T.R | Title | User | Personal Name | Date | Lines |
---|
25.1 | One from Sears catalog | CHARON::BERKNER | | Mon May 19 1986 13:55 | 18 |
| I just finished installing one yesterday which I bought from Sears
last fall on sale for about $70. It included an adjustable thermostat
control. Its a little noisier than I expected when outside of the
house.
Mine mounted on the roof and required cutting a hole through the
shingles, tar paper and sheeting. It is a self flashing unit, so
you just slip it between the shingle with some tar goop (not included)
and fasten it down. The electrical consisted of running a 120v
line from an existing circuit to the fan. I put a regular light
switch in an upstairs closet so I can turn it off in the spring
and fall when I might enjoy a little heat.
The only bad part was having to climb on my roof which is a 11/12
pitch.
Tom
|
25.2 | Ceiling Fan fan | GALLO::KILGORE | Wild Bill | Mon May 19 1986 15:19 | 33 |
| A few years ago, I put a ceiling fan in the upstairs hallway of
my gambrel - it's great. The fan cools the house in two ways; it
pushes hot air out of the attic, and pulls fresh air into the living
area. It's a 24-inch model, which is quite sufficient for our 1600
sq.ft. of living space.
I decided against a thermostat. I turn on the fan around 3:00 PM,
with just the upstairs windows opened, because at that point the
upstairs is usually hotter than outside, but the downstairs is still
comfortable. In the late afternoon the downstairs windows are opened.
On uncomfortable nights we keep the fan on low and strategically
open windows so that there is a constant breeze in the bedrooms.
Even if no one is home to turn it on at the right times, within
ten minutes it will make the house livable.
The fan came with a two-speed switch, but I replaced that with a
continuously variable fan control (looks like a light dimmer, but
may be rated for heavier load) so that we can adjust it to run quietly
enough for sleep.
I also decided to cut a full hole in the ceiling, instead of following
the instructions that came with the fan (cut out the sheetrock,
sit the fan above the ceiling joists with the supplied venturi cut out
to nestle into the joists, and finish off with an automatic ceiling damper).
I mounted the fan in a frame that drops into the ceiling opening.
In the winter, I replace the fan frame with an insulated frame.
I use the same opening for the odd occasion when I want to get into
the attic (which is just a crawl space).
The only caveat with using such a fan - make sure you have enough
venting space in the attic to allow proper air flow. The recommended
minimum, I believe, is twice as much venting area as the opening
of the fan.
|
25.3 | What about in a contemporary? | STAR::FARNHAM | Plain thinking,but on another plane. | Mon May 19 1986 16:30 | 9 |
|
I've lived in houses with whole-house fans, and concur: they're
great. They can cool down a summer-hot house in no time.
My problem is that my current house is a contemporary, without an
attic in which to mount the fan.
Does anyone have suggestions as to how to get the same effect?
|
25.4 | enough venting? | THORBY::MARRA | All I have to be is what You made me. | Tue May 20 1986 09:11 | 16 |
|
I am going to put one of those whole house fans in the hall upstairs in
my split. My question about the venting is this: This house is brand
new, has two louvered openings at either end of the attic, and is
vented allong the (soffets? - is that the right word? - the part where
the roof meets the wall at the outside overhang - there are vents all
allong that part of the structure). Is this enough venting? - also how
much power does the unit need? - is a dedicated fuse necessary?
I will do the same, cut the joists etc. Sounds neat what you did
though, you say that you can lift the unit out and get into the
attic that way? I would guess you have a long wire running to it
then eh? - much easier that emptying the closet to get up thru the
tiny opening there...
.dave.
|
25.5 | Whole-house fan...venting, power | LATOUR::KILGORE | Wild Bill | Tue May 20 1986 09:48 | 25 |
| I think it's `soffit', but you have the right idea. Soffit,
ridge and louvered venting all contribute to attic ventilation and
can be counted when you determine the venting needs for your fan.
More on adequate venting...I think the `book' (wish I could remember what
book that was) said to provide two_times_the_fan_size of *free* venting
space. That is, for a 24-inch fan, if I cut two 24-inch round holes
in my attic, I would be guaranteed enough venting. Of course, real
vents have louvers or screens that further constrict air flow, so
the safe rule was to provide four_times_the_fan_size of actual venting.
I was short of that, but I didn't want my house looking like a wedge
of swiss cheese, so it tried it with the existing venting (about
three_times...) and it seems OK (no toasted fan motors).
As far as power, each fan should have its requirements on the box,
but I recall that it wasn't very much, and I have it hooked into
a circuit that also services two bedrooms and a bath, with no problems.
To bring power to the fan, I got a length of heavy duty braided
wire (for flexibility) and terminated with one of those plugs that
locks into the receptacle with a small twist. I put the receptacle
on a rafter near the fan. That way, I can move the fan out of the way
to get into the attic, and also remove it in the winter.
Need a sketch? Send mail.
|
25.6 | Misc Info | ISWISS::TELSEY | STEVE | Tue May 20 1986 15:41 | 22 |
| Re power requirements, many fans come with a table which lists air
flow, motor hp, and rpm. Note that air flow is often stated for
0 back pressure (i.e., free air movement without restriction).
Estimate the interior volume of the space you want to ventilate
(Not necessarily the volume of your home since you may plan to
vent the first or second floors but not both at the same time.)
and how often you want to exchange the air. The table should
provide you with several options for a given air flow based on rpm
and hp.
If you have a motor available, it may be usable. Depending on how
much volume you need to move, fan diameter, etc., 1/4 or 1/3 hp
may be entirely adequate. You'll need to match pulley diameters for
motor and fan shafts to obtain required fan rpm. We did this with a
Dayton unit we installed several years ago - it came with a universal
motor bracket, we calculated pulleys needed, added a belt, and were
in business.
Check other models depending on your needs. Often the difference
among similar diameter units is the blade pitch. Greater pitch
usually requires more hp but moves more air at slower speed. Slower
speed is often quieter.
|
25.7 | Are Roof Vents different from roof fans? | KELVIN::RPALMER | Mr Wizard take me home! | Tue May 20 1986 17:06 | 10 |
| The house that I am buying has no roof vents. A roofer told
me that I should have two vents installed to prevent heat build
up under the roof. Are the roof fans being discussed here the same as
a roof vent? I would rather put in a vent with a fan to get some
summer cooling.
=Ralph=
The first of many naive DYI questions.
|
25.8 | Roof vents and fans | LATOUR::KILGORE | Wild Bill | Wed May 21 1986 09:57 | 42 |
| A roof (or attic) fan is not a substitute for attic venting. The
purpose of attic venting is to prevent moisture buildup - if done
properly, it will also help reduce attic heat in the summer.
A fan will help air circulation, but you need the vents too.
Most new homes are built with two kinds of attic venting - gable
or ridge, and soffit. A gable vent is a louvered vent, located high
on a wall in the attic. A ridge vent is a long strip that runs along
the ridge of the roof. Soffit vents are located in the overhang
between the roof and outside walls (the soffits). A combination
of gable and soffit venting, or ridge and soffit venting, allows
hot air in the attic to escape from the high vents, replaced by
cooler air sucked in the low vents, thus promoting natural air
circulation in the attic.
Attic venting can be enhanced by the addition of an attic fan, which
draws out the hot air more quickly. A gable fan is mounted behind
a gable vent on an attic wall. A roof fan is mounted over a hole
in the roof, and has a metal cover over it to protect against the
elements. Attic fans do not usually cause air to move in the living
space below.
Whole house fans are mounted in the ceiling below the attic, and
pull air from the living space into the attic. This type of fan
can serve the same purpose as an attic fan, because as it pushes
house air into the attic, the hot attic air is expelled through
the attic vents. It also causes air movement in the living space,
as outside air is pulled in through windows to replace the air
exhausted into the attic.
If you are going to install an attic fan, you must also supply other
venting to allow fresh air to enter the attic. I would think that
the easiest way for a new DIY'er would be a gable fan at one end
of the attic and a louvered vent at the other end (no roof cutting).
This would probably be the choice if you future plans include central
air conditioning.
For a whole house fan, to also circulate air in the living space,
put a louvered vent at each end of the attic and put the fan in
the ceiling of a centrally located hallway.
To determine how much venting you need, see previous replies.
|
25.9 | "Attic" fan in a contemporary | LATOUR::KILGORE | Wild Bill | Wed May 21 1986 10:05 | 5 |
| Re .3:
How about a roof mounted attic fan? You could dress it up with some
fancy louvered wood work on the inside, replaced with some fancy
insulated wood work in the winter.
|
25.10 | A word of caution | SMURF::PARENTI | | Wed May 21 1986 10:34 | 8 |
| One note of caution regarding whole-house fans. Many towns have regulations/
laws regarding their installation or even if they allow them at all. The key is
that if you have a thermostat, it must have a safety cutoff so that the fan
shuts off above a given temperature. The reason is that if you have a house
fire the fan will turn on and very nicely ventilate your house - perhaps a
little more than you desired!
Mark Parenti
|
25.11 | quick and dirty | WHOARU::HARDING | | Thu May 22 1986 10:41 | 10 |
|
I use a quick and dirty method of installing a cooling fan for my
upstairs. I have a attic opening in my upstairs hall (about 27"x27").
I build a frame that fits in the opening and lay a multispeed 24"x24"
floor fan in it. Then as in a previous reply I just manually turn
it on. I've been using this for the last 10 years. Works great.
dave
|
25.12 | Thermal Cutoff Switch | BESPIN::FARRELL | Joe Farrell | Thu May 22 1986 12:39 | 6 |
| RE: .10
I saw a thermal cutoff at SPAGS in the Electrical dept for a
few $, that opens when a certain temperature is reached. Not having
one on an attic fan is a little "dangerous"
|
25.13 | thermal cutoffs | LISZT::LEWIS | | Thu May 22 1986 13:06 | 7 |
|
re: .12
About the thermal cutoffs...They (at least used to) come with the
Sears whole house fans.
- Rich
|
25.14 | Venting on Vents | VLNVAX::FERWERDA | Loptson | Fri May 23 1986 12:47 | 8 |
| I installed a whole house fan last fall. I have the louvered vents
at the ends of the house and they are too small. What is the best
way to add some passive venting? Should I cut 42 million soffits,
should I retrofit a ridge vent? Any and all suggestions are welcome.
Thanks,
Paul
|
25.15 | | LATOUR::KILGORE | Wild Bill | Fri May 23 1986 14:45 | 12 |
| Re .14:
I watched roofers put a ridge vent on my neighbor's addition the
other day. After shingling, they just placed the vent over
a long slit opening left at the ridge, and hammered it down. Retrofit
installation seems to be a matter of slicing the top off the ridge
and anchoring the vent.
On the other hand, I make it a rule to leave the roof alone unless
there are no other options. How about bigger louvered vents? Space
allowing, it shouldn't be hard to frame in a larger opening and
put in a larger vent, two side by side, custom made, etc.
|
25.16 | installing a ridge vent | 24906::FINGERHUT | | Tue May 27 1986 15:32 | 10 |
| I put a ridge vent on a house which previously didn't have
one. We removed the top row of shingles and cut about 1 inch
off the top of the plywood on each side, using a circular saw.
This left about a 3 inch opening, since the plywood wasn't
touching at the top. We then nailed down the ridge vent and
put silicone or something over the nails. If you do it make sure
you cut away only as much of the shingles as you have to so that
the vent will cover the shingles on both sides of the house.
We did it about a year ago and there haven't been any leaks yet.
|
25.107 | house fan fan has problem | STAR::FARNHAM | Plain thinking,but on another plane. | Tue May 27 1986 18:12 | 17 |
|
This never got answered in the note on whole-house fans, so I
thought I'd try again.
The typical whole house fan pulls warm air from the main living
area of the house up into the attic and out whatever ventilation
is present in the attic. Cool air is pulled in through open
windows, with very good results.
This is all well and good if you have a traditional home with
attic or crawlspace.
My problem is that I've got a contemporary, with no attic.
Has anyone seen whole-house fan installations for situations
like mine where there is no enclosed space overhead into which
to ventilate?
|
25.108 | Suggestion | LATOUR::KILGORE | Wild Bill | Wed May 28 1986 09:25 | 34 |
| I haven't seen this anywhere, but it would be my approach if it
were my house.
Use one or more of those mushroom-looking fans
that mount on the roof. Finish off a square opening from
the ceiling, through rafters and up to the roof sheathing. Cut the
sheathing only enough to accomodate the fan. On the other
side of the opening (approximately flush with the ceiling),
finish off with a louvered wood insert, mounted in such a
way that it is easily removed. During the heating season, replace
the louvered insert with an insulated plug that tightly seals the
opening.
--------
Summer / \ <-- fan
/ \
| |
-------------------- --------------- <-- sheathing
* * * * * * * * | | <-- box between
* * * * * * * * *| |* * * rafters
------------------ ------------- <-- ceiling
`- \ \ \ \ -' <-- louver
--------
Winter / \
/ \
| |
-------------------- ----------------
* * * * * * * * ||* * * || * * * * * *
* * * * * * * * *|| * * *||* * * * * * *
------------------|* * * |--------------
`----------' <-- insulated plug
|
25.17 | Ridge vents are quiet too!!! | BEING::PETROVIC | If you don't do it, no one will... | Wed May 28 1986 09:42 | 18 |
| When I put a new roof on our place, I asked the Merrimack NH building
inspector about powered roof vents/fans and he said that Merrimack codes
didn't allow for them. However, the continuous ridge vent was approved.
When the ya-hoo who we bought from built on the family room, his
contractor covered over the gable vent on that side. Needless to say,
the moisture buildup was enough to delaminate the 3/8 sheathing. With
the ridge vent and soffit air intakes, the roof/attic area is well
ventilated, and is so far keeping the house cooler (maybe it's my
imagination :-) )
The bottom line is the ridge vent certainly costs a lot less to purchase
and less to operate...it also works year-'round.
My $.02...for what its worth...
Chris
|
25.18 | PRAISE & CAUTION ON RIDGE VENTS | BEAUTY::SMICK | Van Smick | Wed May 28 1986 09:42 | 33 |
| PRAISE:
A ridge vent will keep the attic much cooler than soffet or louver
vents because it is at the peak of the roof where the hottest air
accumulates. I had "adequate" ventilation area, but wanted to add
more for a whole house fan. When I put in a ridge vent the average
daily temp. dropped by 20 degrees!
CAUTION:
If you decide to retrofit a ridge vent there are a couple of things
you should be aware of.
One is that if you use the circular saw to cut through the asphalt
shingles you will make a mess in the attic. I would suggest putting
drop cloths over any thing you have stored in the attic before cutting.
I didn't know this when I did mine, and had to vacuum-up tons of
asphalt chips.
Two is that a ridge vent may allow soot from your chimney to come
into the attic in the winter. I discovered this "feature" this
past winter when my furnace was burning dirty. I will put drop cloths
over everything up there before next winter.
BOTTOM LINE: I would put in a ridge vent again if I had it to do
over again.
BTW I used a gable fan mounted on a hinged wooden frame over the
attic "hatchway" as my whole house fan. The cost was about
1/3 of a whole house fan and yet the gable fan's volume was correct
for my needs!
|
25.109 | Watch out for noise levels! | BEING::PETROVIC | If you don't do it, no one will... | Wed May 28 1986 09:46 | 9 |
| re .-1
One word of caution about using a 'mushroom' fan, however. I helped my
father install one that is supposed to be for an enclosed attic. As it
turned out, the fan, when running at it's normal speed was *VERY* noisy.
In fact, it was so noisy, he dosen't use it anymore even after trying to
reduce the motor speed. Something to do with the pitch of the fan
blades. You need a large, slow moving fan...not a high-speed whiner...
|
25.19 | Whole-house fans | SWATT::BAUMGART | | Wed May 28 1986 10:11 | 19 |
| Check the latest SEARS sale catalog - they have their better
ceiling-mounted whole house fans on sale for around $220. It comes
with a wall-mounted thermostat control. An option that you can (and
shoud get) is what they call a FIRESTAT - it mounts in the attic
and shuts off the fan if the temperature in the attic gets too high.
The nice thing about this particular fan is that you don't have
to cut any joists - you simply cut slots in the fan housing and
set it on top of the joists. This particular model is supposed to
be very quiet - the blade is belt driven and the moter assemply
is mounted on rubber bumpers ( I think ).
There is another alternative if you want whole-house air circulation.
SEARS also has a window-mounted whole-house fan with a thermostat
that can be mounted anywhere in the house ( it's wireless ). THis
way, you can put the fan in a window on one side of the house, open
the windows on the other side, and pull air thru. THis one is also
on sale for around $130.
Bruce
|
25.110 | Refer to 170.19 for simple solution!!! | SWATT::BAUMGART | | Wed May 28 1986 10:19 | 1 |
|
|
25.20 | Casement or sash mount? | STAR::FARNHAM | Plain thinking,but on another plane. | Wed May 28 1986 10:22 | 10 |
|
re: .19
Will the window-mounted fan fit in casement windows? The trend in
windows these days seems to be toward casement type, while most
window mounted hardware/appliances is still oriented towards sash-
type windows.
Thanks.
|
25.21 | You need both | BEING::WEISS | Forty-Two | Wed May 28 1986 10:41 | 10 |
| > A ridge vent will keep the attic much cooler than soffet or louver
> vents because it is at the peak of the roof where the hottest air
> accumulates.
In general, you need both soffit vents _and_ ridge or gable vents. Making a
hole at the top of the roof for the hot air to get out doesn't do much good
unless you have some ventilation lower down for cooler air to come in and
replace it.
Paul
|
25.22 | See 182 | BOVES::FORTMILLER | Ed Fortmiller | Wed May 28 1986 14:01 | 1 |
| Discussion of ridge vents now started in 182.0.
|
25.111 | WHOLE HOUSE FANS - LINT BLIZZARDS?? | PSGMKG::RODENHISER | | Tue Jun 03 1986 11:25 | 14 |
| I'm considering buying a "whole house fan" - one of those units
that vent through a ceiling into the attic. They're on sale through
the Sears catalog and I've heard good things about them (...as good
as air conditioning in this part of the country..., etc.).
My attic has loose, blown insulation in it (the type that looks
like lint). Attic ventilation seems adequate - two of those vent-type
windows on each side of the house.
Question: Will the "whole house fan" end up blowing around all
that insulation in my attic??? -- I have visions of the place looking
like a lint blizzard.
Any feedback will be appreciated.
|
25.112 | | FURILO::JOHNSON | | Wed Jun 04 1986 09:30 | 6 |
| My attic has bats with 6" of blown insulation on top. I had that concern
also but I did not seem to run into any major problems. A little stuff
around the fan itself got swirled around but the rest of the attic
stayed pretty calm.
-peter
|
25.113 | venting | OURVAX::BBROWN | | Wed Jun 04 1986 12:03 | 9 |
| My neighbor installed a fan of that type with gable louvers on each
end of his house....there was not enough "venting" and the air tries
to push into the electrical outlets in the house!! His "fix" was
to install full ridge vents.
hope this helps
canuck "cut twice still too short"
|
25.114 | Adding an 3rd story with flapping shingles | PSGMKG::RODENHISER | | Wed Jun 04 1986 12:23 | 13 |
| Thnaks for the repsonses: re: (.1) - the blown insulation thing did
concer me - it's reassuring to hear that it stays put.
Re.: (.2) (not enough venting with just the gable louvers?): I'll
look into going the extra ventilation route (full ridge vents seem
that it might be a significant, and costly, "fix" - I'll check it
out, though.
I wonder if insufficient venting would stretch my house to 3 stories
(eg. lift the roof) or whether it would cause my roof shingles to
stand straight out when the fan is going. (just an attempt at humor!).
|
25.115 | Are they Loud? | FRSBEE::PAGLIARULO | | Wed Jun 04 1986 13:27 | 8 |
| In view of this note and others that sing the praises of fans
and my kids complaints about how hot the upstairs is
I'm considering putting in a whole house fan. What about the noise?
Are they loud enough to be a disturbance or prevent normal sleeping?
Thanks,
George
|
25.116 | If you do the work, cost is low | GALLO::PALMIERI | | Wed Jun 04 1986 13:48 | 14 |
| Re .3 Ridge vents generally come in 10 ft lengths and are about
$16-$18 depending on the finish (mill, painted white or brown).
If you are up to doing it yourself (if your roof pitch isn't to
steep) it is not hard to do. The type of vent I used (from Sommerville
Lumber) requires 2 end plugs (<$1) as well or if you want longer than
10 foot runs you can buy couplings (about a buck). I have had the
vents in since '81 I think and have not seen a drop of water or
a flake of snow. As someone mentioned previously, be generous with
the roof cement. I may still have a copy of a Globe article about
how to install the vents. I believe Popular Science had an article
a couple of years back also.
Marty
|
25.117 | Terra firma - the firmer it is, the less terror | PSGMKG::RODENHISER | | Wed Jun 04 1986 14:30 | 21 |
| RE: If you do the work your cost is low:
Thanks for the info. - I'm surprised at how low the cost really
is. One catch (as far as I'm concerned), I would be unable to do
the work myself - I'm useless at any height greater than 6 feet
(afraid of heights). I once considered having hundreds of yards
of loam delivered to my house and dumped against its side so that
I would only have to walk uphill to attach a television antenna.
My wife wanted no part of this approach and I had the antenna
professionally installed.
It's not the height that worries me as much as it is the certain
fall. Any ideas as to how much it would cost to have the ridge
vent installed - I know this contradicts the DIY creedo but I have
to draw the line at heights.
On the matter of noise levels, I've heard that the level depends
upon the manufacturer of the fan (ie. actually, the design of the
fan) and the speed at which it is operated - many have variable
speeds - it's quieter at low speeds. Anybody have more info. on
the noise levels?
|
25.118 | Whole house fan noise | GALLO::KILGORE | Wild Bill | Wed Jun 04 1986 15:00 | 18 |
|
I was a little concerned with the noise when I first installed my
whole-house fan. As a result, I replaced the two-speed switch the
one that is continuously variable.
Suprisingly, even when the fan is on high (hot, humid nights) the
noise quickly fades into the background. I have never had any
complaints about it keeping anyone awake. In fact, I am convinced
that it has helped mask out the annoying barking of a neighborhood
dog, which has kept me awake on many summer nights.
My fan is direct drive. I have heard tha belt driven fans are quieter.
The belt is supposed to isolate motor vibration from the fan blades.
The reduction factor of the belt also allows the motor to operate
at high revs while the blades turn at low revs and a greater pitch
to move the same amount of air. I would definitely investigate these
allegations if I were of a mind to replace the current fan.
|
25.119 | go for it | BELKER::JOHNSON | | Wed Jun 04 1986 16:30 | 10 |
| re. 5
I have a 24" direct drive and find the noise to be not objectionable at all.
I believe the biggest factor for noise is size of fan blades and speed.
Bigger blades, lower speed mean quieter. I find the large amount of air
moving slowly to be minimally noisy (all things considered). Think of it
like pink noise, it's not really loud so the brain absorbs it as background
noise and soon you don't even realize it's there.
-peter
|
25.120 | price of fan please... | THORBY::MARRA | All I have to be is what You made me. | Thu Jun 05 1986 09:26 | 7 |
|
Since Sears is being mean to me and not sending me their sale catalogs
anymore, (probably couse I finally paid off their bill), what is the
style and price of the unit(s) on sale? I'm getting really tired of
having to use a stupid window fan to sleep.
.dave.
|
25.121 | HAD IT with Snears & Rubbish | FURILO::BLESSLEY | | Thu Jun 05 1986 10:22 | 2 |
| Snears isn't being mean to you... they're doing you a favor.
|
25.122 | | WORDS::BADGER | | Mon Jun 23 1986 14:01 | 10 |
| I have a 36" Emerson. Its belt drive. Its noisy. Its good. But
you have to use it smartly. NOT during the heat of the day as it
will suck the heat into the house.
In the morning we close up the house to conserve the cool air.
At night we turn on the fan when the outside is cooler than the
inside. Can NOt be used to vent the attic during the heat of the
day. Need attic fans for that.
Also have blown attic insulation. doesn't appear to be affected.
ed
|
25.223 | Installing switch in fan power line | HALLEY::CARLETON | Dennis Carleton | Tue Jul 22 1986 09:15 | 8 |
| The previous owner of my condominium has installed a ceiling fan
in the living room, and it appears that the power line to the fan
runs directly to the power box. I would like to install a wall
switch, and I think that I have identified the proper power line
in the area above my suspended kitchen ceiling. Is there a way to
tell if this is the proper line without cutting it ?
---Dennis
|
25.224 | | SARAH::TODD | | Tue Jul 22 1986 09:27 | 8 |
| I believe there's a device that may be called a 'tong ammeter' which
senses AC current in a line by induction (the 'tongs' form a loop
around the line, creating an inefficient but adequate transformer).
You could try that (after turning the fan on, of course). It might
be necessary to separate the two leads and place the tongs around
one, however.
- Bill
|
25.225 | | LATOUR::KILGORE | Wild Bill | Tue Jul 22 1986 09:31 | 4 |
| Know abybody with an inductive ammeter? It's head loops around the
wire in question, and the magnetic field from the current flow is
translated into a current reading. I see plant engineering people
using them all the time.
|
25.226 | | MAY11::WARCHOL | | Wed Jul 23 1986 12:05 | 9 |
| To use an inductive ammeter you will have to separate the two wires
and only loop the meter around one of them, otherwise the
electromagnetic fields of the two wires will cancel each other out.
I've usually been able to tug on the wire while someone watches
the inside of the electrical box for movement. This all depends
on staples, length of run, and accessibility.
Nick
|
25.227 | remote unit | SVCRUS::KROLL | | Fri Jul 25 1986 16:47 | 3 |
| why bother sears sells a remote unit in their catalog that involves
just attching it to the existing switch in the fan. Sounds like
a lot less work.
|
25.23 | vertical mounting of WHF ? | TROLL::DCOTE | Dave (Peck) Cote | Sat Jul 26 1986 15:18 | 21 |
| I'd like to install a whole-house fan, but have no attic, just
a wedge-shaped crawlspace running the entire width of the house
behind the second floor knee-wall (cape).
I'd like to try mounting a fan vertically in this knee-wall
just above the stairway, and add triangular vents at both ends.
Any ideas, cautions??
//
//
//|
// |
roof // | <- knee-wall second floor
// F hallway
// A up
// N coming
// | | stairway
// | v
//-----------------------------------------------
|
25.24 | where do I get belt drive unit?. | THORBY::MARRA | All I have to be is what You made me. | Mon Jul 28 1986 09:41 | 11 |
|
..Not an answer to 170.23..
I was wondering where I could get the parts to create my own attic
fan. I want to have a belt driven unit with a 30-36 inch fan on
a variable speed switch. Is there anywhere that actually supplies
this type of unit?
I don't want to get a sears fan - looks really cheap.
.dave.
|
25.228 | RE .-1 | HALLEY::CARLETON | Dennis Carleton | Mon Jul 28 1986 10:29 | 6 |
| That sounds like an interesting idea, do you have any more information
on this switch (ie. catalog page, #, etc .)
Thanks,
---Dennis
|
25.229 | try sears summer catalog | SVCRUS::KROLL | | Mon Jul 28 1986 13:16 | 2 |
| It was in the summer catalog under cealing fans. The control unit
looks just like the one we use on the tv. dont' remember the price.
|
25.230 | Why not a switch leg? | BANZAI::PAL | Paul Lemaire | Mon Jul 28 1986 14:12 | 13 |
| Is there some reason why you can't run a switch leg from the fan?
Then the location/identification of the power lead wouldn't matter.
POWER ________________ F
_______________________________/ A
________________________________________ _____ N
| |
| |
| |
| |
| |
| |
SWITCH
|
25.123 | Love mine. | WILLIE::TIMMONS | | Tue Aug 05 1986 08:41 | 21 |
| I have had my fan installed for 3 years now, and find that the noise
is not a problem. As previously mentioned, it does mask other noises
such as dogs barking, etc.
I have batts of insulation, so I can't say anything about that.
However, I did have a problem with insufficient openings. Rather
that get into the ridge vent, I installed soffit (sp?) vents. These
are round screens which are installed in holes that you cut in the
overhangs, IF your insulation was correctly installed. That means
that there is no insulation right about the overhang. I used a
hole-cutting blade in my drill and just spotted the locations on
16" centers. Seems to work great.
I have a cape with 2 bedrooms upstairs. They get VERY hot during
the day, so I just open their windows in the early evening, even
if the outside air isn't as cool as I want it to be. With the fan
on, this pushes out the superheated air in the space between the
ceiling and roof. When the air cools down, I open some downstairs
windows and clear-out the whole house.
Lee
|
25.25 | Graingers Wholesale Catalog - 1500 pages | THORBY::MARRA | All I have to be is what You made me. | Tue Aug 12 1986 14:28 | 13 |
| Well, I friend has a Graingers wholesale catalog that has about
everything in it from air tools to zip lock bags (almost - atleast
that covers a-z). Anyway I will eventually order a 3 speed whole
house fan that is 30 inches, dynamically balanced and belt drive.
It comes with the switch. The louvers are extra, and are about
40 dollars while the fan is 250$. Since this guy knows somebody
that works there he can get a 20% discount from them, the total
for a really nice whole house fan and the louvers is $250.
They also have the recessed lighting I was talking about at 21$
each before the discount.
.dave.
|
25.26 | Grainger discount to DEC | GENRAL::HUNTER | from SUNNY Colorado, Wayne | Fri Aug 15 1986 17:58 | 9 |
| re .25
Did you know that DEC also has an agreement with Grainger to
buy things. Works like this:
Show them your badge
Pay CASH (No plastic or checks)
get ???? for listed first lower price
(for example of price break, 1-9=$10.00, 9-20=$8.00, you pay $8.00)
This is for any DEC employee across the US.
|
25.27 | | THORBY::MARRA | All I have to be is what You made me. | Mon Aug 18 1986 10:14 | 8 |
|
> (for example of price break, 1-9=$10.00, 9-20=$8.00, you pay $8.00)
eh? is that new math? is 1-9,9-10 the time of day (in 24 hour
time)?
.dave.
|
25.124 | Get a cutoff switch! | PYRITE::BELANGER | Boycott Boycotts! | Mon Aug 18 1986 10:51 | 35 |
| We recently installed a whole house fan, and our experience is
consistent with that of others in this note:
Insulation does not get blown all over the place.
The noise is not bad at all (even at full speed).
It works!
We have a Broan 24" direct drive unit (from Somerville Lumber)
which seems to have an advantage in that it mounts along the
length of a joist with good shock and vibration mounts. The
motor is mounted right on the joist itself which seems to help
with quiet(er) operation (the Sears units mount at right angles
to the joist). The Broan 24" unit will mount on 24" centers
(drop-in) or 16" centers (minimal trimming of the fan shroud
and then drop-in). We also have a variable speed control (nice)
and a thermostat (eh...).
A suggestion for anyone who has or is considering a whole house
fan:
Buy a cutoff switch!!!
This switch is mounted near the fan in the attic and serves two
very important purposes:
It kills power to the fan when you are working in the attic.
It will automatically kill power to the fan if the temperature
rises above 185 degrees. I shudder at the thought of an attic
fire being ventilated by such a fan (mine is rated at 5100
CFM). At $8, a cutoff switch is cheap insurance.
-Roland
|
25.125 | Whole-house vacuum | TROLL::DCOTE | Dave (Peck) Cote | Fri Aug 22 1986 17:22 | 7 |
| I heard a cute story once about someone turning on their
whole-house-fan without first opening any windows, and
sucking all the soot and ash out of their fireplace and
into the living room!
I wonder if the negative pressure in a situation like this
(in a very tight house) could break a picture window?
|
25.126 | comments and a question | CLT::BENNISON | | Fri Sep 12 1986 00:10 | 20 |
| I doubt that a whole house fan can do much damage to picture
windows. Ours slams some doors shut sometimes. And when we
forget to open the windows it does pull air down all the fireplace
and wood stove flues. We've never gotten any ash, but the smell
is somewhat unpleasant. By the way, I built a large box with a
hinged cover, completely insulated, to cover my fan. In the winter
I close it up. Also, if the attic is really hot I close it up also.
I have the lid on a counterbalanced pulley system.
Now I have a question. The louver (is that what you call it? The
thing in the ceiling that covers the fan and has slats that fold
up when the fan is on.) for our fan is all bent up. I'd like to
find a replacement, but so far haven't found a source. Sears has
one that is close, but I'd have to do some carpentry to make it
fit. The fan is a 30' fan. I have not been able to find any
brand name anywhere on the fan. I don't have the measurements on
me, but I could provide them. Does anyone know a good source for
replacement louvers. Grossman's doesn't carry anything as big as
ours.
- Vick
|
25.127 | Graingers | MAY11::WARCHOL | | Fri Sep 12 1986 14:51 | 22 |
| Source for air handling products, they carry whole house fans and
louvers along with all sorts of industrial products.
W.W. Grainger
They have locations all over the U.S., I don't know where your from
but the MA locations are
428 University Ave. Norwood, 617-762-7375
31 Cabot Rd, Worburn 617-935-8808
Many industrial hardware stores are distributors for Graingers
Parker Hardware in Maynard will order anything you want from the
Grainger catalog and they send their own driver there a couple times
a week to pick up the orders.
It is sales to the trades only, but you can always show your DEC
badge and pay for the order in cash.
Nick
|
25.128 | | THORBY::MARRA | All I have to be is what You made me. | Fri Sep 12 1986 17:10 | 15 |
| Graingers in MASS
Norwood 762-7375
Woburn 935-8808
Worcester 853-7300
Springfield 781-7525
NH
Manchester 668-7161
I am getting tthe 30 inch model (someday) - the louvers are 28 dollars
(I think).
.dave.
|
25.129 | big fan... | Q::ROSENBAUM | Rich Rosenbaum | Fri Sep 12 1986 17:51 | 4 |
| > The fan is a 30' fan... Grossman's doesn't carry anything as big as
> ours.
I'm not surprised that Grossman's doesn't carry 30 foot fans. :-)
|
25.231 | Three way dimmer for fan | ARCHER::DEVLIB | | Wed Mar 25 1987 15:25 | 17 |
| Here's my situation. I'll be putting in a whole house fan shortly
using 2 3-way dimmer-type switches to control speed. It will be placed
at the top of the stairs of our gambrel.
What I would like to do is place the 3-ways at the top and bottom
of the stairs. had planned to do this myself but the wiring leaves
me a little leary.
I have 2 3-way switches controlling the light in the stairway
and I planned on putting the dimmers in the same boxes (enlarged,
of course). Would it be possible to use the same common wire
that the current 3-ways use?
I am trying to do this with as little effort as possible, so
I figure with that wire going to and from where I need it to
go, that save me a big headache.
Thanks,
John
|
25.232 | | BEING::WEISS | Trade freedom for security-lose both | Wed Mar 25 1987 16:07 | 0 |
25.233 | .-1 is right on both points | STAR::SWIST | Jim Swist ZKO1-1/D42 381-1264 | Wed Mar 25 1987 16:28 | 0 |
25.234 | OK OK, but can it be done? | ARCHER::DEVLIB | | Wed Mar 25 1987 16:58 | 0 |
25.235 | | ZEN::WINSTON | Jeff Winston (Hudson, MA) | Wed Mar 25 1987 19:15 | 3 |
| Hmmm I bought a real fan speed control at a electrical supply house
for like $15 2 years ago - is that 'uncheap?"
(used it to make my tank humidifier fan "variable-speed")
|
25.236 | not enough time | BOEHM::SEGER | this space intentionally left blank | Thu Mar 26 1987 08:27 | 10 |
| Interesting...
Our house has 2 dimmers on the same circuit. It turns out that only one ever
works and the other must be completely on of completely off.
I've been saying for the last year and a half I should do something about it
but have been to busy doing MAJOR projects to find the 10 minutes it would
take to replace these.
-mark
|
25.237 | 2 dimmers on one circuit - for laughs only... | STAR::SWIST | Jim Swist ZKO1-1/D42 381-1264 | Thu Mar 26 1987 08:36 | 9 |
| I've had instances where this might have been nice to do, but it's
an interesting intellectual exercise to specify exactly how it
should work - e.g. if dimmer #1 is all the way up and you dim the
light with dimmer #2, then is dimmer #1 now "backward" (like a plain
switch would be), so that turning it counterclockwise now increases
the intensity?!
And that's the easy case, think about it for intermediate values
of #1 and #2.
|
25.238 | same direction, intensity changes | ARCHER::DEVLIB | | Thu Mar 26 1987 09:30 | 13 |
| RE .6
It's funny you mentioned that about the relative positions of the
two dimmers.
I stopped by a hardware store on the way home last night and was
asking about this situation. He stated that dimmers are designed
to always work in the same direction regardless of which one is
turned on, however, if one was say up 3/4 full, and one was up
1/4, when you reverse the situation, the fans' speed will be at
whatever the current dimmer is set at. Outside of that, it'll
work fine.
John
|
25.239 | Motor speed control | DIZZY::GINGER | | Sun Mar 29 1987 22:16 | 24 |
| Back to the motor speed control part of the problem.
There are basically two types of electric motors, those with brushes
and those without. Those with brushes are commonly in things like
kitchen appliances, drills, saws, other hand tools. These can us{
simple light dimmer type speed controls- the squared up sine wave
doesnt bother them a bit. The trigger speed control in a drill is
exactly this tyoe of circuit (you can make a variable
speed controller by putting a dimmer in a box with a cord and plug)
Of course you must make sure the dimmer can handle the power
requirement of the motor, but since most dimmers handle 500 watts
and that is equivalent to about 3/4hp that is usually no problem.
The second kind of motor has no brushes- these are the induction
motors and every whole house fan, and most other blowers, I have
ever seen have this tyoe of motor. They can only have spped control
by frequency changing,- unreasonably expensive - or by changing
the internal wiring of the motor. Some fans have two tor three speeds
accomplished by having several leads come out of the motor and
switching them to select one or two fixed speeds.
Bottom line is I doubt you can use dimmer switches to co{trol your
whole house fan.
|
25.240 | see 170.2 | ARCHER::DEVLIB | | Mon Mar 30 1987 12:37 | 7 |
| RE .8
I wasn't planning on using a basic light dimmer. After reading note
170 (esp. 170.2), I became interested in using some sort of variable
speed control. Two, if possible.
John
|
25.241 | Huh? | VIDEO::DCL | David Larrick | Wed Apr 01 1987 18:00 | 16 |
| > dimmers are designed
> to always work in the same direction regardless of which one is
> turned on, however, if one was say up 3/4 full, and one was up
> 1/4, when you reverse the situation, the fans' speed will be at
> whatever the current dimmer is set at. Outside of that, it'll
> work fine.
This makes no sense to me, either electrically or from a human interface
standpoint.
Are you saying that the fan somehow only "listens" to the last dimmer
you changed? (What if both get changed at the same time?)
I don't think two 3-way dimmers on the same load will work under any
circumstances. One dimmer with as many switches as you like, but not
two dimmers. If there is a way, I'd like to know about it.
|
25.242 | I'm just the messenger | ARCHER::DEVLIB | | Sat Apr 04 1987 19:20 | 24 |
| What I was told, was that whichever one TURNED ON THE FAN controls
the speed.
Situation:
Fan is off. Dimmer A happens to be set at 1/4 up. Dimmer A is pushed.
(Fan is turned on by dimmer A) Fan is now at 1/4 speed.
With me so far?
At this point, only dimmer A controls the speed. If dimmer B is turned,
NOT PUSHED, nothing happens.
Dimmer B happens to be set at 3/4 up. Now dimmer B is pushed. Fan goes
off. Dimmer B is pushed again. Fan goes on and is spinning at 3/4
speed (what dimmer B was set at). Now dimmer B controls the speed
and dimmer A has no effect.
That was what the fellow at Aubeshaun (sp) explained to me.
Perhaps these aren't the conventional 3-ways used with standard 3-way
switches. Maybe they are not even 3 way!
I'm not electrical expert, but it makes sense to me that whatever
dimmer turns the fan on, controls the speed. The other dimmer has
no effect until it turns on the fan.
Once I have this installed, I write again (new note), and let you
know how it works.
John
|
25.243 | a two station fan dimmer switch | YODA::BARANSKI | 1's & 0's, what could be simpler??? | Mon Apr 06 1987 14:14 | 15 |
| It seems like these are standard SPDT switches with dimmers...
dimmer1
_#######_______________________
switch1/ \switch2
______________/ _______________________#######_ \______________
dimmer2 #
power # fan
#
______________________________________________________________#
The dimmers may or may not have a connection to AC return, depending on how
they work.
Jim.
|
25.244 | | VIDEO::DCL | David Larrick | Tue Apr 07 1987 09:54 | 14 |
| re .11: Thanks for the clarification. Sounds great, if only it works.
I still don't see how it would work electrically.
re .12: A step in the right direction, but it won't do what .11 describes.
Specifically, if switch1/dimmer1 is set to dim, one wire has 25% power and
the other has zero. No conceivable setting of switch2/dimmer2 would send
more than 25% power to the fan, and .11 calls for 75%.
I think switch2 needs to choose between the dimmed wire from switch1 and a
full-power wire that bypasses switch1. Putting the two dimmers on opposite
legs, as .12 did, looks right.
It annoys me that I can neither design the right circuit, nor prove that
it's impossible. I'm usually pretty good at this type of problem.
|
25.245 | switch the switches | YODA::BARANSKI | One's and Zero's, what could be simpler!? | Tue Apr 07 1987 12:18 | 12 |
| RE: .13 RE: .12
Yes, it will work. If you throw switch2, it switches out dimmer1, and switches
in dimmer2, which you can then adjust to 75%.
...
But, you have to make sure that each dimmer is adjustable at each switch
station, no matter which way the switch at the other switch station is set. This
complicates things, but it's not impossible. I think that you need to use at
least single throw double pole switches. I'll leave the diagram as an exercise
for someone else. It's possible, but confusing. :-)
|
25.28 | What's the story???? | LATOUR::TREMBLAY | | Tue Apr 28 1987 12:35 | 23 |
| RE: 170.26 (Digital/Grainger agreement)
Has anyone actually bought something from Grainger's
by just showing their Digital Badge?
I went to the Grainger's in Worcestor, MA. to buy something
over the counter, but they would not sell anything to me just because
I had a Digital badge. They explained that they are a wholesale
company and can only sell directly to businesses. They said they
could get a PO (purchase order) from Digital and have me pay cash
and then they would forward the PO to Digital with a balance of zero
dollars. But first they would have to call Digital purchasing dept.
for approval. So I said okay. Well, they called and purchasing said
they knew nothing of the agreement and would not approve the purchase.
Then purchasing asked to put me on the phone and they asked me where
I got this information. I explained to them it was in (this) notes
file...that's when she told me I should verify my sources first!
(Nothing personal guys!). I ended up walking out empty handed.
Does anyone know what the story is? Does such an agreement
exist? And if so, how does one take advantage of it?
/Glenn
|
25.130 | an update | BOEHM::SEGER | this space intentionally left blank | Tue Jun 16 1987 09:03 | 11 |
| I just called Parker Hardware in Maynard to check on the Grainger fans. The
36" costs $253.52 and there are a couple of louvers to choose from for around
$40-$50. This seems like a pretty reasonable price as the other places I've
looked go as high as $400.
From the several replies on Grainger, am I to assume that this is indeed a high
quality fan? Is it direct drive or belt drive AND does it matter? Somehow,
belt drive seems like it would be a better mechanism (or am I thinking about
turntables)? Actually, I think the same principle applies...
-mark
|
25.131 | | VINO::KILGORE | Wild Bill | Tue Jun 16 1987 10:58 | 5 |
|
Allegedly, the belt drive decouples the motor buzz from the blades,
which act as a great sounding board. It also provides the torque
conversion necessary to drive a high-pitch blade at lower speed,
which is also supposed to move the same air volume with less noise.
|
25.132 | getting MORE confused rather than less | NETMAN::SEGER | this space intentionally left blank | Mon Jun 22 1987 13:47 | 26 |
| I'm making progress, I've contacted Grainger's and they indeed confirmed
that if you show up with a DEC badge they'll sell to you for CASH. The deal is
that they use DEC's account and they don't want any bugus charges.
Looking through their catalog I see several models of fan and am therefore
reasonable confused as to which model is for me. I've got over 2500 square
feet to cool and from talking to a few stores, it sounds like I need a 36"
fan. I believe shutters are extra on all of them but run around $40-$50. In a
VERY brief summary,
Emerson 30" 1/3 hp 6300 CFM $197.33
Fasco 36" 8250 CFM $247.90
[1]
Dayton 36" 1/3 hp 6500 CFM $263.00
[2] 1/2 hp 8000 CFM $292.18
3/4 hp 10800 CFM $358.48
Dayton 30" 1/3 6500 CFM $260.57
[3]
[1] includes 3 speed switch
[2] 2 speed motor, 1 speed about $10-$50 cheaper
[3] 2 speed motor standard
|
25.133 | Some comments | REGENT::GETTYS | Bob Gettys N1BRM | Mon Jun 22 1987 14:21 | 0 |
25.134 | determining amount of vent space | BOEHM::SEGER | this space intentionally left blank | Wed Jun 24 1987 13:03 | 6 |
| One more question - is there an easy way to determine how much attic venting
you need? Usually there are specs for that but Grainger's doesn't show any.
Does anyone have an address for Dayton? I'll contact them for literature.
-mark
|
25.29 | Winterizing a Whole House Fan | 4GL::FRAMPTON | | Fri Oct 09 1987 12:24 | 9 |
| We have a whole house fan mounted in the ceiling over the top of
our staircase. It has a set of louvers which open when the fan
is on. However now that it has gotten cold we can feel the cold air
pouring in through the supposedly closed louvers. Any suggestions
on how to winterize the fan? We would prefer leave the fan in place
and work around it.
Carol
|
25.30 | make a fan cover | PSTJTT::TABER | Out of sight, out of range. | Fri Oct 09 1987 13:12 | 11 |
| re: .29
I took a couple of big boxes, turned them into one extra-big box
by cutting and using tape, then lined the inside with plain old
fiberglass insulation. (Paper side out so it wouldn't catch on the
corners of the fan.) In the winter, I'd just drop the box over the
fan. Since we didn't use the attic for anything, it didn't matter that
there was a huge box up there in the summer. If you use yours, you
might find the box a litte hard to store.
>>>==>PStJTT
|
25.31 | | MORMPS::WINSTON | Jeff Winston (Hudson, MA) | Fri Oct 09 1987 16:31 | 5 |
|
Or - get a piece of sheetrock (or a ceiling tile) cut it to size, ad
drop it in from above
nail a 2x4 to the back so you can lift it off in the spring
|
25.32 | Been awhile since I've read this conference. | GUMMO::SULLIVAN | The foundation is in!!!! | Tue Oct 27 1987 13:30 | 12 |
|
I remember seeing a device in Practical Homeowner or one of
those mags which had a seemingly clever solution to this (sorry
I don't have the article or reference).
As mentioned in previous notes, the guy built an insulated box
around the fan. He hinged the top and attached it to a weighted
(bucket with rocks in it) pulley system. He then added just enough
weight so that the cover stayed closed when the fan was off. When
the fan came on, the pressure of the moving air was enough to open
up the top and move the air.
|
25.246 | 3-way w/pilot light | WELFAR::PGRANSEWICZ | Auhhhhh, I've been slimed! | Wed Nov 11 1987 13:21 | 16 |
| I have a problem that's 3-way/4-way switch related.
Seems several outdoor lights are connected to multiple switches
(at least 2, maybe 3 switches). What makes it a real pain in the
ass is that you can't see the lights that are switched from the
location of the switch. So you don't know if you're turning the
lights are on or off.
I've seen the switches with the neon pilot lights for around $5.
But do these come in the 3-way variety? If they do, does the pilot
light on each switch light when the lights are on?
Any suggestions from the electrical wizards on how to solve or
get around this one?
Phil
|
25.247 | They do exist | CADSE::MCCARTHY | CADSE software engineering | Wed Nov 11 1987 14:59 | 5 |
| My parents house has a three-way with a pilot lamp in the toggle.
The pilot lamp is ALWAYS on (I think???). Well, at least they I
know they make them :-)
mac
|
25.248 | | HPSMEG::LUKOWSKI | I lost my A$$ in the '87 CRASH! | Wed Nov 11 1987 15:22 | 5 |
| The purpose of the pilot (neon) lamp in the toggle is to see the
switch in the dark.
-Jim
|
25.249 | YaBut | WELFAR::PGRANSEWICZ | Auhhhhh, I've been slimed! | Wed Nov 11 1987 16:50 | 7 |
| RE: .16, .17
I think what you're both referring to is a lighted switched. One
that glows in the dark. The pilot light switches indicate when
the light is actually ON. Or am I imagining all this???
Phil
|
25.250 | | CADSE::MCCARTHY | CADSE software engineering | Wed Nov 11 1987 20:40 | 7 |
| re: .18
Yes what I was refering to was a lighted toggle switch. The
other type that uses a pilot to indicate when the lamp is on may
not be available in a 3-way. If it is, you know it has got to be
mega-priced!
mac
|
25.251 | They do exist | REGENT::GETTYS | Bob Gettys N1BRM 223-6897 | Wed Nov 11 1987 21:13 | 25 |
| I have just such a beast in my house on the garage
light. The switch in the kitchen has a lighted handle which
lights when the garage light is on. The switch does cost more
than a normal 3-way but isn't unreasonable when you consider the
agravation it could save you (it should run about $10). They are
hard to find (I didn't try Spag's) and even all the electical
supply houses don't carry them!
There is one potential gotcha in the system. The light
MUST feed from the box that the lighted switch is in. The light
is really a second (or third, or fourth....) light in the
circuit and needs to have both neutral and switched hot in the
box that it is in.
I believe that 3-way switches are also available with
separate bulbs (incandescent) that can be used in the same way.
(I think the neon bulb in the switch handle looks MUCH better
inside the living area.)
/s/ Bob
p.s. I didn't even know that they existed until I moved into my house
and found one in the kitchen. I had to replace it once in the
ten years that I've lived here - the light died.
|
25.252 | Not at Spags | AKA::SUNG | There's a fungus among us | Wed Nov 11 1987 23:02 | 5 |
| Spag's doesn't carry the switch with the lighted handle. They only
have the type where there's a separate red pilot light. It uses
a double socket wall plate rather than a switch plate.
-al
|
25.253 | | WELFAR::PGRANSEWICZ | Auhhhhh, I've been slimed! | Thu Nov 12 1987 10:43 | 13 |
| RE: .20
> There is one potential gotcha in the system. The light
> MUST feed from the box that the lighted switch is in. The light
> is really a second (or third, or fourth....) light in the
> circuit and needs to have both neutral and switched hot in the
> box that it is in.
Are you saying that only 1 of the switches in a 3-way configuration
can have one of these lighted switches?
Also, anybody know a place that has these switches in MA or NH?
|
25.254 | Go to Sears | TALLIS::SAMARAS | Advanced Vax Engineering LTN | Thu Nov 12 1987 13:19 | 11 |
| Funny you should ask, but I just installed a lighted 3-way last night.
I bought it from SEARS, and it cost under $10. ($7.99 I think). The
toggle is clear and illuminated internally somehow with a neon bulb. The
real "goodie" is that the switch is lighted when it will turn the circuit
on! Sounds exactly what you're looking for.
They also have illuminated toggle dimmers for 3-ways. Believe it or not,
you can have 2 of these dimmers controlling the same light. It works too!
fyi,
...bill
|
25.255 | Someone oughta write a book... | JOET::JOET | Deatht�ngue lives! | Thu Nov 12 1987 13:38 | 7 |
| As I recollect, an n-switch setup has exactly 2 3way switches in
it and n-2 4ways between them. Is this correct?
If so, would the lighted 3ways still work as .23 claims, if they
were one of the two 3ways in an n-switch arrangement (where n>2)?
-joet
|
25.256 | Pilots: anything's possible, some are easy | VIDEO::DCL | David Larrick | Thu Nov 12 1987 15:50 | 27 |
| The entire network of 3-way and 4-way switches taken together determines
whether the switched loads (lights) will be on or off. The network is
designed in such a way that the loads can be turned either on or off from any
of the switches, but that's a detail at this point.
The important thing to note is that the "answer" is only "known" by the last
switch in line, i.e. the one electrically furthest from the power source.
That "answer" can drive all the pilot lights and real lights you want (subject
to circuit loading). The intermediate "answers" which the other switches
along the way "know" don't do any good.
The easiest pilot light to wire, then, is one that is located very near that
last_switch_in_line. This wiring is so easy that some manufacturers do it
for you, and supply 3-way switch, pilot light, and appropriate wiring all in
one package.
To power pilot lights that are located anyplace else, you need to run wires
to them, just as you need to run wires to the real lights you're powering.
Electrically, the only difference between pilot lights and real lights is
wattage.
One way to build your own pilot light is to run those switched wires to an
ordinary outlet, and plug a night light into it.
The above discussion applies to pilot lights that go ON to indicate that the
load is ON. I don't know about lighted switches, which typically go ON when
the load is OFF, theoretically so you can find the switch in the dark.
|
25.258 | So? | VIDEO::DCL | David Larrick | Fri Nov 13 1987 13:25 | 16 |
| re .26
> This note is now discussing TWO types of switch pilot lights!
> The first topic deals with switches which light up when they are off,
> ostensibly so they can be found in the dark to turn them on.
Considering that .15 (the reply that restarted the discussion in this
topic) asked for information about what types of pilots/lighted switches
are available, that's not entirely bad.
If you (.26 or anybody else) feel strongly that these two discussions belong
in separate topics, go ahead and untangle 'em. But my opinion is that the
discussions are sufficiently inter-related that they benefit from being
together here. As long as everyone clearly states which type they're
talking/asking about, it shouldn't get too confusing.
|
25.33 | PATTON PORTABLE WHOLE HOUSE FAN | ELWOOD::DUFORT | | Tue Dec 15 1987 09:08 | 15 |
|
I use a Patton portable whole house fan and it works great. I put
in a window up in my bedroom and open a window in the other rooms
in the house. I point the fan to blow out the window thus drawing
air from the outside and cooling off every room this way. The fan
moves 12,500 cubic feet of air a minute and the new ones have a
25 year warranty on them. They go for $50 on sale to $80 regular
price. I have had mine for 5 years now and have no complaints.
As for the attic, I had ridge vents installed last spring and this
has cooled the attic off tremendiously. I see no need for an attic
fan with the ridge vents and my portable one that i use now.
Dave
|
25.34 | no more attic fan drafts | CLT::ZEHNGUT | | Mon Feb 08 1988 19:26 | 11 |
| Only 4 short months after my wife (.29) asked me to, I got around
to making a box to cover the attic fan for the winter. I used a
one-inch think sheet of Koppers insulation (rigid foam), cut it
into pieces and taped it together with duct tape to form the box.
It fits nicely over the fan opening in the attic. It's only been
up for a day but we have noticed the reduction in drafts already.
The insulation is very light, so it should be easy to take the box
on and off twice a year.
Marc
|
25.35 | An alternate approach | BINKLY::WINSTON | Jeff Winston (Hudson, MA) | Mon Feb 08 1988 23:47 | 9 |
| I took a different approach...the hole in the ceiling that held the
attic fan vent was nicely framed with molding. So, I took a 3/4"
piece of plywood cut to the size of the hole, painted it, backed it
with insulation (reflectex), and built a hatch door. It's held in with
2 hinges on one side, and a door bolt on the other. In the summer, I
can remove the hinge pins and take the whole thing out. Again, it cut
the drafts significantly. (As far as heat is concerned, an attic fan
vent is simply a transparent hole through your insulation and out your
roof).
|
25.135 | Electrical Connection? | AD::DIPINTO | | Fri Apr 08 1988 10:51 | 0 |
25.136 | | VIDEO::DCL | David Larrick | Fri Apr 08 1988 11:27 | 7 |
| I don't know of any specific National Electrical Code provisions about
dedicated circuits for fans. So it's probably OK to add a fan to a
circuit that serves other purposes as well, assuming that the circuit
has sufficient capacity for the fan.
In particular, don't just connect the fan to a convenient nearby circuit
and hope for the best. Add up the loads and make sure.
|
25.137 | | VINO::GRANSEWICZ | Did you see that?! | Fri Apr 08 1988 13:34 | 5 |
|
But will the startup of the fan cause all the lights on the circuit
to dim or flash??
Phil
|
25.138 | | VINO::KILGORE | Wild Bill | Fri Apr 08 1988 16:41 | 1 |
| Not in my experience. (House fan powered from bedroom circuit.)
|
25.139 | group rates? | NETMAN::SEGER | this space intentionally left blank | Fri Apr 08 1988 17:34 | 8 |
| This is probably a dumb idea - but that won't stop me from posting it. Might
there be a possibility that there are enough people interested in fans (after
all, this IS the season to think about them), to do some kind of group purchase
and thereby get a discount?
I would think as little as 3 or 4 people could generate 10% or more off a price.
-mark
|
25.140 | Group purchase: one taker | ERLANG::BLACK | | Wed Apr 13 1988 15:07 | 12 |
| To the contrary -- I think that it is a great idea. Just looking
at the number of people who seem to have put them in last year,
we might be a ble to cut a deal -- or at least lessen the overheads
involved in the process.
Moreover, the mutual commitment involved might mean that I get this
thing installed before the first snows fall!
Are there any other takers?
Andrew
|
25.141 | I need one also! | PALMER::PALMER | half a bubble off plumb | Wed Apr 13 1988 15:51 | 3 |
|
I'm planning on installing one this year also
=Ralph=
|
25.142 | Me Too | SALEM::PAGLIARULO | | Wed Apr 13 1988 16:33 | 4 |
| Count me in. I was planning on buying one sometime this summer
anyway.
George
|
25.143 | | NETMAN::SEGER | this space intentionally left blank | Wed Apr 13 1988 21:16 | 19 |
| Ahh... now we're making some progress!
Last year I went to all the trouble to look at a Grainger's catalog. It looks
like DEC employees can get DEC's discount. The problem is there are several
models and I have no idea which one is the one to get. If I recall, the 2
parameters were RPMs and diameter. Naturally, the bigger the diameter and RPM's
the more air you can move. However, if memory serves, it wasn't that straight
forward as one of the smaller models cost more than the bigger one.
Unfortunately the catalog is back at work on my desk and I'm at home.
Does anyone have any input on this?
The other options I think are SEARS (and I just as soon stay away from them) and
lumber yards. The latter seem to have periodic sales on random brands and none
seem to be better than Graingers. Now it turns out if we went there and got DEC
discount they probably wouldn't give us anything off, but at least we could help
each other make the choice.
-mark
|
25.144 | | SALEM::PAGLIARULO | | Thu Apr 14 1988 09:24 | 5 |
| Note 170 also has some information on whole house fans. haven't
had time to really go through all the replies but it seems that
they do talk, at least a little, about cfm, speed, fan size etc, etc.
George
|
25.145 | Sears a possibility | AD::DIPINTO | | Tue Apr 26 1988 14:05 | 20 |
|
According to note 170.28 DEC employees CANNOT buy from
Graingers. To have a hardware store make the purchase I
assume that they would want at least 10% profit.
Comparing the fans from Graingers and the Sears catalog
it seams that Sears better direct drive fan is exactly the
same as the Emerson in the Graingers catalog but priced
about $15.00 more. The sale price would probably be the same
or better than Graingers.
Has anyone had any good/bad experiences with this or a similar
type of fan? For the price I'm considering going with this fan
with variable speed and 12 hour timer. I have 1500 sq. ft. to
cool and will go with the 30 inch as r.p.m. is only 510 @6300
CFM which is not to much worse than some of the belt driven models.
I noticed some people elect to cut the attic joists instead of
mounting on top of them. What is the benefit of this?
Thanks
Len DiPinto
|
25.146 | | QUARK::LIONEL | We all live in a yellow subroutine | Tue Apr 26 1988 20:42 | 7 |
| I installed a Sears direct-drive fan in my previous house. It
had a temperature sensor that would make the fan run faster when the
air was hotter (first turned on), then slow down as the attic cooled
down. It also had a wall-mounted thermostat for on/off control.
Worked great! But I haven't seen this model for several years.
Steve
|
25.147 | | NETMAN::SEGER | this space intentionally left blank | Thu Apr 28 1988 13:11 | 5 |
| I'm sure the reason you haven't seen the temperature sensitive model is because
they are now illegal (or at least should be!). The problem is that if there is
a fire, the temperature sensor turns on the fan and fans the fire!
-mark
|
25.148 | I don't see a problem | QUARK::LIONEL | We all live in a yellow subroutine | Fri Apr 29 1988 11:33 | 16 |
| Re: .36 [Corrected from earlier entry]
I asked about that. The model I installed also had a heat-sensitive
link that would shut off the fan if the temperature rose above 130.
I don't see a difference between a temperature-sensitive fan and
a normal one in the case of a fire. Both are going to draw
air until something shuts them off. I would hope that ALL whole-house
fans have a high-temp shutoff.
The big advantage of the model I had was that it ran fast at first
and cooled off the house (and attic), then slowed down to a barely
noticeable hum. I couldn't understand why that style wasn't more
popular.
Steve
|
25.149 | | NEXUS::GORTMAKER | the Gort | Sat Apr 30 1988 00:12 | 2 |
| The heat sensitive link is required for UL approval.
|
25.150 | Thats done! | AD::DIPINTO | | Fri May 20 1988 08:49 | 12 |
|
Its done!
I installed the Sears(actually Emerson) 30" direct drive
fan this past weekend. It sits on top of the joists and
was fairly easy to install. It came with a firestat that
mounts in the attic as a shutoff in case of fire and a
variable speed switch. I added a 12 hour timer which fits
in the same double box. The fan makes less noise than I
was expecting. I am very happy with it.
Len DiPinto
|
25.36 | a Rube Goldberg experiment???? | TOLKIN::FARLEY | | Fri Jun 24 1988 14:04 | 21 |
| I have two schemes I'd like to open up for discussion
regarding cooling down the attic as well as the house.
I have a Garrison with about 5.5' of attic. On each side of the
attic is a 1' x 2' (approx) louvered vent. That's it.
Access to the attic is through a cut out in a bedroom closet.
I'd like to try to cool off the house and do it the simplest way
so my plan is to take a 10" muffin fan ($1.00 tag sale) and
hook it up to about 3 feet of galvanized duct, mount it to one
of the vents and pull the hot attic air throught the vent. I assume
the other vent will act as a supply.
Anybody think it'll work?
Also, I thought about taking the 24" regular floor fans and just
resting it flat over the closet opening so it can suck air from
the bedroom and blow it up into the attic.
Whattya think?
|
25.37 | DO NOT USE FLOOR FAN | CURIE::BBARRY | | Fri Jun 24 1988 14:44 | 26 |
|
< Also, I thought about taking the 24" regular floor fans and just
< resting it flat over the closet opening so it can suck air from
< the bedroom and blow it up into the attic.
NO,NO,NO,NO,NO
1) They are not designed for use in a horizontal position. Most
carry warnings about not using in the horizontal position. You
will definitely wear out the motor quickly, the blades probably
are not balanced properly, the draw will be reduced and worst of all
the additional drag on the motor can cause the motor and powercord
to overheat, creating a fire hazard.
2) Cheap fans lack the proper shutoff in case of a fire. This is not
a problem for floor fans in normal operation, because they are only
moving air around in a small area, not pulling it from all parts of
the house.
3) I doubt that you will see a noticable difference. An attic fan
moves a lot more air. Attic fans are designed to be dropped into
24" opennings. Buy one and use the floor fan to direct the fresh
air where you need it.
You will probably want to put the fan in a more central location,
unless you want all your clothes covered with dust, etc.
|
25.38 | Helps a lot | VIDEO::NOTT | | Fri Jun 24 1988 16:17 | 24 |
| Welllll....We put up a "hokey" attic fan last week when it was so
unbearably hot, just to see if it would change our situation any.
We have one 5K BTU window A/C upstairs, and when it's really hot,
it just couldn't keep up with the load.
This year, we took a 16" table fan and put it on a table in the
attic, just in front of the vent at one end. We turn it on in the
AM, and off at evening. The vent is about 12 X 18 inches, so I
wasn't sure if there would be enough air flow, or not.
The result was not very quantiataive, as we didn't actually make
temp measurements before / after. BUT....we did notice that the
ceiling of the bedrooms remained cool to the touch, where they had
been warm to the touch "before fan". Also, the A/C seemed to be
able to do a better job of removing the heat that was there.
Mind you, this is not a "permanent installation", and I don't advocate
anyone else doing it, as the safety implications aren't nice (no
thermal cutout in case of fire). However, I offer it as evidence
that even a "small" attic vent fan can offer significant help in
dealing with the heat. I will be installing a vent fan very soon,
as a result of this experiment.
Bill
|
25.39 | maybe it'll help a little | TOLKIN::FARLEY | | Wed Jun 29 1988 14:57 | 11 |
| re: -2, -1
Well, Thanks for the warning about the floor fan. The sun creates
enough heat without asking an overheating fan to contribute. ;^)
However, I think I'll try the muffin fan-out-the-vent, with a regular
electric cord. Since it was designed to exhaust hot air from CPU-type
cabinets, I don't think the risk of fire due to overheating is
very great. Do you?
|
25.40 | Not the fan, the house! | VIDEO::DCL | David Larrick | Wed Jun 29 1988 17:12 | 11 |
| As I understand it, the purpose of the thermal cutout switch isn't to keep
the fan from overheating and starting a fire; it's to keep the fan from
continuing to run in a house fire, contributing to the chimney effect and
making the house burn down hotter and faster.
Seems to me that if the fan is big enough to make a difference in cooling
the house, it's big enough to make a difference in a fire. And if it's not
big enough to make a difference, why bother?
So the muffin fan is probably fine for an experiment, but if you start using
it all the time, I hope you're self-insured.
|
25.41 | | HPSMEG::LUKOWSKI | I lost my A$$ in the '87 CRASH! | Thu Jun 30 1988 12:36 | 16 |
| Re: .36 and .39
Why not get one of those turbine vents. It's one of those that
spins from the hot air leaving the attic. You ill be amazed at
how it will almost perpetually turn. I installed one last year
and was amazed at how much 'pressure' was in the attic. While I
was cutting out the hole in the roof to install it, most of the
sawdust was actually blowing back at me! They cost around $20 at
Grossmans on sale and are definitely worth it. I had a severe lack
of ventilation in the attic prior to this so I installed this vent
as well as vents under the eaves. I don't consider myself an expert
on this by any means but I wouldn't consider an attic fan (or fan
in the attic in your case) unless I wanted it to draw hot air from
inside the house. That is what they are designed for.
-Jim
|
25.42 | I'd check on using a turbine vent... | ALIEN::PETROVIC | Looking for a simpler place & time... | Thu Jun 30 1988 17:00 | 35 |
| >
>< Note 170.41 by HPSMEG::LUKOWSKI "I lost my A$$ in the '87 CRASH!" >
>
>
> Re: .36 and .39
>
> Why not get one of those turbine vents. It's one of those that
> spins from the hot air leaving the attic. You ill be amazed at
> how it will almost perpetually turn. I installed one last year
> and was amazed at how much 'pressure' was in the attic. While I
> was cutting out the hole in the roof to install it, most of the
> sawdust was actually blowing back at me! They cost around $20 at
> Grossmans on sale and are definitely worth it. I had a severe lack
> of ventilation in the attic prior to this so I installed this vent
> as well as vents under the eaves. I don't consider myself an expert
> on this by any means but I wouldn't consider an attic fan (or fan
> in the attic in your case) unless I wanted it to draw hot air from
> inside the house. That is what they are designed for.
>
> -Jim
>
>
I'd check with your local building inspector on this before going
ahead. When I did a reroofing of my place, I wanted to install a
turbine vent, but the inspector said that they are not acceptable
in Merrimack, NH, stating reasons similar to those voiced for not
using an unprotected electric fan...namely in case of fire.
He went on to say that although the thermostatically controlled
ones are approved, he dosen't recommend them on account of the
possiblity of the thermostat failing in a fire and keeping the
fan going. In summary, I suspect that you should do anything
that is within your town's code and that you feel safe with.
Chris
|
25.43 | | HPSMEG::LUKOWSKI | I lost my A$$ in the '87 CRASH! | Fri Jul 01 1988 11:19 | 10 |
| >> When I did a reroofing of my place, I wanted to install a
>>turbine vent, but the inspector said that they are not acceptable
>>in Merrimack, NH, stating reasons similar to those voiced for not
>>using an unprotected electric fan...namely in case of fire.
I never would have thought about something like this being
against code or even asking a bulding inspector about it...especially
since it is passive. What DID he allow you to install for ventilation?
-Jim
|
25.44 | | BEING::PETROVIC | Looking for a simpler place & time... | Tue Jul 05 1988 10:38 | 20 |
| re: .-1
He (Gene Ledger) was adamant about ridge vents. All new
construction now requires ridge/soffit venting. Although
reroofing isn't new construction, he STRONGLY suggested using a
ridge vent on older homes (mine) with only gable vents.
He muttered something about not passing inspection, however, when
my wife went to get the permit, she got a schedule of permit fees
and nowhere on it was any mention of needing a permit for
reroofing or residing. How he is supposed to 'pass/fail' a
roofing or siding job without knowing about it beats me... Now
this was about 4 years ago and things may have changed..
At any rate, I took his suggestion and am statisfied with the
results in winter and summer. Summer results in a cooler house
and the winter results in an attic space incapable of melting
ice (no ice dams).
Chris
|
25.45 | Vents, fires, and flames | CSSE::BAIRD_2 | CD = Real to Real | Wed Jul 20 1988 14:26 | 27 |
|
If you're looking at turbine vents for the roof a couple of quick
points from my wallet. Don't save money on the off brands - I finally
got 'Whisper-Cool' (spelling?) base and turbine when the bargin
bearings went out after two years. The W-C's were running after
seven years when I sold the house 2 years ago. Second, the energy
savings and comfort level improvement are substantial.
And about vents and fires:
Any inspector killing an install of wind driven turbine vents should
be replaced effective last year. Sure there's a lot of emotion over
the fire issue but any inspector who can't separate fact from fiction
on this one, should be on the sidelines. You need venting to save
the house in normal use. Screened vents, soffit vents, ridge vents,
turbine vents, open windows even, will provide venting and yes,
assist in a speedier more destructive fire. I know of no one I
respect who advocates doing away with venting. Powered fans are
a different issue. Not passive, bad environment, out of sight and
mind - I'm not concerned so much about their venting assisting a
fire, as their lack of servicing causing one. Even here, I'll go
along with power venting in a crunch.
Stopping folks from utilizing vents of whatever (passive) type by
hitting on the fire issue is a disservice. Concerns unduly weighted
on fire control and venting are misplaced and misdirected.
|
25.46 | insulation in my soffits | ATPS::FEENY | | Thu Aug 11 1988 23:47 | 54 |
| oi've been reading all this talk of ventilation with great
interest -- especially in view of the horrid summer we're
suffering thru and the fact that air does not seem to move
AT ALL in my house (sleeping has been horrendous). i've
discovered that at least part of my problem is insulation in
the soffets. it's the 'blown in' type and whoever installed
it did so without any knowledge (or concern) for the
apparent importance of soffit vents -- the insulation
completely fills in the soffit space.
obviously i need to open up the soffit vents and let them
'do their thing'. my problem is this: the distance from
the attic floor to the bottom of the soffit is about 5 feet
and it's quite difficult to get in there and pull out the
insulation.
^
/ \
/ \
/ \
/ ATTIC \
/ _______ \
/*/ \*\
/*/ \*\-----INSULATION
/*/| |\*\
| 2ND |
| FLR |
| |
any sug's on how to suck or pull this stuff out. it's like
molded powder that crumbles when you touch it.
also, would it be a bad idea to take out ALL of the
insulation that's in the soffit space? or, should i take
pains to clear a 'tunnel' thru the insulation from each of
the soffit vents? if so, is getting at the soffits from the
outside the only way to find out just where each vent is
located?
lots of questions, i know. but we're dealing with a first
time homeowner who has a minimum of experience and a
do-it-yourselfer's pocketbook.
by the way, looking at the soffit bottom from the OUTSIDE of
the house (which is 100+ yrs old, with 2 yr. old vinyl
siding), i see that it is perforated vinyl.
any suggestions/comments may help provide a decent night's
sleep for the first time in weeks.
thanx, y'all.
michael
|
25.47 | re-do the insulation | FREDW::MATTHES | | Fri Aug 12 1988 08:57 | 5 |
| Suck it all out with a shop vac.
Install styrofoam proper-vents.
Re-insulate with unfaced fiberglass mats.
|
25.48 | | JULIET::MILLER_PA | Have you hugged your Logistician? | Fri Aug 12 1988 11:10 | 7 |
| If you don't want to suck it *all* out, block off a section above
the ventilation ports at the point where the roof meets the walls,
and suck out *that* portion of the insulation. You will still have
an insulated soffit area and also the venting needed for good air
circulation.
Pat.
|
25.49 | Another approach | GWYNED::MCCABE | | Fri Aug 12 1988 13:28 | 9 |
| I ran into a similar problem in my house and you can push in the
air circulators, a 12" x 48" piece of styrofoam molded to form a
channel, and then use the vacuum to get rid of the insulation in
the channel. The air circulators come 24" x 48" and you break them
in half for 16" o.c. studs, or use them as is for 24" o.c. Most
lumber yards carry them, they cost around $1.50 a piece. The insulation
below the air circulators will hold them in place, but toss in a
few long staples if you can get at one end.
Chris
|
25.259 | Whole house fan switch location | PAMOLA::RECKARD | Jon Reckard, 381-0878, ZKO3-2/T63 | Wed Oct 19 1988 11:43 | 0 |
25.260 | exit | NHL::MAY | IT'S LIKE THE SAME, ONLY DIFFERENT! | Wed Oct 19 1988 12:01 | 3 |
| How about on a double wallplate next to your furnace switch (which
is normally mounted high on the wall inside or close to you cellar door.
|
25.261 | a timer switch makes sense | TFH::DONNELLY | Take my advice- Don't listen to me | Wed Oct 19 1988 13:17 | 6 |
| also, how about a timer. a 1 to 6 hour one for instance? it couldn't be
left on and would be much less likely to be playfully or accidentally
turned on. just put it on the first floor somewhere, our's is on the 2nd
(near the fan) and it's not convenient.
craig
|
25.262 | | CSSE32::NICHOLS | HERB | Wed Oct 19 1988 13:32 | 8 |
| Our emergency furnace switch was installed -when the house was build 30 odd
yrs ago- about 6' high, on a centrally located interior wall -facing
the stairs to the basement. When we installed the "whole house"
attic fan, I put the switch just about the same place one floor
above facing the stairs from the 1st to second floor. Works out
just fine
herb
|
25.263 | seperate control | FRSBEE::DEROSA | Somewhere,Somehow,We've lost it... | Wed Oct 19 1988 13:35 | 11 |
|
The whole house fan CONTROL , which is about the same size as a
ceiling fan control, should be in its own single box up high enough
so it won't be bumped. Also keep in mind the control will put out
a certain amount of heat. Ours is in the hallway a little less than
6' up. I wouldn't put it in with any furnace emergency switch as
it may be against code. It should come with its own electrical box
and cover anyway. Ours did.
Bob
|
25.264 | Disable the fan if you have fireplace lit. | NEXUS::GORTMAKER | Whatsa Gort? | Thu Oct 20 1988 04:54 | 14 |
| My father double switched his so that there was one to turn it on/off
for normal operation and one in the closet that could be switched
off to completely disable the fan. You are probably wondering why,
right? Well my nephew found the switch one winter evening and turned
it on which might have been fine but the fireplace was lit.
Want to talk about a draft problem? Needless to say it made for
a few tense moments until we figured out what was happening.
The second switch was added the next day. Almost a must in my opinion
if you have a fireplace or stove and there's a chance that the fan
could be turned on while you have a fire going.
BTW- both switches are in series ANDed as it were.
-j
|
25.265 | new code on furnace emerg switches | FREDW::MATTHES | | Thu Oct 20 1988 09:09 | 15 |
| The fan control definitely should be in a separate box from the
furnace control. BTW I believe the emergency switch is now located
in the living quarters. Mine is just inside the cellar door so
that you don't have to stare at this big red wall switch. Of course
if there's a fire caused by the furnace, it will be in the cellar
and one of the LAST things you want to do is open the cellar door!
It's a lot like these folks buying one of those Ronco (sp?) fire
extinguishers seen on the tube. where do they put it? Above the
cooking surface of the stove to be nice an handy. Where's the last
place you want to reach when there's a stove fire?? [answer left
as an exercise to the student]
The dual control sounds like a good idea provided it's documented
for the new owners.
|
25.68 | Cost/ease of installing an "attic" fan | WONDER::YOUNG | | Thu Mar 23 1989 09:32 | 16 |
| We're buying a new house and one of the extras is an attic fan.
We're wondering if we should have the builder put it in or wait
and do it ourselves. The specs I have for it are "attic fan, 2
speeds 755 CFM high 500 CMF low with timer". He wants $700 for
this. I found out from reading this notes file that there's a
difference between attic fans and whole house fans. I got the
impression from the realtor that this is a whole house fan even
though it says attic fan. There will be a vent in the ceiling
of the 2nd floor at the top of the stairs. Would this be true
of an attic fan? How difficult is it to put in a whole house
fan (assuming we have adequate attic vents)? We'd have to cut
the hole in the ceiling, mount the fan, bring power to it and
mount the control somewhere. Is that about right?
Thanks,
Barb
|
25.69 | | NSSG::FEINSMITH | I'm the NRA | Thu Mar 23 1989 10:54 | 23 |
| In the previous house I had, a whole house fan was there when we
bought it. It was mounted above the grill in the hall and would
open the grill louvers when it went on (by air flow). The air was
blown into the attic where it exited the house via soffit and gable
vents. This unit was 3' blade tip to tip and was belt driven from
a large electric motor.
The way I understand it, an attic fan is smaller and therefore won't
pull as much air through the house, used primarily to vent the attic.
This may be a question of semantics, so you'd have to speak to the
builder to be sure.
$700 sounds a bit high, but I havn't done any pricing lately. If
you could get the builder to frame out the opening and then just
sheetrock over it to make the inspectors happy (or just install
the louvered grill) the fan itself is an easy DIY job. If the house
is being built, the extra electric line can be run ahead of time
and connected when needed at both ends. Go out and do some pricing
will give you a better idea of what they cost today. Just make sure
that you'll have enough attic vents to exhaust the proposed CFM
that the fan will have.
Eric
|
25.70 | fool him | TOMCAT::FOX | | Thu Mar 23 1989 11:29 | 14 |
| $700 is too high - especially is the house is not complete. A
handyman would probably charge less with the house *complete*.
Most whole house fans don't need any extra framing, or even
a switch (as long as you don't mind a pull switch). A decent
fan (with louvers) will run you $200 max. The labor would
total about an hour between mounting the fan, electrical, and
trim. Tell him to have the electrician put a light where you
want the fan, and a switch where you want to control it. That
should be no more than $100. You can then replace the light
with the fan, and the switch with something to control the fan
whenever you want.
Total expense: $300.00
John
|
25.71 | get it rough framed if you can | NETMAN::SEGER | this space intentionally left blank | Thu Mar 23 1989 13:09 | 8 |
| If you've got a reasonable builder, you might be able to get him to rough frame
the fan opening. Then if you've also got a reasonable electrician you might
be able to get him to run some wires OR at least some power to were your would
eventually mount the fan. I agree that it's NOT a big job even if you had to
do it from scratch, but while framing we're probably not talking more than 15-20
extra minutes worth of labor (if that!).
-mark
|
25.72 | get him to put the vent. in | TOMCAT::FOX | | Thu Mar 23 1989 13:40 | 10 |
| What's there to frame? The fans don't *need* to be framed in. I
installed a 30" Braun fan (from Somerville), and it just mounts
on the existing joists. The thing is steady as a rock.
Power was a little more of a pain. I went off of a closet light
that was close by. I also added a thermostat and a variable
switch which took some more time.
If you ask the builder for anything, make it extra ventilation,
and power to the spot where the fan will be.
John
|
25.73 | 500 CFM is pretty small | ULTRA::WITTENBERG | Secure Systems for Insecure People | Thu Mar 23 1989 14:18 | 17 |
| 500 CFM isn't much. My whole house fan is specced at 5 or 6
thousand CFM. Since I have a fairly large house I bought the
biggest model, but the smaller ones still moved more than 3000
CFM. It does a wonderful job of cooling the house. The specs call
for 8 square feet of windows open in the house and 8 square feet
of gable or ridge vent in the attic. The fan cost about $200. The
instructions said to put it on its own 20 amp circuit, which seems
like a little bit of overkill, since it's not supposed to draw
more than 10 or so amps.
Physical installation is pretty straight-forward. Cut a 30" x 30"
hole in the 2nd floor ceiling, and drop the fan on top of the
joists. Install a shroud or two and wire it up. I spent more time
running a new circuit from the basement than I did on the physical
installation.
--David
|
25.74 | $700 much to high | OASS::B_RAMSEY | My hovercraft is filled with eels. | Thu Mar 23 1989 14:29 | 12 |
| The cost of the fan is about $200 for a whole house fan. It is
worth the money because you wont have to run the a/c for at least
1 month in the spring or fall. It will quickly cool a house in
minutes. Make sure you clean out the fireplace VERY well before
turning it on or you will have soot all over the place.
$700 seems way to high. I agree with the other replies about having
the builder put in the electric as that is the biggest headache
about installing the fan. My dad put one in his house about 2 months
ago and the wiring took him a hour or so but the installation of
the fan took about 30 minutes.
|
25.75 | warning on thermostats | NETMAN::SEGER | this space intentionally left blank | Thu Mar 23 1989 19:27 | 10 |
| I know this has been discussed many times before, but we DO have a new audience.
If the thermostat mentioned in an earlier note was the type that turn the fan
on when the attic gets too hot, please do yourself a favor and throw it away
right now.
The theory sounds great until you stop to think that when there's a fire in
your attic it will also heat up, turning on the fan and whipping up the fire
even more!
-mark
|
25.76 | A MUST for WHF's | ARCHER::FOX | | Thu Mar 23 1989 20:19 | 6 |
| RE .7
Couldn't agree more. I forgot to mention the installation included
a device that *shuts off* the fan at extreme temps. It wasn't any
work really putting it in since it's up there with the fan.
John
|
25.77 | firestat? | THRUST::COOK | Yes, but am I paranoid enough? | Fri Mar 24 1989 08:18 | 10 |
|
I installed whole house fan in my home in Georgia. A device that
I believe was called a firestat was required by the building code.
This device was supposed to cut the power during a fire. It cost
about $10 at a local electrical supply and installed with just a
screwdriver.
al
|
25.78 | | VINO::GRANSEWICZ | Which way to Tahiti? | Fri Mar 24 1989 12:15 | 11 |
|
RE: .9
Is this "firestat" the same thing used above a furnace? Do you
have to put up more than one to cover the entire attic area?
About the electrical, I would imagine code requires a dedicated
line to the fan since it is a "fixed" appliance. I would make it
20 amp since it can't use more than 80% (16 amp) if it is considered
a "continuous load". Check the code in your area but 20 amp should
cover it.
|
25.79 | probably worked the same | THRUST::COOK | Yes, but am I paranoid enough? | Fri Mar 24 1989 13:36 | 18 |
|
Ok, this is going to get technical.;-) The little whosit over my furnace
here in Mass. has a little wheel on it that is made of a material
that has a low melting point. When the wheel melts a spring loaded
screw will be pulled back into the case and cut the power. This
doesn't *look* anything like what I put on the WHF but could work
internally the same. The 'firestat', again I'm only marginally
sure of the name, was a metal box about 2" X 2" X 4" with four
terminals inside a cover. The white and black wires were attached
to the terminal and secured with clamps to the normal romex. The
box was then attached to the rafter with screws. I'm assuming that
there was some low melting point metal or some bimetal that would
break the connection in case of a fire. However, I didn't take
the box apart to look. Oh, and there was just one next to the fan.
I can see where it would be better to have several but the code
only called for one.
al
|
25.80 | What's the cost break-down? | JACKAL::FRITSCHER | | Thu Mar 30 1989 15:56 | 18 |
| The time to have this fan work installed would seem to be now.
If your building a nice new house the last thing your going to
need is to have to do more work when you move in. If your not
going to have the contractor do this work, than i dought that he
would do any special wireing without a price tag. As one mentioned,
these typ fans should be on there own 20 amp,12gage line. If you
tellthe builder that you do not want the fan, he might just bring
power from an already used up 15 amp line. the main reason for the
20 amp is for peak turn on wattage, i have a solar blower with the
same type power surge. If you start adding up all the wire needed
(12 gage) the breaker, the fan, grill work, special fire devices,
switches etc. to do this job you might as well have the builder
do it with a warranty, oh, and dont forget a little something for
the labor. perhaps the builder will talk about the price, or break
down the price to show you what your paying for. Im not saying his
price is right, but i do think it will be more work than is being
let on to be. You might end up haveing an electrician come in to
make connections for you in the long run anyway.
|
25.81 | Do it yourself | PKENT::KENT | Peter Kent - SASE, 223-1933 | Fri Mar 31 1989 17:54 | 8 |
| The installation of today's whole house fans has been simplified. It
used to be that you had to cut ceiling joists and frame it for the fan.
The fans now come with a cowling that installs between the joists so
that you just mount the fan on top of the ceiling joists. The only
thing you have to cut is the drywall in the ceiling and attach the
louvers from the bottom. I would have the electrician install the
wiring and switch and do the rest yourself. It's not difficult. Just
don't wait for a 90 degree day like I did to do the installation.
|
25.82 | Humidity in attic. | DEBUG::DBOISVERT | Dave Boisvert 312-640-2699 (8-421) | Mon Apr 17 1989 13:06 | 9 |
| I added on a 1500 sft addition and included a WHF and an attic fan.
I wired the attic fan with a thermostat for the heat in the summer
and a humidistat for the moisture in the winter.
My question is: What amount of humidity in the attic will allow
me to maintain proper moisture control? (in other words what should
I set the humidistat to?)
Dave
|
25.83 | Aprilaire recommendations | DEBUG::GALLO | Paul Gallo (CEA/SPS Support) | Mon Apr 17 1989 22:58 | 21 |
| Aprilaire recommends the following settings...
Outside
Temperature Humidity
(in Fahrenheit) Setting
----------- ----------
+90 70%
+80 65%
+70 60%
+60 55%
+50 50%
+40 45%
+30 40%
+20 35%
+10 30%
0 25%
-10 20%
-20 15%
-30 10%
You may want to check with your manufacturer to be certain...
|
25.84 | WHF with blown-in insulation ? | PTOVAX::CARLETON | Dennis Carleton | Thu Apr 27 1989 18:40 | 2 |
| Is it possible to install a WHF in an attic that has blown-in
insulation ? Will the insulation get blown all over the attic ?
|
25.85 | Should work. | DELNI::MHARRIS | Mark Jay Harris, DSS & Integ'd Prd Mktg | Thu Apr 27 1989 23:23 | 7 |
| The blown-in insulation should have settled. A small amount of it
may fly away at first, but it will stop soon. The air flow does
not actually disturb the insulation since it goes from the fan to
the roof vents...
M
|
25.86 | See also note 188 | BEING::WEISS | Trade freedom for security-lose both | Fri Apr 28 1989 09:13 | 0 |
25.87 | Blown insulation and attic fan NO PROBLEM! | CSMET2::CHACE | let's go fishin' | Fri Apr 28 1989 10:02 | 5 |
| I have blown-in insulation AND an attic fan. I have used the attic
fan a lot and there has been NO problem with the insulation blowing
around.
Kenny
|
25.151 | <DELTA fans> | RGB::SWEENEY | | Tue Jun 20 1989 09:47 | 32 |
| I want to reopen this topic briefly. I read thru all the FAN notes
and didn't see any mention of a DELTA wholehouse fan. They are the
brand now sold by Sommerville lumber (at least in Westboro) They
no longer carry BRAUN.(sp?).
The specs say:
30" 760RPM 2speed 1/3hp 4.6a 4800CFM beltdrive need 9sq'
of vent.
in attic
36" 460RPM 2speed 1/3hp 4.6a 6500CFM beltdrive need 11sq'
Anyone out there own a DELTA fan or can comment on these specs.
Price for 30" is under $200 and the 36" is $229. Can get a variable
speed switch for $24.99 made by DELTA for this fan. They also
claim that the 30" fan is made to cool a 1700sq' house and the
36" fan is made to cool a 2300sq' house. The 30" fits on the joists
and the 36" I must cut the joists.( Any comments on how easy it
is to box in joists would be appreciated,it looks easy).
I can also get a FASCO but they were about $100 higher in price.
The DELTA fans are on sale at Sommerville until July 1.
As far as attic ventilation goes I have 2 gable vents. I have soffit
vents on both sides of the house (36' each side) and I believe I
have ridge vents on the main part of the house. I know the attached
family room has a ridge vent. Can someone tell me what the actually
ventilation area is for the soffit and ridge vents. The openings
on the soffits look like little slits.
thanks
/Jay sweeney
|
25.152 | | TOKLAS::FELDMAN | PDS, our next success | Tue Jun 20 1989 11:03 | 7 |
| Rumor has it that the next issue of Consumer Reports will report on
home cooling, including air conditioners, attic fans, and whole-house
fans. It should hit the newstands the last week in June. You might
want to try to hold off until then (or arrange to get a rain check from
Sommerville Lumber, which will give you more time to decide).
Gary
|
25.153 | Yet another factor for your decision... :-) | CRAIG::YANKES | | Tue Jun 20 1989 11:47 | 10 |
|
Something else that you might want to consider is the location of the
fan and how quiet you want it to be. All other factors aside (ie. type, and
thus noise, of the motor itself), the 36" diameter blades running at 460rpm
will have the tips of the blades moving around 13% slower than the 30" diameter
blades running at 760rpm. In general, the slower the blades are moving the
quieter the fan will be. You might want to consider asking the dealer if you
can run both fans at full speed for a noise comparison in the store.
-c
|
25.154 | July CONSUMER REPORTS has hit the streets | LYCEUM::CURTIS | Dick "Aristotle" Curtis | Wed Jun 21 1989 22:20 | 6 |
| .41:
That issue should have been delivered sometime last week -- if you
don't have a subscription, check your news-stands now!
Dick
|
25.155 | <CR> | RGB::SWEENEY | | Thu Jun 22 1989 09:15 | 7 |
| I've been checking the bews stands in the Marlboro/Hudson
Framingham/ashland and Milford areas, but no luck so far. Most stores
I've been in have the new magazines in for all other topics except
consumer reports. If anyone sees the July '89 CR issue out there
could you let me know where I can get it.
Thanks
/Jay
|
25.156 | Check your library | HPSTEK::EKOKERNAK | Watch this space | Thu Jun 22 1989 12:26 | 3 |
| MRO1 library has it, but you can't take it out.
Elaine
|
25.157 | <great> | RGB::SWEENEY | | Thu Jun 22 1989 13:57 | 5 |
| Thanks. I work at HLO and can stop by there this afternoon on my way
home. For some reason our library doesn't have the JULY '89 issue
yet. I'll check again this afternoon before leaving.
/Jay
|
25.158 | <read CR> | RGB::SWEENEY | | Fri Jun 23 1989 10:26 | 15 |
| Well I went over to MRO1 and got the JULY '89 CR issue. It was
informative as far as what to look for in a whole house fan but
they didn't do any type of comparison between models. They compared
AC units only. So it's back to making the big decision. Which model
to choose?
I've narrowed it down to 3 fans
FASCO 30"
DELTA 36"
TRI ANGLE ENGINEERING 30"
Have to make a few more calls to get the low speed specs on these
and get a price on the FASCO.
/Jay
|
25.159 | Movable fan. | TYCOBB::C_DENOPOULOS | Who is this guy?!?!?! | Fri Jun 23 1989 14:06 | 7 |
| Is it possible to put in a whole house fan that can be removed?
The best place for one in my house is right where the opening is
to get into the attic. I'll make a new opening if I have to but
would rather not. So, can a fan be installed in a way that I can
just push up and move it aside if I want to get up there?
Chris D.
|
25.160 | | ESCROW::KILGORE | Wild Bill | Wed Jun 28 1989 09:20 | 24 |
| re .48:
Yes - that's how mine is mounted. I built a frame that drops into the
attic opening, and mounted the fan on the frame. Off-season, I replace
it with another frame that matches the woodwork in the hallway and is
heavily insulated.
| ||
| || fan frame
| |`------------------------
| |XXXXX
| |XXXXX <-- foam
| joist |-----.
| | |
| | |
| | |
| | 1x2 |
------------------| |
| |
wall board | |
------------------`-----'
| casing ,-----'
`------------'
|
25.161 | <Fan is installed> | RGB::SWEENEY | | Wed Jun 28 1989 09:42 | 33 |
| I finally mad up my mind and bought the FASCO 30" fan 7800CFM ...
It also has 3 speeds which I find nice.
The installation was easy but the heat in the attic was unbearable.
I worked on the installation Sunday night for 2-3 hrs. Figured out
where it would go and cut the floor joists. The floor joists were
not exactly 16" OC. so some extra work had to be done to compensate.
By the time 8:00pm rolled around I had made all the measurements
and all boards for boxing the joists in were cut and ready but I
had had it w/ the heat. Soaked and 2 lbs lighter slithered out of
there. Monday the electrician came and installed a seperate circuit
breaker and we ran a wire up from the basement to the attic. I let
him wire up the whole thing since I wanted it completed that night
and it only took him 1/2 hr to wire up the fan itself after getting
the wire up to the attic. I spent the most of Monday afternoon in
my attic. 1pm-5pm. I cut out the opening and boxed it in. The fan
is running great and cooled the house right down on Monday and Tuesday
night. Well I lost another 4lbs Monday and was sick all night mosty
likely due to the heat.
One suggestion, if you install the fan this time of year , wait
for cooler weather and work in the mornings rather than the afternoons
Also put a fan in the attic to blow some of the air around while
you are working. I wanted the fan installed ASAP so I didn't want
to wait another week. I figured I'm in shape and could handle the
heat. It has nothing to do w/ being in shape. Your body is trying
to cool itself constantly and the attic temp must have been above
110 F. I was at least smart enough to drink lots of water every
1/2 hr to hr. to keep from dehydrating. I also knew as long as I
was still sweating that my cooling system was still at work.
Anyways I the fan is great . Thnaks for all the help
/Jay
|
25.162 | A Plug for Fan Distributors | FACVAX::SOTTILE | Doit with one knee down | Wed Jun 28 1989 12:15 | 9 |
|
Give Fan Distributors in Cambridge a call. Ask for Dana and
tell him your from DEC. He'll tell you how to calculate the
size fan you need, and he'll probabley have it in stock, for
you to pick up, or he'll ship it out to you.
868-1310
steve
|
25.163 | June 1989 Best Graphics Award | OASS::B_RAMSEY | Just 4 wheelin' | Wed Jun 28 1989 13:52 | 3 |
| re. 49
Nice Graphics.
|
25.164 | Were you pissed at the peep? | MAKITA::MCCABE | | Thu Jun 29 1989 13:24 | 1 |
|
|
25.165 | How do you stop the bugs? | CRAIG::YANKES | | Mon Jul 24 1989 13:43 | 20 |
|
We're now planning on installing a whole-house fan in a stairway
that leads up to the attic. (Of course, the stairway hasn't yet been
built -- this is turning into a merging of the "fan" and "better access
to the attic" projects...) My question is: How do I keep unpleasant
flying critters (such as hornets) from coming down from the attic? I
don't have any nests in the attic, and the vents are screened, but
there are some dead hornets laying about which means the potentials of
live hornets paying us a visit instead of staying up there to die.
Putting a screen in the fan opening looks like a solution that is
too obvious to be right. How much will doing this block the airflow?
Has anyone else screened in the opening? Thanks!
-craig
p.s. Obviousely my first step will be to check out all the vents'
screens and tighten down any openings. It will be a very difficult
job, however, so I'm not acting on the certainty of eliminating all the
access paths.
|
25.166 | | ESCROW::KILGORE | Wild Bill | Mon Jul 24 1989 20:13 | 8 |
| The fan frame I mentioned in .49 is covered with insect screening. It
must cut down a little on the efficiency, but it still moves a whole
lot of air. Other than having to vacuum it once every two weeks
or so during heavy usage (when you can't see the fan through the
screen, it's time to clean), I've had no problems - and no bugs.
The other reason I like the screen approach over the flow-operated
louvers, is that you get some natural venting even when the fan is off.
|
25.167 | | CRAIG::YANKES | | Tue Jul 25 1989 12:25 | 20 |
|
Thanks for the input! Its nice to know that I won't be spending
all that time building it just to have the screen cut the efficiency
down to near worthless.
Incidently, what I'm planning on doing for the time being is mounting
the fan/screen inside of the "summer" door so that accessing the attic is
just a matter of turning off the fan and opening the door. (Hmmm, sounds
like a good place for a pressure switch to cut the power to the fan as
soon as the door is opened...) For the winter, we'll have a "winter" door
that is heavily insulated. At each change in major season, all we'll
have to do is pop off the current door and put on the other one and
we're all set! (If this doesn't work out well, or if we have to
convert the den into another bedroom, I'll install a regular ceiling
fan in the hallway.)
Comments?
-craig
|
25.50 | If it's this hot in my attic... | MOOV00::TRAINOR | Dinghy Thingies | Mon Sep 11 1989 12:04 | 21 |
| I am curious about just how hot an attic should be allowed to get.
I have a "hip roof" colonial, so originally the roof only had soffit
vents. The last owner installed a thermostat controlled fan in the
roof and had the "on" temperature at 100 degrees. The minimum setting
on the unit is 90 degrees and the maximum is 120 degrees. What I have
found is that even at the highest setting, on a typical day, the fan
goes on at 10:00AM and goes off at about 5:00PM. My concern is the
strain on the motor and on the electric bill. I shut the fan off the
other day and watched the temperature and it went up to about 178
degrees on an oven thermometer.
The house is well insulated with 6" of blown in fiberglass on the floor
of the attic, should the "ceiling" of the attic also be insulated?
There is a second vent that was installed with the alarm horn in front
of it, but it doesn't block the entire openning. I should also mention
that the attic is also used to store those things that we expect to
use again some day, but never will.
Charlie
|
25.51 | buy some roof holes at Spags | WEFXEM::DICASTRO | POST NO BILLS HERE | Mon Sep 11 1989 12:51 | 21 |
| re:50
The attic floor insulation is to keep the living space air , in the
living space. Insulating the underside of the roof accomplishes
nothing , as the heat is already lost (from living space) once it is
in the attic.
What you need to do is better vent your attic to exhaust the buildup
of heat from outside. This can be accomplished with end type vents.
Or with a ridge vent, or roof vent.
I lost an end type vent when I added an addition to the side of my
home. The attic got way to hot. So I added a roof vent. It is an
aluminum type w/ a rotating top. I bought it at Grossmans and it
has a lifetime gaurentee ( if the top is not spinning, its broke !)
The benifit of this type is that it is convection drivin. The heat
exiting the vent stack causes the top to spin and pull the heat out.
(No electric consumption) There are vent size calculations for attics,
it takes into account cubic footage etc. .
good luck/bob
|
25.168 | Whole house fan is dead | PAXVAX::ROURKE | Hi Ma! | Mon Jan 08 1990 12:56 | 12 |
| My Sears whole house fan (3 years old) has croaked. Sometimes, though, if
I turn it on and off (say 100 times) it will kick in and start and run
fine. (I have the "dimmer" type of control which puts the fan on high
as you turn it on, then you keep turning it to reduce the speed).
I believe there is a firestat in the circuit too.
Has anyone else had this problem? I don't have any electrical test
equipment to check the thing out (not that I would know what to do in
the first place...)
thanx..
|
25.169 | | NSSG::FEINSMITH | I'm the NRA | Mon Jan 08 1990 14:52 | 7 |
| It its wired like the one I had in my previous house, there are a set
of contacts within the motor for starting. Once its up to a specific
speed, a centrifugal switch transfers the current to the "run" winds.
Does your fan have a belt driven fan or is the motor on the same shaft
as the fan?
Eric
|
25.170 | No belts... | PAXVAX::ROURKE | Hi Ma! | Wed Jan 10 1990 08:18 | 8 |
| re:.58
The fan is on the same shaft. There are no belts.
Thanx....
Jack
|
25.171 | Eliminate the switch first | MAKITA::MCCABE | | Mon Feb 05 1990 18:28 | 10 |
| I would try taking the "dimmer type switch" out of the circuit,
just disconnect the power, remove the switch plate and switch
from the box, disconnect the switch and tie the switch leads
together with a wirenut. Have someone apply the power and see
if the problem is solved.
If you have multiple windings your fan will usually be a 2
speed or 3 speed type and you will have to check out each winding
individually. You may be lucky and have a defective switch.
Chris
|
25.172 | Belt vs. Direct Drive | SALEM::PAGLIARULO_G | | Sun Apr 01 1990 10:21 | 16 |
| Funny how things get dragged out. When this note started I was
going to put in a new fan. Now, after finishing the new roof and
multiple other projects I'm finally ready to do it.
I've got a couple of questions. Anyone know of any advantages of
belt driven fans over direct drive fans? Sears 30" belt driven fan is
about $60 more than the direct drive. Is it worth the extra price?
Also, the fans are made by Patton. Anyone familiar with them?
Some people have added dimmer switches to 2 speed fans. Does this
have any detrimental effect on the fan motor?
Thanks,
George
|
25.173 | | CLOSUS::HOE | Sammy's almost TWO! | Mon Apr 02 1990 11:14 | 8 |
| George,
Mounting the motor off center allows for noise isolation, gear
reduction so that the fan would turn slower for the higher (but
more efficient running) of the motor. Usually, industrial fans
are belt driven.
cal hoe
|
25.174 | | QUARK::LIONEL | Free advice is worth every cent | Mon Apr 02 1990 11:37 | 7 |
| Patton is a well-known maker of fans, and I've been happy with the Patton
fans I've owned.
The whole-house fan I installed years ago was a Sears direct-drive, and
I was happy with it. It varied its speed according to the attic temperature.
Steve
|
25.52 | Thermostat for Whole House Fan | SALEM::PAGLIARULO_G | | Fri Apr 13 1990 08:35 | 10 |
| I am waiting for my Sears (a Patton) whole house fan to come in.
I also ordered the thermostat and a firestat for it. Sears wants
about $45 for the thermostat. That sounds like a lot of money to
me but then again I haven't bought a thermostat before. Rather
than buy the Sears thermostat can I get a less expensive thermostat
at a heating supply dealer that can be used with the fan or is there
something special about a fan thermostat?
Goerge
|
25.53 | Pay the $45 | VINO::DZIEDZIC | | Fri Apr 13 1990 09:01 | 6 |
| Thermostats for the whole-house fans typically control the 120 volt
AC line directly. You CANNOT use (most) thermostats designed for
home heating use since they (most) are low voltage/low current units.
A thermostat for electric baseboard heating is probably not going
to work well as it doesn't have the higher temperature range that
the whole-house fan unit would.
|
25.175 | Hmmm! Mine seems to work ok! | MFGMEM::MICHAUD | Think about software that thinks! | Tue May 08 1990 13:29 | 17 |
|
-.2
That's funny, I just installed a 24" Air Master in the attic
opening and all I have are the two standard gable openings and
everything appears to vent fine. I also have *NO* soffit or ridge
vent openings either. In .2 something was mentioned about the air
being forced into the electrical outlets?? Seems to me that this kind
of thing would be difficult to do today. The only opening from the attic
to any electrical outlet is a whole big enough to pass the wire(s) through.
In any case...if things continue to run as they are right now, I'll
assume I have enough venting in the attic. BTW, I thought the
concept of a 'Whole House Fan' was exactly that, to cool the entire
house, attic and all! I open the slider in the basement and the fan
it draws the cool air upstairs into the living area quite well.
John
|
25.176 | | QUARK::LIONEL | Free advice is worth every cent | Tue May 08 1990 14:52 | 6 |
| I just tried the whole-house fan in my "new" (24-year-old) house, which
definitely has insufficient venting. There is quite a draft out of switch
boxes and outlets when it is running! On the to-do list this year is
a re-roofing which will include ridge and soffit vents.
Steve
|
25.177 | Fan running again! | PAXVAX::ROURKE | VAXELN worker ant | Wed May 30 1990 18:25 | 10 |
| re: .60
Thanx for the tip (5-Feb!) on bypassing the dimmer switch. The fan worked ok
with the switch bypassed. I bought a new dimmer switch ($40 at Sears,
talk about a ripoff!) and the fan is back 'on-line'.
Thanx again
Jack
|
25.54 | Who can fix my fan? | FSHQA2::DWILLIAMS | But words are things | Tue Jul 31 1990 11:19 | 15 |
| After searching through the Yellow Pages and spending too much
time on the phone I turn to Home_Work. I need to have the fan section of
our whole house fan repaired. Any suggestions in teh greater Maynard
area (Boston to Worcester)?
The fan section consists of the blades and a collar. The blades,
connected to each other at a common collar, fit over a collar which sits
on the motor shaft. The blade collar must be pressed on to the collar. The
collar is held onto the shaft with a set screw. My efforts to put this
mess together has always resulted in an unbalanced fan which resulted in
the blade section flying off.
Any assiatance will be greatly appreciated.
Doug Williams
|
25.266 | Whole House Fans and Oil Furnaces... | NECSC::ROODY | | Fri Jan 31 1992 16:19 | 32 |
| {sorry if this is covered in another note - I checked the dir and nothing
seemed to match - please move if needed}
We have a dilemma that nobody else seems to recognize (or admit to), and I'd
like to know if I'm worrying too much.
We are having a new house built, and one of the features being added is a
whole house fan; so far so good. Our dilemma is that the hot water system
is a tankless in-furnace unit, which means that to make hot water the
furnace comes on. Why is that a problem? Well, the whole house fan will
very effectively suck all those furnace gases back down the chimbley and
into our house. The obvious answer is to spend money and have a gas
or electric water heater hooked up for use during the fan seasons, but that
is expensive.
Does anyone have both a whole house fan and a furnace fired hot water
system? If so, can you detect any gases when both are running? Is there
something that can be done to keep the gases from being sucked in?
It won't be practical, or effective, to keep the basement door shut and a
window open, so that's out. Any other (inexpensive) ideas?
Thanks,
/greg
ps - we are already having the furnace thermostats wired so that the heat
cannot come on when the fan is running. This is an important safety tip
that anyone with a furnace and fan should do. It is very easy for the fan
to bring the house temp down below the thermostat settings, especially in
the spring or fall when you get warm days and chilly nights.
|
25.267 | It is something to think about | NICCTR::MILLS | | Fri Jan 31 1992 17:05 | 23 |
| You can directly supply air to the furnace through a seperate intake
directly from outdoors. In fact I've heard it is more efficient to do
so even in winter.
We have not had your setup but did have a attic fan. Where do you plan
to suck the air from, the cellar or the main floor. We never bothered
to get the air from the cellar because it was musty. The main thing the
the attic fan does is remove the heat from the attic and living space.
You don't really need to suck the air from the cellar and possible
cause the problem you describe. I also think if you supply enough air
input the presure of the furnace blower and heat will generate enough
to overpower the draw from attic fan.
Why would a standalone hot water heater be any better (it still has to
be vented)? In fact the setup of gas furnace and seperate gas hot water
(no attic fan) we have today would be even worse. Because the furnace
has a closed system exahaust to the chimney. And the hot water heater
has an intentional gap between the heater and vent pipe in which fumes
could easily be sucked from.
We did have a problem with a dryer vent next to a window that supplied
air into the house and we had to keep it shut when the fan was on.
|
25.268 | | WUMBCK::FOX | | Fri Jan 31 1992 17:12 | 13 |
| I don't understand how the fan will draw what's exiting the chimmney
into the house.
A WHF draws air into the attic, from whatever source is available.
If you have one window open in the house, and turn on the fan, the
air will be drawn from the outside, thru that window, and create
the air flow into the attic and out the vents.
Now if your house is shut tight, and turn on the fan, you might
get something like what you've described. Just don't turn on the
fan unless you have something open to the outside.
Btw, we have a WHF and a tankless WH. I've never noticed anything like
what you've described.
John
|
25.269 | | QUARK::LIONEL | Free advice is worth every cent | Sat Feb 01 1992 08:29 | 9 |
| I agree with John in .2 - my first house had a oil boiler with
tankless hot-water and I installed a whole-house fan. Worked
fine. But you're never supposed to run the fan unless you've
got sufficient air coming in through open windows, etc. If
the flue gases are being pulled in by the fan, either open more
windows or get the boiler /chimney repaired, as that shouldn't
happen.
Steve
|
25.270 | | DPDMAI::FEINSMITH | Politically Incorrect And Proud Of It | Sun Feb 02 1992 19:36 | 6 |
| I had the same setup in a prev house, and even with the downstair
windows open, I would occasionally generate a reverse draft by the
furnace. Just leaving a basement window open near the furnace seemed to
cure it when the fan was on.
Eric
|
25.271 | Moreinfo.... | NECSC::ROODY | | Mon Feb 03 1992 10:47 | 31 |
| re - all
I should have been clearer I guess. For various reasons we will not be
able to "seal" off the basement while the fan is running, and by
definition, even with windows open, the fan creates a negative pressure
in the house and air will flow in from all available points
proportionaly to its resistance. I can leave basement windows open,
but need to know at what point a downdraft will occur in the chimney.
The idea of a fresh air source is a good one; I'll look into whether or
not it can be installed on this furnace.
In any event, all theory aside, we have a WHF in our current house, and
I can still feel the sweat on my palms from the time we were awakened
in the middle of the night to the sound of every smoke alarm in the
house blaring. What happened was that it was a warm fall day and we
were using the fan and left it on when we went to sleep. Well, fall
being what it is here, the outside temp nosedived after midnight and
the fan very efficiently brought the inside temp below what our
thermostat was set at (somewhere between 55 - 58) and the heat came on.
Even with lots of windows open on two floors, and the fan not running
all that fast, there was enough smoke and CO in the house to stink the
place to high h*&&. It is interesting to note that the blocked-chimney
sensor in the furnace did not shut it off because the reverse air flow
did not allow it to recognize the problem. Now granted, the draft may
not have been the strongest in that flue, but it is not something I
want to lose sleep over for the next twenty years.
Thanks,
/greg
|
25.272 | | WLDBIL::KILGORE | DCU Elections -- Vote for a change... | Mon Feb 03 1992 11:26 | 9 |
|
> The idea of a fresh air source is a good one; I'll look into whether or
> not it can be installed on this furnace.
This can be done to just about any furnace -- just enclose it in a
more-or-less airtight closet (with appropriate cleareances) and supply
sufficient venting to it from the outside (specified in furnace
literature).
|
25.273 | | WUMBCK::FOX | | Mon Feb 03 1992 12:18 | 8 |
| The mention of a thermostat reminded me...
I put one in our set-up so the fan could be triggered by temperature,
and be able to leave it on without it running if the house got too
cold. That would solve your Fall night scenario.
This however wouldn't solve the issue where the furnace kicks in
for hot water. The outside source sounds like the best idea.
John
|
25.274 | Timer is a good idea also. | NICCTR::MILLS | | Tue Feb 04 1992 15:33 | 4 |
|
It might even be code. But I think it's a good idea anyway. To put a
timer on the fan.
|
25.275 | | WUMBCK::FOX | | Wed Feb 05 1992 09:01 | 6 |
| Why would it be required to have a timer on a fan (and not other
appliances (ac's etc))? The heat sensing shut off would be a
better code requirement. If the fan gets too hot, regardless of
how long it's been on, it'll shut off.
John
|
25.276 | It just seems right to have a timer | NICCTR::MILLS | | Wed Feb 05 1992 09:21 | 10 |
|
Lets say someone left it on upstairs and shut the windows down stairs
and left the house. The whole house fan needs the right conditions to
operate safely. Having a timer would prevent it from running in a bad
condition indefinetly. But I beleive the heat sensor (not a thermostat)
is code. For practical reasons it's great to put the timer on for an
hour and then go to bed. You really don't need it running all night.
Once the sun is down and the hot air is out of the attic and house it's
done most of the work.
|
25.277 | thermostat is better for us - ymmv | NECSC::ROODY | | Wed Feb 05 1992 10:15 | 14 |
| RE - note about a timer
We addressed this one through the use of a thermostatic cut off. When
the temp falls below a certain point, the fan shuts itself off. This
is a standard fan option, and is a no-brainer to install.
We have decided that the extra hot water tank isn't necessary after all
(esp with a 1k estimate) and we will either be venting the furnace to
the outside directly, setting up a circuit to turn off the fan when the
furnace is running, or both. That should do the trick.
Thanks for the ideas,
/greg
|
25.278 | You can still have a timer too | NICCTR::MILLS | | Wed Feb 05 1992 11:05 | 10 |
| You could use a 3 wire (heat/cool) low voltage thermostat. You would
have to put in a relay (for low to high voltage) which is easy to do.
You could still have a timer in series also. Having both (Timer and
Thermo) would be Ideal. Sooner or later AC or Heat will eventually
satisfy a thermostat. But an attic fan may never satify the setting and
run the whole night. But if you shut it off (after a certain point) it
won't get any hotter (you've already got everything out of the fan it
can give). Therefore your wasting electricity. Remember even though
traditionally AC cost more than a fan to run, that fan has about a 1/3
horse motor on it and is not cheap to run.
|
25.279 | | DPDMAI::FEINSMITH | Politically Incorrect And Proud Of It | Wed Feb 05 1992 16:51 | 5 |
| the hi-temp switch is to make sure the fan shuts off if there is a
house fire! You wouldn't want ther fan to go on because the house is
hot, because its blazing away, would you????
Eric
|
25.280 | | NICCTR::MILLS | | Wed Feb 05 1992 19:02 | 2 |
| That's a good point :-) Ooooh there's a fire lets turn on the FAN and
really get it going :-).
|
25.281 | ex | ELWOOD::DYMON | | Wed Feb 12 1992 11:53 | 3 |
|
Why do you just make the fan run slower????
|
25.178 | one of those year long projects... | SNAX::HURWITZ | | Thu Jun 11 1992 05:26 | 34 |
| Well I've read all the notes and replies on whole house fans and feel
pretty confident I can handle this most extensive (to me)
project...(well I need a ridge vent, needed new 200amp service anyway
might as well be now since I maxed out the existing panel, and so on...)
Anyway I'd just like to know about those "portable" whole-house fans,
which sound like just a Tim Allen turbo-powered window fan you stick in
the far end of the house and suck the staples out of the carpet
padding, the kids need to be tied down, etc...
I need to move 900�ft of living area from what I understand 2x a minute
for the New England area (from a DIY book I read) so I will need a whole
house fan around 2000cfm.
But for now I'd like to get recommendations on a window mounted
powerful whole house "exhaust" fan. I don't just want a window fan but
one that'll at least move 1000cfm and isn't that expensive (both to buy
or operate), until I get the real whole house fan installed.
I need one that'll fit in a 12" high opening too. I was tempted to just
buy a Holmes-air side-by-side double fan that can both exhaust and blow
in on sale for about 40.00 but I really don't feel it'll be able to
handle much more than 1 room. Again I only need to cool 5 rooms, about
900�ft. I plan on putting it in the kitchen and opening the bedroom
windows at night and visa-versa in the daytime.
Any recommendations? Should I just wait until the real one is in and
not bother pursuing this exagerated window fan? I was thinking I could
use it in the bathroom window when I put the real W.H.F. in , since we
don't have a bathroom exhaust fan now (yet)...or maybe not (don't know
if it could handle the moisture)
thanks.........Steve
|
25.179 | Incremental cost? | DEMON::CHALMERS | NOT the mama... | Thu Jun 11 1992 11:13 | 31 |
| Steve,
I'm in a similar situation where I'm planning to install a whole house
fan at some point during the next few weeks. In the meantime, what I've
been using is a 18" high velocity fan (either Patton or Holmes, don't
recall) to exhaust warm air from the house at night while drawing
cooler night air into the house in whichever rooms we've left windows
open. It's portable, and needs a flat surface to rest on. In previous
years, I'd set it up on the floor of the dining room and have it
pointed thru the open slider. However, due to security concerns I now
rest it on a small table set in front of an open window at the high end
of the house. The 18" fan does a great job of cooling down 2 bedrooms
(4 windows total, each open approx 8-12"); it'll do a so-so job of
cooling off three rooms (6 windows), and seems totally useless on any
larger area.
In my situation, I've had the fan for a few years, long before I
considered installing a WHF, so it's a good temporary fix with no
incremental cost. Expect to spend at least $50 for such a portable fan,
or even more if you want one with higher capacity or more bells &
whistles. A whole house fan will set you back anywhere from $120-$200
depending on size/type/model, so the $50+ incremental cost associated
with buying the 'temporary' fan may become a factor.
How long before you expect to install the WHF? If it's a matter of
weeks, you may want to wait. Then again, if we get a hot/humid spell
in the meantime, the incremental $50 might seem like a bargain...:^)
Good luck with your decision.
Freddie
|
25.180 | | WMOIS::MAY_B | IT'S LIKE THE SAME, ONLY DIFFERENT! | Thu Jun 11 1992 14:13 | 1 |
| What your going to miss with a w
|
25.181 | bot that really _would_ have sucked the fiber out of the carpetting | SNAX::HURWITZ | | Thu Jun 11 1992 14:19 | 16 |
| Well it's like one of those usuall planning problems on the time limit.
I'd like to get estimates on upgrading my 100amp service to allow for a
dedicated breaker for the W.H.F. (and fix the overloaded existing
panel), I've got to install a ridge vent, and go shopping around
for a W.H. fan and so on. It may take all summer to complete this project
due to the other things I'm going to do in the preparation for it.
(I may just do the whole roof while I'm putting up the ridge vent).
Also f.w.i.w. I checked back in that d.i.y. book and my calculation was
backwards. I don't need a 2000cfm fan for 900�ft, I need a 450cfm fan
according to the diy book, for the New England area. That's not much
and it may just pay to put in the ridge vent and just do the portable
high power window fan instead. We'll see (and it'll surely save alot
of money and time)...
Steve
|
25.182 | Make a good cross breze... | ESKIMO::CASSIDY | Aspiring conservationist | Fri Jun 12 1992 02:10 | 40 |
|
First off, 24" WHF at Grossmans this week (and perhaps next?)
for ~$110.00. I don't know if this has a louvre. The one I bought
at HQ (don't bother asking for help) had a louvre but was just over
$125.00.
Window fans warm up your house when run during the day. Many
people don't appreciate this fact, so please don't be offended.
They draw the warm outside air into your (hopefully) cool house.
The idea is to run cool nightime air through your house and then
to trap it inside during the day.
Window fans also create a breeze that helps cool your skin.
I feel that ceiling fans do this better and with a whole lot less
noise. This is more or less a wind chill/evaporation (of perspi-
ration) effect. The cooler the air is to begin with, the more
refreshing the effect.
You might want to consider getting two window fans if you're
not going to get a WHF. (I think the WHF works great. I don't own
stock in the company.) With two fans you would be better able to
force a cross breeze throughout your house. With just one fan,
only one room would receive the benefits of the fan. Try to make
sure they're working with each other. Something like this:
closed
+------------------+----====---------------------
| | | |
Fan | | | |
��� >> | |
��� >>> | ���
| | >> | ���
| | ��� |
|------------------+ ��� |
| | | |
Fan | | >> | ���
��� >>> | ���
��� >> | |
| | | |
| | | |
+------------------+----=====--------------------
closed
|
25.183 | Another configuration & more advice | DEMON::CHALMERS | NOT the mama... | Fri Jun 12 1992 10:15 | 25 |
| Re: -.1
I agree with the concept, but my execution is a little different than
yours. I set up the fan at the 'non-bedroom' end of the house and have
it blowing out. I close all windows except those in the two bedrooms
we wish to cool off. The cool night air is drawn in thru these bedroom
windows to replace the warm air being blown out at the other end of the
house. The advantage I gain is twofold: I can cool down two rooms using
only one fan; and the fan noise doesn't bother us as much as if it was
in our room.
Re: WHF in general
Remember, too, that the WHF not only will draw in cool night air, but
will also, in combination with proper venting, force the hot air out
of the attic. This action will also help make the house feel cooler.
Temps in a poorly ventic attic can reach 150 or so, which is sort of
like having an electric blanket draped over the house. An attic that
is well-vented won't get as hot, and will make it easier to dissipate
the heat that builds up in the house. In combination with a WHF, it
becomes even easier to keep things cool.
Again, good luck with your project.
Freddie
|
25.184 | ridge vent and insulation might just do the trick w/o WHF | SNAX::HURWITZ | | Fri Jun 12 1992 19:05 | 15 |
| re: last 2... thank guys
We bought one of those Holmes dual 8" fans from Caldor on slae for
40.00. Either fan can be switched for intake or exhaust independently.
Well the thing works good, but isn't going to cool the house down at
night. Just not strong enough, but a nice fan anyway. Caldor also had
a free standing fan from hell that moved over (I think) 25,000 cfm.
I bet it's noisy though! We didn't get that one. I'm going to try to
pick up a ridge vent this weekend and judge if we even need a WHF after
it's been installed for a few weeks. I noticed that the house stayed
fairly cool for quite a while this morning and probably would have
stayed even cooler had I not opened up the windows and let the outside
hot air in. Now I know better.
Steve
|
25.185 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Mon Jun 15 1992 10:37 | 3 |
| re .73:
25,000 cfm? Are you sure it's not 2500?
|
25.186 | Portable 24" fan | SNAX::HURWITZ | | Mon Jun 15 1992 19:14 | 4 |
| Nope. The box said 25,000. In fact they are on sale this week for
about $50 at Caldor.
Steve
|
25.187 | scale factor hidden? | TARKIN::BEAVEN | Dick BXB2-2/G08 293-5074 | Tue Jun 16 1992 08:20 | 4 |
| Maybe it's CFH? (Cubic feet per hour - looks impressive 'til
you divide by 60!)
Dick
|
25.188 | Wind tunnel | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Tue Jun 16 1992 09:55 | 2 |
| A 25,000 CFM fan in a 3000 sq.ft. house with 8 foot ceilings could do an air
exchange every minute.
|
25.189 | Not exactly a wind tunnel... | XK120::SHURSKY | What's the "reorg du jour". | Tue Jun 16 1992 13:10 | 2 |
| If you push 25000 CFM through a 24 inch square fan, the exhaust air speed
should be 71 mph. A stiff breeze none the less.
|
25.190 | | CREATV::QUODLING | OLIVER is the Solution! | Tue Jun 16 1992 18:50 | 4 |
| Good enough to put parts of your roof, into a low orbit...
q
|
25.55 | Which way to go and how effective. | RESYNC::D_SMITH | | Tue Jul 28 1992 11:45 | 15 |
|
Some good tips here, as far as cut-off, thermostat control, and gabel
venting. I NEED to install attic venting. I would like a draw thru the
attic system, taking air from the cool side of the house and expelling
it out the hot side. Studs are 24" on center, which pretty much limits
my fan size unless I cut and reframe (TIME?). Attic is 1600 sq ft. 58' x
26'.
Any idea on fan RPM's or blade angle for max. CFM? Would I be better
of with a roof fan drawing thru both gabel vents?
Any further experience and info much appreciated!!!
Dave'
|
25.56 | How do I quiet the shutters on the fan? | LEDS::SIMARD | just in time..... | Thu Jul 30 1992 10:22 | 10 |
| WE put in an attic fan last year and haven't had to use the a/c yet
this year although, that might not mean much since it hasn't been hot
enough to use it.
My question is how do I stop the rattle of the shutters? The fan is
quiet, it's the shutters that keep us awake at night!
Thanks in advance
Ferne
|
25.57 | A possible alternative... | LUDWIG::CASSIDY | Aspiring conservationist | Fri Jul 31 1992 07:58 | 12 |
| > My question is how do I stop the rattle of the shutters? The fan is
> quiet, it's the shutters that keep us awake at night!
You might be able to get away with running the fan on high
for about an hour (or so) and then turning it off when you go to
bed. The house should be cool enough for you to sleep comfort-
ably by then. It works for us.
You can run it again in the morning and then turn it off
before you go to work.
Tim
|
25.58 | Could central air be used as whole house fan? | STAR::VANDENHEUVEL | Cherish the bug you know. | Wed Jun 16 1993 01:39 | 19 |
|
Our Nashua split has Central Airconditioning which is quiet pleasant
on the hottest of days. On merely 'warm' days we try using it in 'fan'
only position but that just stirs the air a little.
It would seem better to suck the warm air out of the house.
Well, we have the vents, the ducts and a fan in the attick
all in place... for the airconditioning.
If I could just switch the outlets to suck and redirect the fan
air outlet into the attic (or outside?)... would it work?
would it be worth it? It would require several serious sized
air valves. An idea worth pursueing or plain crazy? Should we
simply go for a standard whole house fan?
Thanks,
Hein.
|
25.59 | What's easier/cheaper??? | STRATA::CASSIDY | | Wed Jun 16 1993 03:39 | 14 |
| > -< Could central air be used as whole house fan? >-
It sounds like a complicated and expensive route to go. A
24" W.H.Fan runs around $130.00 and is fairly easy to install.
That would be big enough for a small to medium size split level
ranch. Either way, you need plenty of ventilation to exhaust
the air you blow into the attic (I need more ventilation).
Another option might be to install an intake vent in the
cellar ductwork. You could draw the cool cellar air and distri-
bute that throughout your house. A couple of paddle (ceiling)
fans to create some wind chill would make the air feel even cooler.
Tim
|
25.60 | From "Fan in the attic" to "Fan in the basement" | HDLITE::NEWMAN | Chuck Newman, 297-5499, MRO4-1/H16, Pole J13 | Wed Jun 16 1993 10:29 | 14 |
| � Another option might be to install an intake vent in the
� cellar ductwork. You could draw the cool cellar air and distri-
� bute that throughout your house.
I had been thinking of doing the same thing by opening up the cold-air return in
the basement and taping over the upstairs return ducts, then turning on the
furnace blower.
I had one concern, and that's concerning the dehumidifier in the basement. Will
I be helping things by bringing in warmer outside air (that has a lower relative
humidity), or causing problems by bringing in outside air that is full of
moisture just waiting to cool off and make my basement more damp?
-- Chuck Newman
|
25.61 | More Power!!!! | SSGV01::CHALMERS | More power! | Wed Jun 16 1993 12:34 | 11 |
| RE; .58
I second .29's suggestion to go with a seperate whole house fan, rather
than piggy-backing off the A/C system. However, rather than the 24" fan,
spend the extra $20-$40 and get the 30" model. Installation is just as
easy (or complicated, depending on your point of view) as the 24", but
you'll have a tremendous increase in capacity, and will be able to cool
off more rooms at the same time.
We've got a 42 x 26 split, and use a 30" Delta belt-drive (2 speed).
Even on the hottest nights, we wind up needing our blankets...
|
25.62 | Keep it cool... | STRATA::CASSIDY | | Thu Jun 17 1993 01:33 | 17 |
|
> concerning the dehumidifier in the basement. Will I be helping things by
> bringing in warmer outside air or causing problems by bringing in outside
> air that is full of moisture just waiting to cool off and make my basement
> more damp?
I leave my cellar windows open most of the time to keep the
moisture and damp, musty smell down. It's a lot cheaper than
running a dehumidifier, although, probably not as effective.
Besides, I don't own a dehumidifier.
Since you have one, your cellar should have plenty of cool
dry air. If you leave the house buttoned up and circulate this
cool dry air throughout, I would imagine you'll keep the house
comfortably cool but less expensively than running A/C. You'll
just have to drain the dehumidifier more often.
Tim
|
25.63 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Thu Jun 17 1993 12:22 | 9 |
| > Since you have one, your cellar should have plenty of cool
> dry air. If you leave the house buttoned up and circulate this
> cool dry air throughout, I would imagine you'll keep the house
> comfortably cool but less expensively than running A/C. You'll
> just have to drain the dehumidifier more often.
I'm not sure if I follow this, but... A dehumidifier is basically the
same as an air conditioner. If (and I emphasize "if) you run the
dehumidifier as much as you'd run the A/C, you're not saving anything.
|
25.64 | Not that I plan to get one... | STRATA::CASSIDY | | Fri Jun 18 1993 04:58 | 15 |
| > Since you have one, your cellar should have plenty of cool
> dry air. If you leave the house buttoned up and circulate this
> cool dry air throughout, I would imagine you'll keep the house
> comfortably cool but less expensively than running A/C. You'll
> just have to drain the dehumidifier more often.
>I'm not sure if I follow this, but... A dehumidifier is basically the
>same as an air conditioner. If (and I emphasize "if) you run the
>dehumidifier as much as you'd run the A/C, you're not saving anything.
I was going under the assumption that the dehumidifier was
going to be run, either way. I know, one shouldn't assume.
Does a dehumidifier cost as much to operate as A/C?
Tim
|
25.65 | | QUARK::LIONEL | Free advice is worth every cent | Fri Jun 18 1993 10:36 | 9 |
| Actually, a dehumidifier could end up costing more, since there isn't any
requirement to put energy usage labels on dehumidifiers and there's less
inclination to build in energy-efficient features. But dehumidifiers also
tend to be "small", so consume less power than even a small room air
conditioner would. Really, a dehumidifier is just an air conditioner which
blows the cooled air past the condensor coils to rewarm it before returning
it to the room.
Steve
|
25.66 | Another thing about dehumidifiers | CADSYS::FLEECE::RITCHIE | Elaine Kokernak Ritchie | Fri Jun 18 1993 11:02 | 13 |
| The dehumidifier you have may not be able to handle the extra moisture. Each
one has a different "capacity", which is the number of pints of water it can
extract from the air in a 24 hour period. Note that this is different from the
size of the bucket. So say yours is rated for 18 pints. If you put it on MAX,
it will run 24 hours a day, and if there is enough moisture, it will remove
18 pints. If you need to remove 20 pints a day to keep the R.H. at 55% in
the basement, you won't be able to do it.
Also, I don't think the buckets of dehumidifiers hold as much as their rating.
So if you ran in 24 hours a day, you'd have to empty it more than once a day,
or rig up a drain hose.
Elaine
|
25.67 | | HDLITE::NEWMAN | Chuck Newman, 297-5499, MRO4-1/H16, Pole J13 | Fri Jun 18 1993 12:13 | 6 |
| I'm just looking to take the bite off the summer temperature in the house for the
wife and kids. Our humidifier drains into the washing machine (when we aren't
doing clothes), and easily keeps up with its current load. I'll try circulating
the basement air as soon as I get my wood furnace blower motor checked out.
-- Chuck Newman
|
25.191 | Whole house fans again? | CALS::HEALEY | DTN 297-2426 | Wed Jul 21 1993 14:18 | 29 |
|
Time to revive this topic...
After the recent heatwave, which I was absolutely melting in, I
started thinking about a whole house fan. My father is a building
contractor so he knows a little about them and he suggested just
putting in fans in the attic windows.
I'm not convinced that this would be sufficient. How much cooler
would this make the house when one arrives home from work? We
keep the house closed up during the day so would it allow the
house to remain cooler during the heatwave than outside? Usually,
our closed up house is cooler, at least downstairs, but during
the heatwave, the whole house got hot!
And, if we do decide to go for the whole house fan, after investing
in attic fans, have we wasted the money spent on attic fans?
Additionally, the attic is accessible from a pull down ladder
in the hallway. I guess the fan could go there and an earlier
reply to this note drew a diagram showing how to do that but
I couldn't figure it out. Anybody tried doing that for their
home?
Finally, about how much in todays dollars would such a project
cost, assuming we can do most of the work ourselves, except the
electrical?
Karen
|
25.192 | Big difference | LANDO::OBRIEN | Give it a TRI | Wed Jul 21 1993 18:38 | 10 |
| We have both a gable fan(attic fan-just for attic air movement) and a
house fan(exhausted into the attic). The gable fan definitely makes a
big difference during the day. The house fan should really only be run
when the temp outside is cooler than the inside(ie/ pull cool air in
and out through the attic). The gable fan keeps the attic from
becoming a heat sink.
Good luck.
-John
|
25.193 | | MSBCS::PAGLIARULO_G | Reality is a cosmic hunch | Thu Jul 22 1993 08:49 | 10 |
| I agree with the last reply. I put a whole house fan in about 3 years
ago. If we ran it during the day it would actually make the house
hotter by pullng in the warmer outside air. But I can live with heat
during the day. It's in the evening that the fan really makes a
difference. On those hot muggy, nights we usually need to get up and turn
the fan off at some point (it has a thermostat on it but it doesn't seem
to work correctly and I haven't bothered to check it out yet.). It really
cools things down. I consider it one of the best improvements I've made.
George
|
25.194 | wiring an attic fan | SMURF::WALTERS | | Thu Jul 22 1993 09:46 | 9 |
|
re: last two
What are the wiring requirements for these? At a pinch, could they be
wired in to the existing 15 amp lighting circuit (feeds 1 bathroom
overhead light and two bathroom vanities).
Colin
|
25.195 | | VERGA::WELLCOME | Steve Wellcome PKO3-1/D30 | Thu Jul 22 1993 10:31 | 7 |
| re: .83
I just put one in; the motor draws 4.5 amps or something like that,
so it should be okay to hook it into a lighting circuit. (Of course,
if you get a BIG (!) fan that has a 1hp motor or something, that would
be a different story, but I expect most anything you get will be in
the 4-5 amp range.)
|
25.196 | | SOLVIT::CHACE | My favorite season is getting nearer! | Thu Jul 22 1993 10:34 | 9 |
|
Yes, the attic gable fan is readily available at most home centers
around NE and sells for about $35. It comes with a setable automatic
thermostat and fire cutout switch. They are easy to mount and can be
used on any normal 15 amp circuit as long as you don't have too much
else on it. My guess is that they draw about 1.5 amps max. They make
a BIG difference in attic temps which really helps the upstairs.
Kenny
|
25.197 | | SOLVIT::CHACE | My favorite season is getting nearer! | Thu Jul 22 1993 10:36 | 8 |
| re .84
Steve, are you talking about a whole house fan or one of the small
(Maybe 1 foot diameter) gable fans?
(My reply in .85 is regarding an attic gable fan)
Kenny
|
25.198 | Some are noisy too | 18889::MASSICOTTE | | Thu Jul 22 1993 10:54 | 26 |
|
A neighbor installed a big one in the 2nd floor ceiling at the top
of the stairs from the living rm. and added gravity dampers in the
attic wall. When the fan started the dampers opened. We knew when
he started it for the TV volume would increase. His was very noisy
and the placement didn't help. Suggest if you go with a big one,
put it in the outside wall in the attic, be sure it has good resilient
mounts also see about having about a 3 or 4 foot section of ductwork
attached to the inlet and line it with egg crate type foam. That'll
stop any noise comming back in.
Have it on a thermostat. Nothing worse than getting up in the morning
and finding out the conditions changed outside to FOGGY and the whole
interior of your house is damp.
If you know an HVAC tech or mechanical engineer, ask him/her to explain
"ENTHALPY" to you, and mention what your doing. It'll be a BIG help.
Those fans bring in everything; pollen, neighbors cooking odors,
lets you know when "pepe le-pew" is around, and anything else thats
airborne. Screens catch'ell too..
They do work good up to a point.
Fred
|
25.199 | Ta | SMURF::WALTERS | | Thu Jul 22 1993 12:34 | 9 |
|
Thanks - I'mn thinking about a gable fan, so it should be a small
motor.
Colin
(If I can't find a gable fan, would a betty davis fan do?)
|
25.200 | more info please? | CALS::HEALEY | DTN 297-2426 | Thu Jul 22 1993 13:26 | 12 |
|
Re: gable fan...
Are these supposed to go in the attic window or are you supposed to
cut a hole in the outside wall for them. We don't have a louvered vent
in the peak of our roof. Would a window suffice?
How do you keep them dry in the rain (if it blows in)?
Karen
|
25.201 | | VERGA::WELLCOME | Steve Wellcome PKO3-1/D30 | Thu Jul 22 1993 15:34 | 3 |
| Re: .86
I'm talking about a whole-house fan in .84.
|
25.202 | | SOLVIT::CHACE | My favorite season is getting nearer! | Thu Jul 22 1993 15:40 | 10 |
|
If you mount a gable fan inside on the gable vent, rain isn't a
problem. If you have it in a window, it defintely can be a problem. If
the fan is on, it will keep the rain out by the air blowing out, but
the %90 of the year when it is off will be a different story. The fan
will likely only last a few years like that. Also, if you mounted it in
a window, you will likely have to make up some sort of plywood with the
right size hole in it that will fit in the window opening.
Kenny
|
25.203 | will attic fan dry hair?? | SALEM::LAYTON | | Fri Jul 23 1993 12:56 | 6 |
| In regard to adding to the existing bathroom circuit, realize that when
the non-follically challenged of your household turn on the hair
blowers and dryers you'll likely trip the breaker. How about one of
the bedroom circuits?
Carl
|
25.204 | quick & dirty wiring? | SMURF::WALTERS | | Fri Jul 23 1993 14:36 | 19 |
|
-1
There are only lights on the circuit that I'm planning to use.
The outlets are on a separate GFI-protected circuit.
Looking at the circuit last night, would it be terribly sinful
to wire the fan INTO a light box so that the fan could be isolated
by an existing switch in the bedroom? The light box is one that is in
a closet, and I could replace the existing lampholder with one
that has a pull-cord. That way I can control the fan & the light
independently (except that the fan would have to be "on" to get the
light - no big deal.)
This would give me a really simple wiring solution.
Colin
|
25.205 | whole house vs attic fans | TFH::DONNELLY | Take my advice- Don't listen to me | Fri Jul 23 1993 14:38 | 21 |
| having installed both (in separate instances) i have to comment on the choice
between attic fans versus whole house fans.
attic fans (1 foot or so diameter) are for power venting the attic. this is
in case your attic is getting so hot that you are worried about your roof
shingles melting off. the only benefit to the living space is reducing the
slight amount of added radiation heating from a hot ceiling on an already hot
day.
whole house fans (big 24 to 36 inch) are for moving 2000 to 7000 cubic feet
of air per minute through your house for cooling. they work great as soon as
the outside temperature starts dropping in the evening. they work ok even on
hot days by providing a breeze when you've given up trying to stay cool by
keeping the house closed up.
the two are not very similar at all. there are situations that require attic
fans and different situations that require whole house fans; in my opinion
there are no situations that present you a choice between the two.
regards,
-craig
|
25.206 | Wiring should make sense | NOVA::SWONGER | Rdb Software Quality Engineering | Fri Jul 23 1993 16:47 | 18 |
| > That way I can control the fan & the light
> independently (except that the fan would have to be "on" to get the
> light - no big deal.)
Well, depending on your point of view it may not be "terribly"
sinful to wire something this way, but just imagine what you'd be
thinking if you bought a house and found things wired like that.
You'd probably think, "whoever did this was a real hack - couldn't
they put in the effort to do it right?"
Depending on how the light is wired, you might be able to isolate
the light from the switch, and leave it controlled by just a
pull-cord. If not, then I personally wold just put in the separate
switch for the fan. I find that I rarely regret doing things the
right way (thought I often regret not getting around to doing
something until I have the time to do it the right way!).
Roy
|
25.207 | fan? what fan?n u | SMURF::WALTERS | | Fri Jul 23 1993 17:49 | 8 |
|
Good point, but the hack would allow me to deinstall the
fan in a few minutes, thus removing the evidence of sloth.
Oh well, I need a light and an outlet in the attic anyway,
might as well do it right. Next year.
Colin
|
25.208 | More Support | CTHQ::DELUCO | height impaired | Wed Jul 28 1993 13:55 | 28 |
| Just to add to some comments a few back re whole-house fans....
I've had one for about 10 or 15 years now and consider it one of the
best investments I've made. It's installed in a gable end of the
attic, is about 36" in diameter and came with a timer and variable
speed. Since the fan and motor are @15 feet from the hall ceiling vent
there's virtually no noise transmitted to the living quarters.
I did see one installed with the fan and motor attached to the hall
ceiling vent and it was extremely noisy. I wouldn't recommend this.
Also as mentioned earlier and as common sense would imply, the best way
to use this on a hot day is to draw cool air into the house using the
fan at about 6 am; shut all windows and pull drapes reasonably closed
to keep out hot air and hot sun; when the temp inside exceeds the temp
outside, open windows, etc. and turn the fan on to bring the cool air
inside. In my opinion, this technique is far cheaper and more
comfortable than using air conditioning.
The drawback is that this doesn't dehumidify the air at all and pulling
in really humid air does little to cool you off...but it does create a
breeze.
You also have to be careful to not leave the boiler room door open when
operating the fan, else the exhaust draft is pulled into the house.
Jim
|
25.282 | Wiring a whole house fan | 58323::KOZAK_A | | Mon Jun 06 1994 11:41 | 32 |
| --Wiring a Whole House Fan--
On Saturday, a friend and I put in a whole house fan, not too bad, but
extremely hot.
However, when I went to wire the thing, I found that I am not as
familiar as I thought I was. I need some help wiring if
anyone can. Here is the situation:
1. I have three strand ROMEX, Hot, Common, and Ground, but here is the
wiring diagram:
2 Speed
Switch HIGH |-----------
--------- (Black) | |
|1 2 |--------------| |
| | LOW | MOTOR |
| | (Red) | |
115 V Power Supply|L 3 |--------------| |
------------------|________| | |
Black | |
| |
------------------------------------------|----------|
White (Common)
I appreciate any assistance.
Andy Kozak
|
25.283 | | WLDBIL::KILGORE | Remember the DCU 3Gs | Mon Jun 06 1994 12:09 | 25 |
|
This should be wired as:
14/2 romex 14/3 romex
supply ============== wall ============== fan
switch
Alternately:
14/2 romex 14/3 romex
supply ============== fan ============== wall
switch
(In the latter case, I believe you can use the white wire from fan to
switch as the supply feed, and the black and red as switched returns to
the fan; just "color" the white wire black in the boxes. Consult your
local code. )
If you'va already run 14/2 all over the place -- well, maybe you can
use it to pull the right cable :-)
|
25.284 | | WLDBIL::KILGORE | Remember the DCU 3Gs | Mon Jun 06 1994 12:10 | 4 |
|
Oh, by the way -- why don't we move all of this to an existing
electrical note...
|
25.209 | Comments/questions | VICKI::DODIER | Single Income, Clan'o Kids | Tue Jul 12 1994 15:46 | 27 |
| After reading through these notes and other material on the subject,
I've come to the conclusion that the belt-drive unit is the way to go.
This was due to slower motor speed (via pulleys) that should result in
more durability and less noise.
For me, it might not be something I have a choice in the matter
on. The 30" units I saw were rated for use with 2100 sq. ft. houses. I
have a 2400+ sq. ft. house which would require at least a 36" fan. All of
the 36" fans that I've seen are belt-drive units anyway.
Re: Mounting in the gable
I have a question about this. I have a continuous ridge vent and
although mounting in the gable would reduce the noise transmitted to
the living quarters, wouldn't it also reduce the effectiveness ? What I'm
afraid would happen is that negative air pressure would be created in
the attic by the fan, which would suck warm air in through the ridge
vent. If true, this would significantly decrease the volume of air pulled
up and through the upstairs hall louver/vent.
If I mounted it in the upstairs hall ceiling, I would think it would
draw much more air volume from downstairs (which I assume is the whole
point) and create a positive air pressure in the attic to push the heated
air out through the ridge vent. Am I missing something here or this the
recommended installation for homes with ridge vents anyway ?
Ray
|
25.210 | | MAY30::CULLISON | | Tue Jul 12 1994 16:24 | 49 |
| What you stated is true far as I know. Only way to mount in gable
end and get the same airflow threw house is if no other vents in
attic which would not be desired anyway or you ran ducting from
opening to house to fan itself, big hassle.
Also I would guess there would be a good chance that the louvers
in the ceiling opening may not open properly when fan starts up if
mounted in gable.
Another way to lower noise but more expensive would be to use
a squirrel cage blower. They can move a lot of air with much less
noise. But they are not typically sold for this application.
One thing I thought about myself was an installation where the blower
is on floor of attic near the hole at 90degrees with homemade ducting
to it. could eliminate some or lot of the noise ?? See below.
More work than ceiling mount shoud reduce noise some, how much I
do not know. Ducting would not have to go to gable end itself, just
go into attic, that helps to cool attic anyway.
maybe3-5' insulate inside to reduce noise
-----------------------+ especially here
| | |
f | <--------
towards <--- a |
gable n |
end | |
--------------+ |
| |
| |
attic floor-------------------+////////+-----------------------------
36" opening
Note, I have an old belt drive model and it really makes a racket
because the belt is too loose and cannot be adjusted anymore.
I need a new belt, but quess what, all the people selling fans
don't bother to sell belts. My suggestion is make sure you can order
more belts and go ahead and order one for future use. I would just
wrap it up tightly in plastic and leave in attic near fan. I know
I can get one for mine but do not have lots of time to search all
over kingdom come for the stupid thing. Getting one for a few bucks
now may save you a big hassle in future when fan belt goes and
no one sells your 20 year old fan anymore.
Harold
|
25.211 | V-belt ? | VICKI::DODIER | Single Income, Clan'o Kids | Wed Jul 13 1994 08:36 | 11 |
| re:belt
Is it a V-belt, like that used for car fan belts ? If yes, any
automotive parts store can match it if you bring the old one in.
Also, was the unit always real noisy or was it significantly
quieter with a tight belt ? I'm not expecting a whisper quiet fan.
The sheer size of the fan blades alone is enough to let you know there
will be some noise. Nature of the beast I suspect.
Ray
|
25.212 | | MAY30::CULLISON | | Wed Jul 13 1994 10:10 | 19 |
| I bought the house with the fan already there. The noise is due
to the belt being too loose, and adjustment is at limit. I know
I can find one, but right now it is not important because we installed
central a/c anyway. I would assume that unit's original noise
was only from blades themselves. I just brought it up to say why
not get an extra belt for future when it is easy instead of
having to search around later.
Speaking of blades, depending on design of blade you could have
two different fans with same capacity to move air but drastically
different noise level due to blade design. Out in arizona old
homes used the old swap coolers (evaporative coolers), most
had squirrel cage blowers, even though they push on average 2 or
3 times more air than a typical 36" whole house fan they made
much less noise. Of course do not think about an evaporative cooler
in humid east, if you did you would really know why they are
called swap coolers.
|
25.213 | | LEEL::LINDQUIST | | Wed Jul 13 1994 10:44 | 4 |
| �� in humid east, if you did you would really know why they are
�� called swap coolers.
I thought it was 'swamp' coolers.
|
25.214 | Thanks, any pointers ? | VICKI::DODIER | Single Income, Clan'o Kids | Wed Jul 13 1994 13:58 | 16 |
| re:101
Thanks for the note on the evaporative coolers. I've seen them
before and wondered why they weren't used out here. After reading your
note, it makes sense why they don't. Probably hard to have effective
evaporation when the humidity is 80% and up.
The squirrel cage blower also sounds like a neat idea. I wonder why
you don't see more of them as whole house fans ? I took a glance
through my Northern Hydraulic and Harbor Freight catalogs and didn't see
any squirrel cage blowers. Any idea where I can find one large enough
to equal or exceed the CFM of a 36" standard fan ? Just seems strange
though if they can make a smaller quieter package for the same (maybe
less) money that they wouldn't be common place .?.
Ray
|
25.215 | never was an ace at spelling | MAY30::CULLISON | | Wed Jul 13 1994 14:25 | 18 |
| swap/swamp, my mind is going. The evap coolers require extremely
low humidity to work well. You use to be able to buy evap
coolers from sears. I think the main reason you do not see a whole
house fan with squirrel cage is they would cost more, seems like
everyone wants to get whole house for real cheap.
I thought one time of using evap cooler with no water hookup, just
as a blower. But they are so different it would require all sorts
of modifications.
I think a standard fan will be fine for you. If you have more than
one to choose from then see if they have any noise specs to go with
it. A two speed is nice also, once house is cool the low
speed keeps it cool and reduces noise to very little.
Harold
|
25.216 | do they really cool during a heatwave? | NAPIER::HEALEY | M&ES, MRO4, 297-2426 | Thu Jul 14 1994 09:19 | 15 |
|
Are these whole house fans really worth the money? The only
time I'm really uncomfortable in the summer is during a heatwave
when the air outside is as hot as inside. The rest of the time,
I put fans in the windows that do the trick quite well. One of
the fans is a "whole house air circulator" that cost about $50
at Walmarts and claims to be 10 times stronger than ordinary
box fans. Its great! Cools off a hot room in seconds.
So... how good are these whole house fans in a heat wave? Will
they bring up the cool basement air if you don't open any
windows? We have a 2 story, 4 bedroom colonial.
Karen
|
25.217 | | QUARK::LIONEL | Free advice is worth every cent | Thu Jul 14 1994 10:49 | 9 |
| They don't do much good if the outside air is unbearable. What they can
do is bring in cool air from the outside in the morning or at night, cooling
off the house (and attic) which will make it stay cooler during the day.
You MUST allow outside air to enter when using a whole-house fan, or else
you create a very dangerous situation that can cause boilers and furnaces
to kill you.
Steve
|
25.218 | | NETRIX::michaud | Jeff Michaud, PATHWORKS for Win. NT | Thu Jul 14 1994 11:43 | 18 |
| > You MUST allow outside air to enter when using a whole-house fan, ....
And not only that, you'll basically get the same situation as when
you cup your hand over the vacuum. Ie. you'll strain the motor
on the fan and the fan will shut off when it overheats (my fan
has this protection, if yours doesn't, then you risk fire).
I just bought/installed my whole house fan a few weeks ago
(ie. after the last heat wave) so I haven't used it yet
during a heatwave, but I've found the nighttime temps outside
are always lower than the indoor temp. Plus I oversized my
fan (36" belt drive for I'm guessing 1,000 sq ft living space)
so I get a nice little breeze moving through.
And don't forget, when the whole house fan is running, it also
acts effectiving as an attic/gable fan by pushing the superhot
air in the attic (hotter than outside air when the sun is out)
outside.
|
25.219 | | MAY30::CULLISON | | Thu Jul 14 1994 11:58 | 30 |
| They do little when hot and humid. They help a little because
attic is usually cooler because large volume of air going threw it.
But if attic is vented properly and floor well insulated then this
affect is very little.
They work very well on hot days followed by cool nights. Typically
when air is much dryer like a few days ago. But even then with
long days the temperature does not drop that fast. With the one's
I've used over years you typically fell asleep in hot room with
noisey blower, then woke up later freezing. I never had a timer
to turn mine off.
Like said before you have to leave windows open. I know for many
people central a/c is not a valid option but besides the fact it
works great, other benefits not always talked about that can be
significant are you keep you windows shut. This helps in two areas,
one your house is not open for burglars all day and you are not
sucking in all of the great outdoors dust etc.
My experience with cellars is leave them closed up with a small
dehumidifier running to keep it dry. Area will stay comfortable and
for many people is an excellent retreat when upstairs is so hot.
A cool but uncomfortably clammy cellar can be turned into a nice
cool and dry area with an inexpensive dehumidifier running just
on low as long as you keep it closed up. Has worked great for
us on various houses.
harold
|
25.220 | Mine dehumidifier heats up. | HOCUS::BLACKMAN | As always..High on Life! | Fri Jul 15 1994 09:57 | 6 |
| I don't know about your dehumidifier, but mine heats up the air as
leaves the unit. net net is that the basement is now dry (Very
happy!), although it is a bit warmer.
-jon
|
25.221 | dehumidiers do warm up the air\ | MAY30::CULLISON | | Fri Jul 15 1994 10:39 | 26 |
| Yes, that is true, a dehumidifier does heat up the air, but that
is usually ok in a basement, the air gets a little warmer but overall
more confortable because the drop in humidity offsets the slight
rise in temperature. But that is why they are useless upstairs,
close off rooms and turn on dehumifier for a few days and you
will have a sauna. If the basement has a lot of the wall area
exposed then the basement may not be cool enough to use one without
heating up the air too much. When using one only set the humidastat
to a seating that removes enough moisture for comfort, if you set it
too high the extra dryness will not offset the extra rise in
temperature.
In my case my previous basement was so humid it was useless. I even
had some stuffed damaged because of the humidity during the
warm spells in summer. basement was cool but clammy and not
comfortable. After putting in the dehumidier, the basement became
very comfortable even though a little warmer. The air was
also much better for things being stored down there. Our house
was an old home that the original living area was built in the
cellar. The house above was built later when they had money. So
we had a bunch of finished rooms downstairs.
Harold
|
25.222 | | QUARK::LIONEL | Free advice is worth every cent | Fri Jul 15 1994 11:50 | 4 |
| I agree - I run a dehumidifier in my basement and even if the upstairs is
in the upper 80s, the basement is in the 60s. Very comfortable.
Steve
|
25.88 | Humidistat??? | DECWET::MARCINKECH | | Mon Nov 28 1994 18:08 | 19 |
|
This note string is pretty old, but I'll give it a try...
I just installed a fan in the attic to control a condensation
problem. Currently, it is wired to a switch, but I would like
to install a humidistat to automate the process.
The problem is no one in this area seems to have the fogiest
idea about what a humidistat is. I am in Seattle, Washington
(humidity capital of the world ;-) One hardware store offered
to special order it for me at a mere $120. Is this a reasonable
price for this item?
I have checked hardware, electronics, and even marine stores
with no luck. Any other suggestions on places or catalogs to
check?
Thank you in advance for any help,
Edit
|
25.89 | | VMSSPT::PAGLIARULO | | Tue Nov 29 1994 07:28 | 4 |
| Try calling some home heating installers - especially those that do FHA.
I'll bet they can help.
George
|
25.90 | Learn from my mistake... | DELNI::CHALMERS | | Wed Nov 30 1994 12:54 | 13 |
| A word of caution about wiring any type of automated on/off device to
the fan. If for some reason the fan is triggered on during the winter,
you must be sure that a window is open, or provide some other source of
fresh air. If not, and the house is tight, your fan will try to draw
air from wherever it can, including your oil/gas fired heating unit...
Not a pretty sight to see a cloud of soot rise from the basement in the
general direction of the whole house fan.
If you do wire in such a device, be sure to deactivate it if no one
will be home to ensure an outside source of air...
Freddie
|
25.91 | | NOVA::SWONGER | DBS Software Quality Engineering | Wed Nov 30 1994 13:27 | 7 |
| > Not a pretty sight to see a cloud of soot rise from the basement in the
> general direction of the whole house fan.
Probably a major safety hazard too, since it could suck carbon
monoxide upstairs from the furnace.
Roy
|
25.92 | Found the humidistat... | DECWET::MARCINKECH | | Wed Nov 30 1994 16:12 | 17 |
|
.21
Thank you for the suggestion. I found one at a building
supply wholesaler for $22.
.22
> A word of caution about wiring any type of automated on/off device to
> the fan. If for some reason the fan is triggered on during the winter,
> you must be sure that a window is open, or provide some other source of
> fresh air. If not, and the house is tight, your fan will try to draw
> air from wherever it can, including your oil/gas fired heating unit...
We have louvers and other sources of ventilation in the attic. We
mounted the fan by one of the louvers to discharge the humid air.
Are we talking about the same kind of fan?
Edit
|
25.93 | | NOVA::SWONGER | Oracle Rdb Software Quality Engineering | Thu Dec 01 1994 10:35 | 8 |
| >We have louvers and other sources of ventilation in the attic. We
>mounted the fan by one of the louvers to discharge the humid air.
>Are we talking about the same kind of fan?
The previous reply was probably talking about a whole-house fan, not
a gable vent attic fan.
Roy
|
25.94 | Sorry for the mixup. | DELNI::CHALMERS | | Thu Dec 01 1994 18:33 | 6 |
| re: -.1 & -.2
Sorry...yes, I was talking about a whole house fan, which draws it's
air supply from the living area. I apologize for the confusion.
Now back to our regularly scheduled program...
|
25.95 | Need garage venting ideas | JUMP4::JOY | Perception is reality | Mon Jun 19 1995 15:29 | 18 |
| We are looking at installing some sort of "attic" fan in our garage.
The garage is uninsulated and has no ceiling over the cars, just the
rafters. We are finding that it is getting very hot in the summer days.
There are two windows in the back of the garage, which we can open but
then the rain also blows in. There are no roof vents of any sort. When
I lived in AZ many homes had the round "spinner" type of roof/attic
vents. The wind turned them and the warm air was sucked out of the
attic. In the winter they were covered with garbage bags to keep out
the cold air. This sort of thing would be ideal since no wiring is
required, but I haven't really seen them used here. Is this a
reasonable vent to use? We are also thinking of adding a cupola to the
garage. Could we somehow install a vent under the cupola opening to
vent the hot air?
Any ideas or experience would be appreciated.
Debbie
|
25.96 | | QUARK::LIONEL | Free advice is worth every cent | Mon Jun 19 1995 16:14 | 5 |
| Add a ridge vent. Far more effective than those spinner vents - cheaper, too.
Make sure you have some sort of soffit vent on the roof overhang for cool
air to enter, though even without this you'll see an improvement.
Steve
|
25.97 | | HELIX::WELLCOME | Steve Wellcome MRO1-1/KL31 Pole HJ33 | Tue Jun 20 1995 12:37 | 11 |
| The ridge vent is probably the simplest solution.
If you install a cupola, sure, cut a hole and let the cupola really
function the way it's supposed to. My uncle had one on his garage
roof, with a rope-and-pulley arrangement so he could open or close
a hinged door at the bottom of it.
(This assumes, I guess, that the cupola design is not totally bogus
and is capable of functioning as a vent, it's not built strictly for
decoration.)
Depending on the size of the cupola, you might be able to put a small
fan in the bottom of it to blow out air. One of the 9" diameter
computer cabinet fans might be good.
|
25.98 | | OOTOOL::CHELSEA | Mostly harmless. | Tue Jun 20 1995 13:57 | 7 |
| I'm pondering either a whole house fan or a window air conditioner. My
house is a roughly 1000 sq ft ranch. The original attic access was a
hole in what was the coat closet and is now a pantry. Someone put
pull-down steps over the basement stairs (which make me nervous, but
that's another issue). So, would it be feasible to use this original
opening as the location for the WHF? Would the closet door need to
stay open? In general, does the WHF need to be in a central location?
|
25.99 | Ours works like a champ! | NETCAD::GAUDET | | Tue Jun 20 1995 14:19 | 17 |
| RE: .30
I don't see why you can't install a fan in the existing hole in the
ceiling. And yes, you would need to keep the closet door open while
the fan was running.
A central location is best to minimize the distance that the fan needs
to "pull" the air from. I have one (louvered opening) in the front
hallway of my house about 5 feet from the front door. This hallway is
in the center of the house. If there is at least a 10 degree
difference between the outside and inside temperatures, I can flip on
the fan and drop the temp in the most remote parts of the house by 5
degrees in about 15 to 20 minutes. BTW, I close all the doors in the
house (including the slider) and crack windows in all the rooms (not
wide open, just a few inches).
...Roger...
|
25.100 | | HELIX::WELLCOME | Steve Wellcome MRO1-1/KL31 Pole HJ33 | Tue Jun 20 1995 16:16 | 18 |
| You may need to enlarge the opening; I think the minimum fan sizes
I've seen need a hole about 32" square (you take out a piece of
one joist and the fan goes between the adjoining joists), but I
haven't looked at that many fans.
Yes, the door will need to be open. Those fans move a LOT of air.
You'll also have to be sure enough outside windows and/or doors
are open to let in enough air. And you'll have to make sure you
have enough ventilation in the attic so the air can get out. I
think the fan I got requires 5 square feet, minimum. A couple of
small gable vents or even a full ridge vent probably won't be
enough area.
Given that those conditions are satisfied though, they work really
well. I'm totally happy with the one we put in a couple of years
ago. The only (minor) complaint is the noise. It may be worth
spending a bit more to get a really good (hopefully quieter) one.
|
25.101 | 30" install w/o cutting ? | FOUNDR::DODIER | Single Income, Clan'o Kids | Tue Jun 20 1995 16:45 | 14 |
| I have seen 30" WH fans in which the installation instructions
claim that you don't have to cut any joists. Does the fan just rest
on top of the joists ? I would think that you'd have to cut at least
one joist and/or nail 2 by X's between the joists so that there is no
gap and something for the fan to screw to.
In my case, it appears that I'd need a 36" fan for the size of the
house that I have ( ~ 2500 sq. ft.), so it sounds as though this
wouldn't be an option anyway.
As an FYI, I heard that using a WHF with an air-conditioner on will
burn out the A/C motor, just in case anyone was thinking of using both.
Ray
|
25.102 | | VMSSPT::PAGLIARULO | | Tue Jun 20 1995 17:44 | 7 |
| You don't have to cut any joists. The fan sits on top of the joists. Some fans
come with a skirt that fits over and between the joists, sort of like a finger
arrangement, so that you have an enclosed area around the fan. Since you need to
keep windows open for a WHF to work, and keep windows closed for AC to work, I'm
not surprised there are problems.
George
|
25.103 | Why use a fan ? | SCHOOL::SEGOOL | Mike Segool DTN 226-5896 | Wed Jun 21 1995 12:50 | 6 |
| A little off the topic. Would there be any benefit from instead of
putting a fan in the hole just leaving it open. (maybe screened).
Wouldn't this produce a chimney effect, drawing the air from the house
up and out through the attic ?
Mike
|
25.104 | | HELIX::WELLCOME | Steve Wellcome MRO1-1/KL31 Pole HJ33 | Wed Jun 21 1995 13:24 | 4 |
| re: .35
Sure, cupolas on barns never had fans; they worked strictly because
of the chimney effect. A fan will just give more airflow than
normal convection can generate.
|
25.105 | | WLDBIL::KILGORE | Missed Woodstock -- *twice*! | Wed Jun 21 1995 13:26 | 25 |
| .35� A little off the topic. Would there be any benefit from instead of
.35� putting a fan in the hole just leaving it open. (maybe screened).
.35� Wouldn't this produce a chimney effect, drawing the air from the house
.35� up and out through the attic ?
Doesn't work very well.
My installation is a hole in the ceiling with a drop-in frame
containing the fan and a screen; no louvers, so the air is free to
circulate even when the fan is off. However, I still have to turn on
the fan to make things comfortable.
The chimney effect depends on the difference in temperature between the
outside air and the air in the "chimney".� I suppose if my upstairs was
120� and the outside temp was 80�, I might get some detectable natural
air flow -- however, my SO and parasites would not let the experiment
continue for any appreciable length of time.
�The height of the chimney is also a factor. It might be interesting
to see what natural air flow results from attaching an 80' vertical
tube to the hole in the ceiling. Don't forget the aircraft warning
lights.
|
25.106 | *SOMEONE* had to say it... | HDLITE::NEWMAN | Chuck Newman, 508/467-5499 (DTN 297), MRO1-2/K5 | Wed Jun 21 1995 17:14 | 6 |
| � �The height of the chimney is also a factor. It might be interesting
� to see what natural air flow results from attaching an 80' vertical
� tube to the hole in the ceiling. Don't forget the aircraft warning
� lights.
Wouldn't you need an air shredder with at vertical tube that long?
|
25.100 | | CSLALL::NASEAM::READIO | A Smith & Wesson beats four aces, Tow trucks beat Chapman Locks | Fri Dec 22 1995 13:30 | 3 |
25.285 | | HELIX::TORRES | Wheel In The Sky Keeps On Turning... | Mon Jun 02 1997 13:05 | 23 |
|
Well, I've read all 284 replies to this topic. Very informative.
With respect to the WHF, is the difference in price between the direct
drive and belt drive worth the money? Currently I can get a 30" direct
drive Leslie fan from Home Depot for $125. The 30" Belt drive model is
$175. I believe the only difference is that the belt drive includes a
2 speed wall switch, instead of a pull chain. Regular fan noises don't
bother me, and the amount of CFM's are within 200, so I guess we're
down to durability (unless the direct drive is unreasonably noisy).
Should I expect a belt drive to last longer? Any other considerations?
Also, I haven't persued the "Grainger" angle, as the notes
mentioning it are pretty old. Can DEC employees still get a discount
from them? Can I expect their WHF to be better than the Home Depot
Leslie fan?
Also, what about accessories. Other than the temperature kill
switch, what other accessories are helpful? Timers? Dimmer (I didn't
see a dimmer for the Leslie)?
Thanks in advance,
Luis
|
25.286 | Grainger | HELIX::WELLCOME | Steve Wellcome SHR3-1/C22 Pole A22 | Mon Jun 02 1997 13:54 | 16 |
| re: Grainger
As of a few months ago, I bought a few things at Grainger by just
showing my badge, no problem.
Don't expect great prices, however. Their "wholesale" price quite
often seems to be the same, or higher, than everyone else's
everyday price. Not always, but don't automatically think you're
getting a great deal.
For instance, Grainger sells Gentran transfer switches for something
like $320 "wholesale." I got one at Maynard Supply for $215, and
Home Depot, if you can stand to do business with them (I can't),
had them even a bit cheaper than that.
Grainger does have the stuff, however, and my experiece with service was
excellent.
|
25.287 | warranty time? | STAR::SCHEN | | Mon Jun 02 1997 15:21 | 11 |
|
Well, I just bought a direct drive 30" fan at HQ and was
wondering some of the same things. Mostly about the noise
factor. One thing we noticed was that the direct drive has
a 10 year warranty and the belt drive has a 15. Seems like
$50 extra dollars is alot to pay for an extra 5 year warranty.
Also, can I install the thing _under_ the joists as opposed
to in_between them? (I confess I have yet to read this whole
string yet).
|
25.288 | | VMSSG::PAGLIARULO | | Tue Jun 03 1997 08:08 | 10 |
| Steve,
Installing a whole house fan under the joists might look a
little wierd but you should be able to install it on top of the joists.
The WHF (belt-drive) that I installed in my old house came with a heavy
cardboard plenum that fit between the joists so that the fan only drew
air from the house not the attic. If your's didn't come with one I
would think you can make one fairly easily.
George
|
25.289 | | STAR::SCHEN | | Tue Jun 03 1997 14:15 | 6 |
|
Ah, on top! Thanks George, sometimes the best ideas
are just one cube over :-)
Steve
|
25.290 | may have to cut joist anyway | cpeedy.lkg.dec.com::BRADLEY | Chuck Bradley | Thu Jun 05 1997 14:42 | 17 |
| i'm assuming the reason for installing over or under is to avoid cutting
the joist. here are two areas of concern.
you want a good seal around the box, so it pulls only house air, not
any attic air at all. i'd use wood, not cardboard between the joists.
think about the louvered opening for the air. are you sure the louvers
can open if you do not cut the joist?
once installed, the opening to the fan is a very effective heat removal
device during the winter. be sure you can cover the fan with insulation
during the heating season. i built four walls around mine from 2"
styrofoam. they are a little higher than the top of the fan. the top
fits like a cooler chest, sits on top and slight press fit inside.
it is covered with 6" of fiberglass insulation. if you make one like that,
mark the top for the proper orientation or make the box square.
you do not want to fuss with a 47"x48" slab in an attic full of trusses
and assorted stuff. it only takes a minute to cover the fan and unplug it
every fall, uncover it and plug it in every spring.
|