T.R | Title | User | Personal Name | Date | Lines |
---|
2151.1 | Some questions | TOOK::ORENSTEIN | | Tue Jan 21 1992 12:36 | 12 |
|
When you said "the rules stopped firing", did you mean that you saw
no more notification on the map, or that you stopped recieving your
command script notification, or that the counters stopped going up?
I don't mean to be picky, but each senario can represent and entirely
different problem. Once we determine exactly what stopped working
we can try to figure out why.
How often did you expect your rules to fire?
aud...
|
2151.2 | More Info | BAHTAT::BOND | | Tue Jan 21 1992 12:49 | 16 |
| Aud,
I was discussing this earlier today with Richard, and in his absence
will attempt to answer. I believe that Richard was saying that the
rule did not fire ie that any batch job associated with the rule
evaluating true did not get launched, and no colour change was seen on
the iconic map. As Richard said, it was an 'OCCURS' type rule and his
OPCOM indicated that the system had seen the event coming from EVL.
It seemed to us that the problem had occurred as a result of having
more than 110 (but less than 130) rules enabled. The only significant
number I can think of between these two is 127 (or maybe 128) so we
were thinking of some sort of resource problem.
Hope this helps,
chris
|
2151.3 | < more clarification > | BAHTAT::TAYLOR | | Wed Jan 22 1992 04:45 | 15 |
|
Aud,
Just to confirm and expand on .3.
The map and script notification both ceased. The only alarm expected to
"fire" was the test alarm which could be executed at will. (Counters
zeroed on a remote node.) Opcom received the relevant event each time
the remote node counters were zeroed but Mcc gave no indication at all.
Once ALL the Alarms had been disabled and the test alarm re-enabled it
"fired" each and every time the counters were zeroed. I left the
station with 78 alarms enabled on "key" routers and everything was
operating fine.
Thanks for the quick response.
R.
|
2151.4 | Further information | BAHTAT::TAYLOR | | Thu Jan 23 1992 08:01 | 35 |
|
Aud,
Further to the previous replies I can now add some more information.
I have spent the last couple of days re-creating the problem back here
in the office. Observations :-
1. The problem IS reproducable.
2. At the first attempt the test worked fine with up to 90 alarms enabled.
Enabling a further 15 alarms caused the test to cease working. Disabling
the last group of alarms resulted in two things :-
1) The last of 3 "undelivered" alarms fired off.
2) The test started working again.
Alarms were then enabled in 5's. At 100 the test stopped working again -
however when the last group were disabled the test still did not work,
in fact ALL alarms had to be disabled before the test could be
re-enabled and would work. Also the Getevent directive would not work
with the test "event".
3. Continuing to enable alarms, the test failed with only 75 alarms enabled,
and could only be recovered by disabling all etc.etc.
4. This continued, surviving a number of complete logouts and even a system
reboot until the test would not even work with 15 alarms enabled.
5. After deleting the Alarm_Instance/Alarm_Attribute .dat files I started
anew. After creating 180 alarms I once again enabled them in groups of
15, testing after each group were enabled. At 75 everything worked fine.
but at 90 the test failed. After disabling alarms 75-90 the test worked
ok again. From here I enabled each alarm manually, allowing several
seconds to elapse between each enable command. After each group of 5
alarms were enabled I checked the test. In this way I managed to enable
all 180 alarms AND have the test work successfully every time.
Does any of this help at all ????
R.
|
2151.5 | Thanks for the detail | TOOK::ORENSTEIN | | Thu Jan 23 1992 12:33 | 8 |
| Thank you so much for the very complete report. With this detail we
will have a better chance of figuring out your problem.
It may be a couple of days before we can get back to you due to the
huge amount of work we need to do for V1.2
aud...
|
2151.6 | | TOOK::SWIST | Jim Swist LKG2-2/T2 DTN 226-7102 | Thu Jan 23 1992 14:51 | 5 |
| The number of alarm rules you can enable in the 1.2 EFT kit is severely
limited and we are working on the problem. Both VMS and Ultrix fail
in the vicinity of 100 rules (for different reasons, but that's no
comfort to the user).
|