I have a site with SWXRC-05 raid controllers (in a CSS custom cabinet) that is having the Environmental Monitor Unit (EMU) detecting an overtemperature condition. I have had the customer measure the air temp outside the cabinet at 25C and internally at 31C. This configuration is running in an open office environment. My understanding is that the SWXRC controllers had an envoronmental temp spec of +18C to +24C, and was intended for operaion in a Class A computer room environment. My question is: At what temperature does the EMU activate its overtemp alarm? Armed with this information I can then state to the customer the internal temperature that the SWXCR is reaching, and then push back onto them to address the problems of air cooling for this configuration. Thanks Patrick Callaghan
T.R | Title | User | Personal Name | Date | Lines |
---|---|---|---|---|---|
768.1 | Overtemp | JULIET::SMITH_P | Thu Feb 13 1997 16:09 | 9 | |
On Page 7-18 of the SWXRC-04 manual -Part #EK-SMCS1-UG. Section 7.8.3 - Error - Temperature Light (Amber) On (See Figure 7-6) The Shelf temperature is above the recommended operating temperature of 35C(95F). The blowers run at high speed. If the shelf teperature rises over 50C(122F) The subsystem shuts down. Paul |