T.R | Title | User | Personal Name | Date | Lines |
---|
204.1 | GFCIs in a bathroom are a good idea | 24766::INGRAM | Larry Ingram | Tue Nov 24 1987 10:34 | 30 |
| > In Massachusetts, can I install a GFCI protected outlet near my
> bathroom sink?
Yes. New wiring requires all bathroom outlets to be GFCI protected
and it's a good idea to install it if you don't already have it.
> Can I install a switch to control the medicine cabinet lights in the
> same junction box as the aforementioned outlet?
Yes, provided the box that the GFCI and switch are mounted in are
large enough according to code. GFCIs are pretty big and you will
have at least 5 wires going through the box. Also, the cutout in the
cover plate is a large rectangle. I have not seen any cover plates
designed for a GFCI and a switch on the same panel. You may have to
modify your own.
Most, if not all, GFCI outlets have an extra hot wire which can be
connected to other outlets downstream and protect them also. You
could power the light which from this lead.
> Does anyone happen to know if, in the town of Arlington, I can do
> this myself, or must I hire an electrician?
In general, wiring, switches, etc. that are replaced do not need
to be inspected, and Massachusetts does not require the work be done
by a licensed electrician. Cities and towns sometimes have their
own code which you must follow. Perhaps someone who lives in Arlington
can answer this?
Larry
|
204.2 | what the NEC says | 4268::CAHILL | Jim Cahill | Tue Nov 24 1987 10:50 | 25 |
| > In the state of MA all switches and outlets within 2' (or maybe
> 3') must be GFCI protected.
I don't know specifically about Mass laws, but quoting from Richter's:
"The Code in Sec. 210-8 requires GFCI protection for all 15- and
20-amp receptacles: in residential bathrooms; over counters within
6 ft. of the kitchen sink; outdoors; in garages, except where not
accessible (as for a garage door operator) or for appliances in
dedicated space (as for a freezer); in electrically wired detached
garages; at least one in the basement; in all boathouses; in bath-
rooms of hotel and motel guest quarters; and for temporary receptacles
used during building construction. Some swimming pool installations
... also require GFCI protection. See Art. 680 of the Code."
> Take the power feed into the room and run it first to the LOAD side
> of the GFCI. Then run the next outlet or switch off of the LINE
> side of the GFCI. All outlets and switches down stream of the LINE
> side of the GFCI will then be protected.
Umm, don't you have LINE and LOAD reversed in the above?? LINE
refers to the GFCI's supply, while LOAD refers to the other protected
receptacles.
Jim
|
204.3 | I think I've got it right this time | 15934::PALMER | half a bubble off plumb | Wed Nov 25 1987 08:18 | 23 |
| RE .3
Yes, I did get LOAD and LINE mixed up in my explanation of .2.
My efforts to correct it lead to deleting the note. I got so
concerned that last night I checked the the GFCI I installed
last weekend!
With existing construction you should first check the extent
of the GFCI protection you can possibly have. Power down the circuit
and disconnect the outlet. Turn the circuit back on being careful
with the loose wires. All the lights and outlets that are down
stream of the outlet you disconnected will be off. If you want
to include them in the GFCI protection connect the power in
to the LINE side of the GFCI and the down stream line to the LOAD
side. If you only want that particular outlet to be GFCI don't
use the LOAD side of the outlet.
In new bathroom construction it is a good idea to protect the
entire circuit, lights, outlets, switches and fans. Run the power
to the bathroom first to the GFCI and take the power out of the
LOAD side of the GFCI.
I would use a double box with an extension on it for a switch
and a GFCI outlet. GFCI's are big and take up a lot of room.
=Ralph=
|
204.4 | Source for cover plates | RICKS::VELTEN | | Wed Nov 25 1987 10:40 | 5 |
| Somerville Lumber (the westboro store) now has a selection of cover plates
for a combination of GFCI with several other switch/outlet types. A few
years ago that type of plate was impossible to find.
--Dave V.
|
204.5 | Grossman | MSEE::CHENG | | Wed Nov 25 1987 10:45 | 3 |
|
Grossman has sale on GFCI for arround $12 now. I just picked 2 up
last night.
|
204.6 | Are there chimney/wiring clearance requirements? | TALLIS::KOCH | Kevin Koch LTN1-2/B17 DTN226-6274 | Mon Nov 30 1987 09:11 | 10 |
| It occurred to me that a hair dryer and heat lamp would overload the
15A circuit that feeds the bathroom and the rest of the second floor. So
I'm going to extend an unused 20A circuit in the basement up to the
bathroom, by running the wire up to the attic parallel to the chimney.
During my preparatory work (carving up the inside of the kitchen
broomcloset) I've made the observation that nowhere does wood appear to
touch the chimney. Are there any restrictions about clearance between
wiring and the chimney? If so, I've got to figure out a different way to
get the wires from the basement to the attic. (I'm also curious about
chimney/wood clearance requirements, but thats another issue.)
|
204.7 | lights out | HYDRA::MBENSON | | Mon Nov 30 1987 16:32 | 2 |
| Don't forget that if you do indeed place the "lights" on the
GFI ..... If and when you blow the GFI, you will be in the DARK.....
|
204.8 | Electrical switches for a bathroom | NETMAN::SEGER | this space intentionally left blank | Wed May 04 1988 22:07 | 21 |
| I know this was discussed before but alas, I can't find the note in the
keywords under bathroom OR electrical.
What is the latest opinions about switches in bathrooms in Mass? My house has
a 1/2 bath with a switch on the inside while the full baths have switches on
the outside. Does the code simply say that all full baths have to have
switches on the outside or is it based on the distance to the tub? I'm putting
in a very large master bath with a whirlpool and between the switch for that,
one for a vent fan and still another for lighting, that would mean a 3-ganged
switch outside the bathroom, making a VERY long walk from the switch to the
tub. Furthermore, if I decide to opt for a heat lamp, that would make for 4
switches.
In another bathroom I want to install another vent fan. The outside wall
to that bathroom already has a switch for the bathroom ganged to one for the
hallway. Adding the fan switch would make that a three-way switch.
Do all these switches have to be outside the bathroom? Can one put them inside
on a ground fault circuit if they are a minimal distance from a sink or tub?
-mark
|
204.9 | You can put 'em inside | ERLANG::BLACK | | Thu May 05 1988 00:12 | 19 |
| As I recall the discussion and the code
All recepticle outlets in bathrooms must be GFCI protected
Thats it. The lihgt switches can be inside, and the lights and
fan don't have to have CFCI protection. Of course, ifthey are on
the same circuit, you may as well give them GFCI protection.
This tallies with what was done in my (1980) house: all the outlets
in both baths and the half bath, as well as the outlets on the deck,
are protected by the same GFCI outlet. The fan and light switches
are on sundry other circuits, and are all inside.
If I were wiring a hot tub, I'll pull a permit. So if I were you,
I'ld talk to my local inspector.
Andrew
|
204.10 | Switches are ok if GFI'ed | PALMER::PALMER | half a bubble off plumb | Thu May 05 1988 09:33 | 18 |
|
Mark,
I second .1's opinion that you can have inside switches as long
as they are GFI protected. I just had my final electrical sign
off and my bathroom has two separate outlets and two switches
on the inside, within a couple of feet of the plumbing. I put the
bathroom on its own 20 amp circuit and wired *everything* GFI.
I know some people don't like the idea of the lights going out when
the GFI trips, but I wanted the added safety, and besides the
electrical inspector loved it.
On a related topic, the electrical inspector warned my about
some bad GFI on the market. It seems that some of the cheap ones
are not doing the job properly. They will trip when you push in
the test button, but the inspector actually shorted from hot to
the metal faucet just to make sure. I don't know how true the info
is, I just thought I'd pass it along.
=Ralph=
|
204.11 | | VIDEO::DCL | David Larrick | Thu May 05 1988 11:16 | 5 |
| Massachusetts code used to prohibit switches in bathrooms, but that restriction
was removed several years ago.
Consider timers for such things as fans and heat lamps. There are several
kinds of timers available that you install in place of single-pole switches.
|
204.12 | inside or outside, legal either way | HPSVAX::POWELL | Reed Powell HPS Marketing | Sun May 08 1988 21:18 | 9 |
| I asked the inspector about this when he did my rough inspection,
and he said that it was never a code requirement, that is was sort
of a phase that contractors went through for a while. Whatever
the reason, he made it clear that there is no requirement either
way these days. The existing house had them outside, and the bath
in the addition has them inside, and he signed it off no problem.
-reed
|
204.65 | Nutone heater/light/vent connections? | LANDO::ANJOORIAN | | Mon Apr 10 1989 11:29 | 38 |
|
I am trying to reconnect a bathroom heater/light/vent unit (Nutone) to
three single-pole switches. A previous tenant removed the switches
from the box and I haven't been able to figure out which wire goes to
which switch. Here's the setup:
Electrical Box: Switches:
(three single-pole)
Light/Vent 1 2 Vent/Heater
WB WB
|| ||
+-||---||-+ A ---o o--- B Light
| || || |
| | A ---o o--- B Vent
| |
| || | A ---o o--- B Heater
+-||------+
||
WB
3
Line
W and B represent thw white and black wires, repectively.
When I connect #3 to #2 (W to W, B to B), the vent and heater are
fully on.
When I connect #3 to #1 (W to W, B to B), the vent and light are
partially on, that is, the vent runs slow and the light is dim.
Is it possible to solve this from the information given? Or has anyone
out there perhaps installed one of these in the recent past and happen
to have saved the wiring diagram? I spent hours yesterday trying to
figure it out. Help!
Jason
|
204.66 | What happens inside the unit? | HANNAH::DCL | David Larrick | Mon Apr 10 1989 11:55 | 25 |
| > Is it possible to solve this from the information given?
No - not for me, anyway.
I assume that your left-hand diagram shows the three pairs of
conductors coming into the switch box, and the manner in which those
pairs of conductors are labelled. What I need to see is the internal
wiring of the unit itself.
But if there are four conductors going from the switch box to the unit,
the obvious approach would be three switched hot wires and one common
wire:
+---(light sw)---------------------(light)----+
hot | |
line --------------+---(vent sw)----------------------(vent)-----+
----------+ | |
common | +---(heater sw)--------------------(heater)---+
| |
| |
+-------------------------------------------------+
The labels "light/vent" and "vent/heater" suggest that it isn't this
simple, though.
|
204.67 | I had a feeling it wouldn't be easy... | LANDO::ANJOORIAN | | Mon Apr 10 1989 13:23 | 4 |
| Thanks for the info. I was hoping to avoid it, but I guess I'll have
to take the fixture out of the ceiling and examine its internal wiring.
|
204.68 | | VINO::GRANSEWICZ | Which way to Tahiti? | Mon Apr 10 1989 15:28 | 4 |
|
Try calling Nutone or going to a place that sells similar equipment
and looking at the instructions that come with the unit. I know
Spag's sells these switches. Maybe they come with a wiring diagram.
|
204.69 | success! | LANDO::ANJOORIAN | | Tue Apr 11 1989 11:00 | 16 |
|
Thank you .1, for the wiring diagram. Using that as a starting point,
I found out that line #2, labeled Vent/Heater was in fact for the
heater only. The 2W conductor was a common. So the solution was:
1B to VB
1W to LB
2B to HB
2W to 3W
3B to LA, VA, and HA
Now if I could only sell the house as easily as that problem was
solved I'd be in good shape. But that's another note.
Jason
|
204.15 | BATHROOM FAN TRIPS GND. FAULT BREAKER | ISLNDS::KOVALCIK | | Tue Dec 05 1989 10:41 | 40 |
| We've had a master bathroom w/o a fan since we've moved into
our house and after cleaning mildew off the ceiling and wall
every month or two, I decided to install a fan/light combination.
The "project" took the better part of a day to cut out the old unit
install the new, along w/ venting it out the soffet.
The unit worked well for a week... until yesterday, the lights went
out in the bathroom while taking a shower.
I suspected that the ground fault breaker tripped and it did!
(I was able to re-set the breaker.)
Last night ...long shower, lots of steam, everything was o.k.
This morning another shower ... the breaker tripped again.
A couple of facts that affect this problem:
1. The fan/light combo. is directly over the shower.
2. The vent/duct runs over the attic insulation about 3ft.
(horizontally) to the soffet w/ 4" stainless expandable hose
and is capped w/ a screen at the outlet.
3. The temperature outside has been 10-20 degrees or less and the
attic is unheated.
4. I talked to the mfgr's rep. and he is sending me another motor
to try.
I've read most of the notes on venting and fan/light installation
and none seem to have had this type of problem.
Any suggestions to troubleshoot/fix this problem?
Thanks.
Jack
|
204.16 | Leakage current | VINO::DZIEDZIC | | Tue Dec 05 1989 10:48 | 4 |
| The next time the breaker trips, examine the connections to the
fan. See if any have moisture on them, perhaps that is providing
a path for leakage current. Otherwise I'd suspect the motor has
defective insulation on the windings or connecting wires.
|
204.17 | check your connections. | QBUS::MULLINS | | Tue Dec 05 1989 14:17 | 9 |
| I am amazed they haven't write locked you yet so I'll squeeze my
ideas in real quickly.
I had a similar problem recently and taking the GFI receptacle out
and re-doing the connections on the receptacle and the switch as
well seems to have corrected this problem. Also make sure no outside
outlets on this same circuit are causing this problem.
|
204.18 | | GIAMEM::LAMPROS | Bill Lampros | Wed Dec 06 1989 15:23 | 4 |
|
My electrician told me that no lights or fans should be on a GFI
line only duplex receptacles. Anybody else hear this?
Bill
|
204.19 | fans/lamps not required to be. | OPUS::CLEMENCE | | Wed Dec 06 1989 22:36 | 7 |
| RE: .3
I can't say that I have heard this, but for the wall plugs in
a bathroom it must be GFI protected. All other typical fixtures like
lights do not require gfi protection. Whirlpools and spas need GFI too.
Bill
|
204.20 | | ALLVAX::DIAMOND | No brag, Just fact. | Thu Dec 07 1989 11:20 | 7 |
|
All 4 of my bathrooms (2 for us and 2 for my tenents) are wired
so everything is a GFI. The GFI is in the breaker box. This includes
lights and fans and outlets. The house is 5 years old, and it was
wired that way by the contractor.
Mike
|
204.21 | "Gorry, Martha, cain't see a thing! Where's the door?" | LYCEUM::CURTIS | Dick "Aristotle" Curtis | Wed Dec 27 1989 23:15 | 8 |
| .3, .4, .5:
Well, isn't it true that (in most cases, at least), outlets and ceiling
fixtures go on seperate circuits? I gather that this is (in part) so
you shouldn't have to worry about breaking a leg tripping over the
furniture, when you head out to reset the tripped circuit breaker.
Dick
|
204.13 | Bathroom/Basement Electrical Outlets Not Working | MLCSSE::SHAH | | Fri Mar 02 1990 11:01 | 11 |
| HI!
ELECTRICAL OUTLET IN MY BASEMENT AND TWO BATHROOMS IS NOT WORKING.
I HAVE CIRCUIT BREAKER BOX IN THE BASEMENT. I THOUGHT CIRCUIT BREAKER
MAY HAVE TRIPPED, SO FLIP THE CIRCUIT BREAKER BUT THOSE OUTLETS
ARE STILL NOT WORKING. HOW DO I FIX IT?? WHAT I HAVE TO DO?? I CAN
DO IT OR I HAVE TO CALL THE ELECTRICIAN WHICH WILL COST ME THE BUNDLE.
IF I HAVE TO CALL ELECTRICIAN ANY RECOMMENDATION IN NASHUA AREA??
ANY HELP APPRECIATED.
BHARAT S. SHAH
|
204.14 | 692, 1504, 1659, 1737, 1111.35, etc. | OASS::RAMSEY_B | Put the wet stuff on the red stuff | Fri Mar 02 1990 12:06 | 20 |
|
This note has been temporarily write-locked pending approval of the author.
To the author: This subject is already under discussion in this file, under
the topics listed in the title. Please look at these notes; you may find that
your question is already answered, or you may find a note where your question
would be an appropriate continuation of the discussion. Note that since
nearly everyone uses NEXT UNSEEN to read notes, your question will get the
same exposure whether it is a response to a three-year-old note or it is its
own new note. These topics were found using the keyword directory (note 1111),
and you may find other notes relating to this subject by examining the
directory yourself.
We do, however, welcome new notes if they explore a specific aspect of a
problem that may be under general discussion. And this moderator has been
known to make mistakes. :^) So if after examining these notes, you wish to
continue the discussion here, send me mail.
Bruce [Moderator]
|
204.77 | Electrical timer in place of a switch | LAVC::CAHILL | Jim Cahill | Mon May 06 1991 12:29 | 18 |
| Although I've seen a few references to them, I couldn't find a note dedicated
to installing a timer instead of a switch on a bathroom fan.
I'm having a bathroom replaced, and thought a timer would be perfect: you
could leave the fan running for awhile after your shower, and it would shut
itself off after venting the steam from the room. Has anyone installed one
and come across problems? Would you do it again?
Also, how about a source for such a switch?
My present plans are to install the timer in the same box as a regular single
pole switch for a light within the shower. Does the NEC say anything about
such combinations, other than the expected "Don't jam too much into too small
a box!"?
Any feedback or advise would be appreciated.
Jim
|
204.78 | | QUARK::LIONEL | Free advice is worth every cent | Mon May 06 1991 13:13 | 9 |
| Most any place that sells bathroom vent fans will have timer switches that
mount in standard electrical boxes. Nutone and Broan should both have them.
Note that these are standard in many hotel bathrooms.
You probably won't be able to find one that can share a single-box with
another switch, though - you'd need a double-gang box. Perhaps you can cut
out the old box and install an "old-work" double-gang box.
Steve
|
204.79 | Walls are open to the studs | LAVC::CAHILL | Jim Cahill | Mon May 06 1991 16:29 | 9 |
| re .1:
Yes, I was planning on having it installed into at least a double-gang box.
I didn't know if the NEC mentioned anything about reducing the number of
wire-nuts or incoming cables into such a box if a timer was present.
This is all new wiring, so there's no need to cut out old boxes, etc.
Jim
|
204.80 | | QUARK::LIONEL | Free advice is worth every cent | Mon May 06 1991 18:07 | 4 |
| I don't recall seeing anything in the NEC about timers, specifically. They're
no bigger than some kinds of regular switches or outlets.
Steve
|
204.81 | Cubic Inches | EVETPU::MCCARTHY | Well Norm, lets go take a look. | Mon May 06 1991 19:21 | 7 |
| The only thing in the NEC book is cubic-inches. The timer is going to take up
more than a normal switch. Someplace there are spec's on allowances for cubic
inches for each type of device. If the timer takes up more than the allowance
there could be a problem. A two-gang box will just make getting a plate cover
harder. You may want a deep box however.
Brian
|
204.82 | | QUARK::LIONEL | Free advice is worth every cent | Mon May 06 1991 20:00 | 5 |
| Argh, I forgot about the cover plate. You'll never find a two-gang plate that
works with the timer (at least I've never seen one). Maybe you should look
into installing a second single-gang box for the timer.
Steve
|
204.83 | | TOKLAS::feldman | Larix decidua, var. decify | Tue May 07 1991 13:57 | 4 |
| Can't you just use a wooden two-gang cover plate that you carve to meet the
requirements of the timer?
Gary
|
204.84 | A knob with no numbers behind it | DDIF::MCCARTHY | Well Norm, lets go take a look. | Wed May 08 1991 07:59 | 6 |
| Yes carving a wood plate cover is possible. What you have left is a two gang
plate cover with only one side used (does not look good, IMO) and a plate cover
without any "numbers" on how to set the timer (which are on the plate cover
that comes with the timer), confuses guests.
Brian
|
204.85 | Sring wound timer...fits the box. | VCSESU::D_SMITH | | Wed May 08 1991 10:00 | 10 |
|
There are spring wound timers you can get that fit right into the
existing switch box. They were used in appartement washrooms to shut
off lights autmatically. They can be set for up to an hour, and the
cover is brushed aluminum.
approx $10.00 a piece, at Marlboro Electrical Outlet.
Dave'
|
204.86 | this can't be that unusual, folks! | LAVC::CAHILL | Jim Cahill | Thu May 09 1991 19:17 | 15 |
| Thanks for the replies so far, but I can't believe one comment:
.5> You'll never find a two-gang plate that
.5> works with the timer (at least I've never seen one).
What's so unusual about wanting to put a switch and a timer together for a
bathroom light/fan combo? Someone's got to have thought of this, considering
the number of light/fan units sold as well as the other combinations of cover
plates that are available.
If anyone knows of a supplier for such a cover plate (timer/switch), please
post it here. I'm thinking of giving Mass. Gas and Electric a call this
weekend.
Jim
|
204.87 | Couldn't find the plate... | LEVERS::SIDES | | Fri May 10 1991 14:21 | 7 |
| I have to agree with the group that says you won't find the plate; in
my bathroom I have a two gang receptacle for the light and whirlpool
timer. I looked everywhere for a plate with a switch on one side an
timer "hole" on the other. Finally gave up an used a wood plate and
glued the timer plate on top, so I would know how long I was soakin'
Jonathan
|
204.88 | | SYSTMX::BEAN | Attila the Hun was a LIBERAL! | Thu May 23 1991 13:29 | 14 |
| I just installed a fan in one of our bathrooms a couple weeks ago. For
a long time I pondered whether to use just a switch or a timer. I
decided to use a switch... because the timers were expensive ($29.00)
and made noise (they were spring wound). Now I am glad I made the
choice I did... because there doesn't appear to be any need for the fan
to continue running after showering. No fog/steam builds up, and no
need to let it run.
So, a $2.00 switch did the job.
By the way... I was at Somerville to get the fan. They had plates to
cover timer/outlet combinations.
tony
|
204.89 | | LAVC::CAHILL | Jim Cahill | Fri Jun 21 1991 18:04 | 8 |
| > By the way... I was at Somerville to get the fan. They had plates to
> cover timer/outlet combinations.
Timer/outlet, or timer/switch? I need the latter.
I know they exist. I walked into the Littleton town house the other day, and
guess what's mounted just inside the front door?
|
204.22 | Electrical code for bathroom? | ERLANG::MILLER | Steve Miller | Tue Mar 09 1993 12:35 | 15 |
| We are about to remodel our bathroom, and yours truly is the electrical
subcontractor. Yes, I will be getting a permit, have done this, legally
with permit, before.
However, I'm trying to figure out exactly what are the MA code requirements for
a bathroom with a tub/shower (not a whirlpool). Anybody know? I know that I
need a GFI outlet, with anything else downstream. Are lights over the shower
required? What kind? What about location of other lights, switches, etc?
(If I can't find out here, I'll go to the library and try to decipher
the NEC.)
Thanks.
Steve
|
204.23 | | TUXEDO::WRAY | John Wray, Secure Systems Engineering | Wed Mar 10 1993 15:15 | 7 |
| Given that you're getting a permit, talk to your town wire-inspector.
Ours (Chelmsford) was very helpful when I was re-wiring our house
recently. Also, he's the one who will eventually have to interpret the
code when he inspects the job, so it can't hurt to have him interpret
it for you ahead of time.
John
|
204.24 | 2C worth | ELWOOD::DYMON | | Thu Mar 11 1993 07:54 | 6 |
|
I did the bath over myself. In the process, I added new wiring.
To play safe, everything went on 20a wire and a GFI.
JD
|
204.25 | | SALEM::TIMMONS | Where's Waldo? | Wed Mar 17 1993 07:19 | 6 |
| Steve, recently heard on a TOH that Mass requires an exhaust fan in
bathrooms, regardless if a window is present or not. That's the only
time I've heard it, and if it's true, I'm not sure it applies to
remodeling or not. Better check it out.
Lee
|
204.26 | Need One in Mass. | NEMAIL::COLVIN | | Fri Mar 19 1993 13:15 | 12 |
| I just put on an addition on which removed the window from a 1/2 bath
on the first floor. The bad news is that Mass. does require a bathroom
vent for one with no window. The good news is that it does NOT need to
be vented outside. It can have a charcoal filter (like a non-vented
range hood) and circulate the air back into the room. It is supposed to
be on the same switch as the light, so it will be on at all times the
light is on, but an electrician friend says they do that just to pass
the inspection, and then put it on it's own switch. I was going to have
a real hard time running the vent hose until he said a non-vented one
would pass code.
Larry
|
204.27 | | PATE::MACNEAL | ruck `n' roll | Fri Mar 19 1993 16:13 | 2 |
| What purpose does a nonvented fan serve in a bathroom? I thought the
whole purpose of the fan was to vent moisture laden air outside.
|
204.28 | suprise | DAVE::MITTON | Token rings happen | Fri Mar 19 1993 16:22 | 8 |
| By crawling around in my attic, I noted that my bathroom fans are
ducted on the the return plenums for my FHA system. My house was
built in MA about 7 years ago.
Works for me. Now I get to keep the humidity in the house
since there is no humdifier on that zone of my HVAC system. ;-)
Dave.
|
204.29 | Non-Vented Fan in 1/2 Bath | NEMAIL::COLVIN | | Tue Mar 30 1993 14:38 | 7 |
| Re: .5
The bath which now has the non-ducted vent fan is a 1/2 bath, with no
shower or tub. It was actually an electrician who recommended it and I did
not ask him if you could use a non-vented fan in a full bath, also.
Larry
|
204.30 | No license, no permit | ERLANG::MILLER | Steve Miller | Wed Apr 07 1993 18:07 | 19 |
| Re: .*
Well, I spent some time in the library with an annotated copy of
the National Electrical Code, and all I could find specific to a
bathroom was that there has to be a GFI protected outlet (or outlet
downstream from a GFI breaker) near the sink. There are additional
restrictions if you have a whirlpool.
Then I talked to one of the city (Newton) electrical inspectors, and he
told me I needed the GFI outlet, a light with a switch near the entrance,
and a vent fan. But I believe the vent fan requirement and light are
technically part of the general building code, rather than the electrical
code.
The bad news is that they refused to give me, the unlicensed homeowner,
a permit, stating that it is illegal according to state law and that they
no longer will overlook it. Damn!!
Steve
|
204.31 | you can thank the union lobbies for your problem | 20438::MCCARTHY | COMPUTER: end simulation | Thu Apr 08 1993 07:41 | 11 |
|
>>The bad news is that they refused to give me, the unlicensed homeowner,
>>a permit, stating that it is illegal according to state law and that they
>>no longer will overlook it. Damn!!
A permit for the entire bathroom remodel or for the electrical portion of
the remodel?
I don't think this was mentioned but I assume you live in MA.
bjm
|
204.32 | outlaw at work | ELWOOD::DYMON | | Thu Apr 08 1993 09:04 | 9 |
|
.....Permit, smermit! all their after is the money!!!!
And since when is the home owner not allowed to do his electrical
work.. I know the plumbing part your "not supposed too".
I'd worry more about doing it right then getting a permit!
|
204.33 | | SMAUG::FLOWERS | IBM Interconnect Eng. | Thu Apr 08 1993 11:06 | 12 |
| re: doing you'r own electrical work
I've just started looking into doing some of my own electical work... But
getting in touch with town officials is impossible. I've tried for over 2
weeks (I live in Charlton, MA). I finally called the [non-emergency number]
fire department - who told me - that's it's perfectly legal in Mass for
homeowners to do their own wiring... But just before it's covered up, it
has to be inspected by the local electrical inspector.
(Now if only I could get in touch with the inspector).
Dan
|
204.34 | Bureaucratic b.s. | ERLANG::MILLER | Steve Miller | Thu Apr 08 1993 12:25 | 17 |
| RRe: .9
They refused to issue an electrical permit. They did issue the general
permit, on which I listed the general contractor, who has a MA license.
I'm willing to pay the fees ($83.70 for a general permit for $4500) and go
through the inconvenience to make sure everything is done ok, for liability
purposes, and eventual resale of the house. So, in this case, I now have a
licensed electrician doing it.
But I'm p.o'd. In addition to costing me a bunch more money, by refusing
to issue permits to homeowners they drive the homeowner to do it without
the permit, which means without the safety inspection I feel is important
for both current and future residents of the property.
Assinine.
Steve
|
204.35 | you pay! | ELWOOD::DYMON | | Fri Apr 09 1993 08:54 | 6 |
|
...Your tax dollars hard at work! Dosnt it make you feel good!!!
|
204.36 | electrical = plumbing | CACHE::BEAUREGARD | Roger Beauregard | Fri Apr 09 1993 11:09 | 6 |
| I seem to recall either hearing or reading that the 1993 MA code now
prohibits non-licensed persons from doing any wiring. So electrical is
now treated the same as plumbing.
Roger
|
204.37 | bureacracy increases | DAVE::MITTON | Token rings happen | Fri Apr 09 1993 14:29 | 7 |
| RE: .14
Grumble, how do they get these things through?
And I'll repeat a question that I've asked before, what does it take
to become a licenced electrician?
Dave.
|
204.38 | just one person killing themself & the law looks good | 20438::MCCARTHY | COMPUTER: end simulation | Fri Apr 09 1993 21:07 | 19 |
| >> Grumble, how do they get these things through?
The unions lobby (IMO). IBEW (intern. brotherhood of Elec Workers) most likely
lobbied hard for the change. Several years ago a licensed electrician (union or
not) could only pull a permit only if they had either proof for liability
insurance for the work or a signed release from the owner of the property
where the work was going to be done. This insurance was not cheap.
>> And I'll repeat a question that I've asked before, what does it take
>> to become a licensed electrician?
Apprentiship (sp?) for, I think three years working under a master electrian,
taking a course cuts 1 year off of that.
I am doing ALL the work (plumbing, heating and electrical) as I complete the
second floor of my NH house. Saving mega $$$$ - I would not even be able to
change a washer if I was still in MA.
Brian J.
|
204.39 | Who did it?? | ELWOOD::DYMON | | Mon Apr 12 1993 07:48 | 8 |
|
.....And just think. All thoes modular homes that come
for out of state with everything wired and plumbed. Who
was the person that did the work? Some "Joe Average" on
the assembly line.....
JD
|
204.40 | Modular homes: licensed electricians usually do them | SPEZKO::LEMIEUX | | Mon Apr 12 1993 09:22 | 50 |
| Hi,
Modular home builders usually have licensed electrician(s) working on the
production line floor. At least all of the ones I've dealt with have had
them on the staff(I field wire modulars on occasion) ....but there are probably
exceptions where the "apprentices" do all of the work under the "guidance"
of the resident Master.
BTW, a few towns in New Hampshire have gone over to not letting homeowners
do their own wiring. I called the N.H. state electrical board about it. They
stated that in N.H. its up to the town to decide if homeowners can or cannot
pull permits. (The N.H. electrical board had a list of the N.H. towns that
don't allow do it yourself permits if anybody is interested).
RE: a couple notes back, "what does it take to get a license"
In NH:
It takes 4 yrs working FULL TIME (4 X 2000 hrs) under a Master electrician who
documents your time, plus X hours( I forget the exact amount of time,400 hours?)
of schooling at a trade school like the NH Vocational Technical trade school
system or equiv union trade school etc.
Once the above is complete you can apply to take the journeymans test.
Masters license is aquired with more on the job time before applying to take
the Masters test. (it used to be one year plus a journeyman license...
not sure what it is today).
To continue to renew your license, Master or Journeyman, you need 15 hours
certified NEC training every 3 years. Basically every time the code changes.
In NH, Master electrician license is needed to pull permits if you are an
electrician...Journeyman license is not sufficient.
The above info may be out of date a little. The requirements will not be less
than the ones I listed above....
Around New England licensing is pretty easy, 1 license per state. Elsewhere in
the country they have State, County, City licenses. Really makes life difficult
if you have to work over a large area.
Well, thats enough long windedness for today :')
later
Paul
|
204.41 | time to move? | DAVE::MITTON | Token rings happen | Mon Apr 12 1993 11:34 | 16 |
| RE: .18
..hmmm...
Well a trip to the library found me the section of the Mass. General Laws
covering Electrical Licensing and the homeowner exclusion. Now I have
to see if and when it was changed. (Chap 141, Section 1, note 7)
Also according to the "laws" MA Electrical License examinations are held
regularly and public notices must be made. I'll have to get in touch
with the administrators to find out any "fine print" on requirements to
take it.
You are right that just being licensed isn't even enough anymore, to
pull a permit. You must also be insured.
Dave.
|
204.42 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Thu Apr 15 1993 15:06 | 2 |
| I seem to recall that while the ban against amateur plumbers is statewide
in Mass, the ban against amateur electricians is local. This may have changed.
|
204.43 | | VERGA::WELLCOME | Steve Wellcome PKO3-1/D30 | Mon Apr 19 1993 08:50 | 6 |
| I talked to a contractor a few days ago. His understanding is that
a statewide requirement was proposed (only licensed electricians
to do wiring) but hasn't passed yet, and in the meantime it's up
to the discretion of the local wiring inspector; if he wants to
allow homeowner wiring he can, if he doesn't, he can deny permission.
|
204.44 | still looking into this | DAVE::MITTON | Token rings happen | Mon Apr 19 1993 13:04 | 17 |
| RE: .21
Well that may explain why I cannot find a trace of it in the books yet.
Actually, it may not be law so much as it was a State Attorney's
General opinion at one time.
RE: Mass Electricians Licencing Requirements:
...hmmm left my notes it the car.... oh well. as memory serves me:
They are clearly spelled out in the CMR (Commonwealth of Mass. Regulations)
Sect 137 (?). There is a requirement for educational courses (stated
rather awkwardly in clock hours) and years of experience as a learner
or apprentice. Sort of prevents anyone from doing it part time.
I was plesantly surprised to find that the Mass law books were
availible and rather easy to access in my local public libraries.
Dave.
|
204.45 | Phone in bathroom | WEDOIT::DEROSA | Kowalski | Wed Oct 12 1994 12:42 | 16 |
|
I thinking of putting a phone in my bathroom. I got the idea when I
recently stayed in a hotel that had one. Does anyone know if this
violates any code or has any restrictions? I live in Mass.
FYI: Looking in replys to notes after doing a dir/title="phone" did not
give me anything I could use.
Thanks in advance,
/Bob
|
204.46 | done before, but not here | WRKSYS::RICHARDSON | | Wed Oct 12 1994 13:43 | 10 |
| My parents' previous house had a phone in the bathroom when they bought
it. The previous owner was a doctor, and had a phone EVERYWHERE - must
have had 20 phones in there! My father took the bathroom one out. I
don't know if he thought it was a safety hazard or simply didn't need
anywhere near that many phones (removed all but two of them I think).
I don't know if it would be legal in Massachusetts - my folks live in
Indiana. You might need a special phone or grounded jack. Definitely
find out before you bother installing it.
/Charlotte
|
204.47 | how about a cordless? | 12363::JP | Telling tales of Parrotheads and Parties | Wed Oct 12 1994 14:10 | 2 |
| Of course, I'm the type of person that firmly believes there is nothing in the
world so important that it can't wait for me to finish taking a dump.
|
204.48 | | QUARK::LIONEL | Free advice is worth every cent | Wed Oct 12 1994 14:15 | 7 |
| Phones are low voltage - they can be installed in a bathroom with no
additional restrictions (though you'd probably want to keep it away from
the bathtub or sink.)
I would never want a phone in the bathroom, myself.
Steve
|
204.49 | OK in MA, at least up until 3 years ago. | ISLNDS::WHITMORE | | Wed Oct 12 1994 14:23 | 5 |
| A friend of mine recently built a house in MA with a phone jack in the
bathroom. So, at least a few years ago code didn't have a problem with
it.
-dana
|
204.50 | Phone for safety... | ASDG::SBILL | | Wed Oct 12 1994 14:46 | 17 |
|
I remember seeing a commercial a long time ago from the phone company that
strongly suggested a phone line in the bathroom for safety reasons. The
example in the commercial was a woman who left her baby in the bathtub
while she went into another room to answer the phone (not a smart thing to
do in any case) the assumption is that the baby drowned.
I could also see it as a good thing for elderly people to have in case
of a fall. They could call for help without dragging themselves into
another room and complicating injuries.
In other cases it could be just a convenience, you're expecting a VERY
IMPORTANT phone call but you have to go SOOO BAAAAD and you just can't
wait. Just don't flush with the other person on the line, it's not
polite ;-).
Steve B.
|
204.51 | | MILORD::BISHOP | Take hold of the life that is truly life | Wed Oct 12 1994 15:51 | 7 |
| > I could also see it as a good thing for elderly people to have in case
> of a fall. They could call for help without dragging themselves into
> another room and complicating injuries.
Help! I've fallen and I can't get up!!
(Sorry....couldn't resist....)
|
204.52 | You must use a phone designed for the environment | WMOIS::BOUDREAU_C | So take your GreyPoupon my freind... | Wed Oct 12 1994 16:41 | 4 |
| The only code (ethical) problem (restriction) for having a phone in the
Bathroom is it MUST BE a princess model (because you will be using it
while on the throne :*) :*)
|
204.53 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Wed Oct 12 1994 17:54 | 2 |
| With cordless phones, I don't see much need for a dedicated phone in
the bathroom.
|
204.54 | Don't Wall-mount Next to the Throne... | WMOIS::FERRARI_G | | Wed Oct 12 1994 18:00 | 8 |
| I put one in the upstairs bathroom (pre-cordless days), out of
convenience, especially when the little ones were getting their baths.
It's a wall-mount, next to the throne. It _is_ convenient, except for
the time my wife knocked it off the receiver and into the toilet.
Naturally, she didn't tell me and just hung it back up. Well, you
guessed it...I was on the throne, and for once, the phone call was for
me. After an earful of water........
|
204.55 | Flush the telemarketeers? | XLSIOR::OTTE | | Wed Oct 12 1994 18:47 | 4 |
| Actually, having a phone in the bathroom gives you a whole new option
for handling telemarketeers...
-Randy
|
204.56 | Can cause unusual problems... | STRATA::CASSIDY | | Thu Oct 13 1994 08:17 | 5 |
| I don't think phones hold up so well under high humidity. It's
probably not a good idea to install one in a full bath. This according
to a friend who works for Ma Bell.
Tim
|
204.57 | | 2398::BECK | Paul Beck | Thu Oct 13 1994 09:51 | 4 |
| > I don't think phones hold up so well under high humidity. It's
> probably not a good idea to install one in a full bath.
Yeah, at least run the water out first.
|
204.58 | Forget the cordless | CUJO::PADILLA | | Thu Oct 13 1994 13:29 | 4 |
| Remember, we techno-nerds can listen to your cordless calls. This
alone, to me, is reason enough to have a dedicated jack.
|
204.59 | I thought they passed a law... | HNDYMN::MCCARTHY | I'm still not ready | Thu Oct 13 1994 13:44 | 10 |
| >> Remember, we techno-nerds can listen to your cordless calls. This
But isn't that against the law now? Like listening to cellular phone calls? I
thought the law was changed from something about 'its ok as long as you don't
act on what you hear' to 'you just can't do that'.
Newer scanners have blocked out the cellular phone frequencies (but of course
there are ways around that).
bjm
|
204.60 | new cordless phones scramble | TUXEDO::MOLSON | Margaret Olson | Thu Oct 13 1994 14:12 | 3 |
| The newer cordless phones have scrambling to prevent eavesdropping by
nosy technoweenies.
Margaret.
|
204.61 | | NETRIX::michaud | Jeff Michaud, PATHWORKS for Win. NT | Thu Oct 13 1994 14:37 | 12 |
| > The newer cordless phones have scrambling to prevent eavesdropping by
> nosy technoweenies.
But elsewhere in this conference someone indicated that the
technique used to scramble is simply to invert the signal,
and hence a real techoweenie can just invert it again with
their equipment.
Of course real technoweenies can evesdrop just by picking the
RF emmenating from the telephone wire strung throughout your
house using a Van parked outside and a coat hanger and other
inexpensive tecnoweenie goodies. :-)
|
204.62 | Sure install it. | STOWOA::CCALCAGNI | A.F.F.A. | Thu Oct 13 1994 14:52 | 8 |
| When I built my house several years ago I installed jacks all over the
house.
I have a phone in all the bathrooms and have no problems yet. I've
found that even with a portable in the house you don't always drag it
around with you.
Cal
|
204.63 | real scrambling | TUXEDO::MOLSON | Margaret Olson | Thu Oct 13 1994 16:28 | 2 |
| Some portables now have real scrambling. They cost extra.
Margaret.
|
204.64 | technoweenie manufacturers | DAVE::MITTON | Token rings happen | Thu Oct 13 1994 18:12 | 4 |
| ...Cinncinati Microwave sells a cordless phone that does spread
spectrum. Try receiving that with your inverter and coat hanger. ;-)
Dave.
|
204.70 | | CONSLT::MCBRIDE | Reformatted to fit your screen | Mon Oct 16 1995 10:58 | 9 |
| I have a similar unit to the one described in .0 but it is a
Light/Fan/Nightlight unit. I also wish to use three single pole
switches to do this. My question is what type of switches to use,
single pole? What is the proper way to power all three from a common
feed? My understanding was that you should only have one conductor per
terminal. Is the correct way to pigtail three conductors off of the feed
to the switch box?
Brian
|
204.71 | can't use terminals as junctions | HNDYMN::MCCARTHY | A Quinn Martin Production | Mon Oct 16 1995 12:26 | 11 |
| Feed -> wire-nut with three short wires coming off (total of four wires to
wire nut)
One to fan switch
one to light switch
one to nightlight switch
It is against code to use the screw terminals as junctions - you can not use
the 'back-stab' and the screw terminals to do this either.
|
204.72 | ex | CONSLT::MCBRIDE | Reformatted to fit your screen | Mon Oct 16 1995 12:29 | 5 |
| That's what I thought. I also came up with the slighlty less than
brilliant idea of using the terminal and the quick connector on the
back but thought I'd ask first. Thanks for the confirmation!
Brian
|
204.73 | | TEKVAX::KOPEC | we're gonna need another Timmy! | Tue Oct 17 1995 10:17 | 13 |
| What I've found a lot of in my current house (built ca. 1987) is the
feed is looped through the screws; in other words, small sections of
insulation were removed from the incoming feed wire, and these bare
sections were looped around the terminal screws.
I have no idea if this is legal, though I do recall some mention of
doing this for wires in conduit that run through a box in my "wiring
simplified" book..
I think my NEC is lost.. I guess it's time to buy a new one.. Gotta
stop loaning that out..
...tom
|
204.74 | effects of removing the device | HNDYMN::MCCARTHY | A Quinn Martin Production | Tue Oct 17 1995 11:36 | 13 |
| >> I have no idea if this is legal, though I do recall some mention of
Don't think so. I think it has something to do with the ability to remove a
device (switch in this case) without effecting any other portions of the
circut.
In the striped off case, you would have to cut and wire nut the wires - or put
electrical tape on it if the switch was removed.
I have also seen that done but more often have I seen the stab/screw "splice"
used.
Brian
|
204.75 | | SHRMSG::BUSKY | | Tue Oct 17 1995 12:01 | 10 |
| > It is against code to use the screw terminals as junctions - you can not use
So... it's against code to use the pair of screws on outlets to
feed the outlet and then the next device down the line?
I can see the problem and issue with two wires under one screw,
but 99% of the installations I've seen, use the pair of outlet
screws as described above.
Charly
|
204.76 | I knew someone was going to bring that up | HNDYMN::MCCARTHY | A Quinn Martin Production | Tue Oct 17 1995 12:32 | 12 |
| >> So... it's against code to use the pair of screws on outlets to
>> feed the outlet and then the next device down the line?
another clause - "unless specificly intended". Or something like that. It was
described to me many years ago - and I don't think its changed. Feed-though
outlets are designed to do this. The little tab can be broken off to break the
connection between the two terminals.
I've seen both screws AND the stab-connector on an receptical used as a
splice - that's a no-go.
bjm
|
204.90 | Whirlpool Wiring/Shower Light | JOKUR::MCCONNEY | I'm a M.D. = Music Director | Thu Apr 11 1996 10:42 | 14 |
| I'm in the process of doing some electrical work on my new bathroom.
Does anyone have any experience wiring for a whirlpool tub? I did a
search in the whirlpool/hot tub note and found nothing specifically
about the wiring. I'm interested in knowing if there should be any
GFCI concerns, emergency switches, etc.
Also, I'm installing a light in the shower that is made for this
purpose (rubber seal, and so forth). Should this light be on a GFCI
circuit?
I appreciate any help on these two questions.
Thanks, Chip
|
204.91 | GFCI..YES!! | 11666::BWHITE | | Thu Apr 11 1996 11:02 | 5 |
| most definitely both should be on GFCI circuits....when my whirlpool
was installed, the electrician put the whirlpool on it's own separate
GFCI circuit at the panel. Also, the on/off/timer switch for the
whirlpool was positioned in the bathroom so that it could not be
used while you are standing in the whirlpool....
|
204.92 | questioning the need for the light | HNDYMN::MCCARTHY | A Quinn Martin Production | Thu Apr 11 1996 12:03 | 7 |
| I don't think the recessed lights in showers need to be GFCI protected. The
ceiling would have to fall for the unit to come in contact with you. But I
don't have a code book in front of me.
Yes to the Whirlpool though.
bjm
|
204.93 | | 2082::LIONEL | Free advice is worth every cent | Thu Apr 11 1996 13:41 | 6 |
| I agree - in fact, the light should not be on a GFCI. The whirlpool's
installation instructions should be very clear as to the wiring requirements.
These will include GFCI protection and a grounding wire to a copper water
pipe.
Steve
|
204.94 | | JOKUR::MCCONNEY | I'm a M.D. = Music Director | Thu Apr 11 1996 14:22 | 3 |
| Thanks for the tips thus far. Unfortunately, I bought the whirlpool
tub used so I don't have instructions. Any other requirements that
you can think of would be appreciated. Thanks!
|
204.95 | Against code to do so? | VAXCPU::michaud | Jeff Michaud - ObjectBroker | Thu Apr 11 1996 15:16 | 3 |
| > I agree - in fact, the light should not be on a GFCI.
Why?
|
204.96 | Try asking manufacturer? | STAR::DZIEDZIC | Tony Dziedzic - DTN 381-2438 | Thu Apr 11 1996 15:16 | 10 |
| Re .94:
How about the obvious - if you can determine who manufactured the
whirlpool tub, call THEM and ask for specifics. You should be
able to get a copy of the installation instructions. You could
also try asking the electrical inspector - he'd know the local
interpretation of the N.E.C. as it applies to the tubs.
I'd go that route first rather than depending on the well-meant
(but possibly incomplete) information you get in this conference.
|
204.97 | | 19096::BUSKY | | Thu Apr 11 1996 16:08 | 11 |
| > > I agree - in fact, the light should not be on a GFCI.
> Why?
It's a saftey issue!
Say you're taking a nice soak in the hot tub some night and the
GFCI trips, if the lights were on the same GFCI circuit, you'd be
sitting there in the dark in a wet slippery tub/bath room.
Charly
|
204.98 | | JOKUR::MCCONNEY | I'm a M.D. = Music Director | Thu Apr 11 1996 16:56 | 11 |
| >if the lights were on the same GFCI circuit,
The tub should be on it's very own circuit. Besides, the shower
light usually is used to illuminate the shower only, not the room.
Maybe there's another reason? Actually, I don't see any harm in putting
the shower light on a GFCI circuit, provided it's not tied into other
lights in the room or the tub (?)
Getting instructions from the manufacturer of the tub is a good
idea - I'll do that. Thanks.
|
204.99 | Or does this only apply when you have electrically powered tubs? | VAXCPU::michaud | Jeff Michaud - ObjectBroker | Thu Apr 11 1996 19:06 | 6 |
| Well the light I put into my bath is part of a bath fan/light
combo that is specifically rated for "wet" locations and the
instructions said it should go on a GFCI circuit/leg.
I'm just curious if my local codes (cause Steve also lives in
Nashua) differ from the manufacturs instructions.
|
204.100 | | 2082::LIONEL | Free advice is worth every cent | Thu Apr 11 1996 20:42 | 15 |
| I don't remember where I read that lights should not be on a GFCI, but
it was indeed because if it trips the light goes out, and that lights
are not typically a shock hazard. If there is some other light in the
room not on a GFCI, that would be fine.
Definitely get the manufacturer's instructions for installing the tub.
Typically you will need a dedicated 30A, 240V circuit (that means #10
wire) and a GFCI rated for 30A. (You may have a unit that will run on
a 20A circuit.) High-current GFCIs are not cheap. You'll need a
separate #8 bare wire that is bonded to the appropriate chassis lug on
the tub and to a copper cold-water pipe (which is electrically
uninterrrupted to the water supply. Check with your local electrical
inspector for any additional requirements.
Steve
|
204.101 | Light is IN the shower | 11666::BWHITE | | Fri Apr 12 1996 11:20 | 14 |
| I again state that the light should be GFCI protected...if you re-read
the original request for info in .90 - the light in question is IN THE
SHOWER!! I agree that normally you would not have to protect ceiling
fixtures in a normal bathroom...
AS for the whirlpool wiring, I have never seen a whirlpool that
requires 240V....jacuzzis or hot tubs that require heaters would, but
whirlpool refers to basically baths that you fill for every usage with
jets. I have the largest whirlpool that I know of sold, 5 x 7, and it
only requires a 1 hp pump wired at 120V. Since the tub is fiberglass,
there was no recommedation to have a separate ground directly to a
water pipe as described in -1. The wiring is standard 3-wire, separate
20A circuit, separate GFCI at panel.
I do go along with the idea of trying to get the manufacturers
installation instructions.
|
204.102 | More on whirlpool | BIGQ::BERNIER | | Mon Apr 15 1996 03:31 | 9 |
| I have and American Standard whirlpool that is 4 x 6. It also has
1HP pump wired at 120V. The wiring is standard 12/3 wire with a
20A separate circuit GFCI at panel.
There are two recessed lights over it. The switch for the lights is
wired with the rest of the bedroom (The whirlpool is in the bedroom)
and located on an opposite wall on a dimmer which cannot be reached
from the tub.
[EOB]
|
204.103 | Info on Whirlpool | JOKUR::MCCONNEY | I'm a M.D. = Music Director | Tue Apr 16 1996 11:44 | 17 |
| After doing some research in code books, I learned that the recessed
light in the shower must be the type specifically made for showers
(rubber seal) and requires GFCI protection. They make a GFCI unit that
contains an outlet and a switch - I'll use this switch for the shower
light. The code book DID say that "hanging" light fixtures can not be
over or within 3 feet of the bathtub/shower. This information was in a
recent update to the code book.
My whirlpool tub is an American Standard and the numbers on the motor
are as follows:
3/4 Hp
115V
60 Hz
14 Amps
So, will a separate 20A GFCI circuit be adequate?
|
204.104 | | 2082::LIONEL | Free advice is worth every cent | Tue Apr 16 1996 13:57 | 5 |
| Yes, a separate 20A GFCI-protected circuit will be fine. You should use
an "outlet-style" GFCI with the reset available in the bathroom rather than
one on the breaker panel.
Steve
|
204.105 | Breaker or Outlet GFCI? | JOKUR::MCCONNEY | I'm a M.D. = Music Director | Tue Apr 16 1996 14:12 | 6 |
| re>You should use an "outlet-style" GFCI with the reset available in
the bathroom rather than one on the breaker panel.
Thanks Steve, but is having the reset in the bathroom strictly a
convenience issue?
|
204.106 | go with GFCI in panel | 11666::BWHITE | | Tue Apr 16 1996 15:31 | 7 |
| dont know why you wouldnt put the GFCI in the panel - separate circuit.
Remember, we are talking a whirlpool here. If you use the
"outlet-style", the outlet will most likely be enclosed in the
whirlpool frame and not easily accessible. Also, running a connection
from the pump to an outlet is one more exposed connection underneath
an area that has the possibility for water contact (leakage, etc.)
|
204.107 | | 2082::LIONEL | Free advice is worth every cent | Tue Apr 16 1996 16:36 | 12 |
| My reasoning is as follows:
1. Convenience should it trip. (I figured the GFCI would be mounted on a
wall in the bathroom, out of reach of the tub.)
2. Breaker-box GFCIs are more prone to false tripping - partly due to
the length of wire between them and the load. The GFCI breaker on
my spa (60A!) trips randomly 1-2 times a week (and I know there is
no actual fault.) But there is some 70 feet of wire between the
GFCI and the spa.
Steve
|
204.108 | | JOKUR::MCCONNEY | I'm a M.D. = Music Director | Tue Apr 16 1996 17:31 | 8 |
| re>The GFCI breaker on my spa (60A!) trips randomly 1-2 times a week
You're right, a friend did mention that the breaker GFCI was very
sensitive. I'll just mount a GFCI outlet behind the access panel and
wire the tub into that. Besides, the price of the breaker was
approximately $35 compared to the $16 GFCI outlet so...
Thanks again.
|
204.109 | | 19096::BUSKY | | Tue Apr 16 1996 22:31 | 12 |
| > sensitive. I'll just mount a GFCI outlet behind the access panel and
> wire the tub into that. Besides, the price of the breaker was
Why hide it behind an access panel, put it on a wall away from the
tub where it can be seen and used. If this is a full bath, then
place it near the sink for hair dryers, razors, etc. If it's not a
bath but a hot tub room, then put the outlet some place that'll be
convient for a radio or TV that you might have in there.
Charly
|
204.110 | Outlet-sized "non-outlet" GFCI | STAR::DZIEDZIC | Tony Dziedzic - DTN 381-2438 | Wed Apr 17 1996 08:32 | 10 |
| FWIW, last night I saw a GFCI "non-outlet" at Home Depot. It's
the same size and shape of a standard rectangular GFCI outlet,
but has only the test and reset buttons - no outlets. It looks
to be intended for use as an easily-accessible alternative for
a direct-wired appliance and panel-mounted GFCI breaker.
This would probably be more appropriate for the case of a single
appliance permanently connected to a dedicated circuit; using a
standard GFCI outlet as was suggested in .109 makes more sense
if you intend to share the circuit.
|
204.111 | | JOKUR::MCCONNEY | I'm a M.D. = Music Director | Thu Apr 18 1996 12:26 | 7 |
| re>GFCI "non-outlet
That's an excellent suggestion, THANKS! I didn't want to put
another outlet in the room so this solves all my concerns.
Thanks to all for your input.
Chip
|
204.112 | | MAET11::SEGER | This space intentionally left blank | Tue Apr 23 1996 13:04 | 10 |
| a litte late on this string, but...
when I did my bathroon (new construction), since I had to put in an outlet and
it needed to be GFCI, I simply tied my whilpool into that! While I was at it,
I also ran the circuit to a couple outside outlets as well. Having already put
in something like 8 separate circuits in my kitchen my 200 amp box was filling
quickly and figuring the likelihood of using the tub at the same time as an
outlet were slim enough not to care.
-mark
|