974.0. "DECHUB900 MANAGEMENT BY GENERIC NMS" by BBOV01::MACKENZIE () Wed May 11 1994 02:19

            I am responding to a large Govt tender for the supply of LAN 
            hubs. I am bidding the DEChub900, DEChub One and the DEChub 
            90 range.
            
            I am seeking assistance on the following sections that deal 
            with how could the hubs be managed htrough a "generic" 
            network management station (HP Ovenview, SUNnet Manager, or 
            possiblly PNV),
            
            What scope and functionality to manage the DEChub900 really 
            exists in the absense of HUBwatch NMS or its avilability on  
            third party NMS.
            
            
            Any assistance greatly accepted...
            
            Tony
            
            
            
            2.5	   MANAGEMENT
            
            2.5.1  General
            Hub management software is required for the network 
            management of the hubs throughout the Queensland Transport 
            data network.  The hub management software is required to be 
            integrated with a generic SNMP enterprise-wide Network 
            Management System (NMS).  The requirements for this NMS are 
            the subject of a separate specification, Specification TU-004 
            Network Management System.
            
            The assessment of hub equipment shall include consideration 
            of the functionality of the hub management software proposed 
            and its level of integration with the enterprise-wide NMS.
            
             2.5.1.1	  Mandatory
            
            (i)	   Hubs shall support both in-band and out-of-band 
            management down to the port level.
            
            The hub management software shall integrate with an 
            enterprise-wide SNMP based NMS. In particular : 
            
            (ii)   The hub management software shall operate over the 
            generic SNMP enterprise-wide NMS hardware and software 
            platform with a shared graphical user interface (X11) and 
            Motif.
            
            (iii)  The hub management software/NMS shall have complete 
            support for all the hub management functions, including all 
            proprietary extensions to hub MIBs.
             
            (iv)   The hub management software shall comply with the 
            underlying NMS database.
            
            (v)	   The hub management software shall utilise a common IP 
            discovery and mapping function (as opposed to separate 
            functions) that simultaneously provides network information 
            to both the hub management software and the NMS.
            
            2.5.1.2	  Desirable
            
            (i)	   The mechanism for out-of-band management should have a 
            graphical user interface.
            
            (ii)   The hub management software/NMS should provide 
            automatic graphic representations of its products to 
            facilitate configuration and fault management.
            
            2.5.1.3	  Additional information to be provided
            
            The proposer shall discuss all mechanisms for management of 
            the hub equipment such as:
            
            *	   hub management software/NMS;
            *	   Telnet access;
            *	   console port/remote dialup access.
            
            Discussion of these mechanisms shall include comparison of:
            
            *	   functionality;
            *	   user interface (e.g. command line, menu-driven);
            *	   performance.
            
            The proposer shall also provide details of the following :
            
            *	   any limitations on the total number of devices that 
            can be managed by the hub management software;
            
            *	   the module requirements to enable management (i.e. 
            whether a specific module required to provide management or 
            whether management functions are inherent in each hub 
            interface module);
            
            *	   hardware and software platform requirements of the hub 
            management software/NMS;
            
            *	   level of proven interoperation with a generic SNMP 
            enterprise-wide Network Management System (NMS).
            
            2.5.2  Protocols/Standards
            
            2.5.2.1	  Mandatory
            
            (i)	   The hubs proposed shall support management via SNMP 
            for fault and performance management.  The hubs shall be MIB 
            II compliant as a minimum.
            
            (ii)   The hubs shall have current or stated future support 
            for all relevant management functions (i.e. configuration, 
            fault, performance and security) via SNMP, CMIS/CMIP and SNMP 
            II.
            
            (iii)  The hubs shall have current or stated future support 
            for RMON.
            
            (iv)   The hubs shall have current or stated future ability 
            to serve as a distributed network management engine to the 
            central hub management software/NMS (for local polling and 
            filtering).
            
            For hub products where total management via SNMP, CMIS/CMIP 
            or SNMP II is not currently available, an estimated timescale 
            for delivery of this functionality shall be provided by the 
            proposer.  Time to deliver RMON and distributed network 
            management engine functionality shall also be provided if 
            these features are not already available.
            
            2.5.2.2	  Desirable
            
            (i)	   The hubs should have current or stated future support 
            for the OSF DME.
            
            (ii)   The hubs should have configuration and security 
            management via SNMP.
            
            2.5.2.3	  Additional information to be provided
            
            The proposer shall detail all relevant management protocols 
            and standards supported, including any extended/proprietary 
            management mechanisms and MIBs.
            
            2.5.3  Configuration Management 
            
            2.5.3.1	  Mandatory
            
            (i)	   The ability to distribute configuration software from 
            a central location is essential. The proposer shall provide 
            details of the mechanism (eg. Flash EPROM) used.
            
            (ii)   There must be a simple recovery path for the situation 
            where a downloaded hub configuration fails.  The proposer 
            shall provide further details.
            
            (iii)  Local and remote support for activating/deactivating 
            hub ports and for resetting  the hub.
            
            (iv)   Support for dynamic configuration. The proposer shall 
            provide further details.
            
            2.5.3.2	  Desirable
            
            (i)	   The ability to maintain central back-ups of 
            configuration data for hubs.
            
            2.5.4  Fault Management
            The ability to accurately identify and resolve faults is 
            essential.
            
            2.5.4.1	  Mandatory
            
            (i)	   The minimum diagnostic LED requirements are:
            
            � active/inactive port;
            � link signal;
            � collision signal;
            � power.
            
            All other supported LEDs shall be detailed by the proposer.
            
            (ii)   A faulty port or interface module must be able to be 
            isolated from the rest of the network such that:
            
            � for both stackable and modular hubs, the failure of a port 
            on an interface module will not impact the operation of other 
            ports on the module. 
             
            � For modular hubs with multiple expansion slots, the failure 
            of an interface module within the hub will not impact the 
            operation of other modules within that hub.
             
            � For stacks, the failure of one hub in the stack will not 
            impact the operation of other hubs in the stack.
            
            	   The operating conditions which prompt a port or 
            interface module to be automatically isolated shall be 
            described in detail by the proposer.
            
            (iii)  The hub must be able to carry out a hardware 
            self-test.  The proposer shall provide details of any alarms 
            (eg. local diagnostic LED, SNMP trap etc.) that can be 
            generated by this test, as well as details of when this test 
            can be performed (eg. power-up, on demand). 
            
            2.5.4.2	  Desirable
            
            (i)	   The hub should be able to maintain a user configurable 
            error log.
            
            (ii)   The ability to configure the alarms, and the 
            thresholds which activate these alarms. The proposer shall 
            provide further details.
            
            2.5.4.3	  Additional information to be provided
            
            For each type of wiring hub offered, the proposer must 
            provide details of the following:
            
            *	   the type of faults (eg. line/port failure, 
            environmental problems) that the hub can notify, and describe 
            the resultant alarms.
            
            *	   any self-test, self-diagnosis and automatic 
            re-configuration capabilities of the hub.
            
            2.5.5  Performance Management
            2.5.5.1	  Mandatory
            
            (i)	   All aspects of hub performance must be able to be 
            monitored via all management methods (ie. hub management 
            software/NMS, telnet, console etc).  Statistics must be 
            available on a per-hub, per-module and per-port basis as 
            applicable.  The measurable values must include:
            
            � utilisation
            � throughput;
            � runt packet count/rate;
            � jabber error count/rate;
            � collision count/rate.
            
            (ii)   There must be user definable thresholds for 
            performance aspects such that an alarm/SNMP traps are 
            generated if these thresholds are exceeded. 
            
            2.5.5.2	  Additional information to be provided
            
            The proposer shall provide details of the presentation format 
            of the performance statistics for all different management 
            methods (i.e. hub management software/NMS, Telnet, console 
            etc).
            
            
            2.5.6  Security Management
            2.5.6.1	  Mandatory
            
            (i)	   The hub management software/NMS shall be capable of 
            keeping an audit trail of users executing management 
            commands.
            
            (ii)   Some form of security protection and user 
            authentication is required for management access for all 
            mechanisms (i.e. hub management software/NMS, Telnet, console 
            etc).
            
            (iii)  Different access levels must be definable for 
            different users or user groups.
            
            (iv)   The ability to assign a community string to the hub 
            for SNMP security.
            
            2.5.6.2	  Desirable
            
            (i)	   The hub should support security protection on ports, 
            for example restriction of access to hub ports based on the 
            Ethernet address of the attached device.  It must be possible 
            to enable and disable the security functions on any given 
            port.
            
            2.5.6.3	  Additional information to be provided
            
            Any security features implemented in the hub shall be 
            detailed by the proposer.
             
T.RTitleUserPersonal
Name
DateLines
974.1possible, but not worth itNAC::FORRESTWed Jul 06 1994 19:008
	Basically, if the generic SNMP manager is flexible enough, then 
	you could manage the DEChubs with a good deal of difficulty. Our 
	position is that the aggravation isn't worth it for the $2600 that 
	HUBwatch costs on a workstation.

	We hope to be able to launch HUBwatch from the platforms you 
	mentioned before year end.