753.1 | Covering the "write hole" | SSDEVO::JACKSON | Jim Jackson, HSx RAID team | Thu Jan 30 1997 09:11 | 17 |
| The HSx controllers use the write-back cache to eliminate the "write hole"
that is a characteristic of all RAID levels (except for striping). In RAID
1 (mirror) sets, the "write hole" causes data to be different on the
different members. In RAID 5 sets, the "write hole" causes the parity to be
inconsistent, which can cause future data corruption.
We view data corruption seriously, which is why we don't permit a RAID 5 set
to operate if the battery is bad.
When the battery is low and CACHE_POLICY=B, the units are accessed in
"write-through" mode. In this mode, no user data is kept in the cache.
However, write hole information *is* kept in the cache, so the cache is
still necessary. If the write hole information is lost, *none* of the
parity on the RAID 5 set can be trusted. This is why a CLEAR LOST_DATA
command destroys all redundancy on a RAID 5 set.
Does this help?
|
753.2 | | UTOPIE::OETTL | hide bug until worst time | Thu Jan 30 1997 13:34 | 9 |
| > parity on the RAID 5 set can be trusted. This is why a CLEAR LOST_DATA
> command destroys all redundancy on a RAID 5 set.
Now I understand why the RAID5 set was reconstructing completely when I issued
a CLEAR LOST_DATA to a RAIDset. The controller threw away and recalculated the
parity information!
Thank you,
�tzi
|
753.3 | OK - but..... | ATZIS1::PUTZENLECHNE | | Fri Jan 31 1997 00:52 | 10 |
| reply .1
Thank you, well i understand this now, but why was this not already in
HSOF 2.5 implemented in the same way? I know that in 2.5 it was
possible to operate with "failed" batteries, or did they experience
data-los-problems with 2.5 and changed it because of this in 2.7?
Thank you so far,
Helmut
|
753.4 | V2.5 vs. V2.7 | SSDEVO::THOMPSON | Paul Thompson, Colorado Springs | Mon Feb 03 1997 15:42 | 9 |
| V2.5 only checked the batteries at boot time. Therefore, if you had a failed
battery, you would not know until either, power failed and you lost the data in
cache, or you rebooted the controller.
V2.7 implemented periodic tests of the battery to proactively identify failed
batteries before the Customer lost data.
Under either version of the firmware, once the battery failure is detected, access
to RAID and Mirro sets is denied.
|
753.5 | Thank You | ATZIS1::PUTZENLECHNE | | Wed Feb 05 1997 12:17 | 11 |
|
> V2.7 implemented periodic tests of the battery to proactively identify failed
> batteries before the Customer lost data.
except the cache_policy is set to B. Because i had a System running
for more than 2 days with failed batteries.
thanks for the informations,
Helmut
|
753.6 | Re: Cache policy "B" | SSDEVO::THOMPSON | Paul Thompson, Colorado Springs | Fri Feb 07 1997 09:51 | 14 |
| Regarding the reference to cache policy "B" in the previous note.
Cache Policy "B" means that after a boot or reboot, if the battery is found to be
"low", access to RAID and Mirror sets will be allowed while the battery is
charging. With cache policy "A", access to the RAID and Mirror sets would be
denied if the battery was low.
If the battery is not found to be fully charged and declared "good" by the
controller within ten (10) hours of a boot or reboot, access to the RAID and
Mirror sets will be denied, regardless of the cache policy.
In other words, ten (10) hours after a boot or reboot, the choice of settings of
the cache policy parameter makes no difference. If the batteries have not been
declared "good", access to RAID and Mirror sets will be denied.
|