292.224 | GFI's and grounding. | LDP::BUSCH | | Thu Aug 27 1987 12:08 | 16 |
| I bought a GFI outlet to install in an outdoor outlet box.
Question: Could I install the device as the outlet of an extension
wire and then use the extension plugged into a two-prong (non-grounded)
outlet? Would it offer me any protection?
I just bought a microwave oven for use in a cottage which doesn't have
grounded outlets.
Question: Should I not use it without adding 3-prong sockets and
upgrading the wiring to include grounding?
Dave
|
292.225 | | VIDEO::DCL | David Larrick | Thu Aug 27 1987 14:42 | 46 |
| > I bought a GFI outlet to install in an outdoor outlet box.
>
> Question: Could I install the device as the outlet of an extension
> wire and then use the extension plugged into a two-prong (non-grounded)
> outlet? Would it offer me any protection?
No and no:
This sort of mixture of permanent and temporary wiring is not permitted by the
National Electrical Code. Components of permanently installed wiring (e.g.
outlet boxes, wiring inside walls) and of temporary wiring (e.g. extension
cords) are used for different purposes, have different requirements for such
things as rigidity vs. flexibility, are manufactured to different standards,
etc. A GFI outlet is permanent wiring, and shouldn't be installed in a
temporary manner such as you describe.
A GFI is useless without a ground anyway.
> I just bought a microwave oven for use in a cottage which doesn't have
> grounded outlets.
>
> Question: Should I not use it without adding 3-prong sockets and
> upgrading the wiring to include grounding?
Strictly speaking, you should indeed not use it without adding grounded service.
However, you're presumably already using electrical appliances in this cottage
with the electrical service the way it is. I don't know of anything special
about microwave ovens that make them more critical to ground properly than
other types of kitchen appliances. So using the oven ungrounded probably
doesn't make your kitchen any more dangerous than it already is.
Keep in mind that internal insulation failure in any electrical appliance can
cause exposed metal parts of the appliance to become electrically charged,
often dangerously so. If your service is grounded, this condition causes a
breaker to trip or a fuse to blow right away. If your service isn't grounded,
you find out about the condition when you get a shock from touching those
metal parts. As grounded service has become common, some appliance
manufacturers have let the quality of their internal insulation slide.
An alternative to re-wiring the entire cottage is just re-wiring the kitchen.
An even simpler workaround is to use a 3-prong-to-2-prong "cheater" adapter,
and run a wire from the adapter's grounding lug to a convenient ground such as
a water pipe.
|
292.226 | Might be grounded | CADSE::MCCARTHY | N�, N�, N� and N� | Thu Aug 27 1987 15:11 | 7 |
| Another note, are you sure that you have no ground at the outlets?
Alot of older houses use BX (metal sheathed) wire and only used
two-prong outlets. The outlet box is grounded because it touches
the metal sheath. You may just have old outlets. Don't just replace
them with new ones until you check it out.
mac
|
292.227 | Portable GFI ? | LDP::BUSCH | | Thu Aug 27 1987 16:56 | 13 |
| Re .28 & .29
The reason I asked about putting a GFI in an extension wire is that
quite frequently I have to use portable power tools at the cottage,
and sometimes right down at the waterfront. I was under the impression
that a GFI operates by sensing the difference between the incoming
current and the current returning on the neutral line. If there
is a difference, the circuit breaks. If that's the case, then what
is the additional ground needed for? Besides, I had no intention of
trying to defeat the purpose of the electrical codes. As I asked before,
are my fears "groundless" (pardon the pun) ?
Dave
|
292.228 | Extension cords with GFI outlets | HOBBIT::GUERRA | | Thu Aug 27 1987 17:02 | 3 |
| I don't know where you live or if it helps at all, but for what
it's worth, Spag's has extension cords with GFI outlets on the end.
Perhaps some other store near you carries them, too.
|
292.229 | Get a GFI extension cord | RIKKI::CBUSKY | | Thu Aug 27 1987 17:05 | 9 |
| I have recently seen an extension cord/GFI outlet combo. Its a heavy
duty extension cord with GFI protected outlets molded in plastic at one
end. It's ideal for protecting your self while doing those outside
chores.
As stated earlier though, it has a grounded plug that shouldn't be
compromised.
Charly
|
292.230 | | STAR::GOLDSTEIN | Andy Goldstein, VMS Development | Fri Aug 28 1987 00:34 | 5 |
| Re .29: It would take me all night to find it in the code, but as I
recall, BX sheathing is not considered a suitable ground. At least,
I was brought up to consider this a no-no. It has too high a
resistance, and the connection between the sheath and the box may
corrode and get flaky.
|
292.231 | | AUTHOR::WELLCOME | Steve | Fri Aug 28 1987 10:24 | 7 |
| re: .33
As I understand it, there's a metal strip inside the BX to provide
a good ground path. You should see it when you cut the BX. I think
you bend the strip over the end of the BX so it gets clamped by
the cable clamp on the box, and that provides the ground. (My
knowledge of how to work with BX is minimal at best, so anybody
else who knows better please correct me.)
|
292.232 | that little metal strip | CADSE::MCCARTHY | N�, N�, N� and N� | Fri Aug 28 1987 12:54 | 10 |
| re: -1
You are correct. There is a thin metal strip (not a
wire, its flat) inside the metal sheath. After the BX has been
cut, and the plastic insulator has been put in (my boss called them
"red caps") the metal strip is wrapped on the outside of the BX
a distance long enough so that it will contact the metal box you
are bringing the wire into. I would like to know if it is not a
"valid" ground, but I do think it is.
mac who_hates_to_work_with_BX_but_will_take_money_any_way_he_can_get_it
|
292.234 | BXnot referenced in the code | HPSVAX::POWELL | Reed Powell (HPS/LCG Marketing | Fri Aug 28 1987 18:42 | 2 |
| FYI, the electrical code makes no mention of BX at all, making me
think it isn't "supported" any mor-reed
|
292.235 | BX is a brand name.... | TOOK::CAHILL | Jim Cahill | Fri Aug 28 1987 19:16 | 5 |
| try looking for "armored cable" in the code. I'm 99% sure the code
still allows it, as it's discussed in all three of my DIY electrical
books (I don't need them, I just like looking at the pictures! - (:> )
Jim
|
292.236 | Still Ok to use (don't mail this out though :-) ) | CADSE::MCCARTHY | N�, N�, N� and N� | Fri Aug 28 1987 20:01 | 5 |
| I know it is still allowed. Go look at any new construction where
steel 2 by 4's are being used. Every time I have seen these walls
there has been BX (armored cable) used in them.
mac
|
292.237 | Oh ya, older BX and the strip | CADSE::MCCARTHY | N�, N�, N� and N� | Fri Aug 28 1987 20:15 | 6 |
| RE: -3?
Older BX (I am not sure when they started) does not have the
flat strip inside.
mac
|
292.238 | | STAR::GOLDSTEIN | Andy Goldstein, VMS Development | Fri Aug 28 1987 23:16 | 9 |
| OK, I stand corrected. This evening I was awake enough to dig through
my 1984 electrical code. 250-91(b) says:
"Types of equipment grounding conductors. The equipment grounding conductor
run with or enclosing the dircuit conductors shall be one or more or a
combination of the following: (1) a copper or other corrosion-resistant
conductor .... (6) armor of Type AC cable ..."
AC is the generic code for so-called BX. (Got that?)
|
292.239 | | Q::ROSENBAUM | Rich Rosenbaum;mail->Boehm::Rosenbaum | Mon Aug 31 1987 09:55 | 2 |
| BX would not be in the code as it is a trademark (you don't find
Romex either).
|
292.240 | Type AC: dos and dont's from the code | HPSVAX::POWELL | Reed Powell (HPS/LCG Marketing | Mon Aug 31 1987 23:28 | 18 |
| OKOKOK! I never realized BX ws the trademark; armored cable I know
about. The code's description (section 333-4) "Cables of the AC
type, expect ACL [lead covered conductors for areas exposed to
weather], what have an internal bonding strip of copper or aluminum,
in intimate contact with the armor for its entire length." Nothing
in section 333-9 on boxes and fittings mentions the internal strap
- just that you have to have a fitting that clamps to the armor
for grounding. AC is legal for branch circuits and feeders, for
both exposed and concealed work, and can be fished through walls,
etc., except in damp locations (where type ACL must be used). OK
to run AC through the air voids in concrete blocks or tile walls.
Cannot bury AC in the earth - must be in a conduit. In attics
with non-permenant stairs for access, it only needs to be protected
with guard strips for the area within 6' of the entrance/scuttle
hole; otherwise it has to have the guards along the entire length.
It can be run along the exposed underside of floor joists in basements
if not subject to physical damage.
-reed
|
292.241 | flex conduit | Q::ROSENBAUM | Rich Rosenbaum;mail->Boehm::Rosenbaum | Tue Sep 01 1987 10:56 | 9 |
| Just to add to the armored cable trivia here, there is also a variant
of wiring in which wires are inserted into flexible conduit. This
conduit looks just like the armor of type AC.
In the tradition of BX and Romex, this is also commonly known under
a tradename. This name escapes me at the moment but I think it
begins with "Green.." something.
Rich
|
292.242 | Greenfield tubing... | 3D::WHITE | Randy White, Doncha love old homes... | Tue Sep 01 1987 11:33 | 9 |
| RE:1204.44
> In the tradition of BX and Romex, this is also commonly known under
> a tradename. This name escapes me at the moment but I think it
> begins with "Green.." something.
Greenfeld or Greenfield tubing is just the flexible armor sheathing
into which you snake the individual wires. Often used for the feeder
from junction box to recessed light.
|
292.243 | FLEX (brand name?) | CADSE::MCCARTHY | N�, N�, N� and N� | Tue Sep 01 1987 12:23 | 11 |
| RE:.44
When I was working as an apprentice, this stuff was refered
to as "FLEX". We used to make the connections between the switches
on the side of gas furnaces to the motor. There is a code ruling
that says something about no-plastic sheathed cable within some
distance of a furnace. The FLEX made things easy.
The FLEX (again probably a brand name) is alot more flexible
then the armored cable and it comes hollow (no wire).
mac
|
292.31 | GFCIs - How Do They Work? | DECWET::MCWILLIAMS | Brian @ DECwest, 206.865.8837 | Fri Oct 30 1987 14:57 | 11 |
|
I was told that any electrical outlets in wet places (bathrooms, kitchens)
should have "Ground Fault Circuit Interrupters" on them.
For the record, could someone explain exactly what they are and how to replace
an old-style outlet with a GFCI?
- Brian
|
292.32 | they see leakage current | REGENT::MERRILL | can you say Par Value? ... | Fri Oct 30 1987 15:21 | 12 |
| layman's explaination: they detect that all the current that is
coming in over the "hot" line is not going out over the "common"
line and it then throws its own local circuit breaker. If the
"lost" current is about 5ma(?) or more it assumes that either you or
something else is conducting the "lost" current.
If by "old style" you mean a two prog outlet, you'll have to supply
a good ground wire; otherwise I believe you just replace the old
outlet.
rmm
|
292.33 | | VAXWRK::INGRAM | Larry Ingram | Fri Oct 30 1987 15:31 | 20 |
| In simple terms, the GFCI monitors the current passing through
the hot (black) and neutral (white) wires downline of the unit.
If there is parity, that is the same amount of current going
through the hot wire is the same as the amount of current coming
back through the neutral wire, nothing happens.
However, if there is a difference between the two of ~40 ma,
the unit trips. This could occur if a razor were to fall in a sink
or if you were to use a defective power tool (hot tied to metal)
on wet grass (good gound). Some of the current would return through
ground (water and drain pipe with the razor example, you in the tool
example) rather than neutral. A circuit breaker would only trip if
it's rated capacity were exceeded. Probably too late.
GFCI outlets also have a "pass through" feature. This allows outlets
past the GFCI to be protected also. Hookup instructions are provided
with the unit. It is not much more difficult to install than an
ordinary outlet.
Larry
|
292.34 | just a comment | YODA::TAYLOR | | Fri Oct 30 1987 15:37 | 8 |
|
I've seen where an electrician placed in a run the gfi in
the kitchen and standard sockets in both baths in effect
giving the protection to the three areas with a third the
cost. Just a comment............
|
292.35 | Good Idea Cheap | LDP::BURKHART | | Fri Oct 30 1987 16:10 | 13 |
| RE .3
This is a good thing to think of when doing a new wire
job. I just finished the rough in on a sunroom and new deck and
planned for a single GFI outlet to take care of all the outlets
in the room and on the deck. Its just a matter of making the first
place your power FEED goes, the GFI recptacle. After that every
thing down line from it is protected.
My 3� worth...
...Dave
|
292.36 | Don't go overboard | VIDEO::DCL | David Larrick | Fri Oct 30 1987 17:05 | 7 |
| As has already been pointed out elsewhere in this conference, I think:
Don't go overboard with many outlets downstream from a single GFI. Remember,
you have to find the GFI to reset it when it trips. If it's many steps (or
even floors) away from the outlet that made it trip, finding out what went
wrong could become extremely inconvenient, even dangerous if lighting or
other safety gear is involved.
|
292.37 | mark downstream outlets | Q::ROSENBAUM | Rich Rosenbaum;mail->Boehm::Rosenbaum | Sun Nov 01 1987 19:21 | 7 |
| Some GFCI outlets are packaged with a bunch of "Ground Fault Protected
Outlet" stickers that you can place on downstream outlets. This
is useful for 1) extra piece of mind when plugging something in
them, and 2) tracking down the problem when one of the outlets seems
to be inoperative.
__Rich
|
292.38 | nother 2 cents | XANADU::SCHNEIDER | Dennis Schneider | Mon Nov 02 1987 09:57 | 22 |
| I finished a basement playroom for my kids - put in ONLY GFCI-protected
outlets since GFCI's provide some protection from electrocution - (but they
aren't 'perfect' since you can electrocute yourself across the hot and neutral
without creating a ground fault). I figured the most likely case is
metal-object-poked-into-hot-side-of-outlet which will trip a GFCI.
A couple of 'practical' notes:
1. GFCI outlets are large (physically) - so cut excess wire lengths inside
the circuit boxes to a minimum to avoid 'cramming'.
2. The special cover plates are generally flimsy - tighten screws carefully.
3. If you do replace an outlet in a line with a GFCI, make SURE it's the
FIRST one in line. The only 'REAL' way to be sure in a house you didn't
wire is: Turn power to the line off; disconnect the rest of the line of
outlets from the outlet you plan to replace; Turn ALL OTHER CIRCUITS IN
THE PANEL off; turn the line you're working on back on: Now NO outlet except
the ONE you plan to replace should have power (a lamp makes a good tester).
Dennis
|
292.39 | A correction... | VAXWRK::INGRAM | Larry Ingram | Mon Nov 02 1987 10:38 | 5 |
| The reply I made stating that the GFCI will trip if it detects
a 40ma difference between hot and neutral should have read 5ma.
The time to trip is ~40ms.
Larry
|
292.40 | cold toes blues | HPSVAX::SHURSKY | Is it spring yet? | Wed Nov 04 1987 09:31 | 7 |
| re: .3 and others
If you are so cheap as to do this, tell the next owner of your house.
It is a royal pain in the a** to run around a 60 deg (I'm cheap
too) house in your nightie to find where the last owner (cheap bugger)
put the GFI receptacle when your electric razor trips the damn thing
in the morning before work.
|
292.41 | once, maby twice | YODA::TAYLOR | | Thu Nov 05 1987 07:42 | 6 |
|
re: .9
Your scenerio should only happen once, and, in your case, perhaps
twice if you have two baths in your house.
|
292.42 | I am not that cheap! | HPSVAX::SHURSKY | Is it spring yet? | Fri Nov 06 1987 11:15 | 6 |
| re: .10
It is still cold even if I know where it is. I put a GFI in the
master bathroom.
Stan
|
292.43 | GFI outlet or Breaker | TOLKIN::RIDGE | | Mon Dec 07 1987 12:55 | 8 |
| In my house I have a GFI circuit breaker, so everything on the
circuit is protected. Are there any pros/cons as to which installation
might be better. 1) A GFI outlet in the first outlet box in a loop,
or 2) a GFI in the pannel.
I don't think that cost is much of a factor.
|
292.44 | GFI packaging comparison synopsis | VIDEO::DCL | David Larrick | Mon Dec 07 1987 13:37 | 19 |
| re .12, outlet GFI vs. breaker GFI
This question has been touched on in several topics in this conference. The
consensus, as I remember it:
1. Convenience/safety: when a GFI trips, you need to be able to get to it,
both to find out that it has indeed tripped and to reset it. If it's in
the breaker panel, it's pretty much guaranteed to be inconveniently
located. That inconvenience becomes a safety problem if your path to
the breaker box is normally lit by lights on the tripped circuit.
2. GFIs packaged as breakers seem to be less reliable than ones packaged as
outlets.
3. Cost is indeed a factor - the breaker-packaged GFIs are more expensive.
#2 and #3 may change as the technology matures. But it appears as though
the outlet-packaged GFIs are more popular, and hence they're receiving the
attention, technology improvements, and cost reductions.
|
292.45 | | CIMNET::LUNGER | Dave Lunger, 291-7797, MET-1/K2 | Tue Dec 08 1987 15:29 | 10 |
| another point:
You use a GFCI breaker when you want to protect something other than
outlets... for example, a jacuzzi.
The breaker is usually less reliable because there is more wire for the
GFCI to detect faults in. If you use an outlet, you don't protect
the circuit from the panel to the first GFCI outlet, thus making
the GFCI circuitry more reliable for the wire it does protect.
|
292.46 | Can't Reset GFCI | DECWET::MCWILLIAMS | Brian @ DECwest, 206.865.8837 | Mon Jan 25 1988 17:19 | 22 |
|
I was installing a new GFCI-protected outlet in my bathroom, taking advantage
of the "downline" protection feature mentioned in previous notes. The main
device I wanted to protect was the shower exhaust fan, but the overhead
light is also on the same branch circuit.
When I went to test out my new wiring job and flipped on the breaker in the
breaker box, I heard a small "pop," and groaned when I realized I must have
goofed up my wiring somewhere. I flipped the breaker pole to off again, and
went to check the GFCI. The RESET button was still pushed in, so I wasn't
able to reset it. Pushing the TEST button produced no results either.
According to the instructions that came with it (Leviton makes it), when
this happens, I'm supposed to "CALL A QUALIFIED ELECTRICIAN!" (emphasis
theirs).
I refuse to give up so easily. Assuming I can figure where I goofed in
my wiring, can anyone explain what has happened to the GFCI?
Thanks,
Brian
|
292.47 | Here's my understanding of it | HPSMEG::LUKOWSKI | I lost my A$$ in the '87 CRASH! | Mon Jan 25 1988 17:57 | 11 |
| I'm not sure I understand why you expected the GFCI to trip if
there was in fact a problem with the wiring. If the fault is after
the GFCI, then I would expect it to trip but if the fault was with
wiring the GFCI or before it, I wouldn't expect it to trip. I don't
know if a short would trip the GFCI because it is measuring the difference
between hot and neutral and with a short between hot and neutral
they would still be the same. As far as the reset button is
concerned, this only works when power is applied...at least with
the Leviton's.
-Jim
|
292.48 | | TOLKIN::RIDGE | | Tue Jan 26 1988 12:34 | 3 |
| Have someone turn on the breaker while you watch the GFI. You might
be able to spot the problem. GFI's, being large, are you sure it
isn't touching the side of the box?
|
292.49 | what else could cause a GFCI to trip? | TOOK::CAHILL | Jim Cahill | Tue Feb 23 1988 22:17 | 27 |
| (Since I can't find a better place for it, I guess I'll stick this
question in here.)
I was over a friend's house last night, installing a ceiling fixture
in the bathroom to some wiring that someone else had previously run.
A GFCI-protected outlet was nearby, apparently installed downstream
from the light. After the light was installed and power turned
back on, we noticed that the GFCI would sometimes trip just as the
light switch was turned off or on. When this happened, the ceiling
light would still operate (thus, I concluded it was upstream from
the GFCI, which therefore could not be protecting the light/switch
wiring).
As I thought about what could be causing this behavior, I remembered
reading that GFCIs seem to go bad fairly often. I wondered if maybe
it was a little soft, and some voltage fluctuation as the switch was
thrown could be tripping it. Does this sound reasonable? Since no
movement of wires is involved, I find it hard to believe a loose
wire rubbing against something it shouldn't be is at fault. The
lights and outlets in this bathroom have never been used, as the
owners were using a light placed on the sink and an extension cord
run across the floor from the bedroom (that's another story!).
As a next step, I suggested replacing the GFCI. Any comments or
different suggestions would be appreciated.
Jim
|
292.50 | I'm lost | DECWET::MCWILLIAMS | Brian @ DECwest, 206.865.8837 | Wed Feb 24 1988 14:06 | 9 |
| RE. -1
I can't quite visualize your set-up. You say the GFCI is "downstream" of the
light and yet it is not "switched" by the light switch (the GFCI still has
power when the light is off, right?).
So how does the GFCI get its power feed?
B.
|
292.51 | 1 picture = 1000 amps | TOOK::CAHILL | Jim Cahill | Wed Feb 24 1988 15:05 | 26 |
| Yes, the GFCI does still have power when the light is switched off.
Perhaps "downstream" was a poor choice of words. I didn't do the
wiring, so I can only guess. Here's a picture:
power ]--------white----+---------------------------------+
source ]------black----+---------------------------------+ |
| | | |
| | +--------+
+--------+ +---------+ +--------+ | GFCI |
| 3-way |====| light |====| 3-way | | outlet |
| switch |----| fixture |----| switch | +--------+
+--------+ +=========+ +--------+ | |
| |
v v
The power source is probably a feed from
other outlets, lights, etc. feed to
additional
outlets
From the above, I can't see how a fault in the wiring for the light
would lead the GFCI to trip. Also, why should it only trip some
of the time when one of the light switches is moved? If it's a
fault, I would think it would trip all the time, given that wires
are not being moved about.
Jim
|
292.52 | | HPSMEG::LUKOWSKI | I lost my A$$ in the '87 CRASH! | Wed Feb 24 1988 15:43 | 4 |
| Was this by any chance a fluorescent light?
-Jim
|
292.53 | | TOOK::CAHILL | Jim Cahill | Wed Feb 24 1988 17:12 | 4 |
|
Nope, it's a regular 60-w incandescent light bulb.
Jim
|
292.54 | | VIDEO::DCL | David Larrick | Wed Feb 24 1988 17:29 | 9 |
| Sounds to me like there's something wrong with the continuity of the ground
as it makes its way through those upstream switch boxes, so the GFCI is
rightly tripping.
Although the diagram in .20 shows a splice in the supply wires themselves,
separate from the light and switches, the splice is of course actually
inside one of the boxes, probably one of the switch boxes. So check the
switch boxes to see which one has a splice in it, and look for a ground
continuity problem there.
|
292.55 | | MENTOR::LUKOWSKI | I lost my A$$ in the '87 CRASH! | Thu Feb 25 1988 10:04 | 22 |
| Re: .23
I'm not sure I understand what you are saying about the ground
continuity causing the GFCI to trip. It is my understanding that
the GFCI does not use the ground but monitors the difference between
hot and neutral and if the difference reaches its threshold, it
trips. This made sense to me because the code* specifies that if
you don't have a ground when replacing a two prong receptacle, you
must either replace it with another two prong receptacle or a GFCI
receptacle. Also, I had a problem a while back in which the ground
in one of my circuits had approx 50 volts in it and yet the GFCI didn't
trip so this also reinforces my understandings above. What had happened
was that someone had spliced a piece of wire in the circuit that had no
ground and the voltage was being induced into the ground. I suspect
in this case that there may be a problem with the neutral. Possibly,
one of the outlets is using ground instead of neutral and is causing
the trip.
*Code in this context refers to 'Wiring Simplified' by Richter and
Schwan
-Jim
|
292.56 | Do florescent lights confuse GFCI | REINIG::REINIG | This too shall change | Tue Mar 22 1988 20:44 | 7 |
| Why the question abour florescent lights? I have trouble with a GFCI
circuit breaker that is in my power panel. This GFCI triggers fairly
often in the summer, but never in the winter. There is a florescent
light on this circuit. The triggering doesn't seem to be tied to
anything that I've noticed. Any ideas?
August G. Reinig
|
292.57 | Maybe you have a summer ground fault | RGB::SEILER | Larry Seiler | Wed Mar 23 1988 01:08 | 7 |
| Maybe there is dampness in the wiring somewhere causing a weak trickle
to ground, that every now and then reaches the critical point and trips it.
In the winter the air would be drier so maybe that's below critical.
Or maybe the thing overheats in some fashion? Doesn't seem likely.
I can't think what flourescent lights would have to do with it.
|
292.58 | | ULTRA::PRIBORSKY | That's the stuff dreams are made of. | Wed Mar 23 1988 10:03 | 5 |
| I had a problem with a GFCI and a flourescent light in my bathroom, the
GFCI would trip when I turned on the light. The electrical supply house
refused to believe that it was a problem with the particular GFCI. I
switched to a different GFCI brand (Leviton), and the problem went
away.
|
292.59 | | HPSMEG::LUKOWSKI | I lost my A$$ in the '87 CRASH! | Wed Mar 23 1988 10:27 | 12 |
| Re: .25
I asked the question about the fluorescent light because of a
situation such as yours that was mentioned to me. From what I
remember, it was a GFCI breaker that was tripping. The person had
checked out the entire circuit but could find nothing wrong. He
finally disconnected the fluorescent light that was on the circuit
and the problem went away. I do not know why this would happen with
a fluorescent light, just that one was determined to be the cause of
this problem.
-Jim
|
292.60 | buy GFCI outlets at Spags | CLT::ZEHNGUT | | Wed Mar 23 1988 12:37 | 5 |
| As an aside... I just replaced a GFCI outlet in a bathroom. After
seeing prices range from $17-$25 for these things (Leviton brand),
I got it at Spags for $8.50.
Marc
|
292.61 | | HPSMEG::LUKOWSKI | I lost my A$$ in the '87 CRASH! | Wed Mar 23 1988 13:10 | 7 |
| Re: .29
Note that the $8.50 price is their sale price. I believe they
will be at this price until the end of the week. Their normal price
for GFCI's is around $13.50 but they do go on sale often.
-Jim
|
292.62 | Spag's Price $9.88 | ELWOOD::DUFORT | | Thu Mar 24 1988 08:12 | 0 |
292.63 | Check the innards of the Flourescent Light | BIMINI::SCHNEIDER | Dennis Schneider | Thu Mar 24 1988 16:10 | 9 |
| A properly wired non-defective flourescent light should not trigger an equally
properly installed non-defective GFCI.
I'd suspect ground leakage in the flourescent ballast. Since the Ballast
is bolted to sheet-metal which is wired to safety ground, a leak there would
do the trick.
Dennis
|
292.64 | another gfci problem.... | NSSG::ALFORD | another fine mess.... | Tue May 24 1988 15:46 | 16 |
| Not having much experience with electrical stuff...I will try
to explain a problem I am having with an outside GFCI.
Yesterday I plugged in the weedeater and -- nothing -- so, I
thought, hmmmm...circuit must have tripped....reset the gfci...
nothing happened. So, tried resetting the breaker....nothing
happened. Now, this particular gfci is on the same circuit
as two inside lamp outlets, and they work okay. So, did
the gfci go bad, or is there a "leak" somewhere? Please say
it's the outlet, cuz all the wiring is in an essentially
non-accessible crawlspace!!
Thanx for any help on how to troublshoot this stupid thing!
Deb
|
292.65 | Isolate the failure | VIDEO::DCL | David Larrick | Tue May 24 1988 16:35 | 15 |
| Are you sure the weedeater works properly?
Has this outlet ever worked properly?
Many GFCIs have pilot lights - does yours? Is it lit?
Is the GFCI unit right there in the outdoor box, or does the outdoor box
contain a regular outlet, protected by a GFCI somewhere upstream?
Are there any more outlets downstream of this one, or is it the end of the
line?
The answers to the above questions should suggest things to try. Note that
wiring failures usually occur inside boxes (connections and devices); cables
seldom fail.
|
292.66 | some answers,,,more questions | NSSG::ALFORD | another fine mess.... | Tue May 24 1988 16:42 | 28 |
|
Well, to answer those questions...which may shed more light on
the situation..
Yes, the weedeater works...I used another outside outlet after
this gfci failed.
No, it doesnt have a "pilot light" --- and it is installed right
in the box.
I assume its the last thing on the circuit, as the other outlets
work okay.
I have a feeling that somehow when the folks next door were
building their house, and "borrowed" my electricity at this
box, they used some saw, or whatever too big, and "blew"
the gfci itself. Is that possible??? I do not know if it
has worked since then, as yesterday was the first time I
tried it.
Pushing in the test button does not cause the reset to pop
as it does on the gfci in my bathroom....so, something
somewhere is wrong, and I will replace the gfci, if I can't
decide anything could be the problem.
Any other possibilities???
Thanx
Deb
|
292.67 | | SMURF::WALLACE | Life's a beach, then you dive! | Tue May 24 1988 17:48 | 8 |
|
Just a thought.
GFI's are very sensitive to moisture. I don't know where you
live, but if it's in New England, we have had quite a few days of
rain here lately, which may be inhibiting it's functionality. I
would wait till you get a good dry day (if this situation applies)
and then try it again.
|
292.68 | yes, in taxachusetts | NSSG::ALFORD | another fine mess.... | Wed May 25 1988 09:36 | 11 |
|
Yes, I do live here in beautiful "mud england" ---
sheesh, have you ever seen so much rain!! I dug up
flowers last night which had rotted out at the roots due
to the excessive moisture.
In any case, I will wait till things dry up (soon hopefully)
before replacing the gfci.
Thanx for the tip.
Deb
|
292.69 | | VIDEO::DCL | David Larrick | Wed May 25 1988 09:56 | 7 |
| If you open up the box, you can determine with a meter or test lamp whether
power is getting to the box at all. If so, the problem is in the GFCI. If
not, it's in the wiring someplace upstream.
Being basically lazy, I would wait until things dry out. (Safer to open up
the box then anyway). If I became impatient, I might help things along
with a hair dryer or heat gun.
|
292.70 | GFCI and outdoors don't mix | ALEX::CONN | Alex Conn, ZKO | Wed May 25 1988 12:48 | 13 |
| I've had a lot of trouble with GFCIs exposed to the elements (i.e., not
strictly indoors). Things seem to work a lot better when an
outdoor or breezeway outlet is wired to the load side of an indoor GFCI.
Maybe the problem has been moisture, but then, in New England that
means your GFCI will be out of service a lot of the time. ;-)
They now sell (or you can easily make) a portable GFCI outlet. You plug
the thing into a standard outlet and then your extension cord into the
portable outlet. Your extension cord is now GFCI protected. You can
store the portable GFCI outlet indoors so that it will be dry and in
service when you need it.
Alex
|
292.71 | GFCI WON'T TRIP | TOLKIN::GUERRA | We must be over the RAINBOW! | Wed May 25 1988 13:28 | 10 |
| I have another GFCI problem. I recently finished my second floor
and installed one of these in the new bathroom. This was about three
months ago and it was working fine. The other day I went to test
it and it won't trip. There is electricity in it and in the other
outlet down the line. What could be causing this? Is it time to
get a new one? I would expect it to last longer than three months.
After all, the one downstairs is three years old and works fine.
With so many GFCI problems on this note I am starting to wonder
if this is some kind of a communist plot :-). Any ideas will be
appreciated.
|
292.72 | GFI/GFCI mortality | SEESAW::PILANT | L. Mark Pilant | Wed May 25 1988 13:39 | 19 |
| RE: .40
As I have been led to believe, GFCIs have a rather limited life
expectancy, usually a couple of years. Unfortunately, this
also seems to include the shelf/storage time. So, if you got
one which had been sitting around for a while it may not last
very long in service.
I discovered this when I had a couple of GFI breakers go bad after
about a month after I installed them. I took them back (to Ralph
Pill) because they had a year guarantee. Well it turns out that
the guarantee is for a year from manufacture, not from point of
sale. Maybe this is the manufacturer or simply the nature of the
beast; I'm not sure.
Anyway...No, I wouldn't be surprised to see a GFI outlet go after
only a couple of months in service.
- Mark
|
292.73 | What is it rated for? | AD::DIPINTO | | Wed May 25 1988 13:43 | 8 |
|
Does anyone know how much current the downstream side of
a GFCI receptacle is rated for?
Thanks
Len DiPinto
|
292.74 | Are they all junk ??? | TOOK::ARN | Tim Arn LKG2-2/BB9 226-7572 | Wed May 25 1988 14:02 | 8 |
| I had the GFI in my bathroom go after two months also. It provides
electricity but won't trip when you push the test button. It happened
right after I used an electric drill in the outlet. My brand was
a Levitron. Maybe if we post all the brands that fail, people can
avoid these when installing new ones.
Tim
|
292.75 | 20 amp ratings | ULTRA::WITTENBERG | Secure Systems for Insecure People | Wed May 25 1988 14:16 | 14 |
| >< Note 1659.42 by AD::DIPINTO >
> -< What is it rated for? >-
>
> Does anyone know how much current the downstream side of
> a GFCI receptacle is rated for?
>
The ones I just bought (Leviton) are rated at 15 amps to the
outlet and 20 amp total. That is if you install them as the first
outlet in a 20 amp circuit, each duplex outlet is good for 15 amps
up to a total of 20 amps. Presumably all 20 amps could be in
downstream outlets.
--David Wittenberg
|
292.76 | They may not like being overloaded | PSTJTT::TABER | Touch-sensitive software engineering | Wed May 25 1988 15:01 | 11 |
| > It happened
> right after I used an electric drill in the outlet. My brand was
> a Levitron.
I had a Leviton croak shortly after a contractor plugged a sawzall into
it. I croaked another when I had a few blade stalls with a circular
saw. I think they might not do well under that kind of load, because
there are two other GFIs in the house from the same lot that that have
never been used for power tools, and they are working just fine.
>>>==>PStJTT
|
292.77 | Plugged my drill on it. | TOLKIN::GUERRA | We must be over the RAINBOW! | Wed Jun 01 1988 11:45 | 3 |
| Mine is also a Leviton. I have plugged my drill on it a few times.
Could it be a problem with the brand not being able to handle power
tools?
|
292.1 | no | RAMBLR::MORONEY | The purpose of diplomacy is to prolong a crisis | Tue Jun 07 1988 00:03 | 0 |
292.2 | GFI Circuit Breaker Keeps Tripping | RICKS::PEKKALA | The Tape Man | Tue Jun 28 1988 11:19 | 39 |
| I've got a problem with my GFI breaker... this is the story...
During the Winter, I noticed that my exterior garage light would go out
if I turned it on during a heavy snow. Each time it went out, my GFI
breaker had tripped.
I managed to put up with the problem, because I thought that I knew what
the problem was, i.e. somewhere, somehow a wee bit of snow was getting
into an exterior socket and tripping the breaker.
The problem seemed to go away in the Spring, or maybe I just didn't use
my exterior lighting all that much. But, anyway, its now the Summer
and I'm back to base 1.
I've explored deeper into the problem. I have confirmed that if I plug
anything at all into any of my exterior plugs, no matter what time of
the day or weather conditions, the GFI immediately trips.
I'm also reasonably convinced, that if I unplug certain "heavy" juice
items in the house, like a refrigerator for instance, the GFI can also
trip, yet these items are not necessarily on the GFI circuit.
Both of my bathrooms, my garage lights and sockets, my exterior lights,
and all of my exterior plugs are wired to the GFI breaker. I believe
that this is normal to wire so many circuits to one GFI. Is this true?
My suspicions are as follows{most suspicious first}:
a) The GFI breaker itself is bad,
b) Some part of the wiring into the GFI is faulty,
c) The GFI is overloaded and therefore trips when anything
at all is plugged into an exterior socket.
Can anybody lend there suggestions or confirm the above? Has anyone
experienced a similar problem? How'd you fix it?
Thx. rep
|
292.3 | Replace it | HAVOC::OELFKE | | Wed Jun 29 1988 10:54 | 8 |
| I have also had a similar problem at my house. Mine though happens
only during damp or muggy weather. I have talked to an electrician
about it and I was informed that that is normal. Since yours is
not limited to the weather conditions, it sounds like it should
be replaced.
Bob O.
|
292.4 | | RICKS::PEKKALA | The Tape Man | Thu Jun 30 1988 13:29 | 13 |
| Other input from around the office indicates that the GFI should be loaded
with at most 4 outlets. I'm beating that without a doubt.
Its still somewhat of a mystery to me why the breaker trips when I plug
something in on an outside receptacle. Maybe a little ground bounce?
Currently, it looks like the best suggestion is to split the circuit with
two separate GFI breakers, one for exterior and one for interior. How
does that sound?
Now to see if I have anymore room in the box...
rep
|
292.5 | More Opinions... | CHART::CBUSKY | | Thu Jun 30 1988 14:54 | 20 |
| > Other input from around the office indicates that the GFI should be
> loaded with at most 4 outlets. I'm beating that without a doubt.
Do you REALLY have things plugged into and turned on, in ALL of your GFI
protected outlets? You're only "beating" the load rating of the GFI (or
a breaker or a fuse for that matter) if you have things plugged in and
turned on and DRAWING current.
I also have many outlets downline of my GFI but they are there for
convience and are not all in use at the same time.
Your problem could be a loose wire or bad connection *SOMEWHERE*
in your house. I say *SOMEWHERE* meaning almost *ANYWHERE* in your
house wiring due to the fact that something on one circuit affects
something on another circuit.
Charly
P.S. What are you plugging in that is causing the problem? Maybe
the GFI is tripping for a REASON!
|
292.6 | GFI outlet, not breaker | VIDEO::DCL | David Larrick | Thu Jun 30 1988 15:14 | 9 |
| .2> Currently, it looks like the best suggestion is to split the circuit with
.2> two separate GFI breakers, one for exterior and one for interior. How
.2> does that sound?
It's my understanding that breaker-box-mounted GFIs are more expensive and
less reliable than outlet-box-mounted ones. So perhaps you'd be happier
with a normal breaker, and a GFI outlet in the first box, for the new
circuit. Be sure to put the GFI outlet in an place where it's easy to
check and reset it.
|
292.7 | Keep 'em Coming | RICKS::PEKKALA | The Tape Man | Thu Jun 30 1988 17:26 | 42 |
| RE: .3
> Do you REALLY have things plugged into and turned on, in ALL of your GFI
> protected outlets? You're only "beating" the load rating of the GFI (or
> a breaker or a fuse for that matter) if you have things plugged in and
> turned on and DRAWING current.
In general, nothing on the GFI circuit was drawing when I tried the exterior
outlets.
> Your problem could be a loose wire or bad connection *SOMEWHERE*
> in your house. I say *SOMEWHERE* meaning almost *ANYWHERE* in your
> house wiring due to the fact that something on one circuit affects
> something on another circuit.
Loose wire may be one possibility but there can be others. For instance,
a long wire run in the house is more susceptible to voltage spikes than
shorter runs, i.e. like an inductive antenna. A good spike source can be
a motor turning on/off, etc. The spike in turn may be large enough to trip
the GFI breaker. There is also the possibility of ground loops.
> P.S. What are you plugging in that is causing the problem? Maybe
> the GFI is tripping for a REASON!
I thought the same, so I deliberately when outside with a flashlight
recharger and showed that the breaker still tripped.
RE: .4
>It's my understanding that breaker-box-mounted GFIs are more expensive and
>less reliable than outlet-box-mounted ones. So perhaps you'd be happier
>with a normal breaker, and a GFI outlet in the first box, for the new
>circuit. Be sure to put the GFI outlet in an place where it's easy to
>check and reset it.
Good suggestion. I'll have to think about that.
I think its becoming clear that I've got to do some more debugging. I
think on Saturday I'll have my wife stand in the cellar while I go plug
my electric razor all over the house! Let you know more.
rep
|
292.8 | Sounds like a typical GFI problem | DECSIM::RICE | | Fri Jul 01 1988 16:11 | 46 |
| First off, sounds like the GFI breaker is bad.
Reliable GFI's are not, why have a test button? The main reason
you hear the panel GFI breakers are not relable is due to the
enviornment they're in. Basements are not the nicest places to
live. Expense wise it costs less for the panel GFI, the other way
you still have the expense of a breaker in the panel and two places
to trip the circuit. Electricians have been drilled to the point
of instict to place GFI's in the panel (reason being that you should
only have to look one place when a circuit trips). It is much nicer
to be pushing the GFI test button in the luxury of your own bath
though!
As far as number of outlets per circuit...
No circuit should exist with greater than an 80% load factor.
In this case it is most likely a 15 amp circuit so 12 amps max.
Each duplex receptacle counts for 1.5 amps so you can have 8 of
them. Of course, this is a general rule of thumb for calculations.
If you have known loads on the circuit then you need to concider
them.
Check the GFI to make sure the connections are good and clean.
If you still have the problem then disconnect the house wires from
it and try connecting a load directly. If it trips then you'll
have your answer.
Just in case you aren't sure...
The GFI "Ground Fault Interruptor" operates by checking that current
flows equally between both conductors (black (or red) and white). A
difference of millamps of current will trip the breaker (typically
anywhere from 10-100 millamps depending on type). Don't get confused
with grounds, phases white-wires, black-wires since they have nothing
to do with it in themselves. A regular breaker checks current on only
one conductor (typically the black or red).
I've seen cases where folks have done their own wiring and got the
returns (whites) of two circuits crossed in the panel. A GFI would
not be very forgiving. In the case I saw the two GFI circuits
tripped together and the guy spent hours looking straight at the
problem.
You should be able to fix this one without an OHM meter ;')
-Tim
|
292.9 | | RICKS::PEKKALA | The Tape Man | Fri Jul 08 1988 10:51 | 12 |
| RE: .6
Good advice. Have you got any suggestions on why the breaker trips when
I plug something into any of my exterior plugs? It happens on sunny days,
when the circuit is known good, and as soon as I plug it in. The "load"
can be as little as an electric shaver.
I'm cross-posting to ELECTRO_HOBBY, I've got to believe that there truly
is something wrong, somewhere. The circuit tripping as soon as I plug
anything in, to me, is a solid indication.
Thx. rep
|
292.10 | current gut you down | KATRA::RICE | | Fri Jul 08 1988 13:08 | 56 |
| I take it you tried this and the GFI looks good?
> Check the GFI to make sure the connections are good and clean.
> If you still have the problem then disconnect the house wires
> from it and try connecting a load directly. If it trips then
> you'll have your answer.
I'm not quite sure what you mean by a "known good circuit"!?!
It gets messy from here because you have to start opening things
up.
Anyway, this is what it looks like you're saying.
1. The GFI is good
2. The inside outlets (?bathrooms?) of the circuit work just fine.
3. The outside ones (including garage light) trip.
4. Other circuits appear to affect tripping.
Here it comes...
Input to your house is single phase three wire 240V. The goal
for the electrician (should he realize) is to balance the load
as closely as possible across the transformer windings (up there
on the telephone pole). The center tap allows you to have 120V
circuits, its also the one that gets connected to earth ground.
The goal is to have no current returning to this center tap.
ie.
transformer
10A ________ 10A cir A
{---------/~\------| |-------}
{ 0A | Fuse |-------}
{---------/~\------| | 10A
{ | Box |-------}
{---------/~\------| |-------}
10A |______| 10A cir B
A little example there. If you tied the neutrals of cir A and
cir B the neutral wouldn't have 20A but would be 0A, the load
balances.
Now the electrician might not run 120V circuits as all 2-wire.
If there are two circuits where he could save money by running
one 3-wire cable instead of two 2-wire ones he'll probably run
the 3-wire (I'm not counting grounds here).
If your GFI circuit was done this way then it would explain
the weirdness. Then again, maybe the neutrals got mixed up
out there somewhere. You'd have to take every box apart
and trace out the wiring, messy.
This is a pretty far fetched problem, but possible nontheless.
So, what have you actually tried? What does the circuit really
look like and how old.
|
292.11 | | RICKS::PEKKALA | The Tape Man | Fri Jul 08 1988 15:00 | 30 |
| RE: .8
> I take it you tried this and the GFI looks good?
I haven't done that yet. I wasn't clear whether or not you were saying
that this may be a reason as to why the breaker trips when I plug something
in. I'll take a look at it.
> I'm not quite sure what you mean by a "known good circuit"!?!
"Known good" means that I can plug things into my bathroom outlets, or turn
on my exterior lights and the circuit will not trip. Its only when I use
an exterior plug that the breaker trips, or in the instance of some wierd
non-deterministic failure, i.e. the bathroom plug was fine before I went
to sleep but when I woke up, it didn't want to work anymore.
> So, what have you actually tried? What does the circuit really
> look like and how old.
The wiring for one of the bathrooms, is less than 1 year old. The house
is roughly 10 years old. I bought the home last year, just as the new
bathroom was being completed. I'd venture to say, that the previous owner
introduced the problem in the wiring of the new bathroom.
I haven't tried much, because I was hoping for a definite answer given the
symptoms I've described. It looks like its going to take some more digging,
and I'll be back with more data in the near future.
Thx. for all your suggestions,
rep
|
292.12 | | HPSCAD::FORTMILLER | Ed Fortmiller, MRO1-3, 297-4160 | Tue Jul 12 1988 13:57 | 3 |
| FYI: Those GFI breakers don't appear to be cheap. A friend bought
one this past weekend at Marlboro Electric and had to shell out
~$42 for one.
|
292.13 | Nuisance tripping...etc. | THESIS::HOHENGASSER | | Thu Jul 14 1988 15:34 | 5 |
| GFI breakers are subject to "nuisance" tripping if the wire run
from the breaker is to long. I believe this is in the range of
75 to 100 feet. You might want to check this out. Also, you want
to be sure all joints and connections in the circuit are secure,
electrical and mechanical.
|
292.14 | ? | ANGORA::ZARLENGA | Yo! Malllooorrreee! | Fri Jul 15 1988 14:30 | 7 |
|
.11> GFI breakers are subject to "nuisance" tripping if the wire run
.11> from the breaker is to long.
Why would this trip a GFI breaker?
-mike z
|
292.17 | GFI switchplates? | AQUA::FIRMANI | | Mon Aug 01 1988 13:13 | 7 |
| I am thinking about connecting a GFI outlet to two existing switches
in my bathroom. I would like to keep all three together in a triple
box. Does anyone know if anyone sells a three box switchplate with
two switches and a GFI outlet?
Mike
|
292.18 | | QUARK::LIONEL | May you live in interesting times | Mon Aug 01 1988 14:46 | 10 |
| There are a couple of different possibilities. One is to replace
the switches with those like the Leviton "Decora" line that have
large rectangular openings like many GFI outlets, then use a triple
plate designed for those. You can also get GFI outlets that fit
a normal two-hole outlet cover, and it should be simple to find
a cover for that. Go to your local electrical supply store (a
REAL one, not just a hardware store), and you will find a large
selection of outlet/switch covers.
Steve
|
292.19 | | ULTRA::PRIBORSKY | Swamps professionally drained. | Tue Aug 02 1988 10:18 | 3 |
| Try an electrical supply house. There's one in Fitchburg that has
them for sure (but I can't remember the name). Wheelen Supply in
Gardner would even special order some special GFI-related covers.
|
292.20 | Consider a GFI in the breaker box | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Tue Aug 02 1988 12:30 | 5 |
| If your home has circuit breakers (not fuses) you can replace the
circuit breaker for the circuit the bathroom is on with a GFI type
breaker. This might be an easier retro-fit for about the same
money. Our bathrooms, kitchen and outside outlets (three different
circuits) were originally wired this way.
|
292.21 | DON'T Consider a GFI in the breaker box | CHART::CBUSKY | | Tue Aug 02 1988 13:53 | 3 |
| Read notes 574.5, 816.16, 1659.13 before considering this approach.
Charly
|
292.15 | As I undertstand it | THESIS::HOHENGASSER | | Tue Aug 02 1988 14:29 | 13 |
| re. .12
You're not dealing with perfect conductors and as a result there is
an imbalance (cable resistance) between the hot and neutral legs of
the circuit. As the length of the wire run increases it is possible
for this imbalance to be greater than the trip point of the GFI
breaker. In the area of nuisance trips it is related to circuit load,
outside temperature, wire routing (tight bends...), etc.
This is my understanding of the problem. Someone else might have
a better or more technically accurate explanation.
/Ernie
|
292.22 | Do consider a GFI in the breaker box | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Tue Aug 02 1988 16:14 | 9 |
| There are two non-issues in the notes referenced by the preceeding
reply: (1) cost -- Breaker-box vs. coubined-outlet GFIs are not
different enough in cost for this to be a serious consideration.
(2) Reliability is a function of the conditions, not the type of
breaker. If _ANY_ GFI trips frequently YOU HAVE A PROBLEM. Either
the GFI or installation/wiring is faulty, or you are usinging it
in an unsafe way.
Go with whichever is easier to install.
|
292.23 | | AQUA::FIRMANI | | Wed Aug 03 1988 12:00 | 8 |
| I need to put an outlet in the bathroom anyway because we don't
have one in there now so I might as well just install the GFI outlet
in the bathroom.
Thanks for all the help!
Mike
|
292.24 | Outlets remind you to test | MEIS::FONSECA | I heard it through the Grapevine... | Wed Aug 03 1988 20:12 | 6 |
| This is probably mentioned in one of the other GFCI notes,
I didn't look throught them all. I believe that it is
recommended that you trip the GFCI every month, this is easier
to do for you or others less interested in things electrical
if its easily available... also you are reminded every time
you use that outlet.
|
292.78 | Ensuring a GFCI Breaker is working | CSCMA::M_ELDRIDGE | | Thu Jan 05 1989 10:24 | 21 |
|
.re .7 (tried to minimize quoting....!)
> I finished a basement playroom for my kids - put in ONLY GFCI-protected
> outlets since GFCI's provide some protection from electrocution -
> (but they aren't 'perfect' since you can electrocute yourself across
> the hot and neutral without creating a ground fault). I figured the
> most likely case is metal-object-poked-into-hot-side-of-outlet which
> will trip a GFCI.
I put in a GFCI Circuit Breaker in my basement for a new laundry
room. How can I know it's working? Does the test button actually
create a ground fault, and if so, will it not trip the circuit if
it is installed incorrectly? Is there any way to test it?
The breaker works fine, but I DID get a little jolt when I was tightening
a screw on a live outlet (yes, stupid, wasn't it?). The breaker
didn't trip. I hope it would have if it was a serious, life
endangering shock.
Any ideas, comments?
|
292.79 | External Test? | LDP::BURKHART | Diaper Repair Man | Thu Jan 05 1989 10:44 | 14 |
|
Good question!
I was wondering the same thing myself. I have a situation where
I can't install a GFCI outlet due to overcrowding the box it has
to go into so I'll end up having to go with a pannel breaker. But
I always wondered how to really make sure outlets down stream from
the GFCI outlet or breaker are indeed protected. I did manage to
trip on once do to plugging in a extention cord that had gotten
wet but thats the only time I ever had a REAL trip!
...Dave
|
292.80 | Testing GFI circuits | SEESAW::PILANT | L. Mark Pilant | Thu Jan 05 1989 11:25 | 14 |
| RE: Testing GFI outlets and breakers.
I had this same question when I replaced our old fuse service
entry with a 30+ circuit breaker panel. To bring it up to code,
I had to (among other things) install about 10 GFI breakers.
(Not knowing how the house was wired, I didn't install the GFI
outlets.)
A real easy to test them is to short the neutral line to ground.
When you do this the breaker/outlet should trip. If it doesn't,
you probably have problems. Note that grounding the hot line
will also trip the breaker :-), but won't test the GFI capability.
- Mark
|
292.81 | Testing Outlets | LDP::BURKHART | Diaper Repair Man | Thu Jan 05 1989 11:45 | 8 |
|
Just so we don't end up with a bunch of dead/fried DECies, What's
a safe way to 'short out' an outlet so as not to cause sparks, flames
and injured people?
...Dave
|
292.82 | buy a tester | STEREO::COUTURE | Gary Couture - Govt. Syst. Group - Merrimack NH | Thu Jan 05 1989 13:57 | 11 |
| I bought a plug-in electrical tester for about 10$ which also has a
little button on it which when pressed causes a slight short which causes
the GFI to trip. You can try it on any outlet and it will trip the GFI
if it is upstream.
I would replace the box with a larger one so that you can put in a GFI
outlet since they are MUCH cheaper than GFI circuit breakers and much more
reliable.
gary
|
292.83 | | VINO::KILGORE | Wild Bill -- DECintact Engineering | Thu Jan 05 1989 16:58 | 14 |
| re .49:
I would assume you need to short neutral to ground, then apply a
load downline, in order to trip the GFCI. According to my
understanding, shorting neutral to ground on an open circuit should not
trip the GFCI, because no current flows. Is that correct?
A better test of the sensitivity of a GFCI would be to connect an
appropriate resistor from hot to ground, allowing you to control
the leakage current (watch the power rating on the resistor).
For safety, you should make your connections inside a screw-togehter
3-prong plug assemply, then button it up and plug into an outlet.
|
292.84 | More on GFI | SEESAW::PILANT | L. Mark Pilant | Fri Jan 06 1989 09:06 | 8 |
| RE: .52
Hmmm. The breakers I have (Gould/ITE) would trip when I shorted
neutral to ground, without a load. Sounds like it is about
time I check out some reference material to find out how those
little things work.
- Mark
|
292.85 | Enquiring minds, etc. etc. | SALEM::MOCCIA | | Fri Jan 06 1989 09:20 | 5 |
| The GFCI discussion raises a question: exactly what happens when
you push the "TEST" button on a GFCI outlet?
pbm
|
292.86 | How They Work? | LDP::BURKHART | Diaper Repair Man | Fri Jan 06 1989 09:30 | 14 |
|
Getting back to the original question does any one know how
these thinks realy work? and are willing to type a lenthy explanation?
Get as technical as you want.
Re back a few:
What size load do you need? I take it that you don't
have to pull 15 amps to get the GFI to trip? What is the min current
that should trip these?
...Dave
|
292.87 | testing for a trip | SALEM::M_TAYLOR | I drink alone...Care to join me? | Fri Jan 06 1989 09:43 | 19 |
| Shorting neutral to ground does trip the GFCI. Do this by simply
shorting the taller slot (next pin on receptacle in a clockwise
rotation from the ground slot) to the ground slot.
After accidentally discovering this, I decided to try the same with
the hot side while wiring inside a metal box; DON'T DO IT! If you
are watching what you are doing, you will see a spot everywhere
you look for the next hour or so... from the intensity of the arc
that you will draw by doing this! Yes, this did trip the GFCI,
and also its supply breaker.
Good idea about totally enclosing your "test fixture", but play
it safe; dont' try to bleed current through the hot side, the neutral
is alot safer to muck around with.
BTW--I had a GFCI that would not trip anymore this past fall, so
make sure you do test yours, to ensure that it still does work.
Mike
|
292.88 | low current can kill you | LAVC::CAHILL | Jim Cahill | Fri Jan 06 1989 13:47 | 9 |
| No, you don't need 15 amps to get the GFI to trip. You better not!
The minimum current that should trip a GFI is somewhere around 50
milliamps, since that's the amount of current that, properly applied,
can kill you! Remember, the GFI is designed to detect and trip if a
*leakage* current is detected.
The Leviton(sp?) GFI I have is speced at 50 milliamps leakage current.
Jim
|
292.89 | A partial explanation | REGENT::GETTYS | Bob Gettys N1BRM 235-8285 | Sun Jan 08 1989 12:17 | 12 |
| Re "Why it works shorting neutral to ground."
In a system where there is nothing drawing any current
from your supply panel (where the ground and neutral are tied
together), it probably wouldn't work. But since that condition
is almost never is true, there will be enough voltage difference
between ground and neutral from the normal IR drop in the
neutral wire to cause enough current to flow in the ground wire
to trip the GFI.
/s/ Bob
|
292.90 | | QUARK::LIONEL | Ad Astra | Sun Jan 08 1989 13:20 | 5 |
| I'm sorry if this seems like a digression, but WHY is there usually
some voltage potential between neutral and ground? After all, they're
both connected to the same block at the breaker panel, aren't they?
Steve
|
292.91 | ohms law | REGENT::GETTYS | Bob Gettys N1BRM 235-8285 | Mon Jan 09 1989 08:38 | 6 |
| If you have any current in the neutral (which you will
with a load applied), then you have IR drop in the neutral. You
do not have this voltage created in the ground as there is no
current flow in the ground.
/s/ Bob
|
292.92 | incorrect installation symptoms | HYDRA::THALLER | A job well done is a job done well... or something like that | Tue Jan 10 1989 16:34 | 21 |
| > I put in a GFCI Circuit Breaker in my basement for a new laundry
> room. How can I know it's working? Does the test button actually
> create a ground fault, and if so, will it not trip the circuit if
> it is installed incorrectly? Is there any way to test it?
I recently bought a house which has a GFCI receptical in the bathroom. The
home inspector I used (Cornell) pointed out that even though pushing the TEST
button caused it to trip, the power was not being disengaged. (I never would
have thought to test this.) Anyway, I bought a replacement but when I went to
install it I found that the original had been installed incorrectly. Power was
connected to the LOAD wires instead of the LINE wires. I just reinstalled the
existing outlet in the correct manner and it works correctly now.
In summary:
So even though the test button may trip the breaker, this doesn't ensure that
power has been disengaged. This situation can be caused by incorrect
installation.
-Kurt*
|
292.93 | A good reason for using a VOM | OFFHK::SCANLAND | Tubes, or not tubes? That is the question. | Wed Jan 11 1989 09:40 | 9 |
| re .61
This is probably the most common mistake made with GFI circuits. On the
surface it usually seems pretty straightforward, however, you'd
probably be surprised how easy it is to screw up an installation.
Not that I've ever made any mistakes though. ;-)
chuck
|
292.94 | GFI Test Plug & Big Box Digression | LDP::BURKHART | Diaper Repair Man | Fri Jan 13 1989 10:22 | 58 |
|
As someone suggested in a earlier note a better solution
to my over crowded box and GFI breaker problem would be a bigger
box as opposed to a GFI breaker in the circuit panel. My biggest
problem is that I don't really have the room for a bigger box.
Unless of course someone knows of a box that will fit my
application as sown below?
|*|*| |*|*|*|
|*|*| |*|*|*|
|*|*|+----+|*|*|*|
|*|*|| ||*|*|*|
|*|*|| ||*|*|*|
|*|*|| ||*|*|*|
|*|*|| ||*|*|*|
|*|*|+----+|*|*|*|
^ ^ ^
| | |
(2)2x4s box (3)2x4s
Now I can't re-wire so as to put the GFI in a area where
there is room for a bigger box. The room is almost all windows
and the framing leaves almost no empty wall cavities. Besides,
this box location is the most convenient for the GFI (right next
to door going out to deck). So has anyone seen a box which is
the standard 2 or 2&� inch width but taller and come with a plate
to reduce the opening for installation of a outlet?
As one can see the SIMPLEST solution is to use a GFI
breaker. This was my reason for wanting to know how to do an
external test of the GFI breaker and with all the bad press about
these types of breakers I want to make sure the circuit is
working properly.
Now if I understand all the comments made here correctly
the best way to test the GFI would be to build a little plug in
adapter wired as follows:
HOT NEUTRAL
|
|
|
+---\/\/\/\/--- GROUND
2.4K ohms =50ma
10 watts
This would most likely imitate the undesired condition
which would cause electrocution, with a person being replaced by
the resister. Even though most said to connect neutral to ground
this seems to me to be of very little danger in a real
environment as there should under most circumstances be very
little potential between neutral and ground. If I really want to
make sure the GFI works the real test would be to run the
resister from HOT to a nearby water pipe rather than the outlet
ground. Any comments?
...Dave
|
292.95 | Plan "C" | CHART::CBUSKY | | Fri Jan 13 1989 11:06 | 7 |
| Dave,
Why don't you install a GFI outlet someplace else (bath, garage,
workshop, etc...) and then wire this outlet downline from the GFI
protected outlet?
Charly
|
292.96 | WIREMOLD Box | SALEM::M_TAYLOR | I drink alone...Care to join me? | Fri Jan 13 1989 11:07 | 9 |
| I don't know if this is up to code, but, a WIREMOLD (tm) surface-mount
single-gang box would extend the box out enough to give extra cubic
space inside for all the wiring. I'm doing this exact thing, and
have the box already, just haven't put it together yet.
The GFCI receptacle mounts in the WIREMOLD (tm) box, so it sticks
out some. In my case, it's not a problem; it's in the garage...
Mike
|
292.97 | | VINO::GRANSEWICZ | Which way to Tahiti? | Fri Jan 13 1989 12:59 | 5 |
|
I've seen some metal boxes that appear to be almost 3" deep. Will
that be big enough? The easiest way was stated in .64 though.
|
292.98 | Huh? | AKOV13::FULTZ | ED FULTZ | Mon Jan 16 1989 11:37 | 11 |
| RE .64 AND .66
What do you mean install a GFCI downline? Do you mean install one
between the breaker and the spot that is being considered? What
will that do? When a person grounds the one outlet, will the GFCI
that is downline (actually upline?) trip and shut off the electricity
to the whole line? Isn't this what a GFCI breaker is, theoretically,
supposed to do?
Ed..
|
292.99 | Maybe a breaker is too small (physical space)?? | REGENT::GETTYS | Bob Gettys N1BRM 235-8285 | Mon Jan 16 1989 13:35 | 14 |
| A GFI outlet usually has four terminals (or wires) on
it. Two are labeled LINE and are to be connected to the line
coming from the source (panel). The other two are labeled LOAD
and are to be connected to any of the circuit located beyond the
GFI outlet. In most (if not all) GFI outlets this means that the
items (outlets usually) located beyond the GFI (away from the
panel) are also protected by the GFI.
Yes, this is the same as a GFI breaker does. However, it
seems that outlet style GFI's are more robust in manufacture and
tend to last longer than GFI breakers (why this is so, I don't
know - I haven't heard a coherent reason).
/s/ Bob
|
292.100 | yes, the CAN act the same | CADSE::MCCARTHY | Illegitimi Non Carborundum | Mon Jan 16 1989 13:40 | 18 |
| RE: < Note 1659.67 by AKOV13::FULTZ "ED FULTZ" >
GFI recep. have 5 terminals (or leads in some cases on them). One is
for ground. Two are marked LINE. This is where the HOT and neutral
wires go that are coming from the panel. The other two are marked
LOAD. You can run a line from these terminals to another recep.
"down line" and that recep. will be GFI'ed also. If you get these
reversed the down line recep will work but will not trip the
GFI when tested. This is very useful in large bathrooms that
require more than one recep. You bring your LINE into one and then
feed your other recep from the LOAD side of the GFI. If it trips,
all you have to do is reset it at the recep (you don't have to go
down to the circuit panel). There are several other applications
that make GFI recep more desireable than GFI breakers.
Yes this does make the GFI recep. act like a GFI breaker.
bjm
|
292.101 | Another reason $$$$ | MAKITA::MCCABE | | Mon Jan 16 1989 17:41 | 5 |
| One of the best reasons to use a GFI receptacle - COST. You can
always find one on sale for $9-$10. A GFI breaker usually runs
close to $40. Also, it is nice not to have to walk down to the
cellar if one trips.
Chris
|
292.102 | GFI - 12 or 14 guage??? | VINO::GRANSEWICZ | Which way to Tahiti? | Tue Jan 31 1989 10:27 | 6 |
|
I want to install a GFI in a bathroom. I will run a new circuit
to the bathroom. Should it be a 15 or 20 amp line? The GFI is
rated for 15 amp but a 20 amp feed thru. Why 2 different ratings?
Phil
|
292.103 | | NSSG::FEINSMITH | I'm the NRA | Tue Jan 31 1989 13:36 | 14 |
| The outlet itself in the GFI is 15 amps (if the outlet looks like
this: | | ,its 15 amp.
| |
| |
If it looks like this: | | its a 20 amp.
| |-
| |
The feedthrough is the current that can pass through the GFI, not
the capacity of the GFI's outlet itself.
Eric
|
292.104 | But the $64,000 question remains... | VINO::GRANSEWICZ | Which way to Tahiti? | Tue Jan 31 1989 14:59 | 5 |
|
OK, but what gauge wire should I use to wire it? 12 or 14? Should
I wire it for the outlet or the pass thru?
Phil
|
292.105 | Bathroom circuit? | WILKIE::THOMS | Ross - 264-6457 | Tue Jan 31 1989 15:51 | 14 |
| >< Note 1659.73 by VINO::GRANSEWICZ "Which way to Tahiti?" >
> -< But the $64,000 question remains... >-
>
>
> OK, but what gauge wire should I use to wire it? 12 or 14? Should
> I wire it for the outlet or the pass thru?
>
> Phil
Wire in a 15 amp branch circuit using 14 gauge romex.
Ross
|
292.106 | what good is the 20amp feed | HPSCAD::DANCONA | | Wed Feb 01 1989 07:41 | 4 |
| what good is it to have a 20 amp pass thru if you wire it
for 15 amps.. or did i miss something ??
tony
|
292.107 | | VLNVAX::HEDERSTEDT | T.B.S. | Wed Feb 01 1989 08:34 | 7 |
| I asked the same question and was told it was for surge protection.
The wire going into and out of a 15amp rated GFI is 14 gauge.
You must use the same gauge wire,14 gauge,to connect it into a
circut.
Acording to my local Wire Inspector,the wirerunmust be of the same
gauge wire.
Wayne
|
292.108 | Add confusion to confusion... | VINO::GRANSEWICZ | Which way to Tahiti? | Wed Feb 01 1989 09:35 | 19 |
|
RE: .75
Exactly my question! I checked the outlets this morning and they
have stickers on the side which say "Rated 20 amps". Less conspicuous
is the stamp on the metal surrounding the outlet which says 15 amp.
Now how can this thing have 2 different ratings???
Also, the instructions clearly state that the GFI is NOT AN OVERCURRENT
DEVICE. So you would need a 15 amp breaker to protect the outlet
I suppose. And this means 14 gauge wire. Seems pretty logical
but why do they through in the "20 amp feed through" if it's
meaningless? And then there is the sentence which says to connect
the outlet to Aluminum wire using 12 gauge.
Can anybody figure this out or should I call the company? What
does the code say about these things?
Phil
|
292.109 | | VINO::GRANSEWICZ | Which way to Tahiti? | Wed Feb 01 1989 09:38 | 9 |
| RE: .76
> I asked the same question and was told it was for surge protection.
What is "it"? I don't see where surge protection comes into this.
Could you explain a little bit more?
Phil
|
292.110 | Gauge must be THE SAME? | EAGLE1::CAMILLI | | Wed Feb 01 1989 09:44 | 11 |
|
-< Add more confusion to confusion... >-
Since when does the code specify a MAXIMUM wire size? For
15 amp circuits, you have to use AT LEAST 14 gauge. Some
recommend using 12 gauge even though it's not required.
It doesn't cost much more (except 12-3), gives a lower
voltage drop when the load is high, and if you ever want to
change it to 20 amps, you don't have to rewire. (You just
have to replace all the 15 amp-rated outlets and such...)
|
292.111 | GFI pass-through rating explained | HANNAH::DCL | David Larrick | Wed Feb 01 1989 09:55 | 41 |
| I don't know if I can succeed in clearing up the confusion here, but
I'll try.
Forget GFIs for the moment, and note that it's common practice (and
perfectly legal) to connect multiple 15A outlets to a 20A circuit, i.e.
to a circuit with a 20A breaker and #12 wire. Your kitchen is probably
wired this way, in fact. The idea is that the circuit can support
multiple devices totalling up to 20A, but the devices on any one outlet
won't be more than 15A. So, for example, you can run an 8A toaster and
a 10A frying pan on different outlets of the same circuit, but running
them on the same outlet would exceed that outlet's capacity.
These multiple outlets are wired in a daisy-chained manner. Electricity
travels from the breaker panel to the first box in line. There it
splits: some goes to the outlet there, and the rest goes to the other
boxes (and outlets) on the circuit. While the outlet in the first box
only needs to handle 15A, the connections there need to handle the full
20A. That's why using the outlet's screws and the little metal strip
between them to make pass-through connections is a bad idea, and why
using the push-in connections is even worse. The preferred technique
is to wire-nut three wires together - the supply, the wire to the next
box, and a tap to the outlet - so the full 20A never gets near the
outlet itself.
Now back to GFIs. Assume that you want to use one GFI to protect
all of the outlets in the circuit described above, so you'll install
the GFI in the first box in line. In order to bestow GFI protection on
the downstream outlets, you need to wire things in such a way that the
full circuit load flows through the GFI package - the split described
above still happens, but it happens _inside_ the GFI package. Although
only 15A can be plugged directly into the GFI outlet, supporting the
downstream outlets requires that the GFI's internal wiring be able to
handle the full 20A.
The "15A direct/20A flow-through" rating simply indicates that the
GFI you bought is capable of supporting the above circuit configuration.
Since you didn't mention any downstream outlets, I suspect that none of
this discussion applies to your installation. If you'll be wiring the
GFI to a dedicated circuit, a 15A circuit (15A breaker, #14 wire) is
sufficient, although a 20A circuit would allow more flexibility for
future changes.
|
292.112 | How about this? | MAMIE::THOMS | Ross - 264-6457 | Wed Feb 01 1989 10:03 | 22 |
| Geez, Some of you guys like making a mountain out of a mole hill!
How about this explanation: Just about any switch, receptacle, etc. for
the home is rated for 20 amps. They can be used in 15 or 20 amp branch circuits.
As stated earlier in this note, receptacles can be purchased to accept either
15 or 20 amp plugs. The GFI receptacle is rated at 20 amps, but accepts only 15
amp configured plugs:
| | | |
| | | ---
|
O 15 amp O 20 amp
Excuse my poor drawings, but you should get the idea.
In a bathroom circuit, there is no reason to run a 20 amp circuit, unless you
like wasting money on 12 guage wire.
Ross
|
292.113 | a slight correction! | VLNVAX::HEDERSTEDT | T.B.S. | Wed Feb 01 1989 10:49 | 22 |
|
rep .80
Thanks,I could not have explained any better!
rep.81.
Not true! It depends on what the bathroom has in it for lighting,over-
head deater/infared bulbs and such. I am putting a overhead light with
a heater,fan,main light and night light in our bathroom. Now if I
attach this to a 15a circuit and my wife runs the hair drier with
the fan and heater going- CLICK- no juice! I am not busting your chops
but this is my real life situation.
The "Flow through" of 20a in a 15a GFI is best explained by .80. I
called the inspector back and he verified it.I must have heard him
incorrectly....
As far as different size wire in a single circuit goes,The wire must
step down in size (12 to 14 gauge) and not the other direction
(14 to 12 gauge). Make sense?
Wayne
|
292.114 | | MAMIE::THOMS | Ross - 264-6457 | Wed Feb 01 1989 11:33 | 13 |
|
> rep.81.
> Not true! It depends on what the bathroom has in it for lighting,over-
> head deater/infared bulbs and such. I am putting a overhead light with
> a heater,fan,main light and night light in our bathroom. Now if I
> attach this to a 15a circuit and my wife runs the hair drier with
> the fan and heater going- CLICK- no juice! I am not busting your chops
> but this is my real life situation.
Calculate your load and figure out what you need. An ordinary (configured)
bathroom can easily get by with a 15 amp circuit.
Ross
|
292.115 | 20amp GFI outlet | LDP::BURKHART | Diaper Repair Man | Wed Feb 01 1989 11:39 | 12 |
|
If you're really conserned about it spend a few extra bucks,
go down to the local electric supply store and box a GFI outlet
with the 20 amp configured plug and rating. They do have them,
all the outlets buy sinks in MRO4 are setup with them. I've
been meaning to get one for the dedicated 20 amp circuit I put
in my garage to run power tools.
...Dave
|
292.116 | Think about it. | MAMIE::THOMS | Ross - 264-6457 | Wed Feb 01 1989 13:13 | 31 |
| How about this scenario: A person cooking in the kitchen that has the minimum
(2) 20 amp small appliance circuits with 15 amp "configure" duplex receptacles.
The person cooking plugs in an electric fry pan that at high temp setting
draws say 12.5 amps. This same person plugs in a toaster on the same duplex
that draws maybe 6 amps. The breaker is within it's threshold of approx. 20
amps and doesn't trip. Does the 15 amp receptacle do a melt down? Not likely
Is this a legal branch circuit? Yes
Table 210-21(b)(2)
Maximum Cord_ and Plug-Connected Load to Receptacle
________________________________________________________________________________
________________________________________________________________________________
Circuit Rating Receptacle Rating Maximum Load
Amperes Amperes Amperes
15 or 20 15 12
This (I believe) is a grey area in the code. The described scenario is a code
legal branch circuit. Does the average homeowner know if he's pulling more
than 12 amps out of a receptacle? I doubt it.
(My thought) The manufacturers build in the extra capacity in the devices.
I'm open to argument and thoughts on this one.
BTW, I don't agree with everything in RE:80. When time permits, I'll get into
it.
Ross
|
292.117 | I will send it to you??! | VLNVAX::HEDERSTEDT | T.B.S. | Wed Feb 01 1989 14:29 | 11 |
| I have a melted down 15a gfi duplex outlet. It came off of temp.
power pole. I am building a house as of now. It is attached to a
20a breaker. The poor sucker died at night while i was working
in the house.
Bear in ming that this is my only source of AC and I was abusing
the heck out of it!! The 20a breaker never tripped but the 15a
GFI with 20a carry through melted down!!
I replaced it with 20a GFI.
Wayne
|
292.118 | | STROKR::DEHAHN | | Wed Feb 01 1989 14:33 | 7 |
|
Realize that you may need a larger than standard box to house a
20A GFI outlet and it's wiring. They are physically larger than
the 15A versions, at least the Leviton brand.
CdH
|
292.119 | | MAMIE::THOMS | Ross - 264-6457 | Wed Feb 01 1989 14:48 | 14 |
| >< Note 1659.86 by VLNVAX::HEDERSTEDT "T.B.S." >
> -< I will send it to you??! >-
>
> I have a melted down 15a gfi duplex outlet. It came off of temp.
In my scenario, I had standard duplex receptacles in mind. However, your
GFCI outlet might of been defective or you were drawing more than 20 amps?
BTW, I'm not a fan of GFCI outlets. I rarely use them due to the fact they're
more trouble prone than GFCI breakers. They're widely used now because they're
less expensive.
Ross
|
292.120 | I killed it! | VLNVAX::HEDERSTEDT | T.B.S. | Wed Feb 01 1989 15:12 | 19 |
| I should not have been drawing more that 20amps or i should have
tripped the 20amp breaker. I have 200'+ of ext. cords to the house.
They are 12awg but the draw + voltage drop killed the GFI.
In my house,since its being built and I am wiring it,the GFI's are
in the main panel.I do not care for the GFI's that are in the outlet
boxes. Any GFI breakers that are in my house are 20a.I would rather
be safe than sorry with the extra $'s invested in 20a service to
certain places in my house. The bathroom is one and the kitchen
is the other. By code I do not have too much of a choice as far as
the GFI's go but I plan to add a bit of fudge factor (extra amps)
to these area's. I know Mr. Murphy and his law's will bite me
in the backside later and I will be pissed that I did not do it
right (for my usage) the first time.
Six or 10 bucks now is cheap compared to running another line at
another date!
Wayne
|
292.121 | Go for it | WOODRO::THOMS | Ross - 264-6457 | Wed Feb 01 1989 15:26 | 7 |
| >< Note 1659.89 by VLNVAX::HEDERSTEDT "T.B.S." >
No one say's you can't oversize your circuit. That's up to you.
BTW, don't forget to ad GFCI for the garage outlets, (1) basement outlet, and
outdoor outlets, also.
Ross
|
292.122 | I'm done! | VLNVAX::HEDERSTEDT | T.B.S. | Wed Feb 01 1989 15:33 | 6 |
|
No problem there, already done.Except the garage..Can't afford it
yet. Maybe if I did not buy 12-2 and bought 14-2......:^)
enough said!
Wayne
|
292.123 | reliability - brkrs or outlets ?? | FREDW::MATTHES | half a bubble off plumb | Thu Feb 02 1989 08:02 | 6 |
| re .88, last few
I was led to believe (I thought I read it here) that the GFI outlets
were more reliable than the GFI circuit breakers.
Which is which ??
|
292.124 | Outlets for reliability | VINO::KILGORE | Wild Bill -- DECintact Engineering | Thu Feb 02 1989 09:15 | 11 |
| re .92:
Experience dictates that the outlets are more reliable than the
breakers.
A couple of years ago we had a lightning strike between my house
and my neighbor's. Outlet GFCIs in both houses came through fine.
A GFCI breaker in his house bit the dust. An elecrtician buddy of
his advised using an outlet replacement if possible - because they're
more reliable.
|
292.125 | | RENFRO::POWELL | Reed Powell HPS Marketing | Thu Feb 02 1989 09:44 | 17 |
| The 20a GFCIs do not need a larger box than the 15a. I have 15a in the
Bath, but there are 2 20a circuits into the garage/shop, and those must
also be GFCI, and so I had to get 20a GFCIs. No problem with size.
The COST, however, is much more - I seem to remember it being around
$20 or so each, where the 15a typically run about $9.99 at most places.
I did find that one color was more expensive than the other (brown or
white, I cannot remember which was higher), which I thought odd.
I agree with .-? on the 15 vs 20a for the bath - 15a is sufficient
unless you have something like a baseboard (non 22v) heater in there.
However, what you will find in a lot of houses is that the bath is not
on a seperate circuit. I ended up rewiring the bath to have its own
because the power would trip when I dried my hair in the summertime
when the attic fan was running at the same time and the lites happened
to be on in two adjacent rooms!
|
292.126 | | WILKIE::THOMS | Ross - 264-6457 | Thu Feb 02 1989 10:23 | 11 |
|
> Experience dictates that the outlets are more reliable than the
> breakers.
My experience has been the opposite. Breakers can take a hell of a lot
more abuse and have a longer longevity. Contractors like the GFCI outlets
because they're $25+ dollars cheaper than using the breakers in a circuit!
Ross
|
292.127 | Sometimes LOW COST <> LOW QUALITY | VINO::GRANSEWICZ | Which way to Tahiti? | Thu Feb 02 1989 10:59 | 18 |
|
DISCLAIMER:
This is all my interpretation and may bear no relationship to reality.
I don't think the cost has anything to do with the reliability/quality
of the breaker vs. outlet. From the description of the GFI, it
performs a different function than a regular breaker. Combine the
GFI capability with a breaker and you now have 1 device performing
2 functions thus more cost. Also, breakers can "stick" (even though
everybody toggles theirs once a month ;-)) and you'd be left without
any protection if this happens on a GFI breaker, right? But I guess
any device coul;d fail for any number of reasons. I would think
that the more complicated the device (more functions), the more
they are prone to fail.
End of GFI cost/quality theory...
|
292.128 | ya missed my point | STROKR::DEHAHN | | Thu Feb 02 1989 12:13 | 8 |
|
20A GFCI outlets are larger than 15A in certain brands. If you intend
to hook up a parallel set of outlets downstream then when using
12G wire they may not fit into a standard box and still *meet Code*.
I had to use an extension box on my installation.
CdH
|
292.129 | | RENFRO::POWELL | Reed Powell HPS Marketing | Thu Feb 02 1989 13:12 | 3 |
| I meant to mention that there are brands that do not use pigtails, but
have screws on them, which reduces the amount of space in the back of
the box needed to make connections.
|
292.130 | more nit's | VLNVAX::HEDERSTEDT | T.B.S. | Fri Feb 03 1989 11:52 | 17 |
|
I did some more checking on this and the 20a service to the bathroom..
I know,what a nit-picker. I was with the Electrical Inspector for
several hours yesterday. I Was enlightened quite a bit by his
knowledge. No armchair coach here!
Any circuits should not be loaded more than 80%. If someone
turns on a 2000 watt hair drier,that happens to be about 16.6amps.
Now if the lights are on the same circuit and are on as well......
The Inspector mentioned that it won't be long before code requires
20a service to a bath.
I replaced a 15a gfi with a 20a gfi. It will fit in the box but it
did take up more room! In act,the gfi will not quite go in all the way
because of the ridgid pipe clamp that protrudes into the box.
wayne
|
292.131 | | WILKIE::THOMS | Ross - 264-6457 | Fri Feb 03 1989 12:42 | 13 |
| > Any circuits should not be loaded more than 80%. If someone
> turns on a 2000 watt hair drier,that happens to be about 16.6amps.
> Now if the lights are on the same circuit and are on as well......
2000 watt hair dryer? Does it heat the room as well as burn hair off
your head. \\8*} There's a chart in the code that gives max load per outlet.
See a couple of replies back. I'm not too worried with my little 15 amp
bathroom circuit, my Wife has every electric hair gadget known to man and
I've had no problems.
BTW, Ask the inspector the question I asked a few back: How does the average
homeowner know if he's exceeding 80%?
Ross
|
292.132 | | MRVAX::HEDERSTEDT | T.B.S. | Fri Feb 03 1989 12:56 | 12 |
| The 2kwatt is NOT uncommon.. Most go up to 1500 on hi setting.Circiut
breakers trip at @120% load,not at 100%. As far as the 80% load goes,
Most people cannot tell! Where that comes in is NEW construction and
good planning. I may not need the full 20a in my down stairs bath but
I will need it for the upstairs bath/master bath! I plan for worst
case involving what might be running in the bath at one time not
what I can get by on. Poor planning will get back to at the worst
time possible. I am not over-building the circuit in the bath,just
adding up wattages used for each appliance that my be on at the same
time and that figure tells me 20a.
Wayne
|
292.133 | | WILKIE::THOMS | Ross - 264-6457 | Fri Feb 03 1989 13:17 | 11 |
| >< Note 1659.101 by MRVAX::HEDERSTEDT "T.B.S." >
> The 2kwatt is NOT uncommon.. Most go up to 1500 on hi setting.Circiut
Take a look at the manufacturer's full load rating on the appliance. Not
the phoney baloney decal number. If you have something that draws 16.6 amps,
it's a heat gun, not a hair dryer.
Btw, Let's take this argument offline.
Ross
|
292.134 | GFI`S ARE GOOD | BTO::CHARBONNEA_G | | Thu Feb 16 1989 18:30 | 16 |
| My big mouth,here it go`s.
You all wire your house the way you want but,I use 12/2 wire less
on the braker then it calls for so the wire in the walls will not
git hot,the braker will go before a fire comes on.
I use ohms law to see what I can plug into the lines.
I use 1 braker for each room and 1 each for frigh,stove and etc.
If you use 15a brakers do the box calls for 20a and 12/2 wire you
will not need a GFI.
The wire and box can`t get hot from overload.
Even if you don`t use ohms law you can`t plug more in because the
braker will go first.
If you do this again and again you need help.
Go ahead tell me I`m wrong.....I`m all your`s,Give me h###.
|
292.135 | So what's wrong with a big mouth ?? | FREDW::MATTHES | half a bubble off plumb | Thu Feb 16 1989 18:49 | 6 |
| > If you use 15a brakers do the box calls for 20a and 12/2 wire you
> will not need a GFI.
> The wire and box can`t get hot from overload.
I'm sorry. I don't understand what this means. Could you restate
it please.
|
292.136 | We try to give people h*ll POLITELY here, don't we? | LYCEUM::CURTIS | Dick "Aristotle" Curtis | Mon Feb 20 1989 13:27 | 25 |
| .103:
� If you use 15a brakers do the box calls for 20a and 12/2 wire you
� will not need a GFI.
If I can say this without sounding nasty...
GFCIs and "over-engineering" are two different things. GFCIs are meant
to trip when they detect more than a certain amount of current (50
milliamps?) going to ground; the intent is to protect humans from
lethal shocks, usually in situations where there is water around to
help make a nice conductive path from the hot side of an outlet to
ground. (Note that they are required for outlets in bathrooms, in
kitchens, and exterior outlets -- all places where you're likely to see
water splashing about.)
IMO, "Over-engineering" or "over-building" isn't such a bad thing, although
it shouldn't be necessary if you're following the code. As long as the
inspectors don't beat you up for putting a 15A breaker on what would
otherwise be good for 20A, *and nobody tries to draw 18A because the
outlet says 20A on it*, you should be OK; it's more expensive, but
the extra expense is buying some peace of mind.
Dick
|
292.137 | | CLOSET::T_PARMENTER | Bite the wax tadpole | Wed Feb 22 1989 09:02 | 3 |
| I usually skip the electrical notes, but isn't it the grounded pipes,
not the splashing water, that makes bathrooms and kitchens dangerous,
electrically speaking?
|
292.138 | | VINO::GRANSEWICZ | Which way to Tahiti? | Wed Feb 22 1989 09:04 | 5 |
|
RE: .106
No. It's the electricity...
|
292.139 | Maybe I was thinking of wet basement floors, or radios in the tub? | LYCEUM::CURTIS | Dick "Aristotle" Curtis | Wed Feb 22 1989 11:35 | 8 |
| .106:
Yeah, now that you mention it, it's probably the pipes more than water;
although if I had my hand in the sink and got zapped, I probably
wouldn't care much whether I was clutching a faucet, or just had my
hand submerged...
Dick
|
292.140 | H20 vs. Water | LDP::BURKHART | Diaper Repair Man | Wed Feb 22 1989 11:56 | 11 |
|
As I recollect from my high school chemistry class water
in it's pure form (H20) is a very poor conductor of electricity
it's the minerals in water that make it conduct. As I remember
the demonstration the professor stuck his hand in a tank of very
pure (H20) with electric probes inserted in the water, and lived
to tell about it.
...Dave
|
292.16 | | WACHU2::HERTZBERG | Modify Brotherinlaw /Nopriv | Mon Mar 13 1989 10:16 | 32 |
| Dragging up this old topic since I just started reading this
conference...
Actually, a resistive imbalance between the hot and neutral legs
wouldn't cause the GFI to trip. As long as there isn't any current
leaking out of the circuit, the GFI stays untripped. In the real
world, there is always some current leakage associated with wiring.
The more wiring present (due to longer runs, etc.), the more leakage
exists. This leakage biases the GFI toward its trip point, increasing
the likelihood of nuisance tripping.
Don't be shy about returning a GFI which exhibits a nuisance tripping
problem. You won't be the first one to do so by any means. In
the early history of GFI production, return rates for nuisance tripping
were often in the 25-50% range! Nuisance tripping continues to
be the single biggest problem for GFI manufacturers.
GFIs must trip with faults of 5ma, but the trip time for such
a small fault is permitted to be in the range of several seconds.
As the fault current increases, the required trip time decreases.
With faults in the 100ma and above range, GFIs trip in well under
100ms.
The test button is there by mandate of UL, not because GFIs are
inherently unreliable. This device is supposed to be able to be
trusted to save your life, so that ability should be verifiable.
The fault injected by the test current is usually between 5 and
10ma, thus it takes a few seconds for most GFIs to respond to a
press of the test button.
Marc
|
292.141 | When the outlet melts, you're at 15.1A... | LEVERS::COLELLA | Now enjoying Area Code 508 | Fri Mar 17 1989 11:33 | 26 |
| Re: .80 -
> So, for example, you can run an 8A toaster and
> a 10A frying pan on different outlets of the same circuit, but running
> them on the same outlet would exceed that outlet's capacity.
So where's the protection against this situation? I don't understand
what happens when you exceed the outlet's 15A capacity when the outlet
is on a 20A circuit.
Re .81 -
> How about this explanation: Just about any switch, receptacle, etc. for
> the home is rated for 20 amps. They can be used in 15 or 20 amp branch
> circuits.
Then why are some marked "rated capacity 15A"? If the only
difference is the plug configuration (and I don't think that's
true. The 20A outlets seem "heavier"), why are they differentiated
in the first place?
Still confused, especially since the 15A outlet/20A feed-through
GFCI do in fact, exist.
Barry
|
292.142 | Read on | MAMIE::THOMS | Ross - 264-6457 | Fri Mar 17 1989 14:11 | 29 |
| >< Note 1659.110 by LEVERS::COLELLA "Now enjoying Area Code 508" >
-< When the outlet melts, you're at 15.1A... >-
> So where's the protection against this situation? I don't understand
> what happens when you exceed the outlet's 15A capacity when the outlet
> is on a 20A circuit.
>
The code allows (rated) 15amp outlets on a 20 amp branch circuit. The idea is
that the Homeowner will/(should) not exceed 12 amps on one device.
Can 12 amps be exceeded? Sure. Will the 15 amp device do a meltdown? Not
likely.
>Re .81 -
> Then why are some marked "rated capacity 15A"? If the only
> difference is the plug configuration (and I don't think that's
> true. The 20A outlets seem "heavier"), why are they differentiated
> in the first place?
>
Yes, The 20a device is more substantial, but 15 amp devices are adequate in
most home branch circuits. Save the 20a outlet for the Mig welder circuit in
the garage.
> Still confused, especially since the 15A outlet/20A feed-through
> GFCI do in fact, exist.
>
> Barry
|
292.143 | Flagellation of Deceased Equine here... | LEVERS::COLELLA | Now enjoying Area Code 508 | Fri Mar 17 1989 14:58 | 20 |
|
< Note 1659.111 by MAMIE::THOMS "Ross - 264-6457" >
-< Read on >-
>The code allows (rated) 15amp outlets on a 20 amp branch circuit. The idea is
>that the Homeowner will/(should) not exceed 12 amps on one device.
>Can 12 amps be exceeded? Sure. Will the 15 amp device do a meltdown? Not
>likely.
This seems very strange. The code is now relying on the good sense
of the user? (!) I agree the outlet wont meltdown, but if it can really
handle 20A, why rate it at 15? I guess I'm beating a dead horse
here, but it still seems to me that everything on the other side
of a 20A fuse should be able to handle hours and hours of 20A
current flow without getting very hot. If 15A receptacles can handle
that, then call them "20A", if not, they (In My Humble Opinion)
shouldn't be on a 20A circuit. Apparently, the Code and the makers
of GFCI 20A flow/15A outlets don't agree.
Barry
|
292.144 | Theory of Operation | WACHU2::HERTZBERG | Modify Brotherinlaw /Nopriv | Fri Mar 17 1989 18:42 | 108 |
| Press next unseen to avoid lengthy technical discussion of GFI
operation.
Being new to this conference, I just found this note. Since there
appear to remain questions about GFI theory of operation, I'll present
what I know for public consumption.
Behold my crude combination block/schematic diagram of a typical GFI:
| Push to test
~16K -----
+--------------/\/\/\--O O-+
| ___ ___ |
| / \Diff / \ |
| / \Xfmr / \ | Breaker (w/manual reset)
Hot ---------------|------------|-----------+--o----o------ Hot
"LINE" | | | | | "LOAD"
Neutral -------+---|------------|--------------o----o------ Neutral
\ / \ / Xcitr ^
\ / \ / Xfmr |
--- --- |
| ^ | "Trip"
V | | Command
+-------+ +-------+ |
| Full | | Oscil-| |
| Wave | | lator | |
| Bridge| +-------+ |
+-------+ |
| |
V |
+-------+ +-------+ |
| Integ-| | Compa | |
| rator |--->| rator |---------+
| | | |
+-------+ +-------+
The heart of the circuit is the differential transformer, through which both
the hot and neutral wires physically pass. This transformer is simply a
torroidal coil with several hundred or thousand wraps. As all you EEs know,
if current flows in a wire which passes through such a coil, a current is
produced in the coil windings as well. The direction of the current in the
wire determines the direction of the current in the transformer windings. If
you pass equal currents through two wires which pass through the transformer,
the current produced in the transformer windings either doubles or goes to
zero by cancellation, depending on the direction of current flow in the two
wires. You can imagine the current flowing in the hot wire to the right,
through a load on the load side, and back to the left through the neutral
wire. In this case, the currents in the two wires are equal and the
direction is opposite, so the differential transformer has no output signal
(in theory, see below).
When someone is getting shocked, current is flowing from the hot wire through
the differential transformer, through the someone and to ground on the load
side. So some of the current in the hot wire isn't being returned in the
neutral wire, but is instead being shunted to ground through some poor
bastard. This is a "ground fault". Since the current in hot and neutral are
nonzero and not equal, the differential transformer starts to produce an
output. The bigger the fault, the larger the output.
The signal processing circuitry is familiar to EEs. The transformer output
is first rectified, then drives an integrator. The integrator's output
charges up at a rate proportional to the size of the fault. When the
integrator's output reaches a preset value, the comparator produces an output
which trips the GFI, disconnecting the load side. Of course, the built-in
receptacle, if present, is wired to the load side of the GFI. In actuality,
the breaker itself is spring loaded with manual reset, and is tripped by a
small pin which is thrust out by a solenoid driven by the comparator
(typically... designs may vary).
Signal processing folks will recognize that the trip time is proportional to
the magnitude of the fault. UL publishes a curve of fault current vs. trip
time which the GFI must adhere to. GFIs must trip with a fault of 5
milliamps, but they have several seconds to do so. As the fault increases,
the trip time decreases until, at faults on the order of hundreds of
milliamps, the circuit will trip very quickly (30 milliseconds and less is
typical).
The test button connects a resistor from the load hot to the line neutral.
Typical test currents vary between vendors, but 10 milliamps is not unusual.
The other transformer ("exciter transformer") is driven by a simple
oscillator to put a small AC waveform through the coil windings. The purpose
of this is to detect installations which have "grounded neutral", where the
neutral and ground are connected on both the load and line sides. This
wiring is a problem because the return current now bypasses the differential
transformer and the GFI trips hard and fast as soon as any load is applied.
Grounding the neutral on both the line and load side effectively creates a
wire loop which passes through both the exciter and differential
transformers. In this case, the oscillator output driving the exciter is
coupled to the differential transformer through the wire loop, and the signal
is sufficient to trip the GFI even if there is no load present. This is done
as an indication that the GFI is improperly installed.
As far as combined breaker/GFIs, I know of no reason why one should be more
reliable than the other, except for brand-to-brand differences in
reliability. The industry is pretty mature now and they're all about the
same, to my knowledge. The biggest problem remains false tripping due to
excessive noise sensitivity. Another problem is imperfect differential
transformers, in which as the load increases, the transformer starts to
generate an output even though there is no fault. This brings the GFI closer
to its trip point, decreasing noise immunity.
Marc
who-ought-to-know-since-he-used-to-design-these-things-and-the-
equipment-that-tests-them-for-a-living.
|
292.145 | | LEVERS::COLELLA | Now enjoying Area Code 508 | Sun Mar 19 1989 21:51 | 15 |
|
RE: .112
Whoops! When I said:
> Apparently, the Code and the makers of GFCI 20A flow/15A outlets
> don't agree.
I meant that neither of them agrees with me. I did not mean to say
that they don't agree with each other.
Barry
|
292.146 | Lax code for houses? | RGB::SEILER | Larry Seiler | Sun Mar 19 1989 23:44 | 36 |
| re .112:
Well, here's my guess as to why the code is less strict here.
I'm not a code expert, but I have browsed through it.
1) Homes tend to have a lot of sockets per circuit -- the
code requires lots of sockets. It would be very expensive
to run separate circuits for each, so it is useful to be
able to have fewer circuits at 20A instead of 15A.
2) Very few home electrical devices require more than 12A,
so it would be overkill to mandate 20A sockets for homes.
3) If a home device can draw enough power to damage the
15A socket, then either it has a 20A plug and can't be
plugged into a 15A socket, or else it has a 15A or less
wire from the plug to the device, and that is going to melt
or arc before the socket does.
Note that the code has lots of rules to try to keep high
current devices on separate circuits. For example, I was going
to put sockets in my kitchen and bathroom on the same circuit,
since they are on opposite sides of the same wall, but the code
specifically disallows this -- I guess they don't want my
toaster oven and my space heater on the same circuit.
Also note that the code demands that all hard-wired parts
of a circuit be able to carry the full current, but does
not require that of mundane home plug-in equiment.
Imagine having every wire on every lamp able to carry 20A.
It's a compromise, and the safety level is probably not
as high as for other situations, but that's life.
Enjoy,
Larry
|
292.147 | Kitchen circuit nit | HANNAH::DCL | David Larrick | Mon Mar 20 1989 08:59 | 16 |
| A nit, in the interests of excruciating accuracy:
.115> ...I was going
.115> to put sockets in my kitchen and bathroom on the same circuit,
.115> since they are on opposite sides of the same wall, but the code
.115> specifically disallows this ...
More precisely, if a circuit is shared between the kitchen and some
other room, that circuit doesn't count as one of the required two 20A
kitchen small applicance circuits. A third small appliance circuit, or
a kitchen lighting circuit, may be shared with one or more other rooms
if its capacity allows.
Even this nit has an exception: as mentioned recently elsewhere in
this conference, a kitchen small appliance circuit may be shared with
the dining room.
|
292.148 | GFCI in screened porch? | NATASH::WEIGL | | Tue Aug 15 1989 15:05 | 14 |
|
I'd like to ask a mundane question about GFCI applications:
I'm installing outlets on a screened porch. I'm planning to put a 15A
breaker in the box, and then a GFCI outlet on the first plug on the
porch. The others will be downstream-protected by the GFCI.
Given that it's a screened porch, is it essential that I put
weather-proof covers on the receptacles? Or will the GFCI be
sufficient protection? I don't think there's going to be a lot of
water coming in, but..... If the GFCI keeps tripping in the rain, I'll
put on covers.
Any thoughts?
|
292.149 | | VLNVAX::HEDERSTEDT | T.B.S. | Tue Aug 15 1989 17:19 | 7 |
|
rep. 117
Why invite problems? Put the weather tight cover on! It also might
be required in your town.
Wayne
|
292.150 | Best to do it the right way. | KAOM25::TOMKINS | This MIND left blank INTENTIONALLY | Wed Aug 16 1989 18:23 | 6 |
| All electrical outlets located outside a building and exposed to
the environment, SHOULD be covered, sealed and calked.
Sure there is a little extra cost associated with the weather tight
outlet covers, but, if you don't cover them and they are mounted
in the body of the house, you can count on rain coming into your
house.
|
292.151 | carry-over from TOH, 1974.345ff | REGENT::POWERS | | Wed Feb 21 1990 09:52 | 29 |
| I want to continue the "stupid electrician tricks" discussion from the
"This Old House" topics (1974.50,+/-10) on GFCIs to this, the GFCI topic.
To recap (so you don't have to retrace the discussion), the electrician on
This Old House demonstrated the efficacy of a GFCI breaker by dropping
a turned-on trouble light into a bucket of water. Some of us questioned
whether such a demonstration was reasonable, and whether it actually did
demonstrate the real-life effect of a GFCI.
For example, where did the fault current go that caused the breaker to trip?
The bucket was plastic, sitting on an apparently dry wooden floor.
I observed that the only way the GFCI could have tripped was if the trouble
light had a grounded plug, which most bathroom appliances (radios, hair
dryers, shavers) don't have.
That got me thinking of other aspects of the ground path, and I asked
whether modern plumbing provides a good enough ground path to cause
a GFCI to trip if the appliance should fall into a sink. With the
more common use of plastic waste pipes and supply lines, and plastic parts
in stops and faucets, is a wet sink a good ground path?
If not, that's both bad and good.
The good is that if I touch a live connection while also touching
the sink, I don't provide part of a ground path that can endanger me.
On the other hand, if I do drop a shaver into a sink of water, there is
no place for fault current to flow, so the GFCI won't trip as soon as it should.
So, should sinks have a separate hard safety ground? I observed that
bathroom fixtures in England do. Is that for just this purpose?
- tom powers]
|
292.152 | | VIA::GLANTZ | Mike, DTN 381-1253 | Wed Feb 21 1990 11:04 | 35 |
| With properly working GFCIs, it doesn't matter whether fixtures are
grounded. The important point is that if enough current returns to
ground through *any* path other than neutral (especially a path which
includes a human body), the GFCI will trip.
I suspect that the reason for grounding fixtures is that if a live
appliance falls into a sink, for example, the sink will not become
live (though any water in it will), and any device protecting the
circuit may eventually trip. The bad part is that anything in the
water is also part of the current path, and if the circuit isn't
protected by a GFI, it won't trip until the current reaches the rating
of whatever's protecting the circuit. So, as you pointed out,
ungrounded fixtures are "better" if you're already in the water when
the appliance falls in. Of course, getting your butt out of an
ungrounded bathtub with a live shaver in it is going to be tricky. In
reality, though, even an ungrounded bathtub may conduct enough current
to ground (through the air and surrounding materials) to be lethal. So
since it may still kill you if you're in the water, might as well at
least save you if you're lucky enough not to be in the water when the
appliance falls in. I guess that's a good enough reason for ALL
plumbing fixtures to be grounded.
In the absence of GFI protection, a sink may be safer grounded
(because you tend not to be in the water), while a bathtub may be
MARGINALLY safer floating (because you're probably in the water when
the appliance falls in). With GFI protection, it doesn't make much
difference.
One thing I've been curious about is to see if a GFI socket will trip
when I stick one of those neon test screwdrivers firmly in it. I've
noticed (by accident) that the screwdriver I have can give a moderate
shock if I hold its metal end firmly in one hand and grab a grounded
object in the other (the neon bulb also lights up nicely). I haven't
tried this on a GFI socket, yet. Has anyone out there been saved by a
GFCI?
|
292.153 | | QUARK::LIONEL | Free advice is worth every cent | Wed Feb 21 1990 11:12 | 7 |
| You cannot rely on plumbing fixtures to have a good ground unless you know that
they are solidly connected with copper pipe all the way back to the house
water inlet. But it really doesn't matter. A GFCI detects leakage as
a difference in current flow between the hot and neutral lines. It doesn't
matter WHERE that leakage goes, as long as it is going somewhere else.
Steve
|
292.154 | | CSC32::GORTMAKER | whatsa Gort? | Thu Feb 22 1990 07:10 | 13 |
| re-.1 ...copper pipe all the way..
I recently had the local cable company out installing cable into my house
while doing the inside work hesaid he had to ground to the CW pipe.
I told him that I had replaced it with plastic all the way to where it entered
the house except for the few feet where he intended to connect( this was partly
in an effort get him to use the ground rod inches away from where the cable came
into the house as I believe grounding causes premature pipe failure) anyway,
he said " oh well I can't help that it's company policy to use the pipe...".
Oh boy and they let these guys climb power poles.....
The guy was still parked in the driveway packing up when I moved the ground
wire to the rod where it could do some good.
-j
|
292.155 | | REGENT::POWERS | | Thu Feb 22 1990 08:43 | 14 |
| > < Note 1659.122 by QUARK::LIONEL "Free advice is worth every cent" >
> ...But it really doesn't matter. A GFCI detects leakage as
> a difference in current flow between the hot and neutral lines. It doesn't
> matter WHERE that leakage goes, as long as it is going somewhere else.
Exactly my point - if the sink is not well grounded, or not grounded at all,
where can the current go to cause the imbalance in hot and return?
Should sinks be grounded separately? Do either the plumbing or electrical
codes have statements on this?
- tom]
side note: Clean water and dry wood are not very good conductors of electricity.
Wet wood is better. Wet skin - now THERE'S a good conductor.
|
292.156 | | QUARK::LIONEL | Free advice is worth every cent | Thu Feb 22 1990 10:28 | 9 |
| Re: .12
Water is a good enough conductor, clean or otherwise, that the few milliamps
needed to stop your heart are very likely to find a path to ground,
whether the sink itself is grounded or not. I don't see any particular
point in ensuring a sink is grounded, but I would not hesitate to
protect any outlets near a water source with a GFCI.
Steve
|
292.157 | | RAMBLR::MORONEY | How do you get this car out of second gear? | Thu Feb 22 1990 11:15 | 6 |
| Pure (distilled) water is a poor conductor. Water with the usual impurities
is a fairly good conductor. It is highly unlikely that you have distilled water
in your plumbing, so it's safe to assume any water in pipes, sinks, etc.
is a good conductor.
-Mike
|
292.158 | Grounding a (plastic) sink? | MVDS02::LOCKRIDGE | Artificial Insanity | Fri Feb 23 1990 11:58 | 6 |
| re: grounding a sink.
How would one ground a plastic sink (or fiberglass) with a plastic
drain pipe? (This is a question of curiosity, not need).
-Bob
|
292.159 | | QUARK::LIONEL | Free advice is worth every cent | Fri Feb 23 1990 15:16 | 5 |
| Re: .12
You wouldn't, any more than you'd ground a toilet.
Steve
|
292.160 | why relatively low currents kill | RGB::SEILER | Larry Seiler | Fri Feb 23 1990 23:08 | 13 |
| To expand a bit on the note a couple back -- it doesn't take many milliamps
to kill you because the way it kills you is by interfering with the neural
signals to your heart and starting "fibrillation", which is a sort of
random twitching. Once the heart gets stuck in fibrillation, it is hard
to get it back to regular beating, and you haven't got long to do it.
A stronger current will instead clamp your heart, and if you get free before
you fry, you have a fair chance that your heart will start beating again by
itself. That's one reason why people have survived lightning bolts that
melted the coins in their pockets.
Enjoy,
Larry
|
292.161 | YeahRight! | ISLNDS::BELKIN | that wild, thin mercury sound | Tue Feb 27 1990 13:08 | 12 |
| re < Note 1659.129 by RGB::SEILER "Larry Seiler" >
> -< why relatively low currents kill >-
>A stronger current will instead clamp your heart, and if you get free before
>you fry, you have a fair chance that your heart will start beating again by
So, what Larry is saying is, if you find yourself getting zapped
by something, grab hold of it tighter, or toss some table salt
in the water, to increase the current so your heart clamps up,
until someone finds you and turns off the juice!
(many many :-) :-) :-)...!!!!) Josh
|
292.162 | Don't make an ash of yourself | SSDEVO::JACKSON | James P. Jackson | Tue Feb 27 1990 16:12 | 15 |
| It also depends upon the frequency of the current.
I once got attached across a 400V DC power supply. Before I was
disconnected, I was drawing 40ma (from one hand to the other). At DC, 10ma
and you can't let go, 100ma and you're dead. (some of my friends claim that
I therefor became 40% dead, explaining many things about my behaviour :-))
The current required to freeze or kill goes down with frequency, with a
minimum at about 47Hz. The 60Hz used in the US is remarkably close to this
minimum. The ring frequency used in telephone systems is even closer (I
seem to recall about 45Hz).
The sensitivity to frequency is due to the fibrillation, as mentioned in
.129.
-JimJ
|
292.163 | hmmm | QUICKR::FISHER | Dictionary is not. | Mon Mar 05 1990 06:17 | 9 |
| RE: "At DC, 10ma and you can't let go, 100ma and you're dead."
Wait a minute, I thought the argument between Edison and Westinghouse
concerning DC vs AC included something about AC could kill you more
easily than DC. 100ma DC ain't that hard to come by.
'course this doesn't matter to the GFCI discussion underway, ...
ed
|
292.164 | | NSSG::FEINSMITH | I'm the NRA | Mon Mar 05 1990 09:47 | 11 |
| RE: .132, that's 100ma flow, which must take into account skin
resistance, which is normally quite high. If the skin is wet though, it
drops considerably. Also, the path of the current flow is critical. A
zap from the thumb to the pinkey on the same hand, though painful,
probably won't be lethal, but the same zap from the left hand to the
right hand (across the heart) could be deadly.
Now back to our regularly scheduled topic........
Eric
|
292.165 | How fast are things supposed to trip anyways? | DAVE::MITTON | Bo knows NETBIOS? | Wed Apr 04 1990 21:39 | 12 |
| Personally, I was curious about how well GFCI's work and did a little
experiment late one night.
I took an ordinary detachable power cable (you know the kind we use for
all sorts of terminals and PCs) and stuck a paper clip into the lead
I wanted to test. When I touched the neutral to a steel sink, the
outlet reset nicely. When I touched the hot to the sink, it MELTED
the paper clip at the point of contact before the outlet reset.
I'm still not sure what to think of this.....
Dave.
|
292.166 | | QUARK::LIONEL | Free advice is worth every cent | Thu Apr 05 1990 09:20 | 4 |
| 1/40 second is the figure I've read. They're not intended to
protect against a direct short.
Steve
|
292.167 | | VIA::GLANTZ | Mike, DTN 381-1253 | Thu Apr 05 1990 09:51 | 12 |
| It is an interesting question, though. When you press the TEST button
on a GFI receptacle, what does it actually test? The delay before the
circuit opens is considerably longer than 1/40 sec (25 ms). It appears
(to me, at least) to be more like 150 to 200 ms. I suppose that this
is still enough time to protect against serious injury, though it
would hurt like heck. The GFCI breaker on my panel trips almost
instantly, though.
I've been considering a similar experiment: measure my skin resistance
(left hand to right hand) with a VOM (it usually runs a around 100K
ohms) and stick the equivalent resistor in a GFI socket to see if/when
it trips. If I remember to try it, I'll let you know what happens.
|
292.168 | re: .136 Ground to Hot | MVDS02::LOCKRIDGE | Artificial Insanity | Thu Apr 05 1990 13:25 | 15 |
| re: .136
> It is an interesting question, though. When you press the TEST button
> on a GFI receptacle, what does it actually test?
Having taken a GFI receptacle apart, the one I had (don't remember the
manufacturer) actually shorted the ground lead to hot (black). I had
wondered the same thing as to what was really tested. I now believe
the test.
I too have noticed that the delay seems rather long. Who knows, maybe
it has AI and "knows" it's only the test button being pressed so it
doesn't have to react all that quickly. :-)
-Bob
|
292.169 | | VIA::GLANTZ | Mike, DTN 381-1253 | Thu Apr 05 1990 13:54 | 6 |
| Hmmm, ground-to-hot doesn't strike me as right, because if I short
ground to hot on a normal socket, the breaker for that circuit will
trip in a couple of milliseconds -- long before the GFI action. I had
therefore surmised that it must be ground-to-hot through some
resistance which wouldn't trip the branch circuit breaker. Can anyone
confirm this?
|
292.170 | | RAMBLR::MORONEY | How do you get this car out of second gear? | Thu Apr 05 1990 16:02 | 9 |
| I believe they connect hot to ground through a resistor that draws enough
current so that it should trip, but not much more. This is how I'd do it
if I were designing such a thing.
If the test button connected hot to ground directly, you'd know it, because
there's be a loud BANG that would scare the %#^$%^#@ out of you.
-Mike (who has accidently connected hot to ground more than once when playing
with old radios as a kid)
|
292.171 | | REGENT::POWERS | | Fri Apr 06 1990 10:07 | 19 |
| > <<< Note 1659.136 by VIA::GLANTZ "Mike, DTN 381-1253" >>>
> I've been considering a similar experiment: measure my skin resistance
> (left hand to right hand) with a VOM (it usually runs a around 100K
> ohms) and stick the equivalent resistor in a GFI socket to see if/when
> it trips. If I remember to try it, I'll let you know what happens.
This won't be a very good test. People are non-linear conductors.
The salts and electrolytes insode our bodies are good conductors, dry skin
is not so good. Note the 100K or so you see is pretty much constant
regardless of the distance between the leads, as left hand to right,
or both in the same hand.
Add a little bit of sweat, and the resistance drops fast. Moisten
your skin and try it, or put the VOM leads on your tongue.
When you touch a voltage source, you'll draw a bit of current, which might
squeeze a few sweat glands, causing you to draw a lot more current very
quickly.
- tom]
|
292.172 | | VIA::GLANTZ | Mike, DTN 381-1253 | Fri Apr 06 1990 10:38 | 12 |
| Of course you're right. I was just looking for a rough test to see how
GFCIs work. I know it will trip at a low resistance, but I'd like to
see it trip at the higher resistance -- it would make me feel safer.
You're probably also aware that skin resistance varies a lot from
person to person, as well as in a single person under different
conditions. I can touch a 110VAC hot (with dry skin) and feel minor
pain. My wife hits the ceiling. An electrician friend can touch both
neutral and hot simultaneously with any parts of his body and feel it
but not be bothered at all. I even watched him put his fingers across
the two hot bus bars in my breaker panel and not complain (and not
trip the 100A main breaker :-).
|
292.173 | | RUNAWY::63797::DVORAK | dtn 297-5386 | Fri Apr 06 1990 14:10 | 9 |
|
Hmmm.. ground to anything does not seem right, because as I understand
it GFIC's work on *ungrounded* outlets as well as grounded ones. So if
a ground is not connected how can you short to it.
My guess is that the test button somehow simulates a current imbalance
between hot and neutral without connecting anything to ground.
gjd
|
292.174 | | VIA::GLANTZ | Mike, DTN 381-1253 | Fri Apr 06 1990 16:09 | 9 |
| That's an interesting point. I just might go home and try this tonight
by lifting the ground on a GFI receptacle.
Meanwhile, I can't imagine any other way to test GFI protection (aside
from sticking your finger in the hot side of the socket), since in
order to trip it, you need to cause a difference in current flow
between neutral and hot, and in order to do that, you need to send
enough current from either of these to some other place. Without a
ground path, what other place is there?
|
292.175 | I think ground is required | DAVE::MITTON | Bo knows NETBIOS? | Thu Apr 12 1990 16:28 | 5 |
| hmmm.... I don't know for sure, but I don't think it's legit to
install a GFCI on an ungrounded circuit. It may not work correctly.
Can someone verify this? (both functional and code?)
Dave.
|
292.176 | | VIA::GLANTZ | Mike, DTN 381-1253 | Thu Apr 12 1990 17:15 | 7 |
| No, in fact the National Electrical Code specifically prescribes GFI
receptacles to be installed on existing ungrounded (two-wire)
circuits, rather than installing a standard (three-wire) receptacle
which couldn't be grounded. You can either do that or install a
two-wire receptacle (the old-fashioned kind). The GFI receptacle still
provides protection, and doesn't need a ground to work. I have no idea
how the test button works in that sort of installation, though.
|
292.177 | | QUARK::LIONEL | Free advice is worth every cent | Thu Apr 12 1990 21:05 | 5 |
| The 1990 NEC now allows you to feed other outlets from the GFCI
using two-conductor wire. I have made use of this in my house, and
yes, the test button works. Don't ask me how....
Steve
|
292.178 | | RAMBLR::MORONEY | How do you get this car out of second gear? | Thu Apr 12 1990 23:33 | 12 |
| The test button probably works by connecting the hot lead after the current
sensor, through a resistor (to limit current flow) to the neutral lead _before_
the current sensor. This way the current flows one way through the current
sensor but not back the other way, so there is a current imbalance, so the gfi
trips.
If you think of this, this is exactly the same as using the ground lead for the
test button, since the neutral and ground are connected directly together at the
main panel anyway (the electricity doesn't care about human laws regarding
where to connect the neutral and ground)
-Mike
|
292.179 | | VIA::GLANTZ | Mike, DTN 381-1253 | Fri Apr 13 1990 10:21 | 1 |
| Bingo. I'm sure you're right.
|
292.180 | 5 ma differential | AKOV12::ANDREWS | | Wed Apr 18 1990 14:18 | 3 |
| Yes, and the bias is calibrated for 5 millamperes.
Erick
|
292.181 | A question... | NITMOI::PESENTI | Only messages can be dragged | Thu Aug 02 1990 08:52 | 14 |
| WHen I bought my house, the owners mentioned something about the outdoor outlet
and the bathroom, which I promptly forgot, until recently.
I recently hooked up a bug zapper to my outdoor outlet, and after a few weeks
of constant zapping (I own the neighborhood swamp, ya know), it quit. Then it
started working again. After a few times, I finally figured out that my the
times my electric toothbrush was discharged in the morning due to the GFCI being
tripped coincided with the nights that the zapper didn't work. Some testing
confirmed that the outside outlet is somehow wired to the GFCI in my bathroom,
and is controlled by the tripping of the reset switch.
Aside from the bizzarity of the circuit connection, is this unusual? Can
GFCIs control other devices? Does this mean my outdoor outlet is protected the
same as my bathroom outlet?
|
292.182 | | STAR::DZIEDZIC | | Thu Aug 02 1990 08:56 | 13 |
| You can string a whole bunch of other outlets from a GFCI
outlet; this is typically done by CHEAP electricians who
use a single GFCI breaker/outlet for ALL bathrooms and outdoor
outlets. All following (fed-through) outlets are then GFI
protected.
Wouldn't be at all suprised if you had water in your outside
outlet box; maybe you could correlate trip times with whether
or not you had rain? The bug zapper could have an insulation
problem of some sort as well.
Then again, maybe you just have too much of a load on that
(supposed) single circuit.
|
292.183 | Ballast another possibility | CSCMA::LEMIEUX | | Thu Aug 02 1990 10:34 | 15 |
|
Hi,
The ballast for the U/V lamps are also a good source of problems
for GFCI trips as are fluorescent fixtures, same principle of
operation. They won't all do it, but a large enough portion of them
will, that I have been avoiding putting them on GFI circuits when
avoidable.
My suggestion is to have a circuit run for the bug light that
is not GFI protected.
PL
|
292.184 | zap the bugs, not the humans | HNDYMN::MCCARTHY | What will I do when the day is 1.5 hr longer? | Thu Aug 02 1990 10:48 | 9 |
| >> My suggestion is to have a circuit run for the bug light that
>>is not GFI protected.
You can't do that by code, outside outlets have to be GFI'ed, except, I
believe, when they are used to control wheelchair lifts (its a long
story....).
bjm
|
292.185 | | QUARK::LIONEL | Free advice is worth every cent | Thu Aug 02 1990 11:41 | 8 |
| In my previous house, the outside outlet was controlled by the GFCI in the
bathroom. Confused the heck out of me when I went to replace the outside
outlet with a GFCI and found it didn't work.
But there was an up-side. If I wanted to disable the outside outlet, all
I had to do was trip the bathroom GFCI!
Steve
|
292.186 | Hmmmmm... | NITMOI::PESENTI | Only messages can be dragged | Thu Aug 02 1990 12:50 | 10 |
| Well... this might explain a few things. For one, I intermittently get one or
both lights lit on the bug zapper for no apparent reason. And, as far as too
much load, I think the zapper ran non-stop while it was dark (I mean in bug-fry
mode, not just turned on) for a couple of weeks. I mean the dead bug pile had
DEPTH! On the down side, the neighborhood ants love the crispy critters so
much they moved in directly under the zapper, and have tried to carry off my
dog.
I'll try a few experiments with pwering the thing from non-gfci outlets, to
see what happens.
|
292.187 | Rathole (bughole?) | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Thu Aug 02 1990 16:17 | 3 |
| Bug zappers supposedly aren't very good at attracting mosquitoes, since
they're attracted by carbon dioxide, not light. Most of the bugs you're
frying are either good bugs or so-so bugs.
|
292.188 | | NITMOI::PESENTI | Only messages can be dragged | Fri Aug 03 1990 07:51 | 20 |
| Living at the swamp, I get lots of bugs. Good, bad or otherwise, they are soo
thick, I can't get in or out of the house in the evening without letting in
a few dozen. My neighbor, a firm believer in zappers, gave me this unit when
he bought his new one (auto on/off). Since I've had it on, there has been a
marked decrease in the amount of bugs in the house, the amount of bugs near our
doors, and the amount of fried bugs piling up on the ground below. Also, I'm
the mosquito attractor in the family. People invite me to parties and ask me
to sit at the end of the yard to keep all the mosquitos away from everyone else.
I get bitten mid day on hot dry days. Each bite I get swells incredibly and
itches a lot. I've always been too skeptical of zappers to go out and buy one,
and I don't like to spray insecticides, and I'm not allowed to have bat houses.
However, this deal was too much to pass up. And so far it works!
But, I digress...this is after all the GFCI note. So,...
I found out the source of all my problems is the GFCI-ness of the outlet.
Is there any way of getting around the code restriction on outdoor outlets?
Like direct wiring? (or violating code? I wouldn't do it, but I would like
to know if it's the ONLY way...)
|
292.189 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Fri Aug 03 1990 10:46 | 17 |
| re .157:
> Living at the swamp, I get lots of bugs.
How serious are you? If you live near the Okefenokee, you're out of luck.
If you have a fairly small amount of stagnant water, you might try
Bt Israelensis, a bacterium that attacks mosquito larvae and is harmless
to other species.
> I'm not allowed to have bat houses.
Are you allowed to have purple martin houses?
> But, I digress...this is after all the GFCI note. So,...
Oops, so do I. If your GFCI outlet is tripping, there's a problem in
something you've got plugged into it, no? Why ignore the problem?
|
292.190 | | CLUSTA::GLANTZ | Mike @TAY Littleton MA, DTN 227-4299 | Fri Aug 03 1990 10:55 | 25 |
| You won't be easily able to eliminate the GFCI on the zapper circuit
without violating code. It would be better to try to figure out why
the zapper is tripping the GFCI.
GFCI receptacles are specifically *not* designed to trip in
overcurrent conditions. The conventional overcurrent protection on the
circuit (fuse or breaker at service panel) is intended to handle this
condition. The GFCI only trips for leakage completely out of the
circuit (and, presumably, into a human body). This is probably what's
happening in your case.
You need to find out where/why current is leaking out of the circuit.
This may be inherent in the nature of bug-zapper operation. Any
high-voltage appliance will leak some current into the surrounding
environment, especially when it's humid. If this is true, then there
are going to be a lot of people with the same problem, as more and
more homes get built or upgraded with GFCIs under existing code.
There are two possible solutions: either find a zapper which doesn't
leak enough current to trip the GFCI (maybe newer models are better in
this regard), or find a way, compatible with code, to install the
zapper on a non-GFCI-protected circuit. I seem to remember some
exceptions in the code (for dedicated appliances) which would allow
you to do this. Maybe somebody with their codebook handy could confirm
this.
|
292.191 | ... | CLUSTA::GLANTZ | Mike @TAY Littleton MA, DTN 227-4299 | Fri Aug 03 1990 10:59 | 2 |
| BTW, the GFCI may be tripping for some other reason having nothing to
do with the zapper. That would be easy to fix.
|
292.192 | GFI's not always needed to meet code | CSCMA::LEMIEUX | | Fri Aug 03 1990 11:34 | 46 |
|
Hi,
There are ways to have the bug light not on a ground fault device.
* 1) hardwire the buglight to the circuit....no GFI needed then.
I would choose #1
2) a little looser interpretation of NEC GFI requirements is
to mount the receptacle higher than 6 foot 6 inches above
grade making sure that the receptacle cannot be reached from
the grade around the receptacle.
3) Change the ballast to a 230 volt ballast, convert the receptacle
to the correct NEMA configuration for the voltage and the
amperage available, add a 2 pole breaker to the circuit.
4) You might also try another ballast, you may get lucky and
get one that works with a GFI.
(Refer to Article 210-8 , paragraph A, section 3, NFPA 70,
1990 National Electrical Code for the specifics.)
The purpose of GFI protection is to protect persons
from being electrocuted while using portable equipment that
is cord and plug connected while in contact with the earth.
If you take away the ability to use cord and plug connected
equipment, or remove access to the earth while using the cord
and plug connected equipment ie, grade level out of reach such as
a second floor deck with no stairs to the grade level or by
placing the receptacle out of reach ie more than 6'6" above
grade level (NEC) or use a branch circuit that is greater than
125 volts and or greater in amperage than 20 amps, you will find
that in most cases you will be complying with NEC....but once
again there are exceptions to every rule and local variations
also exist.
The above only applies to residential, there are other
ground fault rules that apply to commercial and industrial
installs.
Hope this helps some,
|
292.193 | Use good troubleshooting methods first | CSCMA::LEMIEUX | | Fri Aug 03 1990 11:38 | 6 |
|
RE: reply .160
Mike is absolutely correct, check out the circuit with
the Bug light unplugged to be sure that it isn't something else
causing the trip.
|
292.194 | A life is a terrible thing to waste | HNDYMN::MCCARTHY | What will I do when the day is 1.5 hr longer? | Fri Aug 03 1990 12:19 | 17 |
| I was thinking along the same lines as .161, hardwire it. That means
taking it apart and replacing the cord so it is wired directly into
a weatherproof box.
Then I was thinking that if you changed the male end of the plug to a
non-standard configuration (such as a twist-lock) you would eleminate
the issue of having anything else except the bug light pluged into this
receptical.
The problem with these solutions is that neither one of them will save
your life if the bug light falls into the pool of water you happen to
be standing in (or if the metal pole you are cleaning a pool with
contacts the zapper in such a way to electrify (sp?) it). My final
solution would be to see if the GFCI receptical was faulty and then if
that did not work try to fix the bug light.
Brian
|
292.195 | | NITMOI::PESENTI | Only messages can be dragged | Fri Aug 03 1990 12:48 | 7 |
| Well, I've never had a problem with the GFCI tripping 'till now. But, I've
only used the outside outlet for minor short term use (weed whacker) with
ungrounded (2 prong) plugs. The outdoor outlet does look a bit worse for the
wear, so I'll replace it and go from there.
While I'm here, if I wanted to direct wire the unit, what kind of wire is needed
between the house and the tree where it hangs. Is conduit needed?
|
292.196 | make sure your GFCI is not a lemon... | VAXUUM::PELTZ | Extinction is forever. | Fri Aug 03 1990 12:55 | 11 |
|
Another thing you may want to try if you have another GFCI outlet in your
house is to get an extension cord and try to plug the bug zapper into the
other GFCI. I have had faulty GFCI's before, sometimes they are overly
temperamental and trip their breaker at even very low circuit fluctuations.
If you find that this is the case, then just replace the GFCI with a new
one.
Chris
|
292.197 | Check the extension cord connections too. | OPUS::CLEMENCE | | Fri Aug 03 1990 13:42 | 15 |
| re: .164
Some other things that you can do is ensure that your not getting
water into the extension cord connection. I.E. It will short at the juction
of the plug and the extension cord. I would check and ensure its dry and
then tape over this joint.
re: .165
Could be your problem too. (A defective GFCI)
Bill
|
292.198 | AH HA! The plot thickens! | CSCMA::LEMIEUX | | Fri Aug 03 1990 14:02 | 19 |
|
Hi again,
The Bug light is in the tree with an extension cord
running back to the house outside outlet? Had any rain showers lately?
Those flip up covers are not water proof with the plug plugged
in and the cover flipped up. For permanent installations a different
type of outlet cover is required, one that stays waterproof with
the plug plugged into the receptacle.
Is the GFI a breaker type or receptacle type? If receptacle
type is it located outside in that receptacle box? I have also
had problems with GFI's located out of doors in boxes like that.
They get damp and trip. Dampness in the box outside can also trip
GFI's if they are located on the inside of the house too.
Isn't troubleshooting fun over the network :')
|
292.199 | short circuit? | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Fri Aug 03 1990 15:50 | 4 |
| re .161:
The folks who wrote the code must be very short if they think you can't
stand on the ground and plug something into an outlet 6'6" above grade.
|
292.200 | No, they just know that tall people be smarter... | NITMOI::PESENTI | Only messages can be dragged | Mon Aug 06 1990 07:21 | 20 |
| Well, another weekend went by without doing much about it but looking.
The box outside is not a GFCI outlet itself, but us wired to a GFCI outlet
(not breaker) inside. The out door outlet could be having moisture problems.
It is a flip up style outlet, and the plastic surrounding the holes is cracked
in a few places. My first step is going to be to replace this outlet. I am
curious about the outlets that remain weatherproof when something is plagged in.
Is there a name for them? Cost? Place to buy? The existing outdoor outlet
is flush with the house. An outlet whose box is surface mounted would interfere
with traffic up and down the back steps. Are these weatherproof outlets
available in flush mount (or at least such that only the plug and cord stick out
above the surface?
Thanks,
JP
ps: I did tape the plug into the extension cord with too much black plastic
tape. I did resist putting a layer of duct tape over that, however.
(almost any problem can be solved with duct tape...)
|
292.201 | Marine/Marina wiring devices | CSCMA::LEMIEUX | | Mon Aug 06 1990 13:48 | 12 |
|
Hi again,
Try getting a HUBBELL brand wiring device catalog. In
it you will find a section on marine/marina wiring devices...not
cheap but they work well and would satisfy the application you appear
to have. These catalogs can be had for free from your local electrical
supply if they are a HUBBELL dealer. There are other manufacturers
of this type of equipment, BRYANT, EAGLE, happen to come to mind
but my experience has been best with HUBBELL.
|
292.202 | ouch that hurts the wallet | EVETPU::MCCARTHY | What will I do when the day is 1.5 hr longer? | Mon Aug 06 1990 20:40 | 7 |
| >> Try getting a HUBBELL brand wiring device catalog. In
>> it you will find a section on marine/marina wiring devices...not
>> cheap but they work well and would satisfy the application you appear
They do may good stuff but THEY ARE NOWHERE NEAR CHEAP. It is not just
their marine stuff. Anything they make is very good quality and very
high priced.
|
292.203 | | CSCMA::LEMIEUX | | Wed Aug 08 1990 10:13 | 6 |
|
You are correct they are not cheap......I never said they were.
I have been hearing the same comments about certain brands of
electrical equipment (hubbel, square-d) for the fiften years I have
been in the trade. All I can say is you get what you pay for.
|
292.217 | Dual GFCIs and feed-throughs | STAR::DZIEDZIC | | Mon Jan 07 1991 12:55 | 23 |
| Any Master Electricians out there have an opinion on this? I can't
find anything in the NEC which describes this situation.
I want to install double-ganged duplex receptacles above my workbench
to increase the number of outlets available without using up lots of
wall space, feeding each of the two outlets in the double-gang box from
a separate branch circuit to increase the total ampacity available.
In the "pre-GFCI" days this would be easy; run 14-3 from a two-pole
breaker, observe the NEC requirements about integrity of the grounded
conductor, and daisy-chain the 14-3 to subsequent boxes (a total of
three boxes in the chain => six duplex receptacles).
I want to use a similar scheme in my new house, but intend to use GFCI
receptacles at the "head" end of the chain. This means I need to run
two separate 14-2 cables to the subsequent boxes (in which are mounted
standard duplex receptacles). This leads to an interesting question.
In all the subsequent boxes, the grounded conductors (white wires) of
the feed-throughs must remain distinct, otherwise the head-end GFCIs
may become confused due to current imbalances. Does the NEC prohibit
such a distinction? Normally one would expect all grounded conductors
(white wires) to be tied together (discounting the case of "identified"
white wires used for switch loops and etc.).
|
292.218 | | VMSDEV::PAULKM::WEISS | Trade freedom for security-lose both | Mon Jan 07 1991 14:38 | 6 |
| I don't know about the GFCI's, but for a workbench outlet you should definitely
use a 20A circuit, not 15A. Many hand power tools will be too much for a 15A
circuit, particularly at startup. And for the 20A circuit, you'll need 12-2
wire.
Paul
|
292.219 | MA Master # A11840 | WMOIS::BOUDREAU_C | | Mon Jan 07 1991 16:16 | 15 |
| RE:0
You are correct. One must keep the grounded conductors separate as
soon as you leave the GFI's. But the assumption that all grounded
conductors are typically tied together is wrong. If you have 2
separate circuit feeds in a box, one must keep the grounded conductors
separate. Just as you would keep the ungrounded conductors separate.
The only conductors that get tied together in a box regardless of the
circuit that they belong to is the grounding conductors. This ensures
that there is a zero voltage potential between grounding conductors at
each location.
CB
|
292.220 | ed and ing make tough reading | EVETPU::MCCARTHY | Well Norm, lets go take a look. | Tue Jan 08 1991 07:51 | 28 |
| re .2:
I had to read this a few times. Using the correct terms grounding and
grounded may confuse people. If I may:
>> separate circuit feeds in a box, one must keep the grounded conductors
>> separate. Just as you would keep the ungrounded conductors separate.
separate circuit feeds in a box, one must keep the grounded (neutral)
conductors separate. Just as you would keep the ungrounded conductors (hot)
separate.
>> The only conductors that get tied together in a box regardless of the
>> circuit that they belong to is the grounding conductors. This ensures
The only conductors that get tied together in a box regardless of the
circuit that they belong to is the grounding (usually the bare copper, or
green insulated/marked) conductors. This ensures
I also agree with .1, use 12 guage wire and 20 amp breakers. The
price difference is little and the feeling of security is great :-) You can
use the same GFCI outlets and chain them. Just make sure they are rated for 15
Amp and 20 amp through.
I assme you are going with GFCI's because of the change in the NEC
about outlets in an unfinished basement? Just what does constitute an
unfinished living space anyway?
Brian
|
292.221 | | STAR::DZIEDZIC | | Tue Jan 08 1991 08:49 | 18 |
| Re .2: Thanks for the verification!
Re .3: About the only nit I'd pick with your clarification is the
use of the term "neutral" for the grounded conductor. You can only
have a "neutral" conductor in a 3-wire 120/240 volt circuit; once
a 2-wire 120 volt circuit branches from the panel, technically you
no longer have a neutral conductor, but rather a grounded conductor.
You're right, though, that the "ed" and "ing" suffixes can be a
little confusing, but if you're going to do electrical work you
really should learn and understand the differences between the
"grounded" and "grounding" terms.
Yes, 12 gauge is what I will be using (although I might jump to
10 gauge for a long run to minimize voltage drop). I'm using
GFCIs primarily because of the safety factor; I'd probably use
them even if the NEC didn't require them.
|
292.204 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Thu Jan 17 1991 10:06 | 2 |
| I'd like to know what outlets are downstream from a GFCI outlet. If I hit
the test button, will all downstream outlets go dead?
|
292.205 | Yes, assuming the test button works | VMSINT::DZIEDZIC | | Thu Jan 17 1991 11:02 | 2 |
| Yes, assuming the GFCI works properly and the test button really
does trip the interrupter in the outlet.
|
292.222 | some clarification | SLOAN::HOM | | Mon Jan 21 1991 13:35 | 27 |
|
In .0,
> In the "pre-GFCI" days this would be easy; run 14-3 from a
> two-pole breaker, observe the NEC requirements about integrity of the
> grounded conductor, and daisy-chain the 14-3 to subsequent boxes (a
> total of three boxes in the chain => six duplex receptacles).
Is three the maximium number of boxes allowed in a chain? What's
the maximium number of boxes in total? I'm in a house built in
1979 and I think there are circuits with more than 3 boxes.
Of course, the code may have changed since then.
Regarding .3
> I also agree with .1, use 12 guage wire and 20 amp breakers. The price
> difference is little and the feeling of security is great :-) You can
> use the same GFCI outlets and chain them. Just make sure they are rated
> for 15 Amp and 20 amp through.
This in not intuitive. I always thought that you needed 20 amp devices
for 20 amp service. Aren't you required to have 20 amp outlets on
20 circuits? Of course few people do.
|
292.223 | Clarification | STAR::DZIEDZIC | | Mon Jan 21 1991 14:13 | 20 |
| No, the "three boxes" was just in my example. The last time
I checked the NEC there was no explicit limit on the number
of receptacles on a circuit, but most inspectors use the "rule
of thumb" which says allow 1.5A per receptacle. This gives a
limit of 8 per 15A circuit, 12 per 20A circuit. (This is for
120 volt outlets; 240 volt is another matter.)
Regarding the rating of devices on 20A circuits, what is really
necessary is that the device is rated for 20A feed-through
capability (most 15A receptacles ARE 20A feed-through rated).
This simply means that the connections on the device are such
that they can handle a 20A current. The NEC allows you to
connect such a 15A receptacle to a 20A circuit. It also will
allow a 20A receptacle "downstream" of the 15A one.
Most GFCI receptacles have a 20A feed-through rating.
(Note that a 20A plug has the groundED blade at a 90 degree angle
to the normal orientation.)
|
292.244 | Similar but not the same problem | HELIX::SONTAKKE | | Tue May 21 1991 23:43 | 21 |
| I wish my problem had *remained* that simple :-( My wife opened the
garage door but could not close it. I found that it was not receiving
any power. Eventually I traced it GFI ckt in the upstairs bathroom.
It was NOT tripped but TESTing and RESETing it seemed to fixed it, at
least for a while.
However, when I tried to explain and show it to my wife, I discovered
that once I again I have lost all the ckts connected to that GFI. I
have repeatedly TESTed and RESETed it with no effect. I have also reset
the corresponding circuit breaker at the main pannel, just in case.
I borrowed a small plug tester from the neigbor. LED display shows
something like "Hot/Neut Rev". If I trip it with TEST button, no LEDs
light up.
Any advice?
Thanks,
- Vikas
P.S. It is relatively new (1986) construction.
|
292.245 | | QUARK::LIONEL | Free advice is worth every cent | Wed May 22 1991 10:39 | 11 |
| Re: .13
If the tester showed "hot-neutral reversed" you have a miswired outlet and
a VERY dangerous situation. That might also explain why the GFI is not
working properly. Turn off the circuit breaker for that circuit and
rewire the GFI correctly - black wire should go to dark-brass colored
terminal (or black wire), white wire to silver-colored terminal (or
white wire). The tester should show two yellow lights and no red lights
when plugged in.
Steve
|
292.246 | | HELIX::SONTAKKE | | Wed May 22 1991 16:24 | 20 |
| All the wires go to the right places and the screws are tight. I
refused to touch anything if the ck is live. Herre are the results
with breaker off :-
1. GFCI tripped (I needed to turn the breaker on before I could trip
the GFCI, so at least it does create a fault to test it!)
No Continuity between Load Hot and Line Hot
No Continuity between Load Neut and Line Neut
2. GFCI RESET
Continuity between Load Hot and Line Hot
*BUT* No Continuity between Load Neut and Line Neut
It does look like that the GFCI itself has gone bad. This looks like a
Leviton product. Does it come in standard size?
- Vikas
|
292.247 | | QUARK::LIONEL | Free advice is worth every cent | Wed May 22 1991 17:32 | 5 |
| GFIs do go bad. They are standard size, and the Leviton model is the most
widely available and is pretty cheap - prices as low as $7.50 have been
seen lately.
Steve
|
292.248 | circuit tester requires power on to work | POBOX::KAPLOW | Set the WAYBACK machine for 1982 | Thu May 23 1991 19:24 | 11 |
| If you are talking about the "standard" outlet tester, it won't
tell you anything unless the circuit is LIVE. If you suspect
problems and are afraid to plug it in live, then first plug it in,
then turn the breaker back on. Anything other than the two green
lights ON and the red light OFF is a problem.
If that tests OK and the GFI still trips, then either the GFI is
bad, or you have a wiring problem or bad device plugged in
downline of the GFI. With the breaker again off, disconnect the
downstream leg from the GFI to tell if it is the GFI itself is the
problem, or if it is the downstream leg.
|
292.249 | another caveat on 3 prong testers | RGB::SEILER | Larry Seiler | Fri May 24 1991 16:38 | 9 |
| And also, when a 3 prong circuit tester says your circuit is bad, it isn't
always bad in exactly the way the thing says. It depends on how creatively
your circuit was wired! For example, if both the hot and neutral are at
high voltage, a 3 prong tester will tell you that neutral and ground are
reversed. I had to get a 2 prong glow tester to figure that one out.
Enjoy,
Larry
|
292.26 | 204v GFI - roll your own | SEESAW::PILANT | L. Mark Pilant, VMS Security | Mon Jul 01 1991 11:54 | 16 |
| I had a similar question when I was looking for an ITE 240v 50A breaker when I
installed a spa. The folks at Ralph Pill told me that such a beast did not
exist. GFI 240v breakers went to about 30A, and that was it. (Take this
with a grain of salt, however, I didn't persue it very far, so such a beast
may really exist.)
There are two solutions that come to mind:
1) Create your own ganged 240v breaker by bolting the handles if two
120v breakers together. (I'm not sure if NEC code would allow this,
I suspect it may not.) I don't know how 120v go, as far as amperage.
2) Build your own GFI circuit. I have a book with at least one GFI
circuit in it.
- Mark
|
292.27 | Square D makes them | STAR::DZIEDZIC | | Mon Jul 01 1991 12:04 | 10 |
| I checked with Seaman's Supply here in Nashua and was told that ITE
doesn't go above 30A for a 240V GFI breaker - however, Square D does
make such a beast. You COULD use a standard ITE 2-pole (240V)
breaker and feed a Square D subpanel which would contain the Square
D GFI breaker. A little more expensive, but at least you get the
GFI protection for which you're looking.
Bolting two single-pole GFI breakers together wouldn't work - since
there would be NO current through the white (groundED) conductor, the
breakers would immediately trip under any load.
|
292.28 | Its not required, but... | WMOIS::BOUDREAU_C | | Mon Jul 01 1991 19:28 | 24 |
| Bruce,
The NEC does not require GFCI protection on 240v receptacles. The
intent of the law is to protect the fool with the 2 wire (or 3 wire
w/broken grounding conductor pin) extension cord, or cords on tools. If
the tool at the other end has a "ground fault" and there is no ground
in the cord, the GFCI will see the current imbalance and trip. The same
situation without GFCI protection, the fault current would take the
lowest resistance path to ground (this is probably the person using the
tool). Most 240v tools, or those of 30amp and up, have properly
grounded cords, and the cannot plug into standard cords (the big
problem). Thus, the NEC doesn't require protection on "all" outside
receptacles. What would be within the law (although, I will recommend
something else), is to install the receptacle necessary in a weather
proof enclosure and cover. "I" would install the receptacle inside,
where you could run a longer cord to it (this will eliminate allot of
corrosion that will occur if it is installed outside). As long as your
cord is in good shape, and all of the connections are tight, you
shouldn't have a problem. This is what the grounding conductor is there
for. It may not sense a small leakage to ground, but it will provide a
"lower" resistance path (as opposed to you) to ground. And it "will"
trip on a dead short to ground.
CB
|
292.29 | Not a good GFI application. | JVAX::JOHNSON | | Tue Jul 02 1991 14:41 | 31 |
| I have several comments on the situation.
First, ganging breakers, GFI or not, is not recommended unless specifically
permitted by the manufacturer. Most (all?) ganged breakers have internal
common trip hardware in addition to the ganged handle, partly to assure trips
regardless of handle position.
ITE does have provision for special GFI situations. You need to directly
contact ITE and tell them your application, and they will tell you the parts,
e.g. current transformer and breaker, needed for your situation. We have done
this for some of our lab three phase applications.
I doubt if you will be able to use a GFI on a welder, mostly for noise
reasons. GFIs sensitive enough to prevent shock are often fairly sensitive to
electrical transients.
The other welder issue, is what are you trying to protect against. Arc
welders come in two varieties, the first has an isolating transformer which
separates the supply from the welding electrodes. There is no conductive path
from the supply to the electrodes, only magnetic coupling, meaning no path to
trip the GFI. For magnetic reasons, the primary winding is separated from the
secondary, usually by a couple inches, so primary to secondary shorts are
unlikely. In this case, the only thing you may be protecting against is a
short from the supply wiring to the case of the welder, a situation which is
better controlled by good grounding of the equipment.
If you have one of the cheap arc welders which simply uses a choke in series
with the phase conductor, any connection of the work electrode (neutral) to
a grounded object will trip the GFI.
Of course there is always the shock potential between the welding electrodes.
|
292.30 | Home grown ganged breakers are a BAD idea | SEESAW::PILANT | L. Mark Pilant, VMS Security | Tue Jul 02 1991 18:04 | 12 |
| RE: Home grown ganged breakers
I agree that trying to roll your own ganged breaker is a waste of time.
(I suspected there were a number of reasons not to do it, code violation
not the least, but didn't have a good grasp on what they were.)
It is nice to know that GFI breakers are available 240v at higher amperages.
Maybe I'll never need one, but in case I do...
Now if only GFI breakers weren't so darned expensive :-(
- Mark
|
292.206 | Add a few feet of wire, screw up the GFCI circuit | LYCEUM::CURTIS | Dick "Aristotle" Curtis | Tue Feb 04 1992 16:49 | 24 |
| Here's one that is puzzling my father and me:
GFCI in a metal box, fastened to the bottom of the breaker cabinet.
3 wires run from the various breaker terminals, to "LINE" and ground
of the GFCI. 3 more run from "LOAD" and ground (hm, I think that was
true) to go off to bathroom outlets. Worked fine, but the positioning
of the box on the wall was deemed awkward.
Box moved from chest-high to about 16" off the floor; wires cut and
run; GFCI hooked up -- backwards (hot & neutral reversed, smooth
move!) -- and it tripped. Hooked up correctly, and it tripped when
power was applied.
Suggested that perhaps hooking it up with hot and neutral fried
something in the GFCI, and it would have to be replaced. So it has
been replaced -- and also the wires running to and from it, and it
still trips.
It appears that the first outlet downstream from the GFCI is one
mounted on the exterior of the house, FWIW.
Can anyone offer any suggestions?
Dick
|
292.207 | | RAMBLR::MORONEY | Is the electric chair UL approved? | Tue Feb 04 1992 17:19 | 8 |
| I wouldn't think swapping hot and neutral would damage a GFI outlet. Maybe
a corroded contact on the neutral when activated with 110V AC became a
leaky circuit to ground or something.
Try disconnecting all "load" wires and see if it still trips. If so, it is bad
after all.
-Mike
|
292.208 | This I can tell you off the top of my head | LYCEUM::CURTIS | Dick "Aristotle" Curtis | Tue Feb 04 1992 17:33 | 3 |
| With no load, it works; but that leaves the downstream outlets dead.
Dick
|
292.209 | | RAMBLR::MORONEY | Is the electric chair UL approved? | Tue Feb 04 1992 17:37 | 5 |
| I suppose you could go to each outlet in line and disconnect the downstream
side until either 1) you find where the problem is or 2) you get to the last
outlet without finding it, in which case it now works :-)
-Mike
|
292.210 | Old setup maybe not seeing fault | NICCTR::MILLS | | Tue Feb 04 1992 17:37 | 27 |
| Does it trip with no circuit and does the test button work? If not it's
hooked up wrong, you have a bad GF breaker, or you have a bad ground.
If that's ok then continue reading.
Hook just an outlet (or another simple circuit in the house) to the new
ground fault circuit and test it. It should trip when you put a load
between "Hot" (black side with short slot) and Ground. It should also
trip from "neutral" (white side with long slot) to ground. And of
course it should not trip when you put the load between "hot" and
"neutral". You can't use a multi-meter or neon light for a load test. A
coil tester is easiest but you could use a lamp with homemade probes.
If that works then It could be that the old GF was not as sensitive,
not working, or not installed properly. AND that there is a fault in
the circuit. It is very common to have a fault in an outside outlet.
They tend to leak water into them. The fault is very likely between
"neutral" and ground. You'll just have to take each box on the line
apart as you go down the line to find it. Just taking the box apart
will usually cause the fault to go away. Putting the box back together
properly is the trick to doing it right (ground lead does not touch
neutral terminal on outlet).
Is this the outlet style or breaker style GF?
My GUESS is that hooking the GF backwards would not blow it and perhaps
when you hooked up either GF correctly your detecting a fault that has
existed for a while.
|
292.211 | Thank ye, gentlemen! | LYCEUM::CURTIS | Dick "Aristotle" Curtis | Tue Feb 04 1992 17:47 | 6 |
| .178, .179:
Sounds like good advice. I'll report back when we've tried your
suggestions.
Dick
|
292.212 | Aren't GF's great :-) | NICCTR::MILLS | | Tue Feb 04 1992 17:50 | 4 |
|
Remember also that the GF is the best thing since the light bulb. It's
trying to tell you that you have a problem.
|
292.213 | Switched/Unswitched plug in single GFCI unit? | NETRIX::michaud | Jeff Michaud, PATHWORKS for Win. NT | Wed Sep 07 1994 15:35 | 12 |
| Sorry if this was already asked in .25-.181, but does anyone
know if such a thing exists as a GFCI outlet where you can wire
such that one of the two plugs on it can be switched, while
the other is unswitched?
I could of sworn I saw on an older episode of "Home Time" where
Joanne put in a GFCI outlet under the sink to plug in a
dishwasher and garbage disposal, where of course the disposal
would be switched, while the dishwasher is not.
Home Depot sells no such unit that can be wired in this fashion,
and the person I talked to had never heard of such a thing.
|
292.214 | | QUARK::LIONEL | Free advice is worth every cent | Wed Sep 07 1994 15:54 | 3 |
| I've never seen such a thing.
Steve
|
292.215 | ...so we did. | KEPNUT::CORRIGAN | | Wed Sep 07 1994 16:19 | 4 |
| I too tried to find this set up but no luck. It was for a bathroom
sink area with outlet/light switch comination. The electrician
suggested connecting to a GFI circuit breaker at the panel instead.
|
292.216 | re .182: switching a GFCI outlet | WRKSYS::SEILER | Larry Seiler | Wed Sep 07 1994 17:42 | 10 |
| Well, you could wire a receptacle downstream from the GFCI, such
that one plug of the downstream receptacle is switched and the
other isn't. Or place the second receptacle next to the GFCI
and use the GFCI for unswitched power and the adjacent receptacle
for switched power. You'd route the black wire out of the GFCI
to the switch, and from their to the black connection on the
receptacle.
Enjoy,
Larry
|