1390.0. "DECHUB900 UPS Sizing HELP!!" by NCMAIL::MCNALLT (Tom McNall - Rochester NY) Wed Sep 07 1994 17:40

    What's a good size for a UPS on a worst case loaded DECHUB900
    1300VA..or do I need more???
    
    This is a $4M proposal
    
    
    Thanks,
    Tom DTN 252-7096
T.RTitleUserPersonal
Name
DateLines
1390.1KAOFS::S_HYNDMANAcronym Decoder Ring ArchitectThu Sep 08 1994 09:5710
    
    
    Looking at note 717.* and note 4 I would expect a 1200VA UPS would be 
    sufficient.
    
    An APC Smart-UPS 1250RM series (rack mount) would be a good choice
    coupled with their SNMP adapter.
    
    
    Scott
1390.21300VA UPS Is the perfect choice!DELNI::MACARTHURThu Sep 08 1994 15:369
    Tom,
    
       A 1300VA UPS will work fine for a fully loaded DECHUB 900 System.
    The worst case calculations for the HUB show that we need approximately
    1150 VA. 150VA margin is more that enough.....
    
    Regards,
             Bob MacArthur