84.1 | Burners sized by BTU rating. | HPSVAX::SHURSKY | A ghost when Xmas is past. | Mon Jan 18 1988 15:21 | 13 |
| Cost is generally proportional to BTU rating. More BTU's -> more_$.
I doubt anyone can offer a price without knowing what size burner
you will be buying. The rating is usually on a plate on the burner.
Check Consumer Reports, they may have some suggestions. I have
a Burnham America unit. All I know is that a service man commented
about the lack of reliability of the units whose serial numbers start
with BBC. I called the president of BA and told him what I heard.
He asked for the serial number of the unit. I said "BBC....".
He said "That's impossible!" Apparently there was some legal fracas
and they are no longer made but my builder was able to find one
special to install in my new house 3 years ago. (Thank Yew Mr. Builder!)
Stan
|
84.2 | My thoughts | WORDS::DUKE | | Tue Jan 19 1988 07:36 | 19 |
| If the present unit will hang in until spring I would wait. This
is not the time of year to purposely be without heat.
If you are in the Merrimack area, I would recommend either Rochette
Oil in Merrimack or Masi in Nashua. Talk to Bob Rochette or Mr.
Masi (Bob Boisivert). Feel free to use my name in either case.
I know both of them and feel that they are good people.
If you are into DIY, a neighbor of mine bought a Sears FHA unit
at a very good price at the Pheasant Lane store. It was an 'extra'
unit still in the crate with all the warrantees and service for
about half price.
A FHA system that also handles hot water? I have never heard of
such a thing, but I suppose it is possible. I doubt if there is
such a thing today.
Peter Duke
|
84.3 | Ah but they did exist | SIGANA::GOODSTEIN | Stay tuned for station identification | Wed Jan 20 1988 15:46 | 11 |
| There was a house I use to share in Stoneham that used oil and
heated the house by FHW and also provided hot water. While it saved
my landlord lots of money in hot water bills, we would easily run
out of hot water in the winter since we were competing with the
house for heat. Hot water usually lasted 30 seconds. It might have
lasted longer if we used an efficient shower head but I couldn't
convince my roomates to chip in.
Anyways I know the unit was installed in the early eighties.
Hope this helps %-)
Ron
|
84.4 | FHW or FHA that is the question | WORDS::DUKE | | Thu Jan 21 1988 07:21 | 6 |
| I agree with domestic hot water with FHW, mine is. I questioned
it with FHA referenced in .0 That seemed to be a strange combination.
Pete
|
84.5 | There are some new units | MAY11::WARCHOL | | Thu Jan 21 1988 11:24 | 6 |
| There are some new, very high efficiency, FHA units that use an
ethyl glycol solution with a heat exchanger arrangement. They will
also provide domestic hot water. The only ones that I have seen
are gas fired.
Nick
|
84.6 | Do I have an antique ? | TALLIS::LEMIEUX | | Fri Jan 22 1988 13:19 | 10 |
| Yes, it is really, truely, a FHA system that also supplies the hot
water. I hope they still make them. I don't like the idea of gas,
and I'm not much interested in having a FHA system and a separate
water heating system ( don't want to maintain two burners ), and
I do not want an electric water heater.
Somebody tell me they still make FHA systems that also heat the
water.
kl
|
84.7 | | TOPDOC::PHILBROOK | Chico's Daddy | Tue Jan 26 1988 14:55 | 3 |
| > I do not want an electric water heater.
Why not? What are the disadvantages?
|
84.8 | I found one !! | FDCV14::DUNN | Karen Dunn 223-2651 | Tue Jan 26 1988 15:42 | 5 |
|
I went to my in-laws at the cape last weekend. Turns out they have FHA,
oil, that also heats the household water.
Not that I know anything about them, but they do exist.
|
84.9 | And wait, it will go higher! | CRAIG::YANKES | | Tue Jan 26 1988 16:00 | 15 |
|
Re: .7
>> I do not want an electric water heater.
> Why not? What are the disadvantages?
Well, if you live in southern NH, can you spell P-S-N-H? :-)
I recently bought a new water heater and the "cost per year" on
those flame-yellow stickers were around $160+/- (I've forgotten
the exact number already...) for the gas and around $300-350 for
the equivalent electric heaters.
-craig
|
84.58 | Furnace FUMES - help!!! | BPOV10::CLEMENT | | Thu Mar 03 1988 08:54 | 16 |
| Another problem (can't you tell I'm a new homeowner).
I was painting in the kitchen and dining area last nite and noticed
that every time the furnace starts up I smell fumes in this area.
The furnace is located under the kitchen in the basement. The
house is 25 years old, and we are moving in this Saturday.
I am a novice to home maintenance but I suspect that there must
be somekind of damper that opens when the furnace starts up and
the exhaust then goes up and out the chimney. Maybe this is
not opening. I will check it out tonite. Am I on the right
track or not? Can anyone one tell me what it looks like and
location and how to fix?
More info: This is an oil fired FHA system.
|
84.59 | Possible hole in air chamber | SEESAW::PILANT | L. Mark Pilant | Thu Mar 03 1988 09:08 | 28 |
| First question I have is what kind of "fumes". If it is a musty
sort of smell, it could be something as simple as a dirty filter
on the air intake.
If it is really smells like hydrocarbon combustion, then it sounds
like there might be a hole in the air chamber. (Most FHA systems
I have seen use gas, oil, ot hot water to heat an air chamber.
The inlet to this chamber is the col air return, and the outlet
is via the blower motor through the various air vents in the house.)
If there is a hole, it would allow combustion gasses to entry the
chamber.
Another possibility would be that you have a clogged flue. This
could allow the combustion gasses to back up and leak through any
small (or large) holes in the pipe from the furnace to the flue.
The diverted gasses may then be entering the air chamber via the
cold air intake. You could check for this by standing in the same
room as the furnace, and determining if you smell the combustion
gasses. If you don't, and the furnace is an older one, it probably
indicates a hole in the air chamber.
FWIW, my 2� worth. Hope it helps.
One last thought. As you probably already know, this should be
corrected ASAP. Carbon monoxide is odorless, and nasty stuff to
fool around with.
- Mark
|
84.60 | Three things | STAR::SWIST | Jim Swist ZKO1-1/D42 381-1264 | Thu Mar 03 1988 09:12 | 11 |
| 1) Check this out asap, might also mean carbon monoxide escaping.
2) There is usually not a damper that opens electrically, but I
suppose there could be a mechanical damper which is stuck close.
3) Are you painting with oil base paint? If your ventilation is
poor, you can get suspended volatile particles circulated through
your heating system which will c0ome back out with a burnt/fumey
odor. (You can even notice this if there is as much as a pilot
light (stove) in the same room as the paint vapor).
|
84.61 | One possibility: obstructed stovepipe. | TALLIS::KOCH | Kevin Koch LTN1-2/B17 DTN226-6274 | Thu Mar 03 1988 09:16 | 25 |
| > ... every time the furnace starts up I smell fumes in this area.
>
> I am a novice to home maintenance but I suspect that there must
> be somekind of damper that opens when the furnace starts up and
> the exhaust then goes up and out the chimney. Maybe this is
> not opening. I will check it out tonite. Am I on the right
> track or not? Can anyone one tell me what it looks like and
> location and how to fix?
>
> More info: This is an oil fired FHA system.
When I had this problem, it was a piece of flue liner that had broken
off and landed right in front of the furnace stovepipe. The fumes would
blow out through the stovepipe fittings.
This is an expensive problem to fix correctly. First, it means that
your flue liner is falling apart. Second, it means that your chimney has
5 feet of rubble in it from the floor to where the stovepipe fits in. If
there is no cleanout in the bottom of the chimney, one should be put in.
Also a chimney cap. And the rubble must be disposed of as hazardous waste.
To see if this is your problem, pull the stovepipe off. Stick your
hand down the chimney to see if it is full. Vacuum out the boiler and
stovepipe if you have a shop vac. But I would think that your building
inspector would have done this and checked for holes as suggested in .1.
|
84.62 | (cough...cough) | HPSVAX::SHURSKY | Have Mac - will travel | Thu Mar 03 1988 11:25 | 9 |
| I had a similar problem. In a previous house, decaying mortar,
soot, and who knows what fell down the chimney and eventually
clogged the end of the stovepipe from the furnace. I took out a
couple of buckets of soot etc. Wear a mask that stuff is fine
and you don't want it in your lungs. (I didn't, I know!) I
didn't know about any regulations and just tossed the stuff down
the bank behind the house on the poison ivy. (Sorry, MA EPA!)
Stan
|
84.63 | Clogged nozzle in one case | STAR::BECK | Paul Beck | DECnet-VAX | Thu Mar 03 1988 11:57 | 8 |
| I've had similar effects a couple of times when the nozzle which
injects the oil into the burner needed replacement (clogged or
whatever). I gather the spray wasn't as even as it should be,
and didn't always ignite quickly, so there would be a late ignition
with excess oil, causing the furnace to belch a lot of fumes
up the flue. It tended to back out of the flue damper. It was
obvious when this happened, as the furnace made a lot of noise
starting up.
|
84.64 | It may be the points | SAGE::DERAMO | | Thu Mar 03 1988 12:19 | 36 |
|
I was at a friend's house last month, when we heard a significant
explosion. We looked outside to see if a tree had fallen on the
house, but that wasn't it. We opened the door to the basement, and
immediately smelled smoke. We shut off the emergency burner switch,
and went down to the basement (cough, cough). The cleanout door
below where the furnace pipe attaches to the chimney had been blown
out, and across the basement.
We called their oil service man. When he arrived, he knew exactly what
was wrong -- this was apparently a fairly common problem.
He opened up the burner unit (Beckett) looked at the two points
near the fuel nozzle head (my terminology), and found that the points
had burned down considerably -- the gap between nozzle an point
tip was now much too wide. When this happens, the spark that is
supposed to ignite the fuel spray takes much longer to do it's job.
As a result, the fuel continues spraying without ignition, and when
it finally does ignite, the chamber is quite full of fuel, an results
in a mini to a MAXI explosion.
All furnaces have safety devices that prevent the fuel from spraying
too long (over 40 seconds, I think) without ignition, but sprays under
that time can still cause explosions.
The repairman regapped the points, cleaned the fuel spray nozzle,
did some other maintenance tasks, and closed up the burner. It worked,
and has continued to work, just fine. I think he charged just $25.
-- Joe
|
84.65 | | DECSIM::DEMBA | | Thu Mar 03 1988 12:20 | 3 |
| Another possibility, sometimes old cast iron boilers will start
to fall apart. The cement between the boiler sections crumbles,
thus you end up with a leaks in the fire box.
|
84.66 | update... | BPOV10::CLEMENT | | Thu Mar 03 1988 12:28 | 17 |
| Thanks for the information. I will do a visual inspection tonite
of all these things.
I was using a latex semi-gloss paint.
Yes I do have 2 small doors at bottom of chimney. One for furnace
and one for fireplace in livingroom (I suspect).
It is definately a combustion odor. My wife was there most of the
day yesterday and was feeling sick all day, then felt fine after
leaving.
I am trying to get a furnace guy there tomorrow morning. My wife
called around and found this company (COAN) located in Milford
and they have a two year maintenance contract, parts & labor, for
$99.00, they also give us 5 $10 coupons towards fuel, and they
charge .94/gallon. After the first two years the contract is
$99.00 a year.
|
84.67 | Possibilities for differentiating the problem. | TALLIS::KOCH | Kevin Koch LTN1-2/B17 DTN226-6274 | Thu Mar 03 1988 13:15 | 22 |
| 1> My wife was there most of the
1> day yesterday and was feeling sick all day, then felt fine after
1> leaving.
2> I am trying to get a furnace guy there tomorrow morning. My wife
2> called around and found this company (COAN) located in Milford
2> and they have a two year maintenance contract, parts & labor, for
2> $99.00, they also give us 5 $10 coupons towards fuel, and they
2> charge .94/gallon. After the first two years the contract is
2> $99.00 a year.
WRT 1: Whether the smell is only generated when the burner starts, or
is present the entire time the burner is running might differentiate
between ignition/nozzle problems and exhaust blockage. As a further
startup diagnostic, you can turn off the switch at the furnace, crank up
the thermostat, open the boiler door, turn on the switch at the
furnace, and watch what happens. BTW, you're in luck with the
cleanouts! Do you have a cap on the top of the chimney, too?
WRT 2: Once you learn how to take care of these things yourself,
you'll find $99/yr a lot. *IF* you have the inclination, you can maintain
and run your system for $5/yr + $0.75/gal.
|
84.68 | re .9 | BPOV10::CLEMENT | | Thu Mar 03 1988 14:06 | 9 |
| re .9
Yes I think $99/year is quite a bit. But 2 years for $99 is not
so bad. Especially if they clean it yearly.
I am a dedicated DIY and plan to watch the service mans every move
tommorow morning. I have to ask, how does your $5/year plan work?
There must be some basic steps you perform on a periodic basis.
|
84.69 | COAN's OK | REGENT::GETTYS | Bob Gettys N1BRM 223-6897 | Thu Mar 03 1988 15:29 | 20 |
| Assuming that COAN in Milford is the same as COAN in
Natick (and I'm pretty sure they are), then that price probably
does include a yearly cleaning and inspection. We use COAN in
for our furnace and what you are paying for is two things, first
the yearly cleaning (much too much for just that - it takes
about a hour to do it right), and second you are paying for
insurance that will repair most (but not all - read the fine
print) problems that you may have during the year. Last year my
contract paid for itself as I needed a circulator pump replaced.
Cost to me for that service? Except for the contract - ZERO.
You can do the cleaning yourself. You can keep a small
supply of a few critical parts handy. You can do the repairs
yourself. But on Saturday night when the furnace dies, it sure
is nice to be able to call COAN (or whomever) and get it fixed.
And if its one of those very cold nights (when else does it
fail?) and you don't have a contract, guess where your call goes
(can you say - Bottom of the Pile?).
/s/ Bob
|
84.70 | Let me know what he does that I left out. | TALLIS::KOCH | Kevin Koch LTN1-2/B17 DTN226-6274 | Thu Mar 03 1988 15:37 | 35 |
| These are the things you're supposed to do once a year:
You can vacuum the inside yourself with a shop vac. Get a long
handled wire brush to knock the scale off. this is the most time
consuming part.
You can change the filter yourself. It costs $2. Be sure to fill
the canister up with oil before putting the little screw back on, or
you'll get air in the lines and have to prime the pump.
You can change the nozzle yourself. It costs $3. Or if you have the
kind that comes apart, you can disassemble it and clean it with a Qtip.
This is what I had to do two Sunday nights ago when it was going down to
10 degrees! To get to the nozzle [Becket burner instructions] remove the
four small screws holding the steel pipe that goers into the furnace (two
on top, one on each side). Pull out the firing assembly. Use TWO
WRENCHES to remove the nozzle, or you could break off the pipe its on.
After you remove the nozzle, run the pump until the oil runs clear.
When I changed the filter, the glop in the bottom of the canister got into
the line and clogged the nozzle, which is whty I had to learn how to clean
the nozzle. NOTE: Any time you run the burner when its pulled out, flip
the transformer back so that its disconnected!!!
After you put the nozzle back (if cleaned), put the paper cup back
over it and run the pump to make sure its spraying.
Slide the firing assembly back in and reattach the steel pipe.
Note: it is safer to prime the pump after putting the burner back in
place, which cleans out the line and avoids having to flip the transformer
back. But I haven't gotten myself in a situation yet where I've had to
learn to prime the pump!
Total cost $2 + kitty litter. Total time 1 hour.
|
84.71 | what did happen... | BPOV10::CLEMENT | | Fri Mar 04 1988 12:05 | 20 |
| Just to let you know the results...
The burner guy came this morning. He cleaned the system, said it
looks like two years since its been cleaned. Set off some type of
"bomb" that would cause an odor to go thru the vents if the system
was leaking fumes. My wife said she did not smell anything.
End of problem, I hope!
HE did say the system was very old. If she smelled something the
furnace would have to be replaced (so he said, about $2,000).
He did say the burner was running 71% efficient and should be
replaced this summer (he said about $450).
Well i guess I will start scanning the file for burner replacement
tips. I think I could probably do it myself. I have worked on
cars for years. House problems are new to me but I can't imagine
any more difficult.
Thanks again for all your replies. Mark.
|
84.72 | | MILT::JACKSON | who you jivin' with that cosmic debris? | Fri Mar 04 1988 13:54 | 11 |
| First of all, get someone to replace your burner for you. They
know how to set the flame properly, and I'm sure you don't. (I
played with mine this year, and never really got it just right)
Anyway, if you wait till the end of summer, lots of oil companies
run promotions so you'll buy their oil. I've seen some offer free
burners if you sign up for some period of time. (like a year or
something) I'd start calling then (like maybe August)
-bill
|
84.73 | | HPSMEG::LUKOWSKI | I lost my A$$ in the '87 CRASH! | Fri Mar 04 1988 13:58 | 22 |
| >> HE did say the system was very old. If she smelled something the
>> furnace would have to be replaced (so he said, about $2,000).
Maybe he's right but based on the highly technical evaluation above,
I would certainly call someone else to check it out if it does happen again.
>> He did say the burner was running 71% efficient and should be
>> replaced this summer (he said about $450).
For an oil fired FHA, that's really not bad. I believe that mine is
somewhere around the mid 60's. I was concerned when I found this out and the
guy said that he could certainly increase 'efficiency' dramatically but it
would need another cleaning within a few weeks/months because it would be
burning too dirty. I'm really not that concerned about the efficiency in this
case since I use so little fuel to heat my house. I used about 400 gallons
last winter. If you are using a lot of fuel, this may very well be something
to be concerned about but try to get the right expectations on what the payback
of a new burner will be.
-Jim
|
84.74 | GET SEVERAL ESTIMATES | SALEM::SALISBURY | Rae Salisbury 261-3560 | Fri Mar 04 1988 14:52 | 6 |
| JUST A SUGGESTION. I REPLACED MY FORCED HOT AIR FURNACE WITH A
NEW EFFICIENT (BECKETT BURNER) FOR $1076. INCLUDING LABOR. (COST
OF FURNACE AROUND $950.) ALSO, .94 PER GAL FOR OIL SEEMS EXPENSIVE.
I JUST FILLED UP ON TUESDAY FOR .679 PER GAL. I AM IN SO. N.H.
I WOULD GET SEVERAL ESTIMATES IF I WERE YOU FOR REPLACING THE FURNACE.
|
84.75 | DIY oil burner replacement? | BPOV10::CLEMENT | | Mon Mar 07 1988 09:58 | 27 |
|
I checked the fuel bills from the prior owner. One woman living
alone, works during the day. She is using well over 100 gallons
per month since November. Seem like alot to me.
My mother told me yesterday that she had a one year old oil burner
I could have. She had it installed and one year later she had a
whole furnace system installed (with another new burner).
Now that I have a free one year old oil burner. I don't mind
experimenting by replacing the existing one. I am getting a
maintenance contract with the people that just cleaned the
system last friday (COAN OIL). They haven't charged me for the
two hour cleaning they did, because I am signing up for the two
year maint. contract for $99. Now the tricky part is will they
install my one year old burner, or want to install one of their
new ones? If they refuse to do mine, what if I do mine, will I
screw up my maintenance contract? Ofcourse I will ask them when
they come over with the contract. I will pose the "what if"
questions.
I wonder if anyone out there has replaced an oil burner? I can't
imagine it being a difficult task. Can any DIYer tell me the
basics of replacing a burner, any special tools, any special
things to watch out for. Any more pros and cons to DIY?
Thanks, Mark.
|
84.76 | | CHAS::JACKSON | who you jivin' with that cosmic debris? | Mon Mar 07 1988 11:21 | 43 |
| If it's a relatively new furnace (ie: not a converted coal burner)
The mechanics of it are really easy.
Turn off the oil at the tank. Don't trust the little valve there,
disconnect the spring that goes to the safety shutoff. That'll
shut it off in a hurry. (if it doesn't fix it!)
Next, unbolt the flange from the base of the furnace. Disconnect
the oil supply at the oil pump (right on the burner) and pull the
burner out. (the wire should be long enough to allow you to pull
the burner out of the way, if not, disconnect that too)
Bolt the new burner back in (the flange may be different, so you
should use the one that comes with the 'new' burner) Make sure
it is relatively straight and level (doesn't have to be exact)
Next comes the wires. After the power goes throught the low water
cutoff and high pressure cutoff, there should be the equivalent
of a 110 line directly into the burner. Figure where this gets
connected. (It's probably la Honeywell CAD Cell controller)
The other wire is the one for the thermostat. You either have an
external transformer (mounted on the furnace) or an internal
transformer (in the controler) Depends on what you got, how it's
connected.
Connect oil back up, reconnect shutoff, and off you go. You probably
won't have to prime the pump, but if you do, there's a bolt in the
pump somewhere that you take out until oil comes out.
Last thing to do is adjust the fire. That's the tricy part cause
it should be done with stack instrumetns, and things like that.
Maybe the oil company will do that for you.
As for the contract, they'll probably be more than happy to do the
contract on your new burner. It's got less use, so will probably
break down less. (assuming that it's a common burner that they
do service)
Good luck.
-bill
|
84.77 | re.18 | BPOV10::CLEMENT | | Mon Mar 07 1988 12:20 | 9 |
| re. 18
sounds good, thanks.
only thing I am unsure of is your discussion of wire thru low water
cutoff and high pressure cutoff? What do you mean? Are these the
electrical wires? What are these cutoffs all about?
Mark.
|
84.78 | What's WELL OVER ? | NEBR::HARRISON | Bob Harrison, CIM Engineering | Mon Mar 07 1988 12:58 | 10 |
| re .17
A 100 gallons a month isn't bad at all ! The reason why a standard
tank is 275 gallons is because in the pre 1973 time frame, it was
expected that a tank was filled monthly.
I heat from mid October to mid May . I typically use about 600 gallons
a season.
|
84.79 | maybe 700 gals./year | BPOV10::CLEMENT | | Mon Mar 07 1988 15:23 | 21 |
| The tank was being filled once a month as follows:
3/09/87 115 gallons
11/04/87 175 gallons
12/18/87 142 gallons
1/20/88 161 gallons
2/23/88 100 gallons
I think that averages to 135 gallons/month since November.
Maybe 700 gallons for the year if I add up all those numbers.
Seems like this represents a full years worth of purchases. I
don't know for sure, just bought the house this month.
Is 700 gallons a lot? It is a 28' X 36' 4 bedroom cape.
A lot of people out there claiming to use only 300 - 400 gals/year.
Mark.
|
84.80 | Those aren't too bad | REGENT::MERSEREAU | | Mon Mar 07 1988 16:56 | 11 |
|
Re: .21
What I wouldn't give for those oil bills (sigh). Mine have been
easily triple what you are paying.
Keep in mind that this winter has been particularly cold, so
your heating bills are apt to be high.
-tm (just supportin' those Iranians)
|
84.81 | more numbers | CREDIT::LAVASH | Same as it ever was... | Tue Mar 08 1988 09:34 | 11 |
| I just got my 2nd oil delivery, the first one filled the tank.
We used 139 gallons from Jan 15th to March 7th.
I don't think we are typical homeowners, we don't stay home all that
much, and the house is brand new so our insulation is pretty good.
We have a 26x44 split.
Just thought I'd throw out another number for comparison.
George
|
84.82 | too much fuel??? | BPOV10::CLEMENT | | Tue Mar 08 1988 09:55 | 19 |
| Well the numbers I gave in .21 were for one woman living alone
and working during the day.
She was using about 135 gallons per month.
We bought the house last Monday, moved in on Saturday.
I looked at my tank level last nite. It is down 1/4 tank in
one week. That means I may be using 275 gallons per month!
I ran the heat around 60 degrees all last week, and about 66
degrees over the weekend. I know the house is well insulated.
Wonder if I should look into one of those set back thermostats.
At this point I am not sure what to do. I think I should
definately change the burner with my semi-new one, and see what
that does. However I may not end up doing it till summer and
have to wait till winter to see any possible results.
Mark.
|
84.83 | | CHAS::JACKSON | who you jivin' with that cosmic debris? | Tue Mar 08 1988 10:04 | 25 |
| RE: cutoff switches.
There are typically two (on boilers at least, if you're making hot
air, there may be something different)
Let's see if I can make a wiring diagram
White wire
----------------------------------------------------------------
From Pannel __________ ___________ To Motor
-----------| |--------| |--------------------
|Low Water | |High Press | Black wire
----------- ____________
There may be other things in the line such as stack dampers, and
the like, but the principal is the same. Each 'thing' has a switch
in it and when the thing that it is protecting (low water, high
pressure, etc) happens, the switch opens, and thus the motor turns
off.
Hope that helped.
-bill
|
84.84 | Relax! | HPSVAX::SHURSKY | Have Mac - will travel | Tue Mar 08 1988 11:08 | 12 |
| re: .24
Don't get excited (yet). The guages on oil tanks are notoriously
inaccurate. Especially on the full end. They are just good for
telling whether or not you may have some fuel. When my 275 gal.
tank gets below 1/4 full it only takes 150 gals. to fillerup.
I have a colonial with a 24x40 foundation plus a 24x24 family room
over the garage. I think I use about 1000 gals/yr (includes hot
water). My wife is always home though.
Stan
|
84.85 | | HPSMEG::LUKOWSKI | I lost my A$$ in the '87 CRASH! | Tue Mar 08 1988 17:16 | 22 |
| Re: .21
I did state that I only used 400 gallons but that was evidence
for my lack of concern about my burner's inefficiency. What I didn't
state is that I have a *VERY* small three bedroom home, do not heat
one of the bedrooms or basement (usually), and typically leave my
thermostat set at 68. In addition, it costs me approximately $20/month
more to heat this house than the one bedroom apartment with electric
heat that I lived in before this. I don't ever intend to go back
to electric heat but that's another story.
Re: .24
I agree with .26's comment about the guage. Don't look at it
to get an idea of how much fuel you have but whether or not you
have any fuel. To give an example, when my tank is full, it registers
3/4 and when it registered 1/8, I still had at least 100 gallons.
This also is a 275 gallon tank.
-Jim
|
84.86 | On the original topic... | VINO::GRANSEWICZ | Did you see that?! | Wed Mar 09 1988 09:57 | 15 |
| RE: .0
Concerning the original topic of this note, FUMES...
I had a similar problem at the end of last winter (luckily). When
the furnace (FHA) ran, the house filled with fumes. Turned out
to be a cracked heat exchanger. See note 1137 for all the details.
Just a note of an incident which happened in my home town of Gardner,
MA last week. 3 people were found dead in a house and the suspected
cause is carbon monoxide poisoning from a disconnected exhaust
from a gas hot water heater. If you suspect ANY type of fumes may
be in a house, get out and wait for a service person.
Phil
|
84.87 | less fumes... | BPOV10::CLEMENT | | Wed Mar 09 1988 12:35 | 7 |
| yes back to the original topic...
Since we had the system thuroughly cleaned, we only smell fumes
when the system first starts up. Was re .28 only on startup or
continuous?
|
84.88 | | VINO::GRANSEWICZ | Did you see that?! | Wed Mar 09 1988 13:12 | 7 |
| RE: .29
It was continuous. If you still get fumes when the system starts
up, there is probably something wrong with the ignition. But, I'm
not a burner technician...
Phil
|
84.89 | replacing burner | BPOV10::CLEMENT | | Wed Mar 09 1988 15:29 | 17 |
| Well I spoke to the oil service company and they said they
would install my almost "new" burner for me for $32/hour +
parts. Only parts would probably be a flange and nozzle.
So I am picking the burner up on Sunday and will schedule
them to install next week.
The burner I am getting is a 5 year old (used 1 year) Bell +
Gossett Series 100.
Will let you know if this works out. I am anticipating no
more startup fumes and improved efficiency. I am currently
at 71% efficiency. The burner guy says a new burner would
put me at 80%, he said that is the best I can get on my system.
So I could save about $125 for every $1000 of fuel costs,
according to a Beckett burner marketing chart I got.
|
84.90 | LEAKING PRESSURE REGULATOR | HPSMEG::HOLEWA | | Thu Mar 10 1988 12:51 | 11 |
| Although it looks like you have made the decision to replace the
burner already, your problem may stem from a defective oil pressure
regulating valve. On some units the valve may be an integral part of
the fuel (oil) pump, or in other cases a seperate valve mounted
to the pump. What sometimes happens is the valve leaks and creates
an after drip condition (oil drips after the flame is extinguished),
so when the burner starts up again, it ignites more than the normal
amount of atomized fuel but not enough to create a puff back condition.
Just enough to create some extra exhaust fumes.......
Joe
|
84.91 | How would I know? | BPOV10::CLEMENT | | Fri Mar 11 1988 10:06 | 3 |
| RE. .32
Is there anyway of checking this out? Mark.
|
84.92 | CHECK FAN BLADES AS WELL | HPSMEG::HOLEWA | | Fri Mar 11 1988 14:04 | 10 |
| One way would be to change the oil pump and see if the condition
goes away. Otherwise you would have to look around the nozzel
after the burner shuts down to see if there is any oil leaking
out. Also, in thinking about it some more, your fan blades may be dirty
(blower) so that it is not creating (supporting) a good draft
on start up. However after the fan gets completely up to speed
its enough to take the fumes away. Did the service rep state
what the problem was?
Joe
|
84.98 | magic chef furnace? | TOLKIN::COTE | | Mon Mar 14 1988 16:32 | 6 |
| building a new house. plumber quoted a magic chef l6a 95 furnace.
i never heard of a magic chef furnace. has anyone else heard or
had experience with a magic chef furnace? the system will be oil
fha. the price qouted for the oil furnace, oil tank and trim,duct
twork - labor and materials is $3500. how does the price sound?
|
84.99 | I went with Century... | SMURF::WALLACE | Life's a beach, then you dive! | Tue Mar 15 1988 09:25 | 22 |
| Sounds like a pretty good price. My brother-in-law was quoted
$4300 last year for the same thing. I put in the system myself
and got contractor prices for a total of about $1800. One thing
you might want to look into though is getting an 84,000 btu furnace.
I believe magic chef makes one. The only difference between the
84k btu furnace and the 95K btu furnace is the fuel orifice, which
delivers more fuel in the 95K model. But, you might be able to
save a little more money by buying the 84K model and then changing
the orifice to get the extra btu's. It might not be that big of
a deal, but it's worth checking out.
About the Magic Chef furnace, I decided against it because
it had a smaller blower and motor than everyone else. I believe
the model you are being quoted has a 1/6 horspower motor compared
to all the others I've seen (I bought a century) that have a
1/4 motor. The Magic Chef does have a good warranty though, better
than anyone else. One thing to remember is that only two or three
companies make ALL the furnaces in the U.S., and then just put
different names on them for whoever is selling them, so there
really isn't too much difference between most brands.
I've still got the Magic Chef brouchure, I'll try to get some
facts and figures to post.
|
84.100 | Stove not so good! | NRPUR::FORAN | | Tue Mar 15 1988 15:45 | 3 |
| I hope its better than the Magic Chef stove I bought, a few
years ago!! I have never seen such poor quality before or since!!
|
84.93 | Same as .4-clogged flue. | RGB::MCGRATH | | Tue Mar 22 1988 21:01 | 14 |
| In the better late than never department.....
I just had a similar problem and pinpointed the problem to be the
same as in .4 (if two of us had the same problem it must be common).
The smoke alarm in the cellar went off and I could smell(but not
see) fumes in the cellar. I eventually determined that it was
the furnace and noticed that the draft was not opening like
it should. I popped the flue pipe off and sure enough the
pipe was clogged with many years of coroded mortar and what not.
I pulled out two pails full, reassembled and it works just fine.
The only question I have is where does HPSVAX::SHURSKY live so
that I can dump the pails in his back yard :-).
|
84.94 | Hey, It is OK with me! | HPSVAX::SHURSKY | House < $200k = Mass. Miracle | Wed Mar 23 1988 08:38 | 11 |
| I lived in Hyde Park (only real estate mistake I've made) and there
was a bank down to some unused RR tracks. Sold the house after
a year and a half to another couple of unsuspecting yuppies when
interest rates were 15+% (whew). Anyway, I dumped the stuff on the
poison ivy which loved it! {;-)
The address was 1153 Hyde Park Ave. Feel free to dump the stuff
there. I don't know who lives there though so do it when it is
dark. {:-)
Stan
|
84.95 | neighbors smell my oil fumes | DELNI::GOLDSTEIN | Resident curmudgeon | Fri Jul 29 1988 16:19 | 18 |
| Back to the original topic, sort of.
The oil burner in my house is a neighborhood air pollution source.
The next door downwind neighbors had a falling out with the previous
owner of the house over the oil fumes coming out of the chimney.
I don't think it's quite so bad now (we switched oil companies and
the new one does a better cleaning) but I can still smell a little
outside, not to mention in the basement at times. (It's currently
providing tankless hot water too, which is why it's on during a
summer heat wave. And being an UNINSULATED 1932 tankless, it runs
a lot more than it should!)
The oil man said it's running 78% efficient, with a Beckett burner
on a 1932-vintage asbestos-covered (coal?) steam boiler. Not all
that bad for the age. Flue temp is in the 500 degree F range. It
has a 1 gal/hr nozzle. Would a smaller nozzle help? Or is this
more likely the result of chimney crud?
fred
|
84.101 | EL CHEAPO | TOLKIN::COTE | | Fri Oct 07 1988 13:05 | 10 |
| Well, I went with the Magic Chef boiler. When I turned it on it
was extremely noisy. Much noisier than My previous gas fired fha
heating system. Called the oil people in to ensure everything was
adjusted properly. Mentioned the noise . Their response was that
Magic Chef is the cheapest on the market, generally installedx by
contractors because they are cheap. They will be noisy and life
expectency is 10-12 years vs. 20 years for better boilers. Reason
is because of the guage of metal used. Know of another new home-
owner who had same system installed by same plumber and has same
problem.
|
84.96 | Fumes and Heating Bills .. | WILKIE::EARLY | Bob Early CSS/NSG | Wed Apr 05 1989 13:30 | 47 |
| re: Furnace Fumes (from memory, of course)
My mother had an "very old" hot air furnace, which was nothing more
than a large sheet metal vat, and the hot air rose up the pipes.
When it "backed off" one day, she converted to Gas, tand then cleaned
the soot out of the whole house !
I had an older 80K btu furnace in house #1, and it was an indrect
plenum, so the funrace heated a Plenum Chamber, and then the hot
air was forced upstairs. When I called in the "Heat/AC" folks from
my "former favorite" oil company; I was told the only thing they
could do to solve it was replce the furnace (for about $4K more.less).
I bit the bullet, and caled my Gas rep, and they sold me gas
conversion unit, at 5% simple interest, with a 10 year UNconditional
replacement warranty (about 1.50 month). In the process of installing,
they took about 5, 30 gallon buckets of debris from the furnace and
chimney. And get this - the said he used to do Heat before, and
said that this would cause fumes; and not only that, but didn't
understand why the furnace worked at all ! *The furnace was cleaned
annually for about 5 years by "my_fav_oil_co_rep" for about $50./yr!
Needles to say, I was ... irritated.
When the guy saw that I was insulating my cellar, and blocking some
smal infiltration holes, he suggested that if the cellar were "sealed"
from the out of doors air, AND if the cold air returns were blocked;
this could also cause "fumes", due to improper combustion (lack of air)
of the fuel oil.
re: Fuel Bills ?
When I lived in Concord NH (noraml cold spot) my Electric Heat cost
$500/yr in a 3 BR, Gold Medallion home, small, and we practiced
heat conservation, with noone home during the day (small cape, with
1/2 attic, unheated cellar except for a minimal heat blower).
Currently, they average 134/mo for 10 months @ what .. .99/gal ? Of
course, now I live in amuch larger, older, relatively UNinsulated
house, with beaucoup windows (35); fireplaces, with someone home all
day ! (Maybe 1000 gal/yr).
Tightening/Insulation in progress .. but it takes time.
Bob
|
84.97 | overdamping and narrow nozzle = stinko | DELNI::GOLDSTEIN | Abbie Hoffman Died for our Sins | Mon Apr 24 1989 17:12 | 15 |
| re:.37
Answering my own question, we got yet a different oilman to show
up, this time as part of the annual cleanout. This guy walks into
the house and smells the oil... So he cracks open the cement on
the little door above the combustion chamber (there's a big door
where the coal used to go that has the Beckett burner; this is a
little one above it) and pulls out three bricks!
Apparently bricks are put in coal furnaces to slow down the flue
gases and improve efficiency. But this was overdamped, so by cutting
back to only two bricks, the oil burns better. Also, he changed
the nozzle to a wider spray. It's still 1gph, but burns a lot cleaner.
The surprise is that nobody else caught it.
fred
|
84.102 | WHAT?? did you say NOISEY?? | ROULET::ROSS | | Mon Jan 21 1991 13:30 | 9 |
| I also have a magic chef fha system, it is noisey however seems to work
very well. I have a 75 year old cape/cotage w/3 bedrooms. I use
approximately 120 gallons a month.. In addition to that, I have a
numack woodstove that is hooked up to the magic chef. I do not know
how to run it yet. Can anyone direct me to the right note or person
who could give some information on this system..
thanks
Doug
|
84.103 | HI-EFFICIENCY/ AIR-TO-AIR HEAT EXCHANGER FURNACE | CFSCTC::MCSHANE | | Wed Oct 09 1991 12:23 | 12 |
| My current hot-air oil furnace is over twenty years old and will have to be
replaced soon. I am trying to locate a hi-efficiency oil furnace with an air-
to-air heat exchanger feature (draw in cold outside air, exhaust stale inside
air, transfer heat between the two).
Does anyone know of a type that will meet my needs? A supplier near Salem, NH?
Info on free-standing air-to-air heat exchangers would also be appreciated.
Thanks,
John
|
84.104 | Get seperate furnace and air exchanger | VMSDEV::HAMMOND | Charlie Hammond -- ZKO3-04/S23 -- dtn 381-2684 | Fri Oct 11 1991 15:50 | 19 |
| > ...I am trying to locate a hi-efficiency oil furnace with an air-
>to-air heat exchanger feature (draw in cold outside air, exhaust stale inside
>air, transfer heat between the two).
You are looking for one unit to do two jobs -- heat and
air-exchange. From what I've read and heard this is not a good
idea. You get a simpler, easier to maintain system if you use a
separate furnace and air exchanger. Duct the air exchanger to pull
inside air from the kitchen and bath(s), and to supply the make-up
air near the furnace return air intake.
With a separate air exchanger you can run it independent of the
furnace to keep the air in you house fresh year round. Our house
is set up this way. Our air exchanger runs continuously except
when I shut it of, which is during very hot days in July and
August and during very cold nights in January and February.
Separate units will also give you a much wider choice of features
and capacity for both units.
|
84.105 | Window mount air exchanger | CFSCTC::MCSHANE | | Tue Oct 15 1991 10:34 | 14 |
| Re: Reply .01
Charlie, Thanks for the input. Because of the lack of info on combined units, I
suspected that they are not popular.
I am looking at a window unit made by Stirling Technology of Athens, Ohio,
called The RecoupAerator Mod SW-115. It is rated at 65-90 cfm, 90% heat recovery
efficiency, 100 watts power consumption, on sale at $255.
Does anyone know about this company/product?
Thanks,
John
|
84.10 | heating conversion, electric to FHA,(oil heat) | VAXWRK::OXENBERG | illigitimus non conderendum es | Tue Oct 27 1992 07:47 | 26 |
|
I'm converting the the electric heat in my house (colonial) to
forced hot air by oil. I want FHA because I want central a/c.
Gas is not an option.
My questions are:
1. I've heard about two methods of getting the heat to the ducts in
the attic, one is to send ducts up thru a closet from the basement
and the other is to send a hot water pipe up to the attic which
then is somehow rigged to heat the air in the ducts and I guess
there would be a second blower in the attic as well.
Has anyone had any experience or know anything about these two
methods?
2. My second conern is the hot air coming out from the ceiling in
the second floor which will blow straight downward. WIll this be
uncomfortable? Certainly if one is standing directly under it it
would be.
Thanks.
/Phil
|
84.11 | You may want Air later... | AKOCOA::CWALTERS | | Tue Oct 27 1992 08:38 | 18 |
|
I think the hot/water to air conversion is a last resort for situations
where ducting is not possible. You might as well have a FHW system
(And avoid all the dust/dryness problems with FHA.)
If you are able to duct through a closet then that's probably going to
be the simplest solution, and if you ever want to add central air,
the ducts will be already there.
I like idea of the downwards vents. They are a bit more energy efficient
as they circulate warm air in a room - it doesn't stay up by the
ceiling. The baffles allow you to dispers the flow in different
directions, so draughts are not such a problem.
Regards
Colin
|
84.12 | | VAXWRK::OXENBERG | illigitimus non conderendum es | Tue Oct 27 1992 08:59 | 19 |
|
> I think the hot/water to air conversion is a last resort for situations
> where ducting is not possible. You might as well have a FHW system
why do you say last resort, independent of cost, i'd think the
"hydro-air" solution better in that in doesn't waste closet space.
I'm interesterd in their relative strengths / weaknesses, any
knowledge?
> (And avoid all the dust/dryness problems with FHA.)
they use high quality filters (so I'm told) which makes FHA more
attractive to us allergy sufferrers.
thanks
|
84.13 | Works For Me Fine | MSBCS::LIU | | Tue Oct 27 1992 09:28 | 6 |
| My house has its upstairs FHA vents in the ceiling. They work just
fine. The ducting from the basement up to the attic makes a long run
so be sure that they are well insulated in the attic. There is also
an extra switch on the furnace blower so that you can circulate air
in the summer without having the burner on. That puts cooler air
upstairs even without A/C.
|
84.14 | ducts take up space | DUSTER::MCDONOUGH | | Tue Oct 27 1992 09:30 | 12 |
| I'm not familiar with the "hydro-air" solution, but it sounds very
interesting.
If you do the ducts, you need a fair amount of space. Our house has
FHA. It's a small house and the ducts going to the second floor take
up a significant amount of would be closet space. I'd rather have FHW
and a few more closets. The dust is also a factor. You mentioned
filters for the ducts. I've heard of them but never used them. Does
anyone have any informaton on them? (if this should be in a separate
note, please move).
Rhonda
|
84.24 | Oil FHA Maintenance & First Time Primer | APLVEW::DEBRIAE | It's apple picking season! | Tue Oct 27 1992 11:50 | 44 |
|
I've read through all the FHA notes and didn't see anything that answered my
first time basic questions about oil FHA systems, I need a FHA primer of
sorts. Some basic questions are:
1) What does the maintenance of a oil FHA consist of? How often do most
people replace the wiremesh air filter in their furnace and where is a good
place to get them inexpensively?
2) How often do you have to clean the burner? Does it really have to be done
every single year or is that just hype from oil companies who want the
service work dollars? Does the rate of cleaning depend on how heavy you use
the furnace (ie, can light usage make a cleaning last two years, etc)?
What needs to be cleaned (carbon build-up like on a spark-plug), and can you
clean it yourself (may be worth learning if you truly have to do it every
year)?
3) How important is it to insulate the duct work? Mine are all bare, even in
the unheated garage (except for a thin popcorn texture paint covering). If
the duct is mounted against the ceiling (/floor above), you can only
insulate the exposed portion right? What insulation is used to cover
ductwork like this (styrofoam, fiberglass)? Is it hard to do?
4) Where do you caulk on the ducts? The seems are joined sheet metal, no?
(will have to check when I go home)
5) What the heck is a 'plenum' mentioned in several notes, the term's not in
the dictionary. It sounds like it might be the main duct the other ducts
feed from?
6) How does an oil FHA system work? The oil burner heats up a chamber
(called ??), once the chamber is hot enough, the fan motor turns on and
takes air from the cold air input feed, into the fan chamber with the fan
and motor, blows it into the heated oil burner chamber, and then out to the
house, and when the oil burner eventually shuts off, the fan continues on
until the chamber is cool? That's what it seems from observation, am I
anywhere near right?
These probably seem like pretty stupid questions but I've never had to worry
about heating systems before now and need to get filled in. Thanks for any
help...
-Erik
|
84.25 | | MANTHN::EDD | When monkeys fly... | Tue Oct 27 1992 12:01 | 7 |
| The "???? chamber" is called a heat exchanger. Your sequence of events
is pretty accurate.
I change my intake filter once a year, but often pull it out to check.
It rarely looks like it's been used....
Edd
|
84.33 | FHA Problem - Hot Air Comes Out of Vents Very Weakly | APLVEW::DEBRIAE | It's apple picking season! | Tue Oct 27 1992 12:08 | 26 |
|
I'm not sure if my heating system is 'supposed' to work this way, but
when the fan motor is on, I get barely a trickle of air coming out of
the register vents throughout the house. In past FHA systems I had in
places I've rented, the air is blown through just as many register
vents but comes out hard enough to blow a piece of paper across the
room (although the present vents are the 3' long baseboard-like type
vents). In these past systems you could feel the air being blown with
your hand. In my system now, you can't tell whether what you're
feeling at the vent is the air being 'blown' out at a trickle or
whether it is just the heat rising up out of the vent on it's own. The
house does get warm so it's not a catastrophe, but it doesn't seem
right (and I'm probably wasting oil).
I checked the fan motor and saw that the pulley to the fan (a small
circular drum) was loose. I tightened the pulley thinking I found the
problem but the air still comes out very weakly (albiet a tiny little
bit better than before). I haven't replaced the air filter yet (I will
when I find a place to buy them) but that wouldn't impede the air
_that_ much I wouldn't think.
Any ideas?
-Erik
|
84.26 | | VERGA::WELLCOME | Trickled down upon long enough | Tue Oct 27 1992 12:30 | 16 |
| I'd get the burner serviced every year - cheap insurance and better
efficiency. They'll clean out the combustion chamber, replace the
nozzle, set the air intake to the burner for a clean burn, change
the filter on the oil tank, oil what needs to be oiled, and stuff
like that.
Insulate the ducts wherever you don't want to lose heat - the garage
sounds like a likely candidate. You may want some heat in the cellar
to help keep the floors warmer and to keep it warm down there if
you have a shop or something. Up to you. There's some rigid
fiberglass board about 1" thick that is generally used; I've never
done it so don't know about techniques. You could use regular batt
fiberglass wrapped around the ducts if you want, but using that would
be rather unwieldy and not look very neat.
|
84.15 | | PATE::MACNEAL | ruck `n' roll | Tue Oct 27 1992 12:30 | 8 |
| � 2. My second conern is the hot air coming out from the ceiling in
� the second floor which will blow straight downward. WIll this be
� uncomfortable? Certainly if one is standing directly under it it
� would be.
I lived in 2 places where the FHA came out of the ceiling and/or high
up on the walls. One was a basement apartment, the other a house on a
slab. I didn't notice any problems.
|
84.34 | | MANTHN::EDD | When monkeys fly... | Tue Oct 27 1992 12:33 | 4 |
| You could always remove the filter just to see if it's the source of
your problem...
Edd
|
84.27 | some info | DAVE::MITTON | Token rings happen | Tue Oct 27 1992 13:52 | 22 |
| My gas FHA plenums/ducts are covered with a fiberglass insulation with
a vinyl jacket. I assume this is a product designed for this use.
(I was amused to notice that the installer was willing to let it touch
the flue pipe and melt off there.)
It is attached to the sheet metal with some sort of ringed pin and wide
sheet metal "nut".
I presume there is a special pop-rivet type gun that sets them.
Failing that, duct tape (get the real thing) would work.
The jacket is fairly thin, fine for a basement, but an outdoor space
may want something thicker.
I would not caulk a duct. Use real duct tape. (Hence the name)
Some of us in the networking business are well familiar with the word
plenum, as network cables have to be "plenum rated" if you want to
route them through any space in a commercial building that moves air
for heating or cooling. Often the air space above suspended ceilings
is used as the return. Typically that means that the cable jacket plastic
has to be heat resistent and not give off toxic fumes if burned.
Usually Teflon fits that bill. PVC does not.
Dave.
|
84.35 | baffles closed? | AKOCOA::CWALTERS | | Tue Oct 27 1992 14:32 | 15 |
|
Look for small levers on the sides of exposed ductwork near the boiler.
These are connected to a baffle inside the duct to control the passage
of air. (They are used to balance the system). Some may be closed off
completely.
It may also be worth taking off the register and checking inside.
Two of ours had large chunks of baseboard & mud inside. (Don't stick
your hand in - the sheet metal screws are nasty!)
Regards,
Colin
|
84.28 | And use a pleated, high efficiency filter... | ESKIMO::CASSIDY | Aspiring conservationist | Wed Oct 28 1992 00:21 | 27 |
| 2) How often do you have to clean the burner?
It depends on how much you use your furnace. The cost of a
tune up is supposed to be less than the money you'll save on your
oil bill. But if you use your furnace primarily as a back (for a
woodstove, for example) you wont really save any money.
There is a note in this conference that explains how to do a
tune up. Problem is not being able to measure emissions to insure
everything is set properly. The pro's have everything they need
and it doesn't cost all that much to have them do it.
3) How important is it to insulate the duct work?
You would recover the cost of insulation in one heating season.
There's no reason to heat your cellar and more so your garage...
unless you want to. I used craft faced fiberglass to cover the
ducts feeding the heater vents. I just stapled it to the floor
joists. I think you can get a blanket designed for covering the
main duct.
5) What the heck is a 'plenum' mentioned in several notes?
That's the air tank that gets heated inside the furnace. It
isolated the air being heated from the fire/fumes.
6) How does an oil FHA system work? The oil burner heats up a
chamber (called a plenum)... / ...am I anywhere near right?
Sounds very right to me.
Tim
|
84.36 | Other speeds??? | ESKIMO::CASSIDY | Aspiring conservationist | Wed Oct 28 1992 00:32 | 4 |
|
Your blower motor may be wired for three speeds. If so, you
would have to swap some wires around.
Tim
|
84.29 | | WLDBIL::KILGORE | Bill -- 227-4319 | Wed Oct 28 1992 10:44 | 14 |
|
Webster's Ninth New Collegiate Dictionary, 1988
plenum ... 1... b (1): a condition in which the pressure of the air in
an enclosed space is greater than that of the outside air (2): an
enclosed space in which such a condition exists...
According to the definition, anything in an FHA system from the output
side of the fan to the heat registers could be considered part of the
plenum. I've heard people use the term to refer to the section
connecting the heat exchanger to the rest of the duct work, and
possibly the main duct that feeds all the branches (which might also be
referred to as a manifold).
|
84.37 | | WLDBIL::KILGORE | Bill -- 227-4319 | Wed Oct 28 1992 10:55 | 10 |
|
The most important criteria for adjusting blower speed is the air
temperature at the outlet of the heat exchanger. All furnace
installation manuals I've seen indicate the desired outlet temperature,
which reflects a compromise betweem efficiency and comfort.
If you pump air faster through the system, the outlet temperature will
be lower. In striving to create a more forceful air flow at the heat
registers, you might just wind up with cool drafts.
|
84.38 | how's that go..? | AKOCOA::CWALTERS | | Wed Oct 28 1992 11:06 | 15 |
| Re -1
Now I'm "baffled". It's a re-circulating system, so the air has to
gradually get warmer, whatever the speed - Right?. (Unless the heat
loss from the house space was greater). It would just take longer to
reach desired temp.
Wouldn't a higher speed also recover heat more efficiently from the
furnace instead of letting it go up the flue. Like when you put a
blower on a woodstove?
Regards,
Colin
|
84.39 | | MANTHN::EDD | When monkeys fly... | Wed Oct 28 1992 11:51 | 12 |
|
> Wouldn't a higher speed also recover heat more efficiently from the
> furnace instead of letting it go up the flue. Like when you put a
> blower on a woodstove?
I don't think so. What goes up the flue is the "waste" from the
firebox. What gets blown around by the fan is the contents of the
heat exchanger...
No?
Edd
|
84.40 | yep | AKOCOA::CWALTERS | | Wed Oct 28 1992 13:16 | 5 |
| You're right about the flue - I was thinking about the heat that was
exchanged with the flue gases at the exchanger.
c.
|
84.41 | hot issue! | ELWOOD::DYMON | | Wed Oct 28 1992 16:52 | 12 |
|
If you increased your heat disapation area, say more cooling fins
as in a FHW system, you would be able to lower your exause temp.
Maybe thats what you were thinking....
As far as moving the air faster...well I guess if your intent
is to feel cool, I guess thats why you turn the fan up to hi
in the summer. You cool off the air temp with a faster flow...
Works the same way with the blower in the exchanger..
JD
|
84.42 | | WLDBIL::KILGORE | Bill -- 227-4319 | Wed Oct 28 1992 17:01 | 24 |
|
The faster you pump house air through the heat exchanger, the higher
efficiency you will realize. This is one of the thermodynamic laws;
the larger the temp difference, the better the heat flow. If you let
the air in the exchanger heat up more by pumping it more slowly,
efficiency decreases; the logical extreme would be no air flow,
air temp equal to exhaust gas temp, no heat flow, 0 efficiency
(and furnace meltdown).
Now go the other way, increasing air flow to some improbable rate.
Heat transfer efficiency is high, and yes, in a closed system the house
air will eventually rise to the desired temperature. The problem is
that you now have a rather strong air flow in the living space that
is imperceptibly warmer than its surroundings. Because quickly moving air
also removes heat more efficiently from a warm human body, this will be
perceived as a cool draft.
Thus, setting up air flow in the system is a balance between efficiency
and comfort, and the proper setting relates directly to the air temp
at the outlet side of the exchanger; the outlet air temp also relates
directly to the safe operation of the furnace; therefore that setting, and
not the force of the air issuing from the vents, should be the primary
concern in tuning the system.
|
84.43 | they have a control for that too! | AKOCOA::CWALTERS | | Wed Oct 28 1992 17:32 | 19 |
|
Thanks - now I understand where you're coming from.
There's also a preset upper/lower limit on the plenum temperature
which is independent of airflow rates and the setback thermostat.
(usually a honeywell 'stat in a box on the side of the upper plenum.)
When the furnace starts, This device cuts out the fan until the plenum
reaches the low setting.
If the air temp in the upper plenum falls outside of the range
specified on this thermostat, it will start or stop the furnace. This
would prevent the scenario you describe.
Regards,
Colin
|
84.30 | what price range should I expect? Know anyone reasonable? | APLVEW::DEBRIAE | It's apple picking season! | Fri Oct 30 1992 12:51 | 8 |
|
Thanks for the help here. My next job will be insulating the ducts.
> The cost of a tune up is supposed to be less than the money you'll
> save on your oil bill.
That helps to know. What's the typical cost for a cleaning?
|
84.44 | easy solutions turned up empty | APLVEW::DEBRIAE | It's apple picking season! | Fri Oct 30 1992 12:56 | 7 |
|
Well I replaced the filter and made sure the levers were open (they
were all already wide open). Perhaps the fan motor is wired at a
slower speed for some reason like suggested. Maybe I'll just have a
furnace person look at it when I get the burner cleaned...
-Erik
|
84.31 | | VERGA::WELLCOME | Trickled down upon long enough | Fri Oct 30 1992 15:41 | 4 |
| Carlisle Fule in Boylston is charging $50-$55 for a cleaning, I
think (that's for a FHW boiler, not a FHA furnace, but I assume
it's comparable). Parts (new nozzle, filter, etc) add a few bucks
to that.
|
84.32 | only a backup. | ELWOOD::DYMON | | Fri Oct 30 1992 18:27 | 6 |
|
A few years back it cost me $35. I'll find out next year
if the price goes up......
|
84.45 | stuff caught in your vents? | TROOA::BROOKS | | Thu Nov 05 1992 12:31 | 10 |
| My neighbour's two story house was not getting much air out of her
vents on the second floor. She took off the vent covers (registers?)
and found a pair of pants and a shirt that was blocking the duct
completely. (The previous owners were 'not nice people'). Maybe this
is causing some of your air-flow problems.
With me, I too was finding differences in the force coming out of the
different vents. It turned out that the baffles were closed.
Doug
|
84.16 | electronic air filters | VAXWRK::OXENBERG | illigitimus non conderendum es | Fri Nov 06 1992 09:22 | 13 |
| - <<< Note 4772.2 by VAXWRK::OXENBERG "illigitimus non conderendum es" >>>
-
-
-
-> (And avoid all the dust/dryness problems with FHA.)
- they use high quality filters (so I'm told) which makes FHA more
- attractive to us allergy sufferrers.
-
I belive they are electronic filters. Does anyone know anything
about them, good/bad?
Thanks.
-Phil
|
84.46 | is it a gravity system? | DUSTER::MCDONOUGH | | Mon Nov 09 1992 14:59 | 9 |
| Is it an FHA system? We bought an old 2 family and both furnaces were
'FHA'. One blew the air hard enough to move paper (the true FHA
system) while the other felt more like hot air rising. It turned out
that the one that felt like hot air rising was a gravity fed hot air
system not a forced hot air system. I actually preferred the gravity
system to the fha system, less dust more efficient, although it took
longer to raise the temperature of the room.
Rhonda
|
84.47 | perhaps I'll find another chipmunk stash of acorns... | APLVEW::DEBRIAE | It's apple picking season! | Tue Nov 10 1992 11:58 | 24 |
| >found a pair of pants and a shirt that was blocking the duct
> completely.
The vents looked clean when we vacuumed them, but I'll remove them
just to make sure (wouldn't surprise me in this house).
I checked the baffles and they seemed to be in the open position. I
assume they would only put them in accessible places (mine were all
right by the furnace).
> One blew the air hard enough to move paper (the true FHA
> system) while the other felt more like hot air rising.
Well mine feels more like hot air rising, but I believe it is a
true FHA (I'm not sure I understand how a gravity fed system
works however). The furnace has a big drum fan and motor that seems
to take air in from larger intake vents and 'forces' the heated air
through the smaller heat vents.
I'll have to remember to call a furnace service person soon and
have him/her check out the system while cleaning the oil burner.
-Erik
|
84.48 | | BRAT::REDZIN::DCOX | | Tue Nov 10 1992 12:14 | 4 |
| You might also look at the blades on the blower. As they get coated with dust
and grime, they become less effective.
Dave
|
84.17 | 2 - Zone heating system | ALLVAX::ONEILL | | Tue Nov 10 1992 13:32 | 32 |
|
In the orginal note FHA was preferred because of the heating
and central a/c.
Having a mixed system will cost more than a straight FHA
system. Basically you are setting two heating zones. FHA for
the main floor and hotwater to air conversion for the the up
stairs, so each zone have it's own thermostat to regulate temper
ature.
With water you will need a circulating pump to move the water
to the attic were the heat exchange is located. Your furnace
will need to be able to support both types of heating systems.
You will need to run electrical wire to the heat exchange to
power the blower and run wires from the thermostat and back to
the circulating pump (furnace). Since heat will rise from the
main floor, the upstair's zone via the circulating pump will
turn on and off when needed.
How do you plan to cool the upstairs in the summer time?
With central air, the cool air in the basement can be
circulated through the house, on those hot days the a/c compressor
would turn on to maintain the desired temperature.
My .02 worth
Mike
|
84.49 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Tue Nov 10 1992 14:43 | 1 |
| My parents have a gravity hot air system. There's no fan.
|
84.18 | great explanation!! | VAXWRK::OXENBERG | illigitimus non conderendum es | Tue Nov 10 1992 14:47 | 15 |
| > How do you plan to cool the upstairs in the summer time?
> With central air, the cool air in the basement can be
> circulated through the house, on those hot days the a/c compressor
> would turn on to maintain the desired temperature.
Using central w/ an a/c compressor.
Thanks for the great explanation! What do you think of such a
system (aside from initial cost)? How does this type of setuo
compare with a FHA system, ie running a trunk line (air duct) up from
the basement to feed the loop in the attic (aside from wasting more
space in the closets)?
Thanks a lot for your help.
/Phil
|
84.19 | | VERGA::WELLCOME | Okay Bill...now what? | Wed Nov 11 1992 08:39 | 6 |
| Combined FHA and FHW...
Basically, you're talking about having a hot air furnace and a hot
water boiler, i.e. two totally separate heating systems. I suppose
there is no reason why you can't, except you'll need two chimneys
and you'll have the cost of two separate heating systems.
|
84.20 | | ALLVAX::ONEILL | | Wed Nov 11 1992 11:07 | 16 |
|
In your orginal note it sounded like that you didn't want to lose
closet space to the duct going upstairs. But instead running 2 water
pipes, 1 for hot water to the heat exchange the 2nd pipe to return
back to the basement. This is why I ask how do you plan to cool
the upstairs. My opinion is that you will get greater benefit with
one system (FHA). There would be one heating system, in the summer
time the cool basement air can be circulated through the house
along with central a/c. A booster fan can be installed in the duct
upstairs to increase the air output if needed.
Good luck
Mike
|
84.21 | | MILPND::J_TOMAO | | Mon Mar 15 1993 16:02 | 18 |
| Along the same lines of the base note...
Well the loan and all the minor headaches went through so as of April
23 I'll be a happy homeowner, now the questions.
I bought a 5 year old Townhouse, garage/basement/1st floor with
kitch,bath,liv/2nd floor 2 bed, 1 bath. It is currently all electric
and I would like to convert to either gas or oil. Once I choose the
type of fuel I need to decide FHA or FHW. Almost all will be
contingent upon $$$$$. Since I'll be moving in the cooling vs the
heating season I won't be doing much about it until Aug/Sept timeframe.
Which would be cheaper to convert to oil or gas? What type of price
range am I looking at? If I convert to gas I need a plumber right?
Any comments or anyone's 2 cents would be welcomed.
Joyce
|
84.22 | | JUPITR::HILDEBRANT | I'm the NRA | Tue Mar 16 1993 08:16 | 4 |
| If you have gas in the street, I would convert to FHW gas. If you
wanted central air conditioning, I would convert to FHA gas.
Marc H.
|
84.23 | | VAXWRK::OXENBERG | illigitimus non conderendum es | Wed Mar 17 1993 15:11 | 20 |
| > <<< Note 4772.12 by JUPITR::HILDEBRANT "I'm the NRA" >>>
>
> If you have gas in the street, I would convert to FHW gas. If you
> wanted central air conditioning, I would convert to FHA gas.
>
> Marc H.
I second Mark's opinion, with one additional comment. A few
months ago I investigated converting my electric heat to fhw (oil)
or to fha (oil). The reason I was interested in fha was for
central a/c. After getting many quotes for both types of
conversions I opted for fhw (w/o central air) after noting that
adding central a/c (and all the ductwork) later woulddn't cost me
more (assuming prices didn't go up)!
Good Luck,
/Phil
|
84.52 | Leaking Boiler (FHW -Oil) Question.. | KELVIN::ICKES | | Fri Aug 06 1993 13:37 | 19 |
| I recently purchaced a home at an auction. The house set vacant for 2 years.
The heat is oil FHW. The system (seemed) to have been drained but I noticed a
large rust stain on the basement floor. When I filled the system, not only did
I find there were a couple of broken pipes along the floor board fins (I can
deal with these) but the boiler seemed to be leaking. I took the motor/burner
off and the steel face plate and filled the system to locate the leak. Water
was leaking from the seams of the boiler at the bottom. The motor runs when I
turn the furnace on but I haven't been able to check much else without being
able to fill the system with water.
Is it time to throw in the towel and buy a new boiler?
If the burner and pump still work, can I use these with a new boiler or should I
replace the whole thing?
From reading other notes in this conference, it looks like I'm looking at a
price tag of $1,500-$3,000. Is this accurate?
Thanks for any advice,
Dave
|
84.53 | Ice maker?? | ELWOOD::DYMON | | Fri Aug 06 1993 13:48 | 11 |
|
sounds like someone left the water in the boiler over
the winter and it had a chance to freeze up and burst
the water jacket. If its not to old you might be able
to get parts. (depending on make an model) But then again
it might cost almost as much as a new one.
Make a few calls. Have someone come a check it out. Give you
a price and go from there...
JD
|
84.54 | | JUPITR::HILDEBRANT | I'm the NRA | Fri Aug 06 1993 14:35 | 4 |
| I would start reading all the notes in this conference. Sounds like
just the start of an interesting home ownership period.
Marc H.
|
84.55 | Thanks | KELVIN::ICKES | | Fri Aug 06 1993 14:36 | 8 |
| Thanks for the advice!!
Any recommendations on who to call? I live in the Lowell area. (Plumber
or heating person?) This is my first house so I'm new to alot of this.
Thanks again,
Dave
|
84.56 | Try MASI in Nashua NH | RT95::CASAGRANDE | | Mon Aug 09 1993 15:31 | 9 |
| Dave,
I have had very good success with MASI homeowner supply
in Nashua NH. If the boiler is not too old they may be
able to just replace the water jacket. I think that the
burner is usually the most expensive item in these cases.
Good Luck,
Wayne
|
84.57 | MASI deals | SMURF::WALTERS | | Tue Aug 10 1993 09:49 | 6 |
|
MASI just ran an ad about a bulk purchase of new Weil? furnaces
that they are offering - the prices seemed pretty good, ranging from
$900 to $1500.
Colin
|
84.50 | Looking for supplier of a fresh air heat exchanger for a FHA system. | AWECIM::ERICKSON | | Thu Dec 30 1993 11:18 | 29 |
| I am buildings a house with FHA heating. I've seen a air-to-air heat exchange
unit but do not know of any suppliers. The unit performs by the following:
|
inside | outdoors
house |
|
|
vvvvvv=======================|===< intake
\\\\\\ |
\\\\\\ ////////============|===> exhaust
\\\\\\XXXXXXXX\\ |
~20-30% purge \\\\XXXXXXXX\\\\ |
Return stream \\XXXXXXXX\\\\\\ |
==========================>================//////// \\\\\\ |
\\ vvvvvv |
\\ |||||| |
\\ \|||/ |
======>=======================>==|----------| |
| | |
| Furnace | |
| | |
|----------| |
Heated Air Feed | |
<=================================================<=======v |
|
Please advise,
Dave
|
84.51 | Heating and cooling equipment suppliers | MIYATA::LEMIEUX | | Mon Jan 03 1994 08:32 | 5 |
| I've wired a few and believe that the supplier is typically a heating and
cooling supplier....Total Air in Nashua NH comes to mind. Whoever is doing
your ductwork should have access to a dealer for them.
Paul
|
84.107 | Enclosing a Furnace?? | SMURF::PETERT | rigidly defined areas of doubt and uncertainty | Mon Apr 24 1995 16:04 | 8 |
| I'm thinking of enclosing our oilheat furnace to help in finishing off
the basement. I'm wondering if anyone knows of any regulations or
codes that need to be followed. I expect you have to leave a
reasonable space around it for servicing, and of course you need
air circulation to keep the burner actually running. Any other thoughts
or advice would be greatly appreciated.
PeterT
|
84.108 | on the furnace? | SMURF::WALTERS | | Tue Apr 25 1995 15:08 | 3 |
|
The clearance limits might be marked on a plate attached to the
furnace or printed inside a door panel?
|
84.109 | Is wall board o.k. to use? | USCTR1::ESULLIVAN | | Mon May 01 1995 13:32 | 8 |
|
My burner is approx. 2 feet from an unfinished wall - studing +
insulation. I would like to cover this wall with wall board. Is
that o.k., or do I need something fire retardent? I thought that
ordinary wallboard should be o.k., since the studs are wood and the
studs are only 2 feet away from the burner.
eleanor
|
84.110 | type x (firecode) drywall | NETRIX::michaud | Jeff Michaud, That Group | Mon May 01 1995 13:40 | 9 |
| re: .2
depends on where you live i would guess (ie. local codes).
last fall i installed a gas fired boiler within 4-6 feet
from the oil tank for my oil fired boiler (ie. the tank
was/is not going to be removed). the city building inspector
told me i had to put up a fire wall between the gas boiler
and oil tank, and that the drywall had to be type X (firecode) 5/8".
|
84.111 | | HDLITE::CHALTAS | Der Vogelf�nger bin ich, ja | Mon May 01 1995 16:05 | 5 |
| Generally standard wallboard is NOT OK. The norm around here is
to use fire-rated sheetrock (heavier and a tad thicker than blueboard)
coated with plaster (skim-coat, need not be smooth) within four feet
of an oil burner. No exposed wood permitted in that area. The rules
for a gas burner are less stringent.
|
84.112 | meeting fire code | PASTA::MCDONALD | | Tue May 02 1995 13:54 | 5 |
| re .4
Actually, to be specific, one can use 1/2 inch blueboard with a thick
skim coat, or one can use 5/8 inch sheetrock without skimcoat.
|
84.113 | Local codes vary | PATE::JULIEN | | Wed May 03 1995 11:11 | 1 |
| RE: -1 In Uxbridge it must be 5/8" firecode and a skimcoat...
|
84.114 | Flooring? | 10019::ROBINSON | | Thu May 11 1995 13:59 | 6 |
| Any idea about what you would do about flooring? I would like to floor
the part of the basement where the oil furnace is. Would you just
leave a cut-out and with what clearance? It would be neater if I could
floor under the furnace but I guess I would have to use some different
kind of material, like they supply for putting wood stoves on?
|
84.106 | where can you buy these in New England? | DELNI::BARWISE | | Thu Nov 02 1995 15:13 | 19 |
| re: .1
Charlie,
Can you tell me more about your system (i.e. manufacturer, where it was
bought, etc)? They are very common on new construction in Canada
(very tight houses by code). In fact, all the manufacturers I know of
are in Canada. I call places around here (Mass) and they don't even
know what I'm talking about! I just haven't found the right source.
re: .2
I would highly suspect any system's efficiency rated as high as
90%. Also a window unit might service a small area, but a
typical system ducts fresh and return air to and from different
parts of the house.
rob
|
84.115 | Private clubs and Old Boy networks | NUBOAT::HEBERT | Captain Bligh | Mon Mar 18 1996 13:24 | 32 |
| My son has FHA-oil, and just went through a learning experience I wanted
to share.
His furnace quit. At night, naturally. He determined that it wasn't
getting oil, and further determined that his oil pump was not working. He
took the oil pump off the gun and dismantled the pump to see if it was
blocked - it wasn't. However, the plastic coupling between the blower
motor and the pump shaft was stripped. He then set out to find a
replacement. Something over twenty five telephone calls later he got
ahold of Marino's in Manchester NH, who told him that he "wasn't supposed
to" sell to him, but "by law was prevented from denying him." All
previous calls had ended (some rudely) with the business telling Greg
that he had to call an oil burner service man; they "don't sell to the
general public;" they "only deal with professionals" and so forth.
Marino sold him the coupling for $8 and a gasket for $1. Greg reassembled
everthing and the furnace fired right up.
We think that the coupling was damaged a couple of months ago when the
fuel oil in his lines (exposed outside tank) was gelled. There's another
entry somewhere in this conference about that experience.
It's sad that this kind of "old boy" club exists. Lord only knows that
oil burners are not rocket science. I've met some burner service men who
were technicians, and some who were one step above knuckles dragging on
the ground. I happen to believe that the policy of parts suppliers
"protecting their service men" is a bad policy. I use "professional"
service men for many things, but dammit, if I want to replace my furnace
nozzle some night, it shouldn't be impossible for me to buy one just
because some counter man refuses to sell me one.
Art
|
84.116 | oil tank removal | EVER::LALIBERTE | PSG/IAE - OGO | Wed May 28 1997 12:20 | 5 |
| I can't believe this topic doesn't have its own note....?
Looking for reference for reputable
underground oil tank removal
in general Acton, Mass area.
|
84.117 | Reference | FOUNDR::DODIER | Double Income, Clan'o Kids | Wed May 28 1997 14:13 | 5 |
| re:-1
See 2015.28.
Ray
|