I have a site with SWXRC-05 raid controllers (in a CSS custom cabinet)
that is having the Environmental Monitor Unit (EMU) detecting an
overtemperature condition.
I have had the customer measure the air temp outside the cabinet at 25C
and internally at 31C. This configuration is running in an open office
environment.
My understanding is that the SWXRC controllers had an envoronmental
temp spec of +18C to +24C, and was intended for operaion in a Class A
computer room environment.
My question is: At what temperature does the EMU activate its overtemp
alarm?
Armed with this information I can then state to the customer the
internal temperature that the SWXCR is reaching, and then push back
onto them to address the problems of air cooling for this
configuration.
Thanks
Patrick Callaghan
| T.R | Title | User | Personal Name | Date | Lines |
|---|---|---|---|---|---|
| 768.1 | Overtemp | JULIET::SMITH_P | Thu Feb 13 1997 16:09 | 9 | |
On Page 7-18 of the SWXRC-04 manual -Part #EK-SMCS1-UG.
Section 7.8.3 - Error - Temperature Light (Amber) On (See Figure
7-6) The Shelf temperature is above the recommended
operating temperature of 35C(95F). The blowers run
at high speed. If the shelf teperature rises over
50C(122F) The subsystem shuts down.
Paul
| |||||