354.0. "High-rise building FDDI configuration question " by BOSNET::COLUMBUS () Thu Sep 26 1991 13:45

I am working with a customer here in Boston who wants to install an FDDI 
backbone in his building. They currently occupy 15 floors with 2 closets on each 
floor. Since this is the first major FDDI configuration I've done here, I am 
confused as to what is the best way to lay this out. 

My original thought was to put a DAS connected concentrator on each floor. 
Since the fiber will be star wired to the Data Center, I realized that 
I would need a ton of fiber jumpers in the main fiber distribution panel to 
accomplish this (doesn't seen right). This also seems more failure prone!

Would I be correct if I were to put multiple concentrators in the data center
connected to each other via DAS and connect each floor via SAS connected 
concentrators and bridges? 

This may be a simple question but I want to be sure since this will be quite a 
few $$$.  
T.RTitleUserPersonal
Name
DateLines
354.1yes, you're correctBAGELS::LEVYThu Sep 26 1991 14:1710
re:                     <<< Note 354.0 by BOSNET::COLUMBUS >>>
   
>Would I be correct if I were to put multiple concentrators in the data center
>connected to each other via DAS and connect each floor via SAS connected 
>concentrators and bridges? 
    
    Yes, this is perfectly valid, and even preferred, because it minimizes
    the extent of the dual ring. For floors that require higher
    availability, you can dual-home to different concentrators on the dual
    ring.
354.2How would I set up the dual homing on each floor?BOSNET::COLUMBUSThu Sep 26 1991 15:159
Thanks for the quick reply....


How would you suggest I set up dual homing to different concentrators? 
Which port would connect to what. I looked in the NAC buyers guide configuration 
guidelines, but it is unclear to me how this would be accomplished.


John Columbus 
354.3KONING::KONINGBrivu Latviju!Thu Sep 26 1991 18:4020
Read the FDDI Primer...

Dual homing is very simple: rather than connecting only the B port "up", 
i.e., to the next higher level in the wiring tree hierarchy, connect both
A and B ports that way.  If at all possible connect them to different
concentrators.

A simple example: two concentrators on the dual ring, in the "main distribution
frame" (the site hub).  [you mentioned the "data center" for that; that's
fine, or a separate hub room might be used.]  Put concentrators on each
floor.  Any concentrator to which "important" things are attached has its
A port connected to one of the hub concentrators, the B port to the other
hub concentrator.  Both of these connections are to M ports on the
hub concentrators.  Any "not so important" concentrator is just connected
by its B port, to an M port on either of the two hub concentrators.

Given 15 floors and a max of 8 M ports per dual-attached concentrator, you
will of course need more than just two concentrators at the hub/dual ring.

	paul