2340.0. "FDDI Configuration Guide" by DELNI::PIEPER () Fri Jun 02 1995 13:43


  FDDI CONFIGURATION OPTIONS FOR THE DEChub 900MS BACKPLANE AND DEChub ONEs


  This note is the replacement for note 1597, which dealt with the FDDI 
  configuration options for dual rings in DEChub 900 backplanes.  This note
  explains the changes included with the Wave 3 product release, which are:

	- Support for tree connections in the backplane
	- Support for dual homing of the hub in a treed configuration
	- Support for the DECconcentrator 900TH
	- Support for auto healing of both dual ring and tree connections
	- Support for dual rings and trees in the DEChub ONEs
	- Selection of FDDI network building blocks via setup port
	- Support for cold swapping of FDDI modules
	- Support for quick PC-trace recovery
	- Defined token ordering of hub modules

  This memo will detail the configuration capabilities that are supported in 
  DEChub FDDI modules with Wave 3.  It is assumed that the reader knows basic 
  FDDI configuration rules and understands the differences between an A, B, 
  M, and S port.  If these are not familiar, see Appendix A for a brief dis-
  cussion of the important concepts.  These DEChub configuration options will 
  be explained by using the DECconcentrator 900MX, DECconcentrator 900TH, the 
  PEswitch 900TX and the DECswitch 900EF.


  BASIC FDDI RULES

  First, realize that ANY FDDI connection between two adjacent stations is 
  actually two POINT to POINT connections no matter where the stations are in 
  the configuration (tree or dual ring).  This is a basic fact for any vendor's 
  FDDI products, whether they are in a hub or not.  The backplane of the DEC-
  hub 900 is used to make these point to point connections between DECconcen-
  trators, FDDI DECswitches or PEswitches in the hub.  One backplane channel is 
  needed for each connection.  Since two connections are required between any 
  two ports, TWO backplane channels are required for each connection between 
  any two ports on DECconcentrators, FDDI DECswitches, or PEswitches, regard-
  less of the actual configuration.  

  The terminology used is, unfortunately, very ambiguous when it comes to 
  describing configurations.  It is important to understand that dual rings
  and trees are PHYSICAL descriptions of the network topology.  In all cases, 
  the FDDI is a LOGICAL ring, i.e., a token passes from station to station in 
  the ring.  The PHYSICAL implementation may be configured as a tree or a 
  dual ring, but in all cases a logical ring exists. 

  Technically, any type of configuration (dual ring, tree, or dual ring of 
  trees) could be supported in the DEChub 900 backplane.  For ease of use, 
  only dual ring and tree configurations are supported.  A user can build up 
  to FOUR independent FDDI networks across the hub backplane.  Each FDDI net-
  work can be either a dual ring or a tree, but not a mixture of both. 


  BASIC DUAL RING CONFIGURATIONS

  DEChub FDDI modules can typically support front panel as well as backplane
  FDDI ports.  When configured in a dual ring, ports are assigned a RING 
  port type (A or B) via the Station Configuration screen of HUBwatch.  The 
  dual attachment station (DAS) port configurations in Diagram #1 are all 
  possible with this soft assignment capability.  Since individual modules 
  may support a subset of these configurations, each module will be detailed 
  in other sections.




  Diagram #1: Possible DUAL RING Port Configurations

				Front Panel Ports 

    A                                               B          A        B
    |                                               |          |        |
  +-+----------+      +------------+      +---------+-+      +-+--------+-+
  |            |      |            |      |           |      |            |
  +----------+-+      +-+--------+-+      +-+---------+      +----------+-+
             |          |        |          |                                 
             B          A        B          A                           

				Backplane Ports



  BASIC TREE CONFIGURATIONS

  When connected in a tree configuration, front panel ports and backplane 
  ports are assigned a TREE port type (M or S) via the Station Configuration 
  screen of HUBwatch.  The tree port configurations in Diagram #2 are all 
  possible with this soft assignment capability. 


  Diagram #2: Possible TREE Port Configurations

				Front Panel Ports

                         S          M   S          M             A    B
                         |          |   |          |             |    |
  +--------+      +------+-+      +-+---+-+      +-+------+    +-+----+-+
  |        |      |        |      |       |      |        |    |        |
  +-+----+-+      +-+------+      +-------+      +------+-+    +-+------+
    |    |          |                                   |        | 
    M    S          M                                   S        M 

				Backplane Ports

  Note the fifth configuration with an M port in the backplane, and A and B 
  ports on the front panel.  This configuration is only implemented in con-
  centrators, and is used for connecting to a dual ring, or in a dual homed 
  configuration. 

  Another important point to note is that when the user accessible FDDI ports 
  are reconfigured as TREE ports, the A port always becomes an M port and the 
  B port always becomes an S port.  This is true for either front panel ports 
  or MODPMD ports in a DEChub ONE-MX. 


  DECconcentrator 900MX

  The DECconcentrator 900MX is actually an EIGHT port FDDI concentrator where
  SIX ports are on the front panel and TWO ports attach to the DEChub 900 back-
  plane or to the DEChub ONE-MX that supports MODPMDs. 

  As shown in Diagram #3, Port #1 on the front panel of the DECconcentrator 
  900MX can act as either an A or M port and Port #6 can act as either a B, 
  S or M port.  The two backplane ports are also software configurable via 
  HUBwatch. 



  Diagram #3: DECconcentrator 900MX Port Configuration Capabilities

						A,M    B,S
                                     +-----------------------------+
    DEChub 900MS Backplane          /        DEChub ONE-MX        /|
                                   +-----------------------------+ |
       A,M         B,S	          /                             /  +
        |           |	         /      DECconcentrator        / |/
     +--+-----------+---+       /                             /  +
     |  concentrator    |      +-----------------------------+  /
     +-+---+-+-+-+----+-+      |                             | /
       |   | | | |    |        |  A,M   M  M  M  M   B,S,M   |/
      A,M  M M M M  B,S,M      +-----------------------------+ 

      Module Front Panel	      Module Front Panel


  DECconcentrator 900TH

  The DECconcentrator 900TH is a sixteen port FDDI concentrator where four-
  teen ports are on the front panel and TWO ports attach to the DEChub 900 
  backplane or to the DEChub ONE-MX that supports MODPMDs.  Twelve of the 
  front panel ports are fixed UTP connections.  The two remaining ports can 
  be configured for either UTP, multimode fiber, or single mode fiber by the 
  addition of MODPMD modules. 

  As shown in Diagram #4, MODPMD Port #1 on the front panel of the DECconcen-
  trator 900TH can act as either an A or M port and MODPMD Port #2 on the 
  front panel can act as either a B, S or M port.  The two backplane ports 
  are also software configurable via HUBwatch so both dual ring and tree 
  connections can be supported.  


  Diagram #4: DECconcentrator 900TH Port Configuration Capabilities

						A,M       B,S
                                     +-----------------------------+
    DEChub 900MS Backplane          /        DEChub ONE-MX        /|
                                   +-----------------------------+ |
       A,M        B,S	          /                             /  +
        |          |	         /      DECconcentrator        / |/
     +--+----------+----+       /                             /  +
     |  concentrator    |      +-----------------------------+  /
     +-+-----+----+---+-+      |                             | /
       |     |    |...|        | A,M  B,S,M   M  M .... M    |/
      A,M  B,S,M  M   M        +-----------------------------+ 

      Module Front Panel	      Module Front Panel



  DECswitch 900EF

  The DECswitch 900EF (previously called the DECbridge 900MX) differs from 
  the DECconcentrator in that it supports only TWO FDDI ports (Port #1A and
  Port #1B) that can be INDIVIDUALLY ASSIGNED to either the front panel or 
  the backplane.  That means the DECswitch 900EF can have only two active 
  FDDI ports at any one time (two front panel ports, one front panel and one 
  backplane port, or two backplane ports).  The port-type assignments are 
  "software-selectable" via HUBwatch or the set up port menu, where two front 
  panel ports, two backplane ports or a front panel port and a backplane port 
  can act as A and B ports or M and S ports.




  Diagram #5: DECswitch 900EF Port Configuration Capabilities

						A,M    B,S
                                     ------------------------------+
    DEChub 900MS Backplane          /        DEChub ONE-MX        /|
		                   +-----------------------------+ |
      A,M	B,S               /                             /  +
       |  	 |	         /          DECswitch          / |/
     +-+---------+-+            /                             /  +
     |  DECswitch  |	       +-----------------------------+  /
     +--+-------+--+           |                             | /
        |       |              |    A,M  B,S                 |/
       A,M     B,S	       +-----------------------------+ 

      Module Front Panel	      Module Front Panel



  PEswitch 900TX

  The PEswitch 900TX differs from the DECswitch 900EF in that it supports two
  FDDI port connections to the DEChub backplane or DEChub ONE-MX ONLY.  There 
  are NO front panel FDDI ports on the PEswitch 900TX.  The port-type assign-
  ments are also "software-selectable" allowing either A and B or M and S 
  connections at any time. 


  Diagram #6: PEswitch 900TX Port Configuration Capabilities

						 A,M   B,S
                                     ------------------------------+
    DEChub 900MS Backplane          /        DEChub ONE-MX        /|
                   		   +-----------------------------+ |
      A,M 	B,S	          /                             /  +
       |  	 |	         /          PEswitch           / |/
     +-+---------+-+            /                             /  +
     |  PEswitch   |	       +-----------------------------+  /
     +-------------+           |                             | /
                               |                             |/
       			       +-----------------------------+ 



  ADDITIONAL INFORMATION ON THE USE OF M and S PORTS 

  1) In order to simplify the rules as much as possible, a decision was made 
  to allow an individual network to be configured as a dual ring or a tree. 
  This was required to prevent configurations that would automatically be 
  disconnected by the actions of the FDDI configuration rules, which operate
  at the module level, independent of HUBwatch.  The intent is to offer 
  choices which work, not ones that need additional rule checking beyond 
  what HUBwatch can provide.  In hubs with multiple FDDI networks, some 
  of the networks can be configured as dual rings, others can be configured 
  as trees, but each individual network can be of only one type. 

  2) For concentrators, we now have the option of devices with one S port, and 
  up to 15 M ports.  Such a device is known as a Single Attach Concentrator 
  (SAC) in FDDI terminology.  This is a new device type in Digital's FDDI 
  product set.




  3) The FDDI rules require that stations with M ports be called concentrators. 
  Consequently, when a switch is configured with M and S ports, it must report 
  itself as a concentrator in FDDI NIF and SIF frames, and in the FDDI and 
  SNMP MIBs.  Therefore, HUBwatch, FDDI monitors, and FDDI Ring Maps will 
  announce the station type of a treed DECswitch 900EF or PEswitch 900TX as 
  a Single Attach Concentrator (SAC), rather than as a Single Attach Station
  (SAS). 


  FDDI BUILDING BLOCKS

  Since ANSI standard FDDI configuration rules are very complex and various 
  connections are defined as "legal" but result in limited use configurations 
  such as wrapped rings, a simple to use "building block" approach was adopted 
  for configuring FDDI in the backplane of the DEChub 900 and in the DEChub 
  ONE-MX.  The network manager assigns a port type by selecting a "building 
  block".  These building blocks are divided into two groups - RING and TREE.  
  There are a total of 9 building blocks; 4 are used for building dual rings, 
  and 5 are used for building trees.  HUBwatch will only allow connections to 
  be made between building blocks of the same group, in order to minimize 
  annoying errors such as connections that break because of the standard's 
  preference for trees over dual rings. 


  RING BUILDING BLOCKS

  The four RING building blocks, which are used to build dual rings,
  are named as follows and shown in Diagram #7.

  Trunk B:  B port connects to the backplane or DEChub ONE-MX MODPMD, 
	    A port out the front

  Trunk AB: A and B ports connect to the backplane or MODPMDs on the
            DEChub ONE-MX

  Trunk A:  A port connects to the backplane or DEChub ONE-MX MODPMD,
            B port out the front  

  Stump Primary:  A and B ports connect to the front panel 


  Diagram #7: RING Building Blocks

			Front Panel ports

		  A                             B        A   B
		  |                             |        |   |
		+-+-----+    +-------+    +-----+-+    +-+---+-+
		| Trunk |    | Trunk |    | Trunk |    | Stump |
		|   B   |    |  A B  |    |   A   |    |Primary|
		+-----+-+    +-+---+-+    +-+-----+    +-------+
		      |        |   |	    |
		      B        A   B        A	    

		 Backplane or DEChub ONE-MX MODPMD ports 




  TREE BUILDING BLOCKS

  The five TREE building blocks are named as follows, and shown in Diagram #8:
 
  Nonroot MS:	M and S ports connect to the backplane or MODPMDs on the
		DEChub ONE-MX
  Nonroot M:	M port connects to the backplane or DEChub ONE-MX MODPMD, 
		S port out the front
  Nonroot SAC:  M and S ports connect to the front panel 
  Nonroot S: 	S port connects to the backplane or DEChub ONE-MX MODPMD 
		and M port out the front  
  Root Primary: A and B out the front, M connected to backplane or 
		DEChub ONE-MX MODPMD


  Diagram #8: TREE Building Blocks


				Front Panel Ports

                         S          M    S          M             A    B
                         |          |    |          |             |    |
  +--------+      +------+-+      +-+----+-+      +-+------+    +-+----+-+
  | Nonroot|      | Nonroot|      | Nonroot|      | Nonroot|    |  Root  |
  |   MS   |      |    M   |      |   SAC  |      |    S   |    | Primary|
  +-+----+-+      +-+------+      +--------+      +------+-+    +-+------+
    |    |          |                                    |        | 
    M    S          M                                    S        M 


		 Backplane or DEChub ONE-MX MODPMD ports 



  DEFAULT CONFIGURATIONS

  Modules in the DEChub 900

  The default configuration for either the DECconcentrator 900MX, the DEC-
  concentrator 900TH, or the DECswitch 900EF is that ALL front panel ports 
  are active and A and B ports are out the front.  This means that NO 
  redirection to backplane ports or backplane connections are made between 
  FDDI modules unless the Network Manager chooses to do so.  The Network 
  Manager will need to issue the appropriate HUBwatch commands to establish 
  FDDI networks across the backplane of the DEChub 900.  While the default 
  for the PEswitch 900TX is to the backplane ports, no FDDI LAN connections 
  across the backplane are made by default.  The Network Manager will need to 
  issue the appropriate HUBwatch commands to connect PEswitches to an FDDI 
  backplane LAN.


  Modules in DEChub ONE / DEChub ONE-MX

  The default configuration for either the DECconcentrator 900MX, the DEC-
  concentrator 900TH, or the DECswitch 900EF is that ALL front panel ports 
  are active and A and B ports are out the front.  This is true for either 
  the DEChub ONE (DEHUA) which supports one Ethernet connection or the DEChub 
  ONE-MX (DEF1H) which supports one Ethernet connection and up to two MODPMD
  FDDI connections.  The default configuration for the PEswitch 900TX is A 
  and B to the MODPMD ports of the DEChub ONE-MX.  No FDDI connections are 
  available when the PEswitch 900 is used with the DEChub ONE. 



  A Network Manager who wishes to use the MODPMD ports of the DEChub ONE-MX 
  will need to issue the appropriate commands to enable the MODPMD ports, 
  using the building blocks previously described.  This can be done either 
  via HUBwatch or the setup port of the DEChub ONE-MX.

  Modules in a DEChub ONE or DEChub ONE-MX are required to perform two 
  additional tasks.  The first is that they must remember their configuration 
  so that they wake up in the previously configured state following a power 
  failure.  This memory applies if a module is moved to the same type of 
  DEChub ONE - as far as the module can tell, it is in the same environment 
  as when it was powered off. 

  The second task for a module in a DEChub ONE or DEChub ONE-MX is for it to 
  recognize a change of environment when moved between a DEChub 900, the 
  DEChub ONE-MX, or the DEChub ONE.  When the change of environment is detected 
  the module assumes the default condition of A and B out the front panel, 
  except for the PESwitch 900 TX, which is A and B to the backplane or DEChub 
  ONE-MX MODPMD ports.

  For example, if a DECswitch 900EF module which had been configured with
  S and M ports on the back is moved from a DEChub ONE-MX to another DEChub
  ONE-MX, the module will power up with the MODPMDs of the second DEChub ONE-MX
  enabled as S and M ports.  If the module is then moved to a DEChub ONE, it 
  will detect an environment change, and power up with the front panel A and B 
  ports enabled.  If it is then moved back to a DEChub ONE-MX, it will detect 
  a new environment, and power up with the front panel ports enabled as A and 
  B ports. 

  Also, if a module is moved from a DEChub ONE-MX to another DEChub ONE-MX with 
  a different MODPMD configuration, the module will wake up believing that it 
  is still in the original DEChub ONE-MX, and will attempt to configure its 
  ports per the remembered configuration.  It will not detect the change in 
  configuration of the MODPMDs. 


  FDDI AUTO HEALING

  The auto healing features of the FDDI modules have been improved with 
  this Wave of firmware.  New features include:

     1) reconfiguration around modules determined to be "unavailable"
     2) support for cold swapping of modules
     3) indication of a change in the FDDI configuration of the hub via 
	dotted lines on the HUBwatch LAN Interconnect screen 

  When the HUB manager is upgraded, Auto Healing will be disabled by default. 
  Following the upgrade of the modules to the latest version of firmware, Auto
  Healing can be enabled.  It will then continue to be enabled unless it is 
  subsequently turned off by the network manager.   

  Previously, when a module was removed from the hub, the connections on 
  either side of it would first wrap, and then be joined together, once 
  the hub detected the removal of the module.  If a module failed, the 
  connections would wrap, but the healing would never occur, unless the 
  module was physically removed from the hub chassis. 

  In this release, the ability to heal the connections becomes more important, 
  due to the addition of treed connections, which, by their nature, cannot 
  restore the ring by wrapping.  Without the auto-healing feature, the loss of 
  a module results in the loss of all modules below that module in the tree.  
  Now, for both dual ring and tree configurations, if a module is physically 
  

  removed, or, is determined to be "unavailable", the hub will heal the broken 
  connection, thus restoring the network to operation.  "Unavailable" is 
  defined as a condition in which the HUB's built in manager cannot communicate 
  with the module for longer than 3 seconds.  Such a condition is indicated by 
  the word "Unavailable" in the lower line of the slot report in the LCD 
  display on the DEChub 900 front panel. 

  Please note that some outages will not be detected, so healing cannot be 
  guaranteed to always correct the break in a tree, unless the module has 
  been physically removed. 

  In high availability situations where outages longer than 500 milliseconds 
  cannot be tolerated, DIGITAL recommends that a dual ring configuration be 
  implemented, since the dual ring will wrap and connectivity will be 
  maintained in all cases. 

  Before this Wave, the removal of an FDDI module caused the HUB to forget 
  what type of module was in the slot, what building blocks were used, and 
  also the position of the module in the hub's token flow.  With this Wave, 
  the Hub will automatically restore the previous configuration, as long as 
  a module of the same type is inserted in the slot.  This behavior occurs 
  whether the module is replaced with power applied to the hub (hot swapping),
  or when the hub power is shut down (cold swapping).  This makes repair of 
  a faulty module significantly less time consuming. 

  Finally, when an FDDI module is patched out of an FDDI configuration by 
  Auto Healing, the LAN Interconnect screen of HUBwatch will flag that module
  with a dashed line connection instead of a solid line.  This is not auto-
  matically displayed, but will appear when the screen is refreshed.  For 
  example, if a module has become unavailable and has been removed from the 
  ring by Auto Healing, the connections from the module to the LAN will be 
  dotted, indicating that a change of configuration has occurred. 

 ********************* I M P O R T A N T *** N O T E ************************
  	If the Auto Healing function is enabled, HUBwatch will PREVENT the 
        user from adding or deleting FDDI connections, Ethernet connections,
	Ethernet LANs or FDDI LANs via the LAN Interconnect screen.  This 
	is designed to preserve the existing configuration until someone 
	can physically replace any failed modules.  An error message will 
	be displayed informing the user that the requested action cannot 
	be taken, and will offer a list of alternatives.  If the change 
	is still desired the user must first disable Auto Healing by 
	selecting "Disable" from the Auto Healing buttons on the LAN 
	Interconnect screen.  This will delete the patched out connections.
        Following the reconfiguration, Auto Healing can be reenabled.  This 
        new configuration will then be shown on the screen. 
  ********************* I M P O R T A N T *** N O T E ************************



  EXAMPLE CONFIGURATIONS

  FDDI trees and FDDI dual rings are supported across the backplane of the 
  DEChub 900MS.  The dual ring configuration should be used across the back-
  plane if dual ring connections are pulled to the hub since it has more robust 
  and quicker fault tolerance capabilities (ring wrapping plus auto-healing -
  both are detailed later) than tree configurations.  If an FDDI tree connection
  is pulled to the DEChub, obviously a tree configuration should be built across
  the backplane.  The following diagrams attempt to demonstrate the various 
  types of FDDI configurations that are currently supported in the DEChub.




  TREE CONFIGURATIONS
  
  It is possible to build many types of tree configurations in the DEChub900
  backplane.  Trees can be contained within the backplane, they can connect
  an individual tree in the hub to a higher level of a tree, or, they can 
  be used for interconnection of hubs.  The following examples demonstrate 
  different supported tree configurations. 


  EXAMPLE 1: SELF CONTAINED TREE OF CONCENTRATORS IN BACKPLANE

  In this example, a tree is constructed entirely within the backplane.  The 
  backplane ports of the concentrator modules are enabled to be of type M and 
  S, and the front panel ports become M ports.  The module in the highest slot 
  number will be the top of the tree, and its M port will connect to the S 
  port of the module with the second highest slot number, and so on down the 
  line.  Two backplane channels are required per connection.  For the example 
  shown, a total of four backplane channels are in use. 

  
  Diagram #9: DECconcentrator Tree Connections in backplane

			      Front Panel Ports

	  M M M M M M		  M M M M M M 		  M M M M M M
	  | | | | | |		  | | | | | |		  | | | | | |
	+-+-+-+-+-+-+-+		+-+-+-+-+-+-+-+		+-+-+-+-+-+-+-+	
	|   CON #1    |		|   CON #2    |		|   CON #3    |
	+-+---------+-+		+-+---------+-+		+-+---------+-+
	  |	    |		  |	    |		  |	    |
	  |	    +-------------+         +-------------+         |
	  M	    S		  M	    S		  M	    S

				Backplane Ports


  Diagram #10: Building Block Representation of Diagram #9 Configuration

                                                         
              +-------+        +-------+            +-------+
              |Nonroot|        |Nonroot|            |Nonroot|
              |  MS   |        |  MS   |            |  MS   |
              +-+---+-+        +-+---+-+            +-+---+-+
                |   |            |   |                |   |
                M   S            M   S                M   S



  EXAMPLE 2: SELF CONTAINED TREE OF SWITCHES AND CONCENTRATORS IN BACKPLANE

  In this example, a tree is constructed entirely within the backplane, but 
  a mixture of device types is used.  The backplane ports of the modules are 
  enabled to be of type M and S.  The front panel ports of the concentrators 
  become M ports, and the front panel ports of the switches become unusable. 
  The module in the highest slot number will be the top of the tree, and its 
  M port will connect to the S port of the module with the second highest slot 
  number, and so on down the line.  This example also uses a total of four 
  backplane channels.



  
  Diagram #11: Tree Connections to an FDDI Network

			      Front Panel Ports
          M M M M M M
	  | | | | | |		                	          | |
	+-+-+-+-+-+-+-+		+-------------+		+---------+-+-+	
	|DECcon 900TH |		|PEswitch 900 |		|DECsw 900 EF |
	+-+---------+-+		+-+---------+-+		+-+---------+-+
	  |	    |		  |	    |		  |	    |
	  |	    +-------------+         +-------------+         |
	  M	    S		  M	    S		  M	    S

				Backplane Ports


  Diagram #12: Building Block Representation of Diagram #11 Configuration

                                                         
              +-------+        +-------+            +-------+
              |Nonroot|        |Nonroot|            |Nonroot|
              |  MS   |        |  MS   |            |  MS   |
              +-+---+-+        +-+---+-+            +-+---+-+
                |   |            |   |                |   |
                M   S            M   S                M   S



  EXAMPLE 3: TREE CONNECTIONS TO AN EXTERNAL CONCENTRATOR

  Trees within the hub can connect to a higher level concentrator by making 
  one of the modules have a front panel S port, and making all other modules 
  have M and S ports on the backplane.  For example, a tree of PESwitch 900TX 
  modules can be connected to an external ring using either a DECSwitch 900EF 
  or one of the concentrators to make the external connection. 


  Diagram #13: Tree Connections to an FDDI Network

			      Front Panel Ports

                                                                    S
                                                                    |
	+-------------+		+-------------+		+-----------+-+	
	|PEswitch 900 |		|PEswitch 900 |		|DECsw 900 EF |
	+-+---------+-+		+-+---------+-+		+-+-----------+
	  |	    |		  |	    |		  |	    
	  |	    +-------------+         +-------------+         
	  M	    S		  M	    S		  M	    

				Backplane Ports


  Diagram #14: Building Block Representation of Diagram #13 Configuration

                                                          S
                                                          |
              +-------+        +-------+            +-----+-+
              |Nonroot|        |Nonroot|            |Nonroot|
              |  MS   |        |  MS   |            |   M   |
              +-+---+-+        +-+---+-+            +-+-----+
                |   |            |   |                |   
                M   S            M   S                M   



  EXAMPLE 4: DUAL HOMING AND CONNECTION TO AN EXTERNAL DUAL RING

  In some cases it is desirable to connect the hub to an external dual ring, 
  and tree the modules within the backplane.  In other cases, it is desirable
  to have a redundant connection from the hub to higher level concentrators.
  This second case is commonly referred to as dual homing.  Either of these 
  configurations requires the use of a concentrator at the top of the tree.
 
  Note, the modules connected via the hub backplane are single attach 
  modules; the dual homing pertains to the connection between the hub based 
  tree and the external concentrator. 


    Diagram #15: Dual Homed Connections to an FDDI Network

			      Front Panel Ports
                                                          A         B
                                                          | M M M M |
                                                          | | | | | |
	+-------------+		+-------------+		+-+-+-+-+-+-+-+	
	|Switch       |		|Switch       |		|Concentrator |
	+-+---------+-+		+-+---------+-+		+-+-----------+
	  |	    |		  |	    |		  |	    
	  |	    +-------------+         +-------------+         
	  M	    S		  M	    S		  M	    

				Backplane Ports


  Diagram #16: Building Block Representation of Diagram #15 Configuration

                                                      A     B
                                                      |     |
              +-------+        +-------+            +-+-----+-+
              |Nonroot|        |Nonroot|            | Root    |
              |  MS   |        |  MS   |            | Primary |
              +-+---+-+        +-+---+-+            +-+-------+
                |   |            |   |                |   
                M   S            M   S                M   



  EXAMPLE 5: TREE EXTENSION 

  In cases where it is desirable to tree together multiple hubs or hub modules
  (e.g., when more than 8 modules are required in the same closet), it is 
  possible to configure an FDDI module with front panel connections (DECswitch
  900EF or DECconcentrator) at the bottom of the tree to have an M port out 
  the front panel.  This M port can be used to connect an external module or 
  an additional hub to the hub based tree. 




  Diagram #17: Tree Connections to an FDDI Network

                                                                    S
			      		   Front Panel Ports        |
                           +----------------------------------------+-----+
                           |                    DEChub 900          |     |
                    +-------------+                                 |     |
                    |S     |      |M                                |     |
	+-----------+-+	   |	+-+-----------+		+-----------+-+	  |
	|FDDI Module  |	   |	|  DECswitch  |		|  DECswitch  |   |
	+-+-----------+	   |	+-----------+-+		+-+---------+-+   |
	  | 	    	   |	  	    |		  |	          |
	  M 	           |                +-------------+               |
	  	    	   |	  	    S		  M	          |
         External          +----------------------------------------------+
	  Module			    Backplane Ports


  Diagram #18: Building Block Representation of Diagram #17 Configuration

                    S            M                        S
                    |            |                        |
              +-----+-+        +-+-----+            +-----+-+
              |Nonroot|        |Nonroot|            |Nonroot|
              |   M   |        |   S   |            |   M   |
              +-+-----+        +-----+-+            +-+---+-+
                |                    |                |   
                M                    S                M   



  FAULT TOLERANCE IN TREES

  If a concentrator or bridge/switch in a tree fails, the FDDI ring will be 
  broken, and the stations below the break will be isolated from the rest of 
  the network.  Two mechanisms then come into play.  If the module is detected 
  as being "unavailable", Auto Healing will detect the condition and 
  reconnect the two neighboring modules in the DEChub via the backplane, 
  thereby healing the ring.  If the module is physically removed, HUB 
  Management will detect the removal and reconnect the two neighboring FDDI 
  modules via the backplane, thereby healing the ring.  This is a distinct 
  advantage that FDDI modules in a DEChub have over individual non-hub-based
  FDDI products.




  DUAL RING CONFIGURATIONS

  EXAMPLE 1: DUAL RING CONCENTRATORS WITH CONNECTION TO EXTERNAL DUAL RING

  In the Diagram #19 configuration, all the concentrators connect directly to 
  the dual ring.  Concentrator #3 has a front panel port act as the external 
  B-port connection to the dual ring, and one of its backplane ports act as 
  the A-port.  With Concentrator #2, both backplane ports are used as the A/B 
  connections to the dual ring.  Concentrator #1 has the B-port connection to 
  the dual ring via the backplane and the dual ring exits via a front panel
  port that is acting as an A-port.


  Diagram #19: DECconcentrator Dual Ring Connections to an FDDI Network

			      Front Panel Ports

          A                                                         B
	  | M M M M M		  M M M M M M 		  M M M M M |
	  | | | | | |		  | | | | | |		  | | | | | |
	+-+-+-+-+-+-+-+		+-+-+-+-+-+-+-+		+-+-+-+-+-+-+-+	
	|   CON #1    |		|   CON  #2   |		|   CON  #3   |
	+-----------+-+		+-+---------+-+		+-+-----------+
	  	    |		  |	    |		  |	    
	  	    +-------------+         +-------------+         
	  	    B		  A	    B		  A	    

				Backplane Ports



  Diagram #20: Building Block Representation of Diagram #19 Configuration

                A                                         B
                |                                         |
              +-+-----+        +-------+            +-----+-+
              | Trunk |        | Trunk |            | Trunk |
              |   B   |        |  A B  |            |   A   |
              +-----+-+        +-+---+-+            +-+-----+
                    |            |   |                |
                    B            A   B                A



  EXAMPLE 2: DUAL RING SWITCHES WITH CONNECTION TO EXTERNAL DUAL RING

  DECswitch 900EFs can be dual-ringed just like DECconcentrator 900MXs;
  Diagram #21 shows that configuration.  Switch #3 has the B-port assigned to 
  one front panel port and the A port assigned to a backplane port.  Switch #2 
  has the A and B ports assigned to the backplane ports only (front panel ports 
  are not active nor usable).  Switch #1 has the B-port assigned to a backplane 
  port while the A-port is assigned to a front panel port.  



  Diagram #21: Dual Ring Connections for DECswitch 900EFs

			      Front Panel Ports
	    A							  B
	    |							  |
	+---+---------+		+-------------+		+---------+---+	
	|  SWITCH #1  |		|  SWITCH #2  |		|  SWITCH #3  |
	+-+---------+-+		+-+---------+-+		+-+---------+-+
	  	    |		  |	    |		  |	    
	  	    +-------------+         +-------------+         
	  	    B		  A	    B		  A	    

				Backplane Ports


  Diagram #22: Building Block Representation of Diagram #21 Configuration

                A                                           B
                |                                           |
              +-+-----+          +-------+            +-----+-+
              | Trunk |          | Trunk |            | Trunk |
              |   B   |          |  A B  |            |   A   |
              +-----+-+          +-+---+-+            +-+-----+
                    |              |   |                |
                    B              A   B                A


  Obviously, a fourth option is available, which is to assign both A and B to 
  the front panel ports (the Stump Primary building block), which would allow 
  a single DECswitch 900EF or DECconcentrator in a DEChub 900 to connect up 
  to an external FDDI backbone network.


  EXAMPLE 3: PESWITCH CONNECTIONS TO AN EXTERNAL DUAL RING

  One option for PEswitch 900TXs is to configure them in a dual ring, but 
  remember that there are NO front panel FDDI connections on a PEswitch 900
  Therefore dual ring connections to a PEswitch 900TX require that FDDI be 
  brought INTO the DEChub backplane via a DECswitch 900EF or a DECconcentrator,
  and OUT of the DEChub backplane via a DECswitch 900EF or a DECconcentrator.
  In other words, TWO DECswitch or DECconcentrator modules are needed for 
  dual ring connections of PEswitch 900TXs to an external FDDI network.  


  Diagram #23: Dual Ring Connections for PEswitch 900TX

			      Front Panel Ports
            A                                                       B
	    |					          M M M M M |
	    |						  | | | | | |
	+---+---------+		+-------------+		+-+-+-+-+-+-+-+	
	|  DECSWITCH  |		|  PESWITCH   |		|CONCENTRATOR |
	+-+---------+-+		+-+---------+-+		+-+---------+-+
	  	    |		  |	    |		  |	    
	  	    +-------------+         +-------------+         
	  	    B		  A	    B		  A	    

				Backplane Ports



  Diagram #24: Building Block Representation of Diagram #23 Configuration

                A                                           B
                |                                           |
              +-+-----+          +-------+            +-----+-+
              | Trunk |          | Trunk |            | Trunk |
              |   B   |          |  A B  |            |   A   |
              +-----+-+          +-+---+-+            +-+-----+
                    |              |   |                |
                    B              A   B                A



  EXAMPLE 4: SELF CONTAINED DUAL RING ON BACKPLANE

  To create a DUAL RING that is completely contained in the DEChub 900 back-
  plane, you need to connect all the backplane ports of the FDDI modules 
  together.  


  Diagram #25: Self-Contained Dual Ring in the Backplane

			      Front Panel Ports

	  M M M M M M		  	 		  
	  | | | | | |		  			  
	+-+-+-+-+-+-+-+		+-------------+		+-------------+	
	|   CON  #1   |		| PESWITCH #1 |		| PESWITCH #2 |
	+-+---------+-+		+-+---------+-+		+-+---------+-+
	  |	    |		  |	    |		  |	    |
	  |	    +-------------+         +-------------+         |
	  |	    B		  A	    B		  A	    |
	  +---------------------------------------------------------+
	  A			Backplane Ports			    B


  NOTE: You can create a self-contained dual ring in the DEChub backplane 
	with PEswitches by themselves, or PEswitches and DECconcentrators and
	DECswitches, since there is NO EXTERNAL connection to an FDDI DUAL RING 
	required.  Note that the DECconcentrator in Diagram #25 is providing M 
	port tree connections to externally-treed FDDI stations (bridges, 
	concentrators or end user stations with S, A or B ports), and is NOT 
	connected to an external M port (NOT treed off an external concentra-
	tor's M port).


  MULTIPLE RINGS 

  Just repeat configuration #19 (the ring) twice and don't interconnect them.  
  You can support FDDI concentrators or FDDI switches (note that the DECswitch 
  900EF is a power hungry module, so all eight slots cannot be populated with 
  DECswitch 900EFs) in all eight slots of the DEChub 900, and interconnect them 
  across the backplane into a single FDDI network, or into a maximum of four 
  independent FDDI networks. 
  
  




  FAULT TOLERANCE in DUAL RINGS

  When a concentrator or switch in a dual ring is removed (hot swapped), the 
  FDDI ring will wrap per the FDDI standard.  If the removed module has both 
  the A and B ports connected to the DEChub backplane, then the DEChub Manage-
  ment will detect the removal and reconnect the two neighboring FDDI stations 
  in the DEChub via the backplane thereby "un-wrapping" the ring.  If a module 
  is detected as being "unavailable", the HUB manager will also patch around 
  the module (as long as AUTO HEALING has been enabled).  This is a distinct 
  advantage that FDDI modules in a DEChub have over individual non-hub-based 
  FDDI products.

  NOTE:	Ring wrap occurs much faster than "backplane healing", so it will 
	always occur first and then the DEChub management will reconnect 
	the DAS stations via the backplane and the dual ring will "un-wrap".

  NOTE: Fault recovery (unwrapping of the dual ring in the DEChub backplane)
	is supported in all FDDI DEChub modules.


  Looking at Diagram #26, if Concentrator #1 is hot swapped, Concentrator #2 
  and Switch #1 can continue communicating with each other and all other FDDI 
  stations on the DAS backbone, since Concentrator #2 will wrap the FDDI 
  dual ring.  If Concentrator #2 fails, Concentrator #1 and Switch #1 will 
  wrap the dual ring and communications can continue.  Within seconds of this  
  particular ring wrap where Concentrator #2 has become "unavailable", Hub 
  Management will automatically reconnect Switch #1 to Concentrator #1 and the 
  dual ring will unwrap.  If, at a later time, another concentrator of the same 
  type is inserted in the same slot that held Concentrator #2, the replacement 
  concentrator will be reinserted into the ring via the Auto Healing feature. 


  Diagram #26: Ring Configuration

			      Front Panel Ports

                    B                                             A
	  M M M M M |		  M M M M M M		  	  |
	  | | | | | |		  | | | | | |		  	  |
	+-+-+-+-+-+-+-+		+-+-+-+-+-+-+-+		+---------+---+	
	|   CON  #1   |		|   CON  #2   |		|  SWITCH #1  |
	+-+---------+-+		+-+---------+-+		+-+---------+-+
	  	    |		  |	    |		  |	    
	  	    +-------------+         +-------------+         
       		    A		  B	    A		  B

				Backplane Ports



  TOKEN ORDERING OF TREES OR DUAL RINGS

  A new feature for Wave 3 is the introduction of a defined token order 
  for FDDI dual rings or trees in the hub.  The token flow, defined as the 
  order in which the token visits the MACs, is essentially from slot 1 
  towards slot 8, whether the backplane network is a dual ring or a tree.  
  If there are multiple FDDI networks, each network independently orders 
  the token flow from lowest slot to highest slot, as closely as is allowed 
  by the FDDI rules.  This algorithm was designed to ensure that repaired 
  modules return to the same token order that had been assigned prior to 
  the occurrence of a module fault.  It also matches the power shedding 



  algorithm (which sheds modules from slot 1 towards slot 8).  The following
  examples illustrate the concept. 

  Please refer to Diagram #27 for the following discussion.  Suppose a hub is 
  configured as a dual ring, with FDDI modules in slots 1,2,3,4,6, and 8.  
  Assume further that the front panel A port is found on the module in slot 4, 
  and the B port on the module in slot 8.  So the token, which is flowing
  on the primary ring, enters the hub at slot 4 and exits from slot 8. 

  A ringmap will show the order of token flow, based on the ordering of the 
  MACs in the ring.  In this case, HUBwatch will configure the backplane so 
  that the token enters the A port of slot 4, encounters the MAC for slot 4, 
  and the next MAC it sees is in slot 1.  The token flows, in order, through 
  the MACs in slots 1,2,3, 6, and finally slot 8.  In this case a ringmap 
  would record the token order as 4>1>2>3>6>8.  Note that, in order to 
  accomplish this ordering, the built-in DEChub management has automatically 
  connected the B port of Slot 4 to the A port of Slot 1, and so on for the 
  other modules, so that the token flows in the correct order. 


     Diagram #27: Token Flow through Dual Ringed DEChub 900 modules

							@ = location of MAC

  secondary   <............<...........                    ...<.......<
                                      :                    :
  primary      >----------->--------+ :                    : +---->----->
                                    | :                    : |
                                    v ^                    : ^
                                   A| :                    : |B
         +----+                   +-+-:+                 +-:-+-+  
         |   A|                   | | :|                 | : @ |
         | +--+-------<-----------+@+ :|                 | : | |
         | | .|...........>.......|...:|                 | : | |
         | | :|                   |B   |                 | v | |
         | | :|                   +----+                 | : ^ |
         | | :|   +---+   +---+                +---+     | : | | 
         | | .|   |   |   |   |                |   |     | : | |
         | | :|   |A B|   |A B|                |A B|     |A: | |
         | | :|...|...|...|...|.....<..........|...|.....|.: | | 
         | |  |   |   |   |   |                |   |     |   | |
         | +-@+->-+--@+---+--@+----------->----+--@+-->--+---+ |
         |   B|   |   |   |   |                |   |     |     |
         +----+   +---+   +---+                +---+     +-----+  
     Slot  1       2       3        4      5     6    7     8

                 Token Order on Ring MAP = 4>1>2>3>6>8         


  Refer to Diagram #28 for the following discussion.  Suppose the same 
  modules are to be configured as a tree.  The modules are in slots 1,2,3,
  4,6, and 8, and the front panel S port is found on the module in slot 
  4.  So the token enters and exits the hub at slot 4. 

  A ringmap will show the order of token flow, based on the ordering of the 
  MACs in the ring.  FDDI rules require that a station's MAC be located
  immediately prior to the port where the token exits the station.  So in 
  this case, the token enters the S port of slot 4 and the  token flows, in 
  order, through the MACs in slots 1,2,3,6,8 and finally slot 4.  The physical 
  connection to do this requires that the S port of slot 8 connect to the M 
  port of slot 4.  In this case a ringmap would record the token order as  
  1>2>3>6>8>4. 




      Diagram #28: Token Flow through Treed DEChub 900 modules

							@ = location of MAC

      to ring  <-----------<----------+
    from ring  >----------->--------+ |                    
                                    | |                    
                                    v ^                    
                                   S| |                    
         +----+   +---+   +---+   +-+-+-+                 +-----+  
         |    |   |   |   |   |   | | @ |                 |S    |
         |    |   |   |   |   |   | | +-+-----<-----------+@--+ |
         |    |   |   |   |   |   | +---+----------->-----+-+ | |
         |    |   |   |   |   |   |    M|                 | | | |
         |    |   |   |   |   |   |     |      +----+     | v ^ |
         |    |   |   |   |   |   +-----+      |    |     | | | |
         | +--+---+---+---+---+------<---------+----+-----+-+ | | 
         | |  |   |   |   |   |                |    |     |   | |
         | +-@+---+--@+---+--@+------>---------+---@+-----+---+ |
         |   S|   |M S|   |M S|                |M  S|     |M    |
         +----+   +---+   +---+                +----+     +-----+  
     Slot  1        2       3        4      5     6    7     8



                Token Order on Ring MAP = 1>2>3>6>8>4



  QUICK PC TRACE OPTION FOR CONCENTRATORS

  A Quick PC Trace option is supported for all DEChub FDDI concentrator modules.
  As defined by the FDDI standard, a PC Trace is a method for recovering from a 
  stuck beacon condition.  All stations that are in the fault domain perform 
  some level of hardware diagnostic test before attempting to re-enter the FDDI 
  network.  Normally, concentrator modules run their full set of hardware diag-
  nostics.  This will take approximately one minute, but gives the highest level
  of assurance that any hardware failure would be found.  In order to decrease 
  the recovery time following a trace, the quick PC Trace option has been added.
  When this option is enabled, only a subset of the hardware diagnostics is run 
  whenever a PC-trace occurs.  The reduced set of diagnostic tests completes in 
  approximately 10 seconds.  This feature can be enabled and disabled only from 
  the configuration screen of the module's setup port. 

  Note: The DECswitch 900EF and the PEswitch 900TX do not have this optional
	feature since they normally recover from PC Traces very rapidly (less 
	than 10 seconds).  This is due to the fact that these products are FDDI 
	end stations and have a much smaller set of FDDI-specific diagnostics 
	to run than an FDDI concentrator. 


  SUMMARY OF IMPORTANT CONFIGURATION FEATURES

  This section is a short review of the FDDI configuration features for 
  the DEChub FDDI modules:

  o ALL DEChub FDDI modules now support dual ring connections (A and B ports)
    and tree connections (M and S ports) across the DEChub 900 backplane, 
    or out the front panel of individual modules in a DEChub 900. 

  o ALL DEChub FDDI modules now support dual ring connections (A and B ports)
    and tree connections (M and S ports) when configured standalone in either 
    a DEChub ONE or a DEChub ONE-MX.  (Note, PEswitch 900TX requires DEChub 
    ONE-MX with appropriate MODPMDs for standalone FDDI connections.)



  o Multiple independent FDDI networks (trees and/or dual rings) can be 
    supported across the backplane of the DEChub 900. 

  o An automatic healing capability to patch around failed modules is 
    supported for both trees and dual rings across the backplane of the 
    DEChub 900. 

  o A Quick PC Trace capability has been added to concentrators, to minimize
    the time it takes to return to operation following a PC Trace.  This 
    option is selectable from the module setup screens, whether the module 
    is installed in a DEChub 900, a DEChub ONE, or a DEChub ONE-MX.

  o DEChub 900s can participate in a dual ring of trees topology as either part 
    of the dual ring or as part of the tree; however, a dual ring of trees 
    topology is not supported across the backplane (see Diagram #29).  A dual 
    ring of trees can be constructed by first building a dual ring, then a tree,
    and connecting them together with a cable on the front panel (see Diagram 
    #30).  Note though, that while they will all be in one network, HUBwatch 
    will need to manipulate the connections as though they are in unconnected 
    LANs. 



  Diagram #29: ILLEGAL Dual Ring of Trees Topology

				Front Panel Ports 

    A                            B          
    |                            |                           
  +-+----------+      +----------+-+      +-----------+      +------------+
  |            |      |            |      |           |      |            |
  +-+--------+-+      +-+--------+-+      +-+-------+-+      +-+--------+-+
             |          |        |          |       |          |        |      
             +----------+        +----------+       +----------+        M
             B          A        M          S       M          S            

				Backplane Ports


  Diagram #30: LEGAL Dual Ring of Trees Topology

				Front Panel Ports 

    A                   B        M          S
    |                   |        +----------+
    |                   |        |          |                
  +-+----------+      +-+--------+-+      +-+---------+      +------------+
  |            |      |            |      |           |      |            |
  +-+--------+-+      +-+--------+-+      +-+-------+-+      +-+--------+-+
             |          |                           |          |        |      
             +----------+                           +----------+        M
             B          A                           M          S            

				Backplane Ports




  o Dual-homing to multiple FDDI modules in a DEChub 900 can be supported two
    ways: 
	1) Each module can be individually dual-homed via its front panel 
	   ports (assuming the module has front panel ports)
	2) One concentrator module can be dual-homed and the other FDDI 
	   modules can be treed off of that concentrator

  o Additional DEChubs or standalone FDDI modules can be "chained" off of ANY
    DEChub FDDI module (including switches) configured as a tree building
    block.  Previously, only concentrators had this capability.

  o Attempting to build a self-contained dual ring configuration in the DEChub 
    with eight FDDI modules will NOT work.  This is due to the fact that 
    there are 14 backplane channels that can be used for FDDI connections and 
    16 channels would be required to interconnect 8 modules in a hub-contained 
    dual ring.  Note that this configuration can be accomplished with 14 back-
    plane channels AND one cable between two devices' front panel ports.

  o Attempting to build a self-contained tree configuration in the DEChub 
    with eight FDDI modules WILL work.  This configuration can be built 
    because it requires only 14 backplane channels. 
    
  o While the FDDI defaults on the DECswitch 900EF and the DECconcentrator 
    900MX and DECconcentrator 900TH are to the front panel ports, and not the 
    backplane ports, the FDDI default for the PEswitch 900TX is to the 
    backplane.  This is because there are NO front panel FDDI ports on a 
    PEswitch 900TX.  Many people overlook this when considering default 
    configurations.

  o FDDI modules installed in a DEChub ONE-MX can configure their FDDI ports 
    either with HUBwatch, or via an FDDI port configuration menu on the 
    DEChub ONE-MX setup port. 




  Diagram #31: Valid FDDI Configurations for DEChub FDDI Modules


    A                 B    A                  B   A                        B 
     +---------------+      +----------------+     +----------------------+
 +---+DECswitch 900EF+------+ PEswitch 900TX +-----+DECconcentrator 900MX +---+
 | +-+ in DEChub ONE +------+in DEChub ONE-MX+-----+or 900TH in DEChub ONE+-+ |
 | | +---------------+      +----------------+     +----------------------+ | |
 | |									    | |
 | |<-----Dual Ring							    | |
 | |									    | |
 | |	     B		       A		  B			   A| |
 | |          +---------------+                    +----------------------+ | |
 | +----------+	DEChub 900MS  +--------------------+DECconcentrator 900MX +-+ |
 +------------+	with multiple +--------------------+or 900TH in DEChub ONE+---+
	      | FDDI modules  |                    +---+-+-------+-+------+
	      +--+-+-----+-+--+                       M| |      M| |
                M| |    M| +--------------------+      | |       | |
                 | |     +--------------------+ |      | |       | |
                 | |                          | |      | |       | |
       Dual      | |                          | |      | |       | |
       Homing    | |   +-------------------------------+ |       | |
                 | |   | +-------------------------------+       | |
                 | |   | |                    | |     +----------+ |
                A| |  B| |                   A| |    B| +----------+
       	      +--+-+---+-+-+		   +--+-+-----+-+--+ 
	      |	   Any 	   |		   | DEChub 900MS  |
	      |	Standalone |		   | with multiple |
	      |Concentrator|		   | FDDI modules  |
	      +-----+-+----+		   +--+-+------+-+-+
                   M| |                      M| |     M| |
                    | +--------------+  +-----+ |      | +-----+
                    +--------------+ |  | +-----+      +-----+ |
	                          A| |  | |B               S | |
 				+--+-+--+-+-----+       +----+-+-----+
				|  DEChub 900   |       |    Any     |
				| with multiple |       | Standalone |
				| FDDI modules  |       | FDDI module|
				+-+-+-------+-+-+       +------------+
                                 M| |      M| | 
                                  | |       | |
                          +-------+ |       | +----+
                          | +-------+       +----+ |
                          | |                    | |
                         S| |                   S| |     
       	         +--------+-+-+		      +--+-+----------+ 
    	         |     Any    |		      | DEChub 900MS  |
	         | Standalone |		      | with multiple |
	         | FDDI Module|		      | FDDI modules  |
 	         +------------+		      +---------------+


  


  Appendix A - FDDI Basics

  OVERVIEW

  Fiber Distributed Data Interface (FDDI) is a set of ANSI/ISO standards for 
  a 100 Mbps token passing ring which uses  Multimode fiber, Single mode fiber, 
  Unshielded Twisted Pair, Screened/Shielded Twisted Pair or any combination 
  of the four as the transmission medium.  The most basic FDDI network is 
  constructed of two independent rings, referred to as the "dual ring".  The 
  dual ring connects to each FDDI station in the network.  Each ring can span 
  a total distance of up to 100 km, making for an allowable distance of up to 
  200 km (2 x 100 Km/ring) for the FDDI dual ring.  As many as 500 stations may 
  be attached to the dual ring; a typical configuration will usually have no 
  more than 200 stations. 


  Diagram A1: FDDI Dual Ring


	+---------+		+---------+		+---------+
  +-----+  FDDI   +-------------+  FDDI   +-------------+  FDDI   +------+
  | +---+ Station +-------------+ Station +-------------+ Station +----+ |
  | |   +---------+             +---------+             +---------+    | |
  | |                                                                  | |
  | |<----- Dual Ring  (200 km total distance)                         | |
  | |                                                                  | |
  | |	+---------+		+---------+		+---------+    | |
  | +---+  FDDI   +-------------+  FDDI   +-------------+  FDDI   +----+ |
  +-----+ Station +-------------+ Station +-------------+ Station +------+
        +---------+             +---------+             +---------+    


  All FDDI networks operate as logical token rings, in which the right to 
  transmit is granted by the possession of a token.  There is one token per 
  ring, and it is passed from station to station, according to a set of rules 
  known as the "timed token protocol".  A station which wishes to transmit on 
  the ring first "captures" the token.  It then transmits frames for a period 
  of time determined by the timed token rules, and then "releases" the token 
  immediately after completing its transmission.  A transmitting station is 
  also responsible for removing the frames it transmitted from the ring, once 
  they have circled the ring and returned to the station.  This process is 
  called "frame stripping". 



  STATION TYPES

  FDDI networks are constructed using two types of devices, referred to as 
  "Stations" or "Concentrators".  Stations are of two types: Dual Attach 
  Stations (DAS) and Single Attach Stations (SAS).  Dual Attach Stations 
  attach directly to the dual ring.  Single Attach stations connect to the 
  ring via a Concentrator, which can be of two types: Dual Attach 
  Concentrators (DAC) which attach directly to the dual ring and Single 
  Attach Concentrators (SAC) which attach to the ring through other 
  concentrators. 



  Diagram A2: FDDI Station Types
                                   |<  Phys Connection  >|
                                   |                     |
                                   |                     |
	+---------+      +---------+     Phys Link	 +---------+
  +-----+   DAS   +------+   DAS   +---------------------+   DAS   +-----+
  | +---+(station)+------+(station)+---------------------+(station)+---+ |
  | |   +---------+      +---------+     Phys Link       +---------+   | |
  | |                                                                  | |
  | |            		                                       | |
  | |                                                                  | |
  | |             |< Phys Conn >|         |< Phys Conn >|              | |
  | |	+---------+		+---------+		+---------+    | |
  | +---+   DAS   +-------------+   DAC   +-------------+   DAC   +----+ |
  +-----+(station)+-------------+  (con)  +-------------+  (con)  +------+
        +---------+     ^       +--++-----+             +---++----+ 
			|	   ||			    ||      
		    Dual Ring	   ||   		    ||      
				+--++-----+		+---++----+ 
				|   SAS   |		|   SAC   |
				|(station)|             |  (con)  | 
				+---------+		+---++----+ ---
							    ||       ^
	con = concentrator			Tree -----> ||      Phys
							    ||      Conn
							    ||       v
							+---++----+ ---
							|   SAS   |
							|(station)|
							+---------+
	

  All devices, whether single attach or dual attach, connect to each other 
  via a full duplex connection known as a "physical connection".  Each 
  physical connection is comprised of two "physical links" (one fiber per
  physical link).  Single Attach Stations and Single Attach Concentrators 
  connect to a concentrator, or another station, via one physical connection.  
  Dual Attach Stations and Dual Attach Concentrators connect to each other via 
  two physical connections. 



  MEDIA TYPES and SUPPORTABLE DISTANCES

  FDDI allows links to be built from four different media types.  Important 
  characteristics of these media types are:

  Multimode fiber: 62.5/125 micron graded index fiber.  The power budget for 
  these links is 11 dB.  The maximum distance for a link is 2 km. 

  Singlemode fiber: 8 to 10 micron fiber.  The power budget for these links is 
  22 dB.  The maximum distance for a link is 60 km. 
  
  Unshielded twisted pair: Category 5 100 ohm UTP cable.  The maximum distance 
  for a link is 100 meters. 

  Screened twisted pair: Category 5 100 ohm screened cable.  The maximum 
  distance for a link is 100 meters. 

  Shielded twisted pair: 150 ohm Shielded Twisted pair, equivalent to 
  IBM Type 1 cable.  The maximum distance for a link is 100 meters. 




  STATION CONFIGURATIONS

  Stations and Concentrators are identified by the types of "ports" that they 
  use to attach to other stations.  There are four port types, referred to as 
  A, B, M  and S.  ALL concentrators, whether SAC or DAC, are identifiable by 
  the presence of "M" ports, to which other stations or concentrators can 
  attach.  If the concentrator also has an S port, it is a SAC; if it has A 
  and B ports it is a DAC.  A Single Attach Station has an "S" port for 
  connection to a concentrator M port.  Dual Attach Stations have A and B 
  ports for attachment to other stations in the dual ring, or to concentrator 
  M ports.  

  The FDDI rules require that a station's MAC be physically located 
  immediately prior to the port where the token exits the station.  For Dual 
  Attach devices that means that the MAC will be immediately ahead of the B 
  port; for Single Attach devices it will be immediately ahead of the S port. 


  Diagram A3: FDDI Port Types


	+---------+		+---------+	 	+---------+
  +-----+   DAS   +----->-------+   DAS   +------>------+   DAS   +------+
  |     |A       B|             |A       B|             |A       B|      |
  | +---+         +-------------+         +-------------+         +----+ |
  | |   +---------+             +---------+             +---------+    | |
  | |                                                                  | |
  | |            		                                       | |
  | |		                                                       | |
  | |                                                                  | |
  | |	+---------+		+---------+		+---------+    | |
  | +---+   DAS   +-------------+   DAC   +-------------+   DAC   +----+ |
  |     |B       A|             |B       A|             |B       A|      |
  +-----+         +------<------+   M     +------<------+    M    +------+
        +---------+             +--++-----+             +---++----+    
				   ||			    ||
		        	   ||                       ||
		        	   ||			    ||
				+--++-----+		+---++----+
                                |   S     |             |    S    |
				|         |             |         |
				|   SAS   |		|   SAC   |
				+---------+		|         |
							|    M    |
							+---++----+
							    ||
							    ||
							+---++----+
							|    S    |
							|         |
							|   SAS   |
							+---------+
	




  PHYSICAL TOPOLOGIES

  Although all FDDI networks are logical rings, they may be constructed
  using various physical topolgies.  There are three types of topologies:

	1) Dual Rings
	2) Trees
	3) Dual Ring of Trees

  Dual Ring topologies are constructed solely of Dual Attach Stations.  The 
  A port of one station connects to the B port of the next station, forming a 
  physical connection between the two stations.  This can be repeated until 
  up to 500 stations are included in the dual ring.  Remember that there are 
  two physical links per physical connection, so when a ring is formed, there 
  are two operating links between each station.  This allows for two 
  independent rings to be formed; these rings are referred to as the primary 
  ring and the secondary ring.  The Primary ring enters the station on the A 
  port, and exits on the B port.  The Secondary ring enters the station on the 
  B port and exits on the A port.  
  
  In general, all data traffic between stations is carried on the primary ring, 
  and the secondary ring is idle during this time.  The FDDI standards actually
  allow both rings to be used for carrying data traffic, but in practice this 
  is rarely done.  The common practice is to use the secondary ring as a backup 
  for the primary ring. 

  A benefit of having dual rings is that, in case of a failure, the secondary
  ring can be used as a backup ring to the primary ring.  If a station detects 
  that one of its A or B ports has failed, it "wraps" the primary and secondary 
  rings together, thus restoring operation to the other stations in the ring.  
  Wrapping occurs very quickly, usually in well under a half a second. 

  FDDI also allows the construction of tree configurations, which start with a 
  standalone concentrator at the "top" of the tree.  Stations or other 
  concentrators connect to this concentrator, and "branch out" from the top of 
  the tree.  The  distinguishing feature of a tree is the connection to an M 
  port.  Single attach stations (S ports) typically connect to a concentrator,
  but Dual Attach Stations (A and B ports) can also connect to the M ports.  
  A major advantage of the use of trees built with concentrators is the ability
  of the concentrator to electronically disconnect stations from the ring in 
  case of failure, or, by management command. 

  The third, and most common, FDDI configuration is referred to as the Dual 
  Ring of Trees.  This is a very robust topology, which is a hybrid of the Dual 
  Ring and Tree topologies.  Dual Attach Concentrators and Dual Attach Stations 
  attach together in a dual ring, with treed stations connected to the 
  concentrators' M ports.  The concentrator connects stations attached to 
  these M ports into the token flow of the primary ring. 




  Diagram A4: FDDI Topologies

					   Primary Ring
						|
	+---------+		+---------+	v	+---------+
  +-----+   DAS   +----->-------+   DAS   +-------------+   DAS   +------+
  |     |A       B|             |A       B|             |A       B|      |
  | +---+         +-----<-------+         +-------------+         +----+ |
  | |   +---------+             +---------+     ^       +---------+    | |
  | |                                           |                      | |
  | |<--------Dual Ring 	           Secondary Ring              | |
  | |                                                                  | |
  | |	+---------+		+---------+		+---------+    | |
  | +---+   DAS   +-------------+   DAC   +-------------+   DAC   +----+ |
  +-----+B       A+------<------+B       A+------<------+B       A+------+
        +---------+             +--++-----+             +---++----+    
				  M||			   M||
                                   ||                       ||
		        	  S||			   S||<-----Tree
      Dual Ring of Trees	+--++-----+		+---++----+
     Configuration Example	|   SAS   |		|   SAC   |
				+---------+		+---++----+
							   M||
   Stations in the tree are                                 ||
   connected to the primary ring                            ||
							   S||
							+---++----+
							|   SAS   |
							+---------+


  STATION STATES

  The internal configuration of the paths within a station is described by 
  something called the "station state".  Stations can be in one of two states: 
  "thru or "wrapped".  DAS or DAC stations in an unwrapped dual ring will be 
  in the "thru" state.  If a station detects that it should wrap the rings 
  together, that station will be in the "wrap" state.  Only two DAS or DAC can 
  be wrapped in a properly wrapped dual ring; this fact is used to locate the 
  points of failure if a ring wraps unexpectedly. 

  When wrapping, a station can adjust its internal configuration in a number 
  of ways, called out by the FDDI standard.  Each of these configurations has 
  a different name, and a station is required to use that name when telling 
  management about its internal configuration.  All Digital SAS and SAC 
  devices will report wrap_S in their station state reports.  All Digital DAS 
  and DAC products will report c_wrap_A or c_wrap_B in their station state 
  reports.  This means "concatenated wrap A" or "concatenated wrap B".  For 
  example, C_wrap_A means that the B port is not active, the station has 
  wrapped the ring, and the A port is the active port. 




  Diagram A5: Wrapped FDDI Ring


	+-----------+ 		  +---------+		  +---------+
  +-----+  DAS    +-+-------------+  DAS    +-------------+  DAS    +------+
  |     |  FDDI   | |             |  FDDI   |             |  FDDI   |      |
  | +---+ Station +-+-------------+ Station +-------------+ Station +----+ |
  | |   +-----------+ \           +---------+             +---------+    | |
  / /                  \                                                 | |
     <--- Break         Wrapped                                          | |
  / /     in Cable      Stations                                         | |
  | |                  /                                                 | |
  | |	+-----------+ /		+---------+		+---------+      | |
  | +---+  DAS    +-+-----------+  DAS    +-------------+  DAS    +------+ |
  |     |  FDDI   | |           |  FDDI   |             |  FDDI   |        | 
  +-----+ Station +-+-----------+ Station +-------------+ Station +--------+
        +-----------+           +---------+             +---------+    

  

  CONNECTION RULES

  One of the most confusing parts of FDDI is the operation of the FDDI 
  connection rules.  These rules are necessary in order to prevent the 
  formation of non-useful topologies that can disrupt communication among 
  stations in the ring, and also to make sure that the ring will always 
  converge to a pre-defined topology.  For example in Diagram A6, if the A 
  port of DAC#1 is connected to the B port of DAC#2, and then the B port of 
  DAC#1 is connected to an M port of DAC#3, the B port of DAC#1 will make the 
  connection to the M port of DAC#3, and the A port will break its connection 
  to DAC#2.  This behavior is referred to as "taking the tree connection over 
  the ring connection".  This particular rule ensures that the same tree 
  topology always is formed, independent of the order in which the physical 
  connections are made. 


  Diagram A6: FDDI Connection Rules

	+---------+		+---------+		+---------+
  +-----+   DAS   +----->-------+   DAS   +------>------+   DAS   +------+
  | +---+         +-------------+         +-------------+         +----+ |
  | |   +---------+             +---------+             +---------+    | |
  | |                                                                  | |
  | |<--------Dual Ring 	                                       | |
  | |                                                                  | |
  | |	+---------+		+---------+		+---------+    | |
  | +---+   DAS   +-------------+   DAC   +-------------+ DAC #3  +----+ |
  +-----+         +------<------+         +------<------+   M     +------+
        +---------+             +--++-----+             +---+-+---+    
				   			    | |
		        	   			  S ^ V <-----Tree
      				+----------+		+---+-+----+
				|  DAC #2  |            |   | |      |
     				|          +------------+   +-+    |
                                |         B+------------+A  DAC #1 |
				+----------+	 ^	+----------+
                                                 |
				    Rejected Dual Ring Connection
  





  FDDI rings are formed by the completion of physical connections between 
  pairs of ports.  In order to form the connection, the ports signal various 
  parameters necessary for the successful completion of the connection. 
  When a port attempts to form a connection with another port, it indicates
  both its own port type, and whether it wishes to form a connection with 
  the port type that it sees at the other end.  One type of connection, the 
  M-M connection, is always rejected.  Other types, such as A-A and B-B are 
  undesirable, but will be formed if the connection rules of one of the 
  stations allows the connection.  For example, if a Digital FDDI product 
  attempts to form an A-A connection with another Digital FDDI product the 
  connection will not be made, because both ports signal that they do not 
  wish to connect to a remote A port.  If the connection was made to a non-DEC
  station, and that station's A port signaled that it wanted to take the 
  connection to the Digital A port, the Digital station would honor the 
  request, per the ANSI standard's rules for connection of ports.  The 
  result, however, would be that the stations would be connected together, 
  but one stations's MAC would be in the primary ring, and the other station's 
  MAC would be in the secondary ring.  Since the rings are isolated in the 
  non-wrapped case, the stations are unable to talk to one another, even 
  though their ports have formed a valid physical connection. 
  
  The following table summarizes the FDDI connection rules.  The word "peer" 
  means connections in a dual ring.  Tree preference means that when offered
  the opportunity to form a tree and a dual ring simultaneously, the station 
  will form the tree, and disconnect the peer, if it was already connected. 

  For example, the last line of the table indicates that when the A port of a 
  station or concentrator connects to the M port of a concentrator, the A to 
  M connection is taken, a tree is formed, and the Station State will be 
  concatenated_wrap_A (c_wrap_A).  Any existing B to A connection will be 
  disconnected, and, any new B to A will not be made. 


	Table A.1 - FDDI Connection Rules and Station States


    Port A	Port B		Peer/Tree 	Station State
    ------	------		--------        --------------
    M				Tree		c_wrap_A
    		M		Tree            c_wrap_B
    M		M		Tree            c_wrap_B (dual homed)
    B				Peer            c_wrap_A
    		A		Peer            c_wrap_B
    B		A		Peer            thru
    A				Peer            c_wrap_A
    		B		Peer            c_wrap_B
    S				Peer            c_wrap_A
    		S		Peer            c_wrap_B
    S		S		Peer            thru
    S		M		Tree            c_wrap_B (tree preference)
    M		S		Tree            c_wrap_A (tree preference)
    S		A		Peer            thru
    B		S		Peer            thru
    B		M		Tree            c_wrap_B (tree preference)
    M		A		Tree            c_wrap_A (tree preference)



  RING OPERATION

  An FDDI ring operates according to the rules of the "timed token protocol". 
  The operation of the ring can be divided into two parts - intialization of 
  the ring, and steady state operation.  A very short description of these 
  operations is presented below. 

  FDDI initializes the ring by a process known as the "claim token process", 
  which is invoked each time any station enters or leaves the ring, or a 
  failure of the normal ring operation is detected.  The purpose of this 
  process is to set the operational timers for the ring, and to choose the 
  station which will create the token.  All stations send a special frame, 
  known as a "claim frame", which contains a "bid" for the length of time that 
  that station is willing to wait between receipt of tokens.  The station 
  that wins the bidding is the station whose bid indicates that it needs the 
  token the most often.  The outcome of the claim process is that all stations 
  agree to abide by this time, which is known as T_Negotiated (T_Neg).  
  Typical values for T_Neg are in the range of 5-10 ms, with 8 ms being a 
  common choice.

  Varying the value of T_Neg can dramatically change the utilization and the 
  latency of a very busy FDDI ring, but has little to no effect on the 
  utilization or latency of a lightly loaded ring.  It is strongly recommended 
  that the value of T_Neg not be changed from the manufacturer's default.

  If a ring fails to complete the claim process within a certain time, the ring 
  enters the "beacon process".  This process causes special frames known as 
  "beacon frames" to be sent around the ring in an attempt to isolate the 
  location of the fault.  If beacons are seen, it is an indication of a serious
  problem with the operation of the ring. 

  In the steady state, the token circulates around the ring.  The time for a 
  token to circle once around the ring without being used by anyone is known as 
  the "token latency".  Stations that wish to transmit must capture the token, 
  and can transmit as long as allowed by the token holding rules.  All stations 
  keep a timer called the "valid transmission timer" (TVX) which they use for
  timing valid activity on the ring.  If, for some reason, a token gets "lost",
  this timer will expire, and stations will enter the claim process, so that a 
  new token is created. 

  During the steady state, stations in the ring exchange frames which tell 
  each other about their adjacent stations.  This information is communicated 
  via SMT frames, which are sent at a rate of approximately 1 every 10 to 30 
  seconds.  Using these frames, stations determine their "upstream" and 
  "downstream" neighbors.  Station 2 is said to be downstream of Station 1
  if Station 2 receives the token after it was received by Station 1. 




  Appendix B - LEDs on FDDI modules

  FDDI modules for the DEChub 900 family have a number of LEDs that reflect 
  the state of the FDDI connections.  These will be detailed for each module.  
  Note that these LEDs apply to the DEChub family of FDDI modules, and may 
  be different from the LED codes used on other Digital FDDI products. 
  

  DECconcentrator 900 MX and 900TH
 
  The LED next to the # symbol indicates that the module is in the ring, has 
  formed a connection to another module, and LLC traffic can be exchanged 
  (specifically, Ring_Op is true, and a duplicate address has not been 
  detected by this module).  Please note, before this release, this LED
  was lit even when no connection was formed. 
  
  The LED next to the PHY symbol on a MODPMD module indicates the state of 
  the connection for that port.  These options also apply for the 12 UTP port 
  status LEDs of the DECconcentrator 900TH.  Options are:

   Off                       Available for connection
   Solid Green               Connection is Active
   Blinking Green            Management disabled, or broken
   Solid Amber               Link Confidence Test Failure
   Blinking Amber            Topology Rule Violation
   Blinking Green/Amber      Dual Homed connection 

  The other LED on a MODPMD module indicates the status of the MODPMD module, 
  or the FDDI port type.  Options are:

   Off                       M port
   Solid Green               S port
   Blinking Green            A or B port
   Solid Amber               MODPMD fault
   Blinking Amber            No meaning
   Blinking Green/Amber      No meaning



  DECSwitch 900EF and PESwitch 900TX

  The LED next to the # symbol for port 1 indicates the state of forwarding 
  for the FDDI port of the switch.  Options are:

   Off                       Bridging to/from FDDI not active
   Solid Green               Bridging to/from FDDI is active
   Blinking Green            Switch is learning on the FDDI port or
			     FDDI port is in the backup state

  The LED next to the arrow symbol indicates activity on the FDDI port.  A 
  green flashing LED means the front panel FDDI ports are in use.  An amber 
  flashing LED means that the rear panel ports are in use.  The amber color 
  will appear as long as one port is assigned to the backplane. 


  The LED next to the PHY symbol on the front panel indicates the state of 
  the connection for that port.  Note: Since the FDDI ports of the 900EF can 
  be steered to either the front or back panel, this LED is operational when 
  a connection to the port is formed either via the front panel, or on the 
  backplane.  Also, the lights on the MODPMD modules used with the switches 
  will be lit, independent of whether the front panel or MODPMD ports are in 
  use.  Options for the front panel LED are:


   Off                       Available for connection
   Solid Green               Connection is Active
   Blinking Green            Management disabled, or broken
   Solid Amber               Link Confidence Test Failure
   Blinking Amber            Topology Rule Violation
   Blinking Green/Amber      Dual Homed connection 
  


  The LED next to the PHY symbol on a MODPMD module indicates the state of 
  the connection for that port.  The following options apply for MODPMD
  modules used with either the DECswitch 900 EF or the PEswitch 900 TX. 

   Off                       Available for connection
   Solid Green               Connection is Active
   Blinking Green            Management disabled, or broken
   Solid Amber               Link Confidence Test Failure
   Blinking Amber            Topology Rule Violation
   Blinking Green/Amber      Dual Homed connection 

  The other LED on a MODPMD module indicates the status of the MODPMD module, 
  or the FDDI port type.  Options are:

   Off                       M port
   Solid Green               S port
   Blinking Green            A or B port
   Solid Amber               MODPMD fault
   Blinking Amber            No meaning
   Blinking Green/Amber      No meaning








  Appendix C - References

  The following are suggested readings for those wishing to learn more about 
  the operation of FDDI networks.

  "A Primer on FDDI" - published by Digital, this book is a very simple
  introduction to the operation of FDDI.  It is, unfortunately, now out of 
  print, but old copies can sometimes be found.  A different version of this 
  book is available from Digital Press, under the title "FDDI, An Introduction",
  ISBN Number 1-55558-093-9, order number EY-J840E-DP

  "FDDI Handbook" by Raj Jain.  This is a very readable and very recent book on 
  all of the details of FDDI.  It is published by Addison-Wesley, ISBN number 
  0-201-56376-2

  Official FDDI Standards - The actual standards are available from the ANSI 
  Sales office in New York, N.Y. 

   Media Access Control (MAC) X3.139-1987	
   Physical Layer Protocol (PHY) X3.148-1988
   Physical Layer Medium Dependent (PMD) {multimode fiber PMD} X3.166-1990
   Station Management (SMT) X3.229-1994 
   Single Mode Fiber PMD (SMF-PMD) X3.184-1993
   Twisted Pair PMD (TP-PMD) X3.263-199? (AWAITING PUBLICATION)


  Unofficial versions of some of these documents can be gotten by anonymous 
  ftp from fddi.lbl.gov

    
T.RTitleUserPersonal
Name
DateLines
2340.1Copy LocationDELNI::BUZZELLMon Jun 05 1995 09:2110
    
    
         This guide is also available at
         NAC::NIPG:[HUB.PRESENT]FDDICONF.TXT
    
         It will also be turned into a word document so that it can
    be printed and given to customers. As soon as it is ready it will
    be in the location above as FDDICONF.DOC.
    
    
2340.2Digital Confidential or not?CMOTEC::CHOIShaking and MovingTue Jun 13 1995 14:419
    Ed,
    
    I printed out the FDDICONF.PS and it has Digital Confidential on it. 
    Since it appears to have much the same content (if less detail) as
    FDDICONF.TXT, should the "Digital Confidential" be removed if it is OK
    to send to customers?
    
    
    Clinton
2340.3Don't use itDELNI::BUZZELLWed Jun 14 1995 14:189
    
    
         You should not provide the .ps. There are significant differences
    in the naming conventions and representations. The .ps is the old
    information and I have deleted it. The .doc refrenced above is being
    worked and should be ready next week. Until that time the .txt should
    be used.
    
    
2340.4Is it ready yet?MAASUP::PORAMBOMon Aug 28 1995 13:446
    
      I have been waiting for the .DOC version of the FDDI Configuration
    document. What , if anything, can be provided to the customer at this
    time?
    
    Bob
2340.5There AgainCONSLT::BUZZELLMon Aug 28 1995 16:076
    
    
         The .doc version should be accessible in the directory noted
    in .2  NAC::NIPG:[HUB.PRESENT]FDDICONF.DOC.