Are there temperature problems if installing RZ29-xx in a BA350-xx without the 2X fans,ie can u only install so many RZ29s per shelf without the 2X fans. Or is that strictly verboten? Ie cooling issues this would also apply to SW800,SW500,SW300 cabinets. I have a customer that has LEDS on all of his 8 bit personality modules. Some have both on (most) some have 1 on! A precise meaning to the light status on the 8 bit & 16 bit personality mods would be helpful. Also criteria for installing internal cabinet fans in the above cabinets would be very helpful..With part numbers if you have em!!! IE at what point must the Cabinet fans be installed ???? Thanks Mike Turro Baltimore MCS For offline discussions [email protected]
T.R | Title | User | Personal Name | Date | Lines |
---|---|---|---|---|---|
6508.1 | HOUNDD::BASSETT | Bill | Mon Mar 24 1997 16:31 | 31 | |
Mike, see earlier note for LED meaning.... When one has 7200 RPM drives in Storageworks, there are specific rules about cooling. 1) In a pedestal application, dual speed blowers are required along with foam blocks to stop recirculation. 2) In a cabinet (SW500/SW800) the fan tray assembly is required. (DUAL SPEED BLOWERS ARE NOT REQUIRED.) 3) All SW300 and BA356's shipped with dual speed blowers. Late model BA350's shipped with dual speed blowers. 4) Early BA350's CANNOT use the dual speed blower since the backplane does not include the "Dual speed line." (Backplane rev F is not upgradeable, rev H is required.) 5) Quantity of drives per shelf is NOT an issue. Each SBB is allocated so much airflow. The old blower CANNOT supply enough airflow to the individual SBB in a fan failed condition to adequately cool the drive (only the 7200 RPM drives) inside the SBB. So even one drive in the BA350 can have a problem. [Interesting enough, one drive is the WORSE CASE condition.] The number of drives per shelf limitation is related to power not cooling. (BA35X-HF is required for 7 drives.) Bill |