I found that the white wire was indeed insulated like
the other two. So, if I have this correctly, the white wire gets
connected to the wide blade (neutral) terminal, the black wire gets
connected to the small blade (hot) terminal and the green wire gets
connected to the ground terminal. Before I plug it in, did I get it
right?
Steve B.
|
1013.40 | DEC brand | ELWOOD::DYMON | | Fri Apr 24 1992 12:33 | 6 |
| rep11.
Mike,
sounds like you have a DEC power cord..... You didnt take one
home did you....! :)
JD
|
1013.41 | | RAMBLR::MORONEY | Is the electric chair UL approved? | Fri Apr 24 1992 16:05 | 10 |
| re .13:
> Mike,
> sounds like you have a DEC power cord..... You didnt take one
> home did you....! :)
Actually, it came with the house. But previous owner _was_ a DEC employee,
and it does look like a DEC power cord, so...
-Mike
|
1013.13 | | QUIVER::DESMOND | | Tue Jun 15 1993 12:26 | 29 |
| I've always heard that it's a bad idea to use extension cords in a
permanent situation but I'm not sure exactly why. We have a TV, stereo
receiver, CD player, turntable, and VCR plus a couple of 3-way lamps but
not enough outlets within reach of the cords from these. Here's the
basic layout:
____________________________________O___
| BBBBBBBBB VCR TT |
| BBBBBBBBB L TV RCV L |
O CD |
where O is an outlet
B is a bookcase
L is a lamp
and the electronic stuff is stacked up in an entertainment
center in two columns.
The receiver has two outlets in the back of it so I can plug the
TurnTable and CD player in there and then plug the receiver and the
lamp to the right in the outlet to the right. The TV and VCR will not
reach the outlet to the left and if they did, there would still be no
place to plug in the lamp to the left.
So, I thought maybe one of those power strips that are used for
computer equipment might be the way to go. Is there any reason not to
use one here? Any other ideas besides moving things around which is
not an option?
John
|
1013.14 | | LUNER::ROBERTS | I'm the NRA | Tue Jun 15 1993 16:20 | 6 |
|
I'll take a stab at one reason:
Because power cords are stranded wire and as they break down from
use/age the electrical resistance of the cord will increase? House
wiring is solid wire.
|
1013.15 | overloading is common | SPEZKO::LEMIEUX | | Tue Jun 15 1993 18:48 | 16 |
|
Mostly because people overload them. Most home type extension cords
ar 16 or 18 gauge....not exactly designed to handle an entertainment
center, lights etc all at once.
Have an outlet added to the room withing 6 feet of where you want
to place the stuff and the cords that come with the appliances will
reach. Thats really the safest thing to do.
BTW most commercial/industrial buildings are wired with stranded wire
even on the branch circuits...but then again the gauges tend to be #12
and up........
|
1013.16 | | PATE::MACNEAL | ruck `n' roll | Wed Jun 16 1993 10:59 | 3 |
| I've used one of those power strips on my audio and video equipment for
years and haven't had a problem. The strips I have have built in
circuit breakers so that should help at least notify me of overload.
|
1013.17 | re -1 | SPEZKO::LEMIEUX | | Wed Jun 16 1993 13:54 | 16 |
|
Hi,
The cords I was thinking of in my reply are the el-chepo types with
the molded plugs and receptacles. The kind you find for $1.98.
The power strips typically are made with a heavier cord. These should work fine
within reason. They usually have a decent receptacle in them which makes
better contact with the blades of the plug that is plugged in. But there are
terrible versions of these on the market also so you have to be careful when
you buy to get something of quality.
Later
Paul
|
1013.18 | You will be fine with a good power strip | SOLVIT::CHACE | My favorite season is getting nearer! | Wed Jun 16 1993 14:08 | 10 |
|
In actuality, it would be rather hard to overload a 'good' power
strip unless you plug high draw appliances (such as Microwave, toaster,
hairdryer) into them with a bunch of other stuff. Items such aas
stereos and tvs etc use faily low amounts of power. For example, a
decent power strip will be able to handle 1500 watts. A large tv will
draw 250ish, stereos 50-300, cd players like 20 watts, VCRs like 50
watts, etc. That should give you an idea.
Kenny
|
1013.19 | | PATE::MACNEAL | ruck `n' roll | Wed Jun 16 1993 14:32 | 5 |
| � The cords I was thinking of in my reply are the el-chepo types with
�the molded plugs and receptacles. The kind you find for $1.98.
�
Well, the original question was regarding the power strips.
|
1013.20 | | QUIVER::DESMOND | | Wed Jun 16 1993 18:12 | 8 |
| Actually I was wondering about those $1.98 extension cords since my
wife uses them occasionally and I wanted to be able to give her a good
reason why she shouldn't use them in any permanent situation.
But for the TV and stuff I thought the power strip would work fine and
I'm glad to hear that it's acceptable for now.
John
|
1013.21 | | SPEZKO::LEMIEUX | | Wed Jun 16 1993 20:11 | 9 |
|
re .20
Didn't catch the power strip first time around...
I must of had a brown-out :')
|
1013.22 | | DEMING::HAWKE | | Thu Jun 17 1993 08:40 | 4 |
| I looked at the cheaper extension cords at Richs yesterday and they
were rated at 1650 watts. Just FYI
Dean
|
1013.23 | about extension cords | PASTA::SEILER | Larry Seiler | Thu Jun 17 1993 18:13 | 28 |
| I believe that one reason the electrical code requires an outlet within
6' of every point along a wall is so that people will not need extension
cords for consumer appliances with standard 6' cords. I expect that this
rule was added to the code because of a high rate of burndowns that were
traced to the use and abuse of extension cords.
One of the problems with extension cords is that sometimes people route
them under rugs or in places where they can be stepped on. Stepping on
them risks trip injury, breaking the conductors, or damaging the
insulation. Putting them under a rug is an even worse fire hazard. I
believe that the light gauge wires of a cheap extension cord heat up
significantly if you actually use them at anything near their max rated
voltage. It is certainly the case that the cord attached to our electric
heater warms up significantly when it is in use, and it is heavier than
the standard cheap extension cord. Having the extension cord heat up is
ok if:
1) the insulation is rated for that heat,
2) the cord is exposed to air so that it doesn't overheat, and
3) the electrical device can tolerate a voltage loss.
That's the case with lights and heaters (if the cord isn't under a rug).
And things like TVs and VCRs don't draw enough to heat up the cord.
A power strip, however, should be fine -- so long as its cord isn't
where it can be stepped on regularly.
Enjoy,
Larry
|