906.0. "Airflow problem with A1000 4/266" by HAMSUP::KOENIG () Thu May 22 1997 13:19

    Hallo 
    
    
    i have an problem with an A1000 4/266 (PB72A) AY55126702
    
    Configuration
    
    TLZ07 RZ26L RRD45
    
    KZPSC-XA D01
    5 *RZ26L-VW Rev 442e A01
    
    DE435    A03
    
    5 * 32 MB 50-21270-01
    5 * 16 MB 50-23169-01
    
    "" The Machine crashes with ECC error Icache fill Multiple fill errors
    detected ""
    
    We have swapped everything several times during the last half year.
    The crash comes intermittend with an increasing rate over the last
    day.
    
    The problem i found ,without the left cover the machine is ok.
    With the left side cover the machine crashes within 2 hours.
    I checked it about 10 times so that i can say we have an airflow
    problem.
    
    Yesterday i make a litle modification ,i mounted the little fan inside
    the pci/isa box without a distance rubber and the machine is running
    without problems.
    
    Who has similar problems ?
    
    Is it possible that we have a general air flow problem ?
    
    
    thanks in advance 
    
    
    Heiko Koenig
    
    
    49 421 84442 37
    
    
T.RTitleUserPersonal
Name
DateLines
906.1None that we know aboutWRKSYS::DENNINGTue May 27 1997 15:197
    We have no airflows problems that we know about.
    
    What is the temp in the room that the AS is in?
    
    Is the back of the box against a wall? Under a desk?
    
    Don
906.2AirflowHAMSUP::KOENIGThu May 29 1997 08:4218
    Hallo Don,
    
    the Alpha stands on the floor in a computer room.The temperature is
    normal.The environment is ok.
    
    I reproduce these errors with the customer machine in our office.
    We had in our office the same crashes,roundabout 20 times a day.
    
    The machines produce problems over a half year,first we thought that
    we have memory problems.We swaped everything several times,we also 
    had swaped 3 times a RZ26w-va because they was faulty in raid 5 set.
    
    Now with changing the airflow the Alpha works fine since 10 days.
    
    
    Heiko Koenig
    
    Field Service