| Ren�,
I suggest that you contact the engineering group responsible for the HSZ10
array and ask them for a list of all the messages they output, from this
list you will be able to build up a set of events and group them into a scan.
When you have done all this, could you post your completed work here for
everyone else to use.
Cheers,
Phil
|
|
Hello,
During a cleanup of my disk I ran into this, and I remembered that I did
not add it to the note.
Good luck with it.
Ren�.
!------------------------------------------------------------------------------
!
! **** HSZ Events ****
!
ADD EVENT "HSZ_BAD_POWER_SUPPLY_OR_FAN" -
/ABBREVIATION="BADPSF" -
/COUNT=1 -
/INFORMATION="BA350 shelf has a bad power supply or fan" -
/PRIORITY=40 -
/START=0 -
/TEXT="has a bad power supply or fan"
!
ADD EVENT "HSZ_LAST_FAIL" -
/ABBREVIATION="LFAIL" -
/COUNT=1 -
/INFORMATION="Last Fail message, code & data" -
/PRIORITY=80 -
/START=0 -
/TEXT="Last fail "
!
ADD EVENT "HSZ_LAST_GASP" -
/ABBREVIATION="LSTGSP" -
/COUNT=2 -
/INFORMATION="Last Gasp message has been received from other controller" -
/PRIORITY=80 -
/START=0 -
/TEXT="Received LAST GASP message from other controller. Fail Code:"
!
ADD EVENT "HSZ_MIST_DIAG_ERR" -
/ABBREVIATION="DIAGER" -
/COUNT=1 -
/INFORMATION="Catastrophic boot diagnostic error, check fault code on OCP " -
/PRIORITY=80 -
/START=0 -
/TEXT="MIST Diag-err Halting"
!
ADD EVENT "HSZ_OTHER_CONTROLLER_NOT_RESPONDING" -
/ABBREVIATION="NORESP" -
/COUNT=2 -
/INFORMATION="The other controller is not responding" -
/PRIORITY=80 -
/START=0 -
/TEXT="Other controller not responding - RESET signal asserted"
!
ADD EVENT "HSZ_OTHER_CONTROLLER_RESTARTED" -
/ABBREVIATION="STRTED" -
/COUNT=1 -
/INFORMATION="The other controller has restarted" -
/PRIORITY=10 -
/START=0 -
/TEXT="Other controller restarted"
!
ADD EVENT "HSZ_RESTART_OTHER_CONTROLLER" -
/ABBREVIATION="RESCON" -
/COUNT=1 -
/INFORMATION="Restart command is being entered at the -
/PRIORITY=40 -
/START=0 -
/TEXT="RESTART OTHER"
!
ADD EVENT "HSZ_RESTART_REQUIRED" -
/ABBREVIATION="RESREQ" -
/COUNT=1 -
/INFORMATION="Changed parameters require a restart to become effective" -
/PRIORITY=40 -
/START=0 -
/TEXT="A restart of this controller will be required before all"
!
ADD EVENT "HSZ_RESTART_THIS_CONTROLLER" -
/ABBREVIATION="RESCON" -
/COUNT=1 -
/INFORMATION="Restart command is being entered at the prompt" -
/PRIORITY=40 -
/START=0 -
/TEXT="RESTART THIS"
!
ADD EVENT "HSZ_SET_CONTROLLER" -
/ABBREVIATION="SETCON" -
/COUNT=1 -
/INFORMATION="Set controller command is being entered at the prompt" -
/PRIORITY=40 -
/START=0 -
/TEXT="SET CONTROLLER"
!
ADD EVENT "HSZ_UP" -
/ABBREVIATION="HSZUP" -
/COUNT=2 -
/INFORMATION="The HSZ controller has booted" -
/PRIORITY=10 -
/START=1 -
/TEXT="Copyright � Digital Equipment Corporation"
!
ADD SCAN _SCAN$HSZ -
/INFORMATION="HSZ Scan Profile" -
/EVENT=(HSZ_BAD_POWER_SUPPLY_OR_FAN, -
HSZ_CI_PATH_LOOPBACK_FAILED, -
HSZ_LAST_FAIL, -
HSZ_LAST_GASP, -
HSZ_MIST_DIAG_ERR, -
HSZ_OTHER_CONTROLLER_NOT_RESPONDING, -
HSZ_OTHER_CONTROLLER_RESTARTED, -
HSZ_RESTART_OTHER_CONTROLLER, -
HSZ_RESTART_REQUIRED, -
HSZ_RESTART_THIS_CONTROLLER, -
HSZ_SET_CONTROLLER, -
HSZ_UP)
!
!------------------------------------------------------------------------------
|