I have the following configuration at my cusomter
pc
|
10BaseT
|
DECrepeater 90TS
AUI
10BaseT MAU
|
PEswitch 900Tx
DEF1H
|
FDDI
|
GIGAswitch/FDDI
Everyting is working fine. This is repeated on at least 3
different PEswitch' going to different rings and different GS/F ports.
Over this last weekend they had an AirConditioning problem and the
UPS for the DR90TS and PE900TX shut them down. The GS/F stayed up
and running.
Over the weekend the AC was fixed and everything was powered back
up. The DR90TS and PE900TX would have had power applied at the same
time.
On Monday morning everything was up and working fine except the
link between the DR90TS and the PEswitch. There were many systems
directly connected to PEswitch ports, all up and running. The GS/F and all
FDDI rings were fine. The link light on the PEswitch from the DR90TS
never came on. All other ports on that PEswitch were up.
The solution that fixed the problem was to power cycle the DR90TS.
This cleared the problem and each link came up.
This is not preferable.
Any suggestions on why this happened?
| T.R | Title | User | Personal Name | Date | Lines |
|---|---|---|---|---|---|
| 3401.1 | any help on DETMI/DESBF power up? | RDMCS3::STUART | Scott Stuart - NPB SE - 410.315.9954 | Thu Mar 28 1996 08:17 | 6 |
any help or suggestions on where I can take this problem in .0?
What I am looking for is the expected power connection of a DETMI to at
DESBF when both power up at the same time.
thanks
...scott
| |||||
| 3401.2 | I'll see about checking this behavior.... | NETCAD::BATTERSBY | Don't use time/words carelessly | Thu Mar 28 1996 09:59 | 8 |
I have some DR90Ts's and PEswitches configured in my lab.
Maybe I can re-create the powerup situation. I'll see if I can
establish some observations.
The only thing you didn't make clear is if either or both the
PEswitch or DETMI are stand-alone. IE: powered by a brick or docking
station as required by each.
Bob
| |||||
| 3401.3 | Possible explanation for customer's DETMI problem.... | NETCAD::BATTERSBY | Don't use time/words carelessly | Thu Mar 28 1996 13:23 | 35 |
Oookay, I think I may have re-created what you saw Scott.
First some data....
The DETMI looks like it typically takes about 30 seconds to complete
its self test and start looking for a link on either its UTP ports,
its thinwire, or the AUI out the back. I powered up the DETMI several
times to make sure of this time.
The PEswitch 900TX typically takes about 50 seconds to complete its
self test, and another 30 seconds to bring a link up (15 seconds in
learning state, plus 15 seconds in pre-forwarding state).
So with a PEswitch already powered on it takes about 30 seconds for
a DETMI link to come up.
With a DETMI already on, it takes a minute and 20 seconds for the
PEswitch to bring up a link.
With both powered off and then powered up, it will still take at
least 1 minute and 20 seconds for a link to come up.
Now, for the wierdness I think you may have seen....
Once after powering them both up simutaneously, the DETMI seemed to
complete its self test, but shortly after this, it seemed to be
sending out what is referred to as a "jabber" packet, as the traffic
led was on solid. At the PEswitch end, when it completed its self
test (50 seconds), the traffic led for the port which was physically
connected to the DETMI, was also on solid. This lasted for about
3 minutes, after which the DETMI saw the link, and then the PEswitch
too saw the link.
I believe that what might be happening is that with the thinwire port
un-terminated, and seeing no other active lan, it sits on the thinwire,
sees an un-terminated thinwire lan, and sees multiple collisions because
of the un-terminated unused thinwire port, and sends out a jabber packet
for another couple of minutes.
It seems to eventually correct itself and starts hunting through the
ports looking for an active lan.
Does this sound like what the customer might have seen?
Bob
| |||||
| 3401.4 | almost the problem - customer has to power cycle detmi | RDMCS3::STUART | Scott Stuart - NPB SE - 410.315.9954 | Thu Mar 28 1996 15:53 | 12 |
re: .2 - as you figured out they are all standalone.
What my customer saw was that it never connected without repowering on
the DETMI. In other words the DESBF port never connected.
I will ask the cusomter to terminate the thinwire and see if they can
recreate the problem.
thanks for this update. I'll let you know if it contiure.s It will be
a couple of dasy before I get back to you.
...scott
| |||||
| 3401.5 | More info on DETMI - PEswitch link issue.... | NETCAD::BATTERSBY | Don't use time/words carelessly | Thu Mar 28 1996 17:59 | 25 |
>What my customer saw was that it never connected without repowering on
>the DETMI. In other words the DESBF port never connected.
This is ummmm "interesting"... When my DETMI fails to connect to
the AUI, the DESBF sees the link (IE: sees the DETPM MAU), every
time. In other words, the DESBF - DETPM MAU link portion is seen by
the DESBF. The rest of the logical link, (the AUI side of the MAU
into the DETMI) is disconnected. As long as the MAU has power (from
the AUI conn. of the DETMI), the DESBF will see the utp link and
will come up into forwarding. It's the DETMI end which is broken
somehow. I've asked the opinion of someone in the repeater engineering
group, and he says that perhaps the rear cover (which houses the
little pc board that provides the mechanical transition between the
48 pin Secretariat connector and the rear AUI connector may be
presenting the wrong slot ID value to the DETMI internal logic.
I've got to verify this tomorow morning with someone else. Someone
else mentioned a feature the DETMI has where via management (HUBwatch),
one can set the DETMI in one of 3 modes, auto (auto selects between
the side thinwire port and the rear AUI), thinwire, or AUI. The
solution for the customer might be simply to select AUI, and save
this value to the internal nvram of the DETMI. Then it will always
power up and look for the AUI *only*, and won't ever look at the
thinwire.
Bob
| |||||